• ELECTRICAL INSTALLATION CONDITION REPORT question

    From AJH@news@loampitsfarm.co.uk to uk.d-i-y on Thu Aug 6 21:59:16 2026
    From Newsgroup: uk.d-i-y

    My daughter's flat has failed an EICR because the wiring to 20 GU10 down lighters, with LED bulbs, is faulty. The single insulation red and black
    wires are exposed but the outer sheath has not been continued into the
    bulb holder. Now I know if a three pin plug is wired such that the whole
    cable is not in the clamp is a failure as live and neutral single
    insulated conductors are exposed and could be touched but I thought it
    was alright if there was a secondary safety cover, like a meter box door prevents access to the single insulated meter tails. These exposed
    single insulated conductors are only accessible if the units are pried
    from the ceiling-+

    It's an expensive repair as the GU10 fittings are unable to accept the
    full flex, so they will all have to be replaced. The chap who carried
    out the test wants -u700.

    Where's ADW when I want him ;-)
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Theo@theom+news@chiark.greenend.org.uk to uk.d-i-y on Thu Aug 6 22:20:09 2026
    From Newsgroup: uk.d-i-y

    AJH <news@loampitsfarm.co.uk> wrote:
    My daughter's flat has failed an EICR because the wiring to 20 GU10 down lighters, with LED bulbs, is faulty. The single insulation red and black wires are exposed but the outer sheath has not been continued into the
    bulb holder. Now I know if a three pin plug is wired such that the whole cable is not in the clamp is a failure as live and neutral single
    insulated conductors are exposed and could be touched but I thought it
    was alright if there was a secondary safety cover, like a meter box door prevents access to the single insulated meter tails. These exposed
    single insulated conductors are only accessible if the units are pried
    from the ceiling-+

    It's an expensive repair as the GU10 fittings are unable to accept the
    full flex, so they will all have to be replaced. The chap who carried
    out the test wants -u700.

    Where's ADW when I want him ;-)

    What were they scored at? C1, C2 or C3?

    What was the reason for doing the EICR? Is it say a rental, or up for sale?

    Theo
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From AJH@news@loampitsfarm.co.uk to uk.d-i-y on Thu Aug 6 22:38:17 2026
    From Newsgroup: uk.d-i-y

    On 06/08/2026 22:20, Theo wrote:
    What were they scored at? C1, C2 or C3?


    What was the reason for doing the EICR? Is it say a rental, or up for sale?

    Potentially either.

    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From David Wade@g4ugm@dave.invalid to uk.d-i-y on Thu Aug 6 22:39:58 2026
    From Newsgroup: uk.d-i-y

    On 06/08/2026 21:59, AJH wrote:
    My daughter's flat has failed an EICR because the wiring to 20 GU10 down lighters, with LED bulbs, is faulty. The single insulation red and black wires are exposed-a but the outer sheath has not been continued into the bulb holder. Now I know if a three pin plug is wired such that the whole cable is not in the clamp is a failure as live and neutral single
    insulated conductors are exposed and could be touched but I thought it
    was alright if there was a secondary safety cover, like a meter box door prevents access to the single insulated meter tails. These exposed
    single insulated conductors are only accessible if the units are pried
    from the ceiling-+

    That is not sufficient. They must be in an enclosure like these:-

    https://www.ebay.co.uk/itm/274492600355


    It's an expensive repair as the GU10 fittings are unable to accept the
    full flex, so they will all have to be replaced. The chap who carried
    out the test wants -u700.


    That sounds expensive. Even assuming replacement fittings are -u10 each
    which seems a typical trade price that is -u200 for the fittings so -u500
    for the work assuming there is sufficient space and spare cable. If
    there isn't enough cable or space then its a lot more work.

    I would ask for an itemised estimate stating how long the work will
    take, the hourly rate and the cost of parts...

    You do understand that you are under no obligation to use the person who carried out the EICR to do the remedial work.


    Where's ADW when I want him ;-)

    no idea.

    Dave
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From David Wade@g4ugm@dave.invalid to uk.d-i-y on Thu Aug 6 22:43:50 2026
    From Newsgroup: uk.d-i-y

    On 06/08/2026 22:38, AJH wrote:
    On 06/08/2026 22:20, Theo wrote:
    What were they scored at? C1, C2 or C3?



    If it is in-accessible I believe it should be C3 but I am not a
    qualified electrician.

    What was the reason for doing the EICR?-a Is it say a rental, or up for
    sale?

    Potentially either.


    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From The Natural Philosopher@tnp@invalid.invalid to uk.d-i-y on Thu Aug 6 22:44:57 2026
    From Newsgroup: uk.d-i-y

    On 06/08/2026 22:39, David Wade wrote:


    Where's ADW when I want him ;-)

    no idea.

