• Re: Sticking Thermostatic Radiator Valves

    From Handsome Jack@jack@handsome.com to uk.d-i-y on Thu Jan 1 08:39:39 2026
    From Newsgroup: uk.d-i-y

    On Tue, 30 Dec 2025 21:58:52 -0000 (UTC), Brian wrote:

    Tom <ce0537a20a14ccd3ebf37f2484174906@example.com> wrote:
    Just been grappling with this problem. We have a red hot radrCO and lrCOve >> not been able to release the valve following plumbersrCO advice on You
    Tube vids. Been hesitant to touch the brass nut but will give it a go
    as it seems to have worked for others. Thanks Andy Bennet for the
    advice.


    When Thermostatic Rad Valves stick, they tend to stick closed. The usual rCytappingrCO trick is to open them.

    If the rad is hot, the valve is open.

    Either the head isnrCOt fitted correctly or the head is damaged. The temperature sensitive bit is in the head, it presses on the pin.

    If the pin is rCyuprCO the valve is open. Use something metal to push it down.
    If it moves, it isnrCOt stuck. IrCOve never seen one stick open. A rCytaprCO on
    the side of the body normally frees a stuck closed / down pin. ( Remove
    the head first.)

    One of my TRVs has just developed a drip from the centre pin area - I say developed, really it's a problem we had last winter that I thought I had
    fixed by working the pin up and down and adding WD40. Now it's back and
    quite a lot worse, so I've had to put a bowl under it.

    I don't think I can replace the valve myself as there is no way of
    shutting off the water to the rad without draining the system.
    --- Synchronet 3.21a-Linux NewsLink 1.2
  • From David Wade@dave@is.invalid to uk.d-i-y on Thu Jan 1 11:56:39 2026
    From Newsgroup: uk.d-i-y

    On 01/01/2026 09:39, Handsome Jack wrote:
    On Tue, 30 Dec 2025 21:58:52 -0000 (UTC), Brian wrote:

    Tom <ce0537a20a14ccd3ebf37f2484174906@example.com> wrote:
    Just been grappling with this problem. We have a red hot radrCO and lrCOve >>> not been able to release the valve following plumbersrCO advice on You
    Tube vids. Been hesitant to touch the brass nut but will give it a go
    as it seems to have worked for others. Thanks Andy Bennet for the
    advice.


    When Thermostatic Rad Valves stick, they tend to stick closed. The usual
    rCytappingrCO trick is to open them.

    If the rad is hot, the valve is open.

    Either the head isnrCOt fitted correctly or the head is damaged. The
    temperature sensitive bit is in the head, it presses on the pin.

    If the pin is rCyuprCO the valve is open. Use something metal to push it
    down.
    If it moves, it isnrCOt stuck. IrCOve never seen one stick open. A rCytaprCO on
    the side of the body normally frees a stuck closed / down pin. ( Remove
    the head first.)

    One of my TRVs has just developed a drip from the centre pin area - I say developed, really it's a problem we had last winter that I thought I had fixed by working the pin up and down and adding WD40. Now it's back and
    quite a lot worse, so I've had to put a bowl under it.

    I don't think I can replace the valve myself as there is no way of
    shutting off the water to the rad without draining the system.

    https://www.screwfix.com/p/arctic-hayes-pipe-freezing-kit-300ml/900fj

    perhaps.
    --- Synchronet 3.21a-Linux NewsLink 1.2
  • From Tricky Dicky@tricky.dicky@sky.com to uk.d-i-y on Thu Jan 1 11:22:59 2026
    From Newsgroup: uk.d-i-y

    David Wade <dave@is.invalid> wrote:
    On 01/01/2026 09:39, Handsome Jack wrote:
    On Tue, 30 Dec 2025 21:58:52 -0000 (UTC), Brian wrote:

    Tom <ce0537a20a14ccd3ebf37f2484174906@example.com> wrote:
    Just been grappling with this problem. We have a red hot radrCO and lrCOve >>>> not been able to release the valve following plumbersrCO advice on You >>>> Tube vids. Been hesitant to touch the brass nut but will give it a go
    as it seems to have worked for others. Thanks Andy Bennet for the
    advice.


    When Thermostatic Rad Valves stick, they tend to stick closed. The usual >>> rCytappingrCO trick is to open them.

