    ABB B&R Automation Studio

    View CSAF
    Summary
    ABB became aware of vulnerability in the product versions listed as affected in the advisory. An update is available that resolves a vulnerability. Successful exploitation of this vulnerability may enable an attacker to masquerade as a trusted party when B&R Automation Studio establishes a connection with a server via the ANSL over TLS or OPC-UA protocol.
    The following versions of ABB B&R Automation Studio are affected:

    Automation Studio <6.5, 6.5 (CVE-2025-11043)





    CVSS
    Vendor
    Equipment
    Vulnerabilities




    v3 7.4
    ABB
    ABB B&R Automation Studio
    Improper Certificate Validation




    Background

    Critical Infrastructure Sectors: Critical Manufacturing
    Countries/Areas Deployed: Worldwide
    Company Headquarters Location: Switzerland


    Vulnerabilities

    Expand All +

    CVE-2025-11043

    An Improper Certificate Validation vulnerability in the OPC-UA client and ANSL over TLS client used in Automation Studio versions before 6.5 could allow an unauthenticated attacker on the network to position themselves to intercept and interfere with data exchanges.
    View CVE Details

    Affected Products
    ABB B&R Automation Studio

    Vendor:ABB
    Product Version:ABB Automation Studio <6.5
    Product Status:fixed, known_affected


    Remediations
    Vendor fixThe problem is corrected in the following product versions: B&R Automation Studio version 6.5 B&R recommends that customers apply the update at earliest convenience. The process to install updates is described in the user manual. The step to identify the installed product version is de-scribed in the user manual.
    MitigationTo exploit this vulnerability, an attacker would need to intercept and redirect the communication between B&R Automation Studio and the target server, as well as present manipulated certificates that pass validation checks. B&R recommends operating B&R Automation Studio within Level 2 of the ABB ICS Cyber Security Reference Architecture when connecting to Level 1 devices via ANSL over TLS or OPC-UA. Operating in this trusted environment reduces the risk of successful exploitation drastically. Refer to section ?General security recommendations? for further advise on how to keep your system secure.

    Relevant CWE: CWE-295 Improper Certificate Validation

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.1
    7.4
    HIGH
    CVSS:3.1/AV:N/AC:H/PR:N/UI:N/S:U/C:H/I:H/A:N/RL:O/RC:C








    Acknowledgments

    ABB PSIRT reported this vulnerability to CISA.


    Notice
    The information in this document is subject to change without notice, and should not be construed as a commitment by B&R. B&R provides no warranty, express or implied, including warranties of merchantability and fitness for a particular purpose, for the information contained in this document, and assumes no responsibility for any errors that may appear in this document. In no event shall B&R or any of its suppliers be liable for direct, indirect, special, incidental or conse-quential damages of any nature or kind arising from the use of this document, or from the use of any hardware or software described in this document, even if B&R or its suppliers have been advised of the possibility of such damages. This document and parts hereof must not be reproduced or copied without written permission from B&R, and the contents hereof must not be imparted to a third party nor used for any unauthorized purpose. All rights to registrations and trademarks reside with their respective owners.

    Frequently Asked Questions
    What causes the vulnerability? - The vulnerability is caused by insufficient validation mechanisms for server certificates in the ANSL over TLS and OPC-UA client implementations. What is B&R Automation Studio? - B&R Automation Studio is an environment for developing and executing automation solutions, ranging from control and motion technology to HMI, operation, and integrated safety technology. What might an attacker use the vulnerability to do? - An attacker who successfully exploited this vulnerability could spoof a trusted server, potentially leading to the disclosure of confidential information or the alteration of data during transit. How could an attacker exploit the vulnerability? - An attacker could attempt to exploit this vulnerability by generating a maliciously crafted server certificate and manipulating network routing or name resolution to redirect traffic through a compromised node under their control. This would require that the attacker has access to the system network, by connecting to the network either directly or through a wrongly configured or penetrated firewall, or that he installs malicious software on a system node or other-wise infects the network with malicious software. Recommended practices help mitigate such attacks, see section Miti-gating Factors above. Could the vulnerability be exploited remotely? - Yes, an attacker who has network access to an affected system node could exploit this vulnerability. Recommended practices include that process control systems are physically protected, have no direct connections to the Internet, and are separated from other networks by means of a firewall system that has a minimal number of ports exposed. What does the update do? - The update removes the vulnerability by modifying the way that the ANSL and OPC-UA clients are validating server certificates. When this security advisory was issued, had this vulnerability been publicly disclosed? - No, B&R discovered this vulnerability as a part of its own security analysis. When this security advisory was issued, had B&R received any reports that this vulnerability was being exploited? - No, B&R had not received any information indicating that this vulnerability had been exploited when this security advisory was originally issued

    Legal Notice and Terms of Use
    This product is provided subject to this Notification (https://www.cisa.gov/notification) and this Privacy & Use policy (https://www.cisa.gov/privacy-policy).