    Gone to Norway with the parrots I fear...

    Dave
    --
    Canada is all right really, though not for the whole weekend.

    "Saki"

    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Theo@theom+news@chiark.greenend.org.uk to uk.d-i-y on Thu Aug 6 22:48:18 2026
    From Newsgroup: uk.d-i-y

    AJH <news@loampitsfarm.co.uk> wrote:
    On 06/08/2026 22:20, Theo wrote:
    What were they scored at? C1, C2 or C3?


    What was the reason for doing the EICR? Is it say a rental, or up for sale?

    Potentially either.

    I think I would go 'EICR shopping'. Cheaper to get another EICR than spend
    the 700 quid. If the original was a budget EICR outfit then now you know
    how they make their money.

    All of the recessed light fittings that I removed had nowhere to grip the
    cable sheath - they were just two brass screw terminals each with a single-insulated wire going into them, much like a light switch. In the
    EICR they got:

    * 4no downlights not fire rated
    * Non earthed singles in lighting circuit
    * Switch wires no identified

    which were fair enough at C3. No mentions of cable restraint.

    Since it's all tucked up in the ceiling, I can't see how not having a cable grip is going to be a problem if the fitting is left undisturbed.

    Theo
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Andy Burns@usenet@andyburns.uk to uk.d-i-y on Fri Aug 7 07:24:33 2026
    From Newsgroup: uk.d-i-y

    The Natural Philosopher wrote:

    David Wade wrote:

    Where's ADW when I want him ;-)

    no idea.

    Gone to Norway with the parrots I fear...
    He posted last week ...


    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From The Natural Philosopher@tnp@invalid.invalid to uk.d-i-y on Fri Aug 7 11:34:59 2026
    From Newsgroup: uk.d-i-y

    On 06/08/2026 22:48, Theo wrote:
    AJH <news@loampitsfarm.co.uk> wrote:
    On 06/08/2026 22:20, Theo wrote:
    What were they scored at? C1, C2 or C3?


    What was the reason for doing the EICR? Is it say a rental, or up for
    sale?

    Potentially either.

    I think I would go 'EICR shopping'. Cheaper to get another EICR than spend the 700 quid. If the original was a budget EICR outfit then now you know
    how they make their money.

    All of the recessed light fittings that I removed had nowhere to grip the cable sheath - they were just two brass screw terminals each with a single-insulated wire going into them, much like a light switch. In the
    EICR they got:

    * 4no downlights not fire rated
    * Non earthed singles in lighting circuit
    * Switch wires no identified

    which were fair enough at C3. No mentions of cable restraint.

    Since it's all tucked up in the ceiling, I can't see how not having a cable grip is going to be a problem if the fitting is left undisturbed.

    Theo
    I had an electrician who said 'downstairs shower lights are not suitable
    for shower use'. Since they were installed exactly because they were, I disregarded everything else he had to say
    --
    Ideas are more powerful than guns. We would not let our enemies have
    guns, why should we let them have ideas?

    Josef Stalin

    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Timatmarford@tim@marford.uk.com to uk.d-i-y on Fri Aug 7 15:15:16 2026
    From Newsgroup: uk.d-i-y

    On 07/08/2026 11:34, The Natural Philosopher wrote:
    On 06/08/2026 22:48, Theo wrote:
    AJH <news@loampitsfarm.co.uk> wrote:
    On 06/08/2026 22:20, Theo wrote:
    What were they scored at? C1, C2 or C3?


    What was the reason for doing the EICR?-a Is it say a rental, or up for >>>> sale?

    Potentially either.

    I think I would go 'EICR shopping'.-a Cheaper to get another EICR than
    spend
    the 700 quid.-a If the original was a budget EICR outfit then now you know >> how they make their money.

    All of the recessed light fittings that I removed had nowhere to grip the
    cable sheath - they were just two brass screw terminals each with a
    single-insulated wire going into them, much like a light switch.-a In the
    EICR they got:

    * 4no downlights not fire rated
    * Non earthed singles in lighting circuit
    * Switch wires no identified

    which were fair enough at C3. No mentions of cable restraint.

    Since it's all tucked up in the ceiling, I can't see how not having a
    cable
    grip is going to be a problem if the fitting is left undisturbed.

