• Re: Grand Apagon - Electricity (not) in Spain

    From Carlos E.R.@21:1/5 to Bill Sloman on Thu May 1 21:50:29 2025
    On 2025-05-01 15:37, Bill Sloman wrote:
    On 30/04/2025 7:59 pm, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    ... pumped hydro storage has the spinning
    turbines, but grid scale batteries have invereters, which can reacta lot >>> faster than any spinning turbine,

    I thought the stabilising effect of a spinning turbine was because it
    *didn't* react quickly.

    The grid frequency begins to fall so energy from the moving parts is
    converted to electrical power which is fed into the grid to increase.
    the frequency.  This results in a loss of stored mechanical energy which
    causes the turbine to begin slowing down - which is detected by the
    control system and used to feed more water/gas/steam into the turbine so
    its speed is returned to normal.

    The interface between the stored mechanical energy and the electrical
    energy demand has an almost instant response and is inherently stable
    without needing elaborate control algorithms.

    But it isn't actually doing anything. Stabilising the frequency is all
    about feeding in more mechanical energy to compensate for the extra load.

    You can feed in electrical energy from a battery quite a lot faster, and
    get a correspondingly better result, if you've got the right elaborate control algorithm.

    Wouldn't it be just easier to switch to DC?

    Or to at least switch to islands, interconnected by DC.

    Probably not practical by now.


    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Martin Brown on Thu May 1 22:00:05 2025
    On 2025-04-30 20:55, Martin Brown wrote:
    On 29/04/2025 22:33, Carlos E.R. wrote:
    On 2025-04-29 14:24, Martin Brown wrote:

    Spain suffered a very spectacular near total loss of its national
    grid yesterday taking parts of France and all of Portugal down with
    it. This is an unprecedented failure of a supergrid system by cascade
    failure.

    (total loss in the peninsula)

    For those that can follow spoken Spanish, there has just been a
    detailed explanation on Radio Cadena Ser. Aimar Bretos interviewed
    Jorge Morales on Hora 25:

    «Director of Próxima Energía and expert in the energy sector.
    Entrepreneur and industrial engineer from the Polytechnic University
    of Madrid, he has more than 20 years of experience in the Spanish
    electricity sector.»

    Hi Carlos,

    For those of us that can't follow spoken Spanish at all please can you
    precis what he said was the root cause of failure? Options seem to be:

    No, that he didn't say. Not possible to say.



    1. France-Spain interconnect failure
    2. Cyber attack
    3. Human Error
    4. Exceptionally "Rare" atmospheric phenomena
    5. Flying pigs/unicorns [delete as appropriate]
    6. Other

    6, I guess. 2 is a possibility. 3 too, of course. 1 is not.

    That the interconnection to Europe is too small, is a factor. We could
    not rely on Europe for stabilization. Another factor, in reverse, was
    not isolating into small sections inside of Spain, some of them might
    have survived.


    Reuters still hasn't picked up on it at all. Latest is here:

    https://www.reuters.com/world/europe/sanchez-pressed-explain-spains- blackout-grid-says-solar-not-blame-2025-04-30/

    I'm not sure that I believe them.

    I'd stand a bit more of a chance chance with a text based page.
    Thanks.

    Sure, I'm waiting for a good one, letting others decide on which is a
    good one.



    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Joe Gwinn on Thu May 1 22:12:21 2025
    On 2025-04-30 23:28, Joe Gwinn wrote:
    On Tue, 29 Apr 2025 23:33:17 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:



    The Wall Street Journal just published an analysis. The authors are
    Spanish.

    How the Lights Went Out in Spain
    The country flew too close to the sun — which is to say it relied too heavily on unreliable solar power.

    The following link should not require a subscription.

    .<https://www.wsj.com/opinion/how-the-lights-went-out-in-spain-solar-power-electric-grid-0096bbc7?st=MbzSqb&reflink=desktopwebshare_permalink>

    I believe that one to be biased against renewable power.

    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to Martin Brown on Thu May 1 13:49:34 2025
    On 5/1/2025 10:25 AM, Martin Brown wrote:
    Our garage doors roll up and over (i.e., move from the vertical
    plane to the horizontal).  So, with the door open, about half of the
    ceiling is blocked (lights typically affixed to ceilings).

    Same here but my garage or perhaps I should say workshop is a double garage front with room for 4 cars in theory. Realistically only room for one and there
    is an inspection pit too although I have to syphon the water out of it before use. Water table is rather high round here.

    Back half is workspace with a bench, big vice, press drill and a lathe.

    We often work with the door open to improve access to vehicles -- roll
    the vehicle out into the driveway a bit so you have better access to
    all sides.

    This leaves all of the artificial light behind the vehicle (park nose
    facing out) where it does little good.

    [And, of course, you don't work on the vehicle during daylight hours as
    it's way too hot to be exposed in the sunlight, as that would require!]

    [[Of course, in the darkness, one has to worry about being "joined"
    by coyote, tarantula, javelina, bobcat, mountain lion... "youse takes
    yer chances"]]

    It also means the contents of the floor-to-ceiling, front-to-rear
    shelving are hard to see -- without taking the individual containing
    boxes off the shelf and transporting them to a location with more light.

    [Having worked for a large hand tool manufacturer, my "tool box" is
    on the order of 100+ cubic feet]

    My solution has been to install "cord reels" every 6 ft on each side and
    down the center of the garage. The free end (when retracted) rises above
    the plane of the garage door so is out of the way when opened. (ceilings
    are usually 10 ft in a residential garage, here) Yet, still reachable
    (if you are average height) when you want to pull one down for access.

    [These necessary as the walls are inaccessible due to the shelving]

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Martin Brown on Thu May 1 22:13:45 2025
    On 2025-04-29 14:24, Martin Brown wrote:
    Spain suffered a very spectacular near total loss of its national grid yesterday taking parts of France and all of Portugal down with it. This
    is an unprecedented failure of a supergrid system by cascade failure.

    I should say, although too late, that it should be "Gran Apagón" :-)

    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From piglet@21:1/5 to Jeroen Belleman on Thu May 1 21:50:45 2025
    Jeroen Belleman <jeroen@nospam.please> wrote:
    On 5/1/25 12:04, Martin Brown wrote:
    On 01/05/2025 01:36, Chris Jones wrote:
    On 30/04/2025 1:07 am, Martin Brown wrote:
    The idea that renewable sources make the grid frequency harder to
    manage sounds like total nonsense.

    It is pretty much accurate. The local feed in for domestic PV track
    whatever frequency they see on the network. The big problem is that
    without the large spinning generators and the energy stored in that
    angular momentum the frequency is able to shift rather too quickly.

    If the specifications for the inverters are written based on sound
    engineering and simulation of the grid behaviour rather than fear and
    ideology, it would be quite feasible to alter the algorithm in the PV
    inverters to help stabilise the grid frequency. For example, you could
    make it simulate what a spinning generator would do, or very likely
    something much better.

    I don't disagree that inverters at least on the bigger systems could be
    made to behave a lot more like a system that has physical inertia.

    I don't think it is viable for home units though since they are made
    down to a price and the robustness needed to oppose a frequency drift is
    not insignificant. They would be like a flea trying stop an elephant.

    I don't agree here. Since the power injected into the grid by
    large installations is regulated by looking at the frequency,
    once the grid gets dominated by, say, solar PV power, they'd
    better make sure it behaves the same way. Of course, any single
    small unit can't have a noticable effect, but collectively,
    they can!

    Jeroen Belleman


    It looks like most European inverter specs call for disconnect at 47Hz immediately and 47.5Hz within some tens of seconds but older models had to disconnect if the rate of change exceeded 0.2Hz/s but in an effort to
    improve stability newer requirements are to tolerate rate of change up to
    2Hz per second. Perhaps Spain has a large number of older spec inverters?

    This document goes into more detail:


    https://eepublicdownloads.entsoe.eu/clean-documents/SOC%20documents/Inertia%20and%20RoCoF_v17_clean.pdf

    --
    piglet

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Don Y on Thu May 1 23:28:36 2025
    On 2025-04-30 11:57, Don Y wrote:
    A *small* "whole home" generator is about 14KW.  OK if you are
    careful with your sequencing loads.  A normal home service is 24KW.

    A typical home in Spain (a flat) is typically limited to 3.45 KW. Mine
    is nominally limited to 2.3 Kw. Affluent or bigger homes could be 5.75KW.

    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Waldek Hebisch@21:1/5 to Joe Gwinn on Thu May 1 22:19:05 2025
    Joe Gwinn <joegwinn@comcast.net> wrote:
    On Tue, 29 Apr 2025 23:33:17 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-04-29 14:24, Martin Brown wrote:
    Spain suffered a very spectacular near total loss of its national grid
    yesterday taking parts of France and all of Portugal down with it. This
    is an unprecedented failure of a supergrid system by cascade failure.

    (total loss in the peninsula)

    For those that can follow spoken Spanish, there has just been a detailed >>explanation on Radio Cadena Ser. Aimar Bretos interviewed Jorge Morales
    on Hora 25:

    «Director of Próxima Energía and expert in the energy sector. >>Entrepreneur and industrial engineer from the Polytechnic University of >>Madrid, he has more than 20 years of experience in the Spanish
    electricity sector.»

    Direct link to mp3, starting from 31:30
    <https://25673.mc.tritondigital.com/HORA_25_CADENASER_320_P/media-session/9db9ab48-74f6-4fac-9b8f-ab24df840f9f/2025/4/29/cadenaser_hora25_20250429_210000_220000.mp3?dist=cadenaser-web-tfp-permanente&csegid=22000&dl=1>

    and:
    <https://25673.mc.tritondigital.com/HORA_25_CADENASER_320_P/media-session/a06f2199-cd2a-4ce5-8045-ba282565c2c0/2025/4/29/cadenaser_hora25_20250429_220000_230000.mp3?dist=cadenaser-web-tfp-permanente&csegid=22000&dl=1>


    Or, if that fails:
    <https://cadenaser.com/audio/cadenaser_hora25_20250429_210000_220000/?ssm=whatsapp>

    Continues on
    <https://cadenaser.com/audio/cadenaser_hora25_20250429_220000_230000/?ssm=whatsapp>



    Waiting for the podcast to appear [...] got it.
    <https://cadenaser.com/nacional/2025/04/29/se-puede-repetir-el-apagon-un-experto-responde-la-duda-tras-la-caida-de-la-red-electrica-cadena-ser/?ssm=whatsapp>


    The Wall Street Journal just published an analysis. The authors are
    Spanish.

    How the Lights Went Out in Spain
    The country flew too close to the sun ? which is to say it relied too
    heavily on unreliable solar power.

    The following link should not require a subscription.

    .<https://www.wsj.com/opinion/how-the-lights-went-out-in-spain-solar-power-electric-grid-0096bbc7?st=MbzSqb&reflink=desktopwebshare_permalink>

    Useless page:

    : Please enable JS and disable any ad blocker

    --
    Waldek Hebisch

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to Carlos E.R. on Thu May 1 15:16:27 2025
    On 5/1/2025 2:28 PM, Carlos E.R. wrote:
    On 2025-04-30 11:57, Don Y wrote:
    A *small* "whole home" generator is about 14KW.  OK if you are
    careful with your sequencing loads.  A normal home service is 24KW.

    A typical home in Spain (a flat) is typically limited to 3.45 KW. Mine is nominally limited to 2.3 Kw. Affluent or bigger homes could be 5.75KW.

    A smaller home may have a 60A service (~14KW). The 100A service
    (24KW) tends to be the norm (in older developments). Newer homes
    have 200A services (48KW).

    We tend to be bigger energy consumers than the rest of the world
    (i.e., "pigs").

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Gerhard Hoffmann@21:1/5 to All on Fri May 2 00:35:15 2025
    Am 01.05.25 um 23:28 schrieb Carlos E.R.:
    On 2025-04-30 11:57, Don Y wrote:
    A *small* "whole home" generator is about 14KW.  OK if you are
    careful with your sequencing loads.  A normal home service is 24KW.

    A typical home in Spain (a flat) is typically limited to 3.45 KW. Mine
    is nominally limited to 2.3 Kw. Affluent or bigger homes could be 5.75KW.

    The induction oven in my kitchen can apply 7.5 KW to the 2 front plates
    The back burners are OFF then. It's a good idea not to leave the kitchen
    when thusly used. A large pot with noodle water can change to a volcano
    in no time. :-)
    It is connected to the grid via 2 of the 3 phases of 240V. Dish washer,
    hot water, washing machine.. are extra.

    The house fuses are 3*50A @ 240V, not intended for replacement by
    customer. Nothing special here.
    Now if one would switch from star to triangle config @ 400V ...
    Car chargers might use that some day?

    Cheers, Gerhard

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Joe Gwinn@21:1/5 to robin_listas@es.invalid on Thu May 1 19:38:35 2025
    On Thu, 1 May 2025 22:12:21 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-04-30 23:28, Joe Gwinn wrote:
    On Tue, 29 Apr 2025 23:33:17 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:



    The Wall Street Journal just published an analysis. The authors are
    Spanish.

    How the Lights Went Out in Spain
    The country flew too close to the sun ù which is to say it relied too
    heavily on unreliable solar power.

    The following link should not require a subscription.

    .<https://www.wsj.com/opinion/how-the-lights-went-out-in-spain-solar-power-electric-grid-0096bbc7?st=MbzSqb&reflink=desktopwebshare_permalink>

    I believe that one to be biased against renewable power.

    The WSJ is one of the main newspapers of the Finance world. The UK
    equivalent is the Financial Times, although FT's politics are closer
    to the EU than the US.

    Anyway, the Finance folk worry about profit and loss, and so are not
    against renewable power per se.

    What they are against is mandating and subsidizing: If X is such a
    good idea, it will just take over naturally, without requiring
    mandates and subsidies. So they will question X, whatever it happens
    to be. Just stop all government actions there, and let the market
    settle the issue.

    Circling back, basically, the engineering numbers don't work. It's
    easy to show that decarbonizing cannot work, as the total CO2 content
    of the atmosphere is simply immense, and there is 50 times that much
    stored in the ocean deeps. And China is building coal plans as fast
    as they can, so we (US+UK+EU) are a roundoff error compared to China
    et al.

    Joe

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Joe Gwinn@21:1/5 to Hebisch on Thu May 1 19:21:25 2025
    On Thu, 1 May 2025 22:19:05 -0000 (UTC), antispam@fricas.org (Waldek
    Hebisch) wrote:

    Joe Gwinn <joegwinn@comcast.net> wrote:
    On Tue, 29 Apr 2025 23:33:17 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-04-29 14:24, Martin Brown wrote:
    Spain suffered a very spectacular near total loss of its national grid >>>> yesterday taking parts of France and all of Portugal down with it. This >>>> is an unprecedented failure of a supergrid system by cascade failure.

    (total loss in the peninsula)

    For those that can follow spoken Spanish, there has just been a detailed >>>explanation on Radio Cadena Ser. Aimar Bretos interviewed Jorge Morales >>>on Hora 25:

    ½Director of Pr≤xima Energøa and expert in the energy sector. >>>Entrepreneur and industrial engineer from the Polytechnic University of >>>Madrid, he has more than 20 years of experience in the Spanish >>>electricity sector.╗

    Direct link to mp3, starting from 31:30
    <https://25673.mc.tritondigital.com/HORA_25_CADENASER_320_P/media-session/9db9ab48-74f6-4fac-9b8f-ab24df840f9f/2025/4/29/cadenaser_hora25_20250429_210000_220000.mp3?dist=cadenaser-web-tfp-permanente&csegid=22000&dl=1>

    and:
    <https://25673.mc.tritondigital.com/HORA_25_CADENASER_320_P/media-session/a06f2199-cd2a-4ce5-8045-ba282565c2c0/2025/4/29/cadenaser_hora25_20250429_220000_230000.mp3?dist=cadenaser-web-tfp-permanente&csegid=22000&dl=1>


    Or, if that fails:
    <https://cadenaser.com/audio/cadenaser_hora25_20250429_210000_220000/?ssm=whatsapp>

    Continues on
    <https://cadenaser.com/audio/cadenaser_hora25_20250429_220000_230000/?ssm=whatsapp>



    Waiting for the podcast to appear [...] got it.
    <https://cadenaser.com/nacional/2025/04/29/se-puede-repetir-el-apagon-un-experto-responde-la-duda-tras-la-caida-de-la-red-electrica-cadena-ser/?ssm=whatsapp>


    The Wall Street Journal just published an analysis. The authors are
    Spanish.

    How the Lights Went Out in Spain
    The country flew too close to the sun ? which is to say it relied too
    heavily on unreliable solar power.

    The following link should not require a subscription.

    .<https://www.wsj.com/opinion/how-the-lights-went-out-in-spain-solar-power-electric-grid-0096bbc7?st=MbzSqb&reflink=desktopwebshare_permalink>

    Useless page:

    : Please enable JS and disable any ad blocker

    I subscribe to the WSJ, which is why I can "gift" an article to a
    newsgroup. Otherwise, full paywall, so pretty much inaccessible.

    The WSJ's business rationale for allowing this is to find new
    subscribers.

    Joe

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to Gerhard Hoffmann on Thu May 1 16:38:39 2025
    On 5/1/2025 3:35 PM, Gerhard Hoffmann wrote:
    Am 01.05.25 um 23:28 schrieb Carlos E.R.:
    On 2025-04-30 11:57, Don Y wrote:
    A *small* "whole home" generator is about 14KW.  OK if you are
    careful with your sequencing loads.  A normal home service is 24KW.

    A typical home in Spain (a flat) is typically limited to 3.45 KW. Mine is
    nominally limited to 2.3 Kw. Affluent or bigger homes could be 5.75KW.

    The induction oven in my kitchen can apply 7.5 KW to the 2 front plates
    The back burners are OFF then. It's a good idea not to leave the kitchen when thusly used. A large pot with noodle water can change to a volcano
    in no time.  :-)

    Our stovetop (4 burners plus "warmer" can draw 9100W. This, in addition
    to the 8300W in the oven, below.

    This, despite being fused at 9600W. Presumably, the controls contain sufficient "smarts" to ensure an overly zealous cook doesn't blow
    those fuses (the branch circuit is fused at 12000W).

    [I wonder if it displays a message when you approach the available
    power limit? Not a good experiment to attempt when it's this
    hot outside...]

    I noted that some induction cooktops had design limitations
    restricting how many "burners" could be active. One would have
    hoped they would be able to time-division multiplex the
    application of power to allow for all heat sources to be in use.

    It is connected to the grid via 2 of the 3 phases of 240V. Dish washer,
    hot water, washing machine.. are extra.

    The house fuses are 3*50A @ 240V, not intended for replacement by customer. Nothing special here.
    Now if one would switch from star to triangle config @ 400V ...
    Car chargers might use that some day?

    Cheers, Gerhard

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Don Y on Fri May 2 02:56:46 2025
    On 2025-05-02 01:38, Don Y wrote:

    I noted that some induction cooktops had design limitations
    restricting how many "burners" could be active.  One would have
    hoped they would be able to time-division multiplex the
    application of power to allow for all heat sources to be in use.

    Some do. I have seen some stoves that limit the total load, and allow
    the user to configure that limit. Not the number of burners.

    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Don Y on Fri May 2 02:54:39 2025
    On 2025-05-02 00:16, Don Y wrote:
    On 5/1/2025 2:28 PM, Carlos E.R. wrote:
    On 2025-04-30 11:57, Don Y wrote:
    A *small* "whole home" generator is about 14KW.  OK if you are
    careful with your sequencing loads.  A normal home service is 24KW.

    A typical home in Spain (a flat) is typically limited to 3.45 KW. Mine
    is nominally limited to 2.3 Kw. Affluent or bigger homes could be 5.75KW.

    A smaller home may have a 60A service (~14KW).  The 100A service
    (24KW) tends to be the norm (in older developments).  Newer homes
    have 200A services (48KW).

    We tend to be bigger energy consumers than the rest of the world
    (i.e., "pigs").

    We can have as much as we want, as long as we pay. The monthly invoice
    has two basic parts: a variable part, proportional to the watts we
    actually use, and a fixed part, proportional to the maximum watts we
    contract to have. So if we say we want a fuse of 25A on house input, we
    pay 25 times K, a constant in euros.

    Thus it pays to have a small fuse. It is not a fuse, just a calibrated
    switch with a lead seal. Recently, it is some firmware in the smart meter.

    I don't know the reasoning for this system, but the distribution company
    can thus calibrate the maximum power needed, different from the
    statistical max power. If the entire city maxes on power and it goes
    down, we can sue. We contracted and pay for the maximum on the entire
    network!

    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to Carlos E.R. on Thu May 1 18:40:26 2025
    On 5/1/2025 5:56 PM, Carlos E.R. wrote:
    On 2025-05-02 01:38, Don Y wrote:

    I noted that some induction cooktops had design limitations
    restricting how many "burners" could be active.  One would have
    hoped they would be able to time-division multiplex the
    application of power to allow for all heat sources to be in use.

    Some do. I have seen some stoves that limit the total load, and allow the user
    to configure that limit. Not the number of burners.

    I was under the impression (without investigating) that some
    key bit of electronics was multiplexed between the burners,
    based on actual usage.

    Here, we often use the entire stovetop (4 burners plus warmer)
    AND have something in at least one of the ovens. I have assumed
    that the software "schedules" power distribution to meet the
    current (no pun) demands placed on the appliance.

    It would be interesting to test that limit and see if the
    stove is aware of it and what (if anything) it does to
    convey that limitation to us!

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to Carlos E.R. on Thu May 1 18:37:49 2025
    On 5/1/2025 5:54 PM, Carlos E.R. wrote:
    On 2025-05-02 00:16, Don Y wrote:
    On 5/1/2025 2:28 PM, Carlos E.R. wrote:
    On 2025-04-30 11:57, Don Y wrote:
    A *small* "whole home" generator is about 14KW.  OK if you are
    careful with your sequencing loads.  A normal home service is 24KW.

    A typical home in Spain (a flat) is typically limited to 3.45 KW. Mine is >>> nominally limited to 2.3 Kw. Affluent or bigger homes could be 5.75KW.

    A smaller home may have a 60A service (~14KW).  The 100A service
    (24KW) tends to be the norm (in older developments).  Newer homes
    have 200A services (48KW).

    We tend to be bigger energy consumers than the rest of the world
    (i.e., "pigs").

    We can have as much as we want, as long as we pay. The monthly invoice has two
    basic parts: a variable part, proportional to the watts we actually use, and a
    fixed part, proportional to the maximum watts we contract to have. So if we say
    we want a fuse of 25A on house input, we pay 25 times K, a constant in euros.

    Thus it pays to have a small fuse. It is not a fuse, just a calibrated switch with a lead seal. Recently, it is some firmware in the smart meter.

    Our "enforced limit" is determined by the ampacity of the actual
    wire feed to the house, further limited by the physical fusing.

    What we *pay* is based on what we use -- plus a fixed charge that
    applies to all similar residences. My "fixed charge" remains the
    same even if we spend the summer elsewhere (i.e., effectively NO
    power consumed). Similarly, I can run the air conditioner with
    the windows open (!) if I wanted to flaunt wealth.

    The problem comes when your peak needs start to encroach on
    the ampacity of the service that is feeding the residence.
    Upgrading that feed is costly as it requires opening a trench,
    inspections, disconnects and reconnects, etc.

    I don't know the reasoning for this system, but the distribution company can thus calibrate the maximum power needed, different from the statistical max power. If the entire city maxes on power and it goes down, we can sue. We contracted and pay for the maximum on the entire network!

    So, you pay for *capacity* in addition to usage. Here, the assumption
    is that there will always be "enough available" to suit your needs.

    [This has historically been true -- save for an outage with the
    natural gas supply a few years ago when demand exceeded the
    abilities of the pipelines to deliver fuel]

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Bill Sloman@21:1/5 to Joe Gwinn on Fri May 2 18:04:20 2025
    On 2/05/2025 9:38 am, Joe Gwinn wrote:
    On Thu, 1 May 2025 22:12:21 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-04-30 23:28, Joe Gwinn wrote:
    On Tue, 29 Apr 2025 23:33:17 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:



    The Wall Street Journal just published an analysis. The authors are
    Spanish.

    How the Lights Went Out in Spain
    The country flew too close to the sun — which is to say it relied too
    heavily on unreliable solar power.

    The following link should not require a subscription.

    .<https://www.wsj.com/opinion/how-the-lights-went-out-in-spain-solar-power-electric-grid-0096bbc7?st=MbzSqb&reflink=desktopwebshare_permalink>

    I believe that one to be biased against renewable power.

    The WSJ is one of the main newspapers of the Finance world. The UK equivalent is the Financial Times, although FT's politics are closer
    to the EU than the US.

    The Wall Street Journal may be "one of the main newspapers of the
    Finance world" but it s still owned by Rupert Murdoch, and he used it to
    keep his fossil carbon advertisers happy by publishing a lot of climate
    change denial propaganda. The financial world doesn't know much about
    science and couldn't care less.

    Anyway, the Finance folk worry about profit and loss, and so are not
    against renewable power per se.

    In fact they are in favour of it, because it is cheaper. The fact that
    it tends to be intermittent ought to worry them, but engineers are good
    at masking the intermittency with gear like quick-start gas-turbine
    power generators and - recently - grid scale batteries, so the financial
    world ignores what they know to be a soluble problem.

    What they are against is mandating and subsidizing: If X is such a
    good idea, it will just take over naturally, without requiring
    mandates and subsidies. So they will question X, whatever it happens
    to be. Just stop all government actions there, and let the market
    settle the issue.

    Good new ideas don't just take over naturally. People have to invest
    loads of money into the new systems, and governments are good at doing
    that. The natural route is via niche markets, where the new idea is particularly advantageous, and you scale up manufacturing progressively
    to let you exploit economies of scale to make the product cheap enough
    to compete in markets that are closer to the main stream, but it does
    take a while. Anthropogenic global warming is moving fast enough to
    justify investing serious money now to slow it down and eventually
    reverse it.

    Circling back, basically, the engineering numbers don't work. It's
    easy to show that decarbonizing cannot work, as the total CO2 content
    of the atmosphere is simply immense, and there is 50 times that much
    stored in the ocean deeps. And China is building coal plants as fast
    as they can, so we (US+UK+EU) are a roundoff error compared to China
    et al.

    China is investing a lot more in renewable generation that it is in
    replacing old and inefficient coal plants with modern, much more
    efficient coal plants, though it is still spending a lot on that.

    https://www.carbonbrief.org/chinas-construction-of-new-coal-power-plants-reached-10-year-high-in-2024/https://www.carbonbrief.org/chinas-construction-of-new-coal-power-plants-reached-10-year-high-in-2024/

    https://dialogue.earth/en/energy/chinas-renewables-push-fuels-coal-power-investment/

    China added 125GW of wind and solar generating capacity in 2022 compared
    with 146GW of new coal-fired capacity. In 2023 it only added 117GW of
    new coal fired capacity and was expected to add only 69GW in 2024.
    It did retired some old, inefficient cola-fired plants, but not all that
    much geerating capacity.

    They clearly aren't building new coal-fired plants "as fast as they can"
    though they are still building a lot of them.

    The reports make it clear that they have the same problem as the west -
    once you have built a coal-fired plant you want to keep on running it to collect the money from the customers who buy the power.

    --
    Bill Sloman, Sydney

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Martin Brown@21:1/5 to Bill Sloman on Fri May 2 11:03:55 2025
    On 01/05/2025 18:41, Bill Sloman wrote:
    On 2/05/2025 2:21 am, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    On 30/04/2025 7:59 pm, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    ... pumped hydro storage has the spinning
    turbines, but grid scale batteries have invereters, which can
    reacta lot
    faster than any spinning turbine,

    I thought the stabilising effect of a spinning turbine was because it
    *didn't* react quickly.

    The grid frequency begins to fall so energy from the moving parts is
    converted to electrical power which is fed into the grid to increase.
    the frequency.  This results in a loss of stored mechanical energy
    which
    causes the turbine to begin slowing down - which is detected by the
    control system and used to feed more water/gas/steam into the
    turbine so
    its speed is returned to normal.

    The interface between the stored mechanical energy and the electrical
    energy demand has an almost instant response and is inherently stable
    without needing elaborate control algorithms.

    But it isn't actually doing anything.

    Yes it is, basic electrical engineering theory.

    In effect it is a constant speed generator connected to variable load;
    increase the load and more electrical energy immediately flows into the
    load, taking mechanical energy from the inertia of the moving parts.
    They then begin to slow down and the much more heavily damped mechanical
    regulator feeds in more energy to them from the primary source.

    So it is completely passive. A big battery isn't a primary source but it
    can provide enough DC current to let your grid scale inverter generate exactly the AC output that you need.

    There is a surprising amount of kinetic energy that can be stored in a
    flywheel or other rotating piece of big heavy machinery. The grid has
    adopted large scale solar PV and wind farms with some very flaky
    inverter technology whose interractions are not at all well understood.

    One of the internal reports I was reading recently mentioned that they
    were thinking about funding a PhD to look into some of the complexities.
    It is pretty clear that the system is not well thought out.

    Why futz around with the rotating metal? It may entertain tourists, but that's really all that it is good for.

    Because it was always just there and now that it isn't the replacement inverters on many of the big installations are nowhere near good enough
    at simulating the required behaviour. They are too inclined to drop off
    and save themselves (much like nuclear plant also does). I suspect that
    Spain doesn't have a great deal of battery storage or pumped water.

    Based on the time it went tits up it seems likely that it failed due to
    too much power being forced into the network and not enough load of last
    resort or exports to France down the one puny cable they do have.

    UK's intermittent loads of last resort are also diminishing as steel
    works closed although it is never really sunny enough here to matter and
    wind turbines can be easily feathered (and paid handsomely to do SFA).
    There is really only the chloralkali plants at Runcorn left now.

    Silly electricity prices based on the wholesale price for gas have
    pretty much destroyed aluminium and steel making in the UK. Scotland has
    a couple hanging on by their fingernails hoping for a reprieve.

    --
    Martin Brown

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Martin Brown@21:1/5 to Carlos E.R. on Fri May 2 11:17:35 2025
    On 01/05/2025 20:50, Carlos E.R. wrote:
    On 2025-05-01 15:37, Bill Sloman wrote:

    You can feed in electrical energy from a battery quite a lot faster,
    and get a correspondingly better result, if you've got the right
    elaborate control algorithm.

    Wouldn't it be just easier to switch to DC?

    Some of the newer interconnectors are DC and GW capacity (boggle).

    Or to at least switch to islands, interconnected by DC.

    That was how they squared this circle in Japan where the NE are on UK
    mains at 50Hz and the SE are on US mains at 60Hz. Not surprisingly all
    Japanese kit will work quite happily at either frequency and their
    exports will also work on a huge voltage range too.

    There is quite an interesting magnetic deviation near big DC links.

    Probably not practical by now.

    No it is perfectly possible. I'm not sure how they do it.

    One of my mates worked on the civil engineering for the DC link in the
    Irish Sea. This Ireland to UK is 500MW.

    https://www.pv-magazine.com/2025/04/18/irish-uk-grids-linked-via-500-mw-greenlink-interconnector-subsea-cables/

    ISTR there is a N-S one in the Irish Sea rated at ~2GW and two more
    planned for the North Sea although the pylon routing for them on land
    has proved extremely controversial. Southern Nimby's want our northern electricity but they don't want any pylons blighting *their* landscape.

    --
    Martin Brown

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Martin Brown@21:1/5 to Carlos E.R. on Fri May 2 11:28:12 2025
    On 01/05/2025 21:13, Carlos E.R. wrote:
    On 2025-04-29 14:24, Martin Brown wrote:
    Spain suffered a very spectacular near total loss of its national grid
    yesterday taking parts of France and all of Portugal down with it.
    This is an unprecedented failure of a supergrid system by cascade
    failure.

    I should say, although too late, that it should be "Gran Apagón" :-)

    Sorry about that. I remember the phrase from my astronomy days when the
    Gran Canary were persuaded to go completely dark for one night only so
    that the Isaac Newton telescope on its peak could do something special.

    It gave everyone there an opportunity to see a truly dark sky.

    Links to it back in 1985 are now very thin on the ground. An article celebrating 10th anniversary is the best I can find in English page 31.
    (sorry its very big)

    --
    Martin Brown

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Tauno Voipio@21:1/5 to Gerhard Hoffmann on Fri May 2 14:59:21 2025
    On 2.5.2025 1.35, Gerhard Hoffmann wrote:
    Am 01.05.25 um 23:28 schrieb Carlos E.R.:
    On 2025-04-30 11:57, Don Y wrote:
    A *small* "whole home" generator is about 14KW.  OK if you are
    careful with your sequencing loads.  A normal home service is 24KW.

    A typical home in Spain (a flat) is typically limited to 3.45 KW. Mine
    is nominally limited to 2.3 Kw. Affluent or bigger homes could be 5.75KW.

    The induction oven in my kitchen can apply 7.5 KW to the 2 front plates
    The back burners are OFF then. It's a good idea not to leave the kitchen
    when thusly used. A large pot with noodle water can change to a volcano
    in no time.  :-)
    It is connected to the grid via 2 of the 3 phases of 240V. Dish washer,
    hot water, washing machine.. are extra.

    The house fuses are 3*50A @ 240V, not intended for replacement by
    customer. Nothing special here.
    Now if one would switch from star to triangle config @ 400V ...
    Car chargers might use that some day?

    Cheers, Gerhard

    The ISO Type 2 car chargers do it. The maximum is 3 * 400 / 230V at
    32A / phase. The charger and car can negotiate less, my Polestar
    uses max 3 * 16A.

    There are cars that use only 1 phase, or even only 2 phases,
    effectively using only one main phase between the phase inputs.

    --

    -TV

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Bill Sloman@21:1/5 to Martin Brown on Fri May 2 21:50:27 2025
    On 2/05/2025 8:03 pm, Martin Brown wrote:
    On 01/05/2025 18:41, Bill Sloman wrote:
    On 2/05/2025 2:21 am, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    On 30/04/2025 7:59 pm, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    <snip>

    So it is completely passive. A big battery isn't a primary source but
    it can provide enough DC current to let your grid scale inverter
    generate exactly the AC output that you need.

    There is a surprising amount of kinetic energy that can be stored in a flywheel or other rotating piece of big heavy machinery.

    https://en.wikipedia.org/wiki/Mark_Oliphant

    His homopolar generator, finally built in Canberra, is a spectacular
    example.

    "In 1955, Oliphant initiated the design and construction of a 500
    megajoule homopolar generator (HPG), the world's largest. This massive
    machine contained three discs 3.5 metres (11 ft) in diameter and
    weighing 38 tonnes (37 long tons). He obtained £40,000 (equivalent to A$3,000,000 in 2022) initial funding from the Australian Atomic Energy Commission.[82] Completed in 1963, the HPG was intended to be the power
    source for a synchrotron, but this was not built.[83] Instead, it was
    used to power the LT-4 Tokamak and a large-scale railgun that was used
    as a scientific instrument for experiments with plasma physics. It was decommissioned in 1985.

    It started off with sodium-potassium liquid metal brushes, but after an unfortunate explosion they get replaced with big carbon brushes that
    worked fine.

    The grid has adopted large scale solar PV and wind farms with some very flaky inverter technology whose interractions are not at all well
    understood.

    Which is to say that the engineers who designed them didn't know as much
    about what they doing as they should have done.

    The 2017 Hornsdale Reserve grid scale battery seems to have been better engineered. About half it's capacity is devoted to maintaining the cycle
    by cycle stability of the South Australian grid, and it hasn't fallen
    over yet.
    One of the internal reports I was reading recently mentioned that they
    were thinking about funding a PhD to look into some of the complexities.
    It is pretty clear that the system is not well thought out.

    That might be an overkill, but it would be a cheap way to get a decent literature search. A bit hard on the poor graduate student who got stuck
    with doing it - researching the hell out of problem that has been solved elsewhere isn't a royal road to publishable research results.

    Why futz around with the rotating metal? It may entertain tourists,
    but that's really all that it is good for.

    Because it was always just there and now that it isn't the replacement inverters on many of the big installations are nowhere near good enough
    at simulating the required behaviour. They are too inclined to drop off
    and save themselves (much like nuclear plant also does). I suspect that
    Spain doesn't have a great deal of battery storage or pumped water.

    Dropping out and saving themselves may be an easy design choice, but the designer should be able to do better. Whoever designed the Hornsdale
    reserve hardware does seem to have done better.

    Based on the time it went tits up it seems likely that it failed due to
    too much power being forced into the network and not enough load of last resort or exports to France down the one puny cable they do have.

    Grid scale batteries can soak up a lot of power - at least for a short
    while.

    UK's intermittent loads of last resort are also diminishing as steel
    works closed although it is never really sunny enough here to matter and
    wind turbines can be easily feathered (and paid handsomely to do SFA).
    There is really only the chloralkali plants at Runcorn left now.

    Silly electricity prices based on the wholesale price for gas have
    pretty much destroyed aluminium and steel making in the UK. Scotland has
    a couple hanging on by their fingernails hoping for a reprieve.

    Intermittent power sources demand grid scale storage. The UK has had

    https://en.wikipedia.org/wiki/Dinorwig_Power_Station

    since 1984. The wikipedia page talks about planned follow ups, but it's
    all a bit too complicated for the UK civil service.

    --
    Bill Sloman, Sydney

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Chris Jones@21:1/5 to Liz Tuddenham on Fri May 2 22:50:06 2025
    On 1/05/2025 8:24 pm, Liz Tuddenham wrote:
    Chris Jones <lugnut808@spam.yahoo.com> wrote:


    There is nothing magic about the current from a rotating generator that
    cannot be exactly replicated by an inverter ...

    Inertia. Not magic but physics. A store of energy that can be drawn
    on instantly for several seconds. Only an inverter with a massive
    energy storage system could match that; domestic systems can't.