    Recommended Practices
    CISA recommends users take defensive measures to minimize the exploitation risk of these vulnerabilities.
    Minimize network exposure for all control system devices and/or systems, and ensure they are not accessible from the internet.
    Locate control system networks and remote devices behind firewalls and isolate them from business networks.
    When remote access is required, use more secure methods, such as Virtual Private Networks (VPNs), recognizing VPNs may have vulnerabilities and should be updated to the most recent version available. Also recognize VPN is only as secure as its connected devices.
    CISA reminds organizations to perform proper impact analysis and risk assessment prior to deploying defensive measures.
    CISA also provides a section for control systems security recommended practices on the ICS webpage on cisa.gov. Several CISA products detailing cyber defense best practices are available for reading and download, including Improving Industrial Control Systems Cybersecurity with Defense-in-Depth Strategies.
    CISA encourages organizations to implement recommended cybersecurity strategies for proactive defense of ICS assets. Additional mitigation guidance and recommended practices are publicly available on the ICS webpage at cisa.gov in the technical information paper, ICS-TIP-12-146-01B--Targeted Cyber Intrusion Detection and Mitigation Strategies.
    Organizations observing suspected malicious activity should follow established internal procedures and report findings to CISA for tracking and correlation against other incidents.

    Advisory Conversion Disclaimer
    This ICSA is a verbatim republication of ABB PSIRT SA25P004 from a direct conversion of the vendor's Common Security Advisory Framework (CSAF) advisory. This is republished to CISA's website as a means of increasing visibility and is provided "as-is" for informational purposes only. CISA is not responsible for the editorial or technical accuracy of republished advisories and provides no warranties of any kind regarding any information contained within this advisory. Further, CISA does not endorse any commercial product or service. Please contact ABB PSIRT directly for any questions regarding this advisory.
    Revision History

    Initial Release Date: 2026-01-19




    Date
    Revision
    Summary




    2026-01-19
    1
    Initial Version


    2026-05-05
    2
    Initial CISA Republication of ABB PSIRT SA25P004 advisory




    Legal Notice and Terms of Use

    https://www.cisa.gov/news-events/ics-advisories/icsa-26-125-04

    2026-05-05 12:00 UTC
    --- FMail-lnx 2.3.2.6-B20251227
    * Origin: TCOB1 A Mail Only System (2:263/1)
  • From CISA Advisories@2:263/1 to All on Thu May 21 18:11:08 2026
    ABB B&R Automation Studio

    View CSAF
    Summary
    ABB became aware of vulnerability in the product versions listed as affected in the advisory. An update is available that replaces an outdated third-party component. Although no successful exploitation was observed during testing of the affected B&R products, the identified vulnerabilities could present potential attack vectors that might enable unauthorized access, data exposure, or remote code execution.
    The following versions of ABB B&R Automation Studio are affected:

    B&R Automation Studio <6.5, 6.5 (CVE-2025-6965, CVE-2025-3277, CVE-2023-7104, CVE-2022-35737, CVE-2020-15358, CVE-2020-13632, CVE-2020-13631, CVE-2020-13630, CVE-2020-13435, CVE-2020-13434, CVE-2020-11656, CVE-2020-11655, CVE-2019-19646, CVE-2019-19645, CVE-2019-8457, CVE-2018-20506, CVE-2018-20505, CVE-2018-20346, CVE-2018-8740, CVE-2017-10989, CVE-2016-6153, CVE-2015-6607, CVE-2015-5895, CVE-2015-3717, CVE-2015-3416)





    CVSS
    Vendor
    Equipment
    Vulnerabilities




    v3 9.8
    ABB
    ABB B&R Automation Studio
    Numeric Truncation Error, Heap-based Buffer Overflow, Improper Restriction of Operations within the Bounds of a Memory Buffer, Out-of-bounds Write, NULL Pointer Dereference, Incorrect User Management, Use After Free, Integer Overflow or Wraparound, Improper Check for Unusual or Exceptional Conditions, Uncontrolled Recursion, Out-of-bounds Read, Improper Input Validation, Exposure of Sensitive Information to an Unauthorized Actor, Buffer Copy without Checking Size of Input ('Classic Buffer Overflow')




    Background

    Critical Infrastructure Sectors: Energy
    Countries/Areas Deployed: Worldwide
    Company Headquarters Location: Switzerland


    Vulnerabilities

    Expand All +

    CVE-2025-6965

    There exists a vulnerability in SQLite versions before 3.50.2 where the number of aggregate terms could exceed the number of columns available. This could lead to a memory corruption issue.
    View CVE Details

    Affected Products
    ABB B&R Automation Studio

    Vendor:ABB
    Product Version:ABB B&R Automation Studio <6.5
    Product Status:fixed, known_affected


    Remediations
    Vendor fixThe problem is corrected in the following product versions: B&R Automation Studio 6.5 B&R recommends that customers apply the update at earliest convenience. The process to install updates is described in the user manual. The step to identify the installed product version is described in the user manual.
    MitigationRefer to section ?General security recommendations? for advice on how to keep your system secure.