    Theo
    I had an electrician who said 'downstairs shower lights are not suitable
    for shower use'. Since they were installed exactly because they were, I disregarded everything else he had to say

    I have to wonder if some future inspector is going to spot where I
    returned a light switch indicator neon to Earth because there was no
    Neutral available!>

    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Roger Hayter@roger@hayter.org to uk.d-i-y on Fri Aug 7 15:45:13 2026
    From Newsgroup: uk.d-i-y

    On 7 Aug 2026 at 15:15:16 BST, "Timatmarford" <tim@marford.uk.com> wrote:

    On 07/08/2026 11:34, The Natural Philosopher wrote:
    On 06/08/2026 22:48, Theo wrote:
    AJH <news@loampitsfarm.co.uk> wrote:
    On 06/08/2026 22:20, Theo wrote:
    What were they scored at? C1, C2 or C3?


    What was the reason for doing the EICR? Is it say a rental, or up for >>>>> sale?

    Potentially either.

    I think I would go 'EICR shopping'. Cheaper to get another EICR than
    spend
    the 700 quid. If the original was a budget EICR outfit then now you know >>> how they make their money.

    All of the recessed light fittings that I removed had nowhere to grip the >>> cable sheath - they were just two brass screw terminals each with a
    single-insulated wire going into them, much like a light switch. In the >>> EICR they got:

    * 4no downlights not fire rated
    * Non earthed singles in lighting circuit
    * Switch wires no identified

    which were fair enough at C3. No mentions of cable restraint.

    Since it's all tucked up in the ceiling, I can't see how not having a
    cable
    grip is going to be a problem if the fitting is left undisturbed.

    Theo
    I had an electrician who said 'downstairs shower lights are not suitable
    for shower use'. Since they were installed exactly because they were, I
    disregarded everything else he had to say

    I have to wonder if some future inspector is going to spot where I
    returned a light switch indicator neon to Earth because there was no
    Neutral available!>

    There the whole repressive overreach of Part P is justified in a nutshell.
    --

    Roger Hayter
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From brian@nospam@b-howie.co.uk to uk.d-i-y on Fri Aug 7 17:17:12 2026
    From Newsgroup: uk.d-i-y

    In message <ndm7jjFpsutU1@mid.individual.net>, Timatmarford <tim@marford.uk.com> writes

    I have to wonder if some future inspector is going to spot where I
    returned a light switch indicator neon to Earth because there was no
    Neutral available!>


    I've got one like that on my security light. The alternative was to wire
    it across the switch.

    I think as it is it might fail a Megger test.

    Brian
    --
    Brian Howie
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Timatmarford@tim@marford.uk.com to uk.d-i-y on Fri Aug 7 20:55:23 2026
    From Newsgroup: uk.d-i-y

    On 07/08/2026 17:17, brian wrote:
    In message <ndm7jjFpsutU1@mid.individual.net>, Timatmarford <tim@marford.uk.com> writes

    I have to wonder if some future inspector is going to spot where I
    returned a light switch indicator neon to Earth because there was no
    Neutral available!>


    I've got one like that on my security light. The alternative was to wire
    it across the switch.

    Er.. the purpose of the Neon was to alert the catering dept. that they
    had left the Pantry light on rather than off:-)>
    I think as it is it might fail a Megger test.

    Brian

    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From ARW@adamwadsworth@blueyonder.co.uk to uk.d-i-y on Sat Aug 8 07:22:54 2026
    From Newsgroup: uk.d-i-y

    On 06/08/2026 21:59, AJH wrote:
    My daughter's flat has failed an EICR because the wiring to 20 GU10 down lighters, with LED bulbs, is faulty. The single insulation red and black wires are exposed-a but the outer sheath has not been continued into the bulb holder. Now I know if a three pin plug is wired such that the whole cable is not in the clamp is a failure as live and neutral single
    insulated conductors are exposed and could be touched but I thought it
    was alright if there was a secondary safety cover, like a meter box door prevents access to the single insulated meter tails. These exposed
    single insulated conductors are only accessible if the units are pried
    from the ceiling-+

    It's an expensive repair as the GU10 fittings are unable to accept the
    full flex, so they will all have to be replaced. The chap who carried
    out the test wants -u700.

    Where's ADW when I want him ;-)

    Email me

    Adam
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From ARW@adamwadsworth@blueyonder.co.uk to uk.d-i-y on Sat Aug 8 07:34:14 2026
    From Newsgroup: uk.d-i-y

    On 07/08/2026 07:24, Andy Burns wrote:
    The Natural Philosopher wrote:

    David Wade wrote:

    Where's ADW when I want him ;-)

    no idea.

    Gone to Norway with the parrots I fear...
    He posted last week ...



    Working in Bradford for the school holidays.

    Long shifts.

