• Hitachi Energy RTU500

    From CISA Advisories@2:263/1 to All on Thu Jun 4 16:11:08 2026
    Hitachi Energy RTU500

    View CSAF
    Summary
    Hitachi Energy is aware of vulnerabilities that affect RTU500 product versions listed in this document. If exploited, these vulnerabilities primarily impact product availability, with potential secondary impacts on confidentiality and integrity. Please refer to the Recommended Immediate Actions for information about the mitigation/remediation.
    The following versions of Hitachi Energy RTU500 are affected:

    RTU500 series CMU Firmware vers:RTU500_series_CMU_Firmware/>=12.7.1|<=12.7.7, vers:RTU500_series_CMU_Firmware/>=13.5.1|<=13.5.4, vers:RTU500_series_CMU_Firmware/>=13.6.1|<=13.6.3, vers:RTU500_series_CMU_Firmware/>=13.7.1|<=13.7.8, 13.8.1, vers:RTU500_series_CMU_Firmware/>=13.7.1|<=13.7.7 (CVE-2025-69421, CVE-2026-24515, CVE-2026-25210, CVE-2026-32776, CVE-2026-32777, CVE-2026-32778, CVE-2026-8479, CVE-2025-69421, CVE-2026-24515, CVE-2026-25210, CVE-2026-32776, CVE-2026-32777, CVE-2026-32778, CVE-2026-8479, CVE-2025-69421, CVE-2026-24515, CVE-2026-25210, CVE-2026-32776, CVE-2026-32777, CVE-2026-32778, CVE-2026-8479, CVE-2025-69421, CVE-2026-24515, CVE-2026-25210, CVE-2026-32776, CVE-2026-32777, CVE-2026-32778, CVE-2025-69421, CVE-2026-24515, CVE-2026-25210, CVE-2026-32776, CVE-2026-32777, CVE-2026-32778, CVE-2026-8479, CVE-2026-8479)





    CVSS
    Vendor
    Equipment
    Vulnerabilities




    v3 7.8
    Hitachi Energy
    Hitachi Energy RTU500
    NULL Pointer Dereference, Integer Overflow or Wraparound, Loop with Unreachable Exit Condition ('Infinite Loop')




    Background

    Critical Infrastructure Sectors: Dams, Energy, Water and Wastewater Countries/Areas Deployed: Worldwide
    Company Headquarters Location: Switzerland


    Vulnerabilities

    Expand All +

    CVE-2025-69421

    CWE-476: NULL Pointer Dereference. Issue summary: Processing a malformed PKCS#12 file can trigger a NULL pointer dereference in the PKCS12_item_decrypt_d2i_ex() function. Impact summary: A NULL pointer dereference can trigger a crash which leads to Denial of Service for an application processing PKCS#12 files. The PKCS12_item_decrypt_d2i_ex() function does not check whether the oct parameter is NULL before dereferencing it. When called from PKCS12_unpack_p7encdata() with a malformed PKCS#12 file, this parameter can be NULL, causing Denial of Service impact. The vulnerability is limited to Denial of Service and cannot be escalated to achieve code execution or memory disclosure. Product is affected, if a privileged user uploads a malformed PKCS#12 certificate via web interface or if PKI client functionality is configured.
    View CVE Details

    Affected Products
    Hitachi Energy RTU500

    Vendor:Hitachi Energy
    Product Version:RTU500 series CMU Firmware version 12.7.1 ? 12.7.7, RTU500 series CMU Firmware version 13.5.1 ? 13.5.4, RTU500 series CMU Firmware version 13.6.1 ? 13.6.3, RTU500 series CMU Firmware version 13.7.1 ? 13.7.8, RTU500 series CMU Firmware version 13.8.1
    Product Status:known_affected


    Remediations
    Vendor fixUpdate to CMU Firmware version 13.8.2
    MitigationFollow general mitigation factors/workarounds
    Vendor fixUpdate to CMU Firmware version 13.7.9 (when available) or 13.8.2

    Relevant CWE: CWE-476 NULL Pointer Dereference

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.1
    6.5
    MEDIUM
    CVSS:3.1/AV:N/AC:L/PR:L/UI:N/S:U/C:N/I:N/A:H







    CVE-2026-24515

    CWE-476: NULL Pointer Dereference. In libexpat before 2.7.4, XML_ExternalEntityParserCreate does not copy unknown encoding handler user data, causing Denial of Service impact. Product is only affected if IEC 61850 functionality is configured.
    View CVE Details

