    From hubops@hubops@ccanoemail.com to alt.home.repair on Fri Nov 6 17:38:24 2026
    From Newsgroup: alt.home.repair

    After years of procrastination, I finally broke down
    and got a standby generator installed. 14 kW Generac.
    ... and IT IS NOISY !
    I've ordered a decibel meter from amazon to measure it -
    but my neighbour's cell phone app seems pretty close in my
    estimation. It says 101 dB standing right at the noisy end
    of the unit perhaps 2 feet away from the housing.
    Standing in front of it about 2 or 3 feet away you can't shout
    over the noise - it's gotta be 85 dB or more. The literature online
    suggests that it is 67 dB at 23 feet - I had to retreat to about
    30 ft. to get down to about 72 dB on the quiet end.
    Oh well .. live and learn ..
    Anyone here with experience to share ?
    B&S, Kohler, Cummins are the other brands online -
    though Generac seems to win the popularity contest
    - by far - in my area.
    John T.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From danny burstein@dannyb@panix.com to alt.home.repair on Fri Nov 6 23:47:00 2026
    From Newsgroup: alt.home.repair

    In <c4kselpe9cdd7ukp3gg535l17u6um1fi1n@4ax.com> hubops@ccanoemail.com writes:

    After years of procrastination, I finally broke down
    and got a standby generator installed. 14 kW Generac.
    ... and IT IS NOISY !

    all of these are tradeoffs of price, efficiency, maintenence,
    noise, efficiency..

    The basic Generacs are, as you noticed, annoyingly loud but
    you can get quieter ones with the same brand.

    ditto for others, especilly if you get "inverter" models.

    NOTE: you can retrofit sound baffles around them and thet
    can make a big difference.

    We have the ten kw natural gas air cooled basic unit
    and it's loud enough to be annoying, but not too bad...
    --
    _____________________________________________________
    Knowledge may be power, but communications is the key
    dannyb@panix.com
    [to foil spammers, my address has been double rot-13 encoded]
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From frank@"frank "@frank.net to alt.home.repair on Fri Nov 6 19:33:11 2026
    From Newsgroup: alt.home.repair

    On 11/6/2026 5:38 PM, hubops@ccanoemail.com wrote:
    After years of procrastination, I finally broke down
    and got a standby generator installed. 14 kW Generac.
    ... and IT IS NOISY !
    I've ordered a decibel meter from amazon to measure it -
    but my neighbour's cell phone app seems pretty close in my
    estimation. It says 101 dB standing right at the noisy end
    of the unit perhaps 2 feet away from the housing.
    Standing in front of it about 2 or 3 feet away you can't shout
    over the noise - it's gotta be 85 dB or more. The literature online suggests that it is 67 dB at 23 feet - I had to retreat to about
    30 ft. to get down to about 72 dB on the quiet end.
    Oh well .. live and learn ..
    Anyone here with experience to share ?
    B&S, Kohler, Cummins are the other brands online -
    though Generac seems to win the popularity contest
    - by far - in my area.
    John T.

    I have and old Power Boss half that size with a Generac generator and a
    BS engine. It is noisy as hell. A while back I thought I was going to
    have it replaced and looking up generators in the same price range it
    appeared all were noisy. It is basically in the muffler system and
    might cost double to get a quiet one.

    I am surprised an installed Generac is that noisy. I had considered
    whole house but with no natural gas my will did not want a large tank of
    gas in the back yard.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Snag@snag_one@msn.com to alt.home.repair on Fri Nov 6 18:57:28 2026
    From Newsgroup: alt.home.repair

    On 11/6/2026 6:33 PM, Frank wrote:
    On 11/6/2026 5:38 PM, hubops@ccanoemail.com wrote:
    After years of procrastination,-a I finally broke down
    and got a standby generator installed.-a 14 kW Generac.
    -a-a ... and-a-a IT IS NOISY !
    I've ordered a decibel meter from amazon to measure it -
    but my neighbour's cell phone app seems pretty close in my
    estimation.-a-a It says-a 101 dB-a standing right at the noisy end
    of the unit-a perhaps-a 2 feet away from the housing.
    -a Standing in front of it-a about 2 or 3 feet away you can't shout
    over the noise-a --a it's gotta be 85 dB or more.-a The literature online
    suggests that it is-a 67 dB at 23 feet-a --a I had to retreat to about
    30 ft.-a to get down to about 72 dB-a on the quiet end.
    -a-a Oh well-a ..-a-a live and learn-a ..
    Anyone here with experience to share ?
    B&S, Kohler, Cummins-a are the other brands online -
    though Generac seems to win the popularity contest
    --a by far-a-a --a in my area.
    -a-a-a-a John T.

    I have and old Power Boss half that size with a Generac generator and a
    BS engine. It is noisy as hell.-a A while back I thought I was going to
    have it replaced and looking up generators in the same price range it appeared all were noisy.-a It is basically in the muffler system and
    might cost double to get a quiet one.

    I am surprised an installed Generac is that noisy.-a I had considered
    whole house but with no natural gas my will did not want a large tank of
    gas in the back yard.

    Noise level partly depends on RPM's . Many generators run at 3600 RPM
    , some run at 1800 . Not only do the 1800's run quieter , they last
    longer . They also usually cost more .
    --
    Snag
    Muslims hate dogs because they
    protect women , children, and goats .
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From hubops@hubops@ccanoemail.com to alt.home.repair on Sat Nov 7 09:50:53 2026
    From Newsgroup: alt.home.repair

    On Fri, 6 Nov 2026 18:57:28 -0600, Snag <snag_one@msn.com> wrote:

    On 11/6/2026 6:33 PM, Frank wrote:
    On 11/6/2026 5:38 PM, hubops@ccanoemail.com wrote:
    After years of procrastination,a I finally broke down
    and got a standby generator installed.a 14 kW Generac.
    aa ... andaa IT IS NOISY !
    I've ordered a decibel meter from amazon to measure it -
    but my neighbour's cell phone app seems pretty close in my
    estimation.aa It saysa 101 dBa standing right at the noisy end
    of the unita perhapsa 2 feet away from the housing.
    a Standing in front of ita about 2 or 3 feet away you can't shout
    over the noisea -a it's gotta be 85 dB or more.a The literature online
    suggests that it isa 67 dB at 23 feeta -a I had to retreat to about
    30 ft.a to get down to about 72 dBa on the quiet end.
    aa Oh wella ..aa live and learna ..
    Anyone here with experience to share ?
    B&S, Kohler, Cumminsa are the other brands online -
    though Generac seems to win the popularity contest
    -a by faraa -a in my area.
    aaaa John T.

    I have and old Power Boss half that size with a Generac generator and a
    BS engine. It is noisy as hell.a A while back I thought I was going to
    have it replaced and looking up generators in the same price range it
    appeared all were noisy.a It is basically in the muffler system and
    might cost double to get a quiet one.

    I am surprised an installed Generac is that noisy.a I had considered
    whole house but with no natural gas my will did not want a large tank of
    gas in the back yard.

    Noise level partly depends on RPM's . Many generators run at 3600 RPM
    , some run at 1800 . Not only do the 1800's run quieter , they last
    longer . They also usually cost more .


    I think the nice quiet little RV generators are 1800 < ? >
    Onan often.
    If I could have found a 1800 rpm home standby I certainly would
    have paid more for it .. and I could go with a smaller size perhaps
    - I only went 14 kW because the next smaller unit was 1 cylinder.
    John T.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Clare Snyder@clare@snyder.on.ca to alt.home.repair on Sat Nov 7 12:19:03 2026
    From Newsgroup: alt.home.repair

    On Fri, 06 Nov 2026 17:38:24 -0500, hubops@ccanoemail.com wrote:

    After years of procrastination, I finally broke down
    and got a standby generator installed. 14 kW Generac.
    ... and IT IS NOISY !
    I've ordered a decibel meter from amazon to measure it -
    but my neighbour's cell phone app seems pretty close in my
    estimation. It says 101 dB standing right at the noisy end
    of the unit perhaps 2 feet away from the housing.
    Standing in front of it about 2 or 3 feet away you can't shout
    over the noise - it's gotta be 85 dB or more. The literature online >suggests that it is 67 dB at 23 feet - I had to retreat to about
    30 ft. to get down to about 72 dB on the quiet end.
    Oh well .. live and learn ..
    Anyone here with experience to share ?
    B&S, Kohler, Cummins are the other brands online -
    though Generac seems to win the popularity contest
    - by far - in my area.
    John T.
    what engine is in that beast????
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Clare Snyder@clare@snyder.on.ca to alt.home.repair on Sat Nov 7 12:28:03 2026
    From Newsgroup: alt.home.repair

    On Fri, 06 Nov 2026 17:38:24 -0500, hubops@ccanoemail.com wrote:

    After years of procrastination, I finally broke down
    and got a standby generator installed. 14 kW Generac.
    ... and IT IS NOISY !
    I've ordered a decibel meter from amazon to measure it -
    but my neighbour's cell phone app seems pretty close in my
    estimation. It says 101 dB standing right at the noisy end
    of the unit perhaps 2 feet away from the housing.
    Standing in front of it about 2 or 3 feet away you can't shout
    over the noise - it's gotta be 85 dB or more. The literature online >suggests that it is 67 dB at 23 feet - I had to retreat to about
    30 ft. to get down to about 72 dB on the quiet end.
    Oh well .. live and learn ..
    Anyone here with experience to share ?
    B&S, Kohler, Cummins are the other brands online -
    though Generac seems to win the popularity contest
    - by far - in my area.
    John T.
    I just checked - 800cc aircooled Generac specific engine - ya, it WILL
    BE LOUD - and not just the exhaust!!!!Plant trees around it.

    If you want reasonably quiet it needs to be 1800RPM and liquid
    cooked. air cooled 3600RPM unit WILL BE LOUD. The 1800s are ALWAYS
    more expensive, as are liquid cooled - so Double Whammy.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Clare Snyder@clare@snyder.on.ca to alt.home.repair on Sat Nov 7 12:31:22 2026
    From Newsgroup: alt.home.repair

    On Fri, 06 Nov 2026 17:38:24 -0500, hubops@ccanoemail.com wrote:

    After years of procrastination, I finally broke down
    and got a standby generator installed. 14 kW Generac.
    ... and IT IS NOISY !
    I've ordered a decibel meter from amazon to measure it -
    but my neighbour's cell phone app seems pretty close in my
    estimation. It says 101 dB standing right at the noisy end
    of the unit perhaps 2 feet away from the housing.
    Standing in front of it about 2 or 3 feet away you can't shout
    over the noise - it's gotta be 85 dB or more. The literature online >suggests that it is 67 dB at 23 feet - I had to retreat to about
    30 ft. to get down to about 72 dB on the quiet end.
    Oh well .. live and learn ..
    Anyone here with experience to share ?
    B&S, Kohler, Cummins are the other brands online -
    though Generac seems to win the popularity contest
    - by far - in my area.
    John T.
    1800rpm Liquid cooled are just about all twice your size though -
    22Kw and up Generac Protector - or Cummins/Kohler/Kubota
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Clare Snyder@clare@snyder.on.ca to alt.home.repair on Sat Nov 7 12:34:33 2026
    From Newsgroup: alt.home.repair

    On Sat, 07 Nov 2026 09:50:53 -0500, hubops@ccanoemail.com wrote:

    On Fri, 6 Nov 2026 18:57:28 -0600, Snag <snag_one@msn.com> wrote:

    On 11/6/2026 6:33 PM, Frank wrote:
    On 11/6/2026 5:38 PM, hubops@ccanoemail.com wrote:
    After years of procrastination,a I finally broke down
    and got a standby generator installed.a 14 kW Generac.
    aa ... andaa IT IS NOISY !
    I've ordered a decibel meter from amazon to measure it -
    but my neighbour's cell phone app seems pretty close in my
    estimation.aa It saysa 101 dBa standing right at the noisy end
    of the unita perhapsa 2 feet away from the housing.
    a Standing in front of ita about 2 or 3 feet away you can't shout
    over the noisea -a it's gotta be 85 dB or more.a The literature online >>>> suggests that it isa 67 dB at 23 feeta -a I had to retreat to about
    30 ft.a to get down to about 72 dBa on the quiet end.
    aa Oh wella ..aa live and learna ..
    Anyone here with experience to share ?
    B&S, Kohler, Cumminsa are the other brands online -
    though Generac seems to win the popularity contest
    -a by faraa -a in my area.
    aaaa John T.

    I have and old Power Boss half that size with a Generac generator and a >>> BS engine. It is noisy as hell.a A while back I thought I was going to
    have it replaced and looking up generators in the same price range it
    appeared all were noisy.a It is basically in the muffler system and
    might cost double to get a quiet one.

    I am surprised an installed Generac is that noisy.a I had considered
    whole house but with no natural gas my will did not want a large tank of >>> gas in the back yard.

    Noise level partly depends on RPM's . Many generators run at 3600 RPM
    , some run at 1800 . Not only do the 1800's run quieter , they last
    longer . They also usually cost more .


    I think the nice quiet little RV generators are 1800 < ? >
    Onan often.
    If I could have found a 1800 rpm home standby I certainly would
    have paid more for it .. and I could go with a smaller size perhaps
    - I only went 14 kW because the next smaller unit was 1 cylinder.
    John T.
    So the 800cc is just a double400? twin. I thought the 800 was till a
    single (thumper) - thankfully for once (again) I was wrong - - .Years
    ago there were 4 cyl water cooled 850s running at 1800 - can't
    remember but I think Wakeshau engines.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From hubops@hubops@ccanoemail.com to alt.home.repair on Sat Nov 7 14:25:08 2026
    From Newsgroup: alt.home.repair

    On Sat, 07 Nov 2026 12:31:22 -0500, Clare Snyder <clare@snyder.on.ca>
    wrote:

    On Fri, 06 Nov 2026 17:38:24 -0500, hubops@ccanoemail.com wrote:

    After years of procrastination, I finally broke down
    and got a standby generator installed. 14 kW Generac.
    ... and IT IS NOISY !
    I've ordered a decibel meter from amazon to measure it -
    but my neighbour's cell phone app seems pretty close in my
    estimation. It says 101 dB standing right at the noisy end
    of the unit perhaps 2 feet away from the housing.
    Standing in front of it about 2 or 3 feet away you can't shout
    over the noise - it's gotta be 85 dB or more. The literature online >>suggests that it is 67 dB at 23 feet - I had to retreat to about
    30 ft. to get down to about 72 dB on the quiet end.
    Oh well .. live and learn ..
    Anyone here with experience to share ?
    B&S, Kohler, Cummins are the other brands online -
    though Generac seems to win the popularity contest
    - by far - in my area.
    John T.