    Lots going on (everyone has a brother) asbestos everywhere, dementia
    cases diagnosed for the elderly, had a nice trip to Scarborough to watch Jasper Carrott, tickets booked for Peter Kay and Jim Davidson. Bill
    Wright sends his best wishes (on holiday with Helen) etc etc



    --

    Adam
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Jeff Layman@Jeff@invalid.invalid to uk.d-i-y on Sat Aug 8 08:16:13 2026
    From Newsgroup: uk.d-i-y

    On 08/08/2026 07:34, ARW wrote:
    On 07/08/2026 07:24, Andy Burns wrote:
    The Natural Philosopher wrote:

    David Wade wrote:

    Where's ADW when I want him ;-)

    no idea.

    Gone to Norway with the parrots I fear...
    He posted last week ...



    Working in Bradford for the school holidays.

    Are you a biryani or vindaloo fan? ;-)
    Long shifts.

    Always in demand!
    Lots going on (everyone has a brother) asbestos everywhere, dementia
    cases diagnosed for the elderly, had a nice trip to Scarborough to watch Jasper Carrott, tickets booked for Peter Kay and Jim Davidson. Bill
    Wright sends his best wishes (on holiday with Helen) etc etc

    Regards to Bill too, and if anyone hasn't heard of him see <https://www.donvalley.tv/about-us> (when was that middle photo taken?).
    --
    Jeff
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From AJH@news@loampitsfarm.co.uk to uk.d-i-y on Sat Aug 8 08:22:44 2026
    From Newsgroup: uk.d-i-y

    On 08/08/2026 07:22, ARW wrote:


    Email me

    Adam

    Thanks, done with photo

    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From The Natural Philosopher@tnp@invalid.invalid to uk.d-i-y on Sat Aug 8 12:20:54 2026
    From Newsgroup: uk.d-i-y

    On 08/08/2026 07:22, ARW wrote:
    On 06/08/2026 21:59, AJH wrote:
    My daughter's flat has failed an EICR because the wiring to 20 GU10
    down lighters, with LED bulbs, is faulty. The single insulation red
    and black wires are exposed-a but the outer sheath has not been
    continued into the bulb holder. Now I know if a three pin plug is
    wired such that the whole cable is not in the clamp is a failure as
    live and neutral single insulated conductors are exposed and could be
    touched but I thought it was alright if there was a secondary safety
    cover, like a meter box door prevents access to the single insulated
    meter tails. These exposed single insulated conductors are only
    accessible if the units are pried from the ceiling-+

    It's an expensive repair as the GU10 fittings are unable to accept the
    full flex, so they will all have to be replaced. The chap who carried
    out the test wants -u700.

    Where's ADW when I want him ;-)

    Email me

    Adam

    He said ADW...???
    --
    If you tell a lie big enough and keep repeating it, people will
    eventually come to believe it. The lie can be maintained only for such
    time as the State can shield the people from the political, economic
    and/or military consequences of the lie. It thus becomes vitally
    important for the State to use all of its powers to repress dissent, for
    the truth is the mortal enemy of the lie, and thus by extension, the
    truth is the greatest enemy of the State.

    Joseph Goebbels




    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Andrew@Andrew97d@btinternet.com to uk.d-i-y on Sun Aug 9 11:31:14 2026
    From Newsgroup: uk.d-i-y

    On 07/08/2026 20:55, Timatmarford wrote:
    On 07/08/2026 17:17, brian wrote:
    In message <ndm7jjFpsutU1@mid.individual.net>, Timatmarford
    <tim@marford.uk.com> writes

    I have to wonder if some future inspector is going to spot where I
    returned a light switch indicator neon to Earth because there was no
    Neutral available!>


    I've got one like that on my security light. The alternative was to
    wire it across the switch.

    Er.. the purpose of the Neon was to alert the catering dept. that they
    had left the Pantry light on rather than off:-)>

    Why not fit one of those staircase timer switches that you press
    for on and after a short while it turns off.

    Or have a ball and fit a PIR to detect movement in the pantry
    (though this might catch you out if you resort to late-night
    'tasting)

    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Andrew@Andrew97d@btinternet.com to uk.d-i-y on Sun Aug 9 11:34:27 2026
    From Newsgroup: uk.d-i-y

    On 08/08/2026 07:34, ARW wrote:
    On 07/08/2026 07:24, Andy Burns wrote:
    The Natural Philosopher wrote:

    David Wade wrote:

    Where's ADW when I want him ;-)

    no idea.

    Gone to Norway with the parrots I fear...
    He posted last week ...



    Working in Bradford for the school holidays.

    Long shifts.