    Relevant CWE: CWE-197 Numeric Truncation Error

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.1
    9.8
    CRITICAL
    CVSS:3.1/AV:N/AC:L/PR:N/UI:N/S:U/C:H/I:H/A:H/E:P/RL:O/RC:C







    CVE-2025-3277

    An integer overflow vulnerability exists in SQLite's concat_ws() function that can lead to a massive heap buffer overflow. When triggered, the integer overflow results in a truncated size value being used for buffer allocation, while the original untruncated size is used for writing the resulting string, causing a heap buffer overflow of approximately 4GB.
    View CVE Details

    Affected Products
    ABB B&R Automation Studio

    Vendor:ABB
    Product Version:ABB B&R Automation Studio <6.5
    Product Status:fixed, known_affected


    Remediations
    Vendor fixThe problem is corrected in the following product versions: B&R Automation Studio 6.5 B&R recommends that customers apply the update at earliest convenience. The process to install updates is described in the user manual. The step to identify the installed product version is described in the user manual.
    MitigationRefer to section ?General security recommendations? for advice on how to keep your system secure.

    Relevant CWE: CWE-122 Heap-based Buffer Overflow

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.1
    9.8
    CRITICAL
    CVSS:3.1/AV:N/AC:L/PR:N/UI:N/S:U/C:H/I:H/A:H/E:P/RL:O/RC:C







    CVE-2023-7104

    A vulnerability was found in SQLite SQLite3 up to 3.43.0 and classified as critical. This issue affects the function sessionReadRecord of the file ext/session/sqlite3session.c of the component make alltest Handler. The manipulation leads to heap-based buffer overflow.
    View CVE Details

    Affected Products
    ABB B&R Automation Studio

    Vendor:ABB
    Product Version:ABB B&R Automation Studio <6.5
    Product Status:fixed, known_affected


    Remediations
    Vendor fixThe problem is corrected in the following product versions: B&R Automation Studio 6.5 B&R recommends that customers apply the update at earliest convenience. The process to install updates is described in the user manual. The step to identify the installed product version is described in the user manual.
    MitigationRefer to section ?General security recommendations? for advice on how to keep your system secure.

    Relevant CWE: CWE-122 Heap-based Buffer Overflow

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.1
    7.3
    HIGH
    CVSS:3.1/AV:N/AC:L/PR:N/UI:N/S:U/C:L/I:L/A:L/E:P/RL:O/RC:C







    CVE-2022-35737

    SQLite 1.0.12 through 3.39.x before 3.39.2 sometimes allows an array-bounds overflow if billions of bytes are used in a string argument to a C API.
    View CVE Details

    Affected Products
    ABB B&R Automation Studio

    Vendor:ABB
    Product Version:ABB B&R Automation Studio <6.5
    Product Status:fixed, known_affected


    Remediations
    Vendor fixThe problem is corrected in the following product versions: B&R Automation Studio 6.5 B&R recommends that customers apply the update at earliest convenience. The process to install updates is described in the user manual. The step to identify the installed product version is described in the user manual.
    MitigationRefer to section ?General security recommendations? for advice on how to keep your system secure.

    Relevant CWE: CWE-119 Improper Restriction of Operations within the Bounds of a Memory Buffer

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.1
    7.5
    HIGH
    CVSS:3.1/AV:N/AC:L/PR:N/UI:N/S:U/C:N/I:N/A:H/E:P/RL:O/RC:C







    CVE-2020-15358

    In SQLite before 3.32.3, select.c mishandles query-flattener optimization, leading to a multiSelectOrderBy heap overflow because of misuse of transitive properties for constant propagation.
    View CVE Details

    Affected Products
    ABB B&R Automation Studio

    Vendor:ABB
    Product Version:ABB B&R Automation Studio <6.5
    Product Status:fixed, known_affected


    Remediations
    Vendor fixThe problem is corrected in the following product versions: B&R Automation Studio 6.5 B&R recommends that customers apply the update at earliest convenience. The process to install updates is described in the user manual. The step to identify the installed product version is described in the user manual.
    MitigationRefer to section ?General security recommendations? for advice on how to keep your system secure.

