• Subnet Solutions PowerSYSTEM Center

    From CISA Advisories@2:263/1 to All on Tue May 12 16:11:06 2026
    Subnet Solutions PowerSYSTEM Center

    View CSAF
    Summary
    Successful exploitation of these vulnerabilities could allow an authenticated attacker to expose sensitive information or cause a CRLF injection.
    The following versions of Subnet Solutions PowerSYSTEM Center are affected:

    PowerSYSTEM Center 2020 <=5.28.x (CVE-2026-35504)
    PowerSYSTEM Center 2020 >=5.8.x|<=5.28.x (CVE-2026-26289)
    PowerSYSTEM Center 2020 >=5.11.x|<=5.28.x (CVE-2026-33570)
    PowerSYSTEM Center 2024 >=6.0.x|<=6.1.x (CVE-2026-26289, CVE-2026-35555, CVE-2026-35504)
    PowerSYSTEM Center 2026 7.0.x (CVE-2026-26289, CVE-2026-35555, CVE-2026-35504)





    CVSS
    Vendor
    Equipment
    Vulnerabilities




    v3 8.2
    Subnet Solutions Inc.
    Subnet Solutions PowerSYSTEM Center
    Incorrect Authorization, Improper Neutralization of CRLF Sequences ('CRLF Injection')




    Background

    Critical Infrastructure Sectors: Critical Manufacturing, Energy
    Countries/Areas Deployed: Worldwide
    Company Headquarters Location: Canada


    Vulnerabilities

    Expand All +

    CVE-2026-26289

    PowerSYSTEM Center REST API endpoint for device account export allows an authenticated user with limited permissions to expose sensitive information normally restricted to administrative permissions only.
    View CVE Details

    Affected Products
    Subnet Solutions PowerSYSTEM Center

    Vendor:Subnet Solutions Inc.
    Product Version:Subnet Solutions Inc. PowerSYSTEM Center 2020: >=5.8.x|<=5.28.x, Subnet Solutions Inc. PowerSYSTEM Center 2024: >=6.0.x|<=6.1.x, Subnet Solutions Inc. PowerSYSTEM Center 2026: 7.0.x
    Product Status:known_affected


    Remediations
    MitigationSubnet Solutions recommends users update to the latest version of PowerSYSTEM Center PSC 2020 Update 29, PSC 2024 Update 2, and PSC 2026 GA Hotfix.
    MitigationFor assistance in upgrading, users should contact a Subnet Solutions System Integration team member or customer support team at (403) 270-8885 or by email at support@subnet.com.mailto:support@subnet.com
    MitigationSubnet Solutions recommends users do the following in order to reduce risk:Monitor user activity records to ensure users are following acceptable usage policies of the application.Restrict access to Notification Settings to trusted Administrators Monitor "Send from Address" in settings and Activity Records.Configure a notification rule that triggers in any bulk account export activity.

    Relevant CWE: CWE-863 Incorrect Authorization

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.1
    8.2
    HIGH
    CVSS:3.1/AV:A/AC:L/PR:L/UI:N/S:C/C:H/I:L/A:L







    CVE-2026-33570

    PowerSYSTEM Center REST API endpoint for devices allows a low privilege authenticated user to access information normally limited by operational permissions.
    View CVE Details

    Affected Products
    Subnet Solutions PowerSYSTEM Center

    Vendor:Subnet Solutions Inc.
    Product Version:Subnet Solutions Inc. PowerSYSTEM Center 2020: >=5.11.x|<=5.28.x
    Product Status:known_affected


    Remediations
    MitigationSubnet Solutions recommends users update to the latest version of PowerSYSTEM Center PSC 2020 Update 29, PSC 2024 Update 2, and PSC 2026 GA Hotfix.
    MitigationFor assistance in upgrading, users should contact a Subnet Solutions System Integration team member or customer support team at (403) 270-8885 or by email at support@subnet.com.mailto:support@subnet.com
    MitigationSubnet Solutions recommends users do the following in order to reduce risk:Monitor user activity records to ensure users are following acceptable usage policies of the application.Restrict access to Notification Settings to trusted Administrators Monitor "Send from Address" in settings and Activity Records.Configure a notification rule that triggers in any bulk account export activity.