    If there is no battery, then yes, the inverter normally can't increase
    its power output above what the solar was already providing beforehand,
    just as a consequence of a frequency shift. A large and growing
    percentage of installations here have batteries. My next door
    neighbour's PV system has a battery, for example. Similarly, with just a firmware update my EV charger could reduce its current consumption in
    response to the frequency or rate of change of frequency, and this
    reduction in consumption would be equivalent to extra generation. If regulations would allow it, the EV could have a bidirectional charger,
    which could also replicate the effect of inertia.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From john larkin@21:1/5 to All on Fri May 2 07:45:34 2025
    On Thu, 1 May 2025 11:37:46 -0700, KevinJ93 <kevin_es@whitedigs.com>
    wrote:

    On 5/1/25 4:06 AM, Jeroen Belleman wrote:
    On 5/1/25 12:24, Liz Tuddenham wrote:
    Chris Jones <lugnut808@spam.yahoo.com> wrote:


    There is nothing magic about the current from a rotating generator that >>>> cannot be exactly replicated by an inverter ...

    Inertia.á Not magic but physics.áá A store of energy that can be drawn
    on instantly for several seconds.á Only an inverter with a massive
    energy storage system could match that; domestic systems can't.



    I'm convinced it's becoming necessary for small domestic systems
    to servo the injected power to the grid frequency, just as is done
    for large power plants. There is no need for massive storage; Each
    contributes what he is able to. I *do* think the dP/dF will need to
    be adjusted by some central authority to keep a stable system.

    Jeroen Belleman

    In California and many other states it is required that residential
    solar inverters adhere to Rule 21 (aka UL 1741).

    They have some simple rules that are intended to stabilize the grid
    where there are significant amounts of solar power.

    Below 60Hz and 245V the inverters are not restricted but as the
    frequency or voltage rises above the thresholds the inverters will
    curtail their output.

    As there is no energy storage in the inverters it is not possible to go >further and take power from the grid.

    Just pump it back into the solar cells. Return it to the sun.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From john larkin@21:1/5 to Liz Tuddenham on Fri May 2 07:43:29 2025
    On Thu, 1 May 2025 11:24:13 +0100, liz@poppyrecords.invalid.invalid
    (Liz Tuddenham) wrote:

    Chris Jones <lugnut808@spam.yahoo.com> wrote:


    There is nothing magic about the current from a rotating generator that
    cannot be exactly replicated by an inverter ...

    Inertia. Not magic but physics. A store of energy that can be drawn
    on instantly for several seconds. Only an inverter with a massive
    energy storage system could match that; domestic systems can't.

    A boiler full of superheated water stores a lot of energy too. And
    hydraulic steam valve actuators move fast.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Bill Sloman@21:1/5 to john larkin on Sat May 3 00:53:32 2025
    On 3/05/2025 12:45 am, john larkin wrote:
    On Thu, 1 May 2025 11:37:46 -0700, KevinJ93 <kevin_es@whitedigs.com>
    wrote:

    On 5/1/25 4:06 AM, Jeroen Belleman wrote:
    On 5/1/25 12:24, Liz Tuddenham wrote:
    Chris Jones <lugnut808@spam.yahoo.com> wrote:


    There is nothing magic about the current from a rotating generator that >>>>> cannot be exactly replicated by an inverter ...

    Inertia.  Not magic but physics.   A store of energy that can be drawn >>>> on instantly for several seconds.  Only an inverter with a massive
    energy storage system could match that; domestic systems can't.



    I'm convinced it's becoming necessary for small domestic systems
    to servo the injected power to the grid frequency, just as is done
    for large power plants. There is no need for massive storage; Each
    contributes what he is able to. I *do* think the dP/dF will need to
    be adjusted by some central authority to keep a stable system.

    Jeroen Belleman

    In California and many other states it is required that residential
    solar inverters adhere to Rule 21 (aka UL 1741).

    They have some simple rules that are intended to stabilize the grid
    where there are significant amounts of solar power.

    Below 60Hz and 245V the inverters are not restricted but as the
    frequency or voltage rises above the thresholds the inverters will
    curtail their output.

    As there is no energy storage in the inverters it is not possible to go
    further and take power from the grid.

    Just pump it back into the solar cells. Return it to the sun.

    Light-emitting diodes do act as rather ineffective photocells. I'm not
    sure that solar cells are much good as light-emitting diodes. They
    certainly won't be narrow angle emitters, so the sun wouldn't get much
    benefit out of it.

    --
    Bill Sloman, Sydney

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Bill Sloman@21:1/5 to john larkin on Sat May 3 00:56:18 2025
    On 3/05/2025 12:43 am, john larkin wrote:
    On Thu, 1 May 2025 11:24:13 +0100, liz@poppyrecords.invalid.invalid
    (Liz Tuddenham) wrote:

    Chris Jones <lugnut808@spam.yahoo.com> wrote:


    There is nothing magic about the current from a rotating generator that
    cannot be exactly replicated by an inverter ...

    Inertia. Not magic but physics. A store of energy that can be drawn
    on instantly for several seconds. Only an inverter with a massive
    energy storage system could match that; domestic systems can't.

    A boiler full of superheated water stores a lot of energy too. And
    hydraulic steam valve actuators move fast.

    Not all that fast. 50Hz is probably more than they could track. 60Hz
    would be even more difficult.

    --
    Bill Sloman, Sydney

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Joe Gwinn@21:1/5 to robin_listas@es.invalid on Fri May 2 12:01:16 2025
    On Fri, 2 May 2025 02:54:39 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-02 00:16, Don Y wrote:
    On 5/1/2025 2:28 PM, Carlos E.R. wrote:
    On 2025-04-30 11:57, Don Y wrote:
    A *small* "whole home" generator is about 14KW.á OK if you are
    careful with your sequencing loads.á A normal home service is 24KW.

    A typical home in Spain (a flat) is typically limited to 3.45 KW. Mine
    is nominally limited to 2.3 Kw. Affluent or bigger homes could be 5.75KW. >>
    A smaller home may have a 60A service (~14KW).á The 100A service
    (24KW) tends to be the norm (in older developments).á Newer homes
    have 200A services (48KW).

    We tend to be bigger energy consumers than the rest of the world
    (i.e., "pigs").

    We can have as much as we want, as long as we pay. The monthly invoice
    has two basic parts: a variable part, proportional to the watts we
    actually use, and a fixed part, proportional to the maximum watts we
    contract to have. So if we say we want a fuse of 25A on house input, we
    pay 25 times K, a constant in euros.

    Thus it pays to have a small fuse. It is not a fuse, just a calibrated
    switch with a lead seal. Recently, it is some firmware in the smart meter.

    I don't know the reasoning for this system, but the distribution company
    can thus calibrate the maximum power needed, different from the
    statistical max power. If the entire city maxes on power and it goes
    down, we can sue. We contracted and pay for the maximum on the entire >network!

    We have a similar system in the US, basically used for all utilities,
    including piped natural gas, piped water, electrical power, in some
    areas piped steam or hot water, and so on.

    There is a charge that pays for the financial investment in equipment
    and systems to generate and provide your share to you. This cost
    varies only with the size of the physical part that connects you to
    those systems. This is not typically enforced using a fuse, depending
    mainly on the size and kind of use age meter that was ordered, and the
    size (in amps) of your main distribution panel (where the circuit
    breakers live).

    And there is a charge that varies with actual consumption, which
    reflects changes in the cost of what the utility is purchasing versus
    making.

    This is a perfectly rational scheme, because utilities are expensive
    both to build and to operate, but building and operating are different
    from a financial perspective.

    Joe

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Liz Tuddenham@21:1/5 to Bill Sloman on Fri May 2 17:49:48 2025
    Bill Sloman <bill.sloman@ieee.org> wrote:

    On 3/05/2025 12:43 am, john larkin wrote:
    On Thu, 1 May 2025 11:24:13 +0100, liz@poppyrecords.invalid.invalid
    (Liz Tuddenham) wrote:

    Chris Jones <lugnut808@spam.yahoo.com> wrote:


    There is nothing magic about the current from a rotating generator that >>> cannot be exactly replicated by an inverter ...

    Inertia. Not magic but physics. A store of energy that can be drawn
    on instantly for several seconds. Only an inverter with a massive
    energy storage system could match that; domestic systems can't.

    A boiler full of superheated water stores a lot of energy too. And hydraulic steam valve actuators move fast.

    Not all that fast. 50Hz is probably more than they could track. 60Hz
    would be even more difficult.

    They have no problem at a few cycles per second, as London Transport
    discovered in the early days of computers.

    London Transport was powered by Lotts Road Power Station. The load was
    mainly underground electric railways, trams and trolleybuses. but they
    took the electricity supply for their offices from there too. The first computer they installed kept crashing and the problem was traced to dips
    in the power supply rails.

    After a lot of investigation, they discovered that the AC mains supply
    had alternate (or perhaps every third) cycles much lower in voltage than
    the others (and I think there must have been a timing error too). The
    power supply smoothing capacitors were unable to store enough energy to
    tide them over the dips and the result was a regular dropping of the 'stabilised' supply rails.

    The fault was traced back to Lotts Road, where it was found that a steam
    valve was constantly cycling due to an unstable control loop. This
    hadn't had any effect on the trams, so nobody had bothered to do
    anything about it.

    Conclusion:
    A tram stores more energy than a computer capacitor bank.


    --
    ~ Liz Tuddenham ~
    (Remove the ".invalid"s and add ".co.uk" to reply)
    www.poppyrecords.co.uk

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From john larkin@21:1/5 to Liz Tuddenham on Fri May 2 13:41:07 2025
    On Fri, 2 May 2025 17:49:48 +0100, liz@poppyrecords.invalid.invalid
    (Liz Tuddenham) wrote:

    Bill Sloman <bill.sloman@ieee.org> wrote:

    On 3/05/2025 12:43 am, john larkin wrote:
    On Thu, 1 May 2025 11:24:13 +0100, liz@poppyrecords.invalid.invalid
    (Liz Tuddenham) wrote:

    Chris Jones <lugnut808@spam.yahoo.com> wrote:


    There is nothing magic about the current from a rotating generator that >> >>> cannot be exactly replicated by an inverter ...

    Inertia. Not magic but physics. A store of energy that can be drawn
    on instantly for several seconds. Only an inverter with a massive
    energy storage system could match that; domestic systems can't.

    A boiler full of superheated water stores a lot of energy too. And
    hydraulic steam valve actuators move fast.

    Not all that fast. 50Hz is probably more than they could track. 60Hz
    would be even more difficult.

    They have no problem at a few cycles per second, as London Transport >discovered in the early days of computers.

    London Transport was powered by Lotts Road Power Station. The load was >mainly underground electric railways, trams and trolleybuses. but they
    took the electricity supply for their offices from there too. The first >computer they installed kept crashing and the problem was traced to dips
    in the power supply rails.

    After a lot of investigation, they discovered that the AC mains supply
    had alternate (or perhaps every third) cycles much lower in voltage than
    the others (and I think there must have been a timing error too). The
    power supply smoothing capacitors were unable to store enough energy to
    tide them over the dips and the result was a regular dropping of the >'stabilised' supply rails.

    The fault was traced back to Lotts Road, where it was found that a steam >valve was constantly cycling due to an unstable control loop. This
    hadn't had any effect on the trams, so nobody had bothered to do
    anything about it.

    Conclusion:
    A tram stores more energy than a computer capacitor bank.

    I used to design steamship throttle and boiler control systems [1]. A
    steamship throttle valve hydraulic actuator is powered by low pressure
    oil (from a standby gravity tank) and slews in a few seconds. But
    serious high-pressure hydraulic actuators have multi-horsepower
    outputs and bandwidths of hundreds of Hz.

    A decent steam valve will nicely overlap the equivalent bandwidth of a
    big generator's inertia. Field control can be made fast too.

    Control engineers would be better at desiging stable power systems
    than greenie politicians.

    [1] Big ships are mostly diesels now.

    I was once stranded dead in the water in the Gulf Of Mexico/America,
    with maybe 100 other guys, on a LASH ship sea trial, when the main
    turbine steam valve actuator locked up and had to be disassembled and redesigned.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Martin Brown on Fri May 2 23:24:58 2025
    On 2025-05-02 12:17, Martin Brown wrote:
    On 01/05/2025 20:50, Carlos E.R. wrote:
    On 2025-05-01 15:37, Bill Sloman wrote:

    You can feed in electrical energy from a battery quite a lot faster,
    and get a correspondingly better result, if you've got the right
    elaborate control algorithm.

    Wouldn't it be just easier to switch to DC?

    Some of the newer interconnectors are DC and GW capacity (boggle).

    Or to at least switch to islands, interconnected by DC.

    That was how they squared this circle in Japan where the NE are on UK
    mains at 50Hz and the SE are on US mains at 60Hz. Not surprisingly all Japanese kit will work quite happily at either frequency and their
    exports will also work on a huge voltage range too.

    There is quite an interesting magnetic deviation near big DC links.

    I learned today that we can not isolate islands inside the country,
    because there are regions with a lot of demand and little generation,
    and other regions with a lot of generation and little demand. To do that
    would require separate transport.



    Probably not practical by now.

    No it is perfectly possible. I'm not sure how they do it.

    One of my mates worked on the civil engineering for the DC link in the
    Irish Sea. This Ireland to UK is 500MW.

    https://www.pv-magazine.com/2025/04/18/irish-uk-grids-linked-via-500-mw- greenlink-interconnector-subsea-cables/

    ISTR there is a N-S one in the Irish Sea rated at ~2GW and two more
    planned for the North Sea although the pylon routing for them on land
    has proved extremely controversial. Southern Nimby's want our northern electricity but they don't want any pylons blighting *their* landscape.


    Ah, yes, that happens.


    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Don Y on Fri May 2 23:20:57 2025
    On 2025-05-02 03:40, Don Y wrote:
    On 5/1/2025 5:56 PM, Carlos E.R. wrote:
    On 2025-05-02 01:38, Don Y wrote:

    I noted that some induction cooktops had design limitations
    restricting how many "burners" could be active.  One would have
    hoped they would be able to time-division multiplex the
    application of power to allow for all heat sources to be in use.

    Some do. I have seen some stoves that limit the total load, and allow
    the user to configure that limit. Not the number of burners.

    I was under the impression (without investigating) that some
    key bit of electronics was multiplexed between the burners,
    based on actual usage.

    They convert the input AC to DC. That part can be shared.


    Here, we often use the entire stovetop (4 burners plus warmer)
    AND have something in at least one of the ovens.  I have assumed
    that the software "schedules" power distribution to meet the
    current (no pun) demands placed on the appliance.

    It would be interesting to test that limit and see if the
    stove is aware of it and what (if anything) it does to
    convey that limitation to us!

    In my case, I have to be aware of everything that is using electricity
    in the house, and then select the power at the burner, and whether I can
    use both or not, or the microwave simultaneously.

    If I hit the limit, the electricity to the house is cut off, and the
    procedure to restore is a bit cumbersome.

    So far, I have never hit the limit.

    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Martin Brown on Fri May 2 23:30:32 2025
    On 2025-05-02 12:28, Martin Brown wrote:
    On 01/05/2025 21:13, Carlos E.R. wrote:
    On 2025-04-29 14:24, Martin Brown wrote:
    Spain suffered a very spectacular near total loss of its national
    grid yesterday taking parts of France and all of Portugal down with
    it. This is an unprecedented failure of a supergrid system by cascade
    failure.

    I should say, although too late, that it should be "Gran Apagón" :-)

    Sorry about that. I remember the phrase from my astronomy days when the
    Gran Canary were persuaded to go completely dark for one night only so
    that the Isaac Newton telescope on its peak could do something special.

    Don't worry :-)


    It gave everyone there an opportunity to see a truly dark sky.

    Links to it back in 1985 are now very thin on the ground. An article celebrating 10th anniversary is the best I can find in English page 31. (sorry its very big)



    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Martin Brown@21:1/5 to Carlos E.R. on Fri May 2 22:58:32 2025
    On 02/05/2025 22:24, Carlos E.R. wrote:
    On 2025-05-02 12:17, Martin Brown wrote:
    On 01/05/2025 20:50, Carlos E.R. wrote:

    Wouldn't it be just easier to switch to DC?

    Some of the newer interconnectors are DC and GW capacity (boggle).

    Or to at least switch to islands, interconnected by DC.

    That was how they squared this circle in Japan where the NE are on UK
    mains at 50Hz and the SE are on US mains at 60Hz. Not surprisingly all
    Japanese kit will work quite happily at either frequency and their
    exports will also work on a huge voltage range too.

    There is quite an interesting magnetic deviation near big DC links.

    I learned today that we can not isolate islands inside the country,
    because there are regions with a lot of demand and little generation,
    and other regions with a lot of generation and little demand. To do that would require separate transport.

    I don't understand. Surely the Spanish distribution system is pretty
    much like the UK one with maybe the transmission voltages different. The
    main super grid at 400kV and then various other big transmission lines
    at 275kV, 175kV and the lowest EHT at 33kV and circuit breakers so that
    local faults due to trees on the line or lightning strikes remain local.

    There should be a hierarchy of bigger isolators all the way back up the
    chain to drop out as much load as is needed to regain control. UK splash
    up failed because they hadn't allowed for domestic solar PV when they
    tried to shed load and it was very sunny.

    That may be the problem in Spain too. Failure at midday suggests
    oversupply and rising frequency rather than a power shortage.

    USians can't imagine using so little electricity as is the EU norm. The
    maximum amount that you use seems tiny even to me in the UK.

    Our 3kW kettle would blow your supply. Same in Japan.

    Probably not practical by now.

    No it is perfectly possible. I'm not sure how they do it.

    One of my mates worked on the civil engineering for the DC link in the
    Irish Sea. This Ireland to UK is 500MW.

    https://www.pv-magazine.com/2025/04/18/irish-uk-grids-linked-via-500-mw- greenlink-interconnector-subsea-cables/

    ISTR there is a N-S one in the Irish Sea rated at ~2GW and two more
    planned for the North Sea although the pylon routing for them on land
    has proved extremely controversial. Southern Nimby's want our northern
    electricity but they don't want any pylons blighting *their* landscape.

    I found a Wiki reference to the one my mate worked on 2.25GW :

    https://en.wikipedia.org/wiki/Western_HVDC_Link


    Ah, yes, that happens.

    A southern Nimby is worth ten in the north. UK PLC is run entirely for
    the benefit of Londoners and residents of the Home Counties.

    We generate insane amounts of electricity in the north (and always have
    done since coal fired power) now mostly offshore wind and in Scotland on
    shore. The links to the south where it is needed are sadly lacking.

    NESO couldn't run a piss up in a brewery.

    --
    Martin Brown

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From john larkin@21:1/5 to All on Fri May 2 15:40:32 2025
    On Fri, 02 May 2025 13:41:07 -0700, john larkin <jl@glen--canyon.com>
    wrote:

    On Fri, 2 May 2025 17:49:48 +0100, liz@poppyrecords.invalid.invalid
    (Liz Tuddenham) wrote:

    Bill Sloman <bill.sloman@ieee.org> wrote:

    On 3/05/2025 12:43 am, john larkin wrote:
    On Thu, 1 May 2025 11:24:13 +0100, liz@poppyrecords.invalid.invalid
    (Liz Tuddenham) wrote:

    Chris Jones <lugnut808@spam.yahoo.com> wrote:


    There is nothing magic about the current from a rotating generator that >>> >>> cannot be exactly replicated by an inverter ...

    Inertia. Not magic but physics. A store of energy that can be drawn >>> >> on instantly for several seconds. Only an inverter with a massive
    energy storage system could match that; domestic systems can't.

    A boiler full of superheated water stores a lot of energy too. And
    hydraulic steam valve actuators move fast.

    Not all that fast. 50Hz is probably more than they could track. 60Hz
    would be even more difficult.

    They have no problem at a few cycles per second, as London Transport >>discovered in the early days of computers.

    London Transport was powered by Lotts Road Power Station. The load was >>mainly underground electric railways, trams and trolleybuses. but they
    took the electricity supply for their offices from there too. The first >>computer they installed kept crashing and the problem was traced to dips
    in the power supply rails.

    After a lot of investigation, they discovered that the AC mains supply
    had alternate (or perhaps every third) cycles much lower in voltage than >>the others (and I think there must have been a timing error too). The >>power supply smoothing capacitors were unable to store enough energy to >>tide them over the dips and the result was a regular dropping of the >>'stabilised' supply rails.

    The fault was traced back to Lotts Road, where it was found that a steam >>valve was constantly cycling due to an unstable control loop. This
    hadn't had any effect on the trams, so nobody had bothered to do
    anything about it.

    Conclusion:
    A tram stores more energy than a computer capacitor bank.

    I used to design steamship throttle and boiler control systems [1]. A >steamship throttle valve hydraulic actuator is powered by low pressure
    oil (from a standby gravity tank) and slews in a few seconds. But
    serious high-pressure hydraulic actuators have multi-horsepower
    outputs and bandwidths of hundreds of Hz.

    A decent steam valve will nicely overlap the equivalent bandwidth of a
    big generator's inertia. Field control can be made fast too.

    Control engineers would be better at desiging stable power systems
    than greenie politicians.

    [1] Big ships are mostly diesels now.

    I was once stranded dead in the water in the Gulf Of Mexico/America,
    with maybe 100 other guys, on a LASH ship sea trial, when the main
    turbine steam valve actuator locked up and had to be disassembled and >redesigned.


    Of course a big generator can't sink power. If a few million people
    are incentivized to have rooftop solar and to get paid to push it back
    into the grid, and there's no way to stop them, things will get bad on
    a sunny afternoon.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to Carlos E.R. on Fri May 2 16:05:14 2025
    On 5/2/2025 2:20 PM, Carlos E.R. wrote:
    On 2025-05-02 03:40, Don Y wrote:
    On 5/1/2025 5:56 PM, Carlos E.R. wrote:
    On 2025-05-02 01:38, Don Y wrote:

    I noted that some induction cooktops had design limitations
    restricting how many "burners" could be active.  One would have
    hoped they would be able to time-division multiplex the
    application of power to allow for all heat sources to be in use.

    Some do. I have seen some stoves that limit the total load, and allow the >>> user to configure that limit. Not the number of burners.

    I was under the impression (without investigating) that some
    key bit of electronics was multiplexed between the burners,
    based on actual usage.

    They convert the input AC to DC. That part can be shared.

    I was thinking it was more than that; like the drive electronics
    were being shared (only installing enough to run two burners...
    yet allowing the user to decide WHICH two.)

    Here, we often use the entire stovetop (4 burners plus warmer)
    AND have something in at least one of the ovens.  I have assumed
    that the software "schedules" power distribution to meet the
    current (no pun) demands placed on the appliance.

    It would be interesting to test that limit and see if the
    stove is aware of it and what (if anything) it does to
    convey that limitation to us!

    In my case, I have to be aware of everything that is using electricity in the house, and then select the power at the burner, and whether I can use both or not, or the microwave simultaneously.

    It is not uncommon for older homes (that didn't anticipate all
    of the loads that would come along, over time) to "blow a breaker"
    (branch circuit) by temporarily exceeding it's limit. A neighbor
    used to blow a breaker when he turned on the "garbage disposal"
    while the microwave was running. I.e., a poor choice of load
    distributions.

    You are required to have two 20A (2400W derated to ~1800W) circuits
    for countertop appliances -- electric frying pans, toaster ovens,
    stand mixers, etc. This, an acknowledgement that there are
    many such loads that intermittently appear in a kitchen.

    The rest of the (kitchen's) wiring is not as highly prescribed.

    E.g., here, the refrigerator is on a dedicated (1800W derated to 1440W)
    circuit so no other load can trip it (food perishing). The garbage
    disposal, dishwasher, stove/oven (of course), microwave oven, etc.
    are all distributed around other circuits so no combination of
    their operations will trip a breaker.

    The required two counter circuits have been wired so alternating
    outlets are on the same branch circuit. In this way, you can know if
    the outlet you are about to use has any other loads currently attached (splitting the branch circuits "left" and "right" is a poor division
    as one tends to work in a particular AREA -- left/right -- so having
    a choice of two branch circuits in each area is more valuable)

    If I hit the limit, the electricity to the house is cut off, and the procedure
    to restore is a bit cumbersome.

    So far, I have never hit the limit.

    We would frequently exceed your limit -- just with the loads that
    normally cycle.

    My automation system will draw 3000W when fully deployed. Of course, the software is smart enough to adjust the actual load to the available
    power (solar sourced, no significant backup) so it can exploit any
    surplus of power and still not have large static demands.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to Carlos E.R. on Fri May 2 16:10:53 2025
    On 5/2/2025 2:24 PM, Carlos E.R. wrote:
    I learned today that we can not isolate islands inside the country, because there are regions with a lot of demand and little generation, and other regions
    with a lot of generation and little demand. To do that would require separate transport.

    Is there are practical reason why there is not enough (none?)
    generation in those areas? Or, have they just not made the
    investment?

    I.e., is there anything preventing them from FIXING this imbalance?

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From john larkin@21:1/5 to Liz Tuddenham on Fri May 2 16:20:48 2025
    On Fri, 2 May 2025 17:49:47 +0100, liz@poppyrecords.invalid.invalid
    (Liz Tuddenham) wrote:

    Bill Sloman <bill.sloman@ieee.org> wrote:

    On 3/05/2025 12:45 am, john larkin wrote:
    On Thu, 1 May 2025 11:37:46 -0700, KevinJ93 <kevin_es@whitedigs.com>
    wrote:

    On 5/1/25 4:06 AM, Jeroen Belleman wrote:
    On 5/1/25 12:24, Liz Tuddenham wrote:
    Chris Jones <lugnut808@spam.yahoo.com> wrote:


    There is nothing magic about the current from a rotating generator that
    cannot be exactly replicated by an inverter ...

    Inertia.  Not magic but physics.   A store of energy that can be drawn
    on instantly for several seconds.  Only an inverter with a massive
    energy storage system could match that; domestic systems can't.



    I'm convinced it's becoming necessary for small domestic systems
    to servo the injected power to the grid frequency, just as is done
    for large power plants. There is no need for massive storage; Each
    contributes what he is able to. I *do* think the dP/dF will need to
    be adjusted by some central authority to keep a stable system.

    Jeroen Belleman

    In California and many other states it is required that residential
    solar inverters adhere to Rule 21 (aka UL 1741).

    They have some simple rules that are intended to stabilize the grid
    where there are significant amounts of solar power.

    Below 60Hz and 245V the inverters are not restricted but as the
    frequency or voltage rises above the thresholds the inverters will
    curtail their output.

    As there is no energy storage in the inverters it is not possible to go >> >> further and take power from the grid.

    Just pump it back into the solar cells. Return it to the sun.

    Light-emitting diodes do act as rather ineffective photocells. I'm not
    sure that solar cells are much good as light-emitting diodes. They
    certainly won't be narrow angle emitters, so the sun wouldn't get much
    benefit out of it.

    They would probably light up brightly for a very short while if you
    pumped enough power into them.

    I'd imagine that 10 or so square meters of PN diodes, out in the fresh
    air, could dissipate a bunch of power. Certainly more than the panel
    usually generates.

    The controllers just aren't set up to work in that direction, nor is
    there usually a way to tell them to.

    Rooftop solar is kind of silly.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Bill Sloman@21:1/5 to john larkin on Sat May 3 14:10:40 2025
    On 3/05/2025 6:41 am, john larkin wrote:
    On Fri, 2 May 2025 17:49:48 +0100, liz@poppyrecords.invalid.invalid
    (Liz Tuddenham) wrote:

    Bill Sloman <bill.sloman@ieee.org> wrote:

    On 3/05/2025 12:43 am, john larkin wrote:
    On Thu, 1 May 2025 11:24:13 +0100, liz@poppyrecords.invalid.invalid
    (Liz Tuddenham) wrote:

    Chris Jones <lugnut808@spam.yahoo.com> wrote:


    There is nothing magic about the current from a rotating generator that >>>>>> cannot be exactly replicated by an inverter ...

    Inertia. Not magic but physics. A store of energy that can be drawn >>>>> on instantly for several seconds. Only an inverter with a massive
    energy storage system could match that; domestic systems can't.

    A boiler full of superheated water stores a lot of energy too. And
    hydraulic steam valve actuators move fast.

    Not all that fast. 50Hz is probably more than they could track. 60Hz
    would be even more difficult.

    They have no problem at a few cycles per second, as London Transport
    discovered in the early days of computers.

    London Transport was powered by Lotts Road Power Station. The load was
    mainly underground electric railways, trams and trolleybuses. but they
    took the electricity supply for their offices from there too. The first
    computer they installed kept crashing and the problem was traced to dips
    in the power supply rails.

    After a lot of investigation, they discovered that the AC mains supply
    had alternate (or perhaps every third) cycles much lower in voltage than
    the others (and I think there must have been a timing error too). The
    power supply smoothing capacitors were unable to store enough energy to
    tide them over the dips and the result was a regular dropping of the
    'stabilised' supply rails.

    The fault was traced back to Lotts Road, where it was found that a steam
    valve was constantly cycling due to an unstable control loop. This
    hadn't had any effect on the trams, so nobody had bothered to do
    anything about it.

    Conclusion:
    A tram stores more energy than a computer capacitor bank.

    I used to design steamship throttle and boiler control systems [1]. A steamship throttle valve hydraulic actuator is powered by low pressure
    oil (from a standby gravity tank) and slews in a few seconds. But
    serious high-pressure hydraulic actuators have multi-horsepower
    outputs and bandwidths of hundreds of Hz.

    A decent steam valve will nicely overlap the equivalent bandwidth of a
    big generator's inertia. Field control can be made fast too.

    Control engineers would be better at designing stable power systems
    than greenie politicians.

    Politicians don't design power systems. They subcontract that job to
    engineers. They may not give the work to the right engineers, but
    greenie politicians are unlikely to be any worse at picking contractors
    than any other kind of politician.

    [1] Big ships are mostly diesels now.

    I was once stranded dead in the water in the Gulf Of Mexico/America,
    with maybe 100 other guys, on a LASH ship sea trial, when the main
    turbine steam valve actuator locked up and had to be disassembled and redesigned.

    Doesn't sound as if they'd given the job to a good engineer.

    --
    Bill Sloman, Sydney

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Bill Sloman@21:1/5 to john larkin on Sat May 3 14:01:09 2025
    On 3/05/2025 9:20 am, john larkin wrote:
    On Fri, 2 May 2025 17:49:47 +0100, liz@poppyrecords.invalid.invalid
    (Liz Tuddenham) wrote:

    Bill Sloman <bill.sloman@ieee.org> wrote:

    On 3/05/2025 12:45 am, john larkin wrote:
    On Thu, 1 May 2025 11:37:46 -0700, KevinJ93 <kevin_es@whitedigs.com>
    wrote:

    On 5/1/25 4:06 AM, Jeroen Belleman wrote:
    On 5/1/25 12:24, Liz Tuddenham wrote:
    Chris Jones <lugnut808@spam.yahoo.com> wrote:


    There is nothing magic about the current from a rotating generator that
    cannot be exactly replicated by an inverter ...

    Inertia.  Not magic but physics.   A store of energy that can be drawn
    on instantly for several seconds.  Only an inverter with a massive >>>>>>> energy storage system could match that; domestic systems can't.



    I'm convinced it's becoming necessary for small domestic systems
    to servo the injected power to the grid frequency, just as is done >>>>>> for large power plants. There is no need for massive storage; Each >>>>>> contributes what he is able to. I *do* think the dP/dF will need to >>>>>> be adjusted by some central authority to keep a stable system.

    Jeroen Belleman

    In California and many other states it is required that residential
    solar inverters adhere to Rule 21 (aka UL 1741).

    They have some simple rules that are intended to stabilize the grid
    where there are significant amounts of solar power.

    Below 60Hz and 245V the inverters are not restricted but as the
    frequency or voltage rises above the thresholds the inverters will
    curtail their output.

    As there is no energy storage in the inverters it is not possible to go >>>>> further and take power from the grid.

    Just pump it back into the solar cells. Return it to the sun.

    Light-emitting diodes do act as rather ineffective photocells. I'm not
    sure that solar cells are much good as light-emitting diodes. They
    certainly won't be narrow angle emitters, so the sun wouldn't get much
    benefit out of it.

    They would probably light up brightly for a very short while if you
    pumped enough power into them.

    I'd imagine that 10 or so square meters of PN diodes, out in the fresh
    air, could dissipate a bunch of power. Certainly more than the panel
    usually generates.

    The controllers just aren't set up to work in that direction, nor is
    there usually a way to tell them to.

    Rooftop solar is kind of silly.

    About 30% of the roof-tops in Australia have it. It's a profitable
    investment. Adding a Tesla Powerwall or the like makes it a bigger
    investment, but about 40% of the most recent installations have them -
    the extra profit is worth having.

    Silly people don't tend to have that kind of money.

    --
    Bill Sloman, Sydney

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Bill Sloman@21:1/5 to john larkin on Sat May 3 14:19:46 2025
    On 3/05/2025 8:40 am, john larkin wrote:
    On Fri, 02 May 2025 13:41:07 -0700, john larkin <jl@glen--canyon.com>
    wrote:

    On Fri, 2 May 2025 17:49:48 +0100, liz@poppyrecords.invalid.invalid
    (Liz Tuddenham) wrote:

    Bill Sloman <bill.sloman@ieee.org> wrote:

    On 3/05/2025 12:43 am, john larkin wrote:
    On Thu, 1 May 2025 11:24:13 +0100, liz@poppyrecords.invalid.invalid
    (Liz Tuddenham) wrote:

    Chris Jones <lugnut808@spam.yahoo.com> wrote:


    There is nothing magic about the current from a rotating generator that >>>>>>> cannot be exactly replicated by an inverter ...

    Inertia. Not magic but physics. A store of energy that can be drawn >>>>>> on instantly for several seconds. Only an inverter with a massive >>>>>> energy storage system could match that; domestic systems can't.

    A boiler full of superheated water stores a lot of energy too. And
    hydraulic steam valve actuators move fast.

    Not all that fast. 50Hz is probably more than they could track. 60Hz
    would be even more difficult.

    They have no problem at a few cycles per second, as London Transport
    discovered in the early days of computers.

    London Transport was powered by Lotts Road Power Station. The load was
    mainly underground electric railways, trams and trolleybuses. but they
    took the electricity supply for their offices from there too. The first >>> computer they installed kept crashing and the problem was traced to dips >>> in the power supply rails.

    After a lot of investigation, they discovered that the AC mains supply
    had alternate (or perhaps every third) cycles much lower in voltage than >>> the others (and I think there must have been a timing error too). The
    power supply smoothing capacitors were unable to store enough energy to
    tide them over the dips and the result was a regular dropping of the
    'stabilised' supply rails.

    The fault was traced back to Lotts Road, where it was found that a steam >>> valve was constantly cycling due to an unstable control loop. This
    hadn't had any effect on the trams, so nobody had bothered to do
    anything about it.

    Conclusion:
    A tram stores more energy than a computer capacitor bank.

    I used to design steamship throttle and boiler control systems [1]. A
    steamship throttle valve hydraulic actuator is powered by low pressure
    oil (from a standby gravity tank) and slews in a few seconds. But
    serious high-pressure hydraulic actuators have multi-horsepower
    outputs and bandwidths of hundreds of Hz.

    A decent steam valve will nicely overlap the equivalent bandwidth of a
    big generator's inertia. Field control can be made fast too.

    Control engineers would be better at desiging stable power systems
    than greenie politicians.

    [1] Big ships are mostly diesels now.

    I was once stranded dead in the water in the Gulf Of Mexico/America,
    with maybe 100 other guys, on a LASH ship sea trial, when the main
    turbine steam valve actuator locked up and had to be disassembled and
    redesigned.


    Of course a big generator can't sink power. If a few million people
    are incentivized to have rooftop solar and to get paid to push it back
    into the grid, and there's no way to stop them, things will get bad on
    a sunny afternoon.

    In Australia, the utilities cut the price they'd pay for excess current generated by a roof-top solar set-up very early on.

    About 40% of new roof-top solar installation in Australia now include a
    Tesla Powerwall or a similar big battery, so the household can store
    excess energy until they need it. Not paying the utility rates for power
    that you use at night lets you pay off the whole installation over about
    seven years. Not dramatic, but well worth doing if you have the capital.

    --
    Bill Sloman, Sydney

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Chris Jones@21:1/5 to john larkin on Sat May 3 16:11:48 2025
    On 3/05/2025 12:45 am, john larkin wrote:
    On Thu, 1 May 2025 11:37:46 -0700, KevinJ93 <kevin_es@whitedigs.com>
    wrote:

    On 5/1/25 4:06 AM, Jeroen Belleman wrote:
    On 5/1/25 12:24, Liz Tuddenham wrote:
    Chris Jones <lugnut808@spam.yahoo.com> wrote:


    There is nothing magic about the current from a rotating generator that >>>>> cannot be exactly replicated by an inverter ...

    Inertia.  Not magic but physics.   A store of energy that can be drawn >>>> on instantly for several seconds.  Only an inverter with a massive
    energy storage system could match that; domestic systems can't.



    I'm convinced it's becoming necessary for small domestic systems
    to servo the injected power to the grid frequency, just as is done
    for large power plants. There is no need for massive storage; Each
    contributes what he is able to. I *do* think the dP/dF will need to
    be adjusted by some central authority to keep a stable system.

    Jeroen Belleman

    In California and many other states it is required that residential
    solar inverters adhere to Rule 21 (aka UL 1741).

    They have some simple rules that are intended to stabilize the grid
    where there are significant amounts of solar power.

    Below 60Hz and 245V the inverters are not restricted but as the
    frequency or voltage rises above the thresholds the inverters will
    curtail their output.

    As there is no energy storage in the inverters it is not possible to go
    further and take power from the grid.

    Just pump it back into the solar cells. Return it to the sun.