    Lots going on (everyone has a brother) asbestos everywhere, dementia
    cases diagnosed for the elderly, had a nice trip to Scarborough to watch Jasper Carrott, tickets booked for Peter Kay and Jim Davidson. Bill
    Wright sends his best wishes (on holiday with Helen) etc etc



    --

    Adam
    My brother has terminal asbestosis - after working all his life
    as a teacher. Work that one out. Must have been all those buildings
    flung up in a hurry between 1945 and 1970, with storage heaters
    full of asbestos insulation.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From The Natural Philosopher@tnp@invalid.invalid to uk.d-i-y on Sun Aug 9 13:04:09 2026
    From Newsgroup: uk.d-i-y

    On 09/08/2026 11:34, Andrew wrote:
    My brother has terminal asbestosis - after working all his life
    as a teacher. Work that one out. Must have been all those buildings
    flung up in a hurry between 1945 and 1970, with storage heaters
    full of asbestos insulation.

    It can be almost anything. Just living in a city near some traffic
    lights with all that brake dust...

    What it almost never was, was living in a building with*stable* asbestos.
    --
    I would rather have questions that cannot be answered...
    ...than to have answers that cannot be questioned

    Richard Feynman



    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Timatmarford@tim@marford.uk.com to uk.d-i-y on Sun Aug 9 14:17:23 2026
    From Newsgroup: uk.d-i-y

    On 09/08/2026 11:31, Andrew wrote:
    On 07/08/2026 20:55, Timatmarford wrote:
    On 07/08/2026 17:17, brian wrote:
    In message <ndm7jjFpsutU1@mid.individual.net>, Timatmarford
    <tim@marford.uk.com> writes

    I have to wonder if some future inspector is going to spot where I
    returned a light switch indicator neon to Earth because there was no
    Neutral available!>


    I've got one like that on my security light. The alternative was to
    wire it across the switch.

    Er.. the purpose of the Neon was to alert the catering dept. that they
    had left the Pantry light on rather than off:-)>

    Why not fit one of those staircase timer switches that you press
    for on and after a short while it turns off.

    I still only have switched live and earth available.>
    Or have a ball and fit a PIR to detect movement in the pantry
    (though this might catch you out if you resort to late-night
    'tasting)

    I have no problem remembering to turn off the light but I am not
    encumbered with full hands and a brain stressing about the upcoming meal.>

    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From John R Walliker@jrwalliker@gmail.com to uk.d-i-y on Sun Aug 9 16:38:20 2026
    From Newsgroup: uk.d-i-y

    On 09/08/2026 11:34, Andrew wrote:
    On 08/08/2026 07:34, ARW wrote:
    On 07/08/2026 07:24, Andy Burns wrote:
    The Natural Philosopher wrote:

    David Wade wrote:

    Where's ADW when I want him ;-)

    no idea.

    Gone to Norway with the parrots I fear...
    He posted last week ...



    Working in Bradford for the school holidays.

    Long shifts.

    Lots going on (everyone has a brother) asbestos everywhere, dementia
    cases diagnosed for the elderly, had a nice trip to Scarborough to
    watch Jasper Carrott, tickets booked for Peter Kay and Jim Davidson.
    Bill Wright sends his best wishes (on holiday with Helen) etc etc



    --

    Adam
    My brother has terminal asbestosis - after working all his life
    as a teacher. Work that one out. Must have been all those buildings
    flung up in a hurry between 1945 and 1970, with storage heaters
    full of asbestos insulation.

    Or asbestos contamination of blackboard chalk.

    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Rod Speed@rod.speed.aaa@gmail.com to uk.d-i-y on Mon Aug 10 01:55:47 2026
    From Newsgroup: uk.d-i-y

    Andrew <Andrew97d@btinternet.com> wrote
    Timatmarford wrote
    brian wrote
    Timatmarford <tim@marford.uk.com> wrote

    I have to wonder if some future inspector is going to spot where I
    returned a light switch indicator neon to Earth because there was no >>>> Neutral available!>

    I've got one like that on my security light. The alternative was to
    wire it across the switch.

    Er.. the purpose of the Neon was to alert the catering dept. that they
    had left the Pantry light on rather than off:-)>

    Why not fit one of those staircase timer switches that you press
    for on and after a short while it turns off.

    I much prefer a proper movement sensor system like the
    Philips Hue system. Not cheap but brilliant in use, you
    never need to do anything, just walk around where you
    want to go and have the lights come on and off when
    required completely automatically and the you can
    put the sensors anywhere with no wires involved at
    all and the batterys quite literally last for years

    Or have a ball and fit a PIR to detect movement in the pantry

    In my case in the entire house and outside

    (though this might catch you out if you resort to late-night
    'tasting)
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From somewhere else@"somewhere else"@gmail.com to uk.d-i-y on Sun Aug 9 18:09:26 2026
    From Newsgroup: uk.d-i-y

    Timatmarford wrote:
    On 07/08/2026 11:34, The Natural Philosopher wrote:
    On 06/08/2026 22:48, Theo wrote:
    AJH <news@loampitsfarm.co.uk> wrote:
    On 06/08/2026 22:20, Theo wrote:
    What were they scored at? C1, C2 or C3?