    Relevant CWE: CWE-863 Incorrect Authorization

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.1
    5.7
    MEDIUM
    CVSS:3.1/AV:A/AC:L/PR:L/UI:N/S:U/C:H/I:N/A:N







    CVE-2026-35555

    PowerSYSTEM Center feature for device project groups allows an authenticated user with limited permissions to perform an unauthorized deletion of project groups.
    View CVE Details

    Affected Products
    Subnet Solutions PowerSYSTEM Center

    Vendor:Subnet Solutions Inc.
    Product Version:Subnet Solutions Inc. PowerSYSTEM Center 2024: >=6.0.x|<=6.1.x, Subnet Solutions Inc. PowerSYSTEM Center 2026: 7.0.x
    Product Status:known_affected


    Remediations
    MitigationSubnet Solutions recommends users update to the latest version of PowerSYSTEM Center PSC 2020 Update 29, PSC 2024 Update 2, and PSC 2026 GA Hotfix.
    MitigationFor assistance in upgrading, users should contact a Subnet Solutions System Integration team member or customer support team at (403) 270-8885 or by email at support@subnet.com.mailto:support@subnet.com
    MitigationSubnet Solutions recommends users do the following in order to reduce risk:Monitor user activity records to ensure users are following acceptable usage policies of the application.Restrict access to Notification Settings to trusted Administrators Monitor "Send from Address" in settings and Activity Records.Configure a notification rule that triggers in any bulk account export activity.

    Relevant CWE: CWE-863 Incorrect Authorization

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.1
    6.3
    MEDIUM
    CVSS:3.1/AV:A/AC:L/PR:L/UI:N/S:U/C:N/I:H/A:L







    CVE-2026-35504

    PowerSYSTEM Center email notification service is affected by a CRLF injection vulnerability when using SMTPS communication.
    View CVE Details

    Affected Products
    Subnet Solutions PowerSYSTEM Center

    Vendor:Subnet Solutions Inc.
    Product Version:Subnet Solutions Inc. PowerSYSTEM Center 2020: <=5.28.x, Subnet Solutions Inc. PowerSYSTEM Center 2024: >=6.0.x|<=6.1.x, Subnet Solutions Inc. PowerSYSTEM Center 2026: 7.0.x
    Product Status:known_affected


    Remediations
    MitigationSubnet Solutions recommends users update to the latest version of PowerSYSTEM Center PSC 2020 Update 29, PSC 2024 Update 2, and PSC 2026 GA Hotfix.
    MitigationFor assistance in upgrading, users should contact a Subnet Solutions System Integration team member or customer support team at (403) 270-8885 or by email at support@subnet.com.mailto:support@subnet.com
    MitigationSubnet Solutions recommends users do the following in order to reduce risk:Monitor user activity records to ensure users are following acceptable usage policies of the application.Restrict access to Notification Settings to trusted Administrators Monitor "Send from Address" in settings and Activity Records.Configure a notification rule that triggers in any bulk account export activity.

    Relevant CWE: CWE-93 Improper Neutralization of CRLF Sequences ('CRLF Injection')

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.1
    5.5
    MEDIUM
    CVSS:3.1/AV:A/AC:L/PR:L/UI:N/S:U/C:L/I:L/A:L








    Acknowledgments

    Kelly Stich of Subnet Solutions Inc reported these vulnerabilities to CISA


    Legal Notice and Terms of Use
    This product is provided subject to this Notification (https://www.cisa.gov/notification) and this Privacy & Use policy (https://www.cisa.gov/privacy-policy).

    Recommended Practices
    CISA recommends users take defensive measures to minimize the risk of exploitation of these vulnerabilities.
    Minimize network exposure for all control system devices and/or systems, ensuring they are not accessible from the Internet.
    Locate control system networks and remote devices behind firewalls and isolating them from business networks.
    When remote access is required, use more secure methods, such as Virtual Private Networks (VPNs), recognizing VPNs may have vulnerabilities and should be updated to the most current version available. Also recognize VPN is only as secure as the connected devices.
    CISA reminds organizations to perform proper impact analysis and risk assessment prior to deploying defensive measures.
    CISA also provides a section for control systems security recommended practices on the ICS webpage on cisa.gov/ics. Several CISA products detailing cyber defense best practices are available for reading and download, including Improving Industrial Control Systems Cybersecurity with Defense-in-Depth Strategies.
    CISA encourages organizations to implement recommended cybersecurity strategies for proactive defense of ICS assets.
    Additional mitigation guidance and recommended practices are publicly available on the ICS webpage at cisa.gov/ics in the technical information paper, ICS-TIP-12-146-01B--Targeted Cyber Intrusion Detection and Mitigation Strategies.
    Organizations observing suspected malicious activity should follow established internal procedures and report findings to CISA for tracking and correlation against other incidents.
    CISA also recommends users take the following measures to protect themselves from social engineering attacks:
    Do not click web links or open attachments in unsolicited email messages.
    Refer to Recognizing and Avoiding Email Scams for more information on avoiding email scams.
    Refer to Avoiding Social Engineering and Phishing Attacks for more information on social engineering attacks.
    No known public exploitation specifically targeting these vulnerabilities has been reported to CISA at this time. These vulnerabilities are not exploitable remotely.

