• ABB WebPro SNMP Card PowerValue Multiple Vulnerabilities

    From CISA Advisories@2:263/1 to All on Tue May 12 16:11:06 2026
    ABB WebPro SNMP Card PowerValue Multiple Vulnerabilities

    View CSAF
    Summary
    ABB became aware of multiple internally discovered vulnerabilities in the WebPro SNMP card PowerValue for the product versions listed as affected in the advisory. Depending upon the vulnerability, an attacker with access to local network who successfully exploited this vulnerability could have - Unauthorized access - Insufficient Session Expiration leading to resource unavailability - Uncontrolled Resource Consumption leading to DOS attack ABB strongly advises customers to update the latest firmware of affected products.
    The following versions of ABB WebPro SNMP Card PowerValue Multiple Vulnerabilities are affected:

    WebPro SNMP Card <=1.1.8.k, 1.1.8.p





    CVSS
    Vendor
    Equipment
    Vulnerabilities




    v3 8.8
    ABB
    ABB WebPro SNMP Card PowerValue Multiple Vulnerabilities
    Improper Check for Unusual or Exceptional Conditions, Incorrect Implementation of Authentication Algorithm, Insufficient Session Expiration




    Background

    Critical Infrastructure Sectors: Chemical, Communications, Critical Manufacturing, Dams, Energy, Healthcare and Public Health, Information Technology, Water and Wastewater
    Countries/Areas Deployed: Worldwide
    Company Headquarters Location: Switzerland


    Vulnerabilities

    Expand All +

    CVE-2025-4675

    Modus(slave) protocol was implemented incorrectly in the device, port 502 becomes unstable and Modbus service is unavailable until manual reboot of the device.
    View CVE Details

    Affected Products
    ABB WebPro SNMP Card PowerValue Multiple Vulnerabilities

    Vendor:ABB
    Product Version:ABB WebPro SNMP Card PowerValue <=1.1.8.k
    Product Status:fixed, known_affected


    Remediations
    Vendor fixThe problem is corrected in the following product versions: WebPro SNMP card PowerValue version 1.1.8.p ABB advises users of the affected product versions to reach out to ABB Digital Service Support (ch.ups.digital@abb.com) for guidance and recommended actions. Additionally, ABB recommends implementing defensive measures to reduce the risk of vulnerability exploitation, as outlined in the product instruction manual. Please refer to the section ?Mitigation factors? for more information.
    MitigationMitigating factors describe conditions and circumstances that make an attack that exploits the vulnerability difficult or less likely to succeed. In case customer cannot opt for not to upgrade the firmware or it is not feasible then please immediately apply mitigating factors mentioned in ?General security recommendations?.

    Relevant CWE: CWE-754 Improper Check for Unusual or Exceptional Conditions

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.1
    6.5
    MEDIUM
    CVSS:3.1/AV:A/AC:L/PR:N/UI:N/S:U/C:N/I:N/A:H/E:F/RL:O/RC:U







    CVE-2025-4676

    Device web HMI authenticates user by validating the first character of the session cookie and authentication token. So, if only the first characters of the session cookie and token are correct, a user will be validated. An attacker can easily brute force the first character of both session cookie and bearer token. This vulnerability allows an attacker to easily bypass the authentication implemented on the device.
    View CVE Details

    Affected Products
    ABB WebPro SNMP Card PowerValue Multiple Vulnerabilities

    Vendor:ABB
    Product Version:ABB WebPro SNMP Card PowerValue <=1.1.8.k
    Product Status:fixed, known_affected


    Remediations
    Vendor fixThe problem is corrected in the following product versions: WebPro SNMP card PowerValue version 1.1.8.p ABB advises users of the affected product versions to reach out to ABB Digital Service Support (ch.ups.digital@abb.com) for guidance and recommended actions. Additionally, ABB recommends implementing defensive measures to reduce the risk of vulnerability exploitation, as outlined in the product instruction manual. Please refer to the section ?Mitigation factors? for more information.
    MitigationMitigating factors describe conditions and circumstances that make an attack that exploits the vulnerability difficult or less likely to succeed. In case customer cannot opt for not to upgrade the firmware or it is not feasible then please immediately apply mitigating factors mentioned in ?General security recommendations?.

    Relevant CWE: CWE-303 Incorrect Implementation of Authentication Algorithm

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.1
    8.8
    HIGH
    CVSS:3.1/AV:A/AC:L/PR:N/UI:R/S:C/C:H/I:H/A:H/E:F/RL:O/RC:U







    CVE-2025-4677

    Idle session timeout is not configured for port 23 and 502 in device, due to which an attacker can make number of connections to the device and since device is not destroying the connections, it can lead to unavailability of the resources from the device.
    View CVE Details

    Affected Products
    ABB WebPro SNMP Card PowerValue Multiple Vulnerabilities

    Vendor:ABB
    Product Version:ABB WebPro SNMP Card PowerValue <=1.1.8.k
    Product Status:fixed, known_affected


    Remediations
    Vendor fixThe problem is corrected in the following product versions: WebPro SNMP card PowerValue version 1.1.8.p ABB advises users of the affected product versions to reach out to ABB Digital Service Support (ch.ups.digital@abb.com) for guidance and recommended actions. Additionally, ABB recommends implementing defensive measures to reduce the risk of vulnerability exploitation, as outlined in the product instruction manual. Please refer to the section ?Mitigation factors? for more information.
    MitigationMitigating factors describe conditions and circumstances that make an attack that exploits the vulnerability difficult or less likely to succeed. In case customer cannot opt for not to upgrade the firmware or it is not feasible then please immediately apply mitigating factors mentioned in ?General security recommendations?.

