    I have done a bit of web searching but I've not managed to come up
    with a definitive answer.

    Is an Underwriters Laboratory cable voltage rating an AC RMS value or
    a DC value? E.g. I have some cable marked 300v, can I use it for
    carrying mains voltage? (It fits all the other obvious rules like
    being double sheathed etc.)
    --
    Chris Green
    -+
    --- Synchronet 3.21b-Linux NewsLink 1.2
  • From Andy Bennett@aben@ben37j.com to uk.d-i-y on Mon Feb 23 11:48:08 2026
    From Newsgroup: uk.d-i-y

    On 23/02/2026 09:56, Chris Green wrote:
    I have done a bit of web searching but I've not managed to come up
    with a definitive answer.

    Is an Underwriters Laboratory cable voltage rating an AC RMS value or
    a DC value? E.g. I have some cable marked 300v, can I use it for
    carrying mains voltage? (It fits all the other obvious rules like
    being double sheathed etc.)


    It definitely will not be the rms value as the peak voltage is dependant
    on the waveform form factor. rms value gives you the DC heating effect
    voltage into a resistive load. I suspect it is the peak voltage rating.
    --- Synchronet 3.21b-Linux NewsLink 1.2
  • From John R Walliker@jrwalliker@gmail.com to uk.d-i-y on Mon Feb 23 13:51:41 2026
    From Newsgroup: uk.d-i-y

    On 23/02/2026 11:48, Andy Bennett wrote:
    On 23/02/2026 09:56, Chris Green wrote:
    I have done a bit of web searching but I've not managed to come up
    with a definitive answer.

    Is an Underwriters Laboratory cable voltage rating an AC RMS value or
    a DC value?-a E.g. I have some cable marked 300v, can I use it for
    carrying mains voltage? (It fits all the other obvious rules like
    being double sheathed etc.)


    It definitely will not be the rms value as the peak voltage is dependant
    on the waveform form factor. rms value gives you the DC heating effect voltage into a resistive load. I suspect it is the peak voltage rating.

    It is almost certainly the RMS voltage! 300V and 600V ac are both
    very common cable ratings.

    John

    --- Synchronet 3.21b-Linux NewsLink 1.2
  • From Andy Bennett@aben@ben37j.com to uk.d-i-y on Mon Feb 23 13:56:56 2026
    From Newsgroup: uk.d-i-y

    On 23/02/2026 13:51, John R Walliker wrote:
    On 23/02/2026 11:48, Andy Bennett wrote:
    On 23/02/2026 09:56, Chris Green wrote:
    I have done a bit of web searching but I've not managed to come up
    with a definitive answer.

    Is an Underwriters Laboratory cable voltage rating an AC RMS value or
    a DC value?-a E.g. I have some cable marked 300v, can I use it for
    carrying mains voltage? (It fits all the other obvious rules like
    being double sheathed etc.)


    It definitely will not be the rms value as the peak voltage is
    dependant on the waveform form factor. rms value gives you the DC
    heating effect voltage into a resistive load. I suspect it is the peak
    voltage rating.

    It is almost certainly the RMS voltage! 300V and 600V ac are both
    very common cable ratings.

    John


    So a 10kV peak to peak poor form factor a.c. waveform whose rms voltage
    is 230V is perfectly ok on 300V rated cable?

    --- Synchronet 3.21b-Linux NewsLink 1.2
  • From The Natural Philosopher@tnp@invalid.invalid to uk.d-i-y on Mon Feb 23 14:15:00 2026
    From Newsgroup: uk.d-i-y

    On 23/02/2026 13:56, Andy Bennett wrote:
    On 23/02/2026 13:51, John R Walliker wrote:
    On 23/02/2026 11:48, Andy Bennett wrote:
    On 23/02/2026 09:56, Chris Green wrote:
    I have done a bit of web searching but I've not managed to come up
    with a definitive answer.

    Is an Underwriters Laboratory cable voltage rating an AC RMS value or
    a DC value?-a E.g. I have some cable marked 300v, can I use it for
    carrying mains voltage? (It fits all the other obvious rules like
    being double sheathed etc.)