    1800rpm Liquid cooled are just about all twice your size though -
    22Kw and up Generac Protector - or Cummins/Kohler/Kubota


    I bought a used Honda EM5000 in 1999 that's still going -
    it has provided emergency power to my whole house with
    no problems over these 27 + years - with fairly minimal
    load management.. So I know I don't need more than 10 kW
    in a standby unit - I just wanted a 2-cyl rather than a 1-cyl.
    The problem with the noise level isn't so much disturbing me
    or the neighbours - but rather that there's something _wrong_
    with it .. My decibel readings, next week, when I get the meter
    should provide some info to complain about ..
    .. it shouldn't be 80 + dB when the specs say 67 !
    John T.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From hubops@hubops@ccanoemail.com to alt.home.repair on Sat Nov 7 14:35:33 2026
    From Newsgroup: alt.home.repair

    On Sat, 07 Nov 2026 12:28:03 -0500, Clare Snyder <clare@snyder.on.ca>
    wrote:

    On Fri, 06 Nov 2026 17:38:24 -0500, hubops@ccanoemail.com wrote:

    After years of procrastination, I finally broke down
    and got a standby generator installed. 14 kW Generac.
    ... and IT IS NOISY !
    I've ordered a decibel meter from amazon to measure it -
    but my neighbour's cell phone app seems pretty close in my
    estimation. It says 101 dB standing right at the noisy end
    of the unit perhaps 2 feet away from the housing.
    Standing in front of it about 2 or 3 feet away you can't shout
    over the noise - it's gotta be 85 dB or more. The literature online >>suggests that it is 67 dB at 23 feet - I had to retreat to about
    30 ft. to get down to about 72 dB on the quiet end.
    Oh well .. live and learn ..
    Anyone here with experience to share ?
    B&S, Kohler, Cummins are the other brands online -
    though Generac seems to win the popularity contest
    - by far - in my area.
    John T.
    I just checked - 800cc aircooled Generac specific engine - ya, it WILL
    BE LOUD - and not just the exhaust!!!!Plant trees around it.

    If you want reasonably quiet it needs to be 1800RPM and liquid
    cooked. air cooled 3600RPM unit WILL BE LOUD. The 1800s are ALWAYS
    more expensive, as are liquid cooled - so Double Whammy.



    This is an older web source but just for rough reference -
    - mid 60's dB at 20 feet would be fine for me -
    - I'm pretty sure that mine is 75 - 80 .. _big_ difference !

    https://blog.norwall.com/generator-information/generator-noise-levels-how-loud-are-they-2/

    John T.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Retirednoguilt@HapilyRetired@fakeaddress.invalid to alt.home.repair on Sat Nov 7 14:54:13 2026
    From Newsgroup: alt.home.repair

    On 11/7/2026 2:25 PM, hubops@ccanoemail.com wrote:
    On Sat, 07 Nov 2026 12:31:22 -0500, Clare Snyder <clare@snyder.on.ca>
    wrote:

    On Fri, 06 Nov 2026 17:38:24 -0500, hubops@ccanoemail.com wrote:

    After years of procrastination, I finally broke down
    and got a standby generator installed. 14 kW Generac.
    ... and IT IS NOISY !
    I've ordered a decibel meter from amazon to measure it -
    but my neighbour's cell phone app seems pretty close in my
    estimation. It says 101 dB standing right at the noisy end
    of the unit perhaps 2 feet away from the housing.
    Standing in front of it about 2 or 3 feet away you can't shout
    over the noise - it's gotta be 85 dB or more. The literature online
    suggests that it is 67 dB at 23 feet - I had to retreat to about
    30 ft. to get down to about 72 dB on the quiet end.
    Oh well .. live and learn ..
    Anyone here with experience to share ?
    B&S, Kohler, Cummins are the other brands online -
    though Generac seems to win the popularity contest
    - by far - in my area.
    John T.

    1800rpm Liquid cooled are just about all twice your size though -
    22Kw and up Generac Protector - or Cummins/Kohler/Kubota


    I bought a used Honda EM5000 in 1999 that's still going -
    it has provided emergency power to my whole house with
    no problems over these 27 + years - with fairly minimal
    load management.. So I know I don't need more than 10 kW
    in a standby unit - I just wanted a 2-cyl rather than a 1-cyl.
    The problem with the noise level isn't so much disturbing me
    or the neighbours - but rather that there's something _wrong_
    with it .. My decibel readings, next week, when I get the meter
    should provide some info to complain about ..
    .. it shouldn't be 80 + dB when the specs say 67 !
    John T.

    Maybe it got louder over the past 27 years. Maybe the muffler(s) need replacement. May not sound louder to you because you're 27 years older
    and may have lost some hearing acuity over the decades. Intensity is
    affected by the presence of reflecting surfaces. If reflected sound is
    in phase with the source, the total intensity at the site where measured
    will be greater. If the reflected sound is completely out of phase with
    the source, the total intensity will be diminished if measured at that
    same site. Phase interference can drive hifi enthusiasts, acoustic
    engineers and auditorium architects crazy, especially with respect to
    the low frequencies.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Clare Snyder@clare@snyder.on.ca to alt.home.repair on Sat Nov 7 15:01:34 2026
    From Newsgroup: alt.home.repair

    On Sat, 07 Nov 2026 14:25:08 -0500, hubops@ccanoemail.com wrote:

    On Sat, 07 Nov 2026 12:31:22 -0500, Clare Snyder <clare@snyder.on.ca>
    wrote:

    On Fri, 06 Nov 2026 17:38:24 -0500, hubops@ccanoemail.com wrote:

    After years of procrastination, I finally broke down
    and got a standby generator installed. 14 kW Generac.
    ... and IT IS NOISY !
    I've ordered a decibel meter from amazon to measure it -
    but my neighbour's cell phone app seems pretty close in my
    estimation. It says 101 dB standing right at the noisy end
    of the unit perhaps 2 feet away from the housing.
    Standing in front of it about 2 or 3 feet away you can't shout
    over the noise - it's gotta be 85 dB or more. The literature online >>>suggests that it is 67 dB at 23 feet - I had to retreat to about
    30 ft. to get down to about 72 dB on the quiet end.
    Oh well .. live and learn ..
    Anyone here with experience to share ?
    B&S, Kohler, Cummins are the other brands online -
    though Generac seems to win the popularity contest
    - by far - in my area.
    John T.

    1800rpm Liquid cooled are just about all twice your size though -
    22Kw and up Generac Protector - or Cummins/Kohler/Kubota


    I bought a used Honda EM5000 in 1999 that's still going -
    it has provided emergency power to my whole house with
    no problems over these 27 + years - with fairly minimal
    load management.. So I know I don't need more than 10 kW
    in a standby unit - I just wanted a 2-cyl rather than a 1-cyl.
    The problem with the noise level isn't so much disturbing me
    or the neighbours - but rather that there's something _wrong_
    with it .. My decibel readings, next week, when I get the meter
    should provide some info to complain about ..
    .. it shouldn't be 80 + dB when the specs say 67 !
    John T.
    which scale are you on? Aor C 65 Db-a could very well read 75 or 80
    Db-c because C is weighted more towards low frequencies IIRC.
    The resonance of the air cooled engine block plays tricks on sound
    meters - or your ears - one way or the other.

    A generator MAY be 65 Db-A and 85 Db-C , or it may be 65 Db-C. even
    65Db-C will travel farther than 65 Db-A and be more noticeable farther
    away because it is a "rumble" that can be felt as well as heard.Low
    frequencies are not attenuated by air as much as high frequencies.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Clare Snyder@clare@snyder.on.ca to alt.home.repair on Sat Nov 7 15:07:16 2026
    From Newsgroup: alt.home.repair

    On Sat, 07 Nov 2026 14:35:33 -0500, hubops@ccanoemail.com wrote:

    On Sat, 07 Nov 2026 12:28:03 -0500, Clare Snyder <clare@snyder.on.ca>
    wrote:

    On Fri, 06 Nov 2026 17:38:24 -0500, hubops@ccanoemail.com wrote:

    After years of procrastination, I finally broke down
    and got a standby generator installed. 14 kW Generac.
    ... and IT IS NOISY !
    I've ordered a decibel meter from amazon to measure it -
    but my neighbour's cell phone app seems pretty close in my
    estimation. It says 101 dB standing right at the noisy end
    of the unit perhaps 2 feet away from the housing.
    Standing in front of it about 2 or 3 feet away you can't shout
    over the noise - it's gotta be 85 dB or more. The literature online >>>suggests that it is 67 dB at 23 feet - I had to retreat to about
    30 ft. to get down to about 72 dB on the quiet end.
    Oh well .. live and learn ..
    Anyone here with experience to share ?
    B&S, Kohler, Cummins are the other brands online -
    though Generac seems to win the popularity contest
    - by far - in my area.
    John T.
    I just checked - 800cc aircooled Generac specific engine - ya, it WILL
    BE LOUD - and not just the exhaust!!!!Plant trees around it.

    If you want reasonably quiet it needs to be 1800RPM and liquid
    cooked. air cooled 3600RPM unit WILL BE LOUD. The 1800s are ALWAYS
    more expensive, as are liquid cooled - so Double Whammy.



    This is an older web source but just for rough reference -
    - mid 60's dB at 20 feet would be fine for me -
    - I'm pretty sure that mine is 75 - 80 .. _big_ difference !

    https://blog.norwall.com/generator-information/generator-noise-levels-how-loud-are-they-2/

    John T.
    Are you hearing exhaust noise, or engine clatter??. On an aircooled
    Generac, likely both - but at least exhaust noise you can do something
    about. Engine clatter you can only enclose and redirect - ie- plant trees/shrubs to absorb it or fence it to direct noise up and away.
    My Champion 9Kw portable IS noisy - big single 3600. My OLD Onan
    barked, but at 1600 RPM did not sound as loud as far away anmd was
    MOSTLY exhaust noise. Problen is it was SO OLD it didn't even have a
    recoil starter - just a wrap-and-pull rope starter - - -
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From hubops@hubops@ccanoemail.com to alt.home.repair on Sat Nov 7 15:50:54 2026
    From Newsgroup: alt.home.repair

    On Sat, 07 Nov 2026 15:07:16 -0500, Clare Snyder <clare@snyder.on.ca>
    wrote:

    On Sat, 07 Nov 2026 14:35:33 -0500, hubops@ccanoemail.com wrote:

    On Sat, 07 Nov 2026 12:28:03 -0500, Clare Snyder <clare@snyder.on.ca> >>wrote:

    On Fri, 06 Nov 2026 17:38:24 -0500, hubops@ccanoemail.com wrote:

    After years of procrastination, I finally broke down
    and got a standby generator installed. 14 kW Generac.
    ... and IT IS NOISY !
    I've ordered a decibel meter from amazon to measure it -
    but my neighbour's cell phone app seems pretty close in my
    estimation. It says 101 dB standing right at the noisy end
    of the unit perhaps 2 feet away from the housing.
    Standing in front of it about 2 or 3 feet away you can't shout
    over the noise - it's gotta be 85 dB or more. The literature online >>>>suggests that it is 67 dB at 23 feet - I had to retreat to about
    30 ft. to get down to about 72 dB on the quiet end.
    Oh well .. live and learn ..
    Anyone here with experience to share ?
    B&S, Kohler, Cummins are the other brands online -
    though Generac seems to win the popularity contest
    - by far - in my area.
    John T.
    I just checked - 800cc aircooled Generac specific engine - ya, it WILL
    BE LOUD - and not just the exhaust!!!!Plant trees around it.

    If you want reasonably quiet it needs to be 1800RPM and liquid
    cooked. air cooled 3600RPM unit WILL BE LOUD. The 1800s are ALWAYS
    more expensive, as are liquid cooled - so Double Whammy.



    This is an older web source but just for rough reference -
    - mid 60's dB at 20 feet would be fine for me -
    - I'm pretty sure that mine is 75 - 80 .. _big_ difference !
    https://blog.norwall.com/generator-information/generator-noise-levels-how-loud-are-they-2/

    John T.
    Are you hearing exhaust noise, or engine clatter??. On an aircooled
    Generac, likely both - but at least exhaust noise you can do something
    about. Engine clatter you can only enclose and redirect - ie- plant >trees/shrubs to absorb it or fence it to direct noise up and away.
    My Champion 9Kw portable IS noisy - big single 3600. My OLD Onan
    barked, but at 1600 RPM did not sound as loud as far away anmd was
    MOSTLY exhaust noise. Problen is it was SO OLD it didn't even have a
    recoil starter - just a wrap-and-pull rope starter - - -


    The exhaust end is 101 dB standing right beside it ..
    John T.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From hubops@hubops@ccanoemail.com to alt.home.repair on Sat Nov 7 15:53:16 2026
    From Newsgroup: alt.home.repair

    On Sat, 7 Nov 2026 14:54:13 -0500, Retirednoguilt <HapilyRetired@fakeaddress.invalid> wrote:

    On 11/7/2026 2:25 PM, hubops@ccanoemail.com wrote:
    On Sat, 07 Nov 2026 12:31:22 -0500, Clare Snyder <clare@snyder.on.ca>
    wrote:

    On Fri, 06 Nov 2026 17:38:24 -0500, hubops@ccanoemail.com wrote:

    After years of procrastination, I finally broke down
    and got a standby generator installed. 14 kW Generac.
    ... and IT IS NOISY !
    I've ordered a decibel meter from amazon to measure it -
    but my neighbour's cell phone app seems pretty close in my
    estimation. It says 101 dB standing right at the noisy end
    of the unit perhaps 2 feet away from the housing.
    Standing in front of it about 2 or 3 feet away you can't shout
    over the noise - it's gotta be 85 dB or more. The literature online >>>> suggests that it is 67 dB at 23 feet - I had to retreat to about
    30 ft. to get down to about 72 dB on the quiet end.
    Oh well .. live and learn ..
    Anyone here with experience to share ?
    B&S, Kohler, Cummins are the other brands online -
    though Generac seems to win the popularity contest
    - by far - in my area.
    John T.

    1800rpm Liquid cooled are just about all twice your size though -
    22Kw and up Generac Protector - or Cummins/Kohler/Kubota


    I bought a used Honda EM5000 in 1999 that's still going -
    it has provided emergency power to my whole house with
    no problems over these 27 + years - with fairly minimal
    load management.. So I know I don't need more than 10 kW
    in a standby unit - I just wanted a 2-cyl rather than a 1-cyl.
    The problem with the noise level isn't so much disturbing me
    or the neighbours - but rather that there's something _wrong_
    with it .. My decibel readings, next week, when I get the meter
    should provide some info to complain about ..
    .. it shouldn't be 80 + dB when the specs say 67 !
    John T.

    Maybe it got louder over the past 27 years.


