• 1) Moving toilet 2) Shared soil pipes

    From nospam@nospam@please.invalid (AnthonyL) to uk.d-i-y on Mon Sep 28 20:50:49 2026
    From Newsgroup: uk.d-i-y

    Bathroom refurb and advice needed on several fronts concerning:

    1) Is Building Control required?
    2) Is any change necessary to the existing shared soil pipe
    arrangement.

    All the properties on this estate are 1968 build bungalows. It seems
    as if there is only one soil pipe on every other property. We don't
    have a soil pipe, but next door does and our sewage goes from the
    inspection pit, down the driveway a bit, then goes across at an angle
    (all downhill slopes) to join an inspection pit on the neighbours
    path.

    Our toilet is against the wall on the side adjacent to our driveway
    and the trench goes at about 45 deg angle to the inspection pit about
    2.5m away on the far side of the driveway.

    We want to move the toilet across the bathroom* and a couple of metres
    inside. This will require a new trench which will now be directly
    opposite the inspection pit and hence shorter than the old trench.

    The builder says we need our own soil pipe. I don't see why as
    nothing has fundamentally changed. It's been ok for nearly 60 years
    and at best they are unsightly. Who's right.

    The builder has not mentioned any Building Regs. Work is due to start
    in 3 weeks. Are approvals needed?

    * We (SWMBO) want the bath across the exterior wall instead of backing
    to it aligned with the l/hand wall, but the toilet is in the r/h
    corner. So put the bath across (90deg rotation), put the toilet on
    the l/h wall adjacent to the side of the bath and run a pipe to the
    outside to a new trench.
    --
    AnthonyL

    Why ever wait to finish a job before starting the next?
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Roger Hayter@roger@hayter.org to uk.d-i-y on Mon Sep 28 21:26:34 2026
    From Newsgroup: uk.d-i-y

    On 28 Sep 2026 at 21:50:49 BST, "AnthonyL" <AnthonyL> wrote:

    Bathroom refurb and advice needed on several fronts concerning:

    1) Is Building Control required?
    2) Is any change necessary to the existing shared soil pipe
    arrangement.

    All the properties on this estate are 1968 build bungalows. It seems
    as if there is only one soil pipe on every other property. We don't
    have a soil pipe, but next door does and our sewage goes from the
    inspection pit, down the driveway a bit, then goes across at an angle
    (all downhill slopes) to join an inspection pit on the neighbours
    path.

    Our toilet is against the wall on the side adjacent to our driveway
    and the trench goes at about 45 deg angle to the inspection pit about
    2.5m away on the far side of the driveway.

    We want to move the toilet across the bathroom* and a couple of metres inside. This will require a new trench which will now be directly
    opposite the inspection pit and hence shorter than the old trench.

    The builder says we need our own soil pipe. I don't see why as
    nothing has fundamentally changed. It's been ok for nearly 60 years
    and at best they are unsightly. Who's right.

    The builder has not mentioned any Building Regs. Work is due to start
    in 3 weeks. Are approvals needed?

    * We (SWMBO) want the bath across the exterior wall instead of backing
    to it aligned with the l/hand wall, but the toilet is in the r/h
    corner. So put the bath across (90deg rotation), put the toilet on
    the l/h wall adjacent to the side of the bath and run a pipe to the
    outside to a new trench.

    How does water from the bath, kitchen and washing machine get to the soil
    pipe? And will it have to go further?
    --

    Roger Hayter
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Andy Burns@usenet@andyburns.uk to uk.d-i-y on Mon Sep 28 22:48:38 2026
    From Newsgroup: uk.d-i-y

    AnthonyL wrote:

    All the properties on this estate are 1968 build bungalows. It seems
    as if there is only one soil pipe on every other property.

    sounds like from the point the pipe crosses your boundary to the
    neighbour, the pipe becomes the responsibility of the water co (STW?)


    <https://www.stwater.co.uk/my-supply/wastewater/sewer-pipe-responsibility/>

    We don't
    have a soil pipe, but next door does and our sewage goes from the
    inspection pit, down the driveway a bit, then goes across at an angle
    (all downhill slopes) to join an inspection pit on the neighbours
    path.

    Our toilet is against the wall on the side adjacent to our driveway
    and the trench goes at about 45 deg angle to the inspection pit about
    2.5m away on the far side of the driveway.

    We want to move the toilet across the bathroom* and a couple of metres inside. This will require a new trench which will now be directly
    opposite the inspection pit and hence shorter than the old trench.

    The builder says we need our own soil pipe.

    Have they considered a "durgo valve"?

    I don't see why as
    nothing has fundamentally changed. It's been ok for nearly 60 years
    and at best they are unsightly. Who's right.

