• Siemens Industrial Edge Device Kit

    From Cisa Advisories@2:263/1 to All on Thu Oct 22 20:03:14 2026
    Siemens Industrial Edge Device Kit

    View CSAF
    Summary
    Users of Industrial Edge Devices are advised to consult the respective Security Advisories for their devices (for Siemens Industrial Edge devices see Additional Information). Industrial Edge Device Kit contains multiple path traversal vulnerabilities that could facilitate an authenticated remote attacker to access sensitive internal information. Siemens has released new versions for several affected products and recommends to update to the latest versions. Siemens recommends specific countermeasures for products where fixes are not, or not yet available.
    The following versions of Siemens Industrial Edge Device Kit are affected:

    Industrial Edge Device Kit - arm64 V1.10 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - arm64 V1.11 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - arm64 V1.12 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - arm64 V1.13 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - arm64 V1.14 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - arm64 V1.15 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - arm64 V1.16 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - arm64 V1.17 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - arm64 V1.18 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - arm64 V1.19 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - arm64 V1.20 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - arm64 V1.21 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - arm64 V1.22 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - arm64 V1.23 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - arm64 V1.24 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - arm64 V1.25 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - arm64 V1.26 vers:intdot/<1.26.2.1 (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - arm64 V1.27 vers:intdot/<1.27.1.1 (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - arm64 V1.28 vers:intdot/<1.28.0.6 (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - arm64 V1.5 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - arm64 V1.6 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - arm64 V1.7 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - arm64 V1.8 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - arm64 V1.9 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - x86-64 V1.10 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - x86-64 V1.11 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - x86-64 V1.12 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - x86-64 V1.13 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - x86-64 V1.14 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - x86-64 V1.15 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - x86-64 V1.16 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - x86-64 V1.17 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - x86-64 V1.18 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - x86-64 V1.19 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - x86-64 V1.20 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - x86-64 V1.21 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - x86-64 V1.22 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - x86-64 V1.23 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - x86-64 V1.24 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - x86-64 V1.25 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - x86-64 V1.26 vers:intdot/<1.26.2.1 (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - x86-64 V1.27 vers:intdot/<1.27.1.1 (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - x86-64 V1.28 vers:intdot/<1.28.0.6 (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - x86-64 V1.5 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - x86-64 V1.6 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - x86-64 V1.7 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - x86-64 V1.8 vers:all/* (CVE-2026-44414, CVE-2026-44415)
    Industrial Edge Device Kit - x86-64 V1.9 vers:all/* (CVE-2026-44414, CVE-2026-44415)





    CVSS
    Vendor
    Equipment




    v3 9.1
    Siemens
    Industrial Edge Device Kit - arm64 V1.10






    1 Vulnerability




    Path Traversal: '.../...//'




    Background

    Critical Infrastructure Sectors: Critical Manufacturing, Transportation Systems, Energy, Healthcare and Public Health, Financial Services, Government Services and Facilities
    Countries/Areas Deployed: Worldwide Company Headquarters Location: Germany


    Vulnerabilities
    Expand All +

    CVE-2026-44414
    Affected systems do not properly restrict access to internal APIs and paths for authenticated users. This could allow an authenticated remote attacker to access sensitive internal information, which in the worst case could be leveraged to facilitate unauthorized access to the system. Read More

    48 Affected Products

    Industrial Edge Device Kit - arm64 V1.10

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.19

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.20

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.21

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.22

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.23

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.24

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.25

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.26 < V1.26.2-1

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    Vendor fixUpdate to V1.26.2-1 or later version


    Industrial Edge Device Kit - arm64 V1.27 < V1.27.1-1

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    Vendor fixUpdate to V1.27.1-1 or later version


    Industrial Edge Device Kit - arm64 V1.28 < V1.28.0-6

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    Vendor fixUpdate to V1.28.0-6 or later version