    Affected Products
    Hitachi Energy RTU500

    Vendor:Hitachi Energy
    Product Version:RTU500 series CMU Firmware version 12.7.1 ? 12.7.7, RTU500 series CMU Firmware version 13.5.1 ? 13.5.4, RTU500 series CMU Firmware version 13.6.1 ? 13.6.3, RTU500 series CMU Firmware version 13.7.1 ? 13.7.8, RTU500 series CMU Firmware version 13.8.1
    Product Status:known_affected


    Remediations
    Vendor fixUpdate to CMU Firmware version 13.8.2
    MitigationFollow general mitigation factors/workarounds
    Vendor fixUpdate to CMU Firmware version 13.7.9 (when available) or 13.8.2

    Relevant CWE: CWE-476 NULL Pointer Dereference

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.1
    2.5
    LOW
    CVSS:3.1/AV:L/AC:H/PR:L/UI:N/S:U/C:N/I:N/A:L







    CVE-2026-25210

    CWE-190: Integer Overflow or Wraparound. In libexpat before 2.7.4, the doContent function does not properly determine the buffer size bufSize because there is no integer overflow check for tag buffer reallocation, primarily causing Denial of Service and potentially confidentiality and integrity impact to the product. Product is only affected if IEC 61850 functionality is configured.
    View CVE Details

    Affected Products
    Hitachi Energy RTU500

    Vendor:Hitachi Energy
    Product Version:RTU500 series CMU Firmware version 12.7.1 ? 12.7.7, RTU500 series CMU Firmware version 13.5.1 ? 13.5.4, RTU500 series CMU Firmware version 13.6.1 ? 13.6.3, RTU500 series CMU Firmware version 13.7.1 ? 13.7.8, RTU500 series CMU Firmware version 13.8.1
    Product Status:known_affected


    Remediations
    Vendor fixUpdate to CMU Firmware version 13.8.2
    MitigationFollow general mitigation factors/workarounds
    Vendor fixUpdate to CMU Firmware version 13.7.9 (when available) or 13.8.2

    Relevant CWE: CWE-190 Integer Overflow or Wraparound

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.1
    7.8
    HIGH
    CVSS:3.1/AV:L/AC:L/PR:L/UI:N/S:U/C:H/I:H/A:H







    CVE-2026-32776

    CWE-476: NULL Pointer Dereference. libexpat before 2.7.5 allows a NULL pointer dereference with empty external parameter entity content, causing Denial of Service impact. Product is only affected if IEC 61850 functionality is configured.
    View CVE Details

    Affected Products
    Hitachi Energy RTU500

    Vendor:Hitachi Energy
    Product Version:RTU500 series CMU Firmware version 12.7.1 ? 12.7.7, RTU500 series CMU Firmware version 13.5.1 ? 13.5.4, RTU500 series CMU Firmware version 13.6.1 ? 13.6.3, RTU500 series CMU Firmware version 13.7.1 ? 13.7.8, RTU500 series CMU Firmware version 13.8.1
    Product Status:known_affected


    Remediations
    Vendor fixUpdate to CMU Firmware version 13.8.2
    MitigationFollow general mitigation factors/workarounds
    Vendor fixUpdate to CMU Firmware version 13.7.9 (when available) or 13.8.2

    Relevant CWE: CWE-476 NULL Pointer Dereference

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.1
    5.5
    MEDIUM
    CVSS:3.1/AV:L/AC:L/PR:L/UI:N/S:U/C:N/I:N/A:H







    CVE-2026-32777

    CWE-835: Loop with Unreachable Exit Condition ('Infinite Loop'). libexpat before 2.7.5 allows an infinite loop while parsing DTD content, causing Denial of Service impact. Product is only affected if IEC 61850 functionality is configured.
    View CVE Details

    Affected Products
    Hitachi Energy RTU500

    Vendor:Hitachi Energy
    Product Version:RTU500 series CMU Firmware version 12.7.1 ? 12.7.7, RTU500 series CMU Firmware version 13.5.1 ? 13.5.4, RTU500 series CMU Firmware version 13.6.1 ? 13.6.3, RTU500 series CMU Firmware version 13.7.1 ? 13.7.8, RTU500 series CMU Firmware version 13.8.1
    Product Status:known_affected