    The builder has not mentioned any Building Regs. Work is due to start
    in 3 weeks. Are approvals needed?
    I think so, see highlighted section ...

    <https://www.travisperkins.co.uk/content/building-regulations/part-h#:~:text=Do,inspector%2E>
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From nospam@nospam@please.invalid (AnthonyL) to uk.d-i-y on Tue Sep 29 18:53:16 2026
    From Newsgroup: uk.d-i-y

    On 28 Sep 2026 21:26:34 GMT, Roger Hayter <roger@hayter.org> wrote:

    On 28 Sep 2026 at 21:50:49 BST, "AnthonyL" <AnthonyL> wrote:

    Bathroom refurb and advice needed on several fronts concerning:

    1) Is Building Control required?
    2) Is any change necessary to the existing shared soil pipe
    arrangement.

    All the properties on this estate are 1968 build bungalows. It seems
    as if there is only one soil pipe on every other property. We don't
    have a soil pipe, but next door does and our sewage goes from the
    inspection pit, down the driveway a bit, then goes across at an angle
    (all downhill slopes) to join an inspection pit on the neighbours
    path.

    Our toilet is against the wall on the side adjacent to our driveway
    and the trench goes at about 45 deg angle to the inspection pit about
    2.5m away on the far side of the driveway.

    We want to move the toilet across the bathroom* and a couple of metres
    inside. This will require a new trench which will now be directly
    opposite the inspection pit and hence shorter than the old trench.

    The builder says we need our own soil pipe. I don't see why as
    nothing has fundamentally changed. It's been ok for nearly 60 years
    and at best they are unsightly. Who's right.

    The builder has not mentioned any Building Regs. Work is due to start
    in 3 weeks. Are approvals needed?

    * We (SWMBO) want the bath across the exterior wall instead of backing
    to it aligned with the l/hand wall, but the toilet is in the r/h
    corner. So put the bath across (90deg rotation), put the toilet on
    the l/h wall adjacent to the side of the bath and run a pipe to the
    outside to a new trench.

    How does water from the bath, kitchen and washing machine get to the soil >pipe? And will it have to go further?


    Photos including the existing toilet inside, immediately outside, and
    further back showing the general layout of the inspection positions
    and the shared soil pipe are at https://flic.kr/s/aHBqjA8aE8

    Hopefully all fairly self-explanatory.
    --
    AnthonyL

    Why ever wait to finish a job before starting the next?
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Roger Hayter@roger@hayter.org to uk.d-i-y on Wed Sep 30 08:19:42 2026
    From Newsgroup: uk.d-i-y

    On 29 Sep 2026 at 19:53:16 BST, "AnthonyL" <AnthonyL> wrote:

    On 28 Sep 2026 21:26:34 GMT, Roger Hayter <roger@hayter.org> wrote:

    On 28 Sep 2026 at 21:50:49 BST, "AnthonyL" <AnthonyL> wrote:

    Bathroom refurb and advice needed on several fronts concerning:

    1) Is Building Control required?
    2) Is any change necessary to the existing shared soil pipe
    arrangement.

    All the properties on this estate are 1968 build bungalows. It seems
    as if there is only one soil pipe on every other property. We don't
    have a soil pipe, but next door does and our sewage goes from the
    inspection pit, down the driveway a bit, then goes across at an angle
    (all downhill slopes) to join an inspection pit on the neighbours
    path.

    Our toilet is against the wall on the side adjacent to our driveway
    and the trench goes at about 45 deg angle to the inspection pit about
    2.5m away on the far side of the driveway.

    We want to move the toilet across the bathroom* and a couple of metres
    inside. This will require a new trench which will now be directly
    opposite the inspection pit and hence shorter than the old trench.

    The builder says we need our own soil pipe. I don't see why as
    nothing has fundamentally changed. It's been ok for nearly 60 years
    and at best they are unsightly. Who's right.

    The builder has not mentioned any Building Regs. Work is due to start
    in 3 weeks. Are approvals needed?

    * We (SWMBO) want the bath across the exterior wall instead of backing
    to it aligned with the l/hand wall, but the toilet is in the r/h
    corner. So put the bath across (90deg rotation), put the toilet on
    the l/h wall adjacent to the side of the bath and run a pipe to the
    outside to a new trench.

    How does water from the bath, kitchen and washing machine get to the soil
    pipe? And will it have to go further?


    Photos including the existing toilet inside, immediately outside, and
    further back showing the general layout of the inspection positions
    and the shared soil pipe are at https://flic.kr/s/aHBqjA8aE8

    Hopefully all fairly self-explanatory.

