On 22/09/2026 23:51, tony sayer wrote:
Offspring has a small house that has the consumer unit under a worktop
in a very awkward position to get to and it seems to be recessed into
the wall.
Said box has a main 100 amp switch and around 5 or 6 MCB's.
We'd very much like to add in RCD protection but there isn't room.
Assuming that a RCBO would physically fit in the MCB's place is that permitted at all?, anyone done that?
It is acceptable to replace a MCB with a RCBO. However finding one that
will fit an old CU might be a challenge.
Could one relegate the existing CU to function as a switch fuse, and
feed a submain to a new CU sited somewhere better?
--
Cheers,
John.
/=================================================================\