    What was the reason for doing the EICR?-a Is it say a rental, or up for >>>>> sale?

    Potentially either.

    I think I would go 'EICR shopping'.-a Cheaper to get another EICR than
    spend
    the 700 quid.-a If the original was a budget EICR outfit then now you
    know
    how they make their money.

    All of the recessed light fittings that I removed had nowhere to grip
    the
    cable sheath - they were just two brass screw terminals each with a
    single-insulated wire going into them, much like a light switch.-a In the >>> EICR they got:

    * 4no downlights not fire rated
    * Non earthed singles in lighting circuit
    * Switch wires no identified

    which were fair enough at C3. No mentions of cable restraint.

    Since it's all tucked up in the ceiling, I can't see how not having a
    cable
    grip is going to be a problem if the fitting is left undisturbed.

    Theo
    I had an electrician who said 'downstairs shower lights are not
    suitable for shower use'. Since they were installed exactly because
    they were, I disregarded everything else he had to say

    I have to wonder if some future inspector is going to spot where I
    returned a light switch indicator neon to Earth because there was no
    Neutral available!>

    Colour me confused. If the neon is to indicate that a cupboard light was
    on then why not connect an indicator across the cupboard light, or fit a
    PIR to the light to remove the problem ... or replace the bulb with one
    that has an integral PIR?
    Dumping a couple of mA into the CPC isn't a wonderful idea.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Timatmarford@tim@marford.uk.com to uk.d-i-y on Sun Aug 9 22:58:27 2026
    From Newsgroup: uk.d-i-y

    On 09/08/2026 18:09, Sparky wrote:
    Timatmarford wrote:
    On 07/08/2026 11:34, The Natural Philosopher wrote:
    On 06/08/2026 22:48, Theo wrote:
    AJH <news@loampitsfarm.co.uk> wrote:
    On 06/08/2026 22:20, Theo wrote:
    What were they scored at? C1, C2 or C3?


    What was the reason for doing the EICR?-a Is it say a rental, or up >>>>>> for
    sale?

    Potentially either.

    I think I would go 'EICR shopping'.-a Cheaper to get another EICR
    than spend
    the 700 quid.-a If the original was a budget EICR outfit then now you >>>> know
    how they make their money.

    All of the recessed light fittings that I removed had nowhere to
    grip the
    cable sheath - they were just two brass screw terminals each with a
    single-insulated wire going into them, much like a light switch.-a In >>>> the
    EICR they got:

    * 4no downlights not fire rated
    * Non earthed singles in lighting circuit
    * Switch wires no identified

    which were fair enough at C3. No mentions of cable restraint.

    Since it's all tucked up in the ceiling, I can't see how not having
    a cable
    grip is going to be a problem if the fitting is left undisturbed.

    Theo
    I had an electrician who said 'downstairs shower lights are not
    suitable for shower use'. Since they were installed exactly because
    they were, I disregarded everything else he had to say

    I have to wonder if some future inspector is going to spot where I
    returned a light switch indicator neon to Earth because there was no
    Neutral available!>

    Colour me confused. If the neon is to indicate that a cupboard light was
    on then why not connect an indicator across the cupboard light, or fit a
    PIR to the light to remove the problem ... or replace the bulb with one
    that has an integral PIR?
    Dumping a couple of mA into the CPC isn't a wonderful idea.

    Maybe not but it avoids replacing a cable buried in plaster. My
    electrician had used twin+E (suitably colour coded) to connect to the
    switch.

    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From The Natural Philosopher@tnp@invalid.invalid to uk.d-i-y on Mon Aug 10 06:03:17 2026
    From Newsgroup: uk.d-i-y

    On 09/08/2026 22:58, Timatmarford wrote:
    Maybe not but it avoids replacing a cable buried in plaster. My
    electrician had used twin+E (suitably colour coded) to connect to the switch.

    Aha. An interesting conundrum.
    Easy enough to rig the neon to illuminate when the device is OFF...
    ... I'd be inclined to reposition the other end of the wire so that the 'earth' wire was in fact connected to neutral...especially if the switch
    were plastic with no earth point...
    --
    "It was a lot more fun being 20 in the 70's that it is being 70 in the 20's" Joew Walsh

    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Roger Hayter@roger@hayter.org to uk.d-i-y on Mon Aug 10 09:57:29 2026
    From Newsgroup: uk.d-i-y

    On 10 Aug 2026 at 06:03:17 BST, "The Natural Philosopher"
    <tnp@invalid.invalid> wrote:

    On 09/08/2026 22:58, Timatmarford wrote:
    Maybe not but it avoids replacing a cable buried in plaster. My
    electrician had used twin+E (suitably colour coded) to connect to the
    switch.