    Relevant CWE: CWE-787 Out-of-bounds Write

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.1
    5.5
    MEDIUM
    CVSS:3.1/AV:L/AC:L/PR:L/UI:N/S:U/C:N/I:N/A:H/E:P/RL:O/RC:C







    CVE-2020-13632

    There exists a vulnerability in SQLite versions before 3.50.2 where the number of aggregate terms could exceed the number of columns available. This could lead to a memory corruption issue.
    View CVE Details

    Affected Products
    ABB B&R Automation Studio

    Vendor:ABB
    Product Version:ABB B&R Automation Studio <6.5
    Product Status:fixed, known_affected


    Remediations
    Vendor fixThe problem is corrected in the following product versions: B&R Automation Studio 6.5 B&R recommends that customers apply the update at earliest convenience. The process to install updates is described in the user manual. The step to identify the installed product version is described in the user manual.
    MitigationRefer to section ?General security recommendations? for advice on how to keep your system secure.

    Relevant CWE: CWE-476 NULL Pointer Dereference

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.0
    5.5
    MEDIUM
    CVSS:3.0/AV:L/AC:L/PR:L/UI:N/S:U/C:N/I:N/A:H/E:P/RL:O/RC:C







    CVE-2020-13631

    SQLite before 3.32.0 allows a virtual table to be renamed to the name of one of its shadow tables, related to alter.c and build.c.
    View CVE Details

    Affected Products
    ABB B&R Automation Studio

    Vendor:ABB
    Product Version:ABB B&R Automation Studio <6.5
    Product Status:fixed, known_affected


    Remediations
    Vendor fixThe problem is corrected in the following product versions: B&R Automation Studio 6.5 B&R recommends that customers apply the update at earliest convenience. The process to install updates is described in the user manual. The step to identify the installed product version is described in the user manual.
    MitigationRefer to section ?General security recommendations? for advice on how to keep your system secure.

    Relevant CWE: CWE-286 Incorrect User Management

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.1
    5.5
    MEDIUM
    CVSS:3.1/AV:L/AC:L/PR:L/UI:N/S:U/C:N/I:H/A:N/E:P/RL:O/RC:C







    CVE-2020-13630

    ext/fts3/fts3.c in SQLite before 3.32.0 has a use-after-free in fts3EvalNextRow, related to the snippet feature.
    View CVE Details

    Affected Products
    ABB B&R Automation Studio

    Vendor:ABB
    Product Version:ABB B&R Automation Studio <6.5
    Product Status:fixed, known_affected


    Remediations
    Vendor fixThe problem is corrected in the following product versions: B&R Automation Studio 6.5 B&R recommends that customers apply the update at earliest convenience. The process to install updates is described in the user manual. The step to identify the installed product version is described in the user manual.
    MitigationRefer to section ?General security recommendations? for advice on how to keep your system secure.

    Relevant CWE: CWE-416 Use After Free

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.0
    7
    HIGH
    CVSS:3.0/AV:L/AC:H/PR:L/UI:N/S:U/C:H/I:H/A:H/E:P/RL:O/RC:C







    CVE-2020-13435

    SQLite through 3.32.0 has a segmentation fault in sqlite3ExprCodeTarget in expr.c.
    View CVE Details

    Affected Products
    ABB B&R Automation Studio

    Vendor:ABB
    Product Version:ABB B&R Automation Studio <6.5
    Product Status:fixed, known_affected


    Remediations
    Vendor fixThe problem is corrected in the following product versions: B&R Automation Studio 6.5 B&R recommends that customers apply the update at earliest convenience. The process to install updates is described in the user manual. The step to identify the installed product version is described in the user manual.
    MitigationRefer to section ?General security recommendations? for advice on how to keep your system secure.

    Relevant CWE: CWE-476 NULL Pointer Dereference

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.1
    7.5
    HIGH
    CVSS:3.1/AV:N/AC:L/PR:N/UI:N/S:U/C:N/I:N/A:H/E:P/RL:O/RC:C







    CVE-2020-13434

    SQLite through 3.32.0 has an integer overflow in sqlite3_str_vappendf in printf.c.
    View CVE Details

    Affected Products
    ABB B&R Automation Studio

    Vendor:ABB
    Product Version:ABB B&R Automation Studio <6.5
    Product Status:fixed, known_affected


    Remediations
    Vendor fixThe problem is corrected in the following product versions: B&R Automation Studio 6.5 B&R recommends that customers apply the update at earliest convenience. The process to install updates is described in the user manual. The step to identify the installed product version is described in the user manual.
    MitigationRefer to section ?General security recommendations? for advice on how to keep your system secure.