    Some systems do put power back into the solar cells, specifically if it
    is sunny but the panels are covered with snow. If it is sunny enough to
    be worth it, the panels can be electrically heated for a short time so
    the snow slides off and they can generate more than enough energy to
    repay what was used to loosen the snow.

    You could also use the PV modules as a load to dump energy if this is
    ever necessary to stabilise the grid, though doing so for long periods
    when it is very sunny might overheat them and shorten their life. At
    night it would work great though, (presuming someone else is paying you
    to use that power!). Conversely, solar panels run significantly cooler
    when delivering maximum power to the load, since these days they are
    nearly 25 percent efficient so when you disconnect the load, the extra
    energy has to go somewhere.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Martin Brown on Sat May 3 14:24:07 2025
    On 2025-05-02 12:03, Martin Brown wrote:
    On 01/05/2025 18:41, Bill Sloman wrote:
    On 2/05/2025 2:21 am, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    On 30/04/2025 7:59 pm, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    ... pumped hydro storage has the spinning
    turbines, but grid scale batteries have invereters, which can
    reacta lot
    faster than any spinning turbine,

    I thought the stabilising effect of a spinning turbine was because it >>>>> *didn't* react quickly.

    The grid frequency begins to fall so energy from the moving parts is >>>>> converted to electrical power which is fed into the grid to increase. >>>>> the frequency.  This results in a loss of stored mechanical energy
    which
    causes the turbine to begin slowing down - which is detected by the
    control system and used to feed more water/gas/steam into the
    turbine so
    its speed is returned to normal.

    The interface between the stored mechanical energy and the electrical >>>>> energy demand has an almost instant response and is inherently stable >>>>> without needing elaborate control algorithms.

    But it isn't actually doing anything.

    Yes it is, basic electrical engineering theory.

    In effect it is a constant speed generator connected to variable load;
    increase the load and more electrical energy immediately flows into the
    load, taking mechanical energy from the inertia of the moving parts.
    They then begin to slow down and the much more heavily damped mechanical >>> regulator feeds in more energy to them from the primary source.

    So it is completely passive. A big battery isn't a primary source but
    it can provide enough DC current to let your grid scale inverter
    generate exactly the AC output that you need.

    There is a surprising amount of kinetic energy that can be stored in a flywheel or other rotating piece of big heavy machinery. The grid has
    adopted large scale solar PV and wind farms with some very flaky
    inverter technology whose interractions are not at all well understood.

    One of the internal reports I was reading recently mentioned that they
    were thinking about funding a PhD to look into some of the complexities.
    It is pretty clear that the system is not well thought out.

    Why futz around with the rotating metal? It may entertain tourists,
    but that's really all that it is good for.

    Because it was always just there and now that it isn't the replacement inverters on many of the big installations are nowhere near good enough
    at simulating the required behaviour. They are too inclined to drop off
    and save themselves (much like nuclear plant also does). I suspect that
    Spain doesn't have a great deal of battery storage or pumped water.

    Network grade batteries, none, I believe. There are plans for water pump/generators. Some of the islands do have them.

    It seems that solar panels and wind farms mostly have the type of
    inverter that follow the shape of the voltage already in the grid, with detection to bail out if things go nuts. There is the suspicion that
    this was at least part of the problem.

    But there is another type of inverters that force the shape, ie,
    simulate inertia.

    And of course, large batteries on the network can be used to simulate
    very large inertia, much larger than mechanical generators. Minutes vs
    seconds, perhaps.




    Based on the time it went tits up it seems likely that it failed due to
    too much power being forced into the network and not enough load of last resort or exports to France down the one puny cable they do have.

    UK's intermittent loads of last resort are also diminishing as steel
    works closed although it is never really sunny enough here to matter and
    wind turbines can be easily feathered (and paid handsomely to do SFA).
    There is really only the chloralkali plants at Runcorn left now.

    Silly electricity prices based on the wholesale price for gas have
    pretty much destroyed aluminium and steel making in the UK. Scotland has
    a couple hanging on by their fingernails hoping for a reprieve.



    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Don Y on Sat May 3 14:37:12 2025
    On 2025-05-03 01:10, Don Y wrote:
    On 5/2/2025 2:24 PM, Carlos E.R. wrote:
    I learned today that we can not isolate islands inside the country,
    because there are regions with a lot of demand and little generation,
    and other regions with a lot of generation and little demand. To do
    that would require separate transport.

    Is there are practical reason why there is not enough (none?)
    generation in those areas?  Or, have they just not made the
    investment?

    Things happen.


    I.e., is there anything preventing them from FIXING this imbalance?


    Dunno.

    I'll try to expand some information, for you and Martin.

    In Andalucia and Extremadura (south and west of Spain) there are lots of
    rural areas that can accommodate huge solar plants, so lot of
    generation. On the other hand they don't have much of industry (not traditionally developed areas), so not much of demand (relatively).

    On the other hand, Madrid (centre of Spain) and Cataluña (north-east)
    have a lot of industries and less solar/wind generation.

    Nuclear generators are also mostly in the periphery, near the sea or big rivers. Not in the very densely populated Madrid (map here: <https://www.miteco.gob.es/es/energia/nuclear/centrales/espana.html>).

    Gas or oil generators? Also they don't abound in Madrid, the fuel has to
    be transported there.


    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From john larkin@21:1/5 to robin_listas@es.invalid on Sat May 3 08:12:54 2025
    On Sat, 3 May 2025 14:24:07 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-02 12:03, Martin Brown wrote:
    On 01/05/2025 18:41, Bill Sloman wrote:
    On 2/05/2025 2:21 am, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    On 30/04/2025 7:59 pm, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    ... pumped hydro storage has the spinning
    turbines, but grid scale batteries have invereters, which can
    reacta lot
    faster than any spinning turbine,

    I thought the stabilising effect of a spinning turbine was because it >>>>>> *didn't* react quickly.

    The grid frequency begins to fall so energy from the moving parts is >>>>>> converted to electrical power which is fed into the grid to increase. >>>>>> the frequency.á This results in a loss of stored mechanical energy >>>>>> which
    causes the turbine to begin slowing down - which is detected by the >>>>>> control system and used to feed more water/gas/steam into the
    turbine so
    its speed is returned to normal.

    The interface between the stored mechanical energy and the electrical >>>>>> energy demand has an almost instant response and is inherently stable >>>>>> without needing elaborate control algorithms.

    But it isn't actually doing anything.

    Yes it is, basic electrical engineering theory.

    In effect it is a constant speed generator connected to variable load; >>>> increase the load and more electrical energy immediately flows into the >>>> load, taking mechanical energy from the inertia of the moving parts.
    They then begin to slow down and the much more heavily damped mechanical >>>> regulator feeds in more energy to them from the primary source.

    So it is completely passive. A big battery isn't a primary source but
    it can provide enough DC current to let your grid scale inverter
    generate exactly the AC output that you need.

    There is a surprising amount of kinetic energy that can be stored in a
    flywheel or other rotating piece of big heavy machinery. The grid has
    adopted large scale solar PV and wind farms with some very flaky
    inverter technology whose interractions are not at all well understood.

    One of the internal reports I was reading recently mentioned that they
    were thinking about funding a PhD to look into some of the complexities.
    It is pretty clear that the system is not well thought out.

    Why futz around with the rotating metal? It may entertain tourists,
    but that's really all that it is good for.

    Because it was always just there and now that it isn't the replacement
    inverters on many of the big installations are nowhere near good enough
    at simulating the required behaviour. They are too inclined to drop off
    and save themselves (much like nuclear plant also does). I suspect that
    Spain doesn't have a great deal of battery storage or pumped water.

    Network grade batteries, none, I believe. There are plans for water >pump/generators. Some of the islands do have them.

    It seems that solar panels and wind farms mostly have the type of
    inverter that follow the shape of the voltage already in the grid, with >detection to bail out if things go nuts. There is the suspicion that
    this was at least part of the problem.

    But there is another type of inverters that force the shape, ie,
    simulate inertia.

    Where do they get the energy from?

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Bill Sloman@21:1/5 to john larkin on Sun May 4 03:20:48 2025
    On 4/05/2025 1:12 am, john larkin wrote:
    On Sat, 3 May 2025 14:24:07 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-02 12:03, Martin Brown wrote:
    On 01/05/2025 18:41, Bill Sloman wrote:
    On 2/05/2025 2:21 am, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    On 30/04/2025 7:59 pm, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    <snip>

    It seems that solar panels and wind farms mostly have the type of
    inverter that follow the shape of the voltage already in the grid, with
    detection to bail out if things go nuts. There is the suspicion that
    this was at least part of the problem.

    But there is another type of inverter that forces the shape, ie,
    simulate inertia.

    Where do they get the energy from?

    Solar panels and wind farms collect energy from sun and wind. To "force
    the shape" of the output waveform you might need a single cycle's worth
    of energy in a short term store, such as a capacitor.

    The distinction between a capacitor, a super-capacitor and a battery is essentially how long the energy is stored - you can store more energy
    per unit volume as you move towards the battery end of the series. The
    internal resistance goes up along the same axis.

    --
    Bill Sloman, Sydney

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Jeroen Belleman@21:1/5 to john larkin on Sat May 3 19:23:11 2025
    On 5/3/25 17:12, john larkin wrote:
    On Sat, 3 May 2025 14:24:07 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-02 12:03, Martin Brown wrote:
    On 01/05/2025 18:41, Bill Sloman wrote:
    On 2/05/2025 2:21 am, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    On 30/04/2025 7:59 pm, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    ... pumped hydro storage has the spinning
    turbines, but grid scale batteries have invereters, which can
    reacta lot
    faster than any spinning turbine,

    I thought the stabilising effect of a spinning turbine was because it >>>>>>> *didn't* react quickly.

    The grid frequency begins to fall so energy from the moving parts is >>>>>>> converted to electrical power which is fed into the grid to increase. >>>>>>> the frequency.  This results in a loss of stored mechanical energy >>>>>>> which
    causes the turbine to begin slowing down - which is detected by the >>>>>>> control system and used to feed more water/gas/steam into the
    turbine so
    its speed is returned to normal.

    The interface between the stored mechanical energy and the electrical >>>>>>> energy demand has an almost instant response and is inherently stable >>>>>>> without needing elaborate control algorithms.

    But it isn't actually doing anything.

    Yes it is, basic electrical engineering theory.

    In effect it is a constant speed generator connected to variable load; >>>>> increase the load and more electrical energy immediately flows into the >>>>> load, taking mechanical energy from the inertia of the moving parts. >>>>> They then begin to slow down and the much more heavily damped mechanical >>>>> regulator feeds in more energy to them from the primary source.

    So it is completely passive. A big battery isn't a primary source but
    it can provide enough DC current to let your grid scale inverter
    generate exactly the AC output that you need.

    There is a surprising amount of kinetic energy that can be stored in a
    flywheel or other rotating piece of big heavy machinery. The grid has
    adopted large scale solar PV and wind farms with some very flaky
    inverter technology whose interractions are not at all well understood.

    One of the internal reports I was reading recently mentioned that they
    were thinking about funding a PhD to look into some of the complexities. >>> It is pretty clear that the system is not well thought out.

    Why futz around with the rotating metal? It may entertain tourists,
    but that's really all that it is good for.

    Because it was always just there and now that it isn't the replacement
    inverters on many of the big installations are nowhere near good enough
    at simulating the required behaviour. They are too inclined to drop off
    and save themselves (much like nuclear plant also does). I suspect that
    Spain doesn't have a great deal of battery storage or pumped water.

    Network grade batteries, none, I believe. There are plans for water
    pump/generators. Some of the islands do have them.

    It seems that solar panels and wind farms mostly have the type of
    inverter that follow the shape of the voltage already in the grid, with
    detection to bail out if things go nuts. There is the suspicion that
    this was at least part of the problem.

    But there is another type of inverters that force the shape, ie,
    simulate inertia.

    Where do they get the energy from?


    To have a bit of margin to regulate, PV installations will have
    to either run somewhat below the bleeding edge, or to store a bit
    of energy in local batteries.

    Jeroen Belleman

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to All on Sat May 3 10:47:09 2025
    I.e., is there anything preventing them from FIXING this imbalance?

    In Andalucia and Extremadura (south and west of Spain) there are lots of rural
    areas that can accommodate huge solar plants, so lot of generation. On the other hand they don't have much of industry (not traditionally developed areas), so not much of demand (relatively).

    Understandable. This seems to mirror the situation Martin has mentioned
    in the UK (generation to the north, consumption in the south)

    On the other hand, Madrid (centre of Spain) and Cataluña (north-east) have a lot of industries and less solar/wind generation.

    Nuclear generators are also mostly in the periphery, near the sea or big

    For cooling.

    rivers. Not in the very densely populated Madrid (map here: <https://www.miteco.gob.es/es/energia/nuclear/centrales/espana.html>).

    Gas or oil generators? Also they don't abound in Madrid, the fuel has to be transported there.

    But, you can set up smaller PV installations (hundreds of panels)
    on commercial buildings, "cover" parking areas, etc. You don't
    get the same economies of scale as you would with 1,000 panels
    but 100+ panels on every city block makes a lot of power available
    where it is used.

    I suspect the pain hasn't been great enough to force them to
    take their medicine?

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From john larkin@21:1/5 to jeroen@nospam.please on Sat May 3 11:30:28 2025
    On Sat, 3 May 2025 19:23:11 +0200, Jeroen Belleman
    <jeroen@nospam.please> wrote:

    On 5/3/25 17:12, john larkin wrote:
    On Sat, 3 May 2025 14:24:07 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-02 12:03, Martin Brown wrote:
    On 01/05/2025 18:41, Bill Sloman wrote:
    On 2/05/2025 2:21 am, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    On 30/04/2025 7:59 pm, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    ... pumped hydro storage has the spinning
    turbines, but grid scale batteries have invereters, which can >>>>>>>>> reacta lot
    faster than any spinning turbine,

    I thought the stabilising effect of a spinning turbine was because it >>>>>>>> *didn't* react quickly.

    The grid frequency begins to fall so energy from the moving parts is >>>>>>>> converted to electrical power which is fed into the grid to increase. >>>>>>>> the frequency.á This results in a loss of stored mechanical energy >>>>>>>> which
    causes the turbine to begin slowing down - which is detected by the >>>>>>>> control system and used to feed more water/gas/steam into the
    turbine so
    its speed is returned to normal.

    The interface between the stored mechanical energy and the electrical >>>>>>>> energy demand has an almost instant response and is inherently stable >>>>>>>> without needing elaborate control algorithms.

    But it isn't actually doing anything.

    Yes it is, basic electrical engineering theory.

    In effect it is a constant speed generator connected to variable load; >>>>>> increase the load and more electrical energy immediately flows into the >>>>>> load, taking mechanical energy from the inertia of the moving parts. >>>>>> They then begin to slow down and the much more heavily damped mechanical >>>>>> regulator feeds in more energy to them from the primary source.

    So it is completely passive. A big battery isn't a primary source but >>>>> it can provide enough DC current to let your grid scale inverter
    generate exactly the AC output that you need.

    There is a surprising amount of kinetic energy that can be stored in a >>>> flywheel or other rotating piece of big heavy machinery. The grid has
    adopted large scale solar PV and wind farms with some very flaky
    inverter technology whose interractions are not at all well understood. >>>>
    One of the internal reports I was reading recently mentioned that they >>>> were thinking about funding a PhD to look into some of the complexities. >>>> It is pretty clear that the system is not well thought out.

    Why futz around with the rotating metal? It may entertain tourists,
    but that's really all that it is good for.

    Because it was always just there and now that it isn't the replacement >>>> inverters on many of the big installations are nowhere near good enough >>>> at simulating the required behaviour. They are too inclined to drop off >>>> and save themselves (much like nuclear plant also does). I suspect that >>>> Spain doesn't have a great deal of battery storage or pumped water.

    Network grade batteries, none, I believe. There are plans for water
    pump/generators. Some of the islands do have them.

    It seems that solar panels and wind farms mostly have the type of
    inverter that follow the shape of the voltage already in the grid, with
    detection to bail out if things go nuts. There is the suspicion that
    this was at least part of the problem.

    But there is another type of inverters that force the shape, ie,
    simulate inertia.

    Where do they get the energy from?


    To have a bit of margin to regulate, PV installations will have
    to either run somewhat below the bleeding edge, or to store a bit
    of energy in local batteries.

    Jeroen Belleman

    Most run at the MPPT point, so have no reserve to save the grid. And a
    lot of cloud cover or still wind will precipitate the very crisis that
    needs reserve.

    It doesn't make sense to me for a multi-country grid to depend on "a
    bit of energy stored" in household batteries and inverters for
    emergency reserve power.

    As the grids get greener, expect power to get less reliable and much
    more expensive. Hopefuilly the USA will use more NG, build more
    pipelines, and drill, baby, drill.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From KevinJ93@21:1/5 to Martin Brown on Sat May 3 11:20:46 2025
    On 4/29/25 12:32 PM, Martin Brown wrote:
    On 29/04/2025 18:52, Don Y wrote:
    On 4/29/2025 8:07 AM, Martin Brown wrote:

    They try very hard not to mention the fact that their load shedding
    algorithm was shedding a lot of local solar PV generation along with
    the load so that it was playing catch up and never quite getting there.

    Can they disconnect individual residential installations?

    In principle they can disconnect any residential installation with a
    smart meter (although they are normally prohibited from doing so). And
    anyone with a SMETS1 "smart" meter is wide open for a bad actor to flip
    their power on and off deliberately to bring the UK network down.

    https://www.bbc.co.uk/news/technology-22608085

    Unclear if the smart meters from that era that have become disabled by
    the customer changing supplier are still a hacker security risk or not.
    State actors would have no trouble hacking them...

    Some university researchers had no real bother!

    Or, just solar "farms"?

    They can drop out entire blocks of switchgear to take a given region or
    zone offline (as would happen if a fault condition trips a breaker).

    The big problem on a really sunny day is that an individual house roof
    4kW PV installation in late afternoon in the UK will be potentially
    exporting all of it to the grid. That is about 20-30 houses worth of electricity for each solar roof.

    They drop say 100MW of load or approx 500k houses @ 200W but with 2% of
    them generating 4kW then they also drop off 40MW of local generation.

    So the net load shedding is only 60MW which isn't enough to restore the balance and then the cycle repeats until it hits the low frequency total panic limiter. UK stopped it spreading by manual override dropping more
    than the algorithm wanted but leaving a big area without power.



    That doesn't make sense.

    In general it is not possible to centrally separate out residential
    solar from the residential loads so all they will see is a 60MW load,
    the 40MW local generation is invisible to them and is only apparent as a reduction in the load.


    It didn't help that by the time they did that the low frequency had put
    a lot of electric trains into a disabled state requiring a hard reset by
    a qualified service engineer visit and at random positions on the
    intercity train lines. The guys who could do that were in short supply.


    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Jeroen Belleman@21:1/5 to john larkin on Sat May 3 21:17:15 2025
    On 5/3/25 20:30, john larkin wrote:
    On Sat, 3 May 2025 19:23:11 +0200, Jeroen Belleman
    <jeroen@nospam.please> wrote:

    On 5/3/25 17:12, john larkin wrote:
    On Sat, 3 May 2025 14:24:07 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-02 12:03, Martin Brown wrote:
    On 01/05/2025 18:41, Bill Sloman wrote:
    On 2/05/2025 2:21 am, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    On 30/04/2025 7:59 pm, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    ... pumped hydro storage has the spinning
    turbines, but grid scale batteries have invereters, which can >>>>>>>>>> reacta lot
    faster than any spinning turbine,

    I thought the stabilising effect of a spinning turbine was because it >>>>>>>>> *didn't* react quickly.

    The grid frequency begins to fall so energy from the moving parts is >>>>>>>>> converted to electrical power which is fed into the grid to increase. >>>>>>>>> the frequency.  This results in a loss of stored mechanical energy >>>>>>>>> which
    causes the turbine to begin slowing down - which is detected by the >>>>>>>>> control system and used to feed more water/gas/steam into the >>>>>>>>> turbine so
    its speed is returned to normal.

    The interface between the stored mechanical energy and the electrical >>>>>>>>> energy demand has an almost instant response and is inherently stable >>>>>>>>> without needing elaborate control algorithms.

    But it isn't actually doing anything.

    Yes it is, basic electrical engineering theory.

    In effect it is a constant speed generator connected to variable load; >>>>>>> increase the load and more electrical energy immediately flows into the >>>>>>> load, taking mechanical energy from the inertia of the moving parts. >>>>>>> They then begin to slow down and the much more heavily damped mechanical
    regulator feeds in more energy to them from the primary source.

    So it is completely passive. A big battery isn't a primary source but >>>>>> it can provide enough DC current to let your grid scale inverter
    generate exactly the AC output that you need.

    There is a surprising amount of kinetic energy that can be stored in a >>>>> flywheel or other rotating piece of big heavy machinery. The grid has >>>>> adopted large scale solar PV and wind farms with some very flaky
    inverter technology whose interractions are not at all well understood. >>>>>
    One of the internal reports I was reading recently mentioned that they >>>>> were thinking about funding a PhD to look into some of the complexities. >>>>> It is pretty clear that the system is not well thought out.

    Why futz around with the rotating metal? It may entertain tourists, >>>>>> but that's really all that it is good for.

    Because it was always just there and now that it isn't the replacement >>>>> inverters on many of the big installations are nowhere near good enough >>>>> at simulating the required behaviour. They are too inclined to drop off >>>>> and save themselves (much like nuclear plant also does). I suspect that >>>>> Spain doesn't have a great deal of battery storage or pumped water.

    Network grade batteries, none, I believe. There are plans for water
    pump/generators. Some of the islands do have them.

    It seems that solar panels and wind farms mostly have the type of
    inverter that follow the shape of the voltage already in the grid, with >>>> detection to bail out if things go nuts. There is the suspicion that
    this was at least part of the problem.

    But there is another type of inverters that force the shape, ie,
    simulate inertia.

    Where do they get the energy from?


    To have a bit of margin to regulate, PV installations will have
    to either run somewhat below the bleeding edge, or to store a bit
    of energy in local batteries.

    Jeroen Belleman

    Most run at the MPPT point, so have no reserve to save the grid. And a
    lot of cloud cover or still wind will precipitate the very crisis that
    needs reserve.


    With the contribution of solar and wind being oblivious of demand,
    the burden of keeping the grid stable must be taken up by thermal
    or hydro power plants. When Spain's grid crashed, PV amounted to
    well over 50% of the total supply. It makes me wonder why it didn't
    crash sooner.

    Jeroen Belleman

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From john larkin@21:1/5 to jeroen@nospam.please on Sat May 3 13:39:05 2025
    On Sat, 3 May 2025 21:17:15 +0200, Jeroen Belleman
    <jeroen@nospam.please> wrote:

    On 5/3/25 20:30, john larkin wrote:
    On Sat, 3 May 2025 19:23:11 +0200, Jeroen Belleman
    <jeroen@nospam.please> wrote:

    On 5/3/25 17:12, john larkin wrote:
    On Sat, 3 May 2025 14:24:07 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-02 12:03, Martin Brown wrote:
    On 01/05/2025 18:41, Bill Sloman wrote:
    On 2/05/2025 2:21 am, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    On 30/04/2025 7:59 pm, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    ... pumped hydro storage has the spinning
    turbines, but grid scale batteries have invereters, which can >>>>>>>>>>> reacta lot
    faster than any spinning turbine,

    I thought the stabilising effect of a spinning turbine was because it
    *didn't* react quickly.

    The grid frequency begins to fall so energy from the moving parts is >>>>>>>>>> converted to electrical power which is fed into the grid to increase.
    the frequency.á This results in a loss of stored mechanical energy >>>>>>>>>> which
    causes the turbine to begin slowing down - which is detected by the >>>>>>>>>> control system and used to feed more water/gas/steam into the >>>>>>>>>> turbine so
    its speed is returned to normal.

    The interface between the stored mechanical energy and the electrical
    energy demand has an almost instant response and is inherently stable
    without needing elaborate control algorithms.

    But it isn't actually doing anything.

    Yes it is, basic electrical engineering theory.

    In effect it is a constant speed generator connected to variable load; >>>>>>>> increase the load and more electrical energy immediately flows into the
    load, taking mechanical energy from the inertia of the moving parts. >>>>>>>> They then begin to slow down and the much more heavily damped mechanical
    regulator feeds in more energy to them from the primary source. >>>>>>>
    So it is completely passive. A big battery isn't a primary source but >>>>>>> it can provide enough DC current to let your grid scale inverter >>>>>>> generate exactly the AC output that you need.

    There is a surprising amount of kinetic energy that can be stored in a >>>>>> flywheel or other rotating piece of big heavy machinery. The grid has >>>>>> adopted large scale solar PV and wind farms with some very flaky
    inverter technology whose interractions are not at all well understood. >>>>>>
    One of the internal reports I was reading recently mentioned that they >>>>>> were thinking about funding a PhD to look into some of the complexities. >>>>>> It is pretty clear that the system is not well thought out.

    Why futz around with the rotating metal? It may entertain tourists, >>>>>>> but that's really all that it is good for.

    Because it was always just there and now that it isn't the replacement >>>>>> inverters on many of the big installations are nowhere near good enough >>>>>> at simulating the required behaviour. They are too inclined to drop off >>>>>> and save themselves (much like nuclear plant also does). I suspect that >>>>>> Spain doesn't have a great deal of battery storage or pumped water. >>>>>
    Network grade batteries, none, I believe. There are plans for water
    pump/generators. Some of the islands do have them.

    It seems that solar panels and wind farms mostly have the type of
    inverter that follow the shape of the voltage already in the grid, with >>>>> detection to bail out if things go nuts. There is the suspicion that >>>>> this was at least part of the problem.

    But there is another type of inverters that force the shape, ie,
    simulate inertia.

    Where do they get the energy from?


    To have a bit of margin to regulate, PV installations will have
    to either run somewhat below the bleeding edge, or to store a bit
    of energy in local batteries.

    Jeroen Belleman

    Most run at the MPPT point, so have no reserve to save the grid. And a
    lot of cloud cover or still wind will precipitate the very crisis that
    needs reserve.


    With the contribution of solar and wind being oblivious of demand,
    the burden of keeping the grid stable must be taken up by thermal
    or hydro power plants. When Spain's grid crashed, PV amounted to
    well over 50% of the total supply. It makes me wonder why it didn't
    crash sooner.

    Jeroen Belleman

    I'm estimating that half the hazard is the actual physics, power and
    energy storage, and half is bad policy and inadequate control theory.

    A region should be able to isolate itself without bringing in the same
    boat with three or four other contries.

    We have the crazy situation in California where sometimes we have to
    buy coal-fired power from Nevada, and some times we have to *pay them*
    to take our excess power.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to john larkin on Sat May 3 23:55:17 2025
    On 2025-05-03 17:12, john larkin wrote:
    On Sat, 3 May 2025 14:24:07 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-02 12:03, Martin Brown wrote:
    On 01/05/2025 18:41, Bill Sloman wrote:
    On 2/05/2025 2:21 am, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    On 30/04/2025 7:59 pm, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    ... pumped hydro storage has the spinning
    turbines, but grid scale batteries have invereters, which can
    reacta lot
    faster than any spinning turbine,

    I thought the stabilising effect of a spinning turbine was because it >>>>>>> *didn't* react quickly.

    The grid frequency begins to fall so energy from the moving parts is >>>>>>> converted to electrical power which is fed into the grid to increase. >>>>>>> the frequency.  This results in a loss of stored mechanical energy >>>>>>> which
    causes the turbine to begin slowing down - which is detected by the >>>>>>> control system and used to feed more water/gas/steam into the
    turbine so
    its speed is returned to normal.

    The interface between the stored mechanical energy and the electrical >>>>>>> energy demand has an almost instant response and is inherently stable >>>>>>> without needing elaborate control algorithms.

    But it isn't actually doing anything.

    Yes it is, basic electrical engineering theory.

    In effect it is a constant speed generator connected to variable load; >>>>> increase the load and more electrical energy immediately flows into the >>>>> load, taking mechanical energy from the inertia of the moving parts. >>>>> They then begin to slow down and the much more heavily damped mechanical >>>>> regulator feeds in more energy to them from the primary source.

    So it is completely passive. A big battery isn't a primary source but
    it can provide enough DC current to let your grid scale inverter
    generate exactly the AC output that you need.

    There is a surprising amount of kinetic energy that can be stored in a
    flywheel or other rotating piece of big heavy machinery. The grid has
    adopted large scale solar PV and wind farms with some very flaky
    inverter technology whose interractions are not at all well understood.

    One of the internal reports I was reading recently mentioned that they
    were thinking about funding a PhD to look into some of the complexities. >>> It is pretty clear that the system is not well thought out.

    Why futz around with the rotating metal? It may entertain tourists,
    but that's really all that it is good for.

    Because it was always just there and now that it isn't the replacement
    inverters on many of the big installations are nowhere near good enough
    at simulating the required behaviour. They are too inclined to drop off
    and save themselves (much like nuclear plant also does). I suspect that
    Spain doesn't have a great deal of battery storage or pumped water.

    Network grade batteries, none, I believe. There are plans for water
    pump/generators. Some of the islands do have them.

    It seems that solar panels and wind farms mostly have the type of
    inverter that follow the shape of the voltage already in the grid, with
    detection to bail out if things go nuts. There is the suspicion that
    this was at least part of the problem.

    But there is another type of inverters that force the shape, ie,
    simulate inertia.

    Where do they get the energy from?

    Where does a gas turbine get the energy from?

    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to Carlos E.R. on Sat May 3 15:15:26 2025
    On 5/3/2025 2:59 PM, Carlos E.R. wrote:
    But, you can set up smaller PV installations (hundreds of panels)
    on commercial buildings, "cover" parking areas, etc.   You don't
    get the same economies of scale as you would with 1,000 panels
    but 100+ panels on every city block makes a lot of power available
    where it is used.

    There is a regulation that says that every building will have to install some solar panels. I don't know when is the limit.



    I suspect the pain hasn't been great enough to force them to
    take their medicine?

    Sorry, I don't understand this sentence. :-?

    Their "poor planning/engineering" hasn't COST them sufficiently for them
    to actually DO something about the problem! Perhaps now, with an entire
    nation *pissed*, they will decide they can't just wave their hands
    at the problem...

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Don Y on Sat May 3 23:59:59 2025
    On 2025-05-03 19:47, Don Y wrote:
    I.e., is there anything preventing them from FIXING this imbalance?

    In Andalucia and Extremadura (south and west of Spain) there are lots
    of rural areas that can accommodate huge solar plants, so lot of
    generation. On the other hand they don't have much of industry (not
    traditionally developed areas), so not much of demand (relatively).

    Understandable.  This seems to mirror the situation Martin has mentioned
    in the UK (generation to the north, consumption in the south)

    On the other hand, Madrid (centre of Spain) and Cataluña (north-east)
    have a lot of industries and less solar/wind generation.

    Nuclear generators are also mostly in the periphery, near the sea or big

    For cooling.

    rivers. Not in the very densely populated Madrid (map here: <https://
    www.miteco.gob.es/es/energia/nuclear/centrales/espana.html>).

    Gas or oil generators? Also they don't abound in Madrid, the fuel has
    to be transported there.

    But, you can set up smaller PV installations (hundreds of panels)
    on commercial buildings, "cover" parking areas, etc.   You don't
    get the same economies of scale as you would with 1,000 panels
    but 100+ panels on every city block makes a lot of power available
    where it is used.

    There is a regulation that says that every building will have to install
    some solar panels. I don't know when is the limit.



    I suspect the pain hasn't been great enough to force them to
    take their medicine?

    Sorry, I don't understand this sentence. :-?

    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From john larkin@21:1/5 to robin_listas@es.invalid on Sat May 3 16:53:42 2025
    On Sat, 3 May 2025 23:55:17 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-03 17:12, john larkin wrote:
    On Sat, 3 May 2025 14:24:07 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-02 12:03, Martin Brown wrote:
    On 01/05/2025 18:41, Bill Sloman wrote:
    On 2/05/2025 2:21 am, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    On 30/04/2025 7:59 pm, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    ... pumped hydro storage has the spinning
    turbines, but grid scale batteries have invereters, which can >>>>>>>>> reacta lot
    faster than any spinning turbine,

    I thought the stabilising effect of a spinning turbine was because it >>>>>>>> *didn't* react quickly.

    The grid frequency begins to fall so energy from the moving parts is >>>>>>>> converted to electrical power which is fed into the grid to increase. >>>>>>>> the frequency.á This results in a loss of stored mechanical energy >>>>>>>> which
    causes the turbine to begin slowing down - which is detected by the >>>>>>>> control system and used to feed more water/gas/steam into the
    turbine so
    its speed is returned to normal.

    The interface between the stored mechanical energy and the electrical >>>>>>>> energy demand has an almost instant response and is inherently stable >>>>>>>> without needing elaborate control algorithms.

    But it isn't actually doing anything.

    Yes it is, basic electrical engineering theory.

    In effect it is a constant speed generator connected to variable load; >>>>>> increase the load and more electrical energy immediately flows into the >>>>>> load, taking mechanical energy from the inertia of the moving parts. >>>>>> They then begin to slow down and the much more heavily damped mechanical >>>>>> regulator feeds in more energy to them from the primary source.

    So it is completely passive. A big battery isn't a primary source but >>>>> it can provide enough DC current to let your grid scale inverter
    generate exactly the AC output that you need.

    There is a surprising amount of kinetic energy that can be stored in a >>>> flywheel or other rotating piece of big heavy machinery. The grid has
    adopted large scale solar PV and wind farms with some very flaky
    inverter technology whose interractions are not at all well understood. >>>>
    One of the internal reports I was reading recently mentioned that they >>>> were thinking about funding a PhD to look into some of the complexities. >>>> It is pretty clear that the system is not well thought out.

    Why futz around with the rotating metal? It may entertain tourists,
    but that's really all that it is good for.

    Because it was always just there and now that it isn't the replacement >>>> inverters on many of the big installations are nowhere near good enough >>>> at simulating the required behaviour. They are too inclined to drop off >>>> and save themselves (much like nuclear plant also does). I suspect that >>>> Spain doesn't have a great deal of battery storage or pumped water.

    Network grade batteries, none, I believe. There are plans for water
    pump/generators. Some of the islands do have them.

    It seems that solar panels and wind farms mostly have the type of
    inverter that follow the shape of the voltage already in the grid, with
    detection to bail out if things go nuts. There is the suspicion that
    this was at least part of the problem.

    But there is another type of inverters that force the shape, ie,
    simulate inertia.

    Where do they get the energy from?

    Where does a gas turbine get the energy from?

    Wait, wait, let me think....

    Inertia, and then burning gas?

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to john larkin on Sun May 4 02:27:50 2025
    On 2025-05-04 01:53, john larkin wrote:
    On Sat, 3 May 2025 23:55:17 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-03 17:12, john larkin wrote:
    On Sat, 3 May 2025 14:24:07 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-02 12:03, Martin Brown wrote:
    On 01/05/2025 18:41, Bill Sloman wrote:
    On 2/05/2025 2:21 am, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    On 30/04/2025 7:59 pm, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    ... pumped hydro storage has the spinning
    turbines, but grid scale batteries have invereters, which can >>>>>>>>>> reacta lot
    faster than any spinning turbine,

    I thought the stabilising effect of a spinning turbine was because it >>>>>>>>> *didn't* react quickly.

    The grid frequency begins to fall so energy from the moving parts is >>>>>>>>> converted to electrical power which is fed into the grid to increase. >>>>>>>>> the frequency.  This results in a loss of stored mechanical energy >>>>>>>>> which
    causes the turbine to begin slowing down - which is detected by the >>>>>>>>> control system and used to feed more water/gas/steam into the >>>>>>>>> turbine so
    its speed is returned to normal.

    The interface between the stored mechanical energy and the electrical >>>>>>>>> energy demand has an almost instant response and is inherently stable >>>>>>>>> without needing elaborate control algorithms.

    But it isn't actually doing anything.

    Yes it is, basic electrical engineering theory.

    In effect it is a constant speed generator connected to variable load; >>>>>>> increase the load and more electrical energy immediately flows into the >>>>>>> load, taking mechanical energy from the inertia of the moving parts. >>>>>>> They then begin to slow down and the much more heavily damped mechanical
    regulator feeds in more energy to them from the primary source.

    So it is completely passive. A big battery isn't a primary source but >>>>>> it can provide enough DC current to let your grid scale inverter
    generate exactly the AC output that you need.

    There is a surprising amount of kinetic energy that can be stored in a >>>>> flywheel or other rotating piece of big heavy machinery. The grid has >>>>> adopted large scale solar PV and wind farms with some very flaky
    inverter technology whose interractions are not at all well understood. >>>>>
    One of the internal reports I was reading recently mentioned that they >>>>> were thinking about funding a PhD to look into some of the complexities. >>>>> It is pretty clear that the system is not well thought out.

    Why futz around with the rotating metal? It may entertain tourists, >>>>>> but that's really all that it is good for.

    Because it was always just there and now that it isn't the replacement >>>>> inverters on many of the big installations are nowhere near good enough >>>>> at simulating the required behaviour. They are too inclined to drop off >>>>> and save themselves (much like nuclear plant also does). I suspect that >>>>> Spain doesn't have a great deal of battery storage or pumped water.

    Network grade batteries, none, I believe. There are plans for water
    pump/generators. Some of the islands do have them.

    It seems that solar panels and wind farms mostly have the type of
    inverter that follow the shape of the voltage already in the grid, with >>>> detection to bail out if things go nuts. There is the suspicion that
    this was at least part of the problem.

    But there is another type of inverters that force the shape, ie,
    simulate inertia.

    Where do they get the energy from?

    Where does a gas turbine get the energy from?

    Wait, wait, let me think....

    Inertia, and then burning gas?


    Well, same thing.

    Batteries, and panels and wind flaps.