    I agree it looks as though it will probably work ok as it is so near the inspection chamber, but you may have to find another builder if the existing one interprets the regulations as saying he has to provide an air vent.
    --

    Roger Hayter
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From GB@NOTsomeone@microsoft.invalid to uk.d-i-y on Wed Sep 30 10:17:41 2026
    From Newsgroup: uk.d-i-y

    On 28/09/2026 21:50, AnthonyL wrote:
    Bathroom refurb and advice needed on several fronts concerning:

    1) Is Building Control required?
    2) Is any change necessary to the existing shared soil pipe
    arrangement.

    All the properties on this estate are 1968 build bungalows. It seems
    as if there is only one soil pipe on every other property. We don't
    have a soil pipe, but next door does and our sewage goes from the
    inspection pit, down the driveway a bit, then goes across at an angle
    (all downhill slopes) to join an inspection pit on the neighbours
    path.

    Our toilet is against the wall on the side adjacent to our driveway
    and the trench goes at about 45 deg angle to the inspection pit about
    2.5m away on the far side of the driveway.

    We want to move the toilet across the bathroom* and a couple of metres inside. This will require a new trench which will now be directly
    opposite the inspection pit and hence shorter than the old trench.

    The builder says we need our own soil pipe. I don't see why as
    nothing has fundamentally changed. It's been ok for nearly 60 years
    and at best they are unsightly. Who's right.

    The builder has not mentioned any Building Regs. Work is due to start
    in 3 weeks. Are approvals needed?

    * We (SWMBO) want the bath across the exterior wall instead of backing
    to it aligned with the l/hand wall, but the toilet is in the r/h
    corner. So put the bath across (90deg rotation), put the toilet on
    the l/h wall adjacent to the side of the bath and run a pipe to the
    outside to a new trench.



    Saniflos are noisy and occasionally cause problems, but they are a lot
    cheaper than digging a new drain.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From The Natural Philosopher@tnp@invalid.invalid to uk.d-i-y on Wed Sep 30 11:38:41 2026
    From Newsgroup: uk.d-i-y

    On 30/09/2026 10:17, GB wrote:
    On 28/09/2026 21:50, AnthonyL wrote:
    Bathroom refurb and advice needed on several fronts concerning:

    1) Is Building Control required?
    2) Is any change necessary to the existing shared soil pipe
    arrangement.

    All the properties on this estate are 1968 build bungalows.-a It seems
    as if there is only one soil pipe on every other property.-a We don't
    have a soil pipe, but next door does and our sewage goes from the
    inspection pit, down the driveway a bit, then goes across at an angle
    (all downhill slopes) to join an inspection pit on the neighbours
    path.

    Our toilet is against the wall on the side adjacent to our driveway
    and the trench goes at about 45 deg angle to the inspection pit about
    2.5m away on the far side of the driveway.

    We want to move the toilet across the bathroom* and a couple of metres
    inside.-a This will require a new trench which will now be directly
    opposite the inspection pit and hence shorter than the old trench.

    The builder says we need our own soil pipe.-a I don't see why as
    nothing has fundamentally changed.-a It's been ok for nearly 60 years
    and at best they are unsightly. Who's right.

    The builder has not mentioned any Building Regs.-a Work is due to start
    in 3 weeks.-a Are approvals needed?

    * We (SWMBO) want the bath across the exterior wall instead of backing
    to it aligned with the l/hand wall, but the toilet is in the r/h
    corner.-a So put the bath across (90deg rotation), put the toilet on
    the l/h wall adjacent to the side of the bath and run a pipe to the
    outside to a new trench.



    Saniflos are noisy and occasionally cause problems, but they are a lot cheaper than digging a new drain.

    They are a last resort and must not have anything beyond shit, piss and
    toilet paper down them. Sanitary towels and tooth brushes are an
    absolute no-no. Even hard lumps of shit are not always digested

    As long as you have fall, *do not use them*

    Sewage pipery needs to be around 4" dia with a >1:100 fall from the pan u-bend. Basins and baths need similar fall but 2" pipe is OK.

    Building regs don't care where it all goes with the sole proviso that
    every inch of it must be rod-able

    Sewage systems need to be vented either with a high 'exhaust pipe' or at
    least a one way valve to stop U-bends being sucked dry.

    That is all you really need to know, and stick to those regulations:
    They are well founded

    If you want chapter and verse about needing your own soil pipe. contact building control: They are usually incredibly helpful and are mostly
    free and have authority over builders.

    BUT having said that, if it's mini digger time and cut a new course, it doesn't take a lot to do a few extra yards.