    The old Honda portable is fine - it's the brand new Generac
    stand-by that's extremely _noisy_.
    John T.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From hubops@hubops@ccanoemail.com to alt.home.repair on Sat Nov 7 15:58:11 2026
    From Newsgroup: alt.home.repair

    On Sat, 07 Nov 2026 15:01:34 -0500, Clare Snyder <clare@snyder.on.ca>
    wrote:

    On Sat, 07 Nov 2026 14:25:08 -0500, hubops@ccanoemail.com wrote:

    On Sat, 07 Nov 2026 12:31:22 -0500, Clare Snyder <clare@snyder.on.ca> >>wrote:

    On Fri, 06 Nov 2026 17:38:24 -0500, hubops@ccanoemail.com wrote:

    After years of procrastination, I finally broke down
    and got a standby generator installed. 14 kW Generac.
    ... and IT IS NOISY !
    I've ordered a decibel meter from amazon to measure it -
    but my neighbour's cell phone app seems pretty close in my
    estimation. It says 101 dB standing right at the noisy end
    of the unit perhaps 2 feet away from the housing.
    Standing in front of it about 2 or 3 feet away you can't shout
    over the noise - it's gotta be 85 dB or more. The literature online >>>>suggests that it is 67 dB at 23 feet - I had to retreat to about
    30 ft. to get down to about 72 dB on the quiet end.
    Oh well .. live and learn ..
    Anyone here with experience to share ?
    B&S, Kohler, Cummins are the other brands online -
    though Generac seems to win the popularity contest
    - by far - in my area.
    John T.

    1800rpm Liquid cooled are just about all twice your size though -
    22Kw and up Generac Protector - or Cummins/Kohler/Kubota


    I bought a used Honda EM5000 in 1999 that's still going -
    it has provided emergency power to my whole house with
    no problems over these 27 + years - with fairly minimal
    load management.. So I know I don't need more than 10 kW
    in a standby unit - I just wanted a 2-cyl rather than a 1-cyl.
    The problem with the noise level isn't so much disturbing me
    or the neighbours - but rather that there's something _wrong_
    with it .. My decibel readings, next week, when I get the meter
    should provide some info to complain about ..
    .. it shouldn't be 80 + dB when the specs say 67 !
    John T.
    which scale are you on? Aor C 65 Db-a could very well read 75 or 80
    Db-c because C is weighted more towards low frequencies IIRC.
    The resonance of the air cooled engine block plays tricks on sound
    meters - or your ears - one way or the other.

    A generator MAY be 65 Db-A and 85 Db-C , or it may be 65 Db-C. even
    65Db-C will travel farther than 65 Db-A and be more noticeable farther
    away because it is a "rumble" that can be felt as well as heard.Low >frequencies are not attenuated by air as much as high frequencies.



    Good point - I'm pretty sure the meter I ordered does both -
    I have no idea what the neighbour's cell phone app measures.
    ... I didn't think the difference could be that much.
    I'll find out next week.
    John T.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From hubops@hubops@ccanoemail.com to alt.home.repair on Tue Nov 10 13:29:47 2026
    From Newsgroup: alt.home.repair

    On Sat, 07 Nov 2026 15:58:11 -0500, hubops@ccanoemail.com wrote:

    On Sat, 07 Nov 2026 15:01:34 -0500, Clare Snyder <clare@snyder.on.ca>
    wrote:

    On Sat, 07 Nov 2026 14:25:08 -0500, hubops@ccanoemail.com wrote:

    On Sat, 07 Nov 2026 12:31:22 -0500, Clare Snyder <clare@snyder.on.ca> >>>wrote:

    On Fri, 06 Nov 2026 17:38:24 -0500, hubops@ccanoemail.com wrote:

    After years of procrastination, I finally broke down
    and got a standby generator installed. 14 kW Generac.
    ... and IT IS NOISY !
    I've ordered a decibel meter from amazon to measure it -
    but my neighbour's cell phone app seems pretty close in my >>>>>estimation. It says 101 dB standing right at the noisy end
    of the unit perhaps 2 feet away from the housing.
    Standing in front of it about 2 or 3 feet away you can't shout
    over the noise - it's gotta be 85 dB or more. The literature online >>>>>suggests that it is 67 dB at 23 feet - I had to retreat to about >>>>>30 ft. to get down to about 72 dB on the quiet end.
    Oh well .. live and learn ..
    Anyone here with experience to share ?
    B&S, Kohler, Cummins are the other brands online -
    though Generac seems to win the popularity contest
    - by far - in my area.
    John T.

    1800rpm Liquid cooled are just about all twice your size though -
    22Kw and up Generac Protector - or Cummins/Kohler/Kubota


    I bought a used Honda EM5000 in 1999 that's still going -
    it has provided emergency power to my whole house with
    no problems over these 27 + years - with fairly minimal
    load management.. So I know I don't need more than 10 kW
    in a standby unit - I just wanted a 2-cyl rather than a 1-cyl.
    The problem with the noise level isn't so much disturbing me
    or the neighbours - but rather that there's something _wrong_
    with it .. My decibel readings, next week, when I get the meter
    should provide some info to complain about ..
    .. it shouldn't be 80 + dB when the specs say 67 !
    John T.
    which scale are you on? Aor C 65 Db-a could very well read 75 or 80
    Db-c because C is weighted more towards low frequencies IIRC.
    The resonance of the air cooled engine block plays tricks on sound
    meters - or your ears - one way or the other.

    A generator MAY be 65 Db-A and 85 Db-C , or it may be 65 Db-C. even
    65Db-C will travel farther than 65 Db-A and be more noticeable farther
    away because it is a "rumble" that can be felt as well as heard.Low >>frequencies are not attenuated by air as much as high frequencies.



    Good point - I'm pretty sure the meter I ordered does both -
    I have no idea what the neighbour's cell phone app measures.
    ... I didn't think the difference could be that much.
    I'll find out next week.
    John T.



    Today's readings no load A / C :

    left front right

    3 ft 91 /96 80 / 90 85 / 91
    10 ft 82 / 88 75 / 85 78 / 86
    20 ft 77 / 84 70 / 80 73 / 80
    30 ft 72 / 82 67 / 80 69 / 79

    Can't stand next to it without hearing protection ..
    not what I expected ..
    John T.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Clare Snyder@clare@snyder.on.ca to alt.home.repair on Tue Nov 10 22:09:57 2026
    From Newsgroup: alt.home.repair

    On Tue, 10 Nov 2026 13:29:47 -0500, hubops@ccanoemail.com wrote:

    On Sat, 07 Nov 2026 15:58:11 -0500, hubops@ccanoemail.com wrote:

    On Sat, 07 Nov 2026 15:01:34 -0500, Clare Snyder <clare@snyder.on.ca> >>wrote:

    On Sat, 07 Nov 2026 14:25:08 -0500, hubops@ccanoemail.com wrote:

    On Sat, 07 Nov 2026 12:31:22 -0500, Clare Snyder <clare@snyder.on.ca> >>>>wrote:

    On Fri, 06 Nov 2026 17:38:24 -0500, hubops@ccanoemail.com wrote:

    After years of procrastination, I finally broke down
    and got a standby generator installed. 14 kW Generac.
    ... and IT IS NOISY !
    I've ordered a decibel meter from amazon to measure it -
    but my neighbour's cell phone app seems pretty close in my >>>>>>estimation. It says 101 dB standing right at the noisy end
    of the unit perhaps 2 feet away from the housing.
    Standing in front of it about 2 or 3 feet away you can't shout >>>>>>over the noise - it's gotta be 85 dB or more. The literature online >>>>>>suggests that it is 67 dB at 23 feet - I had to retreat to about >>>>>>30 ft. to get down to about 72 dB on the quiet end.
    Oh well .. live and learn ..
    Anyone here with experience to share ?
    B&S, Kohler, Cummins are the other brands online -
    though Generac seems to win the popularity contest
    - by far - in my area.
    John T.

    1800rpm Liquid cooled are just about all twice your size though - >>>>>22Kw and up Generac Protector - or Cummins/Kohler/Kubota


    I bought a used Honda EM5000 in 1999 that's still going -
    it has provided emergency power to my whole house with
    no problems over these 27 + years - with fairly minimal
    load management.. So I know I don't need more than 10 kW
    in a standby unit - I just wanted a 2-cyl rather than a 1-cyl.
    The problem with the noise level isn't so much disturbing me
    or the neighbours - but rather that there's something _wrong_
    with it .. My decibel readings, next week, when I get the meter >>>>should provide some info to complain about ..
    .. it shouldn't be 80 + dB when the specs say 67 !
    John T.
    which scale are you on? Aor C 65 Db-a could very well read 75 or 80
    Db-c because C is weighted more towards low frequencies IIRC.
    The resonance of the air cooled engine block plays tricks on sound
    meters - or your ears - one way or the other.

    A generator MAY be 65 Db-A and 85 Db-C , or it may be 65 Db-C. even >>>65Db-C will travel farther than 65 Db-A and be more noticeable farther >>>away because it is a "rumble" that can be felt as well as heard.Low >>>frequencies are not attenuated by air as much as high frequencies.



    Good point - I'm pretty sure the meter I ordered does both -
    I have no idea what the neighbour's cell phone app measures.
    ... I didn't think the difference could be that much.
    I'll find out next week.
    John T.



    Today's readings no load A / C :

    left front right

    3 ft 91 /96 80 / 90 85 / 91
    10 ft 82 / 88 75 / 85 78 / 86
    20 ft 77 / 84 70 / 80 73 / 80
    30 ft 72 / 82 67 / 80 69 / 79

    Can't stand next to it without hearing protection ..
    not what I expected ..
    John T.

    Sounds worse than my portable
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From hubops@hubops@ccanoemail.com to alt.home.repair on Wed Nov 11 07:04:39 2026
    From Newsgroup: alt.home.repair

    On Tue, 10 Nov 2026 22:09:57 -0500, Clare Snyder <clare@snyder.on.ca>
    wrote:

    On Tue, 10 Nov 2026 13:29:47 -0500, hubops@ccanoemail.com wrote:

    On Sat, 07 Nov 2026 15:58:11 -0500, hubops@ccanoemail.com wrote:

    On Sat, 07 Nov 2026 15:01:34 -0500, Clare Snyder <clare@snyder.on.ca> >>>wrote:

    On Sat, 07 Nov 2026 14:25:08 -0500, hubops@ccanoemail.com wrote:

    On Sat, 07 Nov 2026 12:31:22 -0500, Clare Snyder <clare@snyder.on.ca> >>>>>wrote:

    On Fri, 06 Nov 2026 17:38:24 -0500, hubops@ccanoemail.com wrote:

    After years of procrastination, I finally broke down
    and got a standby generator installed. 14 kW Generac.
    ... and IT IS NOISY !
    I've ordered a decibel meter from amazon to measure it -
    but my neighbour's cell phone app seems pretty close in my >>>>>>>estimation. It says 101 dB standing right at the noisy end
    of the unit perhaps 2 feet away from the housing.
    Standing in front of it about 2 or 3 feet away you can't shout >>>>>>>over the noise - it's gotta be 85 dB or more. The literature online >>>>>>>suggests that it is 67 dB at 23 feet - I had to retreat to about >>>>>>>30 ft. to get down to about 72 dB on the quiet end.
    Oh well .. live and learn ..
    Anyone here with experience to share ?
    B&S, Kohler, Cummins are the other brands online -
    though Generac seems to win the popularity contest
    - by far - in my area.
    John T.

    1800rpm Liquid cooled are just about all twice your size though - >>>>>>22Kw and up Generac Protector - or Cummins/Kohler/Kubota


    I bought a used Honda EM5000 in 1999 that's still going -
    it has provided emergency power to my whole house with
    no problems over these 27 + years - with fairly minimal
    load management.. So I know I don't need more than 10 kW
    in a standby unit - I just wanted a 2-cyl rather than a 1-cyl.
    The problem with the noise level isn't so much disturbing me
    or the neighbours - but rather that there's something _wrong_
    with it .. My decibel readings, next week, when I get the meter >>>>>should provide some info to complain about ..
    .. it shouldn't be 80 + dB when the specs say 67 !
    John T.
    which scale are you on? Aor C 65 Db-a could very well read 75 or 80 >>>>Db-c because C is weighted more towards low frequencies IIRC.
    The resonance of the air cooled engine block plays tricks on sound >>>>meters - or your ears - one way or the other.

    A generator MAY be 65 Db-A and 85 Db-C , or it may be 65 Db-C. even >>>>65Db-C will travel farther than 65 Db-A and be more noticeable farther >>>>away because it is a "rumble" that can be felt as well as heard.Low >>>>frequencies are not attenuated by air as much as high frequencies.



    Good point - I'm pretty sure the meter I ordered does both -
    I have no idea what the neighbour's cell phone app measures.
    ... I didn't think the difference could be that much.
    I'll find out next week.
    John T.



    Today's readings no load A / C :

    left front right

    3 ft 91 /96 80 / 90 85 / 91
    10 ft 82 / 88 75 / 85 78 / 86
    20 ft 77 / 84 70 / 80 73 / 80
    30 ft 72 / 82 67 / 80 69 / 79

    Can't stand next to it without hearing protection ..
    not what I expected ..
    John T.

    Sounds worse than my portable


    No kidding ! I'm wondering if the 1 ft stand is
    contributing to it - causing some extra resonance ..
    John T.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Retirednoguilt@HapilyRetired@fakeaddress.invalid to alt.home.repair on Wed Nov 11 09:57:00 2026
    From Newsgroup: alt.home.repair

    On 11/11/2026 7:04 AM, hubops@ccanoemail.com wrote:
    On Tue, 10 Nov 2026 22:09:57 -0500, Clare Snyder <clare@snyder.on.ca>
    wrote:

    On Tue, 10 Nov 2026 13:29:47 -0500, hubops@ccanoemail.com wrote:

    On Sat, 07 Nov 2026 15:58:11 -0500, hubops@ccanoemail.com wrote:

    On Sat, 07 Nov 2026 15:01:34 -0500, Clare Snyder <clare@snyder.on.ca>
    wrote:

    On Sat, 07 Nov 2026 14:25:08 -0500, hubops@ccanoemail.com wrote:

    On Sat, 07 Nov 2026 12:31:22 -0500, Clare Snyder <clare@snyder.on.ca> >>>>>> wrote:

    On Fri, 06 Nov 2026 17:38:24 -0500, hubops@ccanoemail.com wrote: >>>>>>>
    After years of procrastination, I finally broke down
    and got a standby generator installed. 14 kW Generac.
    ... and IT IS NOISY !
    I've ordered a decibel meter from amazon to measure it -
    but my neighbour's cell phone app seems pretty close in my
    estimation. It says 101 dB standing right at the noisy end >>>>>>>> of the unit perhaps 2 feet away from the housing.
    Standing in front of it about 2 or 3 feet away you can't shout >>>>>>>> over the noise - it's gotta be 85 dB or more. The literature online >>>>>>>> suggests that it is 67 dB at 23 feet - I had to retreat to about >>>>>>>> 30 ft. to get down to about 72 dB on the quiet end.
    Oh well .. live and learn ..
    Anyone here with experience to share ?
    B&S, Kohler, Cummins are the other brands online -
    though Generac seems to win the popularity contest
    - by far - in my area.
    John T.