    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Don Y on Sun May 4 02:29:46 2025
    On 2025-05-04 00:15, Don Y wrote:
    On 5/3/2025 2:59 PM, Carlos E.R. wrote:
    But, you can set up smaller PV installations (hundreds of panels)
    on commercial buildings, "cover" parking areas, etc.   You don't
    get the same economies of scale as you would with 1,000 panels
    but 100+ panels on every city block makes a lot of power available
    where it is used.

    There is a regulation that says that every building will have to
    install some solar panels. I don't know when is the limit.



    I suspect the pain hasn't been great enough to force them to
    take their medicine?

    Sorry, I don't understand this sentence. :-?

    Their "poor planning/engineering" hasn't COST them sufficiently for them
    to actually DO something about the problem!  Perhaps now, with an entire nation *pissed*, they will decide they can't just wave their hands
    at the problem...

    Too early. It will be months before we know what actually happened, and
    this before anybody can think what can be done about it.

    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Chris Jones on Sun May 4 02:34:33 2025
    On 2025-05-01 02:36, Chris Jones wrote:
    On 30/04/2025 1:07 am, Martin Brown wrote:
    The idea that renewable sources make the grid frequency harder to
    manage sounds like total nonsense.

    It is pretty much accurate. The local feed in for domestic PV track
    whatever frequency they see on the network. The big problem is that
    without the large spinning generators and the energy stored in that
    angular momentum the frequency is able to shift rather too quickly.

    The problems are largely self-inflicted (or self-fulfilling prophecies) created by those who fear allowing renewables on the grid. In Australia
    they were so fearful of solar power being fed into the grid under
    unusual circumstances like islanding, thay they set a very tight limit requiring the solar inverters to shut down if the frequency dips
    slightly below nominal. So, once lots of PV was installed, when a coal-
    fired generator fails and the frequency dips, some "dangerous" PV power
    shuts down too, causing the problem to get worse, "just to be safe". It
    isn't an inherent weakness of the technology, it is a direct consequance
    of regulations written by those who fear or oppose renewables.
    Fortunately this particular problem was recognised and new inverters are
    now no longer required to shut down when the frequency dips within the foreseeable range.

    If the specifications for the inverters are written based on sound engineering and simulation of the grid behaviour rather than fear and ideology, it would be quite feasible to alter the algorithm in the PV inverters to help stabilise the grid frequency. For example, you could
    make it simulate what a spinning generator would do, or very likely
    something much better.

    Exactly.


    There is nothing magic about the current from a rotating generator that cannot be exactly replicated by an inverter that synthesises the same waveform and produces it with power semiconductors instead of a steam
    engine. Especially domestic single-phase inverters already incorporate
    enough capacitance to buffer the PV energy supplied to them, so as to
    supply a sinusoidal current to the grid, and this storage allows it to
    shift the phase of the current relative to the voltage however required
    in order to help stabilise the system, if only it were allowed to and required to by regulations.

    That's what I said on another part of the thread, but with less detail
    because I know less :-)

    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to All on Sat May 3 21:49:42 2025
    Their "poor planning/engineering" hasn't COST them sufficiently for them
    to actually DO something about the problem!  Perhaps now, with an entire
    nation *pissed*, they will decide they can't just wave their hands
    at the problem...

    Too early. It will be months before we know what actually happened, and this before anybody can think what can be done about it.

    But, they will now not be able to hand-wave the issue aside.
    People will be EXPECTING "something" to be done with the
    CLAIMED point of being a "solution". Even if it proves not to be!

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Bill Sloman@21:1/5 to Don Y on Sun May 4 16:15:11 2025
    On 4/05/2025 2:49 pm, Don Y wrote:
    Their "poor planning/engineering" hasn't COST them sufficiently for them >>> to actually DO something about the problem!  Perhaps now, with an entire >>> nation *pissed*, they will decide they can't just wave their hands
    at the problem...

    Too early. It will be months before we know what actually happened,
    and this before anybody can think what can be done about it.

    But, they will now not be able to hand-wave the issue aside.
    People will be EXPECTING "something" to be done with the
    CLAIMED point of being a "solution".  Even if it proves not to be!

    Donald Trump has a lot of "solutions" to the "problems" he claims
    American is facing. Hitler's solutions to similar "problems" was to
    invade Russia. Trump's trade war with China is even more foolish.

    Encouraging politicians to "act" often has them picking "solutions" that
    look dramatic but don't actually work.

    Buying lots of grid scale batteries probably would solve the problem,
    but might not provide enough photo-opportunities to be an attractive
    solution. Pumped hydroelectric storage takes a lot longer to install but
    it does offer more dramatic images.

    --
    Bill Sloman, Sydney

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Bill Sloman@21:1/5 to john larkin on Sun May 4 16:00:31 2025
    On 4/05/2025 9:53 am, john larkin wrote:
    On Sat, 3 May 2025 23:55:17 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-03 17:12, john larkin wrote:
    On Sat, 3 May 2025 14:24:07 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-02 12:03, Martin Brown wrote:
    On 01/05/2025 18:41, Bill Sloman wrote:
    On 2/05/2025 2:21 am, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    On 30/04/2025 7:59 pm, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    ... pumped hydro storage has the spinning
    turbines, but grid scale batteries have invereters, which can >>>>>>>>>> reacta lot
    faster than any spinning turbine,

    I thought the stabilising effect of a spinning turbine was because it >>>>>>>>> *didn't* react quickly.

    The grid frequency begins to fall so energy from the moving parts is >>>>>>>>> converted to electrical power which is fed into the grid to increase. >>>>>>>>> the frequency.  This results in a loss of stored mechanical energy >>>>>>>>> which
    causes the turbine to begin slowing down - which is detected by the >>>>>>>>> control system and used to feed more water/gas/steam into the >>>>>>>>> turbine so
    its speed is returned to normal.

    The interface between the stored mechanical energy and the electrical >>>>>>>>> energy demand has an almost instant response and is inherently stable >>>>>>>>> without needing elaborate control algorithms.

    But it isn't actually doing anything.

    Yes it is, basic electrical engineering theory.

    In effect it is a constant speed generator connected to variable load; >>>>>>> increase the load and more electrical energy immediately flows into the >>>>>>> load, taking mechanical energy from the inertia of the moving parts. >>>>>>> They then begin to slow down and the much more heavily damped mechanical
    regulator feeds in more energy to them from the primary source.

    So it is completely passive. A big battery isn't a primary source but >>>>>> it can provide enough DC current to let your grid scale inverter
    generate exactly the AC output that you need.

    There is a surprising amount of kinetic energy that can be stored in a >>>>> flywheel or other rotating piece of big heavy machinery. The grid has >>>>> adopted large scale solar PV and wind farms with some very flaky
    inverter technology whose interractions are not at all well understood. >>>>>
    One of the internal reports I was reading recently mentioned that they >>>>> were thinking about funding a PhD to look into some of the complexities. >>>>> It is pretty clear that the system is not well thought out.

    Why futz around with the rotating metal? It may entertain tourists, >>>>>> but that's really all that it is good for.

    Because it was always just there and now that it isn't the replacement >>>>> inverters on many of the big installations are nowhere near good enough >>>>> at simulating the required behaviour. They are too inclined to drop off >>>>> and save themselves (much like nuclear plant also does). I suspect that >>>>> Spain doesn't have a great deal of battery storage or pumped water.

    Network grade batteries, none, I believe. There are plans for water
    pump/generators. Some of the islands do have them.

    It seems that solar panels and wind farms mostly have the type of
    inverter that follow the shape of the voltage already in the grid, with >>>> detection to bail out if things go nuts. There is the suspicion that
    this was at least part of the problem.

    But there is another type of inverters that force the shape, ie,
    simulate inertia.

    Where do they get the energy from?

    Where does a gas turbine get the energy from?

    Wait, wait, let me think....

    If only you made a habit of it.

    Inertia, and then burning gas?

    It was a rhetorical question.

    --
    Bill Sloman, Sydney

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Bill Sloman@21:1/5 to Jeroen Belleman on Sun May 4 15:57:03 2025
    On 4/05/2025 5:17 am, Jeroen Belleman wrote:
    On 5/3/25 20:30, john larkin wrote:
    On Sat, 3 May 2025 19:23:11 +0200, Jeroen Belleman
    <jeroen@nospam.please> wrote:

    On 5/3/25 17:12, john larkin wrote:
    On Sat, 3 May 2025 14:24:07 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-02 12:03, Martin Brown wrote:
    On 01/05/2025 18:41, Bill Sloman wrote:
    On 2/05/2025 2:21 am, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    On 30/04/2025 7:59 pm, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    <snip>


    Most run at the MPPT point, so have no reserve to save the grid. And a
    lot of cloud cover or still wind will precipitate the very crisis that
    needs reserve.

    With the contribution of solar and wind being oblivious of demand,
    the burden of keeping the grid stable must be taken up by thermal
    or hydro power plants.

    The contributions of wind and solar don't have to be oblivious of demand
    - wind turbines can be feathered and photovoltaic cells can be run at
    higher voltages and lower currents than would give maximum power transfer.

    In fact when you have a variable generating capacity, you need short
    term storage to smooth it out. Pumped hydroelectric storage has been
    around for decades now, and grid scale batteries are becoming popular.
    though the South Australian Hornsdale Reserve was the first one
    installed back in 2017.

    When Spain's grid crashed, PV amounted to
    well over 50% of the total supply. It makes me wonder why it didn't
    crash sooner.

    It make me wonder why they didn't have any grid scale scale storage. Bureaucrats are averse to innovation, but they shouldn't be quite that ignorant. Carlos says that some of the Spanish island communities
    already have grid scale batteries - so it looks like bureaucratic inertia.

    --
    Bill Sloman, Sydney

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Bill Sloman@21:1/5 to john larkin on Sun May 4 15:42:17 2025
    On 4/05/2025 4:30 am, john larkin wrote:
    On Sat, 3 May 2025 19:23:11 +0200, Jeroen Belleman
    <jeroen@nospam.please> wrote:

    On 5/3/25 17:12, john larkin wrote:
    On Sat, 3 May 2025 14:24:07 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-02 12:03, Martin Brown wrote:
    On 01/05/2025 18:41, Bill Sloman wrote:
    On 2/05/2025 2:21 am, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    On 30/04/2025 7:59 pm, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    ... pumped hydro storage has the spinning
    turbines, but grid scale batteries have invereters, which can >>>>>>>>>> reacta lot
    faster than any spinning turbine,

    I thought the stabilising effect of a spinning turbine was because it >>>>>>>>> *didn't* react quickly.

    The grid frequency begins to fall so energy from the moving parts is >>>>>>>>> converted to electrical power which is fed into the grid to increase. >>>>>>>>> the frequency.  This results in a loss of stored mechanical energy >>>>>>>>> which
    causes the turbine to begin slowing down - which is detected by the >>>>>>>>> control system and used to feed more water/gas/steam into the >>>>>>>>> turbine so
    its speed is returned to normal.

    The interface between the stored mechanical energy and the electrical >>>>>>>>> energy demand has an almost instant response and is inherently stable >>>>>>>>> without needing elaborate control algorithms.

    But it isn't actually doing anything.

    Yes it is, basic electrical engineering theory.

    In effect it is a constant speed generator connected to variable load; >>>>>>> increase the load and more electrical energy immediately flows into the >>>>>>> load, taking mechanical energy from the inertia of the moving parts. >>>>>>> They then begin to slow down and the much more heavily damped mechanical
    regulator feeds in more energy to them from the primary source.

    So it is completely passive. A big battery isn't a primary source but >>>>>> it can provide enough DC current to let your grid scale inverter
    generate exactly the AC output that you need.

    There is a surprising amount of kinetic energy that can be stored in a >>>>> flywheel or other rotating piece of big heavy machinery. The grid has >>>>> adopted large scale solar PV and wind farms with some very flaky
    inverter technology whose interractions are not at all well understood. >>>>>
    One of the internal reports I was reading recently mentioned that they >>>>> were thinking about funding a PhD to look into some of the complexities. >>>>> It is pretty clear that the system is not well thought out.

    Why futz around with the rotating metal? It may entertain tourists, >>>>>> but that's really all that it is good for.

    Because it was always just there and now that it isn't the replacement >>>>> inverters on many of the big installations are nowhere near good enough >>>>> at simulating the required behaviour. They are too inclined to drop off >>>>> and save themselves (much like nuclear plant also does). I suspect that >>>>> Spain doesn't have a great deal of battery storage or pumped water.

    Network grade batteries, none, I believe. There are plans for water
    pump/generators. Some of the islands do have them.

    It seems that solar panels and wind farms mostly have the type of
    inverter that follow the shape of the voltage already in the grid, with >>>> detection to bail out if things go nuts. There is the suspicion that
    this was at least part of the problem.

    But there is another type of inverters that force the shape, ie,
    simulate inertia.

    Where do they get the energy from?


    To have a bit of margin to regulate, PV installations will have
    to either run somewhat below the bleeding edge, or to store a bit
    of energy in local batteries.

    Jeroen Belleman

    Most run at the MPPT point, so have no reserve to save the grid.

    They don't have to run at that point all the time, and can be designed
    to move away from it when necessary. The grid system can broadcast an instruction to do that, and the mobile phone system can instruct
    specific PV installations in specific localities to do that.

    And a lot of cloud cover or still wind will precipitate the very crisis
    that needs reserve.

    The system is designed to cope with that. The problem happens when the
    local fluctuations happen to combine in a way that the regular system
    can't cope with.

    It doesn't make sense to me for a multi-country grid to depend on "a
    bit of energy stored" in household batteries and inverters for
    emergency reserve power.

    When 30% of roof-tops solar panels - as they are in Australia - and an increasing proportion these systems are backed up by Tesla Powerwalls
    and the like - it can be quite a bit of energy.

    Back in 2008

    https://en.wikipedia.org/wiki/Hot,_Flat,_and_Crowded

    pointed out that electric car batteries in parked and notionally
    charging electric cars could serve as a very effective gird-scale battery.

    As the grids get greener, expect power to get less reliable and much
    more expensive. Hopefully the USA will use more NG, build more
    pipelines, and drill, baby, drill.

    And the people who paid for the climate change denial propaganda you are parroting will keep on making a lot of money out of wrecking the climate.

    --
    Bill Sloman, Sydney

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Jeroen Belleman@21:1/5 to Carlos E.R. on Sun May 4 10:23:22 2025
    On 5/4/25 02:29, Carlos E.R. wrote:
    On 2025-05-04 00:15, Don Y wrote:
    On 5/3/2025 2:59 PM, Carlos E.R. wrote:
    But, you can set up smaller PV installations (hundreds of panels)
    on commercial buildings, "cover" parking areas, etc.   You don't
    get the same economies of scale as you would with 1,000 panels
    but 100+ panels on every city block makes a lot of power available
    where it is used.

    There is a regulation that says that every building will have to
    install some solar panels. I don't know when is the limit.



    I suspect the pain hasn't been great enough to force them to
    take their medicine?

    Sorry, I don't understand this sentence. :-?

    Their "poor planning/engineering" hasn't COST them sufficiently for them
    to actually DO something about the problem!  Perhaps now, with an entire
    nation *pissed*, they will decide they can't just wave their hands
    at the problem...

    Too early. It will be months before we know what actually happened, and
    this before anybody can think what can be done about it.


    I have this suspicion that power engineers know very well what
    happened. Nobody wants to be the person to tell, because anyone
    who does will be the scapegoat. Spain's politicians were very
    clear: They are looking for someone to punish.

    Jeroen Belleman

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Liz Tuddenham@21:1/5 to Carlos E.R. on Sun May 4 10:12:04 2025
    Carlos E.R. <robin_listas@es.invalid> wrote:

    On 2025-05-03 17:12, john larkin wrote:
    On Sat, 3 May 2025 14:24:07 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-02 12:03, Martin Brown wrote:
    On 01/05/2025 18:41, Bill Sloman wrote:
    On 2/05/2025 2:21 am, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    On 30/04/2025 7:59 pm, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    ... pumped hydro storage has the spinning
    turbines, but grid scale batteries have invereters, which can >>>>>>>> reacta lot
    faster than any spinning turbine,

    I thought the stabilising effect of a spinning turbine was because it >>>>>>> *didn't* react quickly.

    The grid frequency begins to fall so energy from the moving parts is >>>>>>> converted to electrical power which is fed into the grid to increase. >>>>>>> the frequency.  This results in a loss of stored mechanical energy >>>>>>> which
    causes the turbine to begin slowing down - which is detected by the >>>>>>> control system and used to feed more water/gas/steam into the
    turbine so
    its speed is returned to normal.

    The interface between the stored mechanical energy and the electrical >>>>>>> energy demand has an almost instant response and is inherently stable >>>>>>> without needing elaborate control algorithms.

    But it isn't actually doing anything.

    Yes it is, basic electrical engineering theory.

    In effect it is a constant speed generator connected to variable load; >>>>> increase the load and more electrical energy immediately flows into the >>>>> load, taking mechanical energy from the inertia of the moving parts. >>>>> They then begin to slow down and the much more heavily damped mechanical
    regulator feeds in more energy to them from the primary source.

    So it is completely passive. A big battery isn't a primary source but >>>> it can provide enough DC current to let your grid scale inverter
    generate exactly the AC output that you need.

    There is a surprising amount of kinetic energy that can be stored in a >>> flywheel or other rotating piece of big heavy machinery. The grid has
    adopted large scale solar PV and wind farms with some very flaky
    inverter technology whose interractions are not at all well understood. >>>
    One of the internal reports I was reading recently mentioned that they >>> were thinking about funding a PhD to look into some of the complexities. >>> It is pretty clear that the system is not well thought out.

    Why futz around with the rotating metal? It may entertain tourists,
    but that's really all that it is good for.

    Because it was always just there and now that it isn't the replacement >>> inverters on many of the big installations are nowhere near good enough >>> at simulating the required behaviour. They are too inclined to drop off >>> and save themselves (much like nuclear plant also does). I suspect that >>> Spain doesn't have a great deal of battery storage or pumped water.

    Network grade batteries, none, I believe. There are plans for water
    pump/generators. Some of the islands do have them.

    It seems that solar panels and wind farms mostly have the type of
    inverter that follow the shape of the voltage already in the grid, with
    detection to bail out if things go nuts. There is the suspicion that
    this was at least part of the problem.

    But there is another type of inverters that force the shape, ie,
    simulate inertia.

    Where do they get the energy from?

    Where does a gas turbine get the energy from?

    The sun + CO2 > plants > animals > gas > mechanical energy.


    --
    ~ Liz Tuddenham ~
    (Remove the ".invalid"s and add ".co.uk" to reply)
    www.poppyrecords.co.uk

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Martin Brown@21:1/5 to Carlos E.R. on Sun May 4 09:49:22 2025
    On 04/05/2025 01:27, Carlos E.R. wrote:
    On 2025-05-04 01:53, john larkin wrote:
    On Sat, 3 May 2025 23:55:17 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-03 17:12, john larkin wrote:
    On Sat, 3 May 2025 14:24:07 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-02 12:03, Martin Brown wrote:

    Spain doesn't have a great deal of battery storage or pumped water. >>>>>
    Network grade batteries, none, I believe. There are plans for water
    pump/generators. Some of the islands do have them.

    It seems that solar panels and wind farms mostly have the type of
    inverter that follow the shape of the voltage already in the grid,
    with
    detection to bail out if things go nuts. There is the suspicion that >>>>> this was at least part of the problem.

    But there is another type of inverters that force the shape, ie,
    simulate inertia.

    Where do they get the energy from?

    Where does a gas turbine get the energy from?

    Wait, wait, let me think....

    Inertia, and then burning gas?


    Well, same thing.

    Batteries, and panels and wind flaps.

    But you do have to have serious stored energy available at the drop of a
    hat if the inverter is to effectively resist frequency being pulled down
    by the load. It can be done but the engineering will be interesting.

    I suspect from the time of day when this happened it was over supply of
    solar PV leading to too high a frequency and/or over voltage events that
    led to the cascade failure. Unclear why it didn't pass through a stable
    state where supply matched demand though if that really was the case.

    I suspect poor network stability analysis played a large part and the
    network was still relying on the intrinsic stability of the old turbine generators that were no longer present. Have to wait for the report.

    ISTR the electricity supplier in Spain has been warning about this for a
    while but the politicians were not listening. I wonder if the Spanish government *will* actually publish the results of the investigation.

    --
    Martin Brown

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Bill Sloman on Sun May 4 14:41:53 2025
    On 2025-05-04 08:15, Bill Sloman wrote:
    On 4/05/2025 2:49 pm, Don Y wrote:
    Their "poor planning/engineering" hasn't COST them sufficiently for
    them
    to actually DO something about the problem!  Perhaps now, with an
    entire
    nation *pissed*, they will decide they can't just wave their hands
    at the problem...

    Too early. It will be months before we know what actually happened,
    and this before anybody can think what can be done about it.

    But, they will now not be able to hand-wave the issue aside.
    People will be EXPECTING "something" to be done with the
    CLAIMED point of being a "solution".  Even if it proves not to be!

    Donald Trump has a lot of "solutions" to the "problems" he claims
    American is facing. Hitler's solutions to similar "problems" was to
    invade Russia. Trump's trade war with China is even more foolish.

    Encouraging politicians to "act" often has them picking "solutions" that
    look dramatic but don't actually work.

    Buying lots of grid scale batteries probably would solve the problem,
    but might not provide enough photo-opportunities to be an attractive solution. Pumped hydroelectric storage takes a lot longer to install but
    it does offer more dramatic images.


    Indeed. The Right Wing here is demanding action and blaming the
    government for either cover up or negligence, which is ridiculous (being polite). The government can not throw a press conference (or parliament investigation) and say "the cause of the Gran Apagón was this and that,
    and we will do this and that", till the engineers say so.

    The engineers say it will take months to analyze all the data of those 5 seconds, or more, and speak.

    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Bill Sloman on Sun May 4 14:34:23 2025
    On 2025-05-04 07:57, Bill Sloman wrote:
    On 4/05/2025 5:17 am, Jeroen Belleman wrote:
    On 5/3/25 20:30, john larkin wrote:
    On Sat, 3 May 2025 19:23:11 +0200, Jeroen Belleman
    <jeroen@nospam.please> wrote:

    On 5/3/25 17:12, john larkin wrote:
    On Sat, 3 May 2025 14:24:07 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-02 12:03, Martin Brown wrote:
    On 01/05/2025 18:41, Bill Sloman wrote:
    On 2/05/2025 2:21 am, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    On 30/04/2025 7:59 pm, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    <snip>


    Most run at the MPPT point, so have no reserve to save the grid. And a
    lot of cloud cover or still wind will precipitate the very crisis that
    needs reserve.

    With the contribution of solar and wind being oblivious of demand,
    the burden of keeping the grid stable must be taken up by thermal
    or hydro power plants.

    The contributions of wind and solar don't have to be oblivious of demand
    - wind turbines can be feathered and photovoltaic cells can be run at
    higher voltages and lower currents than would give maximum power transfer.

    In fact when you have a variable generating capacity, you need short
    term storage to smooth it out. Pumped hydroelectric storage has been
    around for decades now, and grid scale batteries are becoming popular.
    though the South Australian Hornsdale Reserve was the first one
    installed back in 2017.

    When Spain's grid crashed, PV amounted to
    well over 50% of the total supply. It makes me wonder why it didn't
    crash sooner.

    It make me wonder why they didn't have any grid scale scale storage. Bureaucrats are averse to innovation, but they shouldn't be quite that ignorant. Carlos says that some of the Spanish island communities
    already have grid scale batteries - so it looks like bureaucratic inertia.

    They have it because they need them more. They run isolated, they can
    not rely on others to smooth their loads. As a result, some islands have successfully run for days on solar/wind only.

    I asked chatgpt:


    You said:
    Have the Canary Islands or the Balearic Islands installed grid scale
    batteries?

    ChatGPT said:

    Yes, both the Canary Islands and the Balearic Islands are actively
    implementing grid-scale battery storage projects to enhance energy
    security and support the integration of renewable energy sources.


    ⚡ Canary Islands

    The Canary Islands are advancing several significant energy storage initiatives:
    evwind.es+6REE+6REE+6

    * Salto de Chira Pumped-Storage Hydroelectric Station (Gran
    Canaria): This €400 million project, expected to be operational by 2026,
    will integrate renewable energy, increasing its contribution by 37% and reducing CO₂ emissions by 20% .
    REE+1REE+1

    * Hybrid Storage System in Lanzarote: A pioneering hybrid system
    combining lithium-ion batteries and ultracapacitors is under development
    to stabilize the Lanzarote-Fuerteventura grid .
    pv magazine International+1Energy Storage+1

    * El Matorral Solar Plant with Battery Storage (Gran Canaria):
    Endesa plans to build a 9.3 MW solar plant with a 10.37 MWh battery
    storage capacity, aiming for completion by 2026 .
    evwind.es


    🌴 Balearic Islands

    The Balearic Islands are also progressing with substantial battery
    storage projects:
    REE

    * Mercadal and Sant Antoni Substations (Menorca and Ibiza): Red
    Eléctrica has awarded a €99.9 million contract to NHOA Energy to supply
    140 MW/105 MWh of battery storage, enhancing grid stability and
    supporting renewable energy integration .
    La Voz De Ibiza+3Energy Storage+3REE+3

    * Son Orlandis Solar Farm (Mallorca): Endesa has commissioned a 1.1
    MW/5.5 MWh vanadium redox flow battery, the largest of its kind in
    Europe, to support long-duration storage needs .
    Renewables Now

    * V2G Charging Network Pilot (Multiple Islands): ACCIONA Energía is implementing Spain's first bi-directional electric vehicle charging
    network, enabling vehicles to store and supply electricity to the grid, enhancing energy storage capabilities .
    solutions.acciona-energia.com

    These initiatives reflect a strong commitment in both archipelagos to
    modernize energy infrastructure, reduce reliance on fossil fuels, and facilitate the transition to renewable energy sources.


    ChatGPT can make mistakes. Check important info. See Cookie Preferences.


    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Jeroen Belleman@21:1/5 to Martin Brown on Sun May 4 17:23:11 2025
    On 5/4/25 10:49, Martin Brown wrote:
    On 04/05/2025 01:27, Carlos E.R. wrote:
    On 2025-05-04 01:53, john larkin wrote:
    On Sat, 3 May 2025 23:55:17 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-03 17:12, john larkin wrote:
    On Sat, 3 May 2025 14:24:07 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-02 12:03, Martin Brown wrote:

    Spain doesn't have a great deal of battery storage or pumped water. >>>>>>
    Network grade batteries, none, I believe. There are plans for water >>>>>> pump/generators. Some of the islands do have them.

    It seems that solar panels and wind farms mostly have the type of
    inverter that follow the shape of the voltage already in the grid, >>>>>> with
    detection to bail out if things go nuts. There is the suspicion that >>>>>> this was at least part of the problem.

    But there is another type of inverters that force the shape, ie,
    simulate inertia.

    Where do they get the energy from?

    Where does a gas turbine get the energy from?

    Wait, wait, let me think....

    Inertia, and then burning gas?


    Well, same thing.

    Batteries, and panels and wind flaps.

    But you do have to have serious stored energy available at the drop of a
    hat if the inverter is to effectively resist frequency being pulled down
    by the load.

    Not really. It should have a few percent of margin to increase
    power delivered when the frequency drops. The point is that the
    mains grid is composed of many generators. This only works if they
    take collective action. The European grid collectively has a target
    dP/dF in the 20GW/Hz ballpark. Any single installation will provide
    only a tiny, tiny contribution.

    Solar PV is sufficiently important in Spain that it should contribute
    its part. (It's in the 19GW ballpark, more than half of demand during
    daytime.) I don't know if it does.


    I suspect from the time of day when this happened it was over supply of
    solar PV leading to too high a frequency and/or over voltage events that
    led to the cascade failure. Unclear why it didn't pass through a stable
    state where supply matched demand though if that really was the case.

    Supply = demand is not a sufficient condition for dynamic stability,
    anyway.


    I suspect poor network stability analysis played a large part and the
    network was still relying on the intrinsic stability of the old turbine generators that were no longer present. Have to wait for the report.

    Yes. The problem has been anticipated for years.

    Jeroen Belleman

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From john larkin@21:1/5 to '''newspam'''@nonad.co.uk on Sun May 4 08:35:14 2025
    On Sun, 4 May 2025 09:49:22 +0100, Martin Brown
    <'''newspam'''@nonad.co.uk> wrote:

    On 04/05/2025 01:27, Carlos E.R. wrote:
    On 2025-05-04 01:53, john larkin wrote:
    On Sat, 3 May 2025 23:55:17 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-03 17:12, john larkin wrote:
    On Sat, 3 May 2025 14:24:07 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-02 12:03, Martin Brown wrote:

    Spain doesn't have a great deal of battery storage or pumped water. >>>>>>
    Network grade batteries, none, I believe. There are plans for water >>>>>> pump/generators. Some of the islands do have them.

    It seems that solar panels and wind farms mostly have the type of
    inverter that follow the shape of the voltage already in the grid, >>>>>> with
    detection to bail out if things go nuts. There is the suspicion that >>>>>> this was at least part of the problem.

    But there is another type of inverters that force the shape, ie,
    simulate inertia.

    Where do they get the energy from?

    Where does a gas turbine get the energy from?

    Wait, wait, let me think....

    Inertia, and then burning gas?


    Well, same thing.

    Batteries, and panels and wind flaps.

    But you do have to have serious stored energy available at the drop of a
    hat if the inverter is to effectively resist frequency being pulled down
    by the load. It can be done but the engineering will be interesting.

    I suspect from the time of day when this happened it was over supply of
    solar PV leading to too high a frequency and/or over voltage events that
    led to the cascade failure. Unclear why it didn't pass through a stable
    state where supply matched demand though if that really was the case.

    I suspect poor network stability analysis played a large part and the
    network was still relying on the intrinsic stability of the old turbine >generators that were no longer present. Have to wait for the report.

    ISTR the electricity supplier in Spain has been warning about this for a >while but the politicians were not listening. I wonder if the Spanish >government *will* actually publish the results of the investigation.


    Unlikely.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Martin Brown@21:1/5 to Jeroen Belleman on Sun May 4 16:38:58 2025
    On 04/05/2025 09:23, Jeroen Belleman wrote:
    On 5/4/25 02:29, Carlos E.R. wrote:
    On 2025-05-04 00:15, Don Y wrote:
    On 5/3/2025 2:59 PM, Carlos E.R. wrote:
    But, you can set up smaller PV installations (hundreds of panels)
    on commercial buildings, "cover" parking areas, etc.   You don't
    get the same economies of scale as you would with 1,000 panels
    but 100+ panels on every city block makes a lot of power available
    where it is used.

    There is a regulation that says that every building will have to
    install some solar panels. I don't know when is the limit.



    I suspect the pain hasn't been great enough to force them to
    take their medicine?

    Sorry, I don't understand this sentence. :-?

    Their "poor planning/engineering" hasn't COST them sufficiently for them >>> to actually DO something about the problem!  Perhaps now, with an entire >>> nation *pissed*, they will decide they can't just wave their hands
    at the problem...

    Too early. It will be months before we know what actually happened,
    and this before anybody can think what can be done about it.


    I have this suspicion that power engineers know very well what
    happened. Nobody wants to be the person to tell, because anyone
    who does will be the scapegoat. Spain's politicians were very
    clear: They are looking for someone to punish.

    +1

    When from an engineering point of view it looks like it is the
    politicians who should be flagellated for this major SNAFU.


    --
    Martin Brown

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Bill Sloman@21:1/5 to john larkin on Mon May 5 02:10:08 2025
    On 2/05/2025 1:40 am, john larkin wrote:
    On Thu, 1 May 2025 15:48:45 +0100, Martin Brown
    <'''newspam'''@nonad.co.uk> wrote:

    On 01/05/2025 15:06, john larkin wrote:
    On Thu, 1 May 2025 10:27:36 +0100, Martin Brown
    <'''newspam'''@nonad.co.uk> wrote:


    I hadn't realised that the French government have deliberately limited >>>> 400kV link capacity over the Pyrenees to protect EDF nuclear power from >>>> cheaper competition from Spain's massive solar PV investment.

    One consequence of using a lot of solar power is that interconnected
    networks get bigger hence less stable.

    There is no reason why a larger network should be less stable - if
    anything it should become more stable the more kit attached to it.

    The only caveat is when the magentosphere goes haywire like in the
    Carrington Event of 1859 and then long wires at high latitudes like in
    Canada can get fried. That is a realistic mode of failure for our very
    electricity focussed world. GPS going bad will also cause chaos.

    Big transformers have *very* long lead times.

    And are easily damaged. I wonder if an electronic version will ever be
    a replacement for tons of steel and copper and oil. They could be
    modular, like big RF transmitters are now. Lower voltage would help,
    namely more regional power generation. In other words, pump gas and
    not electricity. Gas pipelines store lots of energy; electric lines
    don't.


    A lot of mid-sized natural gas power plants (or, eventually, small
    nukes) would allow regions to be independent when they have to be.

    The networks have been continent wide for long while now. The newer
    national interconnectors and offshore long distance lines are DC now!

    Seems like stability is getting worse.


    There are schemes to build vast solar arrays in Morroco (pretty good
    location for them) with DC links into Europe and even to the UK!

    Cool. One dragged anchor, or a bomb planted by a robot sub, could make
    Europe go dark.


    Tesla must be turning in his grave.
    (presumably at 60Hz since he was American).

    He may have died in America but he wasn't born there.

    https://ethw.org/Nikola_Tesla

    Installing solar PV in the UK is highly profitable but a wasted
    opportunity since at our high latitude there really is no huge aircon
    peak in the mid summer afternoons and we get too much cloud.

    It is a double benefit in a lower latitude country to have solar panels
    on the roof since it shades the roof from direct sunlight slowing heat
    ingress and provided power as well.

    Residential rooftop solar all over Morroco, to be collected and
    exported to europe? Interesting concept.

    It has been around for a least a decade, if not longer. The politics of
    the region are complicated.

    Sun barely makes it above the horizon in the UK for 5 hours in mid
    winter if it isn't cloudy. Solar powered "smart" road signs invariably
    fail on frosty winters mornings. Ironically they say "please slow for
    the dangerous bend ahead" - they work fine in mid summer but in mid
    winter they wreck their batteries. Guess when there is ice on the road. >
    Solar electricity or water heating makes no sense in San Francisco
    either, but people get big subsidies so many do it. It complicates
    roof repairs.

    John Larkin's climate change denial propaganda sources do like to claim
    that. The fossil fuel extraction companies want to sell as much of their
    output as they can, while they still can.

    --
    Bill Sloman, Sydney

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Bill Sloman@21:1/5 to Jeroen Belleman on Mon May 5 02:24:43 2025
    On 5/05/2025 1:23 am, Jeroen Belleman wrote:
    On 5/4/25 10:49, Martin Brown wrote:
    On 04/05/2025 01:27, Carlos E.R. wrote:
    On 2025-05-04 01:53, john larkin wrote:
    On Sat, 3 May 2025 23:55:17 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-03 17:12, john larkin wrote:
    On Sat, 3 May 2025 14:24:07 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-02 12:03, Martin Brown wrote:

    Spain doesn't have a great deal of battery storage or pumped water. >>>>>>>
    Network grade batteries, none, I believe. There are plans for water >>>>>>> pump/generators. Some of the islands do have them.

    It seems that solar panels and wind farms mostly have the type of >>>>>>> inverter that follow the shape of the voltage already in the
    grid, with
    detection to bail out if things go nuts. There is the suspicion that >>>>>>> this was at least part of the problem.

    But there is another type of inverters that force the shape, ie, >>>>>>> simulate inertia.

    Where do they get the energy from?

    Where does a gas turbine get the energy from?

    Wait, wait, let me think....

    Inertia, and then burning gas?


    Well, same thing.

    Batteries, and panels and wind flaps.

    But you do have to have serious stored energy available at the drop of
    a hat if the inverter is to effectively resist frequency being pulled
    down by the load.

    Not really. It should have a few percent of margin to increase
    power delivered when the frequency drops. The point is that the
    mains grid is composed of many generators. This only works if they
    take collective action. The European grid collectively has a target
    dP/dF in the 20GW/Hz ballpark. Any single installation will provide
    only a tiny, tiny contribution.

    Solar PV is sufficiently important in Spain that it should contribute
    its part. (It's in the 19GW ballpark, more than half of demand during daytime.) I don't know if it does.


    I suspect from the time of day when this happened it was over supply
    of solar PV leading to too high a frequency and/or over voltage events
    that led to the cascade failure. Unclear why it didn't pass through a
    stable state where supply matched demand though if that really was the
    case.

    Supply = demand is not a sufficient condition for dynamic stability,
    anyway.

    I suspect poor network stability analysis played a large part and the
    network was still relying on the intrinsic stability of the old
    turbine generators that were no longer present. Have to wait for the
    report.

    Yes. The problem has been anticipated for years.

    The problem may have been expected for years, but "anticipating a
    problem" involves doing stuff to make it less of a problem when it does
    show up. There doesn't seem to be any evidence that the network had been
    beefed up in any way to prevent the problem, or confine the consequences
    to the area where the problem first kicked in.

    South Australia bought the world's first grid scale battery in 2017
    because they'd been having grid stability problems. They anticipated
    further problems by doing something that made them less likely to show
    up again.

    --
    Bill Sloman, Sydney

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Martin Brown on Sun May 4 19:36:10 2025
    On 2025-05-04 10:49, Martin Brown wrote:
    On 04/05/2025 01:27, Carlos E.R. wrote:
    On 2025-05-04 01:53, john larkin wrote:
    On Sat, 3 May 2025 23:55:17 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-03 17:12, john larkin wrote:
    On Sat, 3 May 2025 14:24:07 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-02 12:03, Martin Brown wrote:

    Spain doesn't have a great deal of battery storage or pumped water. >>>>>>
    Network grade batteries, none, I believe. There are plans for water >>>>>> pump/generators. Some of the islands do have them.