    It definitely will not be the rms value as the peak voltage is
    dependant on the waveform form factor. rms value gives you the DC
    heating effect voltage into a resistive load. I suspect it is the
    peak voltage rating.

    It is almost certainly the RMS voltage! 300V and 600V ac are both
    very common cable ratings.

    John


    So a 10kV peak to peak poor form factor a.c. waveform whose rms voltage
    is 230V is perfectly ok on 300V rated cable?


    Lol.

    As always the problem of specifying complex technical data to the
    'average user' rears its ugly head.

    It's more usual to rate stuff like "250V AC/450V DC"to allow for the above.
    --
    rCLit should be clear by now to everyone that activist environmentalism
    (or environmental activism) is becoming a general ideology about humans,
    about their freedom, about the relationship between the individual and
    the state, and about the manipulation of people under the guise of a
    'noble' idea. It is not an honest pursuit of 'sustainable development,'
    a matter of elementary environmental protection, or a search for
    rational mechanisms designed to achieve a healthy environment. Yet
    things do occur that make you shake your head and remind yourself that
    you live neither in Joseph StalinrCOs Communist era, nor in the Orwellian utopia of 1984.rCY

    Vaclav Klaus

    --- Synchronet 3.21b-Linux NewsLink 1.2
  • From John R Walliker@jrwalliker@gmail.com to uk.d-i-y on Mon Feb 23 16:00:11 2026
    From Newsgroup: uk.d-i-y

    On 23/02/2026 14:15, The Natural Philosopher wrote:
    On 23/02/2026 13:56, Andy Bennett wrote:
    On 23/02/2026 13:51, John R Walliker wrote:
    On 23/02/2026 11:48, Andy Bennett wrote:
    On 23/02/2026 09:56, Chris Green wrote:
    I have done a bit of web searching but I've not managed to come up
    with a definitive answer.

    Is an Underwriters Laboratory cable voltage rating an AC RMS value or >>>>> a DC value?-a E.g. I have some cable marked 300v, can I use it for
    carrying mains voltage? (It fits all the other obvious rules like
    being double sheathed etc.)


    It definitely will not be the rms value as the peak voltage is
    dependant on the waveform form factor. rms value gives you the DC
    heating effect voltage into a resistive load. I suspect it is the
    peak voltage rating.

    It is almost certainly the RMS voltage! 300V and 600V ac are both
    very common cable ratings.

    John


    So a 10kV peak to peak poor form factor a.c. waveform whose rms
    voltage is 230V is perfectly ok on 300V rated cable?


    Lol.

    As always the problem of specifying complex technical data to the
    'average user' rears its ugly head.

    It's more usual to rate stuff like-a "250V AC/450V DC"to allow for the above.


    The standard for testing cables, BS EN 50395 deals with such issues
    as follows:
    "Unless otherwise stated the test voltage shall be ac of approximately
    sine wave form and of frequency between 49 and 61 Hz. The ratio of
    peak value to r.m.s value shall be equal to sqrt 2 with a tolerance
    of +/- 7%.
    The values quoted are r.m.s. values."

    John

    --- Synchronet 3.21b-Linux NewsLink 1.2
  • From John R Walliker@jrwalliker@gmail.com to uk.d-i-y on Mon Feb 23 17:36:41 2026
    From Newsgroup: uk.d-i-y

    On 23/02/2026 16:00, John R Walliker wrote:
    On 23/02/2026 14:15, The Natural Philosopher wrote:
    On 23/02/2026 13:56, Andy Bennett wrote:
    On 23/02/2026 13:51, John R Walliker wrote:
    On 23/02/2026 11:48, Andy Bennett wrote:
    On 23/02/2026 09:56, Chris Green wrote:
    I have done a bit of web searching but I've not managed to come up >>>>>> with a definitive answer.

    Is an Underwriters Laboratory cable voltage rating an AC RMS value or >>>>>> a DC value?-a E.g. I have some cable marked 300v, can I use it for >>>>>> carrying mains voltage? (It fits all the other obvious rules like
    being double sheathed etc.)


    It definitely will not be the rms value as the peak voltage is
    dependant on the waveform form factor. rms value gives you the DC
    heating effect voltage into a resistive load. I suspect it is the
    peak voltage rating.

