The 14kW is a pretty good match for the 100A utility service.
Fair match. I'd have to buy 25kw minimum.
Note if you have central A/C you have to figure in the startup
SURGE requirement. That can easily be double the running power,
if only for a couple of seconds.
Fail to meet that need and you'll pop yer -a-a generator breaker
and/or burn up your A/C -a-a compressor.
An AC with inverter can solve that problem with a slow controlled startup.
Ummmm ... not always. Sometimes the motors DO need a good "kick"
to get 'em going. Anything attached to some kind of 'compressor' -
a moderate/large resistance load - tends to be a bad case.
I am familiar with electronic 'soft starters' and they're good for
many apps - but not ALL.
c186282 <c186282@nnada.net> wrote:
On 10/28/26 13:10, Carlos E.R. wrote:
On 2026-10-28 15:32, c186282 wrote:Ummmm ... not always. Sometimes the motors DO need a good "kick"
On 10/28/26 09:32, Lars Poulsen wrote:
On 10/27/2026 07:11, c186282 wrote:
On 10/27/26 09:19, Lars Poulsen wrote:
On 10/26/2026 06:05, c186282 wrote:
The 14kW is a pretty good match for the 100A utility service.
Fair match. I'd have to buy 25kw minimum.
Note if you have central A/C you have to figure in the startup
SURGE requirement. That can easily be double the running power,
if only for a couple of seconds.
Fail to meet that need and you'll pop yer -a-a generator breaker
and/or burn up your A/C -a-a compressor.
An AC with inverter can solve that problem with a slow controlled startup. >>
to get 'em going. Anything attached to some kind of 'compressor' -
a moderate/large resistance load - tends to be a bad case.
Nope. The "inverter compressors" appear to be variable frequency
drive. So they can start up slow without the typical current burst of
a standard "full on" bang-bang controller.
I am familiar with electronic 'soft starters' and they're good for
many apps - but not ALL.
Not the same thing that Carlos is discussing.
On 2026-11-05 17:18, Rich wrote:
c186282 <c186282@nnada.net> wrote:
On 10/28/26 13:10, Carlos E.R. wrote:
On 2026-10-28 15:32, c186282 wrote:
On 10/28/26 09:32, Lars Poulsen wrote:
On 10/27/2026 07:11, c186282 wrote:
On 10/27/26 09:19, Lars Poulsen wrote:
On 10/26/2026 06:05, c186282 wrote:
The 14kW is a pretty good match for the 100A utility service.
Fair match. I'd have to buy 25kw minimum.
Note if you have central A/C you have to figure in the startup
SURGE requirement. That can easily be double the running power,
if only for a couple of seconds.
Fail to meet that need and you'll pop yer -a-a generator breaker
and/or burn up your A/C -a-a compressor.
An AC with inverter can solve that problem with a slow controlled
startup.
-a-a Ummmm ...-a not always.-a Sometimes the motors DO need a good "kick" >>> -a-a to get 'em going.-a Anything attached to some kind of 'compressor' - >>> -a-a a moderate/large resistance load - tends to be a bad case.
Nope.-a The "inverter compressors" appear to be variable frequency
drive.-a So they can start up slow without the typical current burst of
a standard "full on" bang-bang controller.
Good point, I forgot about that.
-a-a I am familiar with electronic 'soft starters' and they're good for
-a-a many apps - but not ALL.
Not the same thing that Carlos is discussing.
On 05/11/2026 19:32, Carlos E. R. wrote:
On 2026-11-05 17:18, Rich wrote:
c186282 <c186282@nnada.net> wrote:
On 10/28/26 13:10, Carlos E.R. wrote:
On 2026-10-28 15:32, c186282 wrote:
On 10/28/26 09:32, Lars Poulsen wrote:
On 10/27/2026 07:11, c186282 wrote:
On 10/27/26 09:19, Lars Poulsen wrote:
On 10/26/2026 06:05, c186282 wrote:
The 14kW is a pretty good match for the 100A utility service.
Fair match. I'd have to buy 25kw minimum.
Note if you have central A/C you have to figure in the startup
SURGE requirement. That can easily be double the running power,
if only for a couple of seconds.
Fail to meet that need and you'll pop yer -a-a generator breaker
and/or burn up your A/C -a-a compressor.
An AC with inverter can solve that problem with a slow controlled
startup.
-a-a Ummmm ...-a not always.-a Sometimes the motors DO need a good "kick" >>>> -a-a to get 'em going.-a Anything attached to some kind of 'compressor' - >>>> -a-a a moderate/large resistance load - tends to be a bad case.
Nope.-a The "inverter compressors" appear to be variable frequency
drive.-a So they can start up slow without the typical current burst of
a standard "full on" bang-bang controller.
Good point, I forgot about that.
Yes, brushless DC motors powered by custom speed controllers are
becoming cheaper than a commutated motor or an induction motor will
smarts to stop it blowing the grid on startup
On 2026-11-05 22:22, The Natural Philosopher wrote:
On 05/11/2026 19:32, Carlos E. R. wrote:
On 2026-11-05 17:18, Rich wrote:
c186282 <c186282@nnada.net> wrote:
On 10/28/26 13:10, Carlos E.R. wrote:
On 2026-10-28 15:32, c186282 wrote:
On 10/28/26 09:32, Lars Poulsen wrote:
On 10/27/2026 07:11, c186282 wrote:
On 10/27/26 09:19, Lars Poulsen wrote:
On 10/26/2026 06:05, c186282 wrote:
The 14kW is a pretty good match for the 100A utility service.
