One of the UPSs was throwing caniptions, today -- constantly complaining about "distorted input" (though I've never seen a formal definition of
what constitutes "distorted input") and switching to battery power -- and back -- every couple of seconds.
I let it diddle with itself until the line, apparently, settled down.
But, started thinking about what I could use (short of a scope) to
detect irregularities in the mains. And, again, what might
constitute such irregularities!
Suggestions?
One of the UPSs was throwing caniptions, today -- constantly complaining >about "distorted input" (though I've never seen a formal definition of
what constitutes "distorted input") and switching to battery power -- and >back -- every couple of seconds.
I let it diddle with itself until the line, apparently, settled down.
But, started thinking about what I could use (short of a scope) to
detect irregularities in the mains. And, again, what might
constitute such irregularities!
Suggestions?
"Don Y" <blockedofcourse@foo.invalid> wrote in message news:115lrbu$2581i$1@dont-email.me...
One of the UPSs was throwing caniptions, today -- constantly complaining
about "distorted input" (though I've never seen a formal definition of
what constitutes "distorted input") and switching to battery power -- and
back -- every couple of seconds.
I let it diddle with itself until the line, apparently, settled down.
But, started thinking about what I could use (short of a scope) to
detect irregularities in the mains. And, again, what might
constitute such irregularities!
Suggestions?
Something like this perhaps? https://www.amazon.com/Taidacent-Harmonic-Distortion-Frequency-10Hz-1kHz/dp/B07KC6X51M
On 8/13/2026 6:42 PM, Edward Rawde wrote:
"Don Y" <blockedofcourse@foo.invalid> wrote in message news:115lrbu$2581i$1@dont-email.me...
One of the UPSs was throwing caniptions, today -- constantly complaining >>> about "distorted input" (though I've never seen a formal definition of
what constitutes "distorted input") and switching to battery power -- and >>> back -- every couple of seconds.
I let it diddle with itself until the line, apparently, settled down.
But, started thinking about what I could use (short of a scope) to
detect irregularities in the mains. And, again, what might
constitute such irregularities!
Suggestions?
Something like this perhaps?
https://www.amazon.com/Taidacent-Harmonic-Distortion-Frequency-10Hz-1kHz/dp/B07KC6X51M
I don't know. What good will "knowing" this do me? Why does the UPS
get so upset?
Is there some risk -- other than not being able to
deliver sufficient power to the load? If I had a 'scope on the line,
could I *tell* what was problematic??
Is it complaining about an unimportant problem?
But, started thinking about what I could use (short of a scope) to
detect irregularities in the mains. And, again, what might
constitute such irregularities!
Suggestions?
Something like this perhaps?
https://www.amazon.com/Taidacent-Harmonic-Distortion-Frequency-10Hz-1kHz/dp/B07KC6X51M
I don't know. What good will "knowing" this do me? Why does the UPS
get so upset?
I don't know. Ask the UPS :)
Is there some risk -- other than not being able to
deliver sufficient power to the load? If I had a 'scope on the line,
could I *tell* what was problematic??
My crystal ball is in for a service so I don't know.
But if the UPS is complaining about distortion then a
harmonic analysis of the line when it complains might be revealing.
It would be nice to be able to reassure yourself that it is doing itsIs it complaining about an unimportant problem?
Probably.
If you're a UPS then you'll want to make sure the customer knows that you're doing your job.
On 8/13/2026 7:23 PM, Edward Rawde wrote:
But, started thinking about what I could use (short of a scope) to
detect irregularities in the mains. And, again, what might
constitute such irregularities!
Suggestions?
Something like this perhaps?
https://www.amazon.com/Taidacent-Harmonic-Distortion-Frequency-10Hz-1kHz/dp/B07KC6X51M
I don't know. What good will "knowing" this do me? Why does the UPS
get so upset?
I don't know. Ask the UPS :)
It is (apparently) a catchall error that can mean low line, high line, voltage spikes, dropouts, etc. "Mains don't look right"
Is there some risk -- other than not being able to
deliver sufficient power to the load? If I had a 'scope on the line,
could I *tell* what was problematic??
My crystal ball is in for a service so I don't know.
But if the UPS is complaining about distortion then a
harmonic analysis of the line when it complains might be revealing.
Or not. It would be nice if the error was more informative;
e.g., if a typical load wouldn't be bothered by the "distorted
input", then why react to it?
It would be nice to be able to reassure yourself that it is doing itsIs it complaining about an unimportant problem?
Probably.
If you're a UPS then you'll want to make sure the customer knows that you're >> doing your job.
job and not shitting the bed! (I had another UPS of the same make/model
die some years back)
One of the UPSs was throwing caniptions, today -- constantly complaining >about "distorted input" (though I've never seen a formal definition of
what constitutes "distorted input") and switching to battery power -- and >back -- every couple of seconds.
I let it diddle with itself until the line, apparently, settled down.
But, started thinking about what I could use (short of a scope) to
detect irregularities in the mains. And, again, what might
constitute such irregularities!
Suggestions?
"Don Y" <blockedofcourse@foo.invalid> wrote in message news:115luv5$264ik$1@dont-email.me...Depends on the UPS's topology. "Line interactive" tend to let the
On 8/13/2026 7:23 PM, Edward Rawde wrote:
But, started thinking about what I could use (short of a scope) to >>>>>> detect irregularities in the mains. And, again, what might
constitute such irregularities!
Suggestions?
