• circuit breaker peak amperage

    From badgolferman@REMOVETHISbadgolferman@gmail.com to alt.home.repair on Thu Jun 25 12:40:13 2026
    From Newsgroup: alt.home.repair

    I had a dehumidifier installed under the house last year. The
    dedicated wiring goes through a GFCI then to one side of a circuit
    breaker with two 15 amp sides. The breaker is designed to take up only
    one slot in the electrical panel but used for two separate circuits.

    Recently the breaker has been tripping every so often. The GFCI does
    not trip. The electrician from the company troubleshot it yesterday
    with a clamp style amp meter around the wire. He turned the
    dehumidifier on/off with the GFCI and noticed if there isn't sufficient
    rest time, the initial surge of current goes all the way up to 35 amps
    which then trips the circuit breaker. After a few times he declared
    the dehumidifier bad and it's getting replaced under warranty.
    Apparently they've seen this before with that model.

    Why would the GFCI not trip before the circuit breaker? Why would a 15
    amp circuit breaker trip at an initial surge of 35 amps rather than 15
    amps? Is this as designed? Seems like quite a large margin.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Retirednoguilt@HapilyRetired@fakeaddress.invalid to alt.home.repair on Thu Jun 25 10:03:18 2026
    From Newsgroup: alt.home.repair

    On 6/25/2026 8:40 AM, badgolferman wrote:
    I had a dehumidifier installed under the house last year. The
    dedicated wiring goes through a GFCI then to one side of a circuit
    breaker with two 15 amp sides. The breaker is designed to take up only
    one slot in the electrical panel but used for two separate circuits.

    Recently the breaker has been tripping every so often. The GFCI does
    not trip. The electrician from the company troubleshot it yesterday
    with a clamp style amp meter around the wire. He turned the
    dehumidifier on/off with the GFCI and noticed if there isn't sufficient
    rest time, the initial surge of current goes all the way up to 35 amps
    which then trips the circuit breaker. After a few times he declared
    the dehumidifier bad and it's getting replaced under warranty.
    Apparently they've seen this before with that model.

    Why would the GFCI not trip before the circuit breaker? Why would a 15
    amp circuit breaker trip at an initial surge of 35 amps rather than 15
    amps? Is this as designed? Seems like quite a large margin.

    My understanding, not necessarily accurate, is that the GCFI trips if
    there is more than only a few milliamps of stray induced current flowing through the circuit's ground wire. The current measured by the clamp-on ammeter measures current flowing through any two of the three wires in
    the circuit. The surge that's tripping the breaker is flowing through
    the hot and neutral wires and doesn't involve the ground wire (probably
    green in color but it could also be an un-insulated, bare wire. GCFI is designed to detect a bad ground connection. It is not a surge
    protector. If your dehumidifier draws an excessive surge when starting
    up, it would trip a normal, non-GCFI 15 amp breaker as well. It's not
    the GCFI feature that's causing that breaker to trip. I'm sure I'll be corrected if I've got this wrong.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From hubops@hubops@ccanoemail.com to alt.home.repair on Thu Jun 25 10:34:01 2026
    From Newsgroup: alt.home.repair

    On Thu, 25 Jun 2026 12:40:13 -0000 (UTC), "badgolferman" <REMOVETHISbadgolferman@gmail.com> wrote:

    I had a dehumidifier installed under the house last year. The
    dedicated wiring goes through a GFCI then to one side of a circuit
    breaker with two 15 amp sides. The breaker is designed to take up only
    one slot in the electrical panel but used for two separate circuits.

    Recently the breaker has been tripping every so often. The GFCI does
    not trip. The electrician from the company troubleshot it yesterday
    with a clamp style amp meter around the wire. He turned the
    dehumidifier on/off with the GFCI and noticed if there isn't sufficient
    rest time, the initial surge of current goes all the way up to 35 amps
    which then trips the circuit breaker. After a few times he declared
    the dehumidifier bad and it's getting replaced under warranty.
    Apparently they've seen this before with that model.

    Why would the GFCI not trip before the circuit breaker? Why would a 15
    amp circuit breaker trip at an initial surge of 35 amps rather than 15
    amps? Is this as designed? Seems like quite a large margin.



    The GFCI trips on _tiny_ <milliamp> _imbalance_
    in the current carrying wires or tiny flow in the ground wire.
    Breakers and fuses have a time-curve to allow short duration
    "overload" for starting surges. I've heard that breakers can go
    weak if they have been tripping a lot .. if it wasn't a warranty job replacing the breaker might be a first-step ..
    John T.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From scott@scott@slp53.sl.home (Scott Lurndal) to alt.home.repair on Thu Jun 25 14:46:58 2026
    From Newsgroup: alt.home.repair

    "badgolferman" <REMOVETHISbadgolferman@gmail.com> writes:
    I had a dehumidifier installed under the house last year. The
    dedicated wiring goes through a GFCI then to one side of a circuit
    breaker with two 15 amp sides. The breaker is designed to take up only
    one slot in the electrical panel but used for two separate circuits.

    Recently the breaker has been tripping every so often. The GFCI does
    not trip. The electrician from the company troubleshot it yesterday
    with a clamp style amp meter around the wire. He turned the
    dehumidifier on/off with the GFCI and noticed if there isn't sufficient
    rest time, the initial surge of current goes all the way up to 35 amps
    which then trips the circuit breaker. After a few times he declared
    the dehumidifier bad and it's getting replaced under warranty.
    Apparently they've seen this before with that model.

    Why would the GFCI not trip before the circuit breaker? Why would a 15
    amp circuit breaker trip at an initial surge of 35 amps rather than 15
    amps? Is this as designed? Seems like quite a large margin.

    The GFCI is not a circuit breaker. It detects ground faults,
    not overcurrent conditions.
    --- Synchronet 3.22a-Linux NewsLink 1.2
  • From Clare Snyder@clare@snyder.on.ca to alt.home.repair on Thu Jun 25 23:52:48 2026
    From Newsgroup: alt.home.repair

    On Thu, 25 Jun 2026 14:46:58 GMT, scott@slp53.sl.home (Scott Lurndal)
    wrote:

    "badgolferman" <REMOVETHISbadgolferman@gmail.com> writes:
    I had a dehumidifier installed under the house last year. The
    dedicated wiring goes through a GFCI then to one side of a circuit
    breaker with two 15 amp sides. The breaker is designed to take up only
    one slot in the electrical panel but used for two separate circuits.

    Recently the breaker has been tripping every so often. The GFCI does
    not trip. The electrician from the company troubleshot it yesterday
    with a clamp style amp meter around the wire. He turned the
    dehumidifier on/off with the GFCI and noticed if there isn't sufficient >>rest time, the initial surge of current goes all the way up to 35 amps >>which then trips the circuit breaker. After a few times he declared
    the dehumidifier bad and it's getting replaced under warranty.
    Apparently they've seen this before with that model.

    Why would the GFCI not trip before the circuit breaker? Why would a 15
    amp circuit breaker trip at an initial surge of 35 amps rather than 15 >>amps? Is this as designed? Seems like quite a large margin.

    The GFCI is not a circuit breaker. It detects ground faults,
    not overcurrent conditions.
    Had the same problem with my central vac. It was determined to be the
    surge current on startup - which required a "high magnetic" 15 amp
    breaker. Single 15 amp high mag breakers are not carried in Ontario
    and I wasn't about to order one from Quebec. I called Square D and
    they told me all 2 pole Squsre D breakers were high magnetic so I
    just threw in a 2 pole in (thankfully I had space) and the problem was
    solved.