    And if you do get blockages, it makes things easier than having to knock
    up next door and lift their inspection covers.
    --
    I would rather have questions that cannot be answered...
    ...than to have answers that cannot be questioned

    Richard Feynman



    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From The Natural Philosopher@tnp@invalid.invalid to uk.d-i-y on Wed Sep 30 11:40:13 2026
    From Newsgroup: uk.d-i-y

    On 30/09/2026 09:19, Roger Hayter wrote:
    On 29 Sep 2026 at 19:53:16 BST, "AnthonyL" <AnthonyL> wrote:

    On 28 Sep 2026 21:26:34 GMT, Roger Hayter <roger@hayter.org> wrote:

    On 28 Sep 2026 at 21:50:49 BST, "AnthonyL" <AnthonyL> wrote:

    Bathroom refurb and advice needed on several fronts concerning:

    1) Is Building Control required?
    2) Is any change necessary to the existing shared soil pipe
    arrangement.

    All the properties on this estate are 1968 build bungalows. It seems
    as if there is only one soil pipe on every other property. We don't
    have a soil pipe, but next door does and our sewage goes from the
    inspection pit, down the driveway a bit, then goes across at an angle
    (all downhill slopes) to join an inspection pit on the neighbours
    path.

    Our toilet is against the wall on the side adjacent to our driveway
    and the trench goes at about 45 deg angle to the inspection pit about
    2.5m away on the far side of the driveway.

    We want to move the toilet across the bathroom* and a couple of metres >>>> inside. This will require a new trench which will now be directly
    opposite the inspection pit and hence shorter than the old trench.

    The builder says we need our own soil pipe. I don't see why as
    nothing has fundamentally changed. It's been ok for nearly 60 years
    and at best they are unsightly. Who's right.

    The builder has not mentioned any Building Regs. Work is due to start >>>> in 3 weeks. Are approvals needed?

    * We (SWMBO) want the bath across the exterior wall instead of backing >>>> to it aligned with the l/hand wall, but the toilet is in the r/h
    corner. So put the bath across (90deg rotation), put the toilet on
    the l/h wall adjacent to the side of the bath and run a pipe to the
    outside to a new trench.

    How does water from the bath, kitchen and washing machine get to the soil >>> pipe? And will it have to go further?


    Photos including the existing toilet inside, immediately outside, and
    further back showing the general layout of the inspection positions
    and the shared soil pipe are at https://flic.kr/s/aHBqjA8aE8

    Hopefully all fairly self-explanatory.

    I agree it looks as though it will probably work ok as it is so near the inspection chamber, but you may have to find another builder if the existing one interprets the regulations as saying he has to provide an air vent.


    There must be one already. Its mandatory on all sewage systems. What
    isn't mandatory is one per toilet etc etc
    --
    rCLSome people like to travel by train because it combines the slowness of
    a car with the cramped public exposure of rC?an airplane.rCY

    Dennis Miller


    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Roger Hayter@roger@hayter.org to uk.d-i-y on Wed Sep 30 10:56:14 2026
    From Newsgroup: uk.d-i-y

    On 30 Sep 2026 at 11:40:13 BST, "The Natural Philosopher"
    <tnp@invalid.invalid> wrote:

    On 30/09/2026 09:19, Roger Hayter wrote:
    On 29 Sep 2026 at 19:53:16 BST, "AnthonyL" <AnthonyL> wrote:

    On 28 Sep 2026 21:26:34 GMT, Roger Hayter <roger@hayter.org> wrote:

    On 28 Sep 2026 at 21:50:49 BST, "AnthonyL" <AnthonyL> wrote:

    Bathroom refurb and advice needed on several fronts concerning:

    1) Is Building Control required?
    2) Is any change necessary to the existing shared soil pipe
    arrangement.

    All the properties on this estate are 1968 build bungalows. It seems >>>>> as if there is only one soil pipe on every other property. We don't >>>>> have a soil pipe, but next door does and our sewage goes from the
    inspection pit, down the driveway a bit, then goes across at an angle >>>>> (all downhill slopes) to join an inspection pit on the neighbours
    path.

    Our toilet is against the wall on the side adjacent to our driveway
    and the trench goes at about 45 deg angle to the inspection pit about >>>>> 2.5m away on the far side of the driveway.

    We want to move the toilet across the bathroom* and a couple of metres >>>>> inside. This will require a new trench which will now be directly
    opposite the inspection pit and hence shorter than the old trench.

    The builder says we need our own soil pipe. I don't see why as
    nothing has fundamentally changed. It's been ok for nearly 60 years >>>>> and at best they are unsightly. Who's right.

    The builder has not mentioned any Building Regs. Work is due to start >>>>> in 3 weeks. Are approvals needed?