    If the rad is hot, the valve is open.

    Either the head isnrCOt fitted correctly or the head is damaged. The
    temperature sensitive bit is in the head, it presses on the pin.

    If the pin is rCyuprCO the valve is open. Use something metal to push it >>> down.
    If it moves, it isnrCOt stuck. IrCOve never seen one stick open. A rCytaprCO on
    the side of the body normally frees a stuck closed / down pin. ( Remove
    the head first.)

    One of my TRVs has just developed a drip from the centre pin area - I say
    developed, really it's a problem we had last winter that I thought I had
    fixed by working the pin up and down and adding WD40. Now it's back and
    quite a lot worse, so I've had to put a bowl under it.

    I don't think I can replace the valve myself as there is no way of
    shutting off the water to the rad without draining the system.

    https://www.screwfix.com/p/arctic-hayes-pipe-freezing-kit-300ml/900fj

    perhaps.


    +1

    --- Synchronet 3.21a-Linux NewsLink 1.2
  • From Tricky Dicky@tricky.dicky@sky.com to uk.d-i-y on Thu Jan 1 11:31:28 2026
    From Newsgroup: uk.d-i-y

    Tricky Dicky <tricky.dicky@sky.com> wrote:
    David Wade <dave@is.invalid> wrote:
    On 01/01/2026 09:39, Handsome Jack wrote:
    On Tue, 30 Dec 2025 21:58:52 -0000 (UTC), Brian wrote:

    Tom <ce0537a20a14ccd3ebf37f2484174906@example.com> wrote:
    Just been grappling with this problem. We have a red hot radrCO and lrCOve
    not been able to release the valve following plumbersrCO advice on You >>>>> Tube vids. Been hesitant to touch the brass nut but will give it a go >>>>> as it seems to have worked for others. Thanks Andy Bennet for the
    advice.


    When Thermostatic Rad Valves stick, they tend to stick closed. The usual >>>> rCytappingrCO trick is to open them.

    If the rad is hot, the valve is open.

    Either the head isnrCOt fitted correctly or the head is damaged. The
    temperature sensitive bit is in the head, it presses on the pin.

    If the pin is rCyuprCO the valve is open. Use something metal to push it >>>> down.
    If it moves, it isnrCOt stuck. IrCOve never seen one stick open. A rCytaprCO on
    the side of the body normally frees a stuck closed / down pin. ( Remove >>>> the head first.)

    One of my TRVs has just developed a drip from the centre pin area - I say >>> developed, really it's a problem we had last winter that I thought I had >>> fixed by working the pin up and down and adding WD40. Now it's back and
    quite a lot worse, so I've had to put a bowl under it.

    I don't think I can replace the valve myself as there is no way of
    shutting off the water to the rad without draining the system.

    https://www.screwfix.com/p/arctic-hayes-pipe-freezing-kit-300ml/900fj

    perhaps.


    +1



    Or you can do it without freezing or draining down. I have used the method described in this video twice and no floods.

    https://youtu.be/mjsPZirB9Cg?si=Vyb-uVa4kZ3oglkL

    The guy has produced a couple of videos depending on the type of system ie. Header tank or sealed system. Ours is a sealed system and I think this is
    the correct video.

    Richard

    --- Synchronet 3.21a-Linux NewsLink 1.2
  • From alan_m@junk@admac.myzen.co.uk to uk.d-i-y on Thu Jan 1 11:58:30 2026
    From Newsgroup: uk.d-i-y

    On 01/01/2026 11:22, Tricky Dicky wrote:
    David Wade <dave@is.invalid> wrote:


    https://www.screwfix.com/p/arctic-hayes-pipe-freezing-kit-300ml/900fj

    perhaps.


    +1


    May not work too well when close to a massive amount of water/metal such
    as a radiator. The use always seems to be demonstrated on a length of
    copper with no nearby fittings that act as a heat store (albeit at
    ambient temperature)
    --
    mailto : news {at} admac {dot} myzen {dot} co {dot} uk
    --- Synchronet 3.21a-Linux NewsLink 1.2
  • From The Natural Philosopher@tnp@invalid.invalid to uk.d-i-y on Thu Jan 1 13:24:52 2026
    From Newsgroup: uk.d-i-y

    On 01/01/2026 11:58, alan_m wrote:
    On 01/01/2026 11:22, Tricky Dicky wrote:
    David Wade <dave@is.invalid> wrote:


    https://www.screwfix.com/p/arctic-hayes-pipe-freezing-kit-300ml/900fj

    perhaps.