    1800rpm Liquid cooled are just about all twice your size though - >>>>>>> 22Kw and up Generac Protector - or Cummins/Kohler/Kubota


    I bought a used Honda EM5000 in 1999 that's still going -
    it has provided emergency power to my whole house with
    no problems over these 27 + years - with fairly minimal
    load management.. So I know I don't need more than 10 kW
    in a standby unit - I just wanted a 2-cyl rather than a 1-cyl.
    The problem with the noise level isn't so much disturbing me
    or the neighbours - but rather that there's something _wrong_
    with it .. My decibel readings, next week, when I get the meter >>>>>> should provide some info to complain about ..
    .. it shouldn't be 80 + dB when the specs say 67 !
    John T.
    which scale are you on? Aor C 65 Db-a could very well read 75 or 80
    Db-c because C is weighted more towards low frequencies IIRC.
    The resonance of the air cooled engine block plays tricks on sound
    meters - or your ears - one way or the other.

    A generator MAY be 65 Db-A and 85 Db-C , or it may be 65 Db-C. even
    65Db-C will travel farther than 65 Db-A and be more noticeable farther >>>>> away because it is a "rumble" that can be felt as well as heard.Low
    frequencies are not attenuated by air as much as high frequencies.



    Good point - I'm pretty sure the meter I ordered does both -
    I have no idea what the neighbour's cell phone app measures.
    ... I didn't think the difference could be that much.
    I'll find out next week.
    John T.



    Today's readings no load A / C :

    left front right

    3 ft 91 /96 80 / 90 85 / 91
    10 ft 82 / 88 75 / 85 78 / 86
    20 ft 77 / 84 70 / 80 73 / 80
    30 ft 72 / 82 67 / 80 69 / 79

    Can't stand next to it without hearing protection ..
    not what I expected ..
    John T.

    Sounds worse than my portable


    No kidding ! I'm wondering if the 1 ft stand is
    contributing to it - causing some extra resonance ..
    John T.

    Realistically, when it runs, how close to it does anyone in your home
    stand? How close is the nearest neighbor's door or window? And, unless
    you have terrible electrical infrastructure in your community, how many hrs/year is the generator likely to be running? Are you violating any nuisance/noise laws where you live when circumstances justify running
    the generator?

    I grind my own coffee beans before brewing. The grinder is very loud.
    OK, so I put in ear plugs before grinding. Not that big a problem even
    though I grind beans at least twice/day.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From frank@"frank "@frank.net to alt.home.repair on Wed Nov 11 10:08:02 2026
    From Newsgroup: alt.home.repair

    On 11/11/2026 9:57 AM, Retirednoguilt wrote:
    On 11/11/2026 7:04 AM, hubops@ccanoemail.com wrote:
    On Tue, 10 Nov 2026 22:09:57 -0500, Clare Snyder <clare@snyder.on.ca>
    wrote:

    On Tue, 10 Nov 2026 13:29:47 -0500, hubops@ccanoemail.com wrote:

    On Sat, 07 Nov 2026 15:58:11 -0500, hubops@ccanoemail.com wrote:

    On Sat, 07 Nov 2026 15:01:34 -0500, Clare Snyder <clare@snyder.on.ca> >>>>> wrote:

    On Sat, 07 Nov 2026 14:25:08 -0500, hubops@ccanoemail.com wrote:

    On Sat, 07 Nov 2026 12:31:22 -0500, Clare Snyder <clare@snyder.on.ca> >>>>>>> wrote:

    On Fri, 06 Nov 2026 17:38:24 -0500, hubops@ccanoemail.com wrote: >>>>>>>>
    After years of procrastination, I finally broke down
    and got a standby generator installed. 14 kW Generac.
    ... and IT IS NOISY !
    I've ordered a decibel meter from amazon to measure it -
    but my neighbour's cell phone app seems pretty close in my
    estimation. It says 101 dB standing right at the noisy end >>>>>>>>> of the unit perhaps 2 feet away from the housing.
    Standing in front of it about 2 or 3 feet away you can't shout >>>>>>>>> over the noise - it's gotta be 85 dB or more. The literature online
    suggests that it is 67 dB at 23 feet - I had to retreat to about >>>>>>>>> 30 ft. to get down to about 72 dB on the quiet end.
    Oh well .. live and learn ..
    Anyone here with experience to share ?
    B&S, Kohler, Cummins are the other brands online -
    though Generac seems to win the popularity contest
    - by far - in my area.
    John T.

    1800rpm Liquid cooled are just about all twice your size though - >>>>>>>> 22Kw and up Generac Protector - or Cummins/Kohler/Kubota


    I bought a used Honda EM5000 in 1999 that's still going -
    it has provided emergency power to my whole house with
    no problems over these 27 + years - with fairly minimal
    load management.. So I know I don't need more than 10 kW
    in a standby unit - I just wanted a 2-cyl rather than a 1-cyl. >>>>>>> The problem with the noise level isn't so much disturbing me
    or the neighbours - but rather that there's something _wrong_
    with it .. My decibel readings, next week, when I get the meter >>>>>>> should provide some info to complain about ..
    .. it shouldn't be 80 + dB when the specs say 67 !
    John T.
    which scale are you on? Aor C 65 Db-a could very well read 75 or 80 >>>>>> Db-c because C is weighted more towards low frequencies IIRC.
    The resonance of the air cooled engine block plays tricks on sound >>>>>> meters - or your ears - one way or the other.

    A generator MAY be 65 Db-A and 85 Db-C , or it may be 65 Db-C. even >>>>>> 65Db-C will travel farther than 65 Db-A and be more noticeable farther >>>>>> away because it is a "rumble" that can be felt as well as heard.Low >>>>>> frequencies are not attenuated by air as much as high frequencies. >>>>>>


    Good point - I'm pretty sure the meter I ordered does both -
    I have no idea what the neighbour's cell phone app measures.
    ... I didn't think the difference could be that much.
    I'll find out next week.
    John T.



    Today's readings no load A / C :

    left front right

    3 ft 91 /96 80 / 90 85 / 91
    10 ft 82 / 88 75 / 85 78 / 86
    20 ft 77 / 84 70 / 80 73 / 80
    30 ft 72 / 82 67 / 80 69 / 79

    Can't stand next to it without hearing protection ..
    not what I expected ..
    John T.

    Sounds worse than my portable


    No kidding ! I'm wondering if the 1 ft stand is
    contributing to it - causing some extra resonance ..
    John T.

    Realistically, when it runs, how close to it does anyone in your home
    stand? How close is the nearest neighbor's door or window? And, unless
    you have terrible electrical infrastructure in your community, how many hrs/year is the generator likely to be running? Are you violating any nuisance/noise laws where you live when circumstances justify running
    the generator?

    I grind my own coffee beans before brewing. The grinder is very loud.
    OK, so I put in ear plugs before grinding. Not that big a problem even though I grind beans at least twice/day.

    I had considered this too with my generator. It is near my garage door
    and I take it out too use it under the overhang. There is a brick wall
    near it and it is very noisy. It might be a year between use and when
    used it is at night and raining. Would be bothersome to drag out and
    build a sound barrier around it. The only ones annoyed are me and my
    wife so we just tolerate it.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From hubops@hubops@ccanoemail.com to alt.home.repair on Wed Nov 11 11:42:37 2026
    From Newsgroup: alt.home.repair

    On Wed, 11 Nov 2026 09:57:00 -0500, Retirednoguilt <HapilyRetired@fakeaddress.invalid> wrote:

    On 11/11/2026 7:04 AM, hubops@ccanoemail.com wrote:
    On Tue, 10 Nov 2026 22:09:57 -0500, Clare Snyder <clare@snyder.on.ca>
    wrote:

    On Tue, 10 Nov 2026 13:29:47 -0500, hubops@ccanoemail.com wrote:

    On Sat, 07 Nov 2026 15:58:11 -0500, hubops@ccanoemail.com wrote:

    On Sat, 07 Nov 2026 15:01:34 -0500, Clare Snyder <clare@snyder.on.ca> >>>>> wrote:

    On Sat, 07 Nov 2026 14:25:08 -0500, hubops@ccanoemail.com wrote:

    On Sat, 07 Nov 2026 12:31:22 -0500, Clare Snyder <clare@snyder.on.ca> >>>>>>> wrote:

    On Fri, 06 Nov 2026 17:38:24 -0500, hubops@ccanoemail.com wrote: >>>>>>>>
    After years of procrastination, I finally broke down
    and got a standby generator installed. 14 kW Generac.
    ... and IT IS NOISY !
    I've ordered a decibel meter from amazon to measure it -
    but my neighbour's cell phone app seems pretty close in my
    estimation. It says 101 dB standing right at the noisy end >>>>>>>>> of the unit perhaps 2 feet away from the housing.
    Standing in front of it about 2 or 3 feet away you can't shout >>>>>>>>> over the noise - it's gotta be 85 dB or more. The literature online
    suggests that it is 67 dB at 23 feet - I had to retreat to about >>>>>>>>> 30 ft. to get down to about 72 dB on the quiet end.
    Oh well .. live and learn ..
    Anyone here with experience to share ?
    B&S, Kohler, Cummins are the other brands online -
    though Generac seems to win the popularity contest
    - by far - in my area.
    John T.

    1800rpm Liquid cooled are just about all twice your size though - >>>>>>>> 22Kw and up Generac Protector - or Cummins/Kohler/Kubota


    I bought a used Honda EM5000 in 1999 that's still going -
    it has provided emergency power to my whole house with
    no problems over these 27 + years - with fairly minimal
    load management.. So I know I don't need more than 10 kW
    in a standby unit - I just wanted a 2-cyl rather than a 1-cyl. >>>>>>> The problem with the noise level isn't so much disturbing me
    or the neighbours - but rather that there's something _wrong_ >>>>>>> with it .. My decibel readings, next week, when I get the meter >>>>>>> should provide some info to complain about ..
    .. it shouldn't be 80 + dB when the specs say 67 !
    John T.
    which scale are you on? Aor C 65 Db-a could very well read 75 or 80 >>>>>> Db-c because C is weighted more towards low frequencies IIRC.
    The resonance of the air cooled engine block plays tricks on sound >>>>>> meters - or your ears - one way or the other.

    A generator MAY be 65 Db-A and 85 Db-C , or it may be 65 Db-C. even >>>>>> 65Db-C will travel farther than 65 Db-A and be more noticeable farther >>>>>> away because it is a "rumble" that can be felt as well as heard.Low >>>>>> frequencies are not attenuated by air as much as high frequencies. >>>>>>


    Good point - I'm pretty sure the meter I ordered does both -
    I have no idea what the neighbour's cell phone app measures.
    ... I didn't think the difference could be that much.
    I'll find out next week.
    John T.



    Today's readings no load A / C :

    left front right

    3 ft 91 /96 80 / 90 85 / 91
    10 ft 82 / 88 75 / 85 78 / 86
    20 ft 77 / 84 70 / 80 73 / 80
    30 ft 72 / 82 67 / 80 69 / 79

    Can't stand next to it without hearing protection ..
    not what I expected ..
    John T.

    Sounds worse than my portable


    No kidding ! I'm wondering if the 1 ft stand is
    contributing to it - causing some extra resonance ..
    John T.

    Realistically, when it runs, how close to it does anyone in your home
    stand? How close is the nearest neighbor's door or window? And, unless
    you have terrible electrical infrastructure in your community, how many >hrs/year is the generator likely to be running? Are you violating any >nuisance/noise laws where you live when circumstances justify running
    the generator?



    No such problems - just my fussiness - that a generator
    that is advertised to run at 70 dB full load is actually 80 dB
    at no load .. perhaps there's something wrong ?
    80 dB is _twice as loud_ as 70 dB ..
    ... and it won't spill its guts until 2 hours into the ice storm
    of the century ..
    John T.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Clare Snyder@clare@snyder.on.ca to alt.home.repair on Wed Nov 11 20:06:51 2026
    From Newsgroup: alt.home.repair

    On Wed, 11 Nov 2026 07:04:39 -0500, hubops@ccanoemail.com wrote:

    On Tue, 10 Nov 2026 22:09:57 -0500, Clare Snyder <clare@snyder.on.ca>
    wrote:

    On Tue, 10 Nov 2026 13:29:47 -0500, hubops@ccanoemail.com wrote:

    On Sat, 07 Nov 2026 15:58:11 -0500, hubops@ccanoemail.com wrote:

    On Sat, 07 Nov 2026 15:01:34 -0500, Clare Snyder <clare@snyder.on.ca> >>>>wrote:

    On Sat, 07 Nov 2026 14:25:08 -0500, hubops@ccanoemail.com wrote:

    On Sat, 07 Nov 2026 12:31:22 -0500, Clare Snyder <clare@snyder.on.ca> >>>>>>wrote:

    On Fri, 06 Nov 2026 17:38:24 -0500, hubops@ccanoemail.com wrote:

    After years of procrastination, I finally broke down
    and got a standby generator installed. 14 kW Generac.
    ... and IT IS NOISY !
    I've ordered a decibel meter from amazon to measure it -
    but my neighbour's cell phone app seems pretty close in my >>>>>>>>estimation. It says 101 dB standing right at the noisy end >>>>>>>>of the unit perhaps 2 feet away from the housing.
    Standing in front of it about 2 or 3 feet away you can't shout >>>>>>>>over the noise - it's gotta be 85 dB or more. The literature online >>>>>>>>suggests that it is 67 dB at 23 feet - I had to retreat to about >>>>>>>>30 ft. to get down to about 72 dB on the quiet end.
    Oh well .. live and learn ..
    Anyone here with experience to share ?
    B&S, Kohler, Cummins are the other brands online -
    though Generac seems to win the popularity contest
    - by far - in my area.
    John T.

    1800rpm Liquid cooled are just about all twice your size though - >>>>>>>22Kw and up Generac Protector - or Cummins/Kohler/Kubota


    I bought a used Honda EM5000 in 1999 that's still going -
    it has provided emergency power to my whole house with
    no problems over these 27 + years - with fairly minimal
    load management.. So I know I don't need more than 10 kW
    in a standby unit - I just wanted a 2-cyl rather than a 1-cyl.
    The problem with the noise level isn't so much disturbing me
    or the neighbours - but rather that there's something _wrong_ >>>>>>with it .. My decibel readings, next week, when I get the meter >>>>>>should provide some info to complain about ..
    .. it shouldn't be 80 + dB when the specs say 67 !
    John T.
    which scale are you on? Aor C 65 Db-a could very well read 75 or 80 >>>>>Db-c because C is weighted more towards low frequencies IIRC.
    The resonance of the air cooled engine block plays tricks on sound >>>>>meters - or your ears - one way or the other.

