I have done a bit of web searching but I've not managed to come up
with a definitive answer.
Is an Underwriters Laboratory cable voltage rating an AC RMS value or
a DC value? E.g. I have some cable marked 300v, can I use it for
carrying mains voltage? (It fits all the other obvious rules like
being double sheathed etc.)
On 23/02/2026 09:56, Chris Green wrote:
I have done a bit of web searching but I've not managed to come up
with a definitive answer.
Is an Underwriters Laboratory cable voltage rating an AC RMS value or
a DC value?-a E.g. I have some cable marked 300v, can I use it for
carrying mains voltage? (It fits all the other obvious rules like
being double sheathed etc.)
It definitely will not be the rms value as the peak voltage is dependant
on the waveform form factor. rms value gives you the DC heating effect voltage into a resistive load. I suspect it is the peak voltage rating.
On 23/02/2026 11:48, Andy Bennett wrote:
On 23/02/2026 09:56, Chris Green wrote:
I have done a bit of web searching but I've not managed to come up
with a definitive answer.
Is an Underwriters Laboratory cable voltage rating an AC RMS value or
a DC value?-a E.g. I have some cable marked 300v, can I use it for
carrying mains voltage? (It fits all the other obvious rules like
being double sheathed etc.)
It definitely will not be the rms value as the peak voltage is
dependant on the waveform form factor. rms value gives you the DC
heating effect voltage into a resistive load. I suspect it is the peak
voltage rating.
It is almost certainly the RMS voltage! 300V and 600V ac are both
very common cable ratings.
John
On 23/02/2026 13:51, John R Walliker wrote:
On 23/02/2026 11:48, Andy Bennett wrote:
On 23/02/2026 09:56, Chris Green wrote:
I have done a bit of web searching but I've not managed to come up
with a definitive answer.
Is an Underwriters Laboratory cable voltage rating an AC RMS value or
a DC value?-a E.g. I have some cable marked 300v, can I use it for
carrying mains voltage? (It fits all the other obvious rules like
being double sheathed etc.)
It definitely will not be the rms value as the peak voltage is
dependant on the waveform form factor. rms value gives you the DC
heating effect voltage into a resistive load. I suspect it is the
peak voltage rating.
It is almost certainly the RMS voltage! 300V and 600V ac are both
very common cable ratings.
John
So a 10kV peak to peak poor form factor a.c. waveform whose rms voltage
is 230V is perfectly ok on 300V rated cable?
On 23/02/2026 13:56, Andy Bennett wrote:
On 23/02/2026 13:51, John R Walliker wrote:
On 23/02/2026 11:48, Andy Bennett wrote:
On 23/02/2026 09:56, Chris Green wrote:
I have done a bit of web searching but I've not managed to come up
with a definitive answer.
Is an Underwriters Laboratory cable voltage rating an AC RMS value or >>>>> a DC value?-a E.g. I have some cable marked 300v, can I use it for
carrying mains voltage? (It fits all the other obvious rules like
being double sheathed etc.)
It definitely will not be the rms value as the peak voltage is
dependant on the waveform form factor. rms value gives you the DC
heating effect voltage into a resistive load. I suspect it is the
peak voltage rating.
It is almost certainly the RMS voltage! 300V and 600V ac are both
very common cable ratings.
John
So a 10kV peak to peak poor form factor a.c. waveform whose rms
voltage is 230V is perfectly ok on 300V rated cable?
Lol.
As always the problem of specifying complex technical data to the
'average user' rears its ugly head.
It's more usual to rate stuff like-a "250V AC/450V DC"to allow for the above.
On 23/02/2026 14:15, The Natural Philosopher wrote:
On 23/02/2026 13:56, Andy Bennett wrote:The standard for testing cables, BS EN 50395 deals with such issues
On 23/02/2026 13:51, John R Walliker wrote:
On 23/02/2026 11:48, Andy Bennett wrote:
On 23/02/2026 09:56, Chris Green wrote:
I have done a bit of web searching but I've not managed to come up >>>>>> with a definitive answer.
Is an Underwriters Laboratory cable voltage rating an AC RMS value or >>>>>> a DC value?-a E.g. I have some cable marked 300v, can I use it for >>>>>> carrying mains voltage? (It fits all the other obvious rules like
being double sheathed etc.)
It definitely will not be the rms value as the peak voltage is
dependant on the waveform form factor. rms value gives you the DC
heating effect voltage into a resistive load. I suspect it is the
peak voltage rating.
It is almost certainly the RMS voltage! 300V and 600V ac are both
very common cable ratings.
John
So a 10kV peak to peak poor form factor a.c. waveform whose rms
voltage is 230V is perfectly ok on 300V rated cable?
Lol.
As always the problem of specifying complex technical data to the
'average user' rears its ugly head.