    * We (SWMBO) want the bath across the exterior wall instead of backing >>>>> to it aligned with the l/hand wall, but the toilet is in the r/h
    corner. So put the bath across (90deg rotation), put the toilet on
    the l/h wall adjacent to the side of the bath and run a pipe to the
    outside to a new trench.

    How does water from the bath, kitchen and washing machine get to the soil >>>> pipe? And will it have to go further?


    Photos including the existing toilet inside, immediately outside, and
    further back showing the general layout of the inspection positions
    and the shared soil pipe are at https://flic.kr/s/aHBqjA8aE8

    Hopefully all fairly self-explanatory.

    I agree it looks as though it will probably work ok as it is so near the
    inspection chamber, but you may have to find another builder if the existing >> one interprets the regulations as saying he has to provide an air vent.


    There must be one already. Its mandatory on all sewage systems. What
    isn't mandatory is one per toilet etc etc

    The implication of the OP was that there was only one on alternate houses. I doubt if that would meet regulations even if it worked. It would probably work ok if there is only 2.5 of not very steep pipe to the inspection chamber, but as you say I doubt it would meet regulations.
    --

    Roger Hayter
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From The Natural Philosopher@tnp@invalid.invalid to uk.d-i-y on Wed Sep 30 12:09:35 2026
    From Newsgroup: uk.d-i-y

    On 30/09/2026 11:56, Roger Hayter wrote:
    On 30 Sep 2026 at 11:40:13 BST, "The Natural Philosopher" <tnp@invalid.invalid> wrote:

    On 30/09/2026 09:19, Roger Hayter wrote:
    On 29 Sep 2026 at 19:53:16 BST, "AnthonyL" <AnthonyL> wrote:

    On 28 Sep 2026 21:26:34 GMT, Roger Hayter <roger@hayter.org> wrote:

    On 28 Sep 2026 at 21:50:49 BST, "AnthonyL" <AnthonyL> wrote:

    Bathroom refurb and advice needed on several fronts concerning:

    1) Is Building Control required?
    2) Is any change necessary to the existing shared soil pipe
    arrangement.

    All the properties on this estate are 1968 build bungalows. It seems >>>>>> as if there is only one soil pipe on every other property. We don't >>>>>> have a soil pipe, but next door does and our sewage goes from the
    inspection pit, down the driveway a bit, then goes across at an angle >>>>>> (all downhill slopes) to join an inspection pit on the neighbours
    path.

    Our toilet is against the wall on the side adjacent to our driveway >>>>>> and the trench goes at about 45 deg angle to the inspection pit about >>>>>> 2.5m away on the far side of the driveway.

    We want to move the toilet across the bathroom* and a couple of metres >>>>>> inside. This will require a new trench which will now be directly >>>>>> opposite the inspection pit and hence shorter than the old trench. >>>>>>
    The builder says we need our own soil pipe. I don't see why as
    nothing has fundamentally changed. It's been ok for nearly 60 years >>>>>> and at best they are unsightly. Who's right.

    The builder has not mentioned any Building Regs. Work is due to start >>>>>> in 3 weeks. Are approvals needed?

    * We (SWMBO) want the bath across the exterior wall instead of backing >>>>>> to it aligned with the l/hand wall, but the toilet is in the r/h
    corner. So put the bath across (90deg rotation), put the toilet on >>>>>> the l/h wall adjacent to the side of the bath and run a pipe to the >>>>>> outside to a new trench.

    How does water from the bath, kitchen and washing machine get to the soil >>>>> pipe? And will it have to go further?


    Photos including the existing toilet inside, immediately outside, and
    further back showing the general layout of the inspection positions
    and the shared soil pipe are at https://flic.kr/s/aHBqjA8aE8

    Hopefully all fairly self-explanatory.

    I agree it looks as though it will probably work ok as it is so near the >>> inspection chamber, but you may have to find another builder if the existing
    one interprets the regulations as saying he has to provide an air vent.


    There must be one already. Its mandatory on all sewage systems. What
    isn't mandatory is one per toilet etc etc

    The implication of the OP was that there was only one on alternate houses. I doubt if that would meet regulations even if it worked.

    It would and it might well.

    Essentially the purpose of the vent is to allow methane to escape from
    the whole sewage system. So it prevents any positive pressure build up

    A secondary purpose of not allowing a vacuum either, to avoid sucking U
    bends and traps dry, is cated for by additional Durgos type valves where requeired



    It would probably work
    ok if there is only 2.5 of not very steep pipe to the inspection chamber, but as you say I doubt it would meet regulations.

    I think it would.

    But in such matters talk to the BCO at your local council BEFORE
    starting work. They like that.



    --
    Climate Change: Socialism wearing a lab coat.