    Industrial Edge Device Kit - arm64 V1.11

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.5

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.6

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.7

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.8

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.9

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.10

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.11

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.12

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.13

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.14

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.12

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.15

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.16

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.17

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.18

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.19

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.20

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.21

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.22

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.23

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.24

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.13

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.25

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.26 < V1.26.2-1

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    Vendor fixUpdate to V1.26.2-1 or later version


    Industrial Edge Device Kit - x86-64 V1.27 < V1.27.1-1

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    Vendor fixUpdate to V1.27.1-1 or later version


    Industrial Edge Device Kit - x86-64 V1.28 < V1.28.0-6

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    Vendor fixUpdate to V1.28.0-6 or later version


    Industrial Edge Device Kit - x86-64 V1.5

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.6

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.7

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.8

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.9

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.14

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.15

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.16

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.17

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.18

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Additional Metrics
    Relevant CWE: CWE-35 Path Traversal: '.../...//'




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.1
    6.8
    MEDIUM
    CVSS:3.1/AV:N/AC:L/PR:H/UI:N/S:C/C:H/I:N/A:N





    View CVE Details



    CVE-2026-44415
    Affected systems do not properly restrict access to internal APIs and paths for authenticated users. This could allow an authenticated remote attacker to access sensitive internal information, which in the worst case could be leveraged to facilitate unauthorized access to the system or result in the deletion of data.
    Read More

    96 Affected Products

    Industrial Edge Device Kit - arm64 V1.10

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.19

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.20

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.21

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.22

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.23

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.24

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.25

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.26 < V1.26.2-1

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    Vendor fixUpdate to V1.26.2-1 or later version


    Industrial Edge Device Kit - arm64 V1.27 < V1.27.1-1

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    Vendor fixUpdate to V1.27.1-1 or later version


    Industrial Edge Device Kit - arm64 V1.28 < V1.28.0-6

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    Vendor fixUpdate to V1.28.0-6 or later version


    Industrial Edge Device Kit - arm64 V1.11

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.5

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.6

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.7

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.8

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.9

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.10

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.11

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.12

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.13

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.14

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.12

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.15

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.16

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.17

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.18

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.19

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.20

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.21

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.22

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.23

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.24

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.13

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.25

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.26 < V1.26.2-1

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    Vendor fixUpdate to V1.26.2-1 or later version


    Industrial Edge Device Kit - x86-64 V1.27 < V1.27.1-1

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    Vendor fixUpdate to V1.27.1-1 or later version


    Industrial Edge Device Kit - x86-64 V1.28 < V1.28.0-6

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    Vendor fixUpdate to V1.28.0-6 or later version


    Industrial Edge Device Kit - x86-64 V1.5

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.6

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.7

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.8

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.9

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.14

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.15

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.16

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.17

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.18

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.10

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.19

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.20

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.21

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.22

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.23

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.24

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.25

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.26 < V1.26.2-1

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    Vendor fixUpdate to V1.26.2-1 or later version


    Industrial Edge Device Kit - arm64 V1.27 < V1.27.1-1

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    Vendor fixUpdate to V1.27.1-1 or later version


    Industrial Edge Device Kit - arm64 V1.28 < V1.28.0-6

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    Vendor fixUpdate to V1.28.0-6 or later version


    Industrial Edge Device Kit - arm64 V1.11

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.5

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.6

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.7

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.8

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.9

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.10

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.11

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.12

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.13

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.14

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.12

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.15

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.16

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.17

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.18

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.19

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.20

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.21

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.22

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.23

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.24

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.13

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.25

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.26 < V1.26.2-1

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    Vendor fixUpdate to V1.26.2-1 or later version


    Industrial Edge Device Kit - x86-64 V1.27 < V1.27.1-1

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    Vendor fixUpdate to V1.27.1-1 or later version


    Industrial Edge Device Kit - x86-64 V1.28 < V1.28.0-6

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    Vendor fixUpdate to V1.28.0-6 or later version