    Relevant CWE: CWE-190 Integer Overflow or Wraparound

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.0
    5.5
    MEDIUM
    CVSS:3.0/AV:L/AC:L/PR:L/UI:N/S:U/C:N/I:N/A:H/E:P/RL:O/RC:C







    CVE-2020-11656

    In SQLite through 3.31.1, the ALTER TABLE implementation has a use-after-free, as demonstrated by an ORDER BY clause that belongs to a compound SELECT statement.
    View CVE Details

    Affected Products
    ABB B&R Automation Studio

    Vendor:ABB
    Product Version:ABB B&R Automation Studio <6.5
    Product Status:fixed, known_affected


    Remediations
    Vendor fixThe problem is corrected in the following product versions: B&R Automation Studio 6.5 B&R recommends that customers apply the update at earliest convenience. The process to install updates is described in the user manual. The step to identify the installed product version is described in the user manual.
    MitigationRefer to section ?General security recommendations? for advice on how to keep your system secure.

    Relevant CWE: CWE-416 Use After Free

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.1
    7.5
    HIGH
    CVSS:3.1/AV:N/AC:L/PR:N/UI:N/S:U/C:N/I:N/A:H/E:P/RL:O/RC:C







    CVE-2020-11655

    SQLite through 3.31.1 allows attackers to cause a denial of service (segmentation fault) via a malformed window-function query because the AggInfo object's initialization is mishandled.
    View CVE Details

    Affected Products
    ABB B&R Automation Studio

    Vendor:ABB
    Product Version:ABB B&R Automation Studio <6.5
    Product Status:fixed, known_affected


    Remediations
    Vendor fixThe problem is corrected in the following product versions: B&R Automation Studio 6.5 B&R recommends that customers apply the update at earliest convenience. The process to install updates is described in the user manual. The step to identify the installed product version is described in the user manual.
    MitigationRefer to section ?General security recommendations? for advice on how to keep your system secure.

    Relevant CWE: CWE-754 Improper Check for Unusual or Exceptional Conditions

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.1
    7.5
    HIGH
    CVSS:3.1/AV:N/AC:L/PR:N/UI:N/S:U/C:N/I:N/A:H/E:P/RL:O/RC:C







    CVE-2019-19646

    pragma.c in SQLite through 3.30.1 mishandles NOT NULL in an integrity_check PRAGMA command in certain cases of generated columns.
    View CVE Details

    Affected Products
    ABB B&R Automation Studio

    Vendor:ABB
    Product Version:ABB B&R Automation Studio <6.5
    Product Status:fixed, known_affected


    Remediations
    Vendor fixThe problem is corrected in the following product versions: B&R Automation Studio 6.5 B&R recommends that customers apply the update at earliest convenience. The process to install updates is described in the user manual. The step to identify the installed product version is described in the user manual.
    MitigationRefer to section ?General security recommendations? for advice on how to keep your system secure.

    Relevant CWE: CWE-754 Improper Check for Unusual or Exceptional Conditions

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.1
    9.8
    CRITICAL
    CVSS:3.1/AV:N/AC:L/PR:N/UI:N/S:U/C:H/I:H/A:H/E:P/RL:O/RC:C







    CVE-2019-19645

    alter.c in SQLite through 3.30.1 allows attackers to trigger infinite recursion via certain types of self-referential views in conjunction with ALTER TABLE statements.
    View CVE Details

    Affected Products
    ABB B&R Automation Studio

    Vendor:ABB
    Product Version:ABB B&R Automation Studio <6.5
    Product Status:fixed, known_affected


    Remediations
    Vendor fixThe problem is corrected in the following product versions: B&R Automation Studio 6.5 B&R recommends that customers apply the update at earliest convenience. The process to install updates is described in the user manual. The step to identify the installed product version is described in the user manual.
    MitigationRefer to section ?General security recommendations? for advice on how to keep your system secure.

    Relevant CWE: CWE-674 Uncontrolled Recursion

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.1
    5.5
    MEDIUM
    CVSS:3.1/AV:L/AC:L/PR:L/UI:N/S:U/C:N/I:N/A:H/E:P/RL:O/RC:C







    CVE-2019-8457

    SQLite3 from 3.6.0 to and including 3.27.2 is vulnerable to heap out-of-bound read in the rtreenode() function when handling invalid rtree tables.
    View CVE Details

    Affected Products
    ABB B&R Automation Studio

    Vendor:ABB
    Product Version:ABB B&R Automation Studio <6.5
    Product Status:fixed, known_affected


    Remediations
    Vendor fixThe problem is corrected in the following product versions: B&R Automation Studio 6.5 B&R recommends that customers apply the update at earliest convenience. The process to install updates is described in the user manual. The step to identify the installed product version is described in the user manual.
    MitigationRefer to section ?General security recommendations? for advice on how to keep your system secure.