    Relevant CWE: CWE-613 Insufficient Session Expiration

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.1
    6.5
    MEDIUM
    CVSS:3.1/AV:A/AC:L/PR:N/UI:N/S:U/C:N/I:N/A:H/E:F/RL:O/RC:U








    Acknowledgments

    ABB PSIRT reported these vulnerabilities to CISA.


    Notice
    The information in this document is subject to change without notice, and should not be construed as a commitment by ABB. ABB provides no warranty, express or implied, including warranties of merchantability and fitness for a particular purpose, for the information contained in this document, and assumes no responsibility for any errors that may appear in this document. In no event shall ABB or any of its suppliers be liable for direct, indirect, special, incidental or consequential damages of any nature or kind arising from the use of this document, or from the use of any hardware or software described in this document, even if ABB or its suppliers have been advised of the possibility of such damages. This document and parts hereof must not be reproduced or copied without written permission from ABB, and the contents hereof must not be imparted to a third party nor used for any unauthorized purpose. All rights to registrations and trademarks reside with their respective owners.

    Frequently Asked Questions
    What causes the vulnerability? - The vulnerabilities are caused by code defects allowing the attacker to do various unintended, unauthorized actions on the target device. Please look at the description of the respective vulnerabilities in section ?Vulnerability severity and details? for further details. What is WebPro SNMP Card PowerValue? - The WebPro SNMP Card PowerValue provide web server to monitor and manage multiple UPS products in networked environment. It can detect temperature and humidity for the environment via connecting to EMD (Environmental Monitoring Device). It can not only prevent data loss from power outage and safely shutdown systems but also store programming data and scheduled shut down the UPS. All UPS warning and fault event records can be kept in WebPro SNMP Card PowerValue. What might an attacker use the vulnerability to do? - If mentioned vulnerabilities have been successfully exploited by an attacker, this could allow the attacker to take control of the target WebPro SNMP Card PowerValue device. How could an attacker exploit the vulnerability? - An attacker could try to exploit the vulnerability by creating a specially crafted message and sending the message to WebPro SNMP Card PowerValue device. This would require that the attacker has access to the system network, by connecting to the network either directly or through a wrongly configured or penetrated security system. Could the vulnerability be exploited remotely? - Yes, an attacker who has network access to an affected system node could exploit this vulnerability. Recommended practices include that User?s network systems are physically protected, have no direct connections to the Internet nor any other untrusted network, and are separated from other networks by means of a firewall system that has a minimal number of ports exposed. What does the update do? - WebPro SNMP Card PowerValue v1.1.8.p update has fixes for all the vulnerabilities mentioned in ?Vulnerability severity and details? section. When this security advisory was issued, had this vulnerability been publicly disclosed? - No, the vulnerabilities have not been publicly disclosed. When this security advisory was issued, had ABB received any reports that this vulnerability was being exploited? - No, ABB had not received any information indicating that this vulnerability had been exploited when this security advisory was originally issued.

    Legal Notice and Terms of Use
    This product is provided subject to this Notification (https://www.cisa.gov/notification) and this Privacy & Use policy (https://www.cisa.gov/privacy-policy).

    Recommended Practices
    CISA recommends users take defensive measures to minimize the exploitation risk of this vulnerability.
    Minimize network exposure for all control system devices and/or systems, and ensure they are not accessible from the internet.
    Locate control system networks and remote devices behind firewalls and isolate them from business networks.
    When remote access is required, use more secure methods, such as Virtual Private Networks (VPNs), recognizing VPNs may have vulnerabilities and should be updated to the most recent version available. Also recognize VPN is only as secure as its connected devices.
    CISA reminds organizations to perform proper impact analysis and risk assessment prior to deploying defensive measures.
    CISA also provides a section for control systems security recommended practices on the ICS webpage on cisa.gov. Several CISA products detailing cyber defense best practices are available for reading and download, including Improving Industrial Control Systems Cybersecurity with Defense-in-Depth Strategies.
    CISA encourages organizations to implement recommended cybersecurity strategies for proactive defense of ICS assets. Additional mitigation guidance and recommended practices are publicly available on the ICS webpage at cisa.gov in the technical information paper, ICS-TIP-12-146-01B--Targeted Cyber Intrusion Detection and Mitigation Strategies.
    Organizations observing suspected malicious activity should follow established internal procedures and report findings to CISA for tracking and correlation against other incidents.

    Advisory Conversion Disclaimer
    This ICSA is a verbatim republication of ABB PSIRT 2CRT000009 from a direct conversion of the vendor's Common Security Advisory Framework (CSAF) advisory. This is republished to CISA's website as a means of increasing visibility and is provided "as-is" for informational purposes only. CISA is not responsible for the editorial or technical accuracy of republished advisories and provides no warranties of any kind regarding any information contained within this advisory. Further, CISA does not endorse any commercial product or service. Please contact ABB PSIRT directly for any questions regarding this advisory.
    Revision History

    Initial Release Date: 2026-01-07




    Date
    Revision
    Summary




    2026-01-07
    1
    Initial version.


    2026-05-12
    2
    Initial CISA Republication of ABB PSIRT 2CRT000009 advisory




    Legal Notice and Terms of Use

    https://www.cisa.gov/news-events/ics-advisories/icsa-26-132-06

    2026-05-12 12:00 UTC
    --- FMail-lnx 2.3.2.6-B20251227