    It seems that solar panels and wind farms mostly have the type of
    inverter that follow the shape of the voltage already in the grid, >>>>>> with
    detection to bail out if things go nuts. There is the suspicion that >>>>>> this was at least part of the problem.

    But there is another type of inverters that force the shape, ie,
    simulate inertia.

    Where do they get the energy from?

    Where does a gas turbine get the energy from?

    Wait, wait, let me think....

    Inertia, and then burning gas?


    Well, same thing.

    Batteries, and panels and wind flaps.

    But you do have to have serious stored energy available at the drop of a
    hat if the inverter is to effectively resist frequency being pulled down
    by the load. It can be done but the engineering will be interesting.

    I suspect from the time of day when this happened it was over supply of
    solar PV leading to too high a frequency and/or over voltage events that
    led to the cascade failure. Unclear why it didn't pass through a stable
    state where supply matched demand though if that really was the case.

    I suspect poor network stability analysis played a large part and the
    network was still relying on the intrinsic stability of the old turbine generators that were no longer present. Have to wait for the report.

    ISTR the electricity supplier in Spain has been warning about this for a while but the politicians were not listening. I wonder if the Spanish government *will* actually publish the results of the investigation.

    It is a promise, they can not backout on it. Else, it will leak, and speculation will be worse.


    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Jeroen Belleman on Sun May 4 19:34:34 2025
    On 2025-05-04 17:23, Jeroen Belleman wrote:
    On 5/4/25 10:49, Martin Brown wrote:
    On 04/05/2025 01:27, Carlos E.R. wrote:
    On 2025-05-04 01:53, john larkin wrote:
    On Sat, 3 May 2025 23:55:17 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-03 17:12, john larkin wrote:
    On Sat, 3 May 2025 14:24:07 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-02 12:03, Martin Brown wrote:

    Spain doesn't have a great deal of battery storage or pumped water. >>>>>>>
    Network grade batteries, none, I believe. There are plans for water >>>>>>> pump/generators. Some of the islands do have them.

    It seems that solar panels and wind farms mostly have the type of >>>>>>> inverter that follow the shape of the voltage already in the
    grid, with
    detection to bail out if things go nuts. There is the suspicion that >>>>>>> this was at least part of the problem.

    But there is another type of inverters that force the shape, ie, >>>>>>> simulate inertia.

    Where do they get the energy from?

    Where does a gas turbine get the energy from?

    Wait, wait, let me think....

    Inertia, and then burning gas?


    Well, same thing.

    Batteries, and panels and wind flaps.

    But you do have to have serious stored energy available at the drop of
    a hat if the inverter is to effectively resist frequency being pulled
    down by the load.

    Not really. It should have a few percent of margin to increase
    power delivered when the frequency drops. The point is that the
    mains grid is composed of many generators. This only works if they
    take collective action. The European grid collectively has a target
    dP/dF in the 20GW/Hz ballpark. Any single installation will provide
    only a tiny, tiny contribution.

    Solar PV is sufficiently important in Spain that it should contribute
    its part. (It's in the 19GW ballpark, more than half of demand during daytime.) I don't know if it does.

    There are days when renewables have met the entire demand.

    ...


    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to Carlos E.R. on Sun May 4 13:20:27 2025
    On 5/4/2025 5:34 AM, Carlos E.R. wrote:
    They have it because they need them more. They run isolated, they can not rely
    on others to smooth their loads. As a result, some islands have successfully run for days on solar/wind only.

    Is this just "taken in stride"? Or, are residents alerted to special
    "please be extra conservative in your energy use TODAY" requests?

    How does storage capacity correlate with "off hours" demand?

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to Martin Brown on Sun May 4 13:24:58 2025
    On 5/4/2025 1:49 AM, Martin Brown wrote:
    But you do have to have serious stored energy available at the drop of a hat if
    the inverter is to effectively resist frequency being pulled down by the load.
    It can be done but the engineering will be interesting.

    But that storage doesn't have to be in one "lump". The energy that you
    deliver (brake) to the grid can be sourced from each cogenerator. And, one mains cycle later, there is more energy available (from incident light rays).

    It's a different problem from "overnight storage".

    The problem I see is the same one all distributed systems face -- communication and cooperation (assuming designed AS a distributed system).

    Imagine thousands of little 4KW turbines scattered on streams around
    the country. Certainly not the same issue as a single large-scale hydroproject.

    I suspect from the time of day when this happened it was over supply of solar PV leading to too high a frequency and/or over voltage events that led to the cascade failure. Unclear why it didn't pass through a stable state where supply
    matched demand though if that really was the case.

    I suspect poor network stability analysis played a large part and the network was still relying on the intrinsic stability of the old turbine generators that
    were no longer present. Have to wait for the report.

    ISTR the electricity supplier in Spain has been warning about this for a while
    but the politicians were not listening. I wonder if the Spanish government *will* actually publish the results of the investigation.

    Details always leak; its what keeps the conspiracy kooks in business!

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Don Y on Sun May 4 22:55:34 2025
    On 2025-05-04 22:20, Don Y wrote:
    On 5/4/2025 5:34 AM, Carlos E.R. wrote:
    They have it because they need them more. They run isolated, they can
    not rely on others to smooth their loads. As a result, some islands
    have successfully run for days on solar/wind only.

    Is this just "taken in stride"?  Or, are residents alerted to special "please be extra conservative in your energy use TODAY" requests?

    How does storage capacity correlate with "off hours" demand?

    They take it on stride.
    I don't live there, nor have visited. I think that the island that
    stayed for a month on solar/wind doesn't have heavy industries, not by far.

    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to Carlos E.R. on Sun May 4 19:50:02 2025
    On 5/4/2025 1:55 PM, Carlos E.R. wrote:
    On 2025-05-04 22:20, Don Y wrote:
    On 5/4/2025 5:34 AM, Carlos E.R. wrote:
    They have it because they need them more. They run isolated, they can not >>> rely on others to smooth their loads. As a result, some islands have
    successfully run for days on solar/wind only.

    Is this just "taken in stride"?  Or, are residents alerted to special
    "please be extra conservative in your energy use TODAY" requests?

    How does storage capacity correlate with "off hours" demand?

    They take it on stride.
    I don't live there, nor have visited. I think that the island that stayed for a
    month on solar/wind doesn't have heavy industries, not by far.

    So, they did nothing "special" to avoid running out of power for that
    time? I.e., they were CONFIDENT in their available surplus (day
    AND night) to stick with "life as usual"?

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Bill Sloman@21:1/5 to Don Y on Mon May 5 17:39:55 2025
    On 5/05/2025 12:50 pm, Don Y wrote:
    On 5/4/2025 1:55 PM, Carlos E.R. wrote:
    On 2025-05-04 22:20, Don Y wrote:
    On 5/4/2025 5:34 AM, Carlos E.R. wrote:
    They have it because they need them more. They run isolated, they
    can not rely on others to smooth their loads. As a result, some
    islands have successfully run for days on solar/wind only.

    Is this just "taken in stride"?  Or, are residents alerted to special
    "please be extra conservative in your energy use TODAY" requests?

    How does storage capacity correlate with "off hours" demand?

    They take it on stride.
    I don't live there, nor have visited. I think that the island that
    stayed for a month on solar/wind doesn't have heavy industries, not by
    far.

    So, they did nothing "special" to avoid running out of power for that
    time?  I.e., they were CONFIDENT in their available surplus (day
    AND night) to stick with "life as usual"?

    The storage, and the generating capacity, will have been sized with this
    in mind.

    It means installing more than the bare minimum in wind turbines and
    solar panels, but that's cheaper than shipping in loads of diesel fuel,
    and building tanks big enough to hold enough diesel to tide you over a
    bad couple of days.

    --
    Bill Sloman, Sydney

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Bill Sloman@21:1/5 to john larkin on Mon May 5 20:36:03 2025
    On 4/05/2025 6:39 am, john larkin wrote:
    On Sat, 3 May 2025 21:17:15 +0200, Jeroen Belleman
    <jeroen@nospam.please> wrote:

    On 5/3/25 20:30, john larkin wrote:
    On Sat, 3 May 2025 19:23:11 +0200, Jeroen Belleman
    <jeroen@nospam.please> wrote:

    On 5/3/25 17:12, john larkin wrote:
    On Sat, 3 May 2025 14:24:07 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-02 12:03, Martin Brown wrote:
    On 01/05/2025 18:41, Bill Sloman wrote:
    On 2/05/2025 2:21 am, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    On 30/04/2025 7:59 pm, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    ... pumped hydro storage has the spinning
    turbines, but grid scale batteries have invereters, which can >>>>>>>>>>>> reacta lot
    faster than any spinning turbine,

    I thought the stabilising effect of a spinning turbine was because it
    *didn't* react quickly.

    The grid frequency begins to fall so energy from the moving parts is
    converted to electrical power which is fed into the grid to increase.
    the frequency.  This results in a loss of stored mechanical energy >>>>>>>>>>> which
    causes the turbine to begin slowing down - which is detected by the >>>>>>>>>>> control system and used to feed more water/gas/steam into the >>>>>>>>>>> turbine so
    its speed is returned to normal.

    The interface between the stored mechanical energy and the electrical
    energy demand has an almost instant response and is inherently stable
    without needing elaborate control algorithms.

    But it isn't actually doing anything.

    Yes it is, basic electrical engineering theory.

    In effect it is a constant speed generator connected to variable load;
    increase the load and more electrical energy immediately flows into the
    load, taking mechanical energy from the inertia of the moving parts. >>>>>>>>> They then begin to slow down and the much more heavily damped mechanical
    regulator feeds in more energy to them from the primary source. >>>>>>>>
    So it is completely passive. A big battery isn't a primary source but >>>>>>>> it can provide enough DC current to let your grid scale inverter >>>>>>>> generate exactly the AC output that you need.

    There is a surprising amount of kinetic energy that can be stored in a >>>>>>> flywheel or other rotating piece of big heavy machinery. The grid has >>>>>>> adopted large scale solar PV and wind farms with some very flaky >>>>>>> inverter technology whose interractions are not at all well understood. >>>>>>>
    One of the internal reports I was reading recently mentioned that they >>>>>>> were thinking about funding a PhD to look into some of the complexities.
    It is pretty clear that the system is not well thought out.

    Why futz around with the rotating metal? It may entertain tourists, >>>>>>>> but that's really all that it is good for.

    Because it was always just there and now that it isn't the replacement >>>>>>> inverters on many of the big installations are nowhere near good enough >>>>>>> at simulating the required behaviour. They are too inclined to drop off >>>>>>> and save themselves (much like nuclear plant also does). I suspect that >>>>>>> Spain doesn't have a great deal of battery storage or pumped water. >>>>>>
    Network grade batteries, none, I believe. There are plans for water >>>>>> pump/generators. Some of the islands do have them.

    It seems that solar panels and wind farms mostly have the type of
    inverter that follow the shape of the voltage already in the grid, with >>>>>> detection to bail out if things go nuts. There is the suspicion that >>>>>> this was at least part of the problem.

    But there is another type of inverters that force the shape, ie,
    simulate inertia.

    Where do they get the energy from?


    To have a bit of margin to regulate, PV installations will have
    to either run somewhat below the bleeding edge, or to store a bit
    of energy in local batteries.

    Jeroen Belleman

    Most run at the MPPT point, so have no reserve to save the grid. And a
    lot of cloud cover or still wind will precipitate the very crisis that
    needs reserve.


    With the contribution of solar and wind being oblivious of demand,
    the burden of keeping the grid stable must be taken up by thermal
    or hydro power plants. When Spain's grid crashed, PV amounted to
    well over 50% of the total supply. It makes me wonder why it didn't
    crash sooner.

    Jeroen Belleman

    I'm estimating that half the hazard is the actual physics, power and
    energy storage, and half is bad policy and inadequate control theory.

    When John Larkin says he is estimating, he means that he is guessing.

    If you estimate something, you put a number on it, with tolerances and
    if you claim to have made an estimate you should post that estimate,

    A region should be able to isolate itself without bringing in the same
    boat with three or four other countries.

    It's obviously possible, but if you haven't designed your grid to let
    you do that, it's a strictly theoretical possibility.

    We have the crazy situation in California where sometimes we have to
    buy coal-fired power from Nevada, and some times we have to *pay them*
    to take our excess power.

    There's nothing at all crazy about importing power when you need it.
    There's something slightly crazy about not having enough grid storage to
    soak up excess power from intermittent sources like solar cells and
    windmills, but you have to buy that grid storage, which makes it the
    kind of capital investment that the US tends to skip if it can.

    --
    Bill Sloman, Sydney

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Don Y on Mon May 5 13:45:24 2025
    On 2025-05-05 04:50, Don Y wrote:
    On 5/4/2025 1:55 PM, Carlos E.R. wrote:
    On 2025-05-04 22:20, Don Y wrote:
    On 5/4/2025 5:34 AM, Carlos E.R. wrote:
    They have it because they need them more. They run isolated, they
    can not rely on others to smooth their loads. As a result, some
    islands have successfully run for days on solar/wind only.

    Is this just "taken in stride"?  Or, are residents alerted to special
    "please be extra conservative in your energy use TODAY" requests?

    How does storage capacity correlate with "off hours" demand?

    They take it on stride.
    I don't live there, nor have visited. I think that the island that
    stayed for a month on solar/wind doesn't have heavy industries, not by
    far.

    So, they did nothing "special" to avoid running out of power for that
    time?  I.e., they were CONFIDENT in their available surplus (day
    AND night) to stick with "life as usual"?

    Well, they had their diesel generators on standby. They did not have to
    be confident, they simply were not needed for many days.

    <https://www.endesa.com/es/la-cara-e/energias-renovables/gorona-viento-renovable>

    You can read it with an automated translator.

    The island is small.

    <https://maps.app.goo.gl/p5FfPnhvFVKhRN4C8>

    <https://en.wikipedia.org/wiki/El_Hierro>

    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Bill Sloman on Mon May 5 13:47:25 2025
    On 2025-05-05 09:39, Bill Sloman wrote:
    On 5/05/2025 12:50 pm, Don Y wrote:
    On 5/4/2025 1:55 PM, Carlos E.R. wrote:
    On 2025-05-04 22:20, Don Y wrote:
    On 5/4/2025 5:34 AM, Carlos E.R. wrote:
    They have it because they need them more. They run isolated, they
    can not rely on others to smooth their loads. As a result, some
    islands have successfully run for days on solar/wind only.

    Is this just "taken in stride"?  Or, are residents alerted to special >>>> "please be extra conservative in your energy use TODAY" requests?

    How does storage capacity correlate with "off hours" demand?

    They take it on stride.
    I don't live there, nor have visited. I think that the island that
    stayed for a month on solar/wind doesn't have heavy industries, not
    by far.

    So, they did nothing "special" to avoid running out of power for that
    time?  I.e., they were CONFIDENT in their available surplus (day
    AND night) to stick with "life as usual"?

    The storage, and the generating capacity, will have been sized with this
    in mind.

    It means installing more than the bare minimum in wind turbines and
    solar panels, but that's cheaper than shipping in loads of diesel fuel,
    and building tanks big enough to hold enough diesel to tide you over a
    bad couple of days.

    Well, the diesel generator exists since for ever basically :-)

    The storage facility and the wind farms are recent.

    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From john larkin@21:1/5 to robin_listas@es.invalid on Mon May 5 06:58:01 2025
    On Mon, 5 May 2025 13:45:24 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-05 04:50, Don Y wrote:
    On 5/4/2025 1:55 PM, Carlos E.R. wrote:
    On 2025-05-04 22:20, Don Y wrote:
    On 5/4/2025 5:34 AM, Carlos E.R. wrote:
    They have it because they need them more. They run isolated, they
    can not rely on others to smooth their loads. As a result, some
    islands have successfully run for days on solar/wind only.

    Is this just "taken in stride"?á Or, are residents alerted to special
    "please be extra conservative in your energy use TODAY" requests?

    How does storage capacity correlate with "off hours" demand?

    They take it on stride.
    I don't live there, nor have visited. I think that the island that
    stayed for a month on solar/wind doesn't have heavy industries, not by
    far.

    So, they did nothing "special" to avoid running out of power for that
    time?á I.e., they were CONFIDENT in their available surplus (day
    AND night) to stick with "life as usual"?

    Well, they had their diesel generators on standby. They did not have to
    be confident, they simply were not needed for many days.

    <https://www.endesa.com/es/la-cara-e/energias-renovables/gorona-viento-renovable>

    You can read it with an automated translator.

    The island is small.

    <https://maps.app.goo.gl/p5FfPnhvFVKhRN4C8>

    <https://en.wikipedia.org/wiki/El_Hierro>

    I'm thinking that it doesn't snow there very much. A few days without
    power won't kill many people.

    Wind and solar, with 100% diesel backup, probably makes sense for
    them. Diesel is expensive.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Liz Tuddenham@21:1/5 to john larkin on Mon May 5 17:35:38 2025
    john larkin <jl@glen--canyon.com> wrote:

    [...]
    A few days without
    power won't kill many people.

    It will in the UK if all the 'phones need mains power (either at the subscribers' premises or at the masts). Nobody will be able to call out
    the emergency services. How many deaths per day will that be if nobody
    can contact the police, fire brigade or ambulance service?

    --
    ~ Liz Tuddenham ~
    (Remove the ".invalid"s and add ".co.uk" to reply)
    www.poppyrecords.co.uk

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Liz Tuddenham@21:1/5 to Bill Sloman on Mon May 5 20:04:22 2025
    Bill Sloman <bill.sloman@ieee.org> wrote:

    On 6/05/2025 2:35 am, Liz Tuddenham wrote:
    john larkin <jl@glen--canyon.com> wrote:

    [...]
    A few days without
    power won't kill many people.

    It will in the UK if all the 'phones need mains power (either at the subscribers' premises or at the masts). Nobody will be able to call out the emergency services. How many deaths per day will that be if nobody can contact the police, fire brigade or ambulance service?

    Even politicians can be relied on to be less stupid than that.
    [...]

    There is no evidence to support your claim at the moment.


    --
    ~ Liz Tuddenham ~
    (Remove the ".invalid"s and add ".co.uk" to reply)
    www.poppyrecords.co.uk

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Bill Sloman@21:1/5 to Liz Tuddenham on Tue May 6 04:47:09 2025
    On 6/05/2025 2:35 am, Liz Tuddenham wrote:
    john larkin <jl@glen--canyon.com> wrote:

    [...]
    A few days without
    power won't kill many people.

    It will in the UK if all the 'phones need mains power (either at the subscribers' premises or at the masts). Nobody will be able to call out
    the emergency services. How many deaths per day will that be if nobody
    can contact the police, fire brigade or ambulance service?

    Even politicians can be relied on to be less stupid than that.
    Admittedly they were stupid enough to moth-ball the natural gas storage
    set-up which let you store enough natural gas to keep the fast-start gas-turbine generators running for a couple of days, just before Russian
    gas got cut off.

    In the renewable future that storage will probably be repurposed to
    store electrolytic hydrogen - you only get back about 25% of the energy
    you used to make the hydrogen, but emergency back-up don't have to be
    all the cheap - they don't get used all that often.

    --
    Bill Sloman, Sydney

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From john larkin@21:1/5 to Liz Tuddenham on Mon May 5 12:27:18 2025
    On Mon, 5 May 2025 17:35:38 +0100, liz@poppyrecords.invalid.invalid
    (Liz Tuddenham) wrote:

    john larkin <jl@glen--canyon.com> wrote:

    [...]
    A few days without
    power won't kill many people.

    It will in the UK if all the 'phones need mains power (either at the >subscribers' premises or at the masts). Nobody will be able to call out
    the emergency services. How many deaths per day will that be if nobody
    can contact the police, fire brigade or ambulance service?

    I know people who will die if their phones go offline for a full day.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to john larkin on Mon May 5 23:31:47 2025
    On 2025-05-05 15:58, john larkin wrote:
    On Mon, 5 May 2025 13:45:24 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-05 04:50, Don Y wrote:
    On 5/4/2025 1:55 PM, Carlos E.R. wrote:
    On 2025-05-04 22:20, Don Y wrote:
    On 5/4/2025 5:34 AM, Carlos E.R. wrote:
    They have it because they need them more. They run isolated, they
    can not rely on others to smooth their loads. As a result, some
    islands have successfully run for days on solar/wind only.

    Is this just "taken in stride"?  Or, are residents alerted to special >>>>> "please be extra conservative in your energy use TODAY" requests?

    How does storage capacity correlate with "off hours" demand?

    They take it on stride.
    I don't live there, nor have visited. I think that the island that
    stayed for a month on solar/wind doesn't have heavy industries, not by >>>> far.

    So, they did nothing "special" to avoid running out of power for that
    time?  I.e., they were CONFIDENT in their available surplus (day
    AND night) to stick with "life as usual"?

    Well, they had their diesel generators on standby. They did not have to
    be confident, they simply were not needed for many days.

    <https://www.endesa.com/es/la-cara-e/energias-renovables/gorona-viento-renovable>

    You can read it with an automated translator.

    The island is small.

    <https://maps.app.goo.gl/p5FfPnhvFVKhRN4C8>

    <https://en.wikipedia.org/wiki/El_Hierro>

    I'm thinking that it doesn't snow there very much. A few days without
    power won't kill many people.

    Wind and solar, with 100% diesel backup, probably makes sense for
    them. Diesel is expensive.

    It doesn't ever snow, look at the map.

    The diesel has been there since ever, it is not the backup. It is the
    main system, but they are very glad to avoid using it now, thanks to
    wind and solar.


    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Liz Tuddenham on Mon May 5 23:35:00 2025
    On 2025-05-05 18:35, Liz Tuddenham wrote:
    john larkin <jl@glen--canyon.com> wrote:

    [...]
    A few days without
    power won't kill many people.

    It will in the UK if all the 'phones need mains power (either at the subscribers' premises or at the masts). Nobody will be able to call out
    the emergency services. How many deaths per day will that be if nobody
    can contact the police, fire brigade or ambulance service?

    That's a good point that many countries have ignored. And there are no
    phone booths either. Nor that they would be any good in that sense, with
    a fibre network.

    I heard that Switzerland is investigating how to mandate that phone
    towers must have their own power to survive for... I don't remember the
    time, days?

    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Joe Gwinn@21:1/5 to robin_listas@es.invalid on Mon May 5 18:49:21 2025
    On Mon, 5 May 2025 23:31:47 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-05 15:58, john larkin wrote:
    On Mon, 5 May 2025 13:45:24 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-05 04:50, Don Y wrote:
    On 5/4/2025 1:55 PM, Carlos E.R. wrote:
    On 2025-05-04 22:20, Don Y wrote:
    On 5/4/2025 5:34 AM, Carlos E.R. wrote:
    They have it because they need them more. They run isolated, they >>>>>>> can not rely on others to smooth their loads. As a result, some
    islands have successfully run for days on solar/wind only.

    Is this just "taken in stride"?á Or, are residents alerted to special >>>>>> "please be extra conservative in your energy use TODAY" requests?

    How does storage capacity correlate with "off hours" demand?

    They take it on stride.
    I don't live there, nor have visited. I think that the island that
    stayed for a month on solar/wind doesn't have heavy industries, not by >>>>> far.

    So, they did nothing "special" to avoid running out of power for that
    time?á I.e., they were CONFIDENT in their available surplus (day
    AND night) to stick with "life as usual"?

    Well, they had their diesel generators on standby. They did not have to
    be confident, they simply were not needed for many days.

    <https://www.endesa.com/es/la-cara-e/energias-renovables/gorona-viento-renovable>

    You can read it with an automated translator.

    The island is small.

    <https://maps.app.goo.gl/p5FfPnhvFVKhRN4C8>

    <https://en.wikipedia.org/wiki/El_Hierro>

    I'm thinking that it doesn't snow there very much. A few days without
    power won't kill many people.

    Wind and solar, with 100% diesel backup, probably makes sense for
    them. Diesel is expensive.

    It doesn't ever snow, look at the map.

    The diesel has been there since ever, it is not the backup. It is the
    main system, but they are very glad to avoid using it now, thanks to
    wind and solar.

    Back in the days of analog telephones over copper wires, the US
    telephone system central offices had lead-acid battery power
    sufficient for 48 hours full operation, plus a diesel backup
    generator. This allowed the diesel to be brought online only as
    needed, and slowly if repair is needed.

    The objective was 0.99999 operational availability, which was usually
    achieved in practice.

    Cell phone systems are happy to achieve 0.90000; maybe we can get them
    to 0.99.

    Joe

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Joe Gwinn on Tue May 6 02:18:44 2025
    On 2025-05-06 00:49, Joe Gwinn wrote:
    On Mon, 5 May 2025 23:31:47 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-05 15:58, john larkin wrote:
    On Mon, 5 May 2025 13:45:24 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-05 04:50, Don Y wrote:
    On 5/4/2025 1:55 PM, Carlos E.R. wrote:
    On 2025-05-04 22:20, Don Y wrote:
    On 5/4/2025 5:34 AM, Carlos E.R. wrote:
    They have it because they need them more. They run isolated, they >>>>>>>> can not rely on others to smooth their loads. As a result, some >>>>>>>> islands have successfully run for days on solar/wind only.

    Is this just "taken in stride"?  Or, are residents alerted to special >>>>>>> "please be extra conservative in your energy use TODAY" requests? >>>>>>>
    How does storage capacity correlate with "off hours" demand?

    They take it on stride.
    I don't live there, nor have visited. I think that the island that >>>>>> stayed for a month on solar/wind doesn't have heavy industries, not by >>>>>> far.

    So, they did nothing "special" to avoid running out of power for that >>>>> time?  I.e., they were CONFIDENT in their available surplus (day
    AND night) to stick with "life as usual"?

    Well, they had their diesel generators on standby. They did not have to >>>> be confident, they simply were not needed for many days.

    <https://www.endesa.com/es/la-cara-e/energias-renovables/gorona-viento-renovable>

    You can read it with an automated translator.

    The island is small.

    <https://maps.app.goo.gl/p5FfPnhvFVKhRN4C8>

    <https://en.wikipedia.org/wiki/El_Hierro>

    I'm thinking that it doesn't snow there very much. A few days without
    power won't kill many people.

    Wind and solar, with 100% diesel backup, probably makes sense for
    them. Diesel is expensive.

    It doesn't ever snow, look at the map.

    The diesel has been there since ever, it is not the backup. It is the
    main system, but they are very glad to avoid using it now, thanks to
    wind and solar.

    Back in the days of analog telephones over copper wires, the US
    telephone system central offices had lead-acid battery power
    sufficient for 48 hours full operation, plus a diesel backup
    generator. This allowed the diesel to be brought online only as
    needed, and slowly if repair is needed.

    The objective was 0.99999 operational availability, which was usually achieved in practice.

    I know. I worked with the 5. :-)


    Cell phone systems are happy to achieve 0.90000; maybe we can get them
    to 0.99.

    Joe


    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From john larkin@21:1/5 to All on Mon May 5 17:37:34 2025
    On Mon, 05 May 2025 18:49:21 -0400, Joe Gwinn <joegwinn@comcast.net>
    wrote:

    On Mon, 5 May 2025 23:31:47 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-05 15:58, john larkin wrote:
    On Mon, 5 May 2025 13:45:24 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-05 04:50, Don Y wrote:
    On 5/4/2025 1:55 PM, Carlos E.R. wrote:
    On 2025-05-04 22:20, Don Y wrote:
    On 5/4/2025 5:34 AM, Carlos E.R. wrote:
    They have it because they need them more. They run isolated, they >>>>>>>> can not rely on others to smooth their loads. As a result, some >>>>>>>> islands have successfully run for days on solar/wind only.

    Is this just "taken in stride"?á Or, are residents alerted to special >>>>>>> "please be extra conservative in your energy use TODAY" requests? >>>>>>>
    How does storage capacity correlate with "off hours" demand?

    They take it on stride.
    I don't live there, nor have visited. I think that the island that >>>>>> stayed for a month on solar/wind doesn't have heavy industries, not by >>>>>> far.

    So, they did nothing "special" to avoid running out of power for that >>>>> time?á I.e., they were CONFIDENT in their available surplus (day
    AND night) to stick with "life as usual"?

    Well, they had their diesel generators on standby. They did not have to >>>> be confident, they simply were not needed for many days.

    <https://www.endesa.com/es/la-cara-e/energias-renovables/gorona-viento-renovable>

    You can read it with an automated translator.

    The island is small.

    <https://maps.app.goo.gl/p5FfPnhvFVKhRN4C8>

    <https://en.wikipedia.org/wiki/El_Hierro>

    I'm thinking that it doesn't snow there very much. A few days without
    power won't kill many people.

    Wind and solar, with 100% diesel backup, probably makes sense for
    them. Diesel is expensive.

    It doesn't ever snow, look at the map.

    The diesel has been there since ever, it is not the backup. It is the
    main system, but they are very glad to avoid using it now, thanks to
    wind and solar.

    Back in the days of analog telephones over copper wires, the US
    telephone system central offices had lead-acid battery power
    sufficient for 48 hours full operation, plus a diesel backup
    generator. This allowed the diesel to be brought online only as
    needed, and slowly if repair is needed.

    The objective was 0.99999 operational availability, which was usually >achieved in practice.

    Cell phone systems are happy to achieve 0.90000; maybe we can get them
    to 0.99.

    Joe

    My cell phone works at least 99% of the time. Unless it's doing a
    software update.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to Carlos E.R. on Mon May 5 19:47:07 2025
    On 5/5/2025 4:45 AM, Carlos E.R. wrote:
    So, they did nothing "special" to avoid running out of power for that
    time?  I.e., they were CONFIDENT in their available surplus (day
    AND night) to stick with "life as usual"?

    Well, they had their diesel generators on standby. They did not have to be confident, they simply were not needed for many days.

    <https://www.endesa.com/es/la-cara-e/energias-renovables/gorona-viento-renovable>

    You can read it with an automated translator.

    The island is small.

    And, likely, ALL are aware of the potential limitations on available power?
    Do they have some plan already in place to PROMPTLY notify residents of
    an URGENT need to conserve? I.e., so they can react fast enough to
    sudden changes in availability (e.g., gensets can fail, too!)

    Presumably, enlarging the lakes would allow for additional "surplus"
    to be captured?

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to Liz Tuddenham on Mon May 5 19:40:07 2025
    On 5/5/2025 9:35 AM, Liz Tuddenham wrote:
    It will in the UK if all the 'phones need mains power (either at the subscribers' premises or at the masts). Nobody will be able to call out
    the emergency services. How many deaths per day will that be if nobody
    can contact the police, fire brigade or ambulance service?

    In the US, there are many different media used for "telephonic comms".

    - Old land lines (powered by central office battery
    - cell phone (limited backup power at the individual towers)
    - VoIP over cable television service
    - VoIP over (various) wireless services
    - oddball/niche providers (e.g., satellite phones and internet)

    The first is on its way out as the local "phone companies" seem to be
    of a mind to just eke out as much profit from the existing infrastructure without making heavy investments to maintain its viability as an asset.

    [Note there are also "phone company" media that rely on powered
    technologies for the last mile -- SLIC96's, etc.]

    Cell phone is a similarly private investment, not subject to the
    same level of service availability required of the telco providers.
    You get what you pay for.

    Cable television based services are already dubious in their reliability.
    Ask anyone who has had an equipment/service problem about how quickly
    their problem was restored.

    The other VoIP services each have their own vunerabilities and levels
    of commitment/backing.

    But, save for the first (MaBell over copper), you're likely going to see
    some reliance on electric power for continued service.

    There are also many "in home" medical systems that couldn't survive a
    lengthy outage, putting their patients at risk in a prolonged outage
    (you base your backup strategy on the LIKELY outages that you may incur,
    not the POSSIBLE ones -- witness Katrina, 9-11, etc.)

    You also have to consider HOW the outage was caused. E.g., Fukishima
    going off-line resulted in a massive outage in Japan. But, the reason
    for IT going offline also had direct consequences for those same
    populations! (i.e., lack of power may just be ONE of your problems)

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Bill Sloman@21:1/5 to Liz Tuddenham on Tue May 6 16:32:38 2025
    On 6/05/2025 5:04 am, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    On 6/05/2025 2:35 am, Liz Tuddenham wrote:
    john larkin <jl@glen--canyon.com> wrote:

    [...]
    A few days without
    power won't kill many people.

    It will in the UK if all the 'phones need mains power (either at the
    subscribers' premises or at the masts). Nobody will be able to call out >>> the emergency services. How many deaths per day will that be if nobody >>> can contact the police, fire brigade or ambulance service?

    Even politicians can be relied on to be less stupid than that.
    [...]

    There is no evidence to support your claim at the moment.

    There is negative evidence - there haven't been enough deaths that
    anyone can ascribe to political stupidity.

    Covid-19 might be seen as a counter-example - Donald Trump managed to
    get a bigger fraction Americans killed by Covid-19 than Boris Johnson
    did for Britons in the UK - but the sort of ignorance that you envisage
    is a whole lot more thorough-going than anything those two clowns exhibited.

    --
    Bill Sloman, Sydney

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Liz Tuddenham@21:1/5 to Bill Sloman on Tue May 6 08:13:52 2025
    Bill Sloman <bill.sloman@ieee.org> wrote:

    On 6/05/2025 5:04 am, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    On 6/05/2025 2:35 am, Liz Tuddenham wrote:
    john larkin <jl@glen--canyon.com> wrote:

    [...]
    A few days without
    power won't kill many people.

    It will in the UK if all the 'phones need mains power (either at the
    subscribers' premises or at the masts). Nobody will be able to call out >>> the emergency services. How many deaths per day will that be if nobody >>> can contact the police, fire brigade or ambulance service?

    Even politicians can be relied on to be less stupid than that.
    [...]

    There is no evidence to support your claim at the moment.

    There is negative evidence - there haven't been enough deaths that
    anyone can ascribe to political stupidity.

    The conversion to mains-dependency is nowhere near completion yet and
    the change has been so rapid that there haven't been any major power
    cuts during that time.

    It will happen.

    --
    ~ Liz Tuddenham ~
    (Remove the ".invalid"s and add ".co.uk" to reply)
    www.poppyrecords.co.uk

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Martin Brown@21:1/5 to Liz Tuddenham on Tue May 6 10:25:41 2025
    On 05/05/2025 17:35, Liz Tuddenham wrote:
    john larkin <jl@glen--canyon.com> wrote:

    [...]
    A few days without
    power won't kill many people.

    It will in the UK if all the 'phones need mains power (either at the subscribers' premises or at the masts). Nobody will be able to call out

    Rural phone masts last about 24 hours without power before they go dark.
    IDK if it is the same in cities. More of a problem is that the removal
    of POTS copper circuits in favour of FTTC VDSL or fibre means that
    without electricity even a fixed line phone is dead in the water. DECT
    ones obviously don't work at all and neither does care on call.

    Mobile phones need to be put into airplane mode to avoid them doing ET
    phone home until their battery runs out when there is no mobile signal.

    POTS phones on direct copper continued to work using power from
    emergency batteries and/or generators at the exchange. That is no longer
    true for modern telecoms kit which requires mains power for FTTC box.

    Amazingly fibre to premises can still work OK in a power cut since that
    is actually powered off the reserve supply back at the main exchange. Advantages of having a UPS at home.

    the emergency services. How many deaths per day will that be if nobody
    can contact the police, fire brigade or ambulance service?

    Not that many if our region is characteristic.

    We were off power for 48 hours in storm Arwen. Places nearby were off
    grid for one or two weeks. They had "saved" money by cutting back on preventative maintenance so that when a pole failed in the wind it went
    over with enough force to make its equally feeble neighbours fall like dominoes. Took a lot of hard work to re-establish supply.

    It was very a serious MFU. But it happened in the north so that's OK.

    --
    Martin Brown

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Martin Brown on Tue May 6 12:26:36 2025
    On 2025-05-06 11:25, Martin Brown wrote:

    Amazingly fibre to premises can still work OK in a power cut since that
    is actually powered off the reserve supply back at the main exchange. Advantages of having a UPS at home.

    Here there are boxes on the walls of the city blocks, where one fibre
    from the exchange is divided into half a dozen (exact number unknown to
    me). I don't know if these boxes are passive or active.

    <https://www.google.com/imgres?q=cajas%20de%20reparto%20de%20fibra%20telefonica&imgurl=https%3A%2F%2Fcomunidad.movistar.es%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F111764iC1F6FAD7948695D6%3Fv%3Dv2&imgrefurl=https%3A%2F%2Fcomunidad.movistar.es%2Ft5%
    2FSoporte-Fibra-y-ADSL%2FINSTALACION-CAJA-DISTRIBUIDORA-DE-FIBRA-EN-EXTERIOR-DEL-EDIFICIO%2Ftd-p%2F2929655&docid=zZHuHCpt8An46M&tbnid=0T2mKKO1TLeZFM&vet=12ahUKEwiN9onmz46NAxXYVqQEHYnHDk4QM3oECHMQAA..i&w=914&h=611&hcb=2&ved=
    2ahUKEwiN9onmz46NAxXYVqQEHYnHDk4QM3oECHMQAA>

    <https://www.change.org/p/movistar-cambien-cto-caja-donde-se-conecta-la-fibra-optica-para-poder-realizar-mis-estudios>


    I could not test if my landline phone worked during the outage because
    my local UPS went down too soon.

    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Don Y on Tue May 6 12:32:03 2025
    On 2025-05-06 04:47, Don Y wrote:
    On 5/5/2025 4:45 AM, Carlos E.R. wrote:
    So, they did nothing "special" to avoid running out of power for that
    time?  I.e., they were CONFIDENT in their available surplus (day
    AND night) to stick with "life as usual"?

    Well, they had their diesel generators on standby. They did not have
    to be confident, they simply were not needed for many days.

    <https://www.endesa.com/es/la-cara-e/energias-renovables/gorona-
    viento-renovable>

    You can read it with an automated translator.

    The island is small.

