    In a continuing push to shed kit, I'm now turning to my
    herd of UPSs -- effectively one per workstation/server
    (in addition to line conditioning and backup, they
    give me a convenient place to plug the associated
    peripherals and switch everything RELATED on/off in
    one spot)

    I've some 2200VA units gathering dust that could,
    conceivably, replace several smaller units as I
    rarely have more than two or three machines powered
    at the same time.

    This would let me economize on battery purchases
    (as each UPS needs its own battery pack, if I
    can rid myself of a few UPSs then I can similarly rid
    myself of those battery packs!)

    But, 2200VA is a 20A branch circuit. In a residence,
    most are 15A (1440/1800W).

    IF I KNOW THAT I WILL NEVER EXCEED THE AMPACITY OF THE
    BRANCH CIRCUIT, what risk to repurposing a 2200VA unit
    to run off a 15A circuit?

    Steady state, power out is roughly power in, neglecting
    transfer inefficiencies (which are probably comparable
    to those of a comparable load on a smaller UPS) and any
    charging current for battery pack -- which may be higher
    as the battery pack is larger than that of smaller units
    (even though those are all "powered" at all times!).

    In "test" mode (which I typically disable), I *think* the
    UPS switches to battery power and applies a load -- to
    test the inverter and battery. So, that should have
    minimal impact on what the branch circuit sees.

    So, maybe inrush current might be higher?

    I'm hesitant to just "try it" as the things are heavy
    and lugging them into place (only to be disappointed)
    is not something I look forward to doing -- let alone
    sorting through all the cabling, etc.

    Maybe I'll hunt for a schematic and do a cursory analysis
    (you can usually find these things hidden away, online)
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Don Y@blockedofcourse@foo.invalid to sci.electronics.design on Fri Aug 7 01:41:03 2026
    From Newsgroup: sci.electronics.design

    On 8/6/2026 7:40 PM, Don Y wrote:
    In a continuing push to shed kit, I'm now turning to my
    herd of UPSs -- effectively one per workstation/server
    (in addition to line conditioning and backup, they
    give me a convenient place to plug the associated
    peripherals and switch everything RELATED on/off in
    one spot)

    I've some 2200VA units gathering dust that could,
    conceivably, replace several smaller units as I
    rarely have more than two or three machines powered
    at the same time.

    This would let me economize on battery purchases
    (as each UPS needs its own battery pack, if I
    can rid myself of a few UPSs then I can similarly rid
    myself of those battery packs!)

    But, 2200VA is a 20A branch circuit.-a In a residence,
    most are 15A (1440/1800W).

    IF I KNOW THAT I WILL NEVER EXCEED THE AMPACITY OF THE
    BRANCH CIRCUIT, what risk to repurposing a 2200VA unit
    to run off a 15A circuit?

    Steady state, power out is roughly power in, neglecting
    transfer inefficiencies (which are probably comparable
    to those of a comparable load on a smaller UPS) and any
    charging current for battery pack -- which may be higher
    as the battery pack is larger than that of smaller units
    (even though those are all "powered" at all times!).

    In "test" mode (which I typically disable), I *think* the
    UPS switches to battery power and applies a load -- to
    test the inverter and battery.-a So, that should have
    minimal impact on what the branch circuit sees.

    So, maybe inrush current might be higher?

    I'm hesitant to just "try it" as the things are heavy
    and lugging them into place (only to be disappointed)
    is not something I look forward to doing -- let alone
    sorting through all the cabling, etc.

    Maybe I'll hunt for a schematic and do a cursory analysis
    (you can usually find these things hidden away, online)

    Ha! Not an issue! I found four 1500VA units hiding
    which is a much better "wiring fit" than the 2200VA
    (and avoids the issue entirely).

    Now, I need to gather up all of the "unused" devices
    and get them the hell out of here! :<
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Martin Brown@'''newspam'''@nonad.co.uk to sci.electronics.design on Fri Aug 7 10:59:50 2026
    From Newsgroup: sci.electronics.design

    On 07/08/2026 03:40, Don Y wrote:
    In a continuing push to shed kit, I'm now turning to my
    herd of UPSs -- effectively one per workstation/server
    (in addition to line conditioning and backup, they
    give me a convenient place to plug the associated
    peripherals and switch everything RELATED on/off in
    one spot)

    I've some 2200VA units gathering dust that could,
    conceivably, replace several smaller units as I
    rarely have more than two or three machines powered
    at the same time.

    This would let me economize on battery purchases
    (as each UPS needs its own battery pack, if I
    can rid myself of a few UPSs then I can similarly rid
    myself of those battery packs!)