    Revision History

    Initial Release Date: 2026-05-12




    Date
    Revision
    Summary




    2026-05-12
    1
    Initial Publication




    Legal Notice and Terms of Use

    https://www.cisa.gov/news-events/ics-advisories/icsa-26-132-02

    2026-05-12 12:00 UTC
    --- FMail-lnx 2.3.2.6-B20251227
    * Origin: TCOB1 A Mail Only System (2:263/1)
  • From Cisa Advisories@2:263/1 to All on Tue Nov 3 16:33:14 2026
    Subnet Solutions PowerSYSTEM Center

    View CSAF
    Summary
    Successful exploitation of these vulnerabilities could allow an attacker to execute unauthorized SQL commands and gain access to unauthorized resources. The following versions of Subnet Solutions PowerSYSTEM Center are affected:

    PowerSYSTEM Center 2020 <=5.29.x (CVE-2026-63017) PowerSYSTEM Center 2024 >=6.0.x|<=6.2.x (CVE-2026-63017, CVE-2026-63774) PowerSYSTEM Center 2026 >=7.0.x|<=7.1.x (CVE-2026-63017, CVE-2026-63774)





    CVSS
    Vendor
    Equipment




    v3 9
    Subnet Solutions
    PowerSYSTEM Center






    2 Vulnerabilities




    Incorrect Authorization, Improper Neutralization of Special Elements used in an SQL Command ('SQL Injection')




    Background

    Critical Infrastructure Sectors: Critical Manufacturing, Energy Countries/Areas Deployed: Worldwide Company Headquarters Location: Canada


    Vulnerabilities
    Expand All +

    CVE-2026-63017
    Incorrect authorization in PowerSYSTEM Center allows a low-privileged, authenticated user to access resources normally limited to administrators. Read More

    3 Affected Products

    Subnet Solutions PowerSYSTEM Center 2024 >=6.0.x|<=6.2.x

    Product Status: known_affected

    Remediations

    MitigationFor users who are currently using PowerSYSTEM Center 2024, Subnet Solutions recommends users upgrade to PowerSYSTEM Center 2026 Update 1.1. For assistance in upgrading, users should contact the Subnet Solutions System Integration team or customer support team at (403) 270-8885 or by email at support@subnet.com. If unable to update to the latest version, Subnet Solutions recommends users monitor user activity records to ensure users are following acceptable usage policies of the application. Subnet Solutions also recommends disabling PowerSYSTEM Center Client Access Server users' ability to access the browser's F12 Developer Tools.


    Subnet Solutions PowerSYSTEM Center 2020 <=5.29.x

    Product Status: known_affected

    Remediations

    MitigationSubnet Solutions recommends users update to PowerSYSTEM Center 2020 Update 30. For assistance in upgrading, users should contact the Subnet Solutions System Integration team or customer support team at (403) 270-8885 or by email at support@subnet.com. If unable to update to the latest version, Subnet Solutions recommends users monitor user activity records to ensure users are following acceptable usage policies of the application. Subnet Solutions also recommends disabling PowerSYSTEM Center Client Access Server users' ability to access the browser's F12 Developer Tools.


    Subnet Solutions PowerSYSTEM Center 2026 >=7.0.x|<=7.1.x

    Product Status: known_affected

    Remediations

    MitigationSubnet Solutions recommends users update to PowerSYSTEM Center 2026 Update 1.1. For assistance in upgrading, users should contact the Subnet Solutions System Integration team or customer support team at (403) 270-8885 or by email at support@subnet.com. If unable to update to the latest version, Subnet Solutions recommends users monitor user activity records to ensure users are following acceptable usage policies of the application. Subnet Solutions also recommends disabling PowerSYSTEM Center Client Access Server users' ability to access the browser's F12 Developer Tools.


    Additional Metrics
    Relevant CWE: CWE-863 Incorrect Authorization




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.1
    9
    CRITICAL
    CVSS:3.1/AV:A/AC:L/PR:L/UI:N/S:C/C:H/I:H/A:H


    4.0
    9.4
    CRITICAL
    CVSS:4.0/AV:A/AC:L/AT:N/PR:L/UI:N/VC:H/VI:H/VA:H/SC:H/SI:H/SA:H





    View CVE Details



    CVE-2026-63774
    Insufficient input validation in the PowerSYSTEM Center report designer allows an authenticated user to execute unauthorized SQL commands. Read More

    5 Affected Products

    Subnet Solutions PowerSYSTEM Center 2024 >=6.0.x|<=6.2.x

    Product Status: known_affected

    Remediations

    MitigationFor users who are currently using PowerSYSTEM Center 2024, Subnet Solutions recommends users upgrade to PowerSYSTEM Center 2026 Update 1.1. For assistance in upgrading, users should contact the Subnet Solutions System Integration team or customer support team at (403) 270-8885 or by email at support@subnet.com. If unable to update to the latest version, Subnet Solutions recommends users disable user access to the report designer.