Fair match. I'd have to buy 25kw minimum.
Note if you have central A/C you have to figure in the startup
SURGE requirement. That can easily be double the running power,
if only for a couple of seconds.
Fail to meet that need and you'll pop yer generator breaker
and/or burn up your A/C compressor.
An AC with inverter can solve that problem with a slow controlled >>>>>> startup.
Ummmm ...-a not always.-a Sometimes the motors DO need a good
"kick" to get 'em going.-a Anything attached to some kind of
'compressor' - a moderate/large resistance load - tends to be a
bad case.
Nope.-a The "inverter compressors" appear to be variable frequency
drive.-a So they can start up slow without the typical current burst of >>>> a standard "full on" bang-bang controller.
Good point, I forgot about that.
Yes, brushless DC motors powered by custom speed controllers are
becoming cheaper than a commutated motor or an induction motor will
smarts to stop it blowing the grid on startup
I thought they were using induction motors, driven by an inverter which controls the frequency and the voltage. Generating three-phase AC
current and using three-phase motors.
On 2026-11-05 22:22, The Natural Philosopher wrote:
On 05/11/2026 19:32, Carlos E. R. wrote:
On 2026-11-05 17:18, Rich wrote:
c186282 <c186282@nnada.net> wrote:
On 10/28/26 13:10, Carlos E.R. wrote:
On 2026-10-28 15:32, c186282 wrote:
On 10/28/26 09:32, Lars Poulsen wrote:
On 10/27/2026 07:11, c186282 wrote:
On 10/27/26 09:19, Lars Poulsen wrote:
On 10/26/2026 06:05, c186282 wrote:
The 14kW is a pretty good match for the 100A utility service.
Fair match. I'd have to buy 25kw minimum.
Note if you have central A/C you have to figure in the startup
SURGE requirement. That can easily be double the running power,
if only for a couple of seconds.
Fail to meet that need and you'll pop yer -a-a generator breaker >>>>>>> and/or burn up your A/C -a-a compressor.
An AC with inverter can solve that problem with a slow controlled >>>>>> startup.
-a-a Ummmm ...-a not always.-a Sometimes the motors DO need a good "kick" >>>>> -a-a to get 'em going.-a Anything attached to some kind of 'compressor' - >>>>> -a-a a moderate/large resistance load - tends to be a bad case.
Nope.-a The "inverter compressors" appear to be variable frequency
drive.-a So they can start up slow without the typical current burst of >>>> a standard "full on" bang-bang controller.
Good point, I forgot about that.
Yes, brushless DC motors powered by custom speed controllers are
becoming cheaper than a commutated motor or an induction motor will
smarts to stop it blowing the grid on startup
I thought they were using induction motors, driven by an inverter which controls the frequency and the voltage. Generating three-phase AC
current and using three-phase motors.
Carlos E. R. <robin_listas@es.invalid> wrote:
On 2026-11-05 22:22, The Natural Philosopher wrote:
On 05/11/2026 19:32, Carlos E. R. wrote:
On 2026-11-05 17:18, Rich wrote:
c186282 <c186282@nnada.net> wrote:
On 10/28/26 13:10, Carlos E.R. wrote:
On 2026-10-28 15:32, c186282 wrote:
On 10/28/26 09:32, Lars Poulsen wrote:
On 10/27/2026 07:11, c186282 wrote:
On 10/27/26 09:19, Lars Poulsen wrote:
On 10/26/2026 06:05, c186282 wrote:
The 14kW is a pretty good match for the 100A utility service. >>>>>>>>Fair match. I'd have to buy 25kw minimum.
Note if you have central A/C you have to figure in the startup >>>>>>>> SURGE requirement. That can easily be double the running power, >>>>>>>> if only for a couple of seconds.
Fail to meet that need and you'll pop yer generator breaker
and/or burn up your A/C compressor.
An AC with inverter can solve that problem with a slow controlled >>>>>>> startup.
Ummmm ...-a not always.-a Sometimes the motors DO need a good
"kick" to get 'em going.-a Anything attached to some kind of
'compressor' - a moderate/large resistance load - tends to be a
bad case.
Nope.-a The "inverter compressors" appear to be variable frequency
drive.-a So they can start up slow without the typical current burst of >>>>> a standard "full on" bang-bang controller.
Good point, I forgot about that.
Yes, brushless DC motors powered by custom speed controllers are
becoming cheaper than a commutated motor or an induction motor will
smarts to stop it blowing the grid on startup
I thought they were using induction motors, driven by an inverter which
controls the frequency and the voltage. Generating three-phase AC
current and using three-phase motors.
Three-phase AC motors are three-phase because the phases provide the "rotating magnetic field" to produce rotational motion on the armature.
So the motor can just be windings and on-off switches.
But if you drive the coils of a DC motor with a proper controller that "sequences" the coils properly so you get the 'rotating magnetic
field', you can get any speed you desire, and extreme torque even at
startup. Same style of motors that are used on electric cars now.
Also the same style motor driver in all the little 80mm CPU fans
sitting inside all our computers for cooling purposes.
| Sysop: | Amessyroom |
|---|---|
| Location: | Fayetteville, NC |
| Users: | 76 |
| Nodes: | 6 (0 / 6) |
| Uptime: | 55:03:23 |
| Calls: | 1,265 |
| Calls today: | 1 |
| Files: | 1,362 |
| D/L today: |
3 files (2,684K bytes) |
| Messages: | 285,585 |