    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Tricky Dicky@tricky.dicky@sky.com to uk.d-i-y on Wed Sep 30 11:57:51 2026
    From Newsgroup: uk.d-i-y

    AnthonyL <nospam@please.invalid> wrote:
    On 28 Sep 2026 21:26:34 GMT, Roger Hayter <roger@hayter.org> wrote:

    On 28 Sep 2026 at 21:50:49 BST, "AnthonyL" <AnthonyL> wrote:

    Bathroom refurb and advice needed on several fronts concerning:

    1) Is Building Control required?
    2) Is any change necessary to the existing shared soil pipe
    arrangement.

    All the properties on this estate are 1968 build bungalows. It seems
    as if there is only one soil pipe on every other property. We don't
    have a soil pipe, but next door does and our sewage goes from the
    inspection pit, down the driveway a bit, then goes across at an angle
    (all downhill slopes) to join an inspection pit on the neighbours
    path.

    Our toilet is against the wall on the side adjacent to our driveway
    and the trench goes at about 45 deg angle to the inspection pit about
    2.5m away on the far side of the driveway.

    We want to move the toilet across the bathroom* and a couple of metres
    inside. This will require a new trench which will now be directly
    opposite the inspection pit and hence shorter than the old trench.

    The builder says we need our own soil pipe. I don't see why as
    nothing has fundamentally changed. It's been ok for nearly 60 years
    and at best they are unsightly. Who's right.

    The builder has not mentioned any Building Regs. Work is due to start
    in 3 weeks. Are approvals needed?

    * We (SWMBO) want the bath across the exterior wall instead of backing
    to it aligned with the l/hand wall, but the toilet is in the r/h
    corner. So put the bath across (90deg rotation), put the toilet on
    the l/h wall adjacent to the side of the bath and run a pipe to the
    outside to a new trench.

    How does water from the bath, kitchen and washing machine get to the soil
    pipe? And will it have to go further?


    Photos including the existing toilet inside, immediately outside, and
    further back showing the general layout of the inspection positions
    and the shared soil pipe are at https://flic.kr/s/aHBqjA8aE8

    Hopefully all fairly self-explanatory.


    I cannot see why a trench needs digging, your bath and basin wastes seem to empty in a gully and you can bet your bottom dollar that under that gully
    will be a 4rCY clay pipe. Did your plumber lift the manhole cover? I would expect there to be at least one pipe entering it if the toilet and other
    wastes are combined underground or more likely two, one for the toilet and
    one for the bath/basin waste.

    If you have as outlined above and are concerned about venting, you can
    attach a soil stack to the wall and feed it into that existing for the
    basin and bath underground waste pipe. The stack may need cranking at the bottom to avoid the window but both toilet and bath/basin wastes can simply
    be fed into the vertical stack.

    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Spike@aero.spike@mail.com to uk.d-i-y on Wed Sep 30 14:34:29 2026
    From Newsgroup: uk.d-i-y

    The Natural Philosopher <tnp@invalid.invalid> wrote:
    On 30/09/2026 11:56, Roger Hayter wrote:

    The implication of the OP was that there was only one on alternate houses. I >> doubt if that would meet regulations even if it worked.

    It would and it might well.

    ThatrCOs the system here, every second house has a vent pipe, alternating
    with those that have internal Durgo valves.

    Essentially the purpose of the vent is to allow methane to escape from
    the whole sewage system. So it prevents any positive pressure build up

    A secondary purpose of not allowing a vacuum either, to avoid sucking U bends and traps dry, is cated for by additional Durgos type valves where required
    --
    Spike
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From nospam@nospam@please.invalid (AnthonyL) to uk.d-i-y on Wed Sep 30 19:21:12 2026
    From Newsgroup: uk.d-i-y

    On Wed, 30 Sep 2026 11:57:51 -0000 (UTC), Tricky Dicky
    <tricky.dicky@sky.com> wrote:

    AnthonyL <nospam@please.invalid> wrote:
    On 28 Sep 2026 21:26:34 GMT, Roger Hayter <roger@hayter.org> wrote:

    On 28 Sep 2026 at 21:50:49 BST, "AnthonyL" <AnthonyL> wrote:

    Bathroom refurb and advice needed on several fronts concerning:

    1) Is Building Control required?
    2) Is any change necessary to the existing shared soil pipe
    arrangement.

    All the properties on this estate are 1968 build bungalows. It seems
    as if there is only one soil pipe on every other property. We don't
    have a soil pipe, but next door does and our sewage goes from the
    inspection pit, down the driveway a bit, then goes across at an angle
    (all downhill slopes) to join an inspection pit on the neighbours
    path.