It's more usual to rate stuff like-a "250V AC/450V DC"to allow for the
above.
as follows:
"Unless otherwise stated the test voltage shall be ac of approximately
sine wave form and of frequency between 49 and 61 Hz.-a The ratio of
peak value to r.m.s value shall be equal to sqrt 2 with a tolerance
of +/- 7%.
The values quoted are r.m.s. values."
John
On 23/02/2026 16:00, John R Walliker wrote:
On 23/02/2026 14:15, The Natural Philosopher wrote:
On 23/02/2026 13:56, Andy Bennett wrote:The standard for testing cables, BS EN 50395 deals with such issues
On 23/02/2026 13:51, John R Walliker wrote:
On 23/02/2026 11:48, Andy Bennett wrote:
On 23/02/2026 09:56, Chris Green wrote:
I have done a bit of web searching but I've not managed to come up >>>>>> with a definitive answer.
Is an Underwriters Laboratory cable voltage rating an AC RMS value or >>>>>> a DC value?-a E.g. I have some cable marked 300v, can I use it for >>>>>> carrying mains voltage? (It fits all the other obvious rules like >>>>>> being double sheathed etc.)
It definitely will not be the rms value as the peak voltage is
dependant on the waveform form factor. rms value gives you the DC >>>>> heating effect voltage into a resistive load. I suspect it is the >>>>> peak voltage rating.
It is almost certainly the RMS voltage! 300V and 600V ac are both
very common cable ratings.
John
So a 10kV peak to peak poor form factor a.c. waveform whose rms
voltage is 230V is perfectly ok on 300V rated cable?
Lol.
As always the problem of specifying complex technical data to the
'average user' rears its ugly head.
It's more usual to rate stuff like-a "250V AC/450V DC"to allow for the
above.
as follows:
"Unless otherwise stated the test voltage shall be ac of approximately
sine wave form and of frequency between 49 and 61 Hz.-a The ratio of
peak value to r.m.s value shall be equal to sqrt 2 with a tolerance
of +/- 7%.
The values quoted are r.m.s. values."
John
According to BS EN 50525-1 completed cables for general use that are
rated at 300V line to neutral are tested at 2kV rms for at least 15
minutes. Individual cores are tested for at least 5 minutes at 2kV
if the insulation is >0.6mm thick and at 1.5kV if <=0.6mm.
There is a lot of harmonization of standards, so UL is probably
very similar.
John R Walliker <jrwalliker@gmail.com> wrote:
On 23/02/2026 16:00, John R Walliker wrote:
On 23/02/2026 14:15, The Natural Philosopher wrote:According to BS EN 50525-1 completed cables for general use that are
On 23/02/2026 13:56, Andy Bennett wrote:The standard for testing cables, BS EN 50395 deals with such issues
On 23/02/2026 13:51, John R Walliker wrote:
On 23/02/2026 11:48, Andy Bennett wrote:
On 23/02/2026 09:56, Chris Green wrote:
I have done a bit of web searching but I've not managed to come up >>>>>>>> with a definitive answer.
Is an Underwriters Laboratory cable voltage rating an AC RMS value or >>>>>>>> a DC value?-a E.g. I have some cable marked 300v, can I use it for >>>>>>>> carrying mains voltage? (It fits all the other obvious rules like >>>>>>>> being double sheathed etc.)
It definitely will not be the rms value as the peak voltage is
dependant on the waveform form factor. rms value gives you the DC >>>>>>> heating effect voltage into a resistive load. I suspect it is the >>>>>>> peak voltage rating.
It is almost certainly the RMS voltage! 300V and 600V ac are both
very common cable ratings.
John
So a 10kV peak to peak poor form factor a.c. waveform whose rms
voltage is 230V is perfectly ok on 300V rated cable?
Lol.
As always the problem of specifying complex technical data to the
'average user' rears its ugly head.
It's more usual to rate stuff like-a "250V AC/450V DC"to allow for the >>>> above.
as follows:
"Unless otherwise stated the test voltage shall be ac of approximately
sine wave form and of frequency between 49 and 61 Hz.-a The ratio of
peak value to r.m.s value shall be equal to sqrt 2 with a tolerance
of +/- 7%.
The values quoted are r.m.s. values."
John
rated at 300V line to neutral are tested at 2kV rms for at least 15
minutes. Individual cores are tested for at least 5 minutes at 2kV
if the insulation is >0.6mm thick and at 1.5kV if <=0.6mm.
There is a lot of harmonization of standards, so UL is probably
very similar.
Thanks all, the cable certainly looks the part for carrying mains
voltage. As it ahppens the requirement (making a long lead for a
toothbrush charger) has now disappeared but it's still of interest.
Can one reasonably requir/mandate a three amp fuse in the plug on the
end of the cable?
If not then how do you make sure it's not
overloaded?
It's certainly not a requirement that all cables (on a
UK plug top) can carry 13 amps safely.