    +1


    May not work too well when close to a massive amount of water/metal such
    as a radiator. The use always seems to be demonstrated on a length of
    copper with no nearby fittings that act as a heat store (albeit at
    ambient temperature)

    I can assure you that i have had an entire radiator freeze and split...:-)

    Probably climate change. Or Brexit. Or some 'far right' plot.
    --
    rCLit should be clear by now to everyone that activist environmentalism
    (or environmental activism) is becoming a general ideology about humans,
    about their freedom, about the relationship between the individual and
    the state, and about the manipulation of people under the guise of a
    'noble' idea. It is not an honest pursuit of 'sustainable development,'
    a matter of elementary environmental protection, or a search for
    rational mechanisms designed to achieve a healthy environment. Yet
    things do occur that make you shake your head and remind yourself that
    you live neither in Joseph StalinrCOs Communist era, nor in the Orwellian utopia of 1984.rCY

    Vaclav Klaus

    --- Synchronet 3.21a-Linux NewsLink 1.2
  • From alan_m@junk@admac.myzen.co.uk to uk.d-i-y on Thu Jan 1 13:30:16 2026
    From Newsgroup: uk.d-i-y

    On 01/01/2026 13:24, The Natural Philosopher wrote:
    On 01/01/2026 11:58, alan_m wrote:
    On 01/01/2026 11:22, Tricky Dicky wrote:
    David Wade <dave@is.invalid> wrote:


    https://www.screwfix.com/p/arctic-hayes-pipe-freezing-kit-300ml/900fj

    perhaps.


    +1


    May not work too well when close to a massive amount of water/metal
    such as a radiator. The use always seems to be demonstrated on a
    length of copper with no nearby fittings that act as a heat store
    (albeit at ambient temperature)

    I can assure you that i have had an entire radiator freeze and split...:-)

    With a single 300ml can of freezer spray @ -u30 ?
    --
    mailto : news {at} admac {dot} myzen {dot} co {dot} uk
    --- Synchronet 3.21a-Linux NewsLink 1.2
  • From Tim+@timdownieuk@yahoo.co.youkay to uk.d-i-y on Thu Jan 1 14:46:02 2026
    From Newsgroup: uk.d-i-y

    Handsome Jack <jack@handsome.com> wrote:
    On Tue, 30 Dec 2025 21:58:52 -0000 (UTC), Brian wrote:

    Tom <ce0537a20a14ccd3ebf37f2484174906@example.com> wrote:
    Just been grappling with this problem. We have a red hot radrCO and lrCOve >>> not been able to release the valve following plumbersrCO advice on You
    Tube vids. Been hesitant to touch the brass nut but will give it a go
    as it seems to have worked for others. Thanks Andy Bennet for the
    advice.


    When Thermostatic Rad Valves stick, they tend to stick closed. The usual
    rCytappingrCO trick is to open them.

    If the rad is hot, the valve is open.

    Either the head isnrCOt fitted correctly or the head is damaged. The
    temperature sensitive bit is in the head, it presses on the pin.

    If the pin is rCyuprCO the valve is open. Use something metal to push it
    down.
    If it moves, it isnrCOt stuck. IrCOve never seen one stick open. A rCytaprCO on
    the side of the body normally frees a stuck closed / down pin. ( Remove
    the head first.)

    One of my TRVs has just developed a drip from the centre pin area - I say developed, really it's a problem we had last winter that I thought I had fixed by working the pin up and down and adding WD40. Now it's back and quite a lot worse, so I've had to put a bowl under it.

    I don't think I can replace the valve myself as there is no way of
    shutting off the water to the rad without draining the system.


    Rarely necessary to drain a whole system. If itrCOs a sealed system with an expansion vessel and pressure gauge, just depressurise the system, close
    off the lockshield valve and drain the radiator down from the other end
    with something to catch the water. Once the radiator is drained down, very little water will come out of the rest of the pipework. If you can get the same TRV (or at least one with he same fittings and dimensions) you should
    be able to swap the old one out.