    And, likely, ALL are aware of the potential limitations on available power? Do they have some plan already in place to PROMPTLY notify residents of
    an URGENT need to conserve?  I.e., so they can react fast enough to
    sudden changes in availability (e.g., gensets can fail, too!)

    Not that I know.

    They would just start as many generators as needed to meet the demand up
    to contracted capacity, if the pumped storage wouldn't be enough. Same
    as anywhere else.


    Presumably, enlarging the lakes would allow for additional "surplus"
    to be captured?



    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Martin Brown@21:1/5 to Carlos E.R. on Tue May 6 13:27:26 2025
    On 06/05/2025 11:26, Carlos E.R. wrote:
    On 2025-05-06 11:25, Martin Brown wrote:

    Amazingly fibre to premises can still work OK in a power cut since
    that is actually powered off the reserve supply back at the main
    exchange.
    Advantages of having a UPS at home.

    Here there are boxes on the walls of the city blocks, where one fibre
    from the exchange is divided into half a dozen (exact number unknown to
    me). I don't know if these boxes are passive or active.

    <https://www.google.com/imgres?q=cajas%20de%20reparto%20de%20fibra%20telefonica&imgurl=https%3A%2F%2Fcomunidad.movistar.es%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F111764iC1F6FAD7948695D6%3Fv%3Dv2&imgrefurl=https%3A%2F%2Fcomunidad.movistar.es%2Ft5%
    2FSoporte-Fibra-y-ADSL%2FINSTALACION-CAJA-DISTRIBUIDORA-DE-FIBRA-EN-EXTERIOR-DEL-EDIFICIO%2Ftd-p%2F2929655&docid=zZHuHCpt8An46M&tbnid=0T2mKKO1TLeZFM&vet=12ahUKEwiN9onmz46NAxXYVqQEHYnHDk4QM3oECHMQAA..i&w=914&h=611&hcb=2&ved=
    2ahUKEwiN9onmz46NAxXYVqQEHYnHDk4QM3oECHMQAA>

    <https://www.change.org/p/movistar-cambien-cto-caja-donde-se-conecta-la-fibra-optica-para-poder-realizar-mis-estudios>

    Your splitter boxes look to me like they might be powered.

    The ones in the UK look to be entirely passive optical connectors taking
    in about 8 consumer fibres each down to one exchange fibre. They sit in
    places with no mains power. You have to look quite hard to tell them
    apart from the ones used for copper circuits. Many fibre to premises
    drop lines actually use a dual copper and fibre line in a figure of 8 so
    you can tell who has a fibre circuit by looking at the line if it is
    above ground. It looks like a whirly gig with a profile -=--=--=--=--

    The rural ones look a bit like a black plastic policeman's helmet with
    one line in and 8 lines out.

    I could not test if my landline phone worked during the outage because
    my local UPS went down too soon.

    Fibre stayed good through our powercut for as long as the UPS lasted.

    --
    Martin Brown

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Carlos E.R. on Tue May 6 14:23:10 2025
    On 2025-05-06 12:26, Carlos E.R. wrote:
    On 2025-05-06 11:25, Martin Brown wrote:

    Amazingly fibre to premises can still work OK in a power cut since
    that is actually powered off the reserve supply back at the main
    exchange.
    Advantages of having a UPS at home.

    Here there are boxes on the walls of the city blocks, where one fibre
    from the exchange is divided into half a dozen (exact number unknown to
    me). I don't know if these boxes are passive or active.

    <https://www.google.com/imgres? q=cajas%20de%20reparto%20de%20fibra%20telefonica&imgurl=https%3A%2F%2Fcomunidad.movistar.es%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F111764iC1F6FAD7948695D6%3Fv%3Dv2&imgrefurl=https%3A%2F%2Fcomunidad.movistar.es%2Ft5%2FSoporte-Fibra-y-ADSL%2FINSTALACION-
    CAJA-DISTRIBUIDORA-DE-FIBRA-EN-EXTERIOR-DEL-EDIFICIO%2Ftd-p%2F2929655&docid=zZHuHCpt8An46M&tbnid=0T2mKKO1TLeZFM&vet=12ahUKEwiN9onmz46NAxXYVqQEHYnHDk4QM3oECHMQAA..i&w=914&h=611&hcb=2&ved=2ahUKEwiN9onmz46NAxXYVqQEHYnHDk4QM3oECHMQAA>

    <https://www.change.org/p/movistar-cambien-cto-caja-donde-se-conecta-la- fibra-optica-para-poder-realizar-mis-estudios>


    I could not test if my landline phone worked during the outage because
    my local UPS went down too soon.


    I found another link that explains the system. Not sure if this is what everybody here has, but I think yes.

    <https://bandaancha.eu/articulos/puede-fibra-realmente-dar-1gb-simetrico-9834>


    GPON
    16 fibres [exchange]-------[splitter]-----------------[CTO 1:16]---/-------> home
    1:4 \---
    \---
    \---

    Results in 2.488,32 Mbps divided between 64 clients. So, if the other
    clients are not busy, you get the gigabit stream.

    «With this architecture, the laser light coming from the OLT located in
    the central unit simultaneously illuminates the 64 ONTs, passing through
    the two levels of division mentioned above. In order for each ONT to
    receive its information, the GPON standard divides each second into
    8,000 fragments of 125 microseconds, which are dynamically assigned to
    each ONT depending on the throughput requested and available. All of
    them will receive the signal, but they will only be able to read the information that corresponds to them, since the information of the other
    users is encrypted.

    Translated with DeepL.com (free version)»

    It is time multiplexing again, not routing. This way the splitter can be optical, no electronics needed — this is my guess, the article doesn't say.

    <https://en.wikipedia.org/wiki/GPON>
    <https://es.wikipedia.org/wiki/GPON>

    The Spanish Wikipedia has a different content, and says this:


    «Downstream - Broadcast

    All data is transmitted to all ONTs (the splitter is a passive element
    that simply replicates the input data to all outputs). Each ONT filters
    the received data (it only keeps the data that is directed to it). It
    has the problem that the operator/user may want confidentiality of the
    data, which is solved by encrypting the data.


    Upstream - TDMA

    Conceptually similar technology to TDMA (Time Division Multiple Access)
    is used. The OLT controls the upstream channel, allocating time windows
    to the ONTs. Medium access control is required to avoid collisions and
    to distribute bandwidth among users.

    As the optical splitter is a passive element, perfect synchronisation of
    the incoming upstream packets is necessary for it to be able to form the
    GPON frame. It is therefore necessary for the OLT to know the distance
    between the ONTs to take the delay into account.

    Translated with DeepL.com (free version)»


    The other article says that upstream with Movistar each client has
    actually 19,44 Mb



    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Joe Gwinn@21:1/5 to robin_listas@es.invalid on Tue May 6 10:42:24 2025
    On Tue, 6 May 2025 02:18:44 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-06 00:49, Joe Gwinn wrote:
    On Mon, 5 May 2025 23:31:47 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-05 15:58, john larkin wrote:
    On Mon, 5 May 2025 13:45:24 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-05 04:50, Don Y wrote:
    On 5/4/2025 1:55 PM, Carlos E.R. wrote:
    On 2025-05-04 22:20, Don Y wrote:
    On 5/4/2025 5:34 AM, Carlos E.R. wrote:
    They have it because they need them more. They run isolated, they >>>>>>>>> can not rely on others to smooth their loads. As a result, some >>>>>>>>> islands have successfully run for days on solar/wind only.

    Is this just "taken in stride"?á Or, are residents alerted to special >>>>>>>> "please be extra conservative in your energy use TODAY" requests? >>>>>>>>
    How does storage capacity correlate with "off hours" demand?

    They take it on stride.
    I don't live there, nor have visited. I think that the island that >>>>>>> stayed for a month on solar/wind doesn't have heavy industries, not by >>>>>>> far.

    So, they did nothing "special" to avoid running out of power for that >>>>>> time?á I.e., they were CONFIDENT in their available surplus (day
    AND night) to stick with "life as usual"?

    Well, they had their diesel generators on standby. They did not have to >>>>> be confident, they simply were not needed for many days.

    <https://www.endesa.com/es/la-cara-e/energias-renovables/gorona-viento-renovable>

    You can read it with an automated translator.

    The island is small.

    <https://maps.app.goo.gl/p5FfPnhvFVKhRN4C8>

    <https://en.wikipedia.org/wiki/El_Hierro>

    I'm thinking that it doesn't snow there very much. A few days without
    power won't kill many people.

    Wind and solar, with 100% diesel backup, probably makes sense for
    them. Diesel is expensive.

    It doesn't ever snow, look at the map.

    The diesel has been there since ever, it is not the backup. It is the
    main system, but they are very glad to avoid using it now, thanks to
    wind and solar.

    Back in the days of analog telephones over copper wires, the US
    telephone system central offices had lead-acid battery power
    sufficient for 48 hours full operation, plus a diesel backup
    generator. This allowed the diesel to be brought online only as
    needed, and slowly if repair is needed.

    The objective was 0.99999 operational availability, which was usually
    achieved in practice.

    I know. I worked with the 5. :-)

    Ahh. I did wonder. All the big telcos of that day did roughly the
    same thing, largely dictated by the technology of the day.

    Joe



    Cell phone systems are happy to achieve 0.90000; maybe we can get them
    to 0.99.

    Joe

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Martin Brown on Tue May 6 18:56:42 2025
    On 2025-05-06 14:27, Martin Brown wrote:
    On 06/05/2025 11:26, Carlos E.R. wrote:
    On 2025-05-06 11:25, Martin Brown wrote:

    Amazingly fibre to premises can still work OK in a power cut since
    that is actually powered off the reserve supply back at the main
    exchange.
    Advantages of having a UPS at home.

    Here there are boxes on the walls of the city blocks, where one fibre
    from the exchange is divided into half a dozen (exact number unknown
    to me). I don't know if these boxes are passive or active.

    <https://www.google.com/imgres?
    q=cajas%20de%20reparto%20de%20fibra%20telefonica&imgurl=https%3A%2F%2Fcomunidad.movistar.es%2Ft5%2Fimage%2Fserverpage%2Fimage-id%2F111764iC1F6FAD7948695D6%3Fv%3Dv2&imgrefurl=https%3A%2F%2Fcomunidad.movistar.es%2Ft5%2FSoporte-Fibra-y-ADSL%2FINSTALACION-
    CAJA-DISTRIBUIDORA-DE-FIBRA-EN-EXTERIOR-DEL-EDIFICIO%2Ftd-p%2F2929655&docid=zZHuHCpt8An46M&tbnid=0T2mKKO1TLeZFM&vet=12ahUKEwiN9onmz46NAxXYVqQEHYnHDk4QM3oECHMQAA..i&w=914&h=611&hcb=2&ved=2ahUKEwiN9onmz46NAxXYVqQEHYnHDk4QM3oECHMQAA>

    <https://www.change.org/p/movistar-cambien-cto-caja-donde-se-conecta-
    la-fibra-optica-para-poder-realizar-mis-estudios>

    Your splitter boxes look to me like they might be powered.

    They do, but then I found an article that describes the system and it is optical, passive. GPON.

    ...

    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to All on Tue May 6 14:52:25 2025
    Your splitter boxes look to me like they might be powered.

    They do, but then I found an article that describes the system and it is optical, passive. GPON.

    The fallacy, of course, is that anything between you and where you
    want to "go" that is NOT powered limits your reach.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Don Y on Wed May 7 13:04:40 2025
    On 2025-05-06 23:52, Don Y wrote:
    Your splitter boxes look to me like they might be powered.

    They do, but then I found an article that describes the system and it
    is optical, passive. GPON.

    The fallacy, of course, is that anything between you and where you
    want to "go" that is NOT powered limits your reach.



    I couldn't test, my own UPS failed too soon.

    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to Carlos E.R. on Wed May 7 05:09:56 2025
    On 5/7/2025 4:04 AM, Carlos E.R. wrote:
    On 2025-05-06 23:52, Don Y wrote:
    Your splitter boxes look to me like they might be powered.

    They do, but then I found an article that describes the system and it is >>> optical, passive. GPON.

    The fallacy, of course, is that anything between you and where you
    want to "go" that is NOT powered limits your reach.

    I couldn't test, my own UPS failed too soon.

    I suspect it would be hard to get a definitive answer.
    Can you get out of the city? "State"? Country? etc.
    Without knowing the extent of an outage -- and the
    reliance on power that exists for each step up the
    ladder -- it would be hard to generalize your capabilities
    from "simple tests".

    Much like me having carrier doesn't tell me the extent of
    my "reach", here.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Don Y on Wed May 7 14:30:42 2025
    On 2025-05-07 14:09, Don Y wrote:
    On 5/7/2025 4:04 AM, Carlos E.R. wrote:
    On 2025-05-06 23:52, Don Y wrote:
    Your splitter boxes look to me like they might be powered.

    They do, but then I found an article that describes the system and
    it is optical, passive. GPON.

    The fallacy, of course, is that anything between you and where you
    want to "go" that is NOT powered limits your reach.

    I couldn't test, my own UPS failed too soon.

    I suspect it would be hard to get a definitive answer.
    Can you get out of the city?  "State"?  Country?  etc.
    Without knowing the extent of an outage -- and the
    reliance on power that exists for each step up the
    ladder -- it would be hard to generalize your capabilities
    from "simple tests".

    Much like me having carrier doesn't tell me the extent of
    my "reach", here.

    Well, the power outage was "total". :-D

    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to Carlos E.R. on Wed May 7 06:17:48 2025
    On 5/7/2025 5:30 AM, Carlos E.R. wrote:
    On 2025-05-07 14:09, Don Y wrote:
    On 5/7/2025 4:04 AM, Carlos E.R. wrote:
    On 2025-05-06 23:52, Don Y wrote:
    Your splitter boxes look to me like they might be powered.

    They do, but then I found an article that describes the system and it is >>>>> optical, passive. GPON.

    The fallacy, of course, is that anything between you and where you
    want to "go" that is NOT powered limits your reach.

    I couldn't test, my own UPS failed too soon.

    I suspect it would be hard to get a definitive answer.
    Can you get out of the city?  "State"?  Country?  etc.
    Without knowing the extent of an outage -- and the
    reliance on power that exists for each step up the
    ladder -- it would be hard to generalize your capabilities
    from "simple tests".

    Much like me having carrier doesn't tell me the extent of
    my "reach", here.

    Well, the power outage was "total". :-D

    Yeah, but you don't know which services (up the chain) may
    have their own *local*/private backup systems. E.g., I doubt
    your hospitals were without power (?) The extent of backup
    beyond that would be something you'd have to know, in advance.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Liz Tuddenham@21:1/5 to Bill Sloman on Wed May 7 17:48:11 2025
    Bill Sloman <bill.sloman@ieee.org> wrote:

    On 6/05/2025 5:13 pm, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    On 6/05/2025 5:04 am, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    On 6/05/2025 2:35 am, Liz Tuddenham wrote:
    john larkin <jl@glen--canyon.com> wrote:

    <snip>

    Even politicians can be relied on to be less stupid than that.
    [...]

    There is no evidence to support your claim at the moment.

    There is negative evidence - there haven't been enough deaths that
    anyone can ascribe to political stupidity.

    The conversion to mains-dependency is nowhere near completion yet and
    the change has been so rapid that there haven't been any major power
    cuts during that time.

    It will happen.

    Liz Tuddenham, prophet.

    Anything that can go wrong - will.
    Anything that can't go wrong - will eventually.
    Anything that doesn't go wrong eventually hasn't been tested long
    enough.


    --
    ~ Liz Tuddenham ~
    (Remove the ".invalid"s and add ".co.uk" to reply)
    www.poppyrecords.co.uk

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Bill Sloman@21:1/5 to Liz Tuddenham on Thu May 8 02:30:39 2025
    On 6/05/2025 5:13 pm, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    On 6/05/2025 5:04 am, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    On 6/05/2025 2:35 am, Liz Tuddenham wrote:
    john larkin <jl@glen--canyon.com> wrote:

    <snip>

    Even politicians can be relied on to be less stupid than that.
    [...]

    There is no evidence to support your claim at the moment.

    There is negative evidence - there haven't been enough deaths that
    anyone can ascribe to political stupidity.

    The conversion to mains-dependency is nowhere near completion yet and
    the change has been so rapid that there haven't been any major power
    cuts during that time.

    It will happen.

    Liz Tuddenham, prophet.

    Back-up power isn't actually a political question. It gets written into specifications for particular jobs - nothing I've been directly involved
    with, but there is a lively business in providing it.

    https://en.wikipedia.org/wiki/Uninterruptible_power_supply

    It's part of the background that politicians don't bother paying
    attention to, because if the engineers and administrators do their jobs,
    the politicians don't get to hear about it.

    --
    Bill Sloman, Sydney

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Don Y on Wed May 7 22:55:42 2025
    On 2025-05-07 15:17, Don Y wrote:
    On 5/7/2025 5:30 AM, Carlos E.R. wrote:
    On 2025-05-07 14:09, Don Y wrote:
    On 5/7/2025 4:04 AM, Carlos E.R. wrote:
    On 2025-05-06 23:52, Don Y wrote:
    Your splitter boxes look to me like they might be powered.

    They do, but then I found an article that describes the system and >>>>>> it is optical, passive. GPON.

    The fallacy, of course, is that anything between you and where you
    want to "go" that is NOT powered limits your reach.

    I couldn't test, my own UPS failed too soon.

    I suspect it would be hard to get a definitive answer.
    Can you get out of the city?  "State"?  Country?  etc.
    Without knowing the extent of an outage -- and the
    reliance on power that exists for each step up the
    ladder -- it would be hard to generalize your capabilities
    from "simple tests".

    Much like me having carrier doesn't tell me the extent of
    my "reach", here.

    Well, the power outage was "total". :-D

    Yeah, but you don't know which services (up the chain) may
    have their own *local*/private backup systems.  E.g., I doubt
    your hospitals were without power (?)  The extent of backup
    beyond that would be something you'd have to know, in advance.

    If the fibre goes direct to the exchange, they had backup power.
    However, if the distance is great and they have to reconstruct the
    signal with some kind of optical amplifier, then I don't know. The
    distance is about 2.5 Km.


    My mobile phone worked all the day, I could send and receive whatsapp
    messages.

    I have a small computer doing server things, and it tried to email me as
    soon as the UPS said it was running on battery. That email did not reach
    me till the power came back; this could be that the fibre went OOS, or
    that the UPS at my router went down instantly. I do not know.

    I'm considering replacing the UPS at my router. Some UPS "destroy" the
    battery too fast.

    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to All on Wed May 7 16:01:09 2025
    Much like me having carrier doesn't tell me the extent of
    my "reach", here.

    Well, the power outage was "total". :-D

    Yeah, but you don't know which services (up the chain) may
    have their own *local*/private backup systems.  E.g., I doubt
    your hospitals were without power (?)  The extent of backup
    beyond that would be something you'd have to know, in advance.

    If the fibre goes direct to the exchange, they had backup power. However, if the distance is great and they have to reconstruct the signal with some kind of
    optical amplifier, then I don't know. The distance is about 2.5 Km.

    But where can exchange traffic go? See what I mean? Anyone that
    you want to contact (and everyone along the way) must be "up".

    My mobile phone worked all the day, I could send and receive whatsapp messages.

    Are those processed "locally"?

    I have a small computer doing server things, and it tried to email me as soon as the UPS said it was running on battery. That email did not reach me till the
    power came back; this could be that the fibre went OOS, or that the UPS at my router went down instantly. I do not know.

    Doesn't your UPS deliver log messages (to a syslog server or data
    dumps to an FTP service)?

    I have each of mine configured to give me summaries of power consumption
    and line conditions each minute. And, use a syslogd on that same server.

    I'm considering replacing the UPS at my router. Some UPS "destroy" the battery
    too fast.

    Yes. Rather than spend time investigating it, I've taken the approach
    of just rescuing batteries to replace those that have been "cooked".

    I suspect the problem (rationalized by the manufacturers) is trying to
    bring the battery back to full charge ASAP -- as well as keeping the
    highest state of charge that the battery can support.

    Charging at a slower rate and to a lower float voltage would
    compromise the UPS's availability -- but provide less maintenance costs
    (of course, the manufacturer wants to sell you batteries, so you
    can see where their priorities will lie!)

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Waldek Hebisch@21:1/5 to Liz Tuddenham on Thu May 8 00:59:14 2025
    Liz Tuddenham <liz@poppyrecords.invalid.invalid> wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    On 3/05/2025 12:43 am, john larkin wrote:
    On Thu, 1 May 2025 11:24:13 +0100, liz@poppyrecords.invalid.invalid
    (Liz Tuddenham) wrote:

    Chris Jones <lugnut808@spam.yahoo.com> wrote:


    There is nothing magic about the current from a rotating generator that >> >>> cannot be exactly replicated by an inverter ...

    Inertia. Not magic but physics. A store of energy that can be drawn
    on instantly for several seconds. Only an inverter with a massive
    energy storage system could match that; domestic systems can't.

    A boiler full of superheated water stores a lot of energy too. And
    hydraulic steam valve actuators move fast.

    Not all that fast. 50Hz is probably more than they could track. 60Hz
    would be even more difficult.

    They have no problem at a few cycles per second, as London Transport discovered in the early days of computers.

    London Transport was powered by Lotts Road Power Station. The load was mainly underground electric railways, trams and trolleybuses. but they
    took the electricity supply for their offices from there too. The first computer they installed kept crashing and the problem was traced to dips
    in the power supply rails.

    After a lot of investigation, they discovered that the AC mains supply
    had alternate (or perhaps every third) cycles much lower in voltage than
    the others (and I think there must have been a timing error too). The
    power supply smoothing capacitors were unable to store enough energy to
    tide them over the dips and the result was a regular dropping of the 'stabilised' supply rails.

    The fault was traced back to Lotts Road, where it was found that a steam valve was constantly cycling due to an unstable control loop. This
    hadn't had any effect on the trams, so nobody had bothered to do
    anything about it.

    Conclusion:
    A tram stores more energy than a computer capacitor bank.

    That does not look true. Reasonably sized generator have a lot
    of inertia, so large changes on few cycle basis would mean huge
    forces and are likely impossible by changing steam flow. Even
    smaller, but fast changes would mean extra mechanical stress, so
    probably would be worth to fix (to get expected equpement life).

    If the story about computer crashes is true, there are more
    likely reasons. Our physicits got a building that was previously
    used by communist party. They had trouble with electricity
    supply. On osciloscopes they could see really awful waveforms.
    A little investigation showed that the building had common
    connection with rectifiers for trams (our trams use DC).
    Advantage of this was that power for trams was switched off
    only after everthing else in the city, so this was most
    reliable power nearby. But waveform caused trouble for
    computers and scientific equipement.

    --
    Waldek Hebisch

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Bill Sloman@21:1/5 to Liz Tuddenham on Thu May 8 15:54:21 2025
    On 8/05/2025 2:48 am, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    On 6/05/2025 5:13 pm, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    On 6/05/2025 5:04 am, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    On 6/05/2025 2:35 am, Liz Tuddenham wrote:
    john larkin <jl@glen--canyon.com> wrote:

    <snip>

    Even politicians can be relied on to be less stupid than that.
    [...]

    There is no evidence to support your claim at the moment.

    There is negative evidence - there haven't been enough deaths that
    anyone can ascribe to political stupidity.

    The conversion to mains-dependency is nowhere near completion yet and
    the change has been so rapid that there haven't been any major power
    cuts during that time.

    It will happen.

    Liz Tuddenham, prophet.

    Anything that can go wrong - will.

    That's what the uninterruptible power supply business exists to deal with.

    Anything that can't go wrong - will eventually.

    But redundancy can make it very unlikely that they'll all go wrong at
    the same time.

    Anything that doesn't go wrong eventually hasn't been tested long
    enough.

    Perfectly true, but since the human life-time is finite, it may not be
    all that relevant.

    --
    Bill Sloman, Sydney

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Martin Brown@21:1/5 to Don Y on Thu May 8 11:57:39 2025
    On 08/05/2025 00:01, Don Y wrote:
    Much like me having carrier doesn't tell me the extent of
    my "reach", here.

    Well, the power outage was "total". :-D

    Yeah, but you don't know which services (up the chain) may
    have their own *local*/private backup systems.  E.g., I doubt
    your hospitals were without power (?)  The extent of backup
    beyond that would be something you'd have to know, in advance.

    If the fibre goes direct to the exchange, they had backup power.
    However, if the distance is great and they have to reconstruct the
    signal with some kind of optical amplifier, then I don't know. The
    distance is about 2.5 Km.

    But where can exchange traffic go?  See what I mean?  Anyone that
    you want to contact (and everyone along the way) must be "up".

    That was the original point of ARPANET then EPSS and later the internet.
    Packet switching means that any route to the destination at all will do.

    I'm told that my fibre feed is passive optical connectors and splices
    all the way back the regional exchange about 12 miles away. My local
    exchange was about 5 miles away and a so-called exchange only direct
    line (which meant that ADSL 2+ was the limit for me prior to FTTP).

    My mobile phone worked all the day, I could send and receive whatsapp
    messages.

    Are those processed "locally"?

    Mobile phone masts here typically have a lifetime of about 8-40 hours
    after power failure depending on how heavily they are being used.
    Backhaul presumably is optical or microwave.

    Most powercuts tend to be fairly local round here - a regional powercut
    or a national one requires something truly catastrophic to happen.

    I can only recall one UK powercut in that league in the past half
    century (August 9 2019). Of course it directly affected the densely
    populated affluent regions London and the South East. Therefore it was
    much more newsworthy than if it had affected the remote Scottish
    Highlands where weather induced powercuts are quite common.

    The recent big one at Heathrow didn't affect all that many people
    although it did take down the whole airport which shows remarkably bad contingency planning - it should have had supply redundancy and the
    ability to switchover to it before the diesel generators ran out of
    fuel. Heads should roll over them having to shut down completely.

    I have a small computer doing server things, and it tried to email me
    as soon as the UPS said it was running on battery. That email did not
    reach me till the power came back; this could be that the fibre went
    OOS, or that the UPS at my router went down instantly. I do not know.

    Doesn't your UPS deliver log messages (to a syslog server or data
    dumps to an FTP service)?

    I have each of mine configured to give me summaries of power consumption
    and line conditions each minute.  And, use a syslogd on that same server.

    I only log external power failures. Kitchen appliance clocks all reset
    when we lose power for more than a couple of seconds.

    I'm considering replacing the UPS at my router. Some UPS "destroy" the
    battery too fast.

    Yes.  Rather than spend time investigating it, I've taken the approach
    of just rescuing batteries to replace those that have been "cooked".

    That is a feature of UPS design that specsmanship to get the longest run
    time for the sales datasheet means that they cook their batteries. I
    have seen them swell to the point of bursting inside a UPS. Thick rubber
    gloves needed to remove the remains. Support metalwork was a real
    corroded rusty mess but electronics above it remained OK.

    I suspect the problem (rationalized by the manufacturers) is trying to
    bring the battery back to full charge ASAP -- as well as keeping the
    highest state of charge that the battery can support.

    Which taken to extremes is very bad for battery life.

    Charging at a slower rate and to a lower float voltage would
    compromise the UPS's availability -- but provide less maintenance costs
    (of course, the manufacturer wants to sell you batteries, so you
    can see where their priorities will lie!)

    They really think I'm going to buy their vastly overpriced replacements?

    --
    Martin Brown

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to All on Thu May 8 04:49:02 2025
    But where can exchange traffic go?  See what I mean?  Anyone that
    you want to contact (and everyone along the way) must be "up".

    That was the original point of ARPANET then EPSS and later the internet. Packet
    switching means that any route to the destination at all will do.

    But that assumes there *is* a series of hops that can get you "there"... wherever "there" happens to be. In a nationwide outage, what chance
    that everything EXCEPT some critical bit of comms gear is affected?

    I'm told that my fibre feed is passive optical connectors and splices all the way back the regional exchange about 12 miles away. My local exchange was about
    5 miles away and a so-called exchange only direct line (which meant that ADSL 2+ was the limit for me prior to FTTP).

    So, you rely on the exchange having upstream connectivity. Along
    with the fiber link TO the exchange.

    My mobile phone worked all the day, I could send and receive whatsapp messages.

    Are those processed "locally"?

    Mobile phone masts here typically have a lifetime of about 8-40 hours after power failure depending on how heavily they are being used. Backhaul presumably
    is optical or microwave.

    So, also subject to outage.

    Most powercuts tend to be fairly local round here - a regional powercut or a national one requires something truly catastrophic to happen.

    I can only recall one UK powercut in that league in the past half century (August 9 2019). Of course it directly affected the densely populated affluent
    regions London and the South East. Therefore it was much more newsworthy than if it had affected the remote Scottish Highlands where weather induced powercuts are quite common.

    I don't think I've ever (regardless of where I've lived) experienced
    a deliberate power cut. A drunk may take out a telephone pole or
    a branch may fall on some high tension wires but no one has ever
    said "sorry, we're turning the lights out" (for whatever reason)

    The recent big one at Heathrow didn't affect all that many people although it did take down the whole airport which shows remarkably bad contingency planning
    - it should have had supply redundancy and the ability to switchover to it before the diesel generators ran out of fuel. Heads should roll over them having to shut down completely.

    Fukishima?

    I have a small computer doing server things, and it tried to email me as >>> soon as the UPS said it was running on battery. That email did not reach me >>> till the power came back; this could be that the fibre went OOS, or that the
    UPS at my router went down instantly. I do not know.

    Doesn't your UPS deliver log messages (to a syslog server or data
    dumps to an FTP service)?

    I have each of mine configured to give me summaries of power consumption
    and line conditions each minute.  And, use a syslogd on that same server.

    I only log external power failures. Kitchen appliance clocks all reset when we
    lose power for more than a couple of seconds.

    Each UPS has a link to my syslogd (the switches and that server being backed
    up in the event of power outages).

    I additionally configure them to report their loads every minute (to get
    a feel for where I'm "doing work" as well as how heavily each is taxed.

    I'm considering replacing the UPS at my router. Some UPS "destroy" the
    battery too fast.

    Yes.  Rather than spend time investigating it, I've taken the approach
    of just rescuing batteries to replace those that have been "cooked".

    That is a feature of UPS design that specsmanship to get the longest run time for the sales datasheet means that they cook their batteries. I have seen them
    swell to the point of bursting inside a UPS. Thick rubber gloves needed to remove the remains. Support metalwork was a real corroded rusty mess but electronics above it remained OK.

    Yup. They have a rationalization, though -- they are trying to provide the highest availability. Else, how much availability do you sacrifice to
    maximize battery life? Do you then start specifying battery life as a
    primary selection criteria?

    [Most SOHO users buy a UPS -- thinking they are being "professional" -- and then discard it when the battery needs replacing and they discover the
    costs charged by the UPS manufacturer -- or local "battery stores"]

    I suspect the problem (rationalized by the manufacturers) is trying to
    bring the battery back to full charge ASAP -- as well as keeping the
    highest state of charge that the battery can support.

    Which taken to extremes is very bad for battery life.

    Of course. But, they are in the PRIMARY business of selling batteries,
    not UPSs!

    Charging at a slower rate and to a lower float voltage would
    compromise the UPS's availability -- but provide less maintenance costs
    (of course, the manufacturer wants to sell you batteries, so you
    can see where their priorities will lie!)

    They really think I'm going to buy their vastly overpriced replacements?

    If you were a business, it would just be a maintenance expense.
    You would budget for it. If SOHO, you'd likely replace it at
    most once and then realize "Gee, I haven't NEEDED this in the
    past three years so why am I spending more money on it?"

    With the exception of multi-user servers, individual workstations
    usually have auto-backup provisions *in* the key applications.
    And, in the event of an outage (even if the machine stays up),
    the user is usually distracted by the rest of the house/office
    going black; is ~15 minutes of uptime going to be enough if the
    user isn't AT the machine when power fails?

    No one has yet to address the market where TCO is the driving
    criteria.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Miguel Gimenez@21:1/5 to All on Thu May 8 14:31:08 2025
    El 02/05/2025 a las 23:30, Carlos E.R. escribió:
    On 2025-05-02 12:28, Martin Brown wrote:
    On 01/05/2025 21:13, Carlos E.R. wrote:
    On 2025-04-29 14:24, Martin Brown wrote:
    Spain suffered a very spectacular near total loss of its national
    grid yesterday taking parts of France and all of Portugal down with
    it. This is an unprecedented failure of a supergrid system by
    cascade failure.

    I should say, although too late, that it should be "Gran Apagón" :-)

    Sorry about that. I remember the phrase from my astronomy days when
    the Gran Canary were persuaded to go completely dark for one night
    only so that the Isaac Newton telescope on its peak could do something
    special.

    Don't worry :-)


    It gave everyone there an opportunity to see a truly dark sky.

    Links to it back in 1985 are now very thin on the ground. An article
    celebrating 10th anniversary is the best I can find in English page
    31. (sorry its very big)




    As a side note, the Apagón made all my DCF-77 clocks synchronize
    inmediately. Usually Madrid has reception problems, taking even weeks to synchronize, but looks like it is more an interference issue than the
    distance to Mainflingen.

    --
    Saludos
    Miguel Gimenez

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Martin Brown@21:1/5 to Don Y on Thu May 8 13:43:12 2025
    On 08/05/2025 12:49, Don Y wrote:
    But where can exchange traffic go?  See what I mean?  Anyone that
    you want to contact (and everyone along the way) must be "up".

    That was the original point of ARPANET then EPSS and later the
    internet. Packet switching means that any route to the destination at
    all will do.

    But that assumes there *is* a series of hops that can get you "there"... wherever "there" happens to be.  In a nationwide outage, what chance
    that everything EXCEPT some critical bit of comms gear is affected?

    Nationwide outages should be exceptionally rare. Never had one in the UK
    but the way they are going one winter's day it will happen.

    I'm told that my fibre feed is passive optical connectors and splices
    all the way back the regional exchange about 12 miles away. My local
    exchange was about 5 miles away and a so-called exchange only direct
    line (which meant that ADSL 2+ was the limit for me prior to FTTP).

    So, you rely on the exchange having upstream connectivity.  Along
    with the fiber link TO the exchange.

    That is usually a given since the regional and further up the chain concentrators all have UPS and diesel generators or fuel cell supply.

    My mobile phone worked all the day, I could send and receive
    whatsapp messages.

    Are those processed "locally"?

    Mobile phone masts here typically have a lifetime of about 8-40 hours
    after power failure depending on how heavily they are being used.
    Backhaul presumably is optical or microwave.

    So, also subject to outage.

    But the central nodes usually have better battery backup and/or
    generators than the local nodes. Local nodes die first according to how
    much traffic they have to handle.

    Most powercuts tend to be fairly local round here - a regional
    powercut or a national one requires something truly catastrophic to
    happen.

    I can only recall one UK powercut in that league in the past half
    century (August 9 2019). Of course it directly affected the densely
    populated affluent regions London and the South East. Therefore it was
    much more newsworthy than if it had affected the remote Scottish
    Highlands where weather induced powercuts are quite common.

    I don't think I've ever (regardless of where I've lived) experienced
    a deliberate power cut.  A drunk may take out a telephone pole or
    a branch may fall on some high tension wires but no one has ever
    said "sorry, we're turning the lights out" (for whatever reason)

    They do that routinely where I live once a year for trimming trees that
    might otherwise short out live supply lines or worse fall onto them.

    I wouldn't describe that 2019 powercut as deliberate either it was a
    huge MFU caused by a single lightning strike to an insignificant power
    plant that lead to a cascade network failure.

    We typically lose power a couple of times a year due to very high winds toppling poles and/or the sort of snow that sticks onto trees and makes
    them break. The mains poles here are now antique. Installed ~1950's and
    the bases are rotten. Unsafe for linesmen to climb and marked as such.

    The recent big one at Heathrow didn't affect all that many people
    although it did take down the whole airport which shows remarkably bad
    contingency planning - it should have had supply redundancy and the
    ability to switchover to it before the diesel generators ran out of
    fuel. Heads should roll over them having to shut down completely.

    Fukishima?

    Genuine natural disaster beyond what the designers had considered. They
    almost got away with it but didn't. Tsunami are absolutely terrifying.
    Another one when I was in Japan in the hours of darkness was reported as
    2m (which was when the gauge stopped transmitting). The next morning
    there was seaweed hanging off supergrid pylon wires.

    I'm considering replacing the UPS at my router. Some UPS "destroy"
    the battery too fast.

    Yes.  Rather than spend time investigating it, I've taken the approach
    of just rescuing batteries to replace those that have been "cooked".

    That is a feature of UPS design that specsmanship to get the longest
    run time for the sales datasheet means that they cook their batteries.
    I have seen them swell to the point of bursting inside a UPS. Thick
    rubber gloves needed to remove the remains. Support metalwork was a
    real corroded rusty mess but electronics above it remained OK.

    Yup.  They have a rationalization, though -- they are trying to provide the highest availability.  Else, how much availability do you sacrifice to maximize battery life?  Do you then start specifying battery life as a primary selection criteria?

    I think they probably could back off the fast recharge a bit. I'm always nervous of going back on again too soon after power is restored (even
    though my systems are reasonably fault tolerant). Sometimes the mains restoration goes on and off several times a few seconds apart if there
    are still other transient leak to ground faults on the lines.

    [Most SOHO users buy a UPS -- thinking they are being "professional" -- and then discard it when the battery needs replacing and they discover the
    costs charged by the UPS manufacturer -- or local "battery stores"]

    I suspect the problem (rationalized by the manufacturers) is trying to
    bring the battery back to full charge ASAP -- as well as keeping the
    highest state of charge that the battery can support.

    Which taken to extremes is very bad for battery life.

    Of course.  But, they are in the PRIMARY business of selling batteries,
    not UPSs!

    A bit like printers then.

    Charging at a slower rate and to a lower float voltage would
    compromise the UPS's availability -- but provide less maintenance costs
    (of course, the manufacturer wants to sell you batteries, so you
    can see where their priorities will lie!)

    They really think I'm going to buy their vastly overpriced replacements?