    It is almost certainly the RMS voltage! 300V and 600V ac are both
    very common cable ratings.

    John


    So a 10kV peak to peak poor form factor a.c. waveform whose rms
    voltage is 230V is perfectly ok on 300V rated cable?


    Lol.

    As always the problem of specifying complex technical data to the
    'average user' rears its ugly head.

    It's more usual to rate stuff like-a "250V AC/450V DC"to allow for the
    above.


    The standard for testing cables, BS EN 50395 deals with such issues
    as follows:
    "Unless otherwise stated the test voltage shall be ac of approximately
    sine wave form and of frequency between 49 and 61 Hz.-a The ratio of
    peak value to r.m.s value shall be equal to sqrt 2 with a tolerance
    of +/- 7%.
    The values quoted are r.m.s. values."

    John

    According to BS EN 50525-1 completed cables for general use that are
    rated at 300V line to neutral are tested at 2kV rms for at least 15
    minutes. Individual cores are tested for at least 5 minutes at 2kV
    if the insulation is >0.6mm thick and at 1.5kV if <=0.6mm.
    There is a lot of harmonization of standards, so UL is probably
    very similar.
    John

    --- Synchronet 3.21b-Linux NewsLink 1.2
  • From Chris Green@cl@isbd.net to uk.d-i-y on Mon Feb 23 18:03:39 2026
    From Newsgroup: uk.d-i-y

    John R Walliker <jrwalliker@gmail.com> wrote:
    On 23/02/2026 16:00, John R Walliker wrote:
    On 23/02/2026 14:15, The Natural Philosopher wrote:
    On 23/02/2026 13:56, Andy Bennett wrote:
    On 23/02/2026 13:51, John R Walliker wrote:
    On 23/02/2026 11:48, Andy Bennett wrote:
    On 23/02/2026 09:56, Chris Green wrote:
    I have done a bit of web searching but I've not managed to come up >>>>>> with a definitive answer.

    Is an Underwriters Laboratory cable voltage rating an AC RMS value or >>>>>> a DC value?-a E.g. I have some cable marked 300v, can I use it for >>>>>> carrying mains voltage? (It fits all the other obvious rules like >>>>>> being double sheathed etc.)


    It definitely will not be the rms value as the peak voltage is
    dependant on the waveform form factor. rms value gives you the DC >>>>> heating effect voltage into a resistive load. I suspect it is the >>>>> peak voltage rating.

    It is almost certainly the RMS voltage! 300V and 600V ac are both
    very common cable ratings.

    John


    So a 10kV peak to peak poor form factor a.c. waveform whose rms
    voltage is 230V is perfectly ok on 300V rated cable?


    Lol.

    As always the problem of specifying complex technical data to the
    'average user' rears its ugly head.

    It's more usual to rate stuff like-a "250V AC/450V DC"to allow for the
    above.


    The standard for testing cables, BS EN 50395 deals with such issues
    as follows:
    "Unless otherwise stated the test voltage shall be ac of approximately
    sine wave form and of frequency between 49 and 61 Hz.-a The ratio of
    peak value to r.m.s value shall be equal to sqrt 2 with a tolerance
    of +/- 7%.
    The values quoted are r.m.s. values."

    John

    According to BS EN 50525-1 completed cables for general use that are
    rated at 300V line to neutral are tested at 2kV rms for at least 15
    minutes. Individual cores are tested for at least 5 minutes at 2kV
    if the insulation is >0.6mm thick and at 1.5kV if <=0.6mm.
    There is a lot of harmonization of standards, so UL is probably
    very similar.

    Thanks all, the cable certainly looks the part for carrying mains
    voltage. As it ahppens the requirement (making a long lead for a
    toothbrush charger) has now disappeared but it's still of interest.