    A generator MAY be 65 Db-A and 85 Db-C , or it may be 65 Db-C. even >>>>>65Db-C will travel farther than 65 Db-A and be more noticeable farther >>>>>away because it is a "rumble" that can be felt as well as heard.Low >>>>>frequencies are not attenuated by air as much as high frequencies.



    Good point - I'm pretty sure the meter I ordered does both -
    I have no idea what the neighbour's cell phone app measures.
    ... I didn't think the difference could be that much.
    I'll find out next week.
    John T.



    Today's readings no load A / C :

    left front right

    3 ft 91 /96 80 / 90 85 / 91
    10 ft 82 / 88 75 / 85 78 / 86
    20 ft 77 / 84 70 / 80 73 / 80
    30 ft 72 / 82 67 / 80 69 / 79

    Can't stand next to it without hearing protection ..
    not what I expected ..
    John T.

    Sounds worse than my portable


    No kidding ! I'm wondering if the 1 ft stand is
    contributing to it - causing some extra resonance ..
    John T.
    what is the stand made of?? Anything other than compacted earth or
    concrete WILL RESONATE. If it is on a stick framed lumber stand, GET
    RID OF IT!!!!!!!
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Black Republican@black.republican@jury.duty to alt.home.repair on Thu Nov 12 06:54:51 2026
    From Newsgroup: alt.home.repair

    On 11/6/26 17:38, hubops@ccanoemail.com wrote:
    After years of procrastination, I finally broke down
    and got a standby generator installed. 14 kW Generac.
    ... and IT IS NOISY !
    I've ordered a decibel meter from amazon to measure it -
    but my neighbour's cell phone app seems pretty close in my
    estimation. It says 101 dB standing right at the noisy end
    of the unit perhaps 2 feet away from the housing.
    Standing in front of it about 2 or 3 feet away you can't shout
    over the noise - it's gotta be 85 dB or more. The literature online suggests that it is 67 dB at 23 feet - I had to retreat to about
    30 ft. to get down to about 72 dB on the quiet end.
    Oh well .. live and learn ..
    Anyone here with experience to share ?
    B&S, Kohler, Cummins are the other brands online -
    though Generac seems to win the popularity contest
    - by far - in my area.
    John T.



    https://powerequipment.honda.com/generators/models/eu7000is

    Very quiet. Can't hear it running when I'm inside the house.

    Because there are so many sticky-fingered Democrat porch pirates, you do
    need to keep it hidden. Maybe put it in an old fashioned outhouse in
    your back yard?
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Cindy Hamilton@chamilton5280@invalid.com to alt.home.repair on Thu Nov 12 12:31:14 2026
    From Newsgroup: alt.home.repair

    On 2026-11-12, Black Republican <black.republican@jury.duty> wrote:
    On 11/6/26 17:38, hubops@ccanoemail.com wrote:
    After years of procrastination, I finally broke down
    and got a standby generator installed. 14 kW Generac.
    ... and IT IS NOISY !
    I've ordered a decibel meter from amazon to measure it -
    but my neighbour's cell phone app seems pretty close in my
    estimation. It says 101 dB standing right at the noisy end
    of the unit perhaps 2 feet away from the housing.
    Standing in front of it about 2 or 3 feet away you can't shout
    over the noise - it's gotta be 85 dB or more. The literature online
    suggests that it is 67 dB at 23 feet - I had to retreat to about
    30 ft. to get down to about 72 dB on the quiet end.
    Oh well .. live and learn ..
    Anyone here with experience to share ?
    B&S, Kohler, Cummins are the other brands online -
    though Generac seems to win the popularity contest
    - by far - in my area.
    John T.



    https://powerequipment.honda.com/generators/models/eu7000is

    Very quiet. Can't hear it running when I'm inside the house.

    Because there are so many sticky-fingered Democrat porch pirates, you do need to keep it hidden. Maybe put it in an old fashioned outhouse in
    your back yard?

    That's a portable. Not remotely the same as the permanently
    installed generator hubops has, which might be this one:

    https://apelectric.com/generac-7258-14kw-generator/
    --
    Cindy Hamilton
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From hubops@hubops@ccanoemail.com to alt.home.repair on Thu Nov 12 09:34:40 2026
    From Newsgroup: alt.home.repair

    On Wed, 11 Nov 2026 20:06:51 -0500, Clare Snyder <clare@snyder.on.ca>
    wrote:

    On Wed, 11 Nov 2026 07:04:39 -0500, hubops@ccanoemail.com wrote:

    On Tue, 10 Nov 2026 22:09:57 -0500, Clare Snyder <clare@snyder.on.ca> >>wrote:

    On Tue, 10 Nov 2026 13:29:47 -0500, hubops@ccanoemail.com wrote:

    On Sat, 07 Nov 2026 15:58:11 -0500, hubops@ccanoemail.com wrote:

    On Sat, 07 Nov 2026 15:01:34 -0500, Clare Snyder <clare@snyder.on.ca> >>>>>wrote:

    On Sat, 07 Nov 2026 14:25:08 -0500, hubops@ccanoemail.com wrote:

    On Sat, 07 Nov 2026 12:31:22 -0500, Clare Snyder <clare@snyder.on.ca> >>>>>>>wrote:

    On Fri, 06 Nov 2026 17:38:24 -0500, hubops@ccanoemail.com wrote: >>>>>>>>
    After years of procrastination, I finally broke down
    and got a standby generator installed. 14 kW Generac.
    ... and IT IS NOISY !
    I've ordered a decibel meter from amazon to measure it -
    but my neighbour's cell phone app seems pretty close in my >>>>>>>>>estimation. It says 101 dB standing right at the noisy end >>>>>>>>>of the unit perhaps 2 feet away from the housing.
    Standing in front of it about 2 or 3 feet away you can't shout >>>>>>>>>over the noise - it's gotta be 85 dB or more. The literature online >>>>>>>>>suggests that it is 67 dB at 23 feet - I had to retreat to about >>>>>>>>>30 ft. to get down to about 72 dB on the quiet end.
    Oh well .. live and learn ..
    Anyone here with experience to share ?
    B&S, Kohler, Cummins are the other brands online -
    though Generac seems to win the popularity contest
    - by far - in my area.
    John T.

    1800rpm Liquid cooled are just about all twice your size though - >>>>>>>>22Kw and up Generac Protector - or Cummins/Kohler/Kubota


    I bought a used Honda EM5000 in 1999 that's still going -
    it has provided emergency power to my whole house with
    no problems over these 27 + years - with fairly minimal
    load management.. So I know I don't need more than 10 kW
    in a standby unit - I just wanted a 2-cyl rather than a 1-cyl. >>>>>>> The problem with the noise level isn't so much disturbing me >>>>>>>or the neighbours - but rather that there's something _wrong_ >>>>>>>with it .. My decibel readings, next week, when I get the meter >>>>>>>should provide some info to complain about ..
    .. it shouldn't be 80 + dB when the specs say 67 !
    John T.
    which scale are you on? Aor C 65 Db-a could very well read 75 or 80 >>>>>>Db-c because C is weighted more towards low frequencies IIRC.
    The resonance of the air cooled engine block plays tricks on sound >>>>>>meters - or your ears - one way or the other.

    A generator MAY be 65 Db-A and 85 Db-C , or it may be 65 Db-C. even >>>>>>65Db-C will travel farther than 65 Db-A and be more noticeable farther >>>>>>away because it is a "rumble" that can be felt as well as heard.Low >>>>>>frequencies are not attenuated by air as much as high frequencies.



    Good point - I'm pretty sure the meter I ordered does both -
    I have no idea what the neighbour's cell phone app measures.
    ... I didn't think the difference could be that much.
    I'll find out next week.
    John T.



    Today's readings no load A / C :

    left front right

    3 ft 91 /96 80 / 90 85 / 91
    10 ft 82 / 88 75 / 85 78 / 86
    20 ft 77 / 84 70 / 80 73 / 80
    30 ft 72 / 82 67 / 80 69 / 79

    Can't stand next to it without hearing protection ..
    not what I expected ..
    John T.

    Sounds worse than my portable


    No kidding ! I'm wondering if the 1 ft stand is
    contributing to it - causing some extra resonance ..
    John T.
    what is the stand made of?? Anything other than compacted earth or
    concrete WILL RESONATE. If it is on a stick framed lumber stand, GET
    RID OF IT!!!!!!!



    Like this - on a poured concrete pad.

    https://generator-stands.com/shop

    John T.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From hubops@hubops@ccanoemail.com to alt.home.repair on Thu Nov 12 09:43:13 2026
    From Newsgroup: alt.home.repair

    On Thu, 12 Nov 2026 12:31:14 -0000 (UTC), Cindy Hamilton <chamilton5280@invalid.com> wrote:

    On 2026-11-12, Black Republican <black.republican@jury.duty> wrote:
    On 11/6/26 17:38, hubops@ccanoemail.com wrote:
    After years of procrastination, I finally broke down
    and got a standby generator installed. 14 kW Generac.
    ... and IT IS NOISY !
    I've ordered a decibel meter from amazon to measure it -
    but my neighbour's cell phone app seems pretty close in my
    estimation. It says 101 dB standing right at the noisy end
    of the unit perhaps 2 feet away from the housing.
    Standing in front of it about 2 or 3 feet away you can't shout
    over the noise - it's gotta be 85 dB or more. The literature online
    suggests that it is 67 dB at 23 feet - I had to retreat to about
    30 ft. to get down to about 72 dB on the quiet end.
    Oh well .. live and learn ..
    Anyone here with experience to share ?
    B&S, Kohler, Cummins are the other brands online -
    though Generac seems to win the popularity contest
    - by far - in my area.
    John T.



    https://powerequipment.honda.com/generators/models/eu7000is

    Very quiet. Can't hear it running when I'm inside the house.

    Because there are so many sticky-fingered Democrat porch pirates, you do
    need to keep it hidden. Maybe put it in an old fashioned outhouse in
    your back yard?

    That's a portable. Not remotely the same as the permanently
    installed generator hubops has, which might be this one:

    https://apelectric.com/generac-7258-14kw-generator/




    The Honda portable costs almost as much as the Generac
    here in tarriff-land :

    https://kwhonda.com/inventory/lawn-garden-power/2026-honda-eu7000isct1-ultra-quiet-42

    John T.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Black Republican@black.republican@jury.duty to alt.home.repair on Thu Nov 12 11:26:25 2026
    From Newsgroup: alt.home.repair

    On 11/12/26 07:31, Cindy Hamilton wrote:
    On 2026-11-12, Black Republican <black.republican@jury.duty> wrote:
    On 11/6/26 17:38, hubops@ccanoemail.com wrote:
    After years of procrastination, I finally broke down
    and got a standby generator installed. 14 kW Generac.
    ... and IT IS NOISY !
    I've ordered a decibel meter from amazon to measure it -
    but my neighbour's cell phone app seems pretty close in my
    estimation. It says 101 dB standing right at the noisy end
    of the unit perhaps 2 feet away from the housing.
    Standing in front of it about 2 or 3 feet away you can't shout
    over the noise - it's gotta be 85 dB or more. The literature online
    suggests that it is 67 dB at 23 feet - I had to retreat to about
    30 ft. to get down to about 72 dB on the quiet end.
    Oh well .. live and learn ..
    Anyone here with experience to share ?
    B&S, Kohler, Cummins are the other brands online -
    though Generac seems to win the popularity contest
    - by far - in my area.
    John T.



    https://powerequipment.honda.com/generators/models/eu7000is

    Very quiet. Can't hear it running when I'm inside the house.

    Because there are so many sticky-fingered Democrat porch pirates, you do
    need to keep it hidden. Maybe put it in an old fashioned outhouse in
    your back yard?

    That's a portable. Not remotely the same as the permanently
    installed generator hubops has, which might be this one:

    https://apelectric.com/generac-7258-14kw-generator/


    According to far left giggle, the word "permanent" primarily functions
    as an adjective meaning lasting for a long time, indefinitely, or
    forever without fundamental change.

    In my opinion, there's nothing "permanent" about a Gener-wreck install.

    FWIW, I had a 14kW Gener-Wreck but the engine puked. I tried to buy a
    new one but apparently a secret code is needed to activate it. F' that.
    So I bought the Honda eu7000is. Power goes out I roll it out the back of
    the garage, hit the start button and then go flip the breaker interlock.

    And if the Honda pukes, I can get a new one from the local Juan Deere
    dealer in under 2 hours.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Retirednoguilt@HapilyRetired@fakeaddress.invalid to alt.home.repair on Thu Nov 12 12:07:47 2026
    From Newsgroup: alt.home.repair

    On 11/12/2026 11:26 AM, Black Republican wrote:
    On 11/12/26 07:31, Cindy Hamilton wrote:
    On 2026-11-12, Black Republican <black.republican@jury.duty> wrote:
    On 11/6/26 17:38, hubops@ccanoemail.com wrote:
    After years of procrastination, I finally broke down
    and got a standby generator installed. 14 kW Generac.
    ... and IT IS NOISY !
    I've ordered a decibel meter from amazon to measure it -
    but my neighbour's cell phone app seems pretty close in my
    estimation. It says 101 dB standing right at the noisy end
    of the unit perhaps 2 feet away from the housing.
    Standing in front of it about 2 or 3 feet away you can't shout
    over the noise - it's gotta be 85 dB or more. The literature online >>>> suggests that it is 67 dB at 23 feet - I had to retreat to about
    30 ft. to get down to about 72 dB on the quiet end.
    Oh well .. live and learn ..
    Anyone here with experience to share ?
    B&S, Kohler, Cummins are the other brands online -
    though Generac seems to win the popularity contest
    - by far - in my area.
    John T.



    https://powerequipment.honda.com/generators/models/eu7000is

    Very quiet. Can't hear it running when I'm inside the house.

    Because there are so many sticky-fingered Democrat porch pirates, you do >>> need to keep it hidden. Maybe put it in an old fashioned outhouse in
    your back yard?

    That's a portable. Not remotely the same as the permanently
    installed generator hubops has, which might be this one:

    https://apelectric.com/generac-7258-14kw-generator/


    According to far left giggle, the word "permanent" primarily functions
    as an adjective meaning lasting for a long time, indefinitely, or
    forever without fundamental change.

    In my opinion, there's nothing "permanent" about a Gener-wreck install.

