This a newer UPS which has gone through only 1 battery.
New battery is not recieving a charge; diagnostic screens not working
with fully charged battery.
No visible component failures.
I don't have sufficient skills to do much more without a schematic [or probably even with a schematic].
Any hint on where to troubleshoot?
This a newer UPS which has gone through only 1 battery.
New battery is not recieving a charge; diagnostic screens not working
with fully charged battery.
No visible component failures.
I don't have sufficient skills to do much more without a schematic [or >probably even with a schematic].
Any hint on where to troubleshoot?
Thanks.
John Keiser <johnkeiser@juno.com> wrote:
This a newer UPS which has gone through only 1 battery.
New battery is not recieving a charge; diagnostic screens not
working with fully charged battery.
No visible component failures.
I don't have sufficient skills to do much more without a schematic
[or probably even with a schematic].
Any hint on where to troubleshoot?
I'd start by getting a manual. Downloads/Tripp-Lite-Owners-Manual-889464%20(2).pdf
Not much information, but it does say something about
"...press and hold the power button until the alarm..."
To my way of thinking that's rather unusual, I don't
usually hold buttons until something makes noise.
Beyond that, maybe look for fuses inside? The UPS units
I have are absolutely dead unless connected to a battery.
hth,
bob prohaska
On Sat, 13 Sep 2025 20:30:40 GMT, "John Keiser" <johnkeiser@juno.com>
wrote:
This a newer UPS which has gone through only 1 battery.
How long has the UPS been operational? If it killed "only" one
battery, I would guess 5 years.
New battery is not recieving a charge; diagnostic screens not
working with fully charged battery.
No visible component failures.
I don't have sufficient skills to do much more without a schematic
[or probably even with a schematic].
Any hint on where to troubleshoot?
Thanks.
I keep finding bulging electrolytic capacitors in such UPS's. You can visually see the bulging electrolytic capacitors but an ESR tester
will catch more of the smaller electrolytics. Examples:
This might help:
"p-lite SMART1000LCD not charging, no emergency power!"
Yes, that procedure worked in the past.
No joy now.