    Relevant CWE: CWE-125 Out-of-bounds Read

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.1
    9.8
    CRITICAL
    CVSS:3.1/AV:N/AC:L/PR:N/UI:N/S:U/C:H/I:H/A:H/E:P/RL:O/RC:C







    CVE-2018-20506

    SQLite before 3.25.3, when the FTS3 extension is enabled, encounters an integer overflow (and resultant buffer overflow) for FTS3 queries in a "merge" operation that occurs after crafted changes to FTS3 shadow tables, allow-ing remote attackers to execute arbitrary code by leveraging the ability to run arbitrary SQL statements (such as in certain WebSQL use cases). This is a different vulnerability than CVE-2018-20346.
    View CVE Details

    Affected Products
    ABB B&R Automation Studio

    Vendor:ABB
    Product Version:ABB B&R Automation Studio <6.5
    Product Status:fixed, known_affected


    Remediations
    Vendor fixThe problem is corrected in the following product versions: B&R Automation Studio 6.5 B&R recommends that customers apply the update at earliest convenience. The process to install updates is described in the user manual. The step to identify the installed product version is described in the user manual.
    MitigationRefer to section ?General security recommendations? for advice on how to keep your system secure.

    Relevant CWE: CWE-190 Integer Overflow or Wraparound

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.0
    8.1
    HIGH
    CVSS:3.0/AV:N/AC:H/PR:N/UI:N/S:U/C:H/I:H/A:H/E:P/RL:O/RC:C







    CVE-2018-20505

    SQLite 3.25.2, when queries are run on a table with a malformed PRIMARY KEY, allows remote attackers to cause a denial of service (application crash) by leveraging the ability to run arbitrary SQL statements (such as in certain WebSQL use cases).
    View CVE Details

    Affected Products
    ABB B&R Automation Studio

    Vendor:ABB
    Product Version:ABB B&R Automation Studio <6.5
    Product Status:fixed, known_affected


    Remediations
    Vendor fixThe problem is corrected in the following product versions: B&R Automation Studio 6.5 B&R recommends that customers apply the update at earliest convenience. The process to install updates is described in the user manual. The step to identify the installed product version is described in the user manual.
    MitigationRefer to section ?General security recommendations? for advice on how to keep your system secure.

    Relevant CWE: CWE-20 Improper Input Validation

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.0
    7.5
    HIGH
    CVSS:3.0/AV:N/AC:L/PR:N/UI:N/S:U/C:N/I:N/A:H/E:P/RL:O/RC:C







    CVE-2018-20346

    SQLite before 3.25.3, when the FTS3 extension is enabled, encounters an integer overflow (and resultant buffer overflow) for FTS3 queries that occur after crafted changes to FTS3 shadow tables, allowing remote attackers to execute arbitrary code by leveraging the ability to run arbitrary SQL statements (such as in certain WebSQL use cases), aka Magellan.
    View CVE Details

    Affected Products
    ABB B&R Automation Studio

    Vendor:ABB
    Product Version:ABB B&R Automation Studio <6.5
    Product Status:fixed, known_affected


    Remediations
    Vendor fixThe problem is corrected in the following product versions: B&R Automation Studio 6.5 B&R recommends that customers apply the update at earliest convenience. The process to install updates is described in the user manual. The step to identify the installed product version is described in the user manual.
    MitigationRefer to section ?General security recommendations? for advice on how to keep your system secure.

    Relevant CWE: CWE-190 Integer Overflow or Wraparound

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.0
    8.1
    HIGH
    CVSS:3.0/AV:N/AC:H/PR:N/UI:N/S:U/C:H/I:H/A:H/E:P/RL:O/RC:C







    CVE-2018-8740

    In SQLite through 3.22.0, databases whose schema is corrupted using a CREATE TABLE AS statement could cause a NULL pointer dereference, related to build.c and prepare.c.
    View CVE Details

    Affected Products
    ABB B&R Automation Studio

    Vendor:ABB
    Product Version:ABB B&R Automation Studio <6.5
    Product Status:fixed, known_affected


    Remediations
    Vendor fixThe problem is corrected in the following product versions: B&R Automation Studio 6.5 B&R recommends that customers apply the update at earliest convenience. The process to install updates is described in the user manual. The step to identify the installed product version is described in the user manual.
    MitigationRefer to section ?General security recommendations? for advice on how to keep your system secure.