    Aha. An interesting conundrum.
    Easy enough to rig the neon to illuminate when the device is OFF...
    ... I'd be inclined to reposition the other end of the wire so that the 'earth' wire was in fact connected to neutral...especially if the switch
    were plastic with no earth point...

    How about one of those spy glasses for front doors, so, if one cared about a trivial quantity of energy use, one could look through it to see whether the cupboard light was on?
    --

    Roger Hayter
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From somewhere else@"somewhere else"@gmail.com to uk.d-i-y on Mon Aug 10 13:07:35 2026
    From Newsgroup: uk.d-i-y

    Timatmarford wrote:
    On 09/08/2026 18:09, Sparky wrote:
    Timatmarford wrote:
    On 07/08/2026 11:34, The Natural Philosopher wrote:
    On 06/08/2026 22:48, Theo wrote:
    AJH <news@loampitsfarm.co.uk> wrote:
    On 06/08/2026 22:20, Theo wrote:
    What were they scored at? C1, C2 or C3?


    What was the reason for doing the EICR?-a Is it say a rental, or >>>>>>> up for
    sale?

    Potentially either.

    I think I would go 'EICR shopping'.-a Cheaper to get another EICR
    than spend
    the 700 quid.-a If the original was a budget EICR outfit then now
    you know
    how they make their money.

    All of the recessed light fittings that I removed had nowhere to
    grip the
    cable sheath - they were just two brass screw terminals each with a
    single-insulated wire going into them, much like a light switch.
    In the
    EICR they got:

    * 4no downlights not fire rated
    * Non earthed singles in lighting circuit
    * Switch wires no identified

    which were fair enough at C3. No mentions of cable restraint.

    Since it's all tucked up in the ceiling, I can't see how not having >>>>> a cable
    grip is going to be a problem if the fitting is left undisturbed.

    Theo
    I had an electrician who said 'downstairs shower lights are not
    suitable for shower use'. Since they were installed exactly because
    they were, I disregarded everything else he had to say

    I have to wonder if some future inspector is going to spot where I
    returned a light switch indicator neon to Earth because there was no
    Neutral available!>

    Colour me confused. If the neon is to indicate that a cupboard light
    was on then why not connect an indicator across the cupboard light, or
    fit a PIR to the light to remove the problem ... or replace the bulb
    with one that has an integral PIR?
    Dumping a couple of mA into the CPC isn't a wonderful idea.

    Maybe not but it avoids replacing a cable buried in plaster. My
    electrician had used twin+E (suitably colour coded) to connect to the switch.

    Have a look here: https://www.google.co.uk/search?q=bulb+with+integral+pir
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Timatmarford@tim@marford.uk.com to uk.d-i-y on Mon Aug 10 14:44:11 2026
    From Newsgroup: uk.d-i-y

    On 10/08/2026 13:07, Sparky wrote:
    Timatmarford wrote:
    On 09/08/2026 18:09, Sparky wrote:
    Timatmarford wrote:
    On 07/08/2026 11:34, The Natural Philosopher wrote:
    On 06/08/2026 22:48, Theo wrote:
    AJH <news@loampitsfarm.co.uk> wrote:
    On 06/08/2026 22:20, Theo wrote:
    What were they scored at? C1, C2 or C3?


    What was the reason for doing the EICR?-a Is it say a rental, or >>>>>>>> up for
    sale?

    Potentially either.

    I think I would go 'EICR shopping'.-a Cheaper to get another EICR >>>>>> than spend
    the 700 quid.-a If the original was a budget EICR outfit then now >>>>>> you know
    how they make their money.

    All of the recessed light fittings that I removed had nowhere to
    grip the
    cable sheath - they were just two brass screw terminals each with a >>>>>> single-insulated wire going into them, much like a light switch.
    In the
    EICR they got:

    * 4no downlights not fire rated
    * Non earthed singles in lighting circuit
    * Switch wires no identified

    which were fair enough at C3. No mentions of cable restraint.

    Since it's all tucked up in the ceiling, I can't see how not
    having a cable
    grip is going to be a problem if the fitting is left undisturbed.

    Theo
    I had an electrician who said 'downstairs shower lights are not
    suitable for shower use'. Since they were installed exactly because >>>>> they were, I disregarded everything else he had to say

    I have to wonder if some future inspector is going to spot where I
    returned a light switch indicator neon to Earth because there was no
    Neutral available!>

    Colour me confused. If the neon is to indicate that a cupboard light
    was on then why not connect an indicator across the cupboard light,
    or fit a PIR to the light to remove the problem ... or replace the
    bulb with one that has an integral PIR?
    Dumping a couple of mA into the CPC isn't a wonderful idea.