    If you have an open vented system, you will need to seal the feed and
    expansion pipes with suitable bungs. Then proceed as above.

    Tim
    --
    Please don't feed the trolls
    --- Synchronet 3.21a-Linux NewsLink 1.2
  • From Tom@ce0537a20a14ccd3ebf37f2484174906@example.com to uk.d-i-y on Thu Jan 1 22:45:02 2026
    From Newsgroup: uk.d-i-y

    UPDATE - Tried Andy BrCOs suggested solution and pleased to say it worked. The half turn on the brass nut released the pin, allowing movement up and down. Re-tightened the nut and the rad seems to be working fine maintaining the set temperature. Thanks Andy.
    --
    For full context, visit https://www.homeownershub.com/uk-diy/sticking-thermostatic-radiator-valves-106238-.htm

    --- Synchronet 3.21a-Linux NewsLink 1.2
  • From newman@aa111@despammed.com to uk.d-i-y on Fri Jan 2 11:41:20 2026
    From Newsgroup: uk.d-i-y

    On 01/01/2026 14:46, Tim+ wrote:
    Handsome Jack <jack@handsome.com> wrote:
    On Tue, 30 Dec 2025 21:58:52 -0000 (UTC), Brian wrote:

    Tom <ce0537a20a14ccd3ebf37f2484174906@example.com> wrote:
    Just been grappling with this problem. We have a red hot radrCO and lrCOve >>>> not been able to release the valve following plumbersrCO advice on You >>>> Tube vids. Been hesitant to touch the brass nut but will give it a go
    as it seems to have worked for others. Thanks Andy Bennet for the
    advice.


    When Thermostatic Rad Valves stick, they tend to stick closed. The usual >>> rCytappingrCO trick is to open them.

    If the rad is hot, the valve is open.

    Either the head isnrCOt fitted correctly or the head is damaged. The
    temperature sensitive bit is in the head, it presses on the pin.

    If the pin is rCyuprCO the valve is open. Use something metal to push it >>> down.
    If it moves, it isnrCOt stuck. IrCOve never seen one stick open. A rCytaprCO on
    the side of the body normally frees a stuck closed / down pin. ( Remove
    the head first.)

    One of my TRVs has just developed a drip from the centre pin area - I say
    developed, really it's a problem we had last winter that I thought I had
    fixed by working the pin up and down and adding WD40. Now it's back and
    quite a lot worse, so I've had to put a bowl under it.

    I don't think I can replace the valve myself as there is no way of
    shutting off the water to the rad without draining the system.


    Rarely necessary to drain a whole system. If itrCOs a sealed system with an expansion vessel and pressure gauge, just depressurise the system, close
    off the lockshield valve and drain the radiator down from the other end
    with something to catch the water. Once the radiator is drained down, very little water will come out of the rest of the pipework. If you can get the same TRV (or at least one with he same fittings and dimensions) you should
    be able to swap the old one out.

    If you have an open vented system, you will need to seal the feed and expansion pipes with suitable bungs. Then proceed as above.

    Tim

    Best thing to catch the water -


    https://m.media-amazon.com/images/S/aplus-media-library-service-media/cffbfd29-bbcb-4843-a420-1a3ad5a8b4ae.__CR0,0,1500,1500_PT0_SX220_V1___.jpg

    Regards
    --- Synchronet 3.21a-Linux NewsLink 1.2
  • From RJH@patchmoney@gmx.com to uk.d-i-y on Fri Jan 2 14:22:28 2026
    From Newsgroup: uk.d-i-y

    On 2 Jan 2026 at 11:41:20 GMT, newman wrote:

    Rarely necessary to drain a whole system. If itrCOs a sealed system with an >> expansion vessel and pressure gauge, just depressurise the system, close
    off the lockshield valve and drain the radiator down from the other end
    with something to catch the water. Once the radiator is drained down, very >> little water will come out of the rest of the pipework. If you can get the >> same TRV (or at least one with he same fittings and dimensions) you should >> be able to swap the old one out.

    If you have an open vented system, you will need to seal the feed and
    expansion pipes with suitable bungs. Then proceed as above.