    FWIW, I had a 14kW Gener-Wreck but the engine puked. I tried to buy a
    new one but apparently a secret code is needed to activate it. F' that.
    So I bought the Honda eu7000is. Power goes out I roll it out the back of
    the garage, hit the start button and then go flip the breaker interlock.

    And if the Honda pukes, I can get a new one from the local Juan Deere
    dealer in under 2 hours.

    You're so talented!!
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Clare Snyder@clare@snyder.on.ca to alt.home.repair on Thu Nov 12 12:12:25 2026
    From Newsgroup: alt.home.repair

    On Thu, 12 Nov 2026 09:34:40 -0500, hubops@ccanoemail.com wrote:

    On Wed, 11 Nov 2026 20:06:51 -0500, Clare Snyder <clare@snyder.on.ca>
    wrote:

    On Wed, 11 Nov 2026 07:04:39 -0500, hubops@ccanoemail.com wrote:

    On Tue, 10 Nov 2026 22:09:57 -0500, Clare Snyder <clare@snyder.on.ca> >>>wrote:

    On Tue, 10 Nov 2026 13:29:47 -0500, hubops@ccanoemail.com wrote:

    On Sat, 07 Nov 2026 15:58:11 -0500, hubops@ccanoemail.com wrote:

    On Sat, 07 Nov 2026 15:01:34 -0500, Clare Snyder <clare@snyder.on.ca> >>>>>>wrote:

    On Sat, 07 Nov 2026 14:25:08 -0500, hubops@ccanoemail.com wrote:

    On Sat, 07 Nov 2026 12:31:22 -0500, Clare Snyder <clare@snyder.on.ca> >>>>>>>>wrote:

    On Fri, 06 Nov 2026 17:38:24 -0500, hubops@ccanoemail.com wrote: >>>>>>>>>
    After years of procrastination, I finally broke down
    and got a standby generator installed. 14 kW Generac.
    ... and IT IS NOISY !
    I've ordered a decibel meter from amazon to measure it - >>>>>>>>>>but my neighbour's cell phone app seems pretty close in my >>>>>>>>>>estimation. It says 101 dB standing right at the noisy end >>>>>>>>>>of the unit perhaps 2 feet away from the housing.
    Standing in front of it about 2 or 3 feet away you can't shout >>>>>>>>>>over the noise - it's gotta be 85 dB or more. The literature online
    suggests that it is 67 dB at 23 feet - I had to retreat to about >>>>>>>>>>30 ft. to get down to about 72 dB on the quiet end.
    Oh well .. live and learn ..
    Anyone here with experience to share ?
    B&S, Kohler, Cummins are the other brands online -
    though Generac seems to win the popularity contest
    - by far - in my area.
    John T.

    1800rpm Liquid cooled are just about all twice your size though - >>>>>>>>>22Kw and up Generac Protector - or Cummins/Kohler/Kubota


    I bought a used Honda EM5000 in 1999 that's still going -
    it has provided emergency power to my whole house with
    no problems over these 27 + years - with fairly minimal
    load management.. So I know I don't need more than 10 kW
    in a standby unit - I just wanted a 2-cyl rather than a 1-cyl. >>>>>>>> The problem with the noise level isn't so much disturbing me >>>>>>>>or the neighbours - but rather that there's something _wrong_ >>>>>>>>with it .. My decibel readings, next week, when I get the meter >>>>>>>>should provide some info to complain about ..
    .. it shouldn't be 80 + dB when the specs say 67 !
    John T.
    which scale are you on? Aor C 65 Db-a could very well read 75 or 80 >>>>>>>Db-c because C is weighted more towards low frequencies IIRC.
    The resonance of the air cooled engine block plays tricks on sound >>>>>>>meters - or your ears - one way or the other.

    A generator MAY be 65 Db-A and 85 Db-C , or it may be 65 Db-C. even >>>>>>>65Db-C will travel farther than 65 Db-A and be more noticeable farther >>>>>>>away because it is a "rumble" that can be felt as well as heard.Low >>>>>>>frequencies are not attenuated by air as much as high frequencies. >>>>>>>


    Good point - I'm pretty sure the meter I ordered does both -
    I have no idea what the neighbour's cell phone app measures.
    ... I didn't think the difference could be that much.
    I'll find out next week.
    John T.



    Today's readings no load A / C :

    left front right

    3 ft 91 /96 80 / 90 85 / 91
    10 ft 82 / 88 75 / 85 78 / 86
    20 ft 77 / 84 70 / 80 73 / 80
    30 ft 72 / 82 67 / 80 69 / 79

    Can't stand next to it without hearing protection ..
    not what I expected ..
    John T.

    Sounds worse than my portable


    No kidding ! I'm wondering if the 1 ft stand is
    contributing to it - causing some extra resonance ..
    John T.
    what is the stand made of?? Anything other than compacted earth or >>concrete WILL RESONATE. If it is on a stick framed lumber stand, GET
    RID OF IT!!!!!!!



    Like this - on a poured concrete pad.

    https://generator-stands.com/shop

    John T.
    i prefer them rubber mounted directly to concrete pad - eliminates the
    lower surface radiating noise into open air.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Clare Snyder@clare@snyder.on.ca to alt.home.repair on Thu Nov 12 12:14:39 2026
    From Newsgroup: alt.home.repair

    On Thu, 12 Nov 2026 11:26:25 -0500, Black Republican <black.republican@jury.duty> wrote:

    On 11/12/26 07:31, Cindy Hamilton wrote:
    On 2026-11-12, Black Republican <black.republican@jury.duty> wrote:
    On 11/6/26 17:38, hubops@ccanoemail.com wrote:
    After years of procrastination, I finally broke down
    and got a standby generator installed. 14 kW Generac.
    ... and IT IS NOISY !
    I've ordered a decibel meter from amazon to measure it -
    but my neighbour's cell phone app seems pretty close in my
    estimation. It says 101 dB standing right at the noisy end
    of the unit perhaps 2 feet away from the housing.
    Standing in front of it about 2 or 3 feet away you can't shout
    over the noise - it's gotta be 85 dB or more. The literature online >>>> suggests that it is 67 dB at 23 feet - I had to retreat to about
    30 ft. to get down to about 72 dB on the quiet end.
    Oh well .. live and learn ..
    Anyone here with experience to share ?
    B&S, Kohler, Cummins are the other brands online -
    though Generac seems to win the popularity contest
    - by far - in my area.
    John T.



    https://powerequipment.honda.com/generators/models/eu7000is

    Very quiet. Can't hear it running when I'm inside the house.

    Because there are so many sticky-fingered Democrat porch pirates, you do >>> need to keep it hidden. Maybe put it in an old fashioned outhouse in
    your back yard?

    That's a portable. Not remotely the same as the permanently
    installed generator hubops has, which might be this one:

    https://apelectric.com/generac-7258-14kw-generator/


    According to far left giggle, the word "permanent" primarily functions
    as an adjective meaning lasting for a long time, indefinitely, or
    forever without fundamental change.

    In my opinion, there's nothing "permanent" about a Gener-wreck install.

    FWIW, I had a 14kW Gener-Wreck but the engine puked. I tried to buy a
    new one but apparently a secret code is needed to activate it. F' that.
    So I bought the Honda eu7000is. Power goes out I roll it out the back of
    the garage, hit the start button and then go flip the breaker interlock.

    And if the Honda pukes, I can get a new one from the local Juan Deere
    dealer in under 2 hours.
    I WAS going to say GenerAC doesn't have the best reputation - why
    they want you to "exercise" them monthly. (some would say excorcise)
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From danny burstein@dannyb@panix.com to alt.home.repair on Thu Nov 12 17:20:39 2026
    From Newsgroup: alt.home.repair

    In <mtsbfltngf2njg5og5vp0385ka0du08spq@4ax.com> Clare Snyder <clare@snyder.on.ca> writes:

    [snip]

    I WAS going to say GenerAC doesn't have the best reputation - why
    they want you to "exercise" them monthly. (some would say excorcise)

    we have one of the 10 kw natural gas units. In my discussions with
    them they DID have quieter, longer usage, etc., ones, but this is
    fine for our expected needs.

    Note you (the homeowner) can set it to self-test weekly,
    every other week, or once/month. (the installer chose every
    seven days. I switched it to bi-weekly)

    They also push a yearly visit to do all the stanrads (oil and
    self-starting battery check, etc.).
    --
    _____________________________________________________
    Knowledge may be power, but communications is the key
    dannyb@panix.com
    [to foil spammers, my address has been double rot-13 encoded]
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From hubops@hubops@ccanoemail.com to alt.home.repair on Thu Nov 12 12:36:20 2026
    From Newsgroup: alt.home.repair

    On Thu, 12 Nov 2026 12:12:25 -0500, Clare Snyder <clare@snyder.on.ca>
    wrote:

    On Thu, 12 Nov 2026 09:34:40 -0500, hubops@ccanoemail.com wrote:

    On Wed, 11 Nov 2026 20:06:51 -0500, Clare Snyder <clare@snyder.on.ca> >>wrote:

    On Wed, 11 Nov 2026 07:04:39 -0500, hubops@ccanoemail.com wrote:

    On Tue, 10 Nov 2026 22:09:57 -0500, Clare Snyder <clare@snyder.on.ca> >>>>wrote:

    On Tue, 10 Nov 2026 13:29:47 -0500, hubops@ccanoemail.com wrote:

    On Sat, 07 Nov 2026 15:58:11 -0500, hubops@ccanoemail.com wrote:

    On Sat, 07 Nov 2026 15:01:34 -0500, Clare Snyder <clare@snyder.on.ca> >>>>>>>wrote:

    On Sat, 07 Nov 2026 14:25:08 -0500, hubops@ccanoemail.com wrote: >>>>>>>>
    On Sat, 07 Nov 2026 12:31:22 -0500, Clare Snyder <clare@snyder.on.ca> >>>>>>>>>wrote:

    On Fri, 06 Nov 2026 17:38:24 -0500, hubops@ccanoemail.com wrote: >>>>>>>>>>
    After years of procrastination, I finally broke down
    and got a standby generator installed. 14 kW Generac.
    ... and IT IS NOISY !
    I've ordered a decibel meter from amazon to measure it - >>>>>>>>>>>but my neighbour's cell phone app seems pretty close in my >>>>>>>>>>>estimation. It says 101 dB standing right at the noisy end >>>>>>>>>>>of the unit perhaps 2 feet away from the housing.
    Standing in front of it about 2 or 3 feet away you can't shout >>>>>>>>>>>over the noise - it's gotta be 85 dB or more. The literature online
    suggests that it is 67 dB at 23 feet - I had to retreat to about >>>>>>>>>>>30 ft. to get down to about 72 dB on the quiet end.
    Oh well .. live and learn ..
    Anyone here with experience to share ?
    B&S, Kohler, Cummins are the other brands online - >>>>>>>>>>>though Generac seems to win the popularity contest
    - by far - in my area.
    John T.

    1800rpm Liquid cooled are just about all twice your size though - >>>>>>>>>>22Kw and up Generac Protector - or Cummins/Kohler/Kubota


    I bought a used Honda EM5000 in 1999 that's still going - >>>>>>>>>it has provided emergency power to my whole house with
    no problems over these 27 + years - with fairly minimal
    load management.. So I know I don't need more than 10 kW
    in a standby unit - I just wanted a 2-cyl rather than a 1-cyl. >>>>>>>>> The problem with the noise level isn't so much disturbing me >>>>>>>>>or the neighbours - but rather that there's something _wrong_ >>>>>>>>>with it .. My decibel readings, next week, when I get the meter >>>>>>>>>should provide some info to complain about ..
    .. it shouldn't be 80 + dB when the specs say 67 !
    John T.
    which scale are you on? Aor C 65 Db-a could very well read 75 or 80 >>>>>>>>Db-c because C is weighted more towards low frequencies IIRC. >>>>>>>>The resonance of the air cooled engine block plays tricks on sound >>>>>>>>meters - or your ears - one way or the other.

    A generator MAY be 65 Db-A and 85 Db-C , or it may be 65 Db-C. even >>>>>>>>65Db-C will travel farther than 65 Db-A and be more noticeable farther >>>>>>>>away because it is a "rumble" that can be felt as well as heard.Low >>>>>>>>frequencies are not attenuated by air as much as high frequencies. >>>>>>>>


    Good point - I'm pretty sure the meter I ordered does both - >>>>>>>I have no idea what the neighbour's cell phone app measures.
    ... I didn't think the difference could be that much.
    I'll find out next week.
    John T.



    Today's readings no load A / C :

    left front right

    3 ft 91 /96 80 / 90 85 / 91
    10 ft 82 / 88 75 / 85 78 / 86
    20 ft 77 / 84 70 / 80 73 / 80
    30 ft 72 / 82 67 / 80 69 / 79

    Can't stand next to it without hearing protection ..
    not what I expected ..
    John T.

    Sounds worse than my portable


    No kidding ! I'm wondering if the 1 ft stand is
    contributing to it - causing some extra resonance ..
    John T.
    what is the stand made of?? Anything other than compacted earth or >>>concrete WILL RESONATE. If it is on a stick framed lumber stand, GET
    RID OF IT!!!!!!!



    Like this - on a poured concrete pad.

    https://generator-stands.com/shop

    John T.
    i prefer them rubber mounted directly to concrete pad - eliminates the
    lower surface radiating noise into open air.



    The contractor recommended the stand to keep it from
    getting snowed-in so easily - seemed like a good idea
    at the time ..
    John T.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From hubops@hubops@ccanoemail.com to alt.home.repair on Thu Nov 12 12:41:39 2026
    From Newsgroup: alt.home.repair

    On Thu, 12 Nov 2026 17:20:39 -0000 (UTC), danny burstein
    <dannyb@panix.com> wrote:

    In <mtsbfltngf2njg5og5vp0385ka0du08spq@4ax.com> Clare Snyder <clare@snyder.on.ca> writes:

    [snip]

    I WAS going to say GenerAC doesn't have the best reputation - why
    they want you to "exercise" them monthly. (some would say excorcise)

    we have one of the 10 kw natural gas units. In my discussions with
    them they DID have quieter, longer usage, etc., ones, but this is
    fine for our expected needs.

    Note you (the homeowner) can set it to self-test weekly,
    every other week, or once/month. (the installer chose every
    seven days. I switched it to bi-weekly)

    They also push a yearly visit to do all the stanrads (oil and
    self-starting battery check, etc.).



    Yep. Mine is set to exercise every week - I'll leave it there
    for now and maybe set it to 2 weeks eventually.
    ps : beware the new models do not have the lcd display
    on the unit any more - it's all through the APP ..
    even the contractor admitted to hating that ..
    John T.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Cindy Hamilton@chamilton5280@invalid.com to alt.home.repair on Thu Nov 12 18:23:34 2026
    From Newsgroup: alt.home.repair

    On 2026-11-12, Black Republican <black.republican@jury.duty> wrote:

    FWIW, I had a 14kW Gener-Wreck but the engine puked.

