• Re: Catenary design

    From Ulf Kutzner@user2991@newsgrouper.org.invalid to uk.railway on Sun Nov 8 08:38:55 2026
    From Newsgroup: uk.railway

    Graeme Wall <rail@greywall.demon.co.uk> posted:

    On 07/11/2026 16:28, boltar@caprica.universe wrote:
    On Sat, 07 Nov 2026 14:47:57 +0100
    Marc Van Dyck <marc.gr.vandyck@invalid.skynet.be> gabbled:
    Bob has brought this to us :
    On 05/11/2026 18:26, Scott wrote:
    Returning from London last week, I ran out of scenery to watch so
    started looking at the overhead line equipment instead. I can remember >>>> a long time ago there being two horizontal cables, one suspended below >>>> the other. What was the point of this and why was it discontinued?

    On some installations, notably on the GE routes, there was compound
    catenery,
    with a second support wire between the main support wire and the
    contact wire. This was used on lines originally wired for 1500 V DC
    because the much

    lower voltage meant a much higher current and consequently a
    significantly larger/heavier contact wire. With the switch to 25 kV,
    the thickness of wire

    needed was much reduced, and consequently the weight did not require
    the added support of the secondary support wire. When the routes
    originally
    wired
    for 1500 V DC were converted, initially to a mix of 25 kV and 6.25
    kV, then the 6.25 being eliminated for a uniform 25 kV, initially the >>> old 1500 V
    wires
    were retained with larger insulators. The originally 1500 V wiring of >>> the Shenfield scheme was entirely replaced a few years ago,
    eliminating the old compound catenery.

    Robin

    Compound catenary today is only used on DC 1500 and 3000 V territory
    in Belgium and France. Other countries using DC (Netherlands, Spain,
    Italy) do not use it.

    Perhaps I'm being thick but how does it work? Unless you have offset pantographs how can you have 2 voltage wires without risking a train getting
    the wrong voltage?


    You don't have both at the same time, it's either/or. Also a 3kV train
    can operate on 1.5kV but not the other way round.

    You could see that at Modane station with Italian locos.

    Recent ones need to be told half of the voltage is still okay to operate.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From boltar@boltar@caprica.universe to uk.railway on Sun Nov 8 09:13:51 2026
    From Newsgroup: uk.railway

    On Sun, 08 Nov 2026 08:38:55 GMT
    Ulf Kutzner <user2991@newsgrouper.org.invalid> gabbled:
    Graeme Wall <rail@greywall.demon.co.uk> posted:
    You don't have both at the same time, it's either/or. Also a 3kV train
    can operate on 1.5kV but not the other way round.

    You could see that at Modane station with Italian locos.

    Recent ones need to be told half of the voltage is still okay to operate.

    I'm not an electrical expert, but sometimes if you lower a voltage the
    current draw goes up and this can cause stuff to burn out. Is this not a
    risk with a 3KV loco running on 1.5KV?

    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Ulf Kutzner@user2991@newsgrouper.org.invalid to uk.railway on Sun Nov 8 09:52:02 2026
    From Newsgroup: uk.railway

    boltar@caprica.universe posted:

    On Sun, 08 Nov 2026 08:38:55 GMT
    Ulf Kutzner <user2991@newsgrouper.org.invalid> gabbled:
    Graeme Wall <rail@greywall.demon.co.uk> posted:
    You don't have both at the same time, it's either/or. Also a 3kV train
    can operate on 1.5kV but not the other way round.

    You could see that at Modane station with Italian locos.

    Recent ones need to be told half of the voltage is still okay to operate.

    I'm not an electrical expert, but sometimes if you lower a voltage the current draw goes up and this can cause stuff to burn out. Is this not a
    risk with a 3KV loco running on 1.5KV?

    IIRC, FS-headed freight trains out of Modane got rear SNCF helpers
    for the re-start of the trip.

    Regards, ULF
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Charles Ellson@charlesellson@btinternet.com to uk.railway on Mon Nov 9 00:47:08 2026
    From Newsgroup: uk.railway

    On Sun, 8 Nov 2026 09:13:51 -0000 (UTC), boltar@caprica.universe
    wrote:

    On Sun, 08 Nov 2026 08:38:55 GMT
    Ulf Kutzner <user2991@newsgrouper.org.invalid> gabbled:
    Graeme Wall <rail@greywall.demon.co.uk> posted:
    You don't have both at the same time, it's either/or. Also a 3kV train
    can operate on 1.5kV but not the other way round.

    You could see that at Modane station with Italian locos.

    Recent ones need to be told half of the voltage is still okay to operate.

    I'm not an electrical expert, but sometimes if you lower a voltage the >current draw goes up and this can cause stuff to burn out. Is this not a
    risk with a 3KV loco running on 1.5KV?