    Tim

    Best thing to catch the water -


    https://m.media-amazon.com/images/S/aplus-media-library-service-media/cffbfd29-bbcb-4843-a420-1a3ad5a8b4ae.__CR0,0,1500,1500_PT0_SX220_V1___.jpg

    Paint roller trays have always done it for me.

    Might get one of those for next time - but -u10 for a bit of plastic . . .
    --
    Cheers, Rob, Sheffield UK
    --- Synchronet 3.21a-Linux NewsLink 1.2
  • From Sam Plusnet@not@home.com to uk.d-i-y on Fri Jan 2 19:26:35 2026
    From Newsgroup: uk.d-i-y

    On 02/01/2026 11:41, newman wrote:
    On 01/01/2026 14:46, Tim+ wrote:
    Handsome Jack <jack@handsome.com> wrote:
    On Tue, 30 Dec 2025 21:58:52 -0000 (UTC), Brian wrote:

    Tom <ce0537a20a14ccd3ebf37f2484174906@example.com> wrote:
    Just been grappling with this problem. We have a red hot radrCO and lrCOve
    not been able to release the valve following plumbersrCO advice on You >>>>> Tube vids. Been hesitant to touch the brass nut but will give it a go >>>>> as it seems to have worked for others. Thanks Andy Bennet for the
    advice.


    When Thermostatic Rad Valves stick, they tend to stick closed. The
    usual
    rCytappingrCO trick is to open them.

    If the rad is hot, the valve is open.

    Either the head isnrCOt fitted correctly or the head is damaged. The
    temperature sensitive bit is in the head, it presses on the pin.

    If the pin is rCyuprCO the valve is open. Use something metal to push it >>>> down.
    If it moves, it isnrCOt stuck. IrCOve never seen one stick open. A rCytaprCO on
    the side of the body normally frees a stuck closed / down pin. ( Remove >>>> the head first.)

    One of my TRVs has just developed a drip from the centre pin area - I
    say
    developed, really it's a problem we had last winter that I thought I had >>> fixed by working the pin up and down and adding WD40. Now it's back and
    quite a lot worse, so I've had to put a bowl under it.

    I don't think I can replace the valve myself as there is no way of
    shutting off the water to the rad without draining the system.


    Rarely necessary to drain a whole system.-a If itrCOs a sealed system
    with an
    expansion vessel and pressure gauge, just depressurise the system, close
    off the lockshield valve and drain the radiator down from the other end
    with something to catch the water. Once the radiator is drained down,
    very
    little water will come out of the rest of the pipework.-a If you can
    get the
    same TRV (or at least one with he same fittings and dimensions) you
    should
    be able to swap the old one out.

    If you have an open vented system, you will need to seal the feed and
    expansion pipes with suitable bungs. Then proceed as above.

    Tim

    Best thing to catch the water -


    https://m.media-amazon.com/images/S/aplus-media-library-service-media/ cffbfd29-bbcb-4843-a420-1a3ad5a8b4ae.__CR0,0,1500,1500_PT0_SX220_V1___.jpg

    Agreed, but the one shown is getting too full to empty without spillage.
    --
    Sam Plusnet
    --- Synchronet 3.21a-Linux NewsLink 1.2
  • From Sam Plusnet@not@home.com to uk.d-i-y on Fri Jan 2 19:26:22 2026
    From Newsgroup: uk.d-i-y

    On 02/01/2026 11:41, newman wrote:
    On 01/01/2026 14:46, Tim+ wrote:
    Handsome Jack <jack@handsome.com> wrote:
    On Tue, 30 Dec 2025 21:58:52 -0000 (UTC), Brian wrote:

    Tom <ce0537a20a14ccd3ebf37f2484174906@example.com> wrote:
    Just been grappling with this problem. We have a red hot radrCO and lrCOve
    not been able to release the valve following plumbersrCO advice on You >>>>> Tube vids. Been hesitant to touch the brass nut but will give it a go >>>>> as it seems to have worked for others. Thanks Andy Bennet for the
    advice.


    When Thermostatic Rad Valves stick, they tend to stick closed. The
    usual
    rCytappingrCO trick is to open them.

    If the rad is hot, the valve is open.