    Can one reasonably requir/mandate a three amp fuse in the plug on the
    end of the cable? If not then how do you make sure it's not
    overloaded? It's certainly not a requirement that all cables (on a
    UK plug top) can carry 13 amps safely.
    --
    Chris Green
    -+
    --- Synchronet 3.21b-Linux NewsLink 1.2
  • From John Rumm@see.my.signature@nowhere.null to uk.d-i-y on Tue Feb 24 09:45:14 2026
    From Newsgroup: uk.d-i-y

    On 23/02/2026 18:03, Chris Green wrote:
    John R Walliker <jrwalliker@gmail.com> wrote:
    On 23/02/2026 16:00, John R Walliker wrote:
    On 23/02/2026 14:15, The Natural Philosopher wrote:
    On 23/02/2026 13:56, Andy Bennett wrote:
    On 23/02/2026 13:51, John R Walliker wrote:
    On 23/02/2026 11:48, Andy Bennett wrote:
    On 23/02/2026 09:56, Chris Green wrote:
    I have done a bit of web searching but I've not managed to come up >>>>>>>> with a definitive answer.

    Is an Underwriters Laboratory cable voltage rating an AC RMS value or >>>>>>>> a DC value?-a E.g. I have some cable marked 300v, can I use it for >>>>>>>> carrying mains voltage? (It fits all the other obvious rules like >>>>>>>> being double sheathed etc.)


    It definitely will not be the rms value as the peak voltage is
    dependant on the waveform form factor. rms value gives you the DC >>>>>>> heating effect voltage into a resistive load. I suspect it is the >>>>>>> peak voltage rating.

    It is almost certainly the RMS voltage! 300V and 600V ac are both
    very common cable ratings.

    John


    So a 10kV peak to peak poor form factor a.c. waveform whose rms
    voltage is 230V is perfectly ok on 300V rated cable?


    Lol.

    As always the problem of specifying complex technical data to the
    'average user' rears its ugly head.

    It's more usual to rate stuff like-a "250V AC/450V DC"to allow for the >>>> above.


    The standard for testing cables, BS EN 50395 deals with such issues
    as follows:
    "Unless otherwise stated the test voltage shall be ac of approximately
    sine wave form and of frequency between 49 and 61 Hz.-a The ratio of
    peak value to r.m.s value shall be equal to sqrt 2 with a tolerance
    of +/- 7%.
    The values quoted are r.m.s. values."

    John

    According to BS EN 50525-1 completed cables for general use that are
    rated at 300V line to neutral are tested at 2kV rms for at least 15
    minutes. Individual cores are tested for at least 5 minutes at 2kV
    if the insulation is >0.6mm thick and at 1.5kV if <=0.6mm.
    There is a lot of harmonization of standards, so UL is probably
    very similar.

    Thanks all, the cable certainly looks the part for carrying mains
    voltage. As it ahppens the requirement (making a long lead for a
    toothbrush charger) has now disappeared but it's still of interest.

    Can one reasonably requir/mandate a three amp fuse in the plug on the
    end of the cable?

    Mandate, probably not... you could obviously fix a label etc.

    If not then how do you make sure it's not
    overloaded?

    In most cases that is something you control at the appliance end. i.e Is
    there any plausible non fault[1] scenario where the appliance that
    normally draws (say) 150mA could suddenly start to sustain a draw of 13A?

    In the vast majority of cases the answer will be "no".

    [1] Fault in this case having a specific meaning i.e. the (typically
    very large) current that will flow as the result of a fault like a short
    from phase to earth or phase to neutral.

    So an overload is only one of the over current situations that you
    design for, the more important one (typically) is dealing with fault
    currents. Also fault current protection *must* be at the source end of
    the supply, whereas overloads protection can be controlled by design and selection of equipment at the destination end of the circuit.

    It's certainly not a requirement that all cables (on a
    UK plug top) can carry 13 amps safely.

    For an appliance protected by a fuse[2] you are not protecting the cable
    for 13A, but more likely from >100A - typically for a very short
    duration. Possibly counter intuitively, a 13A fuse will often protect a
    "3A" flex in these cases. (you can check this using the Adiabatic check
    as described here:

    https://wiki.diyfaq.org.uk/index.php?title=Calculating_A_Cable_Size#Adiabatic_Check

    [2] for the exceptions see:

    https://wiki.diyfaq.org.uk/index.php?title=Choosing_a_plug_fuse#Special_Cases --
    Cheers,

    John.

    /=================================================================\
    | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------|
    | John Rumm - john(at)internode(dot)co(dot)uk | \=================================================================/
    --- Synchronet 3.21b-Linux NewsLink 1.2