    Remediations
    Vendor fixUpdate to CMU Firmware version 13.8.2
    MitigationFollow general mitigation factors/workarounds
    Vendor fixUpdate to CMU Firmware version 13.7.9 (when available) or 13.8.2

    Relevant CWE: CWE-835 Loop with Unreachable Exit Condition ('Infinite Loop')

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.1
    5.5
    MEDIUM
    CVSS:3.1/AV:L/AC:L/PR:L/UI:N/S:U/C:N/I:N/A:H







    CVE-2026-32778

    CWE-476: NULL Pointer Dereference. libexpat before 2.7.5 allows a NULL pointer dereference in the function setContext on retry after an earlier out-of-memory condition, causing Denial of Service impact. Product is only affected if IEC 61850 functionality is configured.
    View CVE Details

    Affected Products
    Hitachi Energy RTU500

    Vendor:Hitachi Energy
    Product Version:RTU500 series CMU Firmware version 12.7.1 ? 12.7.7, RTU500 series CMU Firmware version 13.5.1 ? 13.5.4, RTU500 series CMU Firmware version 13.6.1 ? 13.6.3, RTU500 series CMU Firmware version 13.7.1 ? 13.7.8, RTU500 series CMU Firmware version 13.8.1
    Product Status:known_affected


    Remediations
    Vendor fixUpdate to CMU Firmware version 13.8.2
    MitigationFollow general mitigation factors/workarounds
    Vendor fixUpdate to CMU Firmware version 13.7.9 (when available) or 13.8.2

    Relevant CWE: CWE-476 NULL Pointer Dereference

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.1
    5.5
    MEDIUM
    CVSS:3.1/AV:L/AC:L/PR:L/UI:N/S:U/C:N/I:N/A:H







    CVE-2026-8479

    CWE-476: NULL Pointer Dereference. IEC 60870-5-104 used in bidirectional mode is vulnerable for a NULL pointer dereferencing, if a specially crafted sequence of messages is sent for a certain time, causing Denial of Service impact. Product is only affected if IEC 60870-5-104 functionality in bidirectional mode (BCI) is configured.
    View CVE Details

    Affected Products
    Hitachi Energy RTU500

    Vendor:Hitachi Energy
    Product Version:RTU500 series CMU Firmware version 12.7.1 ? 12.7.7, RTU500 series CMU Firmware version 13.5.1 ? 13.5.4, RTU500 series CMU Firmware version 13.6.1 ? 13.6.3, RTU500 series CMU Firmware version 13.7.1 ? 13.7.7, RTU500 series CMU Firmware version 13.8.1
    Product Status:known_affected


    Remediations
    Vendor fixUpdate to CMU Firmware version 13.8.2
    MitigationFollow general mitigation factors/workarounds
    Vendor fixUpdate to CMU Firmware version 13.7.8

    Relevant CWE: CWE-476 NULL Pointer Dereference

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.1
    6.5
    MEDIUM
    CVSS:3.1/AV:A/AC:L/PR:N/UI:N/S:U/C:N/I:N/A:H


    4.0
    6.9
    MEDIUM
    CVSS:4.0/AV:A/AC:L/AT:N/PR:L/UI:N/VC:N/VI:N/VA:H/SC:N/SI:N/SA:N








    Acknowledgments

    Hitachi Energy Internal Team reported this vulnerability to CISA.ÿ


    Notice
    The information in this document is subject to change without notice and should not be construed as a commitment by Hitachi Energy. Hitachi Energy provides no warranty, express or implied, including warranties of merchantability and fitness for a particular purpose, for the information contained in this document, and assumes no responsibility for any errors that may appear in this document. In no event shall Hitachi Energy or any of its suppliers be liable for direct, indirect, special, incidental or consequential damages of any nature or kind arising from the use of this document, or from the use of any hardware or software described in this document, even if Hitachi Energy or its suppliers have been advised of the possibility of such damages. This document and parts hereof must not be reproduced or copied without written permission from Hitachi Energy and the contents hereof must not be imparted to a third party nor used for any unauthorized purpose. All rights to registrations and trademarks reside with their respective owners.

    Support
    For additional information and support please contact your product provider or Hitachi Energy service organization. For contact information, see https://www.hitachienergy.com/contact-us/ for Hitachi Energy contact-centers.