    Our toilet is against the wall on the side adjacent to our driveway
    and the trench goes at about 45 deg angle to the inspection pit about
    2.5m away on the far side of the driveway.

    We want to move the toilet across the bathroom* and a couple of metres >>>> inside. This will require a new trench which will now be directly
    opposite the inspection pit and hence shorter than the old trench.

    The builder says we need our own soil pipe. I don't see why as
    nothing has fundamentally changed. It's been ok for nearly 60 years
    and at best they are unsightly. Who's right.

    The builder has not mentioned any Building Regs. Work is due to start >>>> in 3 weeks. Are approvals needed?

    * We (SWMBO) want the bath across the exterior wall instead of backing >>>> to it aligned with the l/hand wall, but the toilet is in the r/h
    corner. So put the bath across (90deg rotation), put the toilet on
    the l/h wall adjacent to the side of the bath and run a pipe to the
    outside to a new trench.

    How does water from the bath, kitchen and washing machine get to the soil >>> pipe? And will it have to go further?


    Photos including the existing toilet inside, immediately outside, and
    further back showing the general layout of the inspection positions
    and the shared soil pipe are at https://flic.kr/s/aHBqjA8aE8

    Hopefully all fairly self-explanatory.


    I cannot see why a trench needs digging, your bath and basin wastes seem to >empty in a gully and you can bet your bottom dollar that under that gully >will be a 4rCY clay pipe. Did your plumber lift the manhole cover? I would >expect there to be at least one pipe entering it if the toilet and other >wastes are combined underground or more likely two, one for the toilet and >one for the bath/basin waste.


    Good point. The builder has not as yet lifted the manhole cover. It
    has dropped an inch or so on one side and he is planning to rebuild it
    as necessary.

    If you have as outlined above and are concerned about venting, you can
    attach a soil stack to the wall and feed it into that existing for the
    basin and bath underground waste pipe. The stack may need cranking at the >bottom to avoid the window but both toilet and bath/basin wastes can simply >be fed into the vertical stack.


    I'm not concerned about venting. It has worked as is since 1968 and I
    don't want an unnecessary soil pipe. The builder has thus far said I
    must have one. I'm trying to ensure I have evidence that shows that
    the current arrangement is satisfactory.
    --
    AnthonyL

    Why ever wait to finish a job before starting the next?
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From nospam@nospam@please.invalid (AnthonyL) to uk.d-i-y on Wed Sep 30 19:26:57 2026
    From Newsgroup: uk.d-i-y

    On Wed, 30 Sep 2026 11:40:13 +0100, The Natural Philosopher <tnp@invalid.invalid> wrote:

    On 30/09/2026 09:19, Roger Hayter wrote:
    On 29 Sep 2026 at 19:53:16 BST, "AnthonyL" <AnthonyL> wrote:

    On 28 Sep 2026 21:26:34 GMT, Roger Hayter <roger@hayter.org> wrote:

    On 28 Sep 2026 at 21:50:49 BST, "AnthonyL" <AnthonyL> wrote:

    Bathroom refurb and advice needed on several fronts concerning:

    1) Is Building Control required?
    2) Is any change necessary to the existing shared soil pipe
    arrangement.

    All the properties on this estate are 1968 build bungalows. It seems >>>>> as if there is only one soil pipe on every other property. We don't >>>>> have a soil pipe, but next door does and our sewage goes from the
    inspection pit, down the driveway a bit, then goes across at an angle >>>>> (all downhill slopes) to join an inspection pit on the neighbours
    path.

    Our toilet is against the wall on the side adjacent to our driveway
    and the trench goes at about 45 deg angle to the inspection pit about >>>>> 2.5m away on the far side of the driveway.

    We want to move the toilet across the bathroom* and a couple of metres >>>>> inside. This will require a new trench which will now be directly
    opposite the inspection pit and hence shorter than the old trench.

    The builder says we need our own soil pipe. I don't see why as
    nothing has fundamentally changed. It's been ok for nearly 60 years >>>>> and at best they are unsightly. Who's right.

    The builder has not mentioned any Building Regs. Work is due to start >>>>> in 3 weeks. Are approvals needed?

    * We (SWMBO) want the bath across the exterior wall instead of backing >>>>> to it aligned with the l/hand wall, but the toilet is in the r/h
    corner. So put the bath across (90deg rotation), put the toilet on
    the l/h wall adjacent to the side of the bath and run a pipe to the
    outside to a new trench.

    How does water from the bath, kitchen and washing machine get to the soil >>>> pipe? And will it have to go further?


    Photos including the existing toilet inside, immediately outside, and
    further back showing the general layout of the inspection positions
    and the shared soil pipe are at https://flic.kr/s/aHBqjA8aE8

    Hopefully all fairly self-explanatory.