    But, 2200VA is a 20A branch circuit.-a In a residence,
    most are 15A (1440/1800W).

    One advantage of UK 240v mains is that the currents are lower.
    I have seen 3kW heaters used in cold rooms cause trouble with cables
    that were not tightly crimped leading to red hot wire devoid of
    insulation and charring of the interior of the plug.

    IF I KNOW THAT I WILL NEVER EXCEED THE AMPACITY OF THE
    BRANCH CIRCUIT, what risk to repurposing a 2200VA unit
    to run off a 15A circuit?

    US style mains is radial rather than ring isn't it so you will be
    sometimes pushing the limit if the UPS needs to supply 2.2kVA. OTOH the
    cable will just run a bit warm when that happens. If it happens too
    often then it will shorten the useful life of the cable.

    A UK mains ring circuit provides twice the nominal capacity of the cable
    used provided that the ring isn't broken.

    Slow blow fuses can stand roughly twice their nominal rated current
    flowing through them for tens of minutes (though get rather hot).

    I'm hesitant to just "try it" as the things are heavy
    and lugging them into place (only to be disappointed)
    is not something I look forward to doing -- let alone
    sorting through all the cabling, etc.

    You could do a test wherever it is presently located to see under what circumstances and for how long it might draw 2.2kW. I don't understand
    the notation (1440/1800W) is that steady load and absolute peak load?

    If it is then you may have your answer since insurerance loss adjusters
    love to find a reason not to pay out if there is a fire.
    --
    Martin Brown

    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Don Y@blockedofcourse@foo.invalid to sci.electronics.design on Fri Aug 7 09:00:20 2026
    From Newsgroup: sci.electronics.design

    On 8/7/2026 2:59 AM, Martin Brown wrote:
    But, 2200VA is a 20A branch circuit.-a In a residence,
    most are 15A (1440/1800W).

    One advantage of UK 240v mains is that the currents are lower.
    I have seen 3kW heaters used in cold rooms cause trouble with cables that were
    not tightly crimped leading to red hot wire devoid of insulation and charring
    of the interior of the plug.

    Here, the emphasis on reducing cost (and labor) leads
    to all sorts of "bad design choices".

    For example, receptacles (typically duplex) tend to have
    a pair of connections for each "conductor".

    <https://www.electrical-forensics.com/Receptacles/F10-052/ReceptacleConnections.jpg>

    The connections used to be screw terminals though now tend to be
    "back stab" self-securing fasteners (the bare end of the wire is
    slipped into a hole in th4e back of the receptacle where a ratcheting
    mechanism "grabs" the wire; to remove the wire, one inserts another
    object -- typically a cabinet-tip screwdriver blade -- into a nearby
    slot to mechanically disengage the "ratchet").

    The metallic part of an outlet -- with all the plastic removed: <https://www.electrical-forensics.com/Receptacles/F10-052/ReceptacleStabInConnection.jpg>

    (Note the "link" at the top can be deliberately severed to allow
    the two receptacles to be independantly wired -- like for an
    "always-powered" and "switched" outlet to be colocated)

    A consequence of this is the wiring at the receptacle is in series
    with all other loads downstream from this point. So, a screw that
    works its way loose (because the receptacle sees repeated mechanical disturbance as items are plugged and unplugged) leads to
    a higher resistance connection AT the receptacle.

    A better (though more labor intensive) practice is to secure the
    upstream and downstream wires directly together and run a short
    pigtail off to the receptacle. As such, any disturbance at the
    receptacle only affects the load plugged into that receptacle
    (which is likely smaller than the SUM of that load and all
    downstream loads)

    This is aggravated by the DIYers who *think* it's just a
    matter of connecting a couple of wires...

    OTOH, our branch circuits tend to be smaller -- lower power
    (ampacity).

    A typical home will have 15A (1440/1800W) circuits for lighting
    and most receptacles; 20A (1920/2400W) for "small appliances at
    the kitchen counter; 30A@220V for an electric clothes dryer;
    50A@220V for a stove; etc. Few "corded" devices require a 20A
    circuit -- the plugs have a "horizontal neutral" to ensure they
    don't mechanically mate with a 15A-only receptacle (which has
    parallel blades for hot and neutral)

    <https://cdn1.bigcommerce.com/server3900/wlejmk/product_images/uploaded_images/info-outlet-types-15a-vs-20-amp.jpg>

    E.g., the 2200VA UPS has a plug with non-parallel blades. Removing
    it to replace it with one with parallel blades is a code violation
    as the device loses it's "listing" (hello insurers!)