    If you were a business, it would just be a maintenance expense.
    You would budget for it.  If SOHO, you'd likely replace it at
    most once and then realize "Gee, I haven't NEEDED this in the
    past three years so why am I spending more money on it?"

    With the exception of multi-user servers, individual workstations
    usually have auto-backup provisions *in* the key applications.
    And, in the event of an outage (even if the machine stays up),
    the user is usually distracted by the rest of the house/office
    going black; is ~15 minutes of uptime going to be enough if the
    user isn't AT the machine when power fails?

    No one has yet to address the market where TCO is the driving
    criteria.

    To some extent it is an insurance policy to not lose what I'm working on
    if the power does go down suddenly. Despite having theoretical lightning protect as well I also shutdown when there are thunderstorms about.

    I saw what a big lightning strike to our works building did to the
    switchboard and mainframe. The surge protection devices on a big chunky
    copper bus bar saved themselves by allowing transients to fry all of the terminal driver boards. The phone lines were just a sooty shadow on the
    wall and it blew the clip on covers off the cable way.

    About once a decade we get lightning to tree strikes within 100m. It
    usually fries bedside clocks and modems (although mine survived OK last
    time). This was despite a 1" calorific spark jumping off it.

    --
    Martin Brown

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Liz Tuddenham@21:1/5 to Don Y on Thu May 8 13:43:47 2025
    Don Y <blockedofcourse@foo.invalid> wrote:


    I don't think I've ever (regardless of where I've lived) experienced
    a deliberate power cut. A drunk may take out a telephone pole or
    a branch may fall on some high tension wires but no one has ever
    said "sorry, we're turning the lights out" (for whatever reason)

    That was exactly what happened in the UK in the early 1970s; we had a
    rota of power cuts lasting 4 hours each. I made up an automatic
    lighting unit based on a car battery for my parents. It used relays to
    switch on when the mains went, then recharge at a fast rate until the
    battery voltage rose high enough, then trickle charge.

    I worked in animal research at the time. The technicians brought in
    portable paraffin heaters from thier own homes to keep the animals warm.
    We worked by the light of paraffin lamps and adapted a pressure stove
    with a bunsen burner gauze to act as a radiant heater. One of my jobs
    was to monitor the voltage of the telephone exchange batteries and warn
    the exchange if they started to run down.

    --
    ~ Liz Tuddenham ~
    (Remove the ".invalid"s and add ".co.uk" to reply)
    www.poppyrecords.co.uk

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Don Y on Thu May 8 14:44:06 2025
    On 2025-05-08 01:01, Don Y wrote:
    Much like me having carrier doesn't tell me the extent of
    my "reach", here.

    Well, the power outage was "total". :-D

    Yeah, but you don't know which services (up the chain) may
    have their own *local*/private backup systems.  E.g., I doubt
    your hospitals were without power (?)  The extent of backup
    beyond that would be something you'd have to know, in advance.

    If the fibre goes direct to the exchange, they had backup power.
    However, if the distance is great and they have to reconstruct the
    signal with some kind of optical amplifier, then I don't know. The
    distance is about 2.5 Km.

    But where can exchange traffic go?  See what I mean?  Anyone that
    you want to contact (and everyone along the way) must be "up".

    Whatsapp worked, Google (search) did not. Browsing a news site was very
    slow.


    My mobile phone worked all the day, I could send and receive whatsapp
    messages.

    Are those processed "locally"?

    No. I don't know if they have centralized server or distributed.


    I have a small computer doing server things, and it tried to email me
    as soon as the UPS said it was running on battery. That email did not
    reach me till the power came back; this could be that the fibre went
    OOS, or that the UPS at my router went down instantly. I do not know.

    Doesn't your UPS deliver log messages (to a syslog server or data
    dumps to an FTP service)?

    The one on the server did, yes, but the one on the router doesn't have
    that facility.


    I have each of mine configured to give me summaries of power consumption
    and line conditions each minute.  And, use a syslogd on that same server.

    I don't think any of mine can report power usage.


    I'm considering replacing the UPS at my router. Some UPS "destroy" the
    battery too fast.

    Yes.  Rather than spend time investigating it, I've taken the approach
    of just rescuing batteries to replace those that have been "cooked".

    I suspect the problem (rationalized by the manufacturers) is trying to
    bring the battery back to full charge ASAP -- as well as keeping the
    highest state of charge that the battery can support.

    And trickle charge continuously.


    Charging at a slower rate and to a lower float voltage would
    compromise the UPS's availability -- but provide less maintenance costs
    (of course, the manufacturer wants to sell you batteries, so you
    can see where their priorities will lie!)

    Indeed.

    I saw in an Eaton model they mentioned two strategies - translated from Spanish:

    UPS Topology: Standby (Offline) or Standby (Offline)

    Eaton Ellipse ECO 650 IEC SAI Offline 650VA 400W
    Eaton P/N: EL650IEC


    I still have not investigated.

    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Martin Brown on Thu May 8 14:54:17 2025
    On 2025-05-08 12:57, Martin Brown wrote:
    On 08/05/2025 00:01, Don Y wrote:
    Much like me having carrier doesn't tell me the extent of
    my "reach", here.

    Well, the power outage was "total". :-D

    Yeah, but you don't know which services (up the chain) may
    have their own *local*/private backup systems.  E.g., I doubt
    your hospitals were without power (?)  The extent of backup
    beyond that would be something you'd have to know, in advance.

    If the fibre goes direct to the exchange, they had backup power.
    However, if the distance is great and they have to reconstruct the
    signal with some kind of optical amplifier, then I don't know. The
    distance is about 2.5 Km.

    But where can exchange traffic go?  See what I mean?  Anyone that
    you want to contact (and everyone along the way) must be "up".

    That was the original point of ARPANET then EPSS and later the internet. Packet switching means that any route to the destination at all will do.

    I'm told that my fibre feed is passive optical connectors and splices
    all the way back the regional exchange about 12 miles away. My local
    exchange was about 5 miles away and a so-called exchange only direct
    line (which meant that ADSL 2+ was the limit for me prior to FTTP).

    My mobile phone worked all the day, I could send and receive whatsapp
    messages.

    Are those processed "locally"?

    Mobile phone masts here typically have a lifetime of about 8-40 hours
    after power failure depending on how heavily they are being used.
    Backhaul presumably is optical or microwave.

    Most powercuts tend to be fairly local round here - a regional powercut
    or a national one requires something truly catastrophic to happen.

    I can only recall one UK powercut in that league in the past half
    century (August 9 2019). Of course it directly affected the densely
    populated affluent regions London and the South East. Therefore it was
    much more newsworthy than if it had affected the remote Scottish
    Highlands where weather induced powercuts are quite common.

    The recent big one at Heathrow didn't affect all that many people
    although it did take down the whole airport which shows remarkably bad contingency planning - it should have had supply redundancy and the
    ability to switchover to it before the diesel generators ran out of
    fuel. Heads should roll over them having to shut down completely.

    Barajas and probably all main airports remained working here, but the
    problem was getting to them. The Metro to Barajas was OOS, so it meant
    bus or taxi; and there were terrible traffic jams because signalling was
    OOS. Even the air crews had trouble arriving at the airports.



    I have a small computer doing server things, and it tried to email me
    as soon as the UPS said it was running on battery. That email did not
    reach me till the power came back; this could be that the fibre went
    OOS, or that the UPS at my router went down instantly. I do not know.

    Doesn't your UPS deliver log messages (to a syslog server or data
    dumps to an FTP service)?

    I have each of mine configured to give me summaries of power consumption
    and line conditions each minute.  And, use a syslogd on that same server.

    I only log external power failures. Kitchen appliance clocks all reset
    when we lose power for more than a couple of seconds.

    I'm considering replacing the UPS at my router. Some UPS "destroy"
    the battery too fast.

    Yes.  Rather than spend time investigating it, I've taken the approach
    of just rescuing batteries to replace those that have been "cooked".

    That is a feature of UPS design that specsmanship to get the longest run
    time for the sales datasheet means that they cook their batteries. I
    have seen them swell to the point of bursting inside a UPS. Thick rubber gloves needed to remove the remains. Support metalwork was a real
    corroded rusty mess but electronics above it remained OK.

    That level of "not working" has not happened to me. Maybe because some
    power failure makes me find out that the battery is dead.


    I suspect the problem (rationalized by the manufacturers) is trying to
    bring the battery back to full charge ASAP -- as well as keeping the
    highest state of charge that the battery can support.

    Which taken to extremes is very bad for battery life.

    Charging at a slower rate and to a lower float voltage would
    compromise the UPS's availability -- but provide less maintenance costs
    (of course, the manufacturer wants to sell you batteries, so you
    can see where their priorities will lie!)

    They really think I'm going to buy their vastly overpriced replacements?

    I don't.

    But last battery I replaced was not even two years old, rather 5 months
    short. I replaced it just in time to serve during the Gran Apagón.


    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Don Y on Thu May 8 15:05:06 2025
    On 2025-05-08 13:49, Don Y wrote:

    ...

    I can only recall one UK powercut in that league in the past half
    century (August 9 2019). Of course it directly affected the densely
    populated affluent regions London and the South East. Therefore it was
    much more newsworthy than if it had affected the remote Scottish
    Highlands where weather induced powercuts are quite common.

    I don't think I've ever (regardless of where I've lived) experienced
    a deliberate power cut.  A drunk may take out a telephone pole or
    a branch may fall on some high tension wires but no one has ever
    said "sorry, we're turning the lights out" (for whatever reason)

    Not the same, but past Monday someone stole the signalling cable in the
    high speed railway to Andalussia, leaving the entire line OOS. I heard
    that trains were authorized to run at 40 Km/h, so that they could see
    the other train in time and tail it. Not sure it worked.

    The authorities talked of sabotage. The price of the cable when new is
    not even a thousand euros, but the damage to thousands of people is huge.

    ...

    I'm considering replacing the UPS at my router. Some UPS "destroy"
    the battery too fast.

    Yes.  Rather than spend time investigating it, I've taken the approach
    of just rescuing batteries to replace those that have been "cooked".

    That is a feature of UPS design that specsmanship to get the longest
    run time for the sales datasheet means that they cook their batteries.
    I have seen them swell to the point of bursting inside a UPS. Thick
    rubber gloves needed to remove the remains. Support metalwork was a
    real corroded rusty mess but electronics above it remained OK.

    Yup.  They have a rationalization, though -- they are trying to provide the highest availability.  Else, how much availability do you sacrifice to maximize battery life?  Do you then start specifying battery life as a primary selection criteria?

    [Most SOHO users buy a UPS -- thinking they are being "professional" -- and then discard it when the battery needs replacing and they discover the
    costs charged by the UPS manufacturer -- or local "battery stores"]

    25€. A 9Ah item, high discharge rate.



    I suspect the problem (rationalized by the manufacturers) is trying to
    bring the battery back to full charge ASAP -- as well as keeping the
    highest state of charge that the battery can support.

    Which taken to extremes is very bad for battery life.

    Of course.  But, they are in the PRIMARY business of selling batteries,
    not UPSs!

    Ugh.

    And having disgruntled customers.


    Charging at a slower rate and to a lower float voltage would
    compromise the UPS's availability -- but provide less maintenance costs
    (of course, the manufacturer wants to sell you batteries, so you
    can see where their priorities will lie!)

    They really think I'm going to buy their vastly overpriced replacements?

    If you were a business, it would just be a maintenance expense.
    You would budget for it.  If SOHO, you'd likely replace it at
    most once and then realize "Gee, I haven't NEEDED this in the
    past three years so why am I spending more money on it?"

    With the exception of multi-user servers, individual workstations
    usually have auto-backup provisions *in* the key applications.
    And, in the event of an outage (even if the machine stays up),
    the user is usually distracted by the rest of the house/office
    going black; is ~15 minutes of uptime going to be enough if the
    user isn't AT the machine when power fails?

    You need software monitoring to hibernate or power off the machine.


    No one has yet to address the market where TCO is the driving
    criteria.



    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Carlos E.R. on Thu May 8 15:41:29 2025
    On 2025-05-08 14:44, Carlos E.R. wrote:
    On 2025-05-08 01:01, Don Y wrote:
    Much like me having carrier doesn't tell me the extent of
    my "reach", here.

    ...

    I'm considering replacing the UPS at my router. Some UPS "destroy"
    the battery too fast.

    Yes.  Rather than spend time investigating it, I've taken the approach
    of just rescuing batteries to replace those that have been "cooked".

    I suspect the problem (rationalized by the manufacturers) is trying to
    bring the battery back to full charge ASAP -- as well as keeping the
    highest state of charge that the battery can support.

    And trickle charge continuously.


    Charging at a slower rate and to a lower float voltage would
    compromise the UPS's availability -- but provide less maintenance costs
    (of course, the manufacturer wants to sell you batteries, so you
    can see where their priorities will lie!)

    Indeed.

    I saw in an Eaton model they mentioned two strategies - translated from Spanish:

    UPS Topology: Standby (Offline) or Standby (Offline)

    {Phrase translated by DeepL, so inconsistent: Topología UPS: En espera
    (Fuera de línea) o Standby (Offline)}


    Eaton Ellipse ECO 650 IEC SAI Offline 650VA 400W
    Eaton P/N: EL650IEC


    I still have not investigated.

    I have investigated. There are two models, IEC and DIN. It refers to the connectors.

    <https://www.eaton.com/es/es-es/skuPage.EL650DIN.html>

    Specs: <https://www.eaton.com/es/es-es/skuPage.EL650DIN.pdf>

    Manual: <https://www.eaton.com/content/dam/eaton/products/backup-power-ups-surge-it-power-distribution/backup-power-ups/eaton-ellipse-eco/Eaton%20Ellipse%20ECO%20-%20500-650-800-1200-1600%20VA%20-%20Installation%20and%20user%20manual%20(En-Fr-De-It-Es-Pt).pdf>


    I do not see a reference to that "topology" except at the vendor. But it
    says that the expected battery life is 4 years.

    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Miguel Gimenez on Thu May 8 15:45:42 2025
    On 2025-05-08 14:31, Miguel Gimenez wrote:
    El 02/05/2025 a las 23:30, Carlos E.R. escribió:
    On 2025-05-02 12:28, Martin Brown wrote:
    On 01/05/2025 21:13, Carlos E.R. wrote:
    On 2025-04-29 14:24, Martin Brown wrote:
    Spain suffered a very spectacular near total loss of its national
    grid yesterday taking parts of France and all of Portugal down with
    it. This is an unprecedented failure of a supergrid system by
    cascade failure.

    I should say, although too late, that it should be "Gran Apagón" :-)

    Sorry about that. I remember the phrase from my astronomy days when
    the Gran Canary were persuaded to go completely dark for one night
    only so that the Isaac Newton telescope on its peak could do
    something special.

    Don't worry :-)


    It gave everyone there an opportunity to see a truly dark sky.

    Links to it back in 1985 are now very thin on the ground. An article
    celebrating 10th anniversary is the best I can find in English page
    31. (sorry its very big)




    As a side note, the Apagón made all my DCF-77 clocks synchronize inmediately. Usually Madrid has reception problems, taking even weeks to synchronize, but looks like it is more an interference issue than the distance to Mainflingen.

    Wow! :-D

    I did not notice that one, but instead I noticed that my DAB+ radio got reception in Cartagena. The transmitter is probably in Murcia, at the mountains. Still, the reception was choppy, once every few seconds.
    Today is even more choppy, and doesn't work downstairs at all.

    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Martin Brown@21:1/5 to Liz Tuddenham on Thu May 8 15:08:10 2025
    On 08/05/2025 13:43, Liz Tuddenham wrote:
    Don Y <blockedofcourse@foo.invalid> wrote:


    I don't think I've ever (regardless of where I've lived) experienced
    a deliberate power cut. A drunk may take out a telephone pole or
    a branch may fall on some high tension wires but no one has ever
    said "sorry, we're turning the lights out" (for whatever reason)

    That was exactly what happened in the UK in the early 1970s; we had a
    rota of power cuts lasting 4 hours each. I made up an automatic
    lighting unit based on a car battery for my parents. It used relays to switch on when the mains went, then recharge at a fast rate until the
    battery voltage rose high enough, then trickle charge.

    That was during the various coal miners strikes which were at their peak
    then. Local newspapers had rotas for planned supply cuts.

    ISTR there was still the odd planned power cut even in the late 1970's
    but they became increasingly rare after that.

    --
    Martin Brown

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Martin Brown@21:1/5 to Carlos E.R. on Thu May 8 15:18:07 2025
    On 08/05/2025 14:41, Carlos E.R. wrote:
    On 2025-05-08 14:44, Carlos E.R. wrote:

    UPS Topology: Standby (Offline) or Standby (Offline)

    {Phrase translated by DeepL, so inconsistent: Topología UPS: En espera (Fuera de línea) o Standby (Offline)}

    There are (at least) two major UPS topologies in play.

    One is where the power to the protected device is always made by the
    inverter and maintained at the correct main voltage irrespective of
    input voltage to the UPS. Useful in places where the local mains supply
    voltage goes up and down a lot depending on load.

    The other is a pass through of input mains voltage to the load under
    normal conditions and an isolation relay plus cold start of the inverter
    within a couple of cycles of the supply failure. This is more than good
    enough for PCs. Mine can withstand a 1s blackout unprotected without any difficulty but kitchen white goods clocks cannot.

    I do not see a reference to that "topology" except at the vendor. But it
    says that the expected battery life is 4 years.



    --
    Martin Brown

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Liz Tuddenham@21:1/5 to Martin Brown on Thu May 8 17:19:54 2025
    Martin Brown <'''newspam'''@nonad.co.uk> wrote:

    On 08/05/2025 13:43, Liz Tuddenham wrote:
    Don Y <blockedofcourse@foo.invalid> wrote:


    I don't think I've ever (regardless of where I've lived) experienced
    a deliberate power cut. A drunk may take out a telephone pole or
    a branch may fall on some high tension wires but no one has ever
    said "sorry, we're turning the lights out" (for whatever reason)

    That was exactly what happened in the UK in the early 1970s; we had a
    rota of power cuts lasting 4 hours each. I made up an automatic
    lighting unit based on a car battery for my parents. It used relays to switch on when the mains went, then recharge at a fast rate until the battery voltage rose high enough, then trickle charge.

    That was during the various coal miners strikes which were at their peak then. Local newspapers had rotas for planned supply cuts.

    ISTR there was still the odd planned power cut even in the late 1970's
    but they became increasingly rare after that.

    A "Disconnection Rota" marker has recently started appearing on my
    electricity bill.


    --
    ~ Liz Tuddenham ~
    (Remove the ".invalid"s and add ".co.uk" to reply)
    www.poppyrecords.co.uk

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Bill Sloman@21:1/5 to Liz Tuddenham on Fri May 9 04:33:26 2025
    On 1/05/2025 1:05 am, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    On 30/04/2025 8:41 pm, Carlos E.R. wrote:
    On 2025-04-30 11:59, Liz Tuddenham wrote:
    Bill Sloman <bill.sloman@ieee.org> wrote:

    ... pumped hydro storage has the spinning
    turbines, but grid scale batteries have invereters, which can reacta lot >>>>> faster than any spinning turbine,

    I thought the stabilising effect of a spinning turbine was because it
    *didn't* react quickly.

    The grid frequency begins to fall so energy from the moving parts is
    converted to electrical power which is fed into the grid to increase.
    the frequency.  This results in a loss of stored mechanical energy which
    causes the turbine to begin slowing down - which is detected by the
    control system and used to feed more water/gas/steam into the turbine so >>>> its speed is returned to normal.

    I understand that the turbine doesn't actually slow down, because the
    generator starts working as a synchronous motor drawing energy from the
    network instead; this is detected by the control system and feeds more
    water/gas/steam, etc.

    It doesn't slow down much, but there's no such thing as instantaneous
    feedback - you have to an input change before you can start correcting
    the output.

    As long as the network keeps the frequency.

    The "network" can't keep the frequency - it's the corrections that keep
    the low term frequency stable

    The interface between the stored mechanical energy and the electrical
    energy demand has an almost instant response and is inherently stable
    without needing elaborate control algorithms.

    But the stored mechanical energy in the spinning rotor can only get fed
    into the grid if the rotor slows down.

    The generator has to have a control system to control the power being
    feed into the rotor to keep it spinning at the same speed while more
    energy is being extracted from it.

    There's nothing magically stable about that kind of control system - it
    has to be designed to stable like any other feedback mechanism.

    There are two mechanisms at work here:

    1) The coupling between the rotating machine and the grid, which is virtually instantaneous and extracts mechanical energy from the rotating 'store' without any special control system. It is inherently stable.

    Only in the sense that it doesn't do anything unpredictable.

    2) The coupling between the rotating machine and the 'prime mover'
    power source, which puts mechanical energy into the rotating 'store'.
    This is slower to respond and does need careful control to keep it
    stable.

    The point about inverter-based controls taking energy from grid-scale
    batteries (or feeding it into them) is that they can operate much
    faster. They can force the voltage at their connection to the grid to sinusoidal on a millisecond to millisecond basis.

    The difference between these two shows up as a change in the speed of rotation.

    If the current output from the rotating machinery dominates the energy
    being feed into the grid, that will happen. If most of the energy is
    coming from solar cells through inverters that isn't a useful way of
    looking at what's going on.

    --
    Bil Sloman, Sydney

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Martin Brown@21:1/5 to Liz Tuddenham on Thu May 8 20:39:30 2025
    On 08/05/2025 17:19, Liz Tuddenham wrote:
    Martin Brown <'''newspam'''@nonad.co.uk> wrote:

    On 08/05/2025 13:43, Liz Tuddenham wrote:
    Don Y <blockedofcourse@foo.invalid> wrote:


    I don't think I've ever (regardless of where I've lived) experienced
    a deliberate power cut. A drunk may take out a telephone pole or
    a branch may fall on some high tension wires but no one has ever
    said "sorry, we're turning the lights out" (for whatever reason)

    That was exactly what happened in the UK in the early 1970s; we had a
    rota of power cuts lasting 4 hours each. I made up an automatic
    lighting unit based on a car battery for my parents. It used relays to
    switch on when the mains went, then recharge at a fast rate until the
    battery voltage rose high enough, then trickle charge.

    That was during the various coal miners strikes which were at their peak
    then. Local newspapers had rotas for planned supply cuts.

    ISTR there was still the odd planned power cut even in the late 1970's
    but they became increasingly rare after that.

    A "Disconnection Rota" marker has recently started appearing on my electricity bill.

    You still get paper ones? I confess I haven't actually looked at my
    virtual "paper" electricity bill for ages. I use the online portal to
    check usage and how much they have taken in DD for prepayment.

    Electricity companies have a nasty habit of always increasing DDs when
    the price goes up and never reducing them so that if you don't keep an
    eye on it they can borrow your money. Officially to smooth out winter.

    I'll take a look on mine. I only have water and sewage as physical paper
    bills to satisfy what laughingly passes for "proof of identity" in the
    UK! The other utilities are on DD to get preferential rates.

    I can't see why we would ever be inline for rationing power cuts though
    we are pretty much on the nexus where under all foreeable scenarios we
    have an oversupply of power that can't move any further south!

    It might fail for over voltage though.

    --
    Martin Brown

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From KevinJ93@21:1/5 to Liz Tuddenham on Thu May 8 12:51:50 2025
    On 5/8/25 5:43 AM, Liz Tuddenham wrote:
    Don Y <blockedofcourse@foo.invalid> wrote:


    I don't think I've ever (regardless of where I've lived) experienced
    a deliberate power cut. A drunk may take out a telephone pole or
    a branch may fall on some high tension wires but no one has ever
    said "sorry, we're turning the lights out" (for whatever reason)

    That was exactly what happened in the UK in the early 1970s; we had a
    rota of power cuts lasting 4 hours each. I made up an automatic
    lighting unit based on a car battery for my parents. It used relays to switch on when the mains went, then recharge at a fast rate until the
    battery voltage rose high enough, then trickle charge.

    <...>

    When the coal miner's strike power usage reductions were in effect I was working at Marconi-Elliott in Borehamwood. We were not allowed to have
    the lights or heating on but it was permitted to use test equipment so
    we would huddle around our Tektronix 547 scopes to keep warm, they used
    to put out a lot of heat.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Martin Brown on Thu May 8 22:23:44 2025
    On 2025-05-08 16:18, Martin Brown wrote:
    On 08/05/2025 14:41, Carlos E.R. wrote:
    On 2025-05-08 14:44, Carlos E.R. wrote:

    UPS Topology: Standby (Offline) or Standby (Offline)

    {Phrase translated by DeepL, so inconsistent: Topología UPS: En espera
    (Fuera de línea) o Standby (Offline)}

    There are (at least) two major UPS topologies in play.

    One is where the power to the protected device is always made by the
    inverter and maintained at the correct main voltage irrespective of
    input voltage to the UPS. Useful in places where the local mains supply voltage goes up and down a lot depending on load.

    The other is a pass through of input mains voltage to the load under
    normal conditions and an isolation relay plus cold start of the inverter within a couple of cycles of the supply failure. This is more than good enough for PCs. Mine can withstand a 1s blackout unprotected without any difficulty but kitchen white goods clocks cannot.

    Ah! Yes, I remember now, I have seen this before. It was the
    terminology that was confusing me.

    Thanks.

    I do not see a reference to that "topology" except at the vendor. But
    it says that the expected battery life is 4 years.





    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to Martin Brown on Thu May 8 14:05:36 2025
    On 5/8/2025 5:43 AM, Martin Brown wrote:
    On 08/05/2025 12:49, Don Y wrote:
    But where can exchange traffic go?  See what I mean?  Anyone that
    you want to contact (and everyone along the way) must be "up".

    That was the original point of ARPANET then EPSS and later the internet. >>> Packet switching means that any route to the destination at all will do.

    But that assumes there *is* a series of hops that can get you "there"...
    wherever "there" happens to be.  In a nationwide outage, what chance
    that everything EXCEPT some critical bit of comms gear is affected?

    Nationwide outages should be exceptionally rare. Never had one in the UK but the way they are going one winter's day it will happen.

    Yes, but they *do* happen. As well as events that take out large
    geographical areas (e.g., 9/11).

    One can't protect against (e.g.) 10 sigma occurrences as it's not economical. But, people still have to potentially deal with them.

    Most powercuts tend to be fairly local round here - a regional powercut or a
    national one requires something truly catastrophic to happen.

    I can only recall one UK powercut in that league in the past half century >>> (August 9 2019). Of course it directly affected the densely populated
    affluent regions London and the South East. Therefore it was much more
    newsworthy than if it had affected the remote Scottish Highlands where
    weather induced powercuts are quite common.

    I don't think I've ever (regardless of where I've lived) experienced
    a deliberate power cut.  A drunk may take out a telephone pole or
    a branch may fall on some high tension wires but no one has ever
    said "sorry, we're turning the lights out" (for whatever reason)

    They do that routinely where I live once a year for trimming trees that might otherwise short out live supply lines or worse fall onto them.

    I don't recall it in any of the places that I've lived with overhead
    services. Here, things are below grade.

    In the former case, outages were frequent enough (one place they occurred monthly) that any sort of PM would be lost in the noise. In the latter,
    it's decades between *clusters* of failures.

    I wouldn't describe that 2019 powercut as deliberate either it was a huge MFU caused by a single lightning strike to an insignificant power plant that lead to a cascade network failure.

    We typically lose power a couple of times a year due to very high winds toppling poles and/or the sort of snow that sticks onto trees and makes them break. The mains poles here are now antique. Installed ~1950's and the bases are rotten. Unsafe for linesmen to climb and marked as such.

    I don't know how our "area" is fed as it has to be overhead *somewhere*.
    But. most of the high tension lines are on metal support towers or
    metal "poles" (18-24" diameter at base)

    The other side of town has overhead service and frequently is down
    for a day or so as high winds play dominoes with the poles.

    The recent big one at Heathrow didn't affect all that many people although >>> it did take down the whole airport which shows remarkably bad contingency >>> planning - it should have had supply redundancy and the ability to
    switchover to it before the diesel generators ran out of fuel. Heads should >>> roll over them having to shut down completely.

    Fukishima?

    Genuine natural disaster beyond what the designers had considered. They almost

    Like grid failures the designers hadn't considered? :>

    got away with it but didn't. Tsunami are absolutely terrifying. Another one when I was in Japan in the hours of darkness was reported as >2m (which was when the gauge stopped transmitting). The next morning there was seaweed hanging off supergrid pylon wires.

    I'm considering replacing the UPS at my router. Some UPS "destroy" the >>>>> battery too fast.

    Yes.  Rather than spend time investigating it, I've taken the approach >>>> of just rescuing batteries to replace those that have been "cooked".

    That is a feature of UPS design that specsmanship to get the longest run >>> time for the sales datasheet means that they cook their batteries. I have >>> seen them swell to the point of bursting inside a UPS. Thick rubber gloves >>> needed to remove the remains. Support metalwork was a real corroded rusty >>> mess but electronics above it remained OK.

    Yup.  They have a rationalization, though -- they are trying to provide the >> highest availability.  Else, how much availability do you sacrifice to
    maximize battery life?  Do you then start specifying battery life as a
    primary selection criteria?

    I think they probably could back off the fast recharge a bit. I'm always nervous of going back on again too soon after power is restored (even though my
    systems are reasonably fault tolerant). Sometimes the mains restoration goes on
    and off several times a few seconds apart if there are still other transient leak to ground faults on the lines.

    Our outages tend to be clean on/off/on events as they are simple equipment failures. One cable segment replacement was followed by a *second*
    when the line was reenergized but that was unusual. And, the second
    failure was almost immediate.

    I have every machine (save the 24/7/365 "services" box) set to stay
    off in the event of power failure. I don't need to have them all
    spin up of their own accord if unattended.

    Of course.  But, they are in the PRIMARY business of selling batteries,
    not UPSs!

    A bit like printers then.

    There are depressingly many "toilet paper" products (products where
    the main business is selling toilet paper, NOT the "free dispensers").
    One firm sells distilled water in tiny vials. The vials are *chipped*
    to ensure you don't substitute some other distilled water for THEIR
    distilled water. <rolls eyes>

    [Yes, of course there are likely standards of purity ionvolved
    but I'm sure the real issue is continued revenue stream]

    Some years ago, I designed a box; lots of pressure to get the
    costs down (about $300 DM+DL). The boxes were "sold" for $6000.
    But, all were given away -- to sell chemical reagents!

    An acquaintance makes his living buying drug stores (pharmacies).
    All of the content is treated as crap and resold for pennies
    on the dollar. What he's after is the prescriptions that the
    store handles. So, when you laugh at the outrageous prices
    that they charge for common items (that you can easily buy
    elsewhere), know that those aren't the real profit drivers!

    With the exception of multi-user servers, individual workstations
    usually have auto-backup provisions *in* the key applications.
    And, in the event of an outage (even if the machine stays up),
    the user is usually distracted by the rest of the house/office
    going black; is ~15 minutes of uptime going to be enough if the
    user isn't AT the machine when power fails?

    No one has yet to address the market where TCO is the driving
    criteria.

    To some extent it is an insurance policy to not lose what I'm working on if the
    power does go down suddenly. Despite having theoretical lightning protect as well I also shutdown when there are thunderstorms about.

    That hasn't been a problem, here. Whichever machines happen to be powered
    up will just go in and out of "sleep" based on how long I've been "away"
    from them. Booting is costly (add-in cards with legacy BIOS that
    have to come up sequentially -- usually probing external busses in the process). So, I'd rather just let them idle at a lower power.

    I saw what a big lightning strike to our works building did to the switchboard
    and mainframe. The surge protection devices on a big chunky copper bus bar saved themselves by allowing transients to fry all of the terminal driver boards. The phone lines were just a sooty shadow on the wall and it blew the clip on covers off the cable way.

    I took some steps to protect the comms wiring for my automation system
    from "deliberate acts of sabotage" (e.g., holding a tesla coil to the
    8P8c's). But, unless you are building from scratch, I don't think
    it is possible to address this issue (how do you know which wires
    travel alongside each other)

    About once a decade we get lightning to tree strikes within 100m. It usually fries bedside clocks and modems (although mine survived OK last time). This was
    despite a 1" calorific spark jumping off it.

    Our home was struck many years ago. (CRT) TV ended up "magnetized"
    (color distortion). Solid state phones were all toasted (leaving the
    house looking to be "off hook"). My other half (home at the time;
    I was at work) in a panic cuz "the phones don't work" -- it's one
    thing to lose power, yet another to lose POTS!

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to All on Thu May 8 14:32:02 2025
    I don't think I've ever (regardless of where I've lived) experienced
    a deliberate power cut.  A drunk may take out a telephone pole or
    a branch may fall on some high tension wires but no one has ever
    said "sorry, we're turning the lights out" (for whatever reason)

    Not the same, but past Monday someone stole the signalling cable in the high speed railway to Andalussia, leaving the entire line OOS. I heard that trains were authorized to run at 40 Km/h, so that they could see the other train in time and tail it. Not sure it worked.

    The authorities talked of sabotage. The price of the cable when new is not even
    a thousand euros, but the damage to thousands of people is huge.

    There are places where copper products (wire, plumbing) are stolen
    for their "recycle value". The solution, so far, has been to
    require recyclers to get and record identification of people
    bringing in such items.

    A friend had the copper stripped from the roof-mounted cooling unit at
    his business. Landlord held *him* responsible for its repair/replacement.

    I think there have been cases of people trying to steal the wiring in
    outside lighting systems -- and not taking adequate provisions to
    protect against electrocution!

    I would like to make some backlit copper lighted displays for the house
    (AZ is The Copper State) but am afraid its oxidized color would attract
    some thief eager to make a few dollars off it.

    Yup.  They have a rationalization, though -- they are trying to provide the >> highest availability.  Else, how much availability do you sacrifice to
    maximize battery life?  Do you then start specifying battery life as a
    primary selection criteria?

    [Most SOHO users buy a UPS -- thinking they are being "professional" -- and >> then discard it when the battery needs replacing and they discover the
    costs charged by the UPS manufacturer -- or local "battery stores"]

    25€. A 9Ah item, high discharge rate.

    Different grades exist, here. If you buy from an electronics supplier
    (e.g., Digikey), you will likely get a "fairer" price (value for money)
    than a local battery store (which may be 50% higher). UPS manufacturers typically charge about double what a reasonable price might be (though
    the usually assemble the batteries into the requisite "packs"...
    a trivial exercise for even 48V units).

    Digikey used to have a policy of free shipping for prepaid (cash)
    orders. I would buy batteries in lots of 10 and send prepayment.
    Shipping charges can be a significant fraction of a battery's
    cost. They now exclude batteries from this policy (when I last
    checked).

    I suspect the problem (rationalized by the manufacturers) is trying to >>>> bring the battery back to full charge ASAP -- as well as keeping the
    highest state of charge that the battery can support.

    Which taken to extremes is very bad for battery life.

    Of course.  But, they are in the PRIMARY business of selling batteries,
    not UPSs!

    Ugh.

    And having disgruntled customers.

    Think about it. If the *UPS* (hardware) failed at 3 year intervals,
    no one would buy them! They'd be seen as poor quality.

    But, no one is surprised that BATTERIES need replacement!

    With the exception of multi-user servers, individual workstations
    usually have auto-backup provisions *in* the key applications.
    And, in the event of an outage (even if the machine stays up),
    the user is usually distracted by the rest of the house/office
    going black; is ~15 minutes of uptime going to be enough if the
    user isn't AT the machine when power fails?

    You need software monitoring to hibernate or power off the machine.

    I have every workstation set to hibernate after ~20 minutes
    of inactivity. This gives me time to get a cup of tea, go to
    the bathroom, answer the door/phone, etc. without the workstation
    cycling off and on.

    As "activity" is defined by user interactions, this means I
    have to deliberately start an application that disables "sleep"
    if I won't be interacting with the machine and want to prevent
    it from sleeping. E.g., an SSH session with a remote host that
    will be busy for a while; if the workstation sleeps, the SSH
    session terminates and the shell on the remote is killed off.

    <frown>

    No one has yet to address the market where TCO is the driving
    criteria.




    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to All on Thu May 8 14:57:41 2025
    That is a feature of UPS design that specsmanship to get the longest run time
    for the sales datasheet means that they cook their batteries. I have seen
    them swell to the point of bursting inside a UPS. Thick rubber gloves needed >> to remove the remains. Support metalwork was a real corroded rusty mess but >> electronics above it remained OK.

    That level of "not working" has not happened to me. Maybe because some power failure makes me find out that the battery is dead.

    I've rescued a fair number of UPSs over the years. In probably 80% of
    them, the batteries have swollen to the point where removing the battery
    or battery PACK is difficult. This is especially true of the "better"
    UPSs (sine output, 48V battery, metal fabrication) where there is
    little "give" in the mechanical design. Often one has to disassemble
    the UPS to see where one can gain leverage on the battery pack
    to force it from the case.

    They really think I'm going to buy their vastly overpriced replacements?

    I don't.

    But last battery I replaced was not even two years old, rather 5 months short.
    I replaced it just in time to serve during the Gran Apagón.

    That's the problem; you don't KNOW how long a particular battery will last, even in an environment where it is never called on for backup!

    Instead, you are forced into a "reactive" mode -- waiting for something
    to tell you you're screwed and need a replacement, now!

    My largest UPS uses 50 pound batteries (8 of them). It's
    REALLY inconvenient to have to replace them *now* cuz they
    are costly and physically inconvenient to man-handle. I
    would much appreciate some advance notice that they are likely
    to need replacement in, say, 30 days (given the current usage
    pattern).

    Maybe folks will start putting more smarts into their product
    designs instead of simple "threshold" events.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to All on Thu May 8 14:18:47 2025
    On 5/8/2025 12:51 PM, KevinJ93 wrote:
    When the coal miner's strike power usage reductions were in effect I was working at Marconi-Elliott in Borehamwood.  We were not allowed to have the lights or heating on but it was permitted to use test equipment so we would huddle around our Tektronix 547 scopes to keep warm, they used to put out a lot
    of heat.