    Relevant CWE: CWE-476 NULL Pointer Dereference

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.0
    7.5
    HIGH
    CVSS:3.0/AV:N/AC:L/PR:N/UI:N/S:U/C:N/I:N/A:H/E:P/RL:O/RC:C







    CVE-2017-10989

    The getNodeSize function in ext/rtree/rtree.c in SQLite through 3.19.3, as used in GDAL and other products, mis-handles undersized RTree blobs in a crafted database, leading to a heap-based buffer over-read or possibly un-specified other impact.
    View CVE Details

    Affected Products
    ABB B&R Automation Studio

    Vendor:ABB
    Product Version:ABB B&R Automation Studio <6.5
    Product Status:fixed, known_affected


    Remediations
    Vendor fixThe problem is corrected in the following product versions: B&R Automation Studio 6.5 B&R recommends that customers apply the update at earliest convenience. The process to install updates is described in the user manual. The step to identify the installed product version is described in the user manual.
    MitigationRefer to section ?General security recommendations? for advice on how to keep your system secure.

    Relevant CWE: CWE-125 Out-of-bounds Read

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.0
    9.8
    CRITICAL
    CVSS:3.0/AV:N/AC:L/PR:N/UI:N/S:U/C:H/I:H/A:H/E:P/RL:O/RC:C







    CVE-2016-6153

    There exists a vulnerability in SQLite versions before 3.50.2 where the number of aggregate terms could exceed the number of columns available. This could lead to a memory corruption issue.
    View CVE Details

    Affected Products
    ABB B&R Automation Studio

    Vendor:ABB
    Product Version:ABB B&R Automation Studio <6.5
    Product Status:fixed, known_affected


    Remediations
    Vendor fixThe problem is corrected in the following product versions: B&R Automation Studio 6.5 B&R recommends that customers apply the update at earliest convenience. The process to install updates is described in the user manual. The step to identify the installed product version is described in the user manual.
    MitigationRefer to section ?General security recommendations? for advice on how to keep your system secure.

    Relevant CWE: CWE-20 Improper Input Validation

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.0
    5.9
    MEDIUM
    CVSS:3.0/AV:L/AC:L/PR:N/UI:N/S:U/C:L/I:L/A:L/E:P/RL:O/RC:C







    CVE-2015-6607

    SQLite before 3.8.9, as used in Android before 5.1.1 LMY48T, allows attackers to gain privileges via a crafted application, aka internal bug 20099586.
    View CVE Details

    Affected Products
    ABB B&R Automation Studio

    Vendor:ABB
    Product Version:ABB B&R Automation Studio <6.5
    Product Status:fixed, known_affected


    Remediations
    Vendor fixThe problem is corrected in the following product versions: B&R Automation Studio 6.5 B&R recommends that customers apply the update at earliest convenience. The process to install updates is described in the user manual. The step to identify the installed product version is described in the user manual.
    MitigationRefer to section ?General security recommendations? for advice on how to keep your system secure.

    Relevant CWE: CWE-286 Incorrect User Management

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.0
    3.7
    LOW
    CVSS:3.0/AV:N/AC:H/PR:N/UI:N/S:U/C:L/I:N/A:N/E:P/RL:O/RC:C







    CVE-2015-5895

    Multiple unspecified vulnerabilities in SQLite before 3.8.10.2, as used in Apple iOS before 9, have unknown im-pact and attack vectors.
    View CVE Details

    Affected Products
    ABB B&R Automation Studio

    Vendor:ABB
    Product Version:ABB B&R Automation Studio <6.5
    Product Status:fixed, known_affected


    Remediations
    Vendor fixThe problem is corrected in the following product versions: B&R Automation Studio 6.5 B&R recommends that customers apply the update at earliest convenience. The process to install updates is described in the user manual. The step to identify the installed product version is described in the user manual.
    MitigationRefer to section ?General security recommendations? for advice on how to keep your system secure.

    Relevant CWE: CWE-200 Exposure of Sensitive Information to an Unauthorized Actor

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.1
    9.8
    CRITICAL
    CVSS:3.1/AV:N/AC:L/PR:N/UI:N/S:U/C:H/I:H/A:H/E:P/RL:O/RC:C







    CVE-2015-3717

    Multiple buffer overflows in the printf functionality in SQLite, as used in Apple iOS before 8.4 and OS X before 10.10.4, allow remote attackers to execute arbitrary code or cause a denial of service (application crash) via un-specified vectors.
    View CVE Details

    Affected Products
    ABB B&R Automation Studio

    Vendor:ABB
    Product Version:ABB B&R Automation Studio <6.5
    Product Status:fixed, known_affected


    Remediations
    Vendor fixThe problem is corrected in the following product versions: B&R Automation Studio 6.5 B&R recommends that customers apply the update at earliest convenience. The process to install updates is described in the user manual. The step to identify the installed product version is described in the user manual.
    MitigationRefer to section ?General security recommendations? for advice on how to keep your system secure.