    I agree it looks as though it will probably work ok as it is so near the
    inspection chamber, but you may have to find another builder if the existing >> one interprets the regulations as saying he has to provide an air vent.


    There must be one already. Its mandatory on all sewage systems. What
    isn't mandatory is one per toilet etc etc


    There is. That's how this thread started. It is clearly shown on the
    photo on my neighbour's bungalow.

    I am trying to establish that, contrary to the builder's view, there
    need be no change to that arrangement just because a minor change in
    alignment of the outlets on my side is taking place.
    --
    AnthonyL

    Why ever wait to finish a job before starting the next?
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From nospam@nospam@please.invalid (AnthonyL) to uk.d-i-y on Wed Sep 30 19:29:52 2026
    From Newsgroup: uk.d-i-y

    On 30 Sep 2026 14:34:29 GMT, Spike <aero.spike@mail.com> wrote:

    The Natural Philosopher <tnp@invalid.invalid> wrote:
    On 30/09/2026 11:56, Roger Hayter wrote:

    The implication of the OP was that there was only one on alternate houses. I
    doubt if that would meet regulations even if it worked.

    It would and it might well.

    ThatrCOs the system here, every second house has a vent pipe, alternating >with those that have internal Durgo valves.



    Is "here" bungalows as well? Do you know the regs that allow that?
    How does one establish whether and where Durgo valves are?
    --
    AnthonyL

    Why ever wait to finish a job before starting the next?
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From The Natural Philosopher@tnp@invalid.invalid to uk.d-i-y on Thu Oct 1 10:39:36 2026
    From Newsgroup: uk.d-i-y

    On 30/09/2026 20:21, AnthonyL wrote:


    I'm not concerned about venting. It has worked as is since 1968 and I
    don't want an unnecessary soil pipe. The builder has thus far said I
    must have one. I'm trying to ensure I have evidence that shows that
    the current arrangement is satisfactory.


    Ask a BCO. Seriously. Costs nothing bar a cuppa and some bikkies
    --
    To ban Christmas, simply give turkeys the vote.

    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From The Natural Philosopher@tnp@invalid.invalid to uk.d-i-y on Thu Oct 1 10:40:23 2026
    From Newsgroup: uk.d-i-y

    On 30/09/2026 20:26, AnthonyL wrote:
    I am trying to establish that, contrary to the builder's view, there
    need be no change to that arrangement just because a minor change in alignment of the outlets on my side is taking place.

    If builders were that smart they'd be politicians
    --
    To ban Christmas, simply give turkeys the vote.

    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From The Natural Philosopher@tnp@invalid.invalid to uk.d-i-y on Thu Oct 1 10:52:42 2026
    From Newsgroup: uk.d-i-y

    On 30/09/2026 20:29, AnthonyL wrote:
    On 30 Sep 2026 14:34:29 GMT, Spike <aero.spike@mail.com> wrote:

    The Natural Philosopher <tnp@invalid.invalid> wrote:
    On 30/09/2026 11:56, Roger Hayter wrote:

    The implication of the OP was that there was only one on alternate houses. I
    doubt if that would meet regulations even if it worked.

    It would and it might well.

    ThatrCOs the system here, every second house has a vent pipe, alternating
    with those that have internal Durgo valves.



    Is "here" bungalows as well? Do you know the regs that allow that?
    How does one establish whether and where Durgo valves are?


    1/. The necessity for vent stacks arises to allow *positive* pressure
    to vent to stop methane build up in otherwise closed pipes. Essentially
    the whole sewer system has to be open to the air with pongs directed
    well away from street or house level.

    This is a 'sewer wide' issue. It does not require one stack per house.
    many stacks were built as street furniture.

    2/. The necessity for a *Durgo* valve is to prevent *vacuum* (negative pressure) in the soil pipes. A large out-rush of water on your houses
    sewage system from e.g. a toilet flush can reduce the pressure behind
    it and suck other traps and U bends dry, leaving them open to the sewer
    and smelly as fuck.

    So you may need to install a Durgo where a toilet connects to a shower
    or bath trap directly. Durgos are on a per bathroom basis often as not,
    if all the appliances share the same pipe into the manhole


    I have two routes out of my (private) sewage system, that join under a manhole. Each serves two bogs, two showers and one or two baths.

    One has an eaves level vent. the other has just a Durgo.

    With hindsight I would probably have put in two vents, because Durgos
    are not 100% perfect and can allow a little suck.

    But its good enough
    --
    To ban Christmas, simply give turkeys the vote.

    --- Synchronet 3.22a-Linux NewsLink 1.2