Something like this perhaps?
https://www.amazon.com/Taidacent-Harmonic-Distortion-Frequency-10Hz-1kHz/dp/B07KC6X51M
I don't know. What good will "knowing" this do me? Why does the UPS
get so upset?
I don't know. Ask the UPS :)
It is (apparently) a catchall error that can mean low line, high line,
voltage spikes, dropouts, etc. "Mains don't look right"
Then you'll probably never know what upset it.
I sometimes hear a click from the relay in the UPS attached to this computer. But not often. If there's a storm brewing nearby I might get a few clicks.
Why does a UPS need a relay anyway?
Can't today's technology just down convert the incoming power to 12V
and also up convert it back to line voltage?
What's the relay doing?
On Thu, 13 Aug 2026 18:34:51 -0700, Don Y
<blockedofcourse@foo.invalid> wrote:
One of the UPSs was throwing caniptions, today -- constantly complaining
about "distorted input" (though I've never seen a formal definition of
what constitutes "distorted input") and switching to battery power -- and
back -- every couple of seconds.
I let it diddle with itself until the line, apparently, settled down.
Your unspecified model UPS probably has adjustable limits for how much distortion (i.e. harmonic) in can tolerate on the AC input. For
example:
"Adjusting Input Sensitivity on APC Smart-UPS SMT & SMX Series |
Schneider Electric"
<https://www.youtube.com/watch?v=PRJb1GDdskI> (1:12)
"Understanding the full implications of harmonic distortion" <https://www.ups.rehlko.co.uk/understanding-full-implications-harmonic-distortion/>
I run into distortion problems when utility power is switched to
generator backup power during power outages. The inverter generators,
which produce low distortion sine waves work the best. The modified staircase approximations of a sine wave, produced by cheap commodity generators, are horrible.
Another source of distorted power line waveforms are non-linear loads.But, what are the consequences of those disturbances?
"Understanding Total Harmonic Distortion" <https://powerquality.blog/2021/02/11/understanding-total-harmonic-distortion/>
<https://powerquality.blog/wp-content/uploads/2021/02/understanding-total-harmonic-distortion.pdf>
"Analysis of Total Harmonic Distortion on the U.S. Electric Grid" <https://www.tingfire.com/blog/analysis-of-total-harmonic-distortion-on-the-u-s-electric-grid/>
But, started thinking about what I could use (short of a scope) to
detect irregularities in the mains. And, again, what might
constitute such irregularities!
Suggestions?
There should be something here. I'm not familiar with todays power
line test equipment.
"Power quality meter THD" <https://www.google.com/search?q=power%20quality%20meter%20THD&udm=2>
"Clamp meter THD" <https://www.google.com/search?q=clamp%20meter%20THD&num=10&udm=2>
Incidentally, IEEE 519-2022 sets "voltage distortion limits" at 8% for
power lines under 1000v:
"Power quality - IEEE 519-2022" <https://comsys.se/en-us/our-adf-technology/power-quality-ieee-519-2022/>
Don Y <blockedofcourse@foo.invalid>wrote:
One of the UPSs was throwing caniptions, today -- constantly complaining >about "distorted input" (though I've never seen a formal definition ofwhat constitutes "distorted input") and switching to battery power -- and >back -- every couple of seconds.
I let it diddle with itself until the line, apparently, settled down.
But, started thinking about what I could use (short of a scope) to
detect irregularities in the mains. And, again, what might
constitute such irregularities!
Suggestions?
One of the UPSs was throwing caniptions, today -- constantly complaining about "distorted input" (though I've never seen a formal definition of
what constitutes "distorted input") and switching to battery power -- and back -- every couple of seconds.
I let it diddle with itself until the line, apparently, settled down.
But, started thinking about what I could use (short of a scope) to
detect irregularities in the mains.-a And, again, what might
constitute such irregularities!
Suggestions?
The one that upsets mine is when one of the three hot phases goes down and instead of 240vac we get 87% of that. Everything being on switched mode PSUs these days you don't notice until you try to boil a kettle!
In the good old days of CRTs the height and width would shrink (if it worked at
all). Incandescent lamps would be redder and dimmer too.
Easiest way is put a scope on it to see the actual mains waveform, or perhaps
on an old ac transformer output at a safer voltage.
"Don Y" <blockedofcourse@foo.invalid> wrote in message news:115ls2e$25c5a$1@dont-email.me...
On 8/13/2026 6:42 PM, Edward Rawde wrote:
"Don Y" <blockedofcourse@foo.invalid> wrote in message news:115lrbu$2581i$1@dont-email.me...
One of the UPSs was throwing caniptions, today -- constantly complaining >>>> about "distorted input" (though I've never seen a formal definition of >>>> what constitutes "distorted input") and switching to battery power -- and >>>> back -- every couple of seconds.
I let it diddle with itself until the line, apparently, settled down.
But, started thinking about what I could use (short of a scope) to
detect irregularities in the mains. And, again, what might
constitute such irregularities!
Suggestions?
Something like this perhaps?
https://www.amazon.com/Taidacent-Harmonic-Distortion-Frequency-10Hz-1kHz/dp/B07KC6X51M
I don't know. What good will "knowing" this do me? Why does the UPS
get so upset?
I don't know. Ask the UPS :)
On 8/14/2026 2:57 AM, Martin Brown wrote:
The one that upsets mine is when one of the three hot phases goes down
and instead of 240vac we get 87% of that. Everything being on switched
mode PSUs these days you don't notice until you try to boil a kettle!
Here, the worry is an open neutral as few homes have truly balanced loads (especially when users can switch individual loads on and off)