    A house typically has a 60A ("dated"), 100A or 200A (all at 220V)
    "service" but this is distributed over 20 or 30 branch circuits.

    IF I KNOW THAT I WILL NEVER EXCEED THE AMPACITY OF THE
    BRANCH CIRCUIT, what risk to repurposing a 2200VA unit
    to run off a 15A circuit?

    US style mains is radial rather than ring isn't it so you will be sometimes

    Yes.

    pushing the limit if the UPS needs to supply 2.2kVA. OTOH the cable will just
    run a bit warm when that happens. If it happens too often then it will shorten
    the useful life of the cable.

    The 15A circuit would barely support a 2200VA load (assuming a PF of ~0.8). But, I wouldn't have such loads powered simultaneously -- I would be exceeding the circuit's ampacity even if they were plugged into discrete outlets
    in the absence of a UPS.

    A UK mains ring circuit provides twice the nominal capacity of the cable used
    provided that the ring isn't broken.

    "cable" meaning "wiring internal to the residence"

    The "cord" to the UPS would still see the full load.

    Slow blow fuses can stand roughly twice their nominal rated current flowing through them for tens of minutes (though get rather hot).

    I'm hesitant to just "try it" as the things are heavy
    and lugging them into place (only to be disappointed)
    is not something I look forward to doing -- let alone
    sorting through all the cabling, etc.

    You could do a test wherever it is presently located to see under what

    <frown> I may have mentioned that I have a lot of kit? <grin>

    These UPSs are all rack units -- typically 2U to 5U. Big. Heavy.
    There's no easy way to store them other than to stack them atop
    each other AS IF they were mounted in a rack.

    The 5KVA units are >> 100f pounds -- even without batteries
    (the batteries add another 100 pounds). The 2200, 3KVA, etc. units
    are a bit lighter -- but, not the sort of things you would encounter
    in most SOHO environments (that you can lift and transport without
    much effort).

    So, I'd have to test them "in place". Which means bringing power *to*
    them. I have a 100ft #12AWG "cord reel" but *it* weighs almost 40 pounds! Then, getting access to the outlets on the back side, etc.

    I.e., decide to use it (and invest the time to get it into position)
    or NOT use it (and leave it where it is).

    But, as I said in another post, I found several 1500VA units (same physical size but their magnetics are lighter weight). That will let me stage
    them in different places, closer to their respective loads.

    [Goal is to move all the machines -- and the BTUs they throw off -- out
    to the lab and access them headless. There, I can be more deliberate
    in how they are wired -- and make them more accessible, at the same
    time (instead of hiding them under workbenches, etc.)]

    circumstances and for how long it might draw 2.2kW. I don't understand the notation (1440/1800W) is that steady load and absolute peak load?

    The 1800W is the rating of the circuit (15A @ 120V = 1800W) at nominal
    line voltage. "Best practices" are to derate branch circuits by 20%,
    hence the 1440W is the nominal "maximum expected load". This being
    important where users can add loads to the circuit at will (vs.
    dedicated circuits where the load is unalterable).

    If it is then you may have your answer since insurerance loss adjusters love to
    find a reason not to pay out if there is a fire.

    There's a *reason* for those "requirements". They're not just
    trying to bust your balls...

    [I've a buddy who does a lot of DIY stuff. To his credit, he at least
    makes an effort to make it *look* nice! But, he omits things like
    conduit (EMC) as it's extra cost and labor. As if the *sole* reason
    for its use is to drive UP that cost!]
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Don Y@blockedofcourse@foo.invalid to sci.electronics.design on Fri Aug 7 09:14:58 2026
    From Newsgroup: sci.electronics.design

    On 8/7/2026 9:00 AM, Don Y wrote:
    These UPSs are all rack units -- typically 2U to 5U.-a Big.-a Heavy.
    There's no easy way to store them other than to stack them atop
    each other AS IF they were mounted in a rack.
    This, for example:

    <https://www.se.com/us/en/product/SMX1000/apc-smartups-x-1000va-rack-tower-lcd-120v/>
    powers the computer (and modem) I'm typing at, presently. A bit
    of overkill as the computer, monitor, router, modem, etc. draw less
    than 70W (of the 1000VA/800W capacity) -- giving me almost 3 hours
    "on battery" in the event of an outage.

    But, as you can see, it's BIG (17H 3.5W 19D) and heavy (50 pounds).
    Not like the "shoebox" size units more commonly encountered.