    General Mitigation Factors
    Recommended security practices and firewall configurations can help protect a process control network from attacks that originate from outside the network. Such practices include that process control systems are physically protected from direct access by unauthorized personnel, have no direct connections to the Internet, and are separated from other networks by means of a firewall system that has a minimal number of ports exposed, and others that have to be evaluated case by case. Process control systems should not be used for Internet surfing, instant messaging, or receiving e-mails. Portable computers and removable storage media should be carefully scanned for viruses before they are connected to a control system. Proper password policies and processes should be followed. Additional information on Industrial Control Systems Cybersecurity Best Practices can be found in the following Hitachi Energy Cybersecurity Notification. Cybersecurity Advisory - Industrial Control Systems Cybersecurity Best Practices

    SSVC
    SSVCv2/E:N/A:N/2026-05-26T08:50:36Z/

    Legal Notice and Terms of Use
    This product is provided subject to this Notification (https://www.cisa.gov/notification) and this Privacy & Use policy (https://www.cisa.gov/privacy-policy).

    Recommended Practices
    CISA recommends users take defensive measures to minimize the exploitation risk of this vulnerability.
    Minimize network exposure for all control system devices and/or systems, and ensure they are not accessible from the internet.
    Locate control system networks and remote devices behind firewalls and isolate them from business networks.
    When remote access is required, use more secure methods, such as Virtual Private Networks (VPNs), recognizing VPNs may have vulnerabilities and should be updated to the most recent version available. Also recognize VPN is only as secure as its connected devices.
    CISA reminds organizations to perform proper impact analysis and risk assessment prior to deploying defensive measures.
    CISA also provides a section for control systems security recommended practices on the ICS webpage on cisa.gov. Several CISA products detailing cyber defense best practices are available for reading and download, including Improving Industrial Control Systems Cybersecurity with Defense-in-Depth Strategies.
    CISA encourages organizations to implement recommended cybersecurity strategies for proactive defense of ICS assets. Additional mitigation guidance and recommended practices are publicly available on the ICS webpage at cisa.gov in the technical information paper, ICS-TIP-12-146-01B--Targeted Cyber Intrusion Detection and Mitigation Strategies.
    Organizations observing suspected malicious activity should follow established internal procedures and report findings to CISA for tracking and correlation against other incidents.

    Advisory Conversion Disclaimer
    This ICSA is a verbatim republication of Hitachi Energy PSIRT 8DBD000252 from a direct conversion of the vendor's Common Security Advisory Framework (CSAF) advisory. This is republished to CISA's website as a means of increasing visibility and is provided "as-is" for informational purposes only. CISA is not responsible for the editorial or technical accuracy of republished advisories and provides no warranties of any kind regarding any information contained within this advisory. Further, CISA does not endorse any commercial product or service. Please contact Hitachi Energy PSIRT directly for any questions regarding this advisory.
    Revision History

    Initial Release Date: 2026-05-26




    Date
    Revision
    Summary




    2026-05-26
    1
    Initial public release


    2026-06-04
    2
    Initial CISA Republication of Hitachi Energy PSIRT 8DBD000252 advisory




    Legal Notice and Terms of Use

    https://www.cisa.gov/news-events/ics-advisories/icsa-26-155-04

    2026-06-04 12:00 UTC
    --- FMail-lnx 2.3.4.1-B20260522
    * Origin: TCOB1 A Mail Only System (2:263/1)
  • From Cisa Advisories@2:263/1 to All on Tue Oct 6 18:03:06 2026
    Hitachi Energy RTU500

    View CSAF
    Summary
    Hitachi Energy is publishing this cybersecurity advisory in response to the security findings reported by Dragos affecting end-of-life RTU500 CMU firmware version 9.x. The reported findings are associated with legacy RTU500 firmware versions that were developed according to the cybersecurity requirements, threat landscape, and industry practices that existed at the time of their release. As cybersecurity threats and security expectations have evolved, these end-of-life versions no longer incorporate many of the security controls and hardening measures that are standard in modern industrial control systems. Over successive RTU500 releases, Hitachi Energy has continuously enhanced the security of the product through the introduction of additional security features, protocol hardening, stronger authentication and access controls, encrypted communications, and other security-by-design improvements. While the findings reported by Dragos do not affect currently supported RTU500 CMU firmware versions, there is a li
    kelihood that the end-of-life versions 11.x and prior are affected by these vulnerabilities. Since the end-of-life versions are no longer maintained with security updates, Hitachi Energy strongly recommends upgrading to a currently supported RTU500 firmware version. Customers should also implement appropriate defense-in-depth measures and cybersecurity best practices to reduce risk and strengthen the security posture of their operational environments. Please refer to the Recommended Immediate Actions for information about the mitigation/remediation.
    The following versions of Hitachi Energy RTU500 are affected:

    RTU500 series CMU Firmware vers:RTU500_series_CMU_Firmware/<=11.x (CVE-2026-8065, CVE-2026-8066, CVE-2026-8067, CVE-2010-2965, CVE-2014-9195, CVE-2023-46143)





    CVSS
    Vendor
    Equipment




    v3 9.8
    Hitachi Energy
    RTU500 series CMU Firmware






    5 Vulnerabilities




    Missing Authentication for Critical Function, Relative Path Traversal, Missing Authorization, Incorrect Authorization, Download of Code Without Integrity Check




    Background

    Critical Infrastructure Sectors: Energy Countries/Areas Deployed: Worldwide Company Headquarters Location: Switzerland


    Vulnerabilities
    Expand All +

    CVE-2026-8065
    An authentication bypass vulnerability in the firmware update endpoint of Hitachi Energy RTU500 allows an unauthenticated attacker to upload arbitrary firmware through a crafted POST request. Successful exploitation could allow the attacker to modify device functionality or compromise the integrity or availability of the device.
    Read More

    1 Affected Product

    RTU500 series CMU Firmware versions 11.x and prior (End-of-Life)

    Product Status: known_affected

    Remediations

    Vendor fixUpgrade to version 12.7.8 or 13.9.1 or latest


    Additional Metrics
    Relevant CWE: CWE-306 Missing Authentication for Critical Function




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.1
    9.1
    CRITICAL
    CVSS:3.1/AV:N/AC:L/PR:N/UI:N/S:U/C:N/I:H/A:H





    View CVE Details



    CVE-2026-8066
    A directory traversal vulnerability in the file upload functionality of Hitachi Energy RTU500 allows an unauthenticated attacker to write or overwrite arbitrary files on the device file system. Depending on the files affected, successful exploitation could result in unauthorized modification of device data or disruption of the device?s intended operation. Read More

    2 Affected Products

    RTU500 series CMU Firmware versions 11.x and prior (End-of-Life)

    Product Status: known_affected

    Remediations

    Vendor fixUpgrade to version 12.7.8 or 13.9.1 or latest


    RTU500 series CMU Firmware versions 11.x and prior (End-of-Life)

    Product Status: known_affected

    Remediations

    Vendor fixUpgrade to version 12.7.8 or 13.9.1 or latest


    Additional Metrics
    Relevant CWE: CWE-23 Relative Path Traversal




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.1
    9.1
    CRITICAL
    CVSS:3.1/AV:N/AC:L/PR:N/UI:N/S:U/C:N/I:H/A:H





    View CVE Details



    CVE-2026-8067
    An improper authorization vulnerability in the RTU500?s web application allows an authenticated user to trigger the RTU500 to reboot through the reset endpoint. Successful exploitation could cause temporary device unavailability and disruption of its intended operation. Read More

    3 Affected Products

    RTU500 series CMU Firmware versions 11.x and prior (End-of-Life)

    Product Status: known_affected

    Remediations

    Vendor fixUpgrade to version 12.7.8 or 13.9.1 or latest


    RTU500 series CMU Firmware versions 11.x and prior (End-of-Life)

    Product Status: known_affected

    Remediations

    Vendor fixUpgrade to version 12.7.8 or 13.9.1 or latest


    RTU500 series CMU Firmware versions 11.x and prior (End-of-Life)

    Product Status: known_affected

    Remediations

    Vendor fixUpgrade to version 12.7.8 or 13.9.1 or latest


    Additional Metrics
    Relevant CWE: CWE-862 Missing Authorization




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.1
    6.5
    MEDIUM
    CVSS:3.1/AV:N/AC:L/PR:L/UI:N/S:U/C:N/I:N/A:H





    View CVE Details



    CVE-2010-2965
    The WDB target agent debug service in Wind River VxWorks 6.x, 5.x, and earlier, as used on few of the Hitachi Energy RTU500 CMU firmware legacy versions, allows remote attackers to read or modify arbitrary memory locations, perform function calls, or manage tasks via requests to UDP port 17185. Read More

    4 Affected Products

    RTU500 series CMU Firmware versions 11.x and prior (End-of-Life)