    I've had an 8-kW Generac for 13 years. We did the annual maintenance
    on it last Monday.
    --
    Cindy Hamilton
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Cindy Hamilton@chamilton5280@invalid.com to alt.home.repair on Thu Nov 12 18:24:36 2026
    From Newsgroup: alt.home.repair

    On 2026-11-12, Clare Snyder <clare@snyder.on.ca> wrote:

    I WAS going to say GenerAC doesn't have the best reputation - why
    they want you to "exercise" them monthly. (some would say excorcise)

    Mine exercises itself every week. Just a 15-minute stretch and
    then it lays back down again.
    --
    Cindy Hamilton
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Cindy Hamilton@chamilton5280@invalid.com to alt.home.repair on Thu Nov 12 18:25:26 2026
    From Newsgroup: alt.home.repair

    On 2026-11-12, danny burstein <dannyb@panix.com> wrote:
    In <mtsbfltngf2njg5og5vp0385ka0du08spq@4ax.com> Clare Snyder <clare@snyder.on.ca> writes:

    [snip]

    I WAS going to say GenerAC doesn't have the best reputation - why
    they want you to "exercise" them monthly. (some would say excorcise)

    we have one of the 10 kw natural gas units. In my discussions with
    them they DID have quieter, longer usage, etc., ones, but this is
    fine for our expected needs.

    Note you (the homeowner) can set it to self-test weekly,
    every other week, or once/month. (the installer chose every
    seven days. I switched it to bi-weekly)

    They also push a yearly visit to do all the stanrads (oil and
    self-starting battery check, etc.).

    They can push whatever they like. We do our own maintenance.
    --
    Cindy Hamilton
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Cindy Hamilton@chamilton5280@invalid.com to alt.home.repair on Thu Nov 12 18:26:58 2026
    From Newsgroup: alt.home.repair

    On 2026-11-12, hubops@ccanoemail.com <hubops@ccanoemail.com> wrote:

    The contractor recommended the stand to keep it from
    getting snowed-in so easily - seemed like a good idea
    at the time ..

    I guess it depends on how much snow you get. And whether
    it melts away between snowfalls.
    --
    Cindy Hamilton
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Clare Snyder@clare@snyder.on.ca to alt.home.repair on Thu Nov 12 17:32:17 2026
    From Newsgroup: alt.home.repair

    John, a few things you CAN do to reduce the noise on that install.
    First of all, make sure you have iso-mounts between the genset and the
    frame. Then cross brace the base. You can use angle iron bars or
    tensoin cables, or even hardwood bolted on. Then skirt the entire
    stand with 5/4" cedar, preferably at 45 degrees, more or less - t&G if
    you can get it. That thing is vibrating like crazy and acting like a
    Tympani. The iso mounts will reduce the energization of the stand. The
    cross bracing will reduce the resonance, and the 5/4 cedar will damp
    the radiated noise. Laying 2" of foil backed urethane insulation board
    on the concrete base will also stop the reflection of the noise off
    the concrete - or just use a double layer of rubber stable mat. SHould
    get you down to a measured 60 dba, more or less.
    Putting hardibacker cement board behind the cedar to accoustically
    load it will also help.It will damp the vibration and the cedar will
    absorb it and protect the hardibacker.
    Bolt your strapping to the frame then screw on the hardiBacker and
    cedar.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Clare Snyder@clare@snyder.on.ca to alt.home.repair on Thu Nov 12 17:36:06 2026
    From Newsgroup: alt.home.repair

    On Thu, 12 Nov 2026 12:14:39 -0500, Clare Snyder <clare@snyder.on.ca>
    wrote:



    One oither thing to check FIRST!!!! Make sure the yellow shipping
    bolts were removed. That unit ships with the engine solidly bolted to
    the mounting tray - to protect the mounts. If those bolts are not
    removed you basically do not have any engine mounts, and the whole
    thing WILL buzz LIKE CRAZY!!!!!

    On Thu, 12 Nov 2026 11:26:25 -0500, Black Republican ><black.republican@jury.duty> wrote:

    On 11/12/26 07:31, Cindy Hamilton wrote:
    On 2026-11-12, Black Republican <black.republican@jury.duty> wrote:
    On 11/6/26 17:38, hubops@ccanoemail.com wrote:
    After years of procrastination, I finally broke down
    and got a standby generator installed. 14 kW Generac.
    ... and IT IS NOISY !
    I've ordered a decibel meter from amazon to measure it -
    but my neighbour's cell phone app seems pretty close in my
    estimation. It says 101 dB standing right at the noisy end
    of the unit perhaps 2 feet away from the housing.
    Standing in front of it about 2 or 3 feet away you can't shout
    over the noise - it's gotta be 85 dB or more. The literature online >>>>> suggests that it is 67 dB at 23 feet - I had to retreat to about
    30 ft. to get down to about 72 dB on the quiet end.
    Oh well .. live and learn ..
    Anyone here with experience to share ?
    B&S, Kohler, Cummins are the other brands online -
    though Generac seems to win the popularity contest
    - by far - in my area.
    John T.



    https://powerequipment.honda.com/generators/models/eu7000is

    Very quiet. Can't hear it running when I'm inside the house.

    Because there are so many sticky-fingered Democrat porch pirates, you do >>>> need to keep it hidden. Maybe put it in an old fashioned outhouse in
    your back yard?

    That's a portable. Not remotely the same as the permanently
    installed generator hubops has, which might be this one:

    https://apelectric.com/generac-7258-14kw-generator/


    According to far left giggle, the word "permanent" primarily functions
    as an adjective meaning lasting for a long time, indefinitely, or
    forever without fundamental change.

    In my opinion, there's nothing "permanent" about a Gener-wreck install.

    FWIW, I had a 14kW Gener-Wreck but the engine puked. I tried to buy a
    new one but apparently a secret code is needed to activate it. F' that.
    So I bought the Honda eu7000is. Power goes out I roll it out the back of >>the garage, hit the start button and then go flip the breaker interlock.

    And if the Honda pukes, I can get a new one from the local Juan Deere >>dealer in under 2 hours.
    I WAS going to say GenerAC doesn't have the best reputation - why
    they want you to "exercise" them monthly. (some would say excorcise)
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From hubops@hubops@ccanoemail.com to alt.home.repair on Thu Nov 12 17:45:32 2026
    From Newsgroup: alt.home.repair

    On Thu, 12 Nov 2026 17:32:17 -0500, Clare Snyder <clare@snyder.on.ca>
    wrote:

    John, a few things you CAN do to reduce the noise on that install.
    First of all, make sure you have iso-mounts between the genset and the
    frame. Then cross brace the base. You can use angle iron bars or
    tensoin cables, or even hardwood bolted on. Then skirt the entire
    stand with 5/4" cedar, preferably at 45 degrees, more or less - t&G if
    you can get it. That thing is vibrating like crazy and acting like a
    Tympani. The iso mounts will reduce the energization of the stand. The
    cross bracing will reduce the resonance, and the 5/4 cedar will damp
    the radiated noise. Laying 2" of foil backed urethane insulation board
    on the concrete base will also stop the reflection of the noise off
    the concrete - or just use a double layer of rubber stable mat. SHould
    get you down to a measured 60 dba, more or less.
    Putting hardibacker cement board behind the cedar to accoustically
    load it will also help.It will damp the vibration and the cedar will
    absorb it and protect the hardibacker.
    Bolt your strapping to the frame then screw on the hardiBacker and
    cedar.


    Thanks for the ideas. I'll maybe check the stand vibration with a
    glass of water. There is a "gasket" between the generator housing
    and the stand. I'm still thinking about what to use on top of the
    concrete pad and skirt for the stand. And on the brick wall behind
    it.. something quick & cheap just to test the effect - and then
    perhaps something better later-on. I'll peruse the Re-Stores
    tomorrow.
    John T.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Clare Snyder@clare@snyder.on.ca to alt.home.repair on Thu Nov 12 17:52:43 2026
    From Newsgroup: alt.home.repair

    On Thu, 12 Nov 2026 17:32:17 -0500, Clare Snyder <clare@snyder.on.ca>
    wrote:

    John, a few things you CAN do to reduce the noise on that install.
    First of all, make sure you have iso-mounts between the genset and the
    frame. Then cross brace the base. You can use angle iron bars or
    tensoin cables, or even hardwood bolted on. Then skirt the entire
    stand with 5/4" cedar, preferably at 45 degrees, more or less - t&G if
    you can get it. That thing is vibrating like crazy and acting like a
    Tympani. The iso mounts will reduce the energization of the stand. The
    cross bracing will reduce the resonance, and the 5/4 cedar will damp
    the radiated noise. Laying 2" of foil backed urethane insulation board
    on the concrete base will also stop the reflection of the noise off
    the concrete - or just use a double layer of rubber stable mat. SHould
    get you down to a measured 60 dba, more or less.
    Putting hardibacker cement board behind the cedar to accoustically
    load it will also help.It will damp the vibration and the cedar will
    absorb it and protect the hardibacker.
    Bolt your strapping to the frame then screw on the hardiBacker and
    cedar.
    Leave an inch opening between the cladding and the concrete - put
    mesh to keep critters out - and good idea to isolate the strapping
    from the legs with some rubber padding. Good idea to leave one side
    detachable for any service access if wiring or gaslines enter from
    below.
    Put a small flashing on the top of the cladding to shed rain etc.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Clare Snyder@clare@snyder.on.ca to alt.home.repair on Thu Nov 12 17:57:05 2026
    From Newsgroup: alt.home.repair

    On Thu, 12 Nov 2026 17:45:32 -0500, hubops@ccanoemail.com wrote:

    On Thu, 12 Nov 2026 17:32:17 -0500, Clare Snyder <clare@snyder.on.ca>
    wrote:

    John, a few things you CAN do to reduce the noise on that install.
    First of all, make sure you have iso-mounts between the genset and the >>frame. Then cross brace the base. You can use angle iron bars or
    tensoin cables, or even hardwood bolted on. Then skirt the entire
    stand with 5/4" cedar, preferably at 45 degrees, more or less - t&G if
    you can get it. That thing is vibrating like crazy and acting like a >>Tympani. The iso mounts will reduce the energization of the stand. The >>cross bracing will reduce the resonance, and the 5/4 cedar will damp
    the radiated noise. Laying 2" of foil backed urethane insulation board
    on the concrete base will also stop the reflection of the noise off
    the concrete - or just use a double layer of rubber stable mat. SHould
    get you down to a measured 60 dba, more or less.
    Putting hardibacker cement board behind the cedar to accoustically
    load it will also help.It will damp the vibration and the cedar will
    absorb it and protect the hardibacker.
    Bolt your strapping to the frame then screw on the hardiBacker and
    cedar.


    Thanks for the ideas. I'll maybe check the stand vibration with a
    glass of water. There is a "gasket" between the generator housing
    and the stand. I'm still thinking about what to use on top of the
    concrete pad and skirt for the stand. And on the brick wall behind
    it.. something quick & cheap just to test the effect - and then
    perhaps something better later-on. I'll peruse the Re-Stores
    tomorrow.
    John T.
    How far from the brick wall? Quiet end towards the house? 6 foot high
    cedar fence with alternated 5/5 x6 planks extending at least 2 feet
    past each end of the genset will attenuate the bounce from the brick -
    6 inches from the wall????
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From hubops@hubops@ccanoemail.com to alt.home.repair on Thu Nov 12 18:22:18 2026
    From Newsgroup: alt.home.repair

    On Thu, 12 Nov 2026 17:36:06 -0500, Clare Snyder <clare@snyder.on.ca>
    wrote:

    On Thu, 12 Nov 2026 12:14:39 -0500, Clare Snyder <clare@snyder.on.ca>
    wrote:



    One oither thing to check FIRST!!!! Make sure the yellow shipping
    bolts were removed. That unit ships with the engine solidly bolted to
    the mounting tray - to protect the mounts. If those bolts are not
    removed you basically do not have any engine mounts, and the whole
    thing WILL buzz LIKE CRAZY!!!!!



    I went out and checked - didn't see any shipping bolts and
    no mention of them in the literature - except the bolts that hold
    it onto the pallet. I'll have a closer look tomorrow in the daylight.
    John T.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From hubops@hubops@ccanoemail.com to alt.home.repair on Thu Nov 12 18:24:49 2026
    From Newsgroup: alt.home.repair

    On Thu, 12 Nov 2026 17:57:05 -0500, Clare Snyder <clare@snyder.on.ca>
    wrote:

    On Thu, 12 Nov 2026 17:45:32 -0500, hubops@ccanoemail.com wrote:

    On Thu, 12 Nov 2026 17:32:17 -0500, Clare Snyder <clare@snyder.on.ca> >>wrote:

    John, a few things you CAN do to reduce the noise on that install.
    First of all, make sure you have iso-mounts between the genset and the >>>frame. Then cross brace the base. You can use angle iron bars or
    tensoin cables, or even hardwood bolted on. Then skirt the entire
    stand with 5/4" cedar, preferably at 45 degrees, more or less - t&G if >>>you can get it. That thing is vibrating like crazy and acting like a >>>Tympani. The iso mounts will reduce the energization of the stand. The >>>cross bracing will reduce the resonance, and the 5/4 cedar will damp
    the radiated noise. Laying 2" of foil backed urethane insulation board
    on the concrete base will also stop the reflection of the noise off
    the concrete - or just use a double layer of rubber stable mat. SHould >>>get you down to a measured 60 dba, more or less.
    Putting hardibacker cement board behind the cedar to accoustically
    load it will also help.It will damp the vibration and the cedar will >>>absorb it and protect the hardibacker.
    Bolt your strapping to the frame then screw on the hardiBacker and
    cedar.


    Thanks for the ideas. I'll maybe check the stand vibration with a
    glass of water. There is a "gasket" between the generator housing
    and the stand. I'm still thinking about what to use on top of the
    concrete pad and skirt for the stand. And on the brick wall behind
    it.. something quick & cheap just to test the effect - and then
    perhaps something better later-on. I'll peruse the Re-Stores
    tomorrow.
    John T.
    How far from the brick wall? Quiet end towards the house? 6 foot high
    cedar fence with alternated 5/5 x6 planks extending at least 2 feet
    past each end of the genset will attenuate the bounce from the brick -
    6 inches from the wall????