    Not unless there is no current-based overload protection to kick in if
    the motors take an "infinite" load. On third rail you have shoe fuses
    and OH trains would presumably have something similar. When a cl.501
    did a farewell tour of the Southern Region running on higher voltage
    it was alleged to have blown a couple of shoe fuses while travelling
    at up to 80mph. On a straight DC train with no fancy electronics a
    lower voltage will reduce the current that can be drawn.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Scott@newsgroups@gefion.myzen.co.uk to uk.railway on Mon Nov 9 10:29:29 2026
    From Newsgroup: uk.railway

    On Thu, 5 Nov 2026 21:49:54 +0100, Bob <nospam@gmail.com> wrote:

    On 05/11/2026 18:26, Scott wrote:
    Returning from London last week, I ran out of scenery to watch so
    started looking at the overhead line equipment instead. I can remember
    a long time ago there being two horizontal cables, one suspended below
    the other. What was the point of this and why was it discontinued?

    On some installations, notably on the GE routes, there was compound >catenery, with a second support wire between the main support wire and
    the contact wire. This was used on lines originally wired for 1500 V DC >because the much lower voltage meant a much higher current and
    consequently a significantly larger/heavier contact wire. With the
    switch to 25 kV, the thickness of wire needed was much reduced, and >consequently the weight did not require the added support of the
    secondary support wire. When the routes originally wired for 1500 V DC
    were converted, initially to a mix of 25 kV and 6.25 kV, then the 6.25
    being eliminated for a uniform 25 kV, initially the old 1500 V wires
    were retained with larger insulators. The originally 1500 V wiring of
    the Shenfield scheme was entirely replaced a few years ago, eliminating
    the old compound catenery.

    I thought compound catenary was used on the WCML (25 kV AC) at the
    start of electrification. I thought, but could be wrong, that standard
    catenary was employed in the Glasgow suburban area then compound for
    higher speeds. I am wondering why they did this at all when it seems
    to be unnecessary. Maybe it was similar to dropping the voltage in
    tunnels, which has also subsequently turned out to be unnecessary.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Nick Finnigan@nix@genie.co.uk to uk.railway on Mon Nov 9 13:46:08 2026
    From Newsgroup: uk.railway

    On 09/11/2026 10:29, Scott wrote:
    On Thu, 5 Nov 2026 21:49:54 +0100, Bob <nospam@gmail.com> wrote:

    On 05/11/2026 18:26, Scott wrote:
    Returning from London last week, I ran out of scenery to watch so
    started looking at the overhead line equipment instead. I can remember
    a long time ago there being two horizontal cables, one suspended below
    the other. What was the point of this and why was it discontinued?

    On some installations, notably on the GE routes, there was compound
    catenery, with a second support wire between the main support wire and
    the contact wire. This was used on lines originally wired for 1500 V DC
    because the much lower voltage meant a much higher current and
    consequently a significantly larger/heavier contact wire. With the
    switch to 25 kV, the thickness of wire needed was much reduced, and
    consequently the weight did not require the added support of the
    secondary support wire. When the routes originally wired for 1500 V DC
    were converted, initially to a mix of 25 kV and 6.25 kV, then the 6.25
    being eliminated for a uniform 25 kV, initially the old 1500 V wires
    were retained with larger insulators. The originally 1500 V wiring of
    the Shenfield scheme was entirely replaced a few years ago, eliminating
    the old compound catenery.

    I thought compound catenary was used on the WCML (25 kV AC) at the
    start of electrification. I thought, but could be wrong, that standard catenary was employed in the Glasgow suburban area then compound for
    higher speeds. I am wondering why they did this at all when it seems
    to be unnecessary. Maybe it was similar to dropping the voltage in
    tunnels, which has also subsequently turned out to be unnecessary.

    10 years may be a long time, but the Blackpool electrification seems to
    have a compound catenary (e.g. level crossing in Carleton).
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Scott@newsgroups@gefion.myzen.co.uk to uk.railway on Mon Nov 9 14:14:14 2026
    From Newsgroup: uk.railway

    On Mon, 9 Nov 2026 13:46:08 +0000, Nick Finnigan <nix@genie.co.uk>
    wrote:

    On 09/11/2026 10:29, Scott wrote:
    On Thu, 5 Nov 2026 21:49:54 +0100, Bob <nospam@gmail.com> wrote:

    On 05/11/2026 18:26, Scott wrote:
    Returning from London last week, I ran out of scenery to watch so
    started looking at the overhead line equipment instead. I can remember >>>> a long time ago there being two horizontal cables, one suspended below >>>> the other. What was the point of this and why was it discontinued?

    On some installations, notably on the GE routes, there was compound
    catenery, with a second support wire between the main support wire and
    the contact wire. This was used on lines originally wired for 1500 V DC
    because the much lower voltage meant a much higher current and
    consequently a significantly larger/heavier contact wire. With the
    switch to 25 kV, the thickness of wire needed was much reduced, and
    consequently the weight did not require the added support of the
    secondary support wire. When the routes originally wired for 1500 V DC
    were converted, initially to a mix of 25 kV and 6.25 kV, then the 6.25
    being eliminated for a uniform 25 kV, initially the old 1500 V wires
    were retained with larger insulators. The originally 1500 V wiring of
    the Shenfield scheme was entirely replaced a few years ago, eliminating
    the old compound catenery.