    Subnet Solutions PowerSYSTEM Center 2020 <=5.29.x

    Product Status: known_affected

    Remediations

    Subnet Solutions PowerSYSTEM Center 2026 >=7.0.x|<=7.1.x

    Product Status: known_affected

    Remediations

    MitigationSubnet Solutions recommends users update to PowerSYSTEM Center 2026 Update 1.1. For assistance in upgrading, users should contact the Subnet Solutions System Integration team or customer support team at (403) 270-8885 or by email at support@subnet.com. If unable to update to the latest version, Subnet Solutions recommends users disable user access to the report designer.


    Subnet Solutions PowerSYSTEM Center 2024 >=6.0.x|<=6.2.x

    Product Status: known_affected

    Remediations

    MitigationFor users who are currently using PowerSYSTEM Center 2024, Subnet Solutions recommends users upgrade to PowerSYSTEM Center 2026 Update 1.1. For assistance in upgrading, users should contact the Subnet Solutions System Integration team or customer support team at (403) 270-8885 or by email at support@subnet.com. If unable to update to the latest version, Subnet Solutions recommends users disable user access to the report designer.


    Subnet Solutions PowerSYSTEM Center 2026 >=7.0.x|<=7.1.x

    Product Status: known_affected

    Remediations

    MitigationSubnet Solutions recommends users update to PowerSYSTEM Center 2026 Update 1.1. For assistance in upgrading, users should contact the Subnet Solutions System Integration team or customer support team at (403) 270-8885 or by email at support@subnet.com. If unable to update to the latest version, Subnet Solutions recommends users disable user access to the report designer.


    Additional Metrics
    Relevant CWE: CWE-89 Improper Neutralization of Special Elements used in an SQL Command ('SQL Injection')




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.1
    9
    CRITICAL
    CVSS:3.1/AV:A/AC:L/PR:L/UI:N/S:C/C:H/I:H/A:H


    4.0
    9.4
    CRITICAL
    CVSS:4.0/AV:A/AC:L/AT:N/PR:L/UI:N/VC:H/VI:H/VA:H/SC:H/SI:H/SA:H





    View CVE Details



    Acknowledgments

    Chinmay Patel of Digital Boundary Group reported these vulnerabilities to CISA. Subnet Solutions reported these vulnerabilities to CISA.


    Recommended Practices
    CISA recommends users take defensive measures to minimize the risk of exploitation of these vulnerabilities.

    Minimize network exposure for all control system devices and/or systems, ensuring they are not accessible from the internet. Locate control system networks and remote devices behind firewalls and isolating them from business networks. When remote access is required, use more secure methods, such as Virtual Private Networks (VPNs), recognizing VPNs may have vulnerabilities and should be updated to the most current version available. Also recognize VPN is only as secure as the connected devices.

    CISA reminds organizations to perform proper impact analysis and risk assessment prior to deploying defensive measures. CISA also provides a section for control systems security recommended practices
    on the ICS webpage on cisa.gov/ics. Several CISA products detailing cyber defense best practices are available for reading and download, including Improving Industrial Control Systems Cybersecurity with Defense-in-Depth Strategies.
    CISA encourages organizations to implement recommended cybersecurity strategies for proactive defense of ICS assets. Additional mitigation guidance and recommended practices are publicly available on the ICS webpage at cisa.gov/ics in the technical information paper, ICS-TIP-12-146-01B--Targeted Cyber Intrusion Detection and Mitigation
    Strategies.
    Organizations observing suspected malicious activity should follow established internal procedures and report findings to CISA for tracking and correlation against other incidents.
    CISA also recommends users take the following measures to protect themselves from social engineering attacks:

    Do not click web links or open attachments in unsolicited email messages. Refer to Recognizing and Avoiding Email Scams for more information on avoiding email scams.
    Refer to Avoiding Social Engineering and Phishing Attacks for more information on social engineering attacks.

    No known public exploitation specifically targeting these vulnerabilities has been reported to CISA at this time. These vulnerabilities are not exploitable remotely.

    Revision History

    Initial Release Date: 2026-11-03




    Date
    Revision
    Summary




    2026-11-03
    1
    Initial Publication




    Legal Notice and Terms of Use

    https://www.cisa.gov/news-events/ics-advisories/icsa-26-307-01

    2026-11-03 12:00 UTC

    --- BBBS/LiR v4.10 Toy-7