    20 inches from the wall.
    John T.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Clare Snyder@clare@snyder.on.ca to alt.home.repair on Thu Nov 12 18:32:48 2026
    From Newsgroup: alt.home.repair

    On Thu, 12 Nov 2026 17:52:43 -0500, Clare Snyder <clare@snyder.on.ca>
    wrote:

    On Thu, 12 Nov 2026 17:32:17 -0500, Clare Snyder <clare@snyder.on.ca>
    wrote:

    John, a few things you CAN do to reduce the noise on that install.
    First of all, make sure you have iso-mounts between the genset and the >>frame. Then cross brace the base. You can use angle iron bars or
    tensoin cables, or even hardwood bolted on. Then skirt the entire
    stand with 5/4" cedar, preferably at 45 degrees, more or less - t&G if
    you can get it. That thing is vibrating like crazy and acting like a >>Tympani. The iso mounts will reduce the energization of the stand. The >>cross bracing will reduce the resonance, and the 5/4 cedar will damp
    the radiated noise. Laying 2" of foil backed urethane insulation board
    on the concrete base will also stop the reflection of the noise off
    the concrete - or just use a double layer of rubber stable mat. SHould
    get you down to a measured 60 dba, more or less.
    Putting hardibacker cement board behind the cedar to accoustically
    load it will also help.It will damp the vibration and the cedar will
    absorb it and protect the hardibacker.
    Bolt your strapping to the frame then screw on the hardiBacker and
    cedar.
    Leave an inch opening between the cladding and the concrete - put
    mesh to keep critters out - and good idea to isolate the strapping
    from the legs with some rubber padding. Good idea to leave one side >detachable for any service access if wiring or gaslines enter from
    below.
    Put a small flashing on the top of the cladding to shed rain etc.
    Being a 12 inch stand I wouldn't worry about cross bracing with the
    perscribed skirting. Vertical or 45 degree very close to the same
    effectiveness - 45 degree slightly better. Using the brown PT instead
    of cedar will cost you a dB or 2 but cost you about 40% less - - - . I
    would install the "fence" with ground spikes - with the 2x4 posts on
    the "flat side" - need to double the 2X4 in the spike saddles - keep
    the horizontal fence boards 6 inches to a foot from the ground - high
    enough to be able to mow under it but close enough to the ground to
    catch the noise. posts a foot from each end plus in the middle to keep
    the boards stiff. (I am assuming there is enough space between the
    genset and wall to give 18 inches between the genset and the fence)
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Clare Snyder@clare@snyder.on.ca to alt.home.repair on Thu Nov 12 18:45:13 2026
    From Newsgroup: alt.home.repair

    On Thu, 12 Nov 2026 18:24:49 -0500, hubops@ccanoemail.com wrote:

    On Thu, 12 Nov 2026 17:57:05 -0500, Clare Snyder <clare@snyder.on.ca>
    wrote:

    On Thu, 12 Nov 2026 17:45:32 -0500, hubops@ccanoemail.com wrote:

    On Thu, 12 Nov 2026 17:32:17 -0500, Clare Snyder <clare@snyder.on.ca> >>>wrote:

    John, a few things you CAN do to reduce the noise on that install. >>>>First of all, make sure you have iso-mounts between the genset and the >>>>frame. Then cross brace the base. You can use angle iron bars or >>>>tensoin cables, or even hardwood bolted on. Then skirt the entire
    stand with 5/4" cedar, preferably at 45 degrees, more or less - t&G if >>>>you can get it. That thing is vibrating like crazy and acting like a >>>>Tympani. The iso mounts will reduce the energization of the stand. The >>>>cross bracing will reduce the resonance, and the 5/4 cedar will damp >>>>the radiated noise. Laying 2" of foil backed urethane insulation board >>>>on the concrete base will also stop the reflection of the noise off
    the concrete - or just use a double layer of rubber stable mat. SHould >>>>get you down to a measured 60 dba, more or less.
    Putting hardibacker cement board behind the cedar to accoustically
    load it will also help.It will damp the vibration and the cedar will >>>>absorb it and protect the hardibacker.
    Bolt your strapping to the frame then screw on the hardiBacker and >>>>cedar.


    Thanks for the ideas. I'll maybe check the stand vibration with a
    glass of water. There is a "gasket" between the generator housing
    and the stand. I'm still thinking about what to use on top of the >>>concrete pad and skirt for the stand. And on the brick wall behind
    it.. something quick & cheap just to test the effect - and then >>>perhaps something better later-on. I'll peruse the Re-Stores
    tomorrow.
    John T.
    How far from the brick wall? Quiet end towards the house? 6 foot high >>cedar fence with alternated 5/5 x6 planks extending at least 2 feet
    past each end of the genset will attenuate the bounce from the brick -
    6 inches from the wall????



    20 inches from the wall.
    John T.
    That's pushing it for clearance to get the absorber wall in there - -
    - You need to keep the "fence" at least an inch from the brick - more
    is better - so you MIGHT need to have a longer fence 2 feet from the
    genset on the other side - which MIGHT be a "snow fence" problem -
    -The idea is REALLY to disrupt the sound waves from the genset to the
    wall - absorbing some of it, and then catch it again on the way back
    from the wall when it bounces absorbing some more, and scattering it.
    The outside wall only catches it coming OFF the wall, but also catches
    some coming straight from the genset, so MAY be close in
    effectiveness, but I'm not confident of that.( likely better than half
    - but not much)


    2 inches of board (2x 5/4) plus 1.5" 2x4 flatside, plus 1 inch wall
    space takes up 4.5 inches - leaving you only 14.5 inches instead of
    the specified 18". Going to 1X instead of 5/4 only gains you 1/2 inch
    and cuts down the absoption somewhat - as well as increasing radiation
    from vibration (but MAY absorb more BY vibrating - might win back
    SOME of the loss, but not all.)
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From frank@"frank "@frank.net to alt.home.repair on Thu Nov 12 18:53:15 2026
    From Newsgroup: alt.home.repair

    On 11/12/2026 12:14 PM, Clare Snyder wrote:
    On Thu, 12 Nov 2026 11:26:25 -0500, Black Republican <black.republican@jury.duty> wrote:

    On 11/12/26 07:31, Cindy Hamilton wrote:
    On 2026-11-12, Black Republican <black.republican@jury.duty> wrote:
    On 11/6/26 17:38, hubops@ccanoemail.com wrote:
    After years of procrastination, I finally broke down
    and got a standby generator installed. 14 kW Generac.
    ... and IT IS NOISY !
    I've ordered a decibel meter from amazon to measure it -
    but my neighbour's cell phone app seems pretty close in my
    estimation. It says 101 dB standing right at the noisy end
    of the unit perhaps 2 feet away from the housing.
    Standing in front of it about 2 or 3 feet away you can't shout
    over the noise - it's gotta be 85 dB or more. The literature online >>>>> suggests that it is 67 dB at 23 feet - I had to retreat to about
    30 ft. to get down to about 72 dB on the quiet end.
    Oh well .. live and learn ..
    Anyone here with experience to share ?
    B&S, Kohler, Cummins are the other brands online -
    though Generac seems to win the popularity contest
    - by far - in my area.
    John T.



    https://powerequipment.honda.com/generators/models/eu7000is

    Very quiet. Can't hear it running when I'm inside the house.

    Because there are so many sticky-fingered Democrat porch pirates, you do >>>> need to keep it hidden. Maybe put it in an old fashioned outhouse in
    your back yard?

    That's a portable. Not remotely the same as the permanently
    installed generator hubops has, which might be this one:

    https://apelectric.com/generac-7258-14kw-generator/


    According to far left giggle, the word "permanent" primarily functions
    as an adjective meaning lasting for a long time, indefinitely, or
    forever without fundamental change.

    In my opinion, there's nothing "permanent" about a Gener-wreck install.

    FWIW, I had a 14kW Gener-Wreck but the engine puked. I tried to buy a
    new one but apparently a secret code is needed to activate it. F' that.
    So I bought the Honda eu7000is. Power goes out I roll it out the back of
    the garage, hit the start button and then go flip the breaker interlock.

    And if the Honda pukes, I can get a new one from the local Juan Deere
    dealer in under 2 hours.
    I WAS going to say GenerAC doesn't have the best reputation - why
    they want you to "exercise" them monthly. (some would say excorcise)

    My brother got one a few years ago and it is exercised weekly. Even
    though warranted it costs him about $400/year for monitoring and propane
    even not used. I understand with tanked in propane it can cost nearly $100/day to run.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From hubops@hubops@ccanoemail.com to alt.home.repair on Thu Nov 12 19:50:17 2026
    From Newsgroup: alt.home.repair



    My brother got one a few years ago and it is exercised weekly. Even
    though warranted it costs him about $400/year for monitoring and propane >even not used. I understand with tanked in propane it can cost nearly >$100/day to run.



    I just ran the numbers for my 14 kW standby on propane :

    half-load 1.8 US gal per hour

    X 3.7854 litres per US gal X $ 1.40 per litre + tax =
    ~ $ 260. per day in the 51st state.

    John T.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Clare Snyder@clare@snyder.on.ca to alt.home.repair on Thu Nov 12 22:05:14 2026
    From Newsgroup: alt.home.repair

    On Thu, 12 Nov 2026 19:50:17 -0500, hubops@ccanoemail.com wrote:



    My brother got one a few years ago and it is exercised weekly. Even >>though warranted it costs him about $400/year for monitoring and propane >>even not used. I understand with tanked in propane it can cost nearly >>$100/day to run.



    I just ran the numbers for my 14 kW standby on propane :

    half-load 1.8 US gal per hour

    X 3.7854 litres per US gal X $ 1.40 per litre + tax =
    ~ $ 260. per day in the 51st state.

    John T.



    1. Walk a 4-Point Perimeter Check with the Meter

    Take a reading 3 to 5 feet off each of the four sides (front door,
    rear brick side, left intake end, right exhaust end) to see where the
    energy is spiking:
    o If it spikes massively on the right-hand exhaust end (90+ dBA): The
    unit likely has a cracked muffler weld, loose exhaust manifold gasket,
    or detached flex pipe inside the muffler bayuwhich does happen on
    brand-new units from shipping jolts.
    o If it spikes at the bottom gap or the stand legs ring: The 12-inch
    open stand is acting like a speaker cabinet, letting raw cooling-fan
    and crankcase noise blast straight downward onto the concrete pad and
    shoot out horizontally, while the rigid metal-to-metal mounting
    couples 3,600 RPM vibration straight into the stand.
    o If the cabinet panels themselves are buzzing: Check the internal
    metal divider firewall between the engine bay and the muffler
    compartment, as well as the roof acoustic foam and side access door
    latches. If the firewall isn't seated or a latch isn't cammed shut,
    exhaust roar pours straight out the intake louvers.

    2. Confirm Exercise Mode vs. Full-Speed Load

    o Make sure the 85 dBA measurement wasn't taken during a normal-speed
    self-test where Quiet-Test was left disabled in the Evolution
    controlleruand if it was running at full 3,600 RPM load, compare dBA
    vs. dBC at 20 feet. A massive spread (e.g., 95+ dBC vs. 85 dBA)
    confirms heavy low-frequency structural coupling through the 12-inch
    stand and brick bounce, whereas a tighter spread points straight to an unmuffled exhaust leak or open cabinet panel.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From frank@"frank "@frank.net to alt.home.repair on Fri Nov 13 07:12:09 2026
    From Newsgroup: alt.home.repair

    On 11/12/2026 7:50 PM, hubops@ccanoemail.com wrote:


    My brother got one a few years ago and it is exercised weekly. Even
    though warranted it costs him about $400/year for monitoring and propane
    even not used. I understand with tanked in propane it can cost nearly
    $100/day to run.



    I just ran the numbers for my 14 kW standby on propane :

    half-load 1.8 US gal per hour

    X 3.7854 litres per US gal X $ 1.40 per litre + tax =
    ~ $ 260. per day in the 51st state.

    John T.

    Wow! I just ran it through google and it said it would be about $60 on natural gas. The power company had cut off natural gas to half our development when my house was built. If we had it I would have
    installed a whole house generator.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Ed P@esp@snet.n to alt.home.repair on Fri Nov 13 08:42:14 2026
    From Newsgroup: alt.home.repair

    On 11/13/2026 7:12 AM, Frank wrote:

    Wow!-a I just ran it through google and it said it would be about $60 on natural gas.-a The power company had cut off natural gas to half our development when my house was built.-a If we had it I would have
    installed a whole house generator.


    I like NG. I use it for cooking, grilling, hot water, drying clothes.
    There is a monthly charge just for the hookup, but may actual gas use
    runs about $6 a month. Even with a family it would be cheap.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From hubops@hubops@ccanoemail.com to alt.home.repair on Fri Nov 13 10:48:18 2026
    From Newsgroup: alt.home.repair

    On Fri, 13 Nov 2026 07:12:09 -0500, Frank <"frank "@frank.net> wrote:

    On 11/12/2026 7:50 PM, hubops@ccanoemail.com wrote:


    My brother got one a few years ago and it is exercised weekly. Even
    though warranted it costs him about $400/year for monitoring and propane >>> even not used. I understand with tanked in propane it can cost nearly
    $100/day to run.



    I just ran the numbers for my 14 kW standby on propane :

    half-load 1.8 US gal per hour

    X 3.7854 litres per US gal X $ 1.40 per litre + tax =
    ~ $ 260. per day in the 51st state.

    John T.

    Wow! I just ran it through google and it said it would be about $60 on >natural gas. The power company had cut off natural gas to half our >development when my house was built. If we had it I would have
    installed a whole house generator.



    This link says that the Cummins 13 kW is rated a little quieter
    and a little less thirsty :

    https://norwall.com/content/norwall-pim-app/assets/documents/5a7ae040-c97e-49ff-9aae-2ea2502b8cdc_Cummins13kW17kW20kWSpecifications72021NAS6254RevH.PDF

    If I had known ...

    I think this is the brand that Clare's buddy Ed was selling
    when I spoke to him a few years back.

    John T.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From frank@"frank "@frank.net to alt.home.repair on Fri Nov 13 11:09:21 2026
    From Newsgroup: alt.home.repair

    On 11/13/2026 8:42 AM, Ed P wrote:
    On 11/13/2026 7:12 AM, Frank wrote:

    Wow!-a I just ran it through google and it said it would be about $60
    on natural gas.-a The power company had cut off natural gas to half our
    development when my house was built.-a If we had it I would have
    installed a whole house generator.


    I like NG.-a I use it for cooking, grilling, hot water, drying clothes. There is a monthly charge just for the hookup, but may actual gas use
    runs about $6 a month.-a Even with a family it would be cheap.

    I do too but we are 100% electric and wife loves the cleanliness of it.

    I had mentioned here that a couple of years ago my oil furnace and tank
    had gone kaput and we replaced it with a heat pump. If we had gas it
    would have been a gas furnace.

    Relating to generators my problem is that my generator cannot handle the
    heat pump while it did the oil furnace.