    Product Status: known_affected

    Remediations

    Vendor fixUpgrade to version 12.7.8 or 13.9.1 or latest


    RTU500 series CMU Firmware versions 11.x and prior (End-of-Life)

    Product Status: known_affected

    Remediations

    Vendor fixUpgrade to version 12.7.8 or 13.9.1 or latest


    RTU500 series CMU Firmware versions 11.x and prior (End-of-Life)

    Product Status: known_affected

    Remediations

    Vendor fixUpgrade to version 12.7.8 or 13.9.1 or latest


    RTU500 series CMU Firmware versions 11.x and prior (End-of-Life)

    Product Status: known_affected

    Remediations

    Vendor fixUpgrade to version 12.7.8 or 13.9.1 or latest


    Additional Metrics
    Relevant CWE: CWE-863 Incorrect Authorization




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.1
    9.8
    CRITICAL
    CVSS:3.1/AV:N/AC:L/PR:N/UI:N/S:U/C:H/I:H/A:H





    View CVE Details



    CVE-2014-9195
    Missing authentication vulnerability in a network service of Hitachi Energy RTU500 allows an unauthenticated remote attacker to execute arbitrary commands
    using protocol-compliant network traffic. Successful exploitation could result in unauthorized modification of the device or disruption of its intended operation.
    Read More

    5 Affected Products

    RTU500 series CMU Firmware versions 11.x and prior (End-of-Life)

    Product Status: known_affected

    Remediations

    Vendor fixUpgrade to version 12.7.8 or 13.9.1 or latest


    RTU500 series CMU Firmware versions 11.x and prior (End-of-Life)

    Product Status: known_affected

    Remediations

    Vendor fixUpgrade to version 12.7.8 or 13.9.1 or latest


    RTU500 series CMU Firmware versions 11.x and prior (End-of-Life)

    Product Status: known_affected

    Remediations

    Vendor fixUpgrade to version 12.7.8 or 13.9.1 or latest


    RTU500 series CMU Firmware versions 11.x and prior (End-of-Life)

    Product Status: known_affected

    Remediations

    Vendor fixUpgrade to version 12.7.8 or 13.9.1 or latest


    RTU500 series CMU Firmware versions 11.x and prior (End-of-Life)

    Product Status: known_affected

    Remediations

    Vendor fixUpgrade to version 12.7.8 or 13.9.1 or latest


    Additional Metrics
    Relevant CWE: CWE-306 Missing Authentication for Critical Function




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.1
    8.1
    HIGH
    CVSS:3.1/AV:N/AC:H/PR:N/UI:N/S:U/C:H/I:H/A:H





    View CVE Details



    CVE-2023-46143
    A download of code without integrity check vulnerability in Hitachi Energy RTU500 allows an unauthenticated remote attacker to modify some or all
    applications running on the device. Successful exploitation could result in unauthorized modification of device functionality or disruption of its intended operation.
    Read More

    6 Affected Products

    RTU500 series CMU Firmware versions 11.x and prior (End-of-Life)

    Product Status: known_affected

    Remediations

    Vendor fixUpgrade to version 12.7.8 or 13.9.1 or latest


    RTU500 series CMU Firmware versions 11.x and prior (End-of-Life)

    Product Status: known_affected

    Remediations

    Vendor fixUpgrade to version 12.7.8 or 13.9.1 or latest


    RTU500 series CMU Firmware versions 11.x and prior (End-of-Life)

    Product Status: known_affected

    Remediations

    Vendor fixUpgrade to version 12.7.8 or 13.9.1 or latest


    RTU500 series CMU Firmware versions 11.x and prior (End-of-Life)

    Product Status: known_affected

    Remediations

    Vendor fixUpgrade to version 12.7.8 or 13.9.1 or latest


    RTU500 series CMU Firmware versions 11.x and prior (End-of-Life)

    Product Status: known_affected

    Remediations

    Vendor fixUpgrade to version 12.7.8 or 13.9.1 or latest


    RTU500 series CMU Firmware versions 11.x and prior (End-of-Life)

    Product Status: known_affected

    Remediations

    Vendor fixUpgrade to version 12.7.8 or 13.9.1 or latest


    Additional Metrics
    Relevant CWE: CWE-494 Download of Code Without Integrity Check




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.1
    7.5
    HIGH
    CVSS:3.1/AV:N/AC:L/PR:N/UI:N/S:U/C:N/I:H/A:N





    View CVE Details



    Acknowledgments

    Dragos reported these vulnerabilities to CISA.