    Either the head isnrCOt fitted correctly or the head is damaged. The
    temperature sensitive bit is in the head, it presses on the pin.

    If the pin is rCyuprCO the valve is open. Use something metal to push it >>>> down.
    If it moves, it isnrCOt stuck. IrCOve never seen one stick open. A rCytaprCO on
    the side of the body normally frees a stuck closed / down pin. ( Remove >>>> the head first.)

    One of my TRVs has just developed a drip from the centre pin area - I
    say
    developed, really it's a problem we had last winter that I thought I had >>> fixed by working the pin up and down and adding WD40. Now it's back and
    quite a lot worse, so I've had to put a bowl under it.

    I don't think I can replace the valve myself as there is no way of
    shutting off the water to the rad without draining the system.


    Rarely necessary to drain a whole system.-a If itrCOs a sealed system
    with an
    expansion vessel and pressure gauge, just depressurise the system, close
    off the lockshield valve and drain the radiator down from the other end
    with something to catch the water. Once the radiator is drained down,
    very
    little water will come out of the rest of the pipework.-a If you can
    get the
    same TRV (or at least one with he same fittings and dimensions) you
    should
    be able to swap the old one out.

    If you have an open vented system, you will need to seal the feed and
    expansion pipes with suitable bungs. Then proceed as above.

    Tim

    Best thing to catch the water -


    https://m.media-amazon.com/images/S/aplus-media-library-service-media/ cffbfd29-bbcb-4843-a420-1a3ad5a8b4ae.__CR0,0,1500,1500_PT0_SX220_V1___.jpg

    Agreed, but the one shown is getting too full to empty without spillage.
    --
    Sam Plusnet
    --- Synchronet 3.21a-Linux NewsLink 1.2
  • From Tim+@timdownieuk@yahoo.co.youkay to uk.d-i-y on Fri Jan 2 20:14:56 2026
    From Newsgroup: uk.d-i-y

    Sam Plusnet <not@home.com> wrote:
    On 02/01/2026 11:41, newman wrote:
    On 01/01/2026 14:46, Tim+ wrote:
    Handsome Jack <jack@handsome.com> wrote:
    On Tue, 30 Dec 2025 21:58:52 -0000 (UTC), Brian wrote:

    Tom <ce0537a20a14ccd3ebf37f2484174906@example.com> wrote:
    Just been grappling with this problem. We have a red hot radrCO and lrCOve
    not been able to release the valve following plumbersrCO advice on You >>>>>> Tube vids. Been hesitant to touch the brass nut but will give it a go >>>>>> as it seems to have worked for others. Thanks Andy Bennet for the
    advice.


    When Thermostatic Rad Valves stick, they tend to stick closed. The
    usual
    rCytappingrCO trick is to open them.

    If the rad is hot, the valve is open.

    Either the head isnrCOt fitted correctly or the head is damaged. The >>>>> temperature sensitive bit is in the head, it presses on the pin.

    If the pin is rCyuprCO the valve is open. Use something metal to push it >>>>> down.
    If it moves, it isnrCOt stuck. IrCOve never seen one stick open. A rCytaprCO on
    the side of the body normally frees a stuck closed / down pin. ( Remove >>>>> the head first.)

    One of my TRVs has just developed a drip from the centre pin area - I >>>> say
    developed, really it's a problem we had last winter that I thought I had >>>> fixed by working the pin up and down and adding WD40. Now it's back and >>>> quite a lot worse, so I've had to put a bowl under it.

    I don't think I can replace the valve myself as there is no way of
    shutting off the water to the rad without draining the system.


    Rarely necessary to drain a whole system.-a If itrCOs a sealed system
    with an
    expansion vessel and pressure gauge, just depressurise the system, close >>> off the lockshield valve and drain the radiator down from the other end
    with something to catch the water. Once the radiator is drained down,
    very
    little water will come out of the rest of the pipework.-a If you can
    get the
    same TRV (or at least one with he same fittings and dimensions) you
    should
    be able to swap the old one out.

    If you have an open vented system, you will need to seal the feed and
    expansion pipes with suitable bungs. Then proceed as above.