    Industrial Edge Device Kit - x86-64 V1.5

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.6

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.7

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.8

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - x86-64 V1.9

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.14

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.15

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.16

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.17

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Industrial Edge Device Kit - arm64 V1.18

    Product Status: known_affected

    Remediations

    MitigationEnsure network access to affected products is limited to trusted parties only


    No fix plannedCurrently no fix is planned


    Additional Metrics
    Relevant CWE: CWE-35 Path Traversal: '.../...//'




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.1
    9.1
    CRITICAL
    CVSS:3.1/AV:N/AC:L/PR:H/UI:N/S:C/C:H/I:H/A:H





    View CVE Details



    Acknowledgments

    Siemens ProductCERT reported these vulnerabilities to CISA.


    General Recommendations
    As a general security measure, Siemens strongly recommends to protect network access to devices with appropriate mechanisms. In order to operate the devices in a protected IT environment, Siemens recommends to configure the environment according to Siemens' operational guidelines for Industrial Security (Download: https://www.siemens.com/cert/operational-guidelines-industrial-security), and to follow the recommendations in the product manuals. Additional information on Industrial Security by Siemens can be found at: https://www.siemens.com/industrialsecurity

    Additional Resources
    For further inquiries on security vulnerabilities in Siemens products and solutions, please contact the Siemens ProductCERT: https://www.siemens.com/cert/advisories

    Terms of Use
    The use of Siemens Security Advisories is subject to the terms and conditions listed on: https://www.siemens.com/productcert/terms-of-use.

    Recommended Practices
    CISA recommends users take defensive measures to minimize the risk of exploitation of these vulnerabilities.

    Minimize network exposure for all control system devices and/or systems, ensuring they are not accessible from the internet. Locate control system networks and remote devices behind firewalls and isolating them from business networks. When remote access is required, use more secure methods, such as Virtual Private Networks (VPNs), recognizing VPNs may have vulnerabilities and should be updated to the most current version available. Also recognize VPN is only as secure as the connected devices.

    CISA reminds organizations to perform proper impact analysis and risk assessment prior to deploying defensive measures. CISA also provides a section for control systems security recommended practices
    on the ICS webpage on cisa.gov/ics. Several CISA products detailing cyber defense best practices are available for reading and download, including Improving Industrial Control Systems Cybersecurity with Defense-in-Depth Strategies.
    CISA encourages organizations to implement recommended cybersecurity strategies for proactive defense of ICS assets. Additional mitigation guidance and recommended practices are publicly available on the ICS webpage at cisa.gov/ics in the technical information paper, ICS-TIP-12-146-01B--Targeted Cyber Intrusion Detection and Mitigation
    Strategies.
    Organizations observing suspected malicious activity should follow established internal procedures and report findings to CISA for tracking and correlation against other incidents.

    Advisory Conversion Disclaimer
    This ICSA is a verbatim republication of Siemens ProductCERT SSA-377139 from a direct conversion of the vendor's Common Security Advisory Framework (CSAF) advisory. This is republished to CISA's website as a means of increasing visibility and is provided "as-is" for informational purposes only. CISA is not responsible for the editorial or technical accuracy of republished advisories and provides no warranties of any kind regarding any information contained within this advisory. Further, CISA does not endorse any commercial product or service. Please contact Siemens ProductCERT directly for any questions regarding this advisory.
    Revision History

    Initial Release Date: 2026-10-13




    Date
    Revision
    Summary




    2026-10-13
    1
    Publication Date


    2026-10-22
    2
    Initial CISA Republication of Siemens ProductCERT SSA-377139 advisory




    Legal Notice and Terms of Use

    https://www.cisa.gov/news-events/ics-advisories/icsa-26-295-09

    2026-10-22 12:00 UTC

    --- BBBS/LiR v4.10 Toy-7
    * Origin: LISTS. from TCOB1 READ ONLY (2:263/1)