    Notice
    The information in this document is subject to change without notice and should not be construed as a commitment by Hitachi Energy. Hitachi Energy provides no warranty, express or implied, including warranties of merchantability and fitness for a particular purpose, for the information contained in this document, and assumes no responsibility for any errors that may appear in this document. In no event shall Hitachi Energy or any of its suppliers be liable for direct, indirect, special, incidental or consequential damages of any nature or kind arising from the use of this document, or from the use of any hardware or software described in this document, even if Hitachi Energy or its suppliers have been advised of the possibility of such damages. This document and parts hereof must not be reproduced or copied without written permission from Hitachi Energy and the contents hereof must not be imparted to a third party nor used for any unauthorized purpose. All rights to registrations and trademarks reside with t
    heir respective owners.

    Support
    For additional information and support please contact your product provider or Hitachi Energy service organization. For contact information, see https://www.hitachienergy.com/contact-us/ for Hitachi Energy contact-centers.

    General Mitigation Factors
    Recommended security practices and firewall configurations can help protect a process control network from attacks that originate from outside the network. Such practices include that process control systems are physically protected from direct access by unauthorized personnel, have no direct connections to the Internet, and are separated from other networks by means of a firewall system that has a minimal number of ports exposed, and others that have to be evaluated case by case. Process control systems should not be used for Internet surfing, instant messaging, or receiving e-mails. Portable computers and removable storage media should be carefully scanned for viruses before they are connected to a control system. Proper password policies and processes should be followed. Additional information on Industrial Control Systems Cybersecurity Best Practices can be found in the Hitachi Energy ?Industrial Control Systems Cybersecurity Best Practices? Cybersecurity Notification. [1]

    SSVC
    SSVCv2/E:N/A:N/2026-09-28T14:38:32Z/

    Legal Notice and Terms of Use
    This product is provided subject to this Notification (https://www.cisa.gov/notification) and this Privacy & Use policy (https://www.cisa.gov/privacy-policy).

    Recommended Practices
    CISA recommends users take defensive measures to minimize the exploitation risk of this vulnerability.
    Minimize network exposure for all control system devices and/or systems, and ensure they are not accessible from the internet. Locate control system networks and remote devices behind firewalls and isolate them from business networks.
    When remote access is required, use more secure methods, such as Virtual Private Networks (VPNs), recognizing VPNs may have vulnerabilities and should be updated to the most recent version available. Also recognize VPN is only as secure as its connected devices.
    CISA reminds organizations to perform proper impact analysis and risk assessment prior to deploying defensive measures. CISA also provides a section for control systems security recommended practices
    on the ICS webpage on cisa.gov. Several CISA products detailing cyber defense best practices are available for reading and download, including Improving Industrial Control Systems Cybersecurity with Defense-in-Depth Strategies. CISA encourages organizations to implement recommended cybersecurity strategies
    for proactive defense of ICS assets. Additional mitigation guidance and recommended practices are publicly available on the ICS webpage at cisa.gov in the technical information paper, ICS-TIP-12-146-01B--Targeted Cyber Intrusion Detection and Mitigation Strategies. Organizations observing suspected malicious activity should follow established internal procedures and report findings to CISA for tracking and correlation against other incidents.

    Advisory Conversion Disclaimer
    This ICSA is a verbatim republication of Hitachi Energy PSIRT 8DBD000251 from a direct conversion of the vendor's Common Security Advisory Framework (CSAF) advisory. This is republished to CISA's website as a means of increasing visibility and is provided "as-is" for informational purposes only. CISA is not responsible for the editorial or technical accuracy of republished advisories and provides no warranties of any kind regarding any information contained within this advisory. Further, CISA does not endorse any commercial product or service. Please contact Hitachi Energy PSIRT directly for any questions regarding this advisory.
    Revision History

    Initial Release Date: 2026-09-29




    Date
    Revision
    Summary




    2026-09-29
    1
    Initial public release


    2026-10-06
    2
    Initial CISA Republication of Hitachi Energy PSIRT 8DBD000251 advisory




    Legal Notice and Terms of Use

    https://www.cisa.gov/news-events/ics-advisories/icsa-26-279-06

    2026-10-06 12:00 UTC

    --- BBBS/LiR v4.10 Toy-7