    Tim

    Best thing to catch the water -


    https://m.media-amazon.com/images/S/aplus-media-library-service-media/
    cffbfd29-bbcb-4843-a420-1a3ad5a8b4ae.__CR0,0,1500,1500_PT0_SX220_V1___.jpg

    Agreed, but the one shown is getting too full to empty without spillage.



    A wetrCOnrCOdry vacuum cleaner is your friend in these situations. ;-)

    Tim
    --
    Please don't feed the trolls
    --- Synchronet 3.21a-Linux NewsLink 1.2
  • From Handsome Jack@jack@handsome.com to uk.d-i-y on Sat Jan 3 08:39:37 2026
    From Newsgroup: uk.d-i-y

    On 1 Jan 2026 14:46:02 GMT, Tim+ wrote:

    Handsome Jack <jack@handsome.com> wrote:
    One of my TRVs has just developed a drip from the centre pin area - I
    say developed, really it's a problem we had last winter that I thought
    I had fixed by working the pin up and down and adding WD40. Now it's
    back and quite a lot worse, so I've had to put a bowl under it.

    I don't think I can replace the valve myself as there is no way of
    shutting off the water to the rad without draining the system.


    Rarely necessary to drain a whole system. If itrCOs a sealed system with
    an expansion vessel and pressure gauge, just depressurise the system,
    close off the lockshield valve and drain the radiator down from the
    other end with something to catch the water. Once the radiator is
    drained down, very little water will come out of the rest of the
    pipework. If you can get the same TRV (or at least one with he same
    fittings and dimensions) you should be able to swap the old one out.

    If you have an open vented system, you will need to seal the feed and expansion pipes with suitable bungs. Then proceed as above.


    Thanks to you and others for this; the youtube video is helpful too.

    I have temporarily stopped the leak by inserting a tap washer over the pin assembly and screwing the TRV head down tight. When the weather warms up a
    bit I'll try swapping in a new valve.
    --- Synchronet 3.21a-Linux NewsLink 1.2
  • From wasbit@wasbit@REMOVEhotmail.com to uk.d-i-y on Sat Jan 3 09:50:02 2026
    From Newsgroup: uk.d-i-y

    On 02/01/2026 11:41, newman wrote:
    snip <

    Best thing to catch the water -


    https://m.media-amazon.com/images/S/aplus-media-library-service-media/cffbfd29-bbcb-4843-a420-1a3ad5a8b4ae.__CR0,0,1500,1500_PT0_SX220_V1___.jpg



    Poorly thought out gadget. How are you going to remove it from the pipe?
    Might be slightly easier if the pipe didn't go into one of the corner holes.
    --
    Regards
    wasbit
    --- Synchronet 3.21a-Linux NewsLink 1.2
  • From Tricky Dicky@tricky.dicky@sky.com to uk.d-i-y on Sat Jan 3 14:15:43 2026
    From Newsgroup: uk.d-i-y

    wasbit <wasbit@REMOVEhotmail.com> wrote:
    On 02/01/2026 11:41, newman wrote:
    snip <

    Best thing to catch the water -


    https://m.media-amazon.com/images/S/aplus-media-library-service-media/cffbfd29-bbcb-4843-a420-1a3ad5a8b4ae.__CR0,0,1500,1500_PT0_SX220_V1___.jpg




    Poorly thought out gadget. How are you going to remove it from the pipe? Might be slightly easier if the pipe didn't go into one of the corner holes.





    The corner holes have a split to allow fitting to pipes and for easy
    removal. I have two and found it easy to swap over as they fill by opening
    and closing the air vent you can control the draining.

    --- Synchronet 3.21a-Linux NewsLink 1.2
  • From newman@aa111@despammed.com to uk.d-i-y on Sat Jan 3 15:10:02 2026
    From Newsgroup: uk.d-i-y

    On 03/01/2026 09:50, wasbit wrote:
    On 02/01/2026 11:41, newman wrote:
    snip <

    Best thing to catch the water -


    https://m.media-amazon.com/images/S/aplus-media-library-service-media/cffbfd29-bbcb-4843-a420-1a3ad5a8b4ae.__CR0,0,1500,1500_PT0_SX220_V1___.jpg


    Poorly thought out gadget. How are you going to remove it from the pipe? Might be slightly easier if the pipe didn't go into one of the corner
    holes.




    It is made of soft material and slips off the pipe easily.