    Relevant CWE: CWE-120 Buffer Copy without Checking Size of Input ('Classic Buffer Overflow')

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.0
    7.5
    HIGH
    CVSS:3.0/AV:N/AC:L/PR:N/UI:N/S:U/C:N/I:N/A:H/E:P/RL:O/RC:C







    CVE-2015-3416

    The sqlite3VXPrintf function in printf.c in SQLite before 3.8.9 does not properly handle precision and width values during floating-point conversions, which allows context-dependent attackers to cause a denial of service (integer overflow and stack-based buffer overflow) or possibly have unspecified other impact via large integers in a crafted printf function call in a SELECT statement.
    View CVE Details

    Affected Products
    ABB B&R Automation Studio

    Vendor:ABB
    Product Version:ABB B&R Automation Studio <6.5
    Product Status:fixed, known_affected


    Remediations
    Vendor fixThe problem is corrected in the following product versions: B&R Automation Studio 6.5 B&R recommends that customers apply the update at earliest convenience. The process to install updates is described in the user manual. The step to identify the installed product version is described in the user manual.
    MitigationRefer to section ?General security recommendations? for advice on how to keep your system secure.

    Relevant CWE: CWE-190 Integer Overflow or Wraparound

    Metrics




    CVSS Version
    Base Score
    Base Severity
    Vector String




    3.0
    7.8
    HIGH
    CVSS:3.0/AV:L/AC:L/PR:L/UI:N/S:U/C:H/I:H/A:H/E:P/RL:O/RC:C








    Acknowledgments

    ABB PSIRT reported these vulnerabilities to CISA.


    Notice
    The information in this document is subject to change without notice, and should not be construed as a commitment by B&R. B&R provides no warranty, express or implied, including warranties of merchantability and fitness for a particular purpose, for the information contained in this document, and assumes no responsibility for any errors that may appear in this document. In no event shall B&R or any of its suppliers be liable for direct, indirect, special, incidental or consequential damages of any nature or kind arising from the use of this document, or from the use of any hardware or software described in this document, even if B&R or its suppliers have been advised of the possibility of such damages. This document and parts hereof must not be reproduced or copied without written permission from B&R, and the contents hereof must not be imparted to a third party nor used for any unauthorized purpose. All rights to registrations and trademarks reside with their respective owners.

    Legal Notice and Terms of Use
    This product is provided subject to this Notification (https://www.cisa.gov/notification) and this Privacy & Use policy (https://www.cisa.gov/privacy-policy).

    Recommended Practices
    CISA recommends users take defensive measures to minimize the exploitation risk of this vulnerability.
    Minimize network exposure for all control system devices and/or systems, and ensure they are not accessible from the internet.
    Locate control system networks and remote devices behind firewalls and isolate them from business networks.
    When remote access is required, use more secure methods, such as Virtual Private Networks (VPNs), recognizing VPNs may have vulnerabilities and should be updated to the most recent version available. Also recognize VPN is only as secure as its connected devices.
    CISA reminds organizations to perform proper impact analysis and risk assessment prior to deploying defensive measures.
    CISA also provides a section for control systems security recommended practices on the ICS webpage on cisa.gov. Several CISA products detailing cyber defense best practices are available for reading and download, including Improving Industrial Control Systems Cybersecurity with Defense-in-Depth Strategies.
    CISA encourages organizations to implement recommended cybersecurity strategies for proactive defense of ICS assets. Additional mitigation guidance and recommended practices are publicly available on the ICS webpage at cisa.gov in the technical information paper, ICS-TIP-12-146-01B--Targeted Cyber Intrusion Detection and Mitigation Strategies.
    Organizations observing suspected malicious activity should follow established internal procedures and report findings to CISA for tracking and correlation against other incidents.

    Advisory Conversion Disclaimer
    This ICSA is a verbatim republication of ABB PSIRT SA25P007 from a direct conversion of the vendor's Common Security Advisory Framework (CSAF) advisory. This is republished to CISA's website as a means of increasing visibility and is provided "as-is" for informational purposes only. CISA is not responsible for the editorial or technical accuracy of republished advisories and provides no warranties of any kind regarding any information contained within this advisory. Further, CISA does not endorse any commercial product or service. Please contact ABB PSIRT directly for any questions regarding this advisory.
    Revision History

    Initial Release Date: 2026-02-18




    Date
    Revision
    Summary




    2026-02-18
    1
    Initial version.


    2026-05-21
    2
    Initial CISA Republication of ABB PSIRT SA25P007 advisory