    I thought compound catenary was used on the WCML (25 kV AC) at the
    start of electrification. I thought, but could be wrong, that standard
    catenary was employed in the Glasgow suburban area then compound for
    higher speeds. I am wondering why they did this at all when it seems
    to be unnecessary. Maybe it was similar to dropping the voltage in
    tunnels, which has also subsequently turned out to be unnecessary.

    10 years may be a long time, but the Blackpool electrification seems to
    have a compound catenary (e.g. level crossing in Carleton).

    We may be at cross purposes here. I was talking about two horizontal
    cables, one suspended below the other mile after mile.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Ulf Kutzner@user2991@newsgrouper.org.invalid to uk.railway on Mon Nov 9 14:20:56 2026
    From Newsgroup: uk.railway

    Marc Van Dyck <marc.gr.vandyck@invalid.skynet.be> posted:

    Bob has brought this to us :
    On 05/11/2026 18:26, Scott wrote:
    Returning from London last week, I ran out of scenery to watch so
    started looking at the overhead line equipment instead. I can remember
    a long time ago there being two horizontal cables, one suspended below
    the other. What was the point of this and why was it discontinued?

    On some installations, notably on the GE routes, there was compound catenery,
    with a second support wire between the main support wire and the contact wire. This was used on lines originally wired for 1500 V DC because the much
    lower voltage meant a much higher current and consequently a significantly larger/heavier contact wire. With the switch to 25 kV, the thickness of wire
    needed was much reduced, and consequently the weight did not require the added support of the secondary support wire. When the routes originally wired
    for 1500 V DC were converted, initially to a mix of 25 kV and 6.25 kV, then
    the 6.25 being eliminated for a uniform 25 kV, initially the old 1500 V wires
    were retained with larger insulators. The originally 1500 V wiring of the Shenfield scheme was entirely replaced a few years ago, eliminating the old
    compound catenery.


    Compound catenary today is only used on DC 1500 and 3000 V territory
    in Belgium and France. Other countries using DC (Netherlands, Spain,
    Italy) do not use it.

    Other countries seem to use it: https://upload.wikimedia.org/wikipedia/commons/a/a4/RZD_VL10U-922_2008-05_Sheremetyevskaya_1210441844.JPG?utm_source=commons.wikimedia.org&utm_campaign=imageinfo&utm_content=original

    Regards, ULF
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Anna Noyd-Dryver@anna@noyd-dryver.com to uk.railway on Mon Nov 9 14:23:33 2026
    From Newsgroup: uk.railway

    Nick Finnigan <nix@genie.co.uk> wrote:
    On 09/11/2026 10:29, Scott wrote:
    On Thu, 5 Nov 2026 21:49:54 +0100, Bob <nospam@gmail.com> wrote:

    On 05/11/2026 18:26, Scott wrote:
    Returning from London last week, I ran out of scenery to watch so
    started looking at the overhead line equipment instead. I can remember >>>> a long time ago there being two horizontal cables, one suspended below >>>> the other. What was the point of this and why was it discontinued?

    On some installations, notably on the GE routes, there was compound
    catenery, with a second support wire between the main support wire and
    the contact wire. This was used on lines originally wired for 1500 V DC
    because the much lower voltage meant a much higher current and
    consequently a significantly larger/heavier contact wire. With the
    switch to 25 kV, the thickness of wire needed was much reduced, and
    consequently the weight did not require the added support of the
    secondary support wire. When the routes originally wired for 1500 V DC
    were converted, initially to a mix of 25 kV and 6.25 kV, then the 6.25
    being eliminated for a uniform 25 kV, initially the old 1500 V wires
    were retained with larger insulators. The originally 1500 V wiring of
    the Shenfield scheme was entirely replaced a few years ago, eliminating
    the old compound catenery.

    I thought compound catenary was used on the WCML (25 kV AC) at the
    start of electrification. I thought, but could be wrong, that standard
    catenary was employed in the Glasgow suburban area then compound for
    higher speeds. I am wondering why they did this at all when it seems
    to be unnecessary. Maybe it was similar to dropping the voltage in
    tunnels, which has also subsequently turned out to be unnecessary.

    10 years may be a long time, but the Blackpool electrification seems to have a compound catenary (e.g. level crossing in Carleton).


    Google maps shows ordinary OLE there - contact wire plus catenary wire <https://maps.app.goo.gl/TwL5oxAsrEUoy9H49>

    Compound catenary OLE looks like this <https://www.eeeguide.com/wp-content/uploads/2023/07/Compound-Catenary-Construction-03.jpg>