    Maybe not but it avoids replacing a cable buried in plaster. My
    electrician had used twin+E (suitably colour coded) to connect to the
    switch.

    Have a look here: https://www.google.co.uk/search?q=bulb+with+integral+pir

    The existing light fitting is a 4ft. fluorescent. I have several
    *automatic* exterior lamps so am not opposed to the principle. It was
    the simplest solution in 1919:-)

    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Rod Speed@rod.speed.aaa@gmail.com to uk.d-i-y on Tue Aug 11 08:53:19 2026
    From Newsgroup: uk.d-i-y

    On Mon, 10 Aug 2026 22:07:35 +1000, Sparky <"somewhere else"@gmail.com> wrote:

    Timatmarford wrote:
    On 09/08/2026 18:09, Sparky wrote:
    Timatmarford wrote:
    On 07/08/2026 11:34, The Natural Philosopher wrote:
    On 06/08/2026 22:48, Theo wrote:
    AJH <news@loampitsfarm.co.uk> wrote:
    On 06/08/2026 22:20, Theo wrote:
    What were they scored at? C1, C2 or C3?


    What was the reason for doing the EICR? Is it say a rental, or >>>>>>>> up for
    sale?

    Potentially either.

    I think I would go 'EICR shopping'. Cheaper to get another EICR >>>>>> than spend
    the 700 quid. If the original was a budget EICR outfit then now >>>>>> you know
    how they make their money.

    All of the recessed light fittings that I removed had nowhere to >>>>>> grip the
    cable sheath - they were just two brass screw terminals each with a >>>>>> single-insulated wire going into them, much like a light switch. >>>>>> In the
    EICR they got:

    * 4no downlights not fire rated
    * Non earthed singles in lighting circuit
    * Switch wires no identified

    which were fair enough at C3. No mentions of cable restraint.

    Since it's all tucked up in the ceiling, I can't see how not having >>>>>> a cable
    grip is going to be a problem if the fitting is left undisturbed.

    Theo
    I had an electrician who said 'downstairs shower lights are not
    suitable for shower use'. Since they were installed exactly because >>>>> they were, I disregarded everything else he had to say

    I have to wonder if some future inspector is going to spot where I
    returned a light switch indicator neon to Earth because there was no >>>> Neutral available!>

    Colour me confused. If the neon is to indicate that a cupboard light
    was on then why not connect an indicator across the cupboard light, or >>> fit a PIR to the light to remove the problem ... or replace the bulb
    with one that has an integral PIR?
    Dumping a couple of mA into the CPC isn't a wonderful idea.
    Maybe not but it avoids replacing a cable buried in plaster. My
    electrician had used twin+E (suitably colour coded) to connect to the
    switch.

    Have a look here:
    https://www.google.co.uk/search?q=bulb+with+integral+pir

    Problem with that approach is that quite a bit of
    the time the bulb is not the best place for the pir

    The Philips Hue pirs are a much better approach
    because you put the pir anywhere it works best
    with no wires at all and the battery lasts for years

    Not cheap tho, but that doesn't really matter given
    that they last forever
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From AJH@news@loampitsfarm.co.uk to uk.d-i-y on Thu Aug 13 08:39:54 2026
    From Newsgroup: uk.d-i-y

    On 08/08/2026 12:20, The Natural Philosopher wrote:
    On 08/08/2026 07:22, ARW wrote:
    On 06/08/2026 21:59, AJH wrote:
    My daughter's flat has failed an EICR because the wiring to 20 GU10
    down lighters, with LED bulbs, is faulty. The single insulation red
    and black wires are exposed-a but the outer sheath has not been
    continued into the bulb holder. Now I know if a three pin plug is
    wired such that the whole cable is not in the clamp is a failure as
    live and neutral single insulated conductors are exposed and could be
    touched but I thought it was alright if there was a secondary safety
    cover, like a meter box door prevents access to the single insulated
    meter tails. These exposed single insulated conductors are only
    accessible if the units are pried from the ceiling-+

    It's an expensive repair as the GU10 fittings are unable to accept
    the full flex, so they will all have to be replaced. The chap who
    carried out the test wants -u700.

    Where's ADW when I want him ;-)

    Email me

    Adam

    He said ADW...???

    Yes a typo, Adam, or the denizen who tipped him off, knew who I meant,
    and I'm grateful for the responses.
    --- Synchronet 3.22a-Linux NewsLink 1.2