    The only "utility" that I can recall being VOLUNTARILY rationed was water,
    back east, during a period of drought. We were "strongly discouragd"
    from watering lawns, washing cars (car washes are far more efficient
    at this as they recycle the water), etc.

    Here, of course (desert southwest), peer pressure and threats of fines
    tend to keep folks inline.

    The idea of using a garden hose to "sweep" debris off your
    driveway or sidewalk would be met with a gasp and a glare.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to All on Thu May 8 15:38:05 2025
    My mobile phone worked all the day, I could send and receive whatsapp messages.

    Are those processed "locally"?

    No. I don't know if they have centralized server or distributed.

    Some have "content distribution networks".

    I have a small computer doing server things, and it tried to email me as >>> soon as the UPS said it was running on battery. That email did not reach me >>> till the power came back; this could be that the fibre went OOS, or that the
    UPS at my router went down instantly. I do not know.

    Doesn't your UPS deliver log messages (to a syslog server or data
    dumps to an FTP service)?

    The one on the server did, yes, but the one on the router doesn't have that facility.

    I used to think syslogd support was just another gimmick. But,
    I've come to appreciate being able to find ALL of the logs
    on ONE server (that is always up). Hard to examine a log on
    a device that won't boot, etc.

    I have each of mine configured to give me summaries of power consumption
    and line conditions each minute.  And, use a syslogd on that same server.

    I don't think any of mine can report power usage.

    IIRC, they report:
    Date/Time
    Vmin/Vmax (input)
    Vout/Iout
    %Wout/%VAout/%capacity
    Frequency
    Vbat
    Internal temperature
    "external" temperature & humidity (intended for use in a server room)

    Charging at a slower rate and to a lower float voltage would
    compromise the UPS's availability -- but provide less maintenance costs
    (of course, the manufacturer wants to sell you batteries, so you
    can see where their priorities will lie!)

    Indeed.

    I saw in an Eaton model they mentioned two strategies - translated from Spanish:

    UPS Topology: Standby (Offline) or Standby (Offline)

    Eaton Ellipse ECO 650 IEC SAI Offline 650VA 400W
    Eaton P/N: EL650IEC

    I have a couple of eatons in the garage. I didn't like them for
    use in the office as their fans (run continuously) are louder
    than I would like (and I have no desire to go tweaking fans)

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to Martin Brown on Thu May 8 17:13:32 2025
    On 5/8/2025 7:18 AM, Martin Brown wrote:
    On 08/05/2025 14:41, Carlos E.R. wrote:
    On 2025-05-08 14:44, Carlos E.R. wrote:

    UPS Topology: Standby (Offline) or Standby (Offline)

    {Phrase translated by DeepL, so inconsistent: Topología UPS: En espera (Fuera
    de línea) o Standby (Offline)}

    There are (at least) two major UPS topologies in play.

    One is where the power to the protected device is always made by the inverter and maintained at the correct main voltage irrespective of input voltage to the
    UPS. Useful in places where the local mains supply voltage goes up and down a lot depending on load.

    These are usually called "double conversion" (some call them "online"
    but that can be misleading).

    Most of these (that I've encountered) are less efficient (cuz they
    are always in-the-loop) and often won't START without a functioning battery.

    The other is a pass through of input mains voltage to the load under normal conditions and an isolation relay plus cold start of the inverter within a couple of cycles of the supply failure. This is more than good enough for PCs.
    Mine can withstand a 1s blackout unprotected without any difficulty but kitchen
    white goods clocks cannot.

    These often can do some line voltage adjusting with an autotransformer
    "for free" (part of the design).

    They, also, are available in models that can be started only with a
    valid battery or not. Some require mains voltage to be present, as well.

    There are also cheaper units that use "stepped" waveforms to approximate
    a sine wave; others that are more religious in their determination.

    I do not see a reference to that "topology" except at the vendor. But it says
    that the expected battery life is 4 years.

    Ask for a guarantee on that... :>

    [ObTrivia: SWMBO's vehicle needed a starting battery replacement
    ~3 years after purchase (battery life is about that for all vehicles,
    here; the heat cooks them). As that was within the ~5 year "factory
    warranty" period, it was no charge -- so I didn't bother to get
    involved!

    THAT battery, of course, failed 3 years later. But, as it was
    considered part of the original vehicle (despite being a replacement),
    there was no warranty extended to it.

    So, I went to Costco and bought one to avoid the dealer's insane
    charges!]

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Tom Del Rosso@21:1/5 to Martin Brown on Fri May 9 02:20:09 2025
    Martin Brown wrote:
    Spain suffered a very spectacular near total loss of its national grid yesterday taking parts of France and all of Portugal down with it.
    This is an unprecedented failure of a supergrid system by cascade
    failure.
    It seems likely they had got the effect of widespread solar PV has on
    load shedding wrong (much like happened in the UK) and so it failed completely. Two events a second apart delivered the coup de grace.

    It looks like they spent a lot more effort simulating climate than they
    did simulating the grid system.

    --
    Defund the Thought Police

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Tom Del Rosso@21:1/5 to john larkin on Fri May 9 02:16:55 2025
    john larkin wrote:

    Making money implies efficiency. And vice versa.

    That's what the Left fundamentally fails to understand.


    --
    Defund the Thought Police

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Martin Brown@21:1/5 to Don Y on Fri May 9 09:21:32 2025
    On 08/05/2025 22:18, Don Y wrote:
    On 5/8/2025 12:51 PM, KevinJ93 wrote:
    When the coal miner's strike power usage reductions were in effect I
    was working at Marconi-Elliott in Borehamwood.  We were not allowed to
    have the lights or heating on but it was permitted to use test
    equipment so we would huddle around our Tektronix 547 scopes to keep
    warm, they used to put out a lot of heat.

    The only "utility" that I can recall being VOLUNTARILY rationed was water, back east, during a period of drought.  We were "strongly discouragd"
    from watering lawns, washing cars (car washes are far more efficient
    at this as they recycle the water), etc.

    We also live on the watershed for that. Just far enough north to be on
    the copious Northumbrian water supply (intended for all the now defunct steelworks) but with sewage outflow going downhill to Yorkshire Water.

    It has great advantages - Yorkshire Water has many leaks and not enough reservoirs so hose pipe bans are almost inevitable every summer. One particularly bad year they were moving drinking water in tankers from Northumberland Water to Yorkshire to maintain supply. When it gets
    really serious they have had to resort to stand pipes in the street.

    Looks like this year will be a bumper year for drought orders as there
    hasn't been any significant rain here for nearly a month now and we have
    have broken record temperatures for May already. Reservoirs in sensitive
    areas are at abnormally low levels for this time of year.

    https://www.theguardian.com/environment/2025/may/06/england-faces-drought-summer-reservoir-water-levels-dwindle

    Here, of course (desert southwest), peer pressure and threats of fines
    tend to keep folks inline.

    The idea of using a garden hose to "sweep" debris off your
    driveway or sidewalk would be met with a gasp and a glare.

    Fair enough. Where I live the water supply is the huge Kielder reservoir
    built to service a once thriving major steel industry on Teesside. Even
    if it didn't rain at all for a year we would still be on supply.

    Next village is on Yorkshire and often get hosepipe bans in summer.


    --
    Martin Brown

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Liz Tuddenham@21:1/5 to Martin Brown on Fri May 9 09:23:31 2025
    Martin Brown <'''newspam'''@nonad.co.uk> wrote:

    On 08/05/2025 17:19, Liz Tuddenham wrote:
    Martin Brown <'''newspam'''@nonad.co.uk> wrote:

    On 08/05/2025 13:43, Liz Tuddenham wrote:
    Don Y <blockedofcourse@foo.invalid> wrote:


    I don't think I've ever (regardless of where I've lived) experienced >>>> a deliberate power cut. A drunk may take out a telephone pole or
    a branch may fall on some high tension wires but no one has ever
    said "sorry, we're turning the lights out" (for whatever reason)

    That was exactly what happened in the UK in the early 1970s; we had a
    rota of power cuts lasting 4 hours each. I made up an automatic
    lighting unit based on a car battery for my parents. It used relays to >>> switch on when the mains went, then recharge at a fast rate until the
    battery voltage rose high enough, then trickle charge.

    That was during the various coal miners strikes which were at their peak >> then. Local newspapers had rotas for planned supply cuts.

    ISTR there was still the odd planned power cut even in the late 1970's
    but they became increasingly rare after that.

    A "Disconnection Rota" marker has recently started appearing on my electricity bill.

    You still get paper ones? I confess I haven't actually looked at my
    virtual "paper" electricity bill for ages. I use the online portal to
    check usage and how much they have taken in DD for prepayment.

    I still pay individual paper bills. Last year they sent me a ridiculous
    bill which they said was recalculated from several bills going back over
    more than a year. Their calculations were a load of nonsense and, after
    three hours working on it, a friend who is a retired accountant gave up
    in despair.

    I made payment conditional on a satisfactory explanation of how they had calculated the bill. Then they started sending weekly automated threats
    of bailiffs being sent to recover the 'debt' and the damage they would
    do to my credit rating. I sent many letters asking for an explanation,
    which merely received standard replies that didn't address my questions. Eventually they ceased replying and I never paid the bill.

    The government has now made that practice illegal, but if I had been on
    Direct Debit, they would have taken the money and I wouldn't have been
    able to get it back.


    --
    ~ Liz Tuddenham ~
    (Remove the ".invalid"s and add ".co.uk" to reply)
    www.poppyrecords.co.uk

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Don Y on Fri May 9 12:29:22 2025
    On 2025-05-09 02:13, Don Y wrote:
    On 5/8/2025 7:18 AM, Martin Brown wrote:
    On 08/05/2025 14:41, Carlos E.R. wrote:
    On 2025-05-08 14:44, Carlos E.R. wrote:

    UPS Topology: Standby (Offline) or Standby (Offline)

    {Phrase translated by DeepL, so inconsistent: Topología UPS: En
    espera (Fuera de línea) o Standby (Offline)}

    There are (at least) two major UPS topologies in play.

    One is where the power to the protected device is always made by the
    inverter and maintained at the correct main voltage irrespective of
    input voltage to the UPS. Useful in places where the local mains
    supply voltage goes up and down a lot depending on load.

    These are usually called "double conversion" (some call them "online"
    but that can be misleading).

    Yes, I have seen that name, online, on some units.


    The DeepL translation is not good. The vendor said "on wait (out of
    line) or Standby (Offline)", the second part in English. Probably a
    translation itself. I'm thinking the "or" is because they used "Spanish
    term or English term"


    Most of these (that I've encountered) are less efficient (cuz they
    are always in-the-loop) and often won't START without a functioning
    battery.

    Right.

    At a telephone exchange I found one "online" UPS cascaded from an
    "offline" UPS, IIRC. Used on the control room hardware (displays and
    printers).




    The other is a pass through of input mains voltage to the load under
    normal conditions and an isolation relay plus cold start of the
    inverter within a couple of cycles of the supply failure. This is more
    than good enough for PCs. Mine can withstand a 1s blackout unprotected
    without any difficulty but kitchen white goods clocks cannot.

    These often can do some line voltage adjusting with an autotransformer
    "for free" (part of the design).

    Yes, I have seen this. The house goes slightly "brown" and the UPS
    becomes active, I hear the clack of the relais and the buzz of the
    transformer.


    They, also, are available in models that can be started only with a
    valid battery or not.  Some require mains voltage to be present, as well.

    Right, they call this "cold start".


    There are also cheaper units that use "stepped" waveforms to approximate
    a sine wave; others that are more religious in their determination.

    This is more difficult to find from the specs. Price could be an indication.


    I do not see a reference to that "topology" except at the vendor. But
    it says that the expected battery life is 4 years.

    Ask for a guarantee on that... :>

    Hah! The warranty is two years :-D

    However, I do have another unit from this brand, and the battery did
    last longer. This particular unit uses two batteries, 24 volts, actually.

    Usually, I stick a label outside where I write the date when I replace
    the battery, and the price, but on this particular UPS I don't see the
    label. So I don't know the actual duration. Maybe I put the label inside?


    [ObTrivia:  SWMBO's vehicle needed a starting battery replacement
    ~3 years after purchase (battery life is about that for all vehicles,
    here; the heat cooks them).  As that was within the ~5 year "factory warranty" period, it was no charge -- so I didn't bother to get
    involved!

    THAT battery, of course, failed 3 years later.  But, as it was
    considered part of the original vehicle (despite being a replacement),
    there was no warranty extended to it.

    So, I went to Costco and bought one to avoid the dealer's insane
    charges!]

    That's funny. My car battery is currently 6 year old, and going fine,
    according to the garage (they just checked it). There was some
    "sulphate" on the lead stud which I told them to check.

    And here it is hot weather, for about 5 months a year. :-?

    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to Martin Brown on Fri May 9 03:38:27 2025
    On 5/9/2025 1:21 AM, Martin Brown wrote:
    On 08/05/2025 22:18, Don Y wrote:
    On 5/8/2025 12:51 PM, KevinJ93 wrote:
    When the coal miner's strike power usage reductions were in effect I was >>> working at Marconi-Elliott in Borehamwood.  We were not allowed to have the
    lights or heating on but it was permitted to use test equipment so we would >>> huddle around our Tektronix 547 scopes to keep warm, they used to put out a >>> lot of heat.

    The only "utility" that I can recall being VOLUNTARILY rationed was water, >> back east, during a period of drought.  We were "strongly discouragd"
    from watering lawns, washing cars (car washes are far more efficient
    at this as they recycle the water), etc.

    We also live on the watershed for that. Just far enough north to be on the copious Northumbrian water supply (intended for all the now defunct steelworks)
    but with sewage outflow going downhill to Yorkshire Water.

    We always had ample water -- so it was *common* to use a hose as a broom.
    Or, to water a lawn, wash a car in the driveway, etc.

    The "drought restrictions" were a bit of a shock to people as everyone
    always thought water was limitless. Driving around town there were
    many reservoirs -- some in places where only a single lane road would
    separate you from the reservoir to your left vs. the one on your right.

    It has great advantages - Yorkshire Water has many leaks and not enough reservoirs so hose pipe bans are almost inevitable every summer. One particularly bad year they were moving drinking water in tankers from Northumberland Water to Yorkshire to maintain supply. When it gets really serious they have had to resort to stand pipes in the street.

    Looks like this year will be a bumper year for drought orders as there hasn't been any significant rain here for nearly a month now and we have have broken record temperatures for May already. Reservoirs in sensitive areas are at abnormally low levels for this time of year.

    We've (here) been in a state of drought for ~25 years. And, that's
    with an normal annual precipitation of ~11 inches. The shift in mindset
    is astonishing -- to go from ~50 in/yr to less than a quarter of that.
    And, for it to be confined to just 2.5 months out of the year...

    Here, of course (desert southwest), peer pressure and threats of fines
    tend to keep folks inline.

    The idea of using a garden hose to "sweep" debris off your
    driveway or sidewalk would be met with a gasp and a glare.

    Fair enough. Where I live the water supply is the huge Kielder reservoir built
    to service a once thriving major steel industry on Teesside. Even if it didn't
    rain at all for a year we would still be on supply.

    Next village is on Yorkshire and often get hosepipe bans in summer.

    We "store" water in the ground. The hope being that we can extract
    it when the time comes.

    There have been some foreign companies exploiting our water supplies
    (deep wells to farm and then export the farmed products). I htink
    there is some action being taken to confound this practice.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Don Y on Fri May 9 12:29:11 2025
    On 2025-05-09 00:38, Don Y wrote:
    My mobile phone worked all the day, I could send and receive
    whatsapp messages.

    Are those processed "locally"?

    No. I don't know if they have centralized server or distributed.

    Some have "content distribution networks".

    I have a small computer doing server things, and it tried to email
    me as soon as the UPS said it was running on battery. That email did
    not reach me till the power came back; this could be that the fibre
    went OOS, or that the UPS at my router went down instantly. I do not
    know.

    Doesn't your UPS deliver log messages (to a syslog server or data
    dumps to an FTP service)?

    The one on the server did, yes, but the one on the router doesn't have
    that facility.

    I used to think syslogd support was just another gimmick.  But,
    I've come to appreciate being able to find ALL of the logs
    on ONE server (that is always up).  Hard to examine a log on
    a device that won't boot, etc.

    I agree. But my current router, for instance, doesn't have the feature.
    Doesn't even log locally. It is supplied by the ISP. The previous unit
    did have remote syslog capability, so I used it.


    I have each of mine configured to give me summaries of power consumption >>> and line conditions each minute.  And, use a syslogd on that same
    server.

    I don't think any of mine can report power usage.

    IIRC, they report:
    Date/Time
    Vmin/Vmax (input)
    Vout/Iout
    %Wout/%VAout/%capacity
    Frequency
    Vbat
    Internal temperature
    "external" temperature & humidity (intended for use in a server room)

    cer@Isengard:~> upsc salicru
    battery.charge: 100
    battery.voltage: 13.60
    battery.voltage.high: 13.60
    battery.voltage.low: 10.40
    battery.voltage.nominal: 12.0
    device.type: ups
    driver.name: blazer_usb
    driver.parameter.pollinterval: 2
    driver.parameter.port: auto
    driver.parameter.synchronous: no
    driver.version: 2.7.4
    driver.version.internal: 0.12
    input.current.nominal: 3.0
    input.frequency: 50.0
    input.frequency.nominal: 50
    input.voltage: 229.4
    input.voltage.fault: 229.4
    input.voltage.nominal: 230
    output.voltage: 229.4
    ups.beeper.status: enabled
    ups.delay.shutdown: 30
    ups.delay.start: 180
    ups.load: 13
    ups.productid: 5161
    ups.status: FSD OL
    ups.temperature: 25.0
    ups.type: offline / line interactive
    ups.vendorid: 0665
    cer@Isengard:~>


    It doesn't report current. There is "ups.load: 13", but no idea of the
    units.



    Charging at a slower rate and to a lower float voltage would
    compromise the UPS's availability -- but provide less maintenance costs
    (of course, the manufacturer wants to sell you batteries, so you
    can see where their priorities will lie!)

    Indeed.

    I saw in an Eaton model they mentioned two strategies - translated
    from Spanish:

    UPS Topology: Standby (Offline) or Standby (Offline)

    Eaton Ellipse ECO 650 IEC SAI Offline 650VA 400W
    Eaton P/N: EL650IEC

    I have a couple of eatons in the garage.  I didn't like them for
    use in the office as their fans (run continuously) are louder
    than I would like (and I have no desire to go tweaking fans)

    Ah, no, no fan in mine.

    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to Carlos E.R. on Fri May 9 04:05:00 2025
    On 5/9/2025 3:29 AM, Carlos E.R. wrote:
    cer@Isengard:~> upsc salicru
    battery.charge: 100
    battery.voltage: 13.60
    battery.voltage.high: 13.60
    battery.voltage.low: 10.40
    battery.voltage.nominal: 12.0
    device.type: ups
    driver.name: blazer_usb
    driver.parameter.pollinterval: 2
    driver.parameter.port: auto
    driver.parameter.synchronous: no
    driver.version: 2.7.4
    driver.version.internal: 0.12
    input.current.nominal: 3.0
    input.frequency: 50.0
    input.frequency.nominal: 50
    input.voltage: 229.4
    input.voltage.fault: 229.4
    input.voltage.nominal: 230
    output.voltage: 229.4
    ups.beeper.status: enabled
    ups.delay.shutdown: 30
    ups.delay.start: 180
    ups.load: 13
    ups.productid: 5161
    ups.status: FSD OL
    ups.temperature: 25.0
    ups.type: offline / line interactive
    ups.vendorid: 0665
    cer@Isengard:~>


    It doesn't report current. There is "ups.load: 13", but no idea of the units.

    It may be percent of maximum or somesuch.

    I saw in an Eaton model they mentioned two strategies - translated from
    Spanish:

    UPS Topology: Standby (Offline) or Standby (Offline)

    Eaton Ellipse ECO 650 IEC SAI Offline 650VA 400W
    Eaton P/N: EL650IEC

    I have a couple of eatons in the garage.  I didn't like them for
    use in the office as their fans (run continuously) are louder
    than I would like (and I have no desire to go tweaking fans)

    Ah, no, no fan in mine.

    These are 2KVA and larger. When on battery, there is a
    fair bit of waste heat that has to be blown off lest the
    internal temperature rise too much.

    I figure whoever specified the fans must have considered
    their efficiency so wouldn't want to go playing around
    with alternate devices and discover something died
    prematurely, as a result.

    [And, lots of UPSs available for rescue. I brought home
    four 2200VA units two weeks ago and decided to scrap them
    as they were double-conversion models. I cut off the
    #12AWG power cords and made four "extension cords" from
    the set!]

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Don Y on Fri May 9 13:24:51 2025
    On 2025-05-09 12:38, Don Y wrote:
    On 5/9/2025 1:21 AM, Martin Brown wrote:
    On 08/05/2025 22:18, Don Y wrote:
    On 5/8/2025 12:51 PM, KevinJ93 wrote:
    When the coal miner's strike power usage reductions were in effect I
    was working at Marconi-Elliott in Borehamwood.  We were not allowed
    to have the lights or heating on but it was permitted to use test
    equipment so we would huddle around our Tektronix 547 scopes to keep
    warm, they used to put out a lot of heat.

    The only "utility" that I can recall being VOLUNTARILY rationed was
    water,
    back east, during a period of drought.  We were "strongly discouragd"
    from watering lawns, washing cars (car washes are far more efficient
    at this as they recycle the water), etc.

    We also live on the watershed for that. Just far enough north to be on
    the copious Northumbrian water supply (intended for all the now
    defunct steelworks) but with sewage outflow going downhill to
    Yorkshire Water.

    We always had ample water -- so it was *common* to use a hose as a broom.
    Or, to water a lawn, wash a car in the driveway, etc.

    The "drought restrictions" were a bit of a shock to people as everyone
    always thought water was limitless.  Driving around town there were
    many reservoirs -- some in places where only a single lane road would separate you from the reservoir to your left vs. the one on your right.

    It has great advantages - Yorkshire Water has many leaks and not
    enough reservoirs so hose pipe bans are almost inevitable every
    summer. One particularly bad year they were moving drinking water in
    tankers from Northumberland Water to Yorkshire to maintain supply.
    When it gets really serious they have had to resort to stand pipes in
    the street.

    Looks like this year will be a bumper year for drought orders as there
    hasn't been any significant rain here for nearly a month now and we
    have have broken record temperatures for May already. Reservoirs in
    sensitive areas are at abnormally low levels for this time of year.

    We've (here) been in a state of drought for ~25 years.  And, that's
    with an normal annual precipitation of ~11 inches.  The shift in mindset
    is astonishing -- to go from ~50 in/yr to less than a quarter of that.
    And, for it to be confined to just 2.5 months out of the year...

    Here, of course (desert southwest), peer pressure and threats of fines
    tend to keep folks inline.

    The idea of using a garden hose to "sweep" debris off your
    driveway or sidewalk would be met with a gasp and a glare.

    Fair enough. Where I live the water supply is the huge Kielder
    reservoir built to service a once thriving major steel industry on
    Teesside. Even if it didn't rain at all for a year we would still be
    on supply.

    Next village is on Yorkshire and often get hosepipe bans in summer.

    We "store" water in the ground.  The hope being that we can extract
    it when the time comes.

    There have been some foreign companies exploiting our water supplies
    (deep wells to farm and then export the farmed products).  I htink
    there is some action being taken to confound this practice.


    Yesterday I heard on the news that most cities in the USA are sinking
    down, due to water extraction from wells.

    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Bill Sloman@21:1/5 to Tom Del Rosso on Fri May 9 21:25:55 2025
    On 9/05/2025 4:16 pm, Tom Del Rosso wrote:
    john larkin wrote:

    Making money implies efficiency. And vice versa.

    That's what the Left fundamentally fails to understand.

    What the right fails to mention is that making money mostly involves
    cheating people. If you can do something more efficiently that other
    people you can make money out of it, but it's a lot easier to claim that
    you are more efficient and simply cheat.

    The left goes in for detailed enquiries about what is actually going on,
    which the right like to characterise as officious invasions of privacy,
    and often subvert by tricks like regulatory capture.

    Look up "rent-seeking" sometime.

    https://en.wikipedia.org/wiki/Rent-seeking

    That's what Trump's tariffs are doing for American manufacturers - they
    can suddenly 10% more (or whatever) for their products than their
    foreign competitors, purely because they are American.

    --
    Bill Sloman, Sydney

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Bill Sloman@21:1/5 to Tom Del Rosso on Fri May 9 21:35:59 2025
    On 9/05/2025 4:20 pm, Tom Del Rosso wrote:
    Martin Brown wrote:
    Spain suffered a very spectacular near total loss of its national grid
    yesterday taking parts of France and all of Portugal down with it.
    This is an unprecedented failure of a supergrid system by cascade
    failure.
    It seems likely they had got the effect of widespread solar PV has on
    load shedding wrong (much like happened in the UK) and so it failed
    completely. Two events a second apart delivered the coup de grace.

    It looks like they spent a lot more effort simulating climate than they
    did simulating the grid system.

    Simulating the climate is science, and nobody spends a lot on that.
    Simulating the grid system is business, if it is done right, but there
    are lot of different mechanisms active in regulating the grid, and most
    of them are commercial in confidence, so only the businesses that make
    the mechanisms know enough to be able simulate them, and it takes a
    regulatory agency to force all the businesses involved to get together
    to work out how their various mechanisms will interact.

    Regulatory capture means that the agency is unlikely to force the
    businesses to do it.

    --
    Bill Sloman, Sydney

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Don Y on Fri May 9 14:07:29 2025
    On 2025-05-08 23:32, Don Y wrote:
    I don't think I've ever (regardless of where I've lived) experienced
    a deliberate power cut.  A drunk may take out a telephone pole or
    a branch may fall on some high tension wires but no one has ever
    said "sorry, we're turning the lights out" (for whatever reason)

    Not the same, but past Monday someone stole the signalling cable in
    the high speed railway to Andalussia, leaving the entire line OOS. I
    heard that trains were authorized to run at 40 Km/h, so that they
    could see the other train in time and tail it. Not sure it worked.

    The authorities talked of sabotage. The price of the cable when new is
    not even a thousand euros, but the damage to thousands of people is huge.

    There are places where copper products (wire, plumbing) are stolen
    for their "recycle value".  The solution, so far, has been to
    require recyclers to get and record identification of people
    bringing in such items.

    Not enough, apparently.

    The hut they vandalized has a notice board that says all the cables are aluminum.


    A friend had the copper stripped from the roof-mounted cooling unit at
    his business.  Landlord held *him* responsible for its repair/replacement.


    Uff.

    I think there have been cases of people trying to steal the wiring in
    outside lighting systems -- and not taking adequate provisions to
    protect against electrocution!

    Yeah, here too. They even tried to rip the railway catenary at some
    place. Some of those died on the spot.



    I would like to make some backlit copper lighted displays for the house
    (AZ is The Copper State) but am afraid its oxidized color would attract
    some thief eager to make a few dollars off it.

    Sigh.

    Some places have copper roofs.


    Yup.  They have a rationalization, though -- they are trying to
    provide the
    highest availability.  Else, how much availability do you sacrifice to
    maximize battery life?  Do you then start specifying battery life as a
    primary selection criteria?

    [Most SOHO users buy a UPS -- thinking they are being "professional"
    -- and
    then discard it when the battery needs replacing and they discover the
    costs charged by the UPS manufacturer -- or local "battery stores"]

    25€. A 9Ah item, high discharge rate.

    Different grades exist, here.  If you buy from an electronics supplier (e.g., Digikey), you will likely get a "fairer" price (value for money)
    than a local battery store (which may be 50% higher).  UPS manufacturers typically charge about double what a reasonable price might be (though
    the usually assemble the batteries into the requisite "packs"...
    a trivial exercise for even 48V units).

    Let me check. The computer place here offers:


    Phasak PHB 1209 Batería SAI/UPS 9Ah 12V 29,17€

    Salicru UBT 12/9 Batería para SAI/UPS 9aH 12v 18,98€ (was 20,63€)

    So the brand name battery replacement for my UPS is actually cheaper
    than what I paid. Surprise!


    Digikey used to have a policy of free shipping for prepaid (cash)
    orders.  I would buy batteries in lots of 10 and send prepayment.
    Shipping charges can be a significant fraction of a battery's
    cost.  They now exclude batteries from this policy (when I last
    checked).

    Right, they are very heavy. Yep, the place above charges 5.25€ for shipping.


    I suspect the problem (rationalized by the manufacturers) is trying to >>>>> bring the battery back to full charge ASAP -- as well as keeping the >>>>> highest state of charge that the battery can support.

    Which taken to extremes is very bad for battery life.

    Of course.  But, they are in the PRIMARY business of selling batteries, >>> not UPSs!

    Ugh.

    And having disgruntled customers.

    Think about it.  If the *UPS* (hardware) failed at 3 year intervals,
    no one would buy them!  They'd be seen as poor quality.

    But, no one is surprised that BATTERIES need replacement!

    With the exception of multi-user servers, individual workstations
    usually have auto-backup provisions *in* the key applications.
    And, in the event of an outage (even if the machine stays up),
    the user is usually distracted by the rest of the house/office
    going black; is ~15 minutes of uptime going to be enough if the
    user isn't AT the machine when power fails?

    You need software monitoring to hibernate or power off the machine.

    I have every workstation set to hibernate after ~20 minutes
    of inactivity.  This gives me time to get a cup of tea, go to
    the bathroom, answer the door/phone, etc. without the workstation
    cycling off and on.

    As "activity"  is defined by user interactions, this means I
    have to deliberately start an application that disables "sleep"
    if I won't be interacting with the machine and want to prevent
    it from sleeping.  E.g., an SSH session with a remote host that
    will be busy for a while; if the workstation sleeps, the SSH
    session terminates and the shell on the remote is killed off.

    <frown>

    Right.


    No one has yet to address the market where TCO is the driving
    criteria.







    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Liz Tuddenham on Fri May 9 13:20:24 2025
    On 2025-05-09 10:23, Liz Tuddenham wrote:
    Martin Brown <'''newspam'''@nonad.co.uk> wrote:

    On 08/05/2025 17:19, Liz Tuddenham wrote:
    Martin Brown <'''newspam'''@nonad.co.uk> wrote:

    On 08/05/2025 13:43, Liz Tuddenham wrote:
    Don Y <blockedofcourse@foo.invalid> wrote:


    I don't think I've ever (regardless of where I've lived) experienced >>>>>> a deliberate power cut. A drunk may take out a telephone pole or
    a branch may fall on some high tension wires but no one has ever
    said "sorry, we're turning the lights out" (for whatever reason)

    That was exactly what happened in the UK in the early 1970s; we had a >>>>> rota of power cuts lasting 4 hours each. I made up an automatic
    lighting unit based on a car battery for my parents. It used relays to >>>>> switch on when the mains went, then recharge at a fast rate until the >>>>> battery voltage rose high enough, then trickle charge.

    That was during the various coal miners strikes which were at their peak >>>> then. Local newspapers had rotas for planned supply cuts.

    ISTR there was still the odd planned power cut even in the late 1970's >>>> but they became increasingly rare after that.

    A "Disconnection Rota" marker has recently started appearing on my
    electricity bill.

    You still get paper ones? I confess I haven't actually looked at my
    virtual "paper" electricity bill for ages. I use the online portal to
    check usage and how much they have taken in DD for prepayment.

    I still pay individual paper bills. Last year they sent me a ridiculous
    bill which they said was recalculated from several bills going back over
    more than a year. Their calculations were a load of nonsense and, after three hours working on it, a friend who is a retired accountant gave up
    in despair.

    I made payment conditional on a satisfactory explanation of how they had calculated the bill. Then they started sending weekly automated threats
    of bailiffs being sent to recover the 'debt' and the damage they would
    do to my credit rating. I sent many letters asking for an explanation,
    which merely received standard replies that didn't address my questions. Eventually they ceased replying and I never paid the bill.

    The government has now made that practice illegal, but if I had been on Direct Debit, they would have taken the money and I wouldn't have been
    able to get it back.

    Over here, it is not possible to not use direct debit.

    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to Carlos E.R. on Fri May 9 05:52:33 2025
    On 5/9/2025 4:24 AM, Carlos E.R. wrote:
    We "store" water in the ground.  The hope being that we can extract
    it when the time comes.

    There have been some foreign companies exploiting our water supplies
    (deep wells to farm and then export the farmed products).  I htink
    there is some action being taken to confound this practice.

    Yesterday I heard on the news that most cities in the USA are sinking down, due
    to water extraction from wells.

    I don't know about "most cities"; here, we rely on ground water
    pumped FROM wells. But, other places I've lived had surface
    reservoirs to draw from, filled "from above" (precipitation)

    "Subsidence" is a problem as buildings tend to crack as they
    settle. And, once that portion of an aquifer collapses,
    there's no real way to "refill" it. So, you lose capacity.

    I suspect most parts of the country will start having water
    problems. It will likely be hardest on those places who
    have been gluttonous with their water usage.

    Great Salt Lake is apparently a foul waste puddle, now.
    Folks in Utah have tended to feel water was theirs to use
    without concerns for conservation.

    <https://www.sciencenews.org/article/great-salt-lake-shrinking-utah-drought>

    Note before and after pics about 1/3 of the way through the article.

    "Daddy, my teacher said there used to be a LAKE here..."

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to All on Fri May 9 05:21:51 2025
    They, also, are available in models that can be started only with a
    valid battery or not.  Some require mains voltage to be present, as well.

    Right, they call this "cold start".

    It's handy during outages -- especially if you have a lot
    of UPSs! :> With CFL and LED lights, you can light up
    a house for hours off battery, run a TV, computer,
    etc.

    But, if you can't get the UPSs to power on in the absence of mains
    voltage, then you are limited to whichever units happen to be
    on at the time of the outage!

    There are also cheaper units that use "stepped" waveforms to approximate
    a sine wave; others that are more religious in their determination.

    This is more difficult to find from the specs. Price could be an indication.

    Usually "pure sine wave" is part of the description

    I do not see a reference to that "topology" except at the vendor. But it >>>> says that the expected battery life is 4 years.

    Ask for a guarantee on that... :>

    Hah! The warranty is two years :-D

    Why is that not surprising?

    However, I do have another unit from this brand, and the battery did last longer. This particular unit uses two batteries, 24 volts, actually.

    Usually, I stick a label outside where I write the date when I replace the battery, and the price, but on this particular UPS I don't see the label. So I
    don't know the actual duration. Maybe I put the label inside?

    When you replace the battery pack in my units, you are prompted
    to make that declaration and the date (month/yr) is remembered.
    Mine have alphanumeric displays so you can query these things
    if you don't have a network interface installed.

    [ObTrivia:  SWMBO's vehicle needed a starting battery replacement
    ~3 years after purchase (battery life is about that for all vehicles,
    here; the heat cooks them).  As that was within the ~5 year "factory
    warranty" period, it was no charge -- so I didn't bother to get
    involved!

    THAT battery, of course, failed 3 years later.  But, as it was
    considered part of the original vehicle (despite being a replacement),
    there was no warranty extended to it.

    So, I went to Costco and bought one to avoid the dealer's insane
    charges!]

    That's funny. My car battery is currently 6 year old, and going fine, according
    to the garage (they just checked it). There was some "sulphate" on the lead stud which I told them to check.

    And here it is hot weather, for about 5 months a year. :-?

    It is hot almost all year round, here. We've already hit 100F and will
    be back there in another day or two (brief cold spell -- 70's -- from
    a storm front).

    Driveways have tire marks as the hot concrete makes it far too
    easy to "scuff".

    The three years is so predictable that you just remove the
    battery AT three years, even if it isn't defective. It
    will be replaced (without prorating) no questions asked.

    Wait for it to die of its own accord and you'll be grumbling
    about the inconvenience and cost (as the warranty prorates
    the value of the battery beyond the 3 year mark)!

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Don Y on Fri May 9 14:20:41 2025
    On 2025-05-09 13:05, Don Y wrote:
    On 5/9/2025 3:29 AM, Carlos E.R. wrote:
    cer@Isengard:~> upsc salicru
    battery.charge: 100
    battery.voltage: 13.60
    battery.voltage.high: 13.60
    battery.voltage.low: 10.40
    battery.voltage.nominal: 12.0
    device.type: ups
    driver.name: blazer_usb
    driver.parameter.pollinterval: 2
    driver.parameter.port: auto
    driver.parameter.synchronous: no
    driver.version: 2.7.4
    driver.version.internal: 0.12
    input.current.nominal: 3.0
    input.frequency: 50.0
    input.frequency.nominal: 50
    input.voltage: 229.4
    input.voltage.fault: 229.4
    input.voltage.nominal: 230
    output.voltage: 229.4
    ups.beeper.status: enabled
    ups.delay.shutdown: 30
    ups.delay.start: 180
    ups.load: 13
    ups.productid: 5161
    ups.status: FSD OL
    ups.temperature: 25.0
    ups.type: offline / line interactive
    ups.vendorid: 0665
    cer@Isengard:~>


    It doesn't report current. There is "ups.load: 13", but no idea of the
    units.

    It may be percent of maximum or somesuch.

    I saw in an Eaton model they mentioned two strategies - translated
    from Spanish:

    UPS Topology: Standby (Offline) or Standby (Offline)

    Eaton Ellipse ECO 650 IEC SAI Offline 650VA 400W
    Eaton P/N: EL650IEC

    I have a couple of eatons in the garage.  I didn't like them for
    use in the office as their fans (run continuously) are louder
    than I would like (and I have no desire to go tweaking fans)

    Ah, no, no fan in mine.

    These are 2KVA and larger.  When on battery, there is a
    fair bit of waste heat that has to be blown off lest the
    internal temperature rise too much.

    Ah, ok.


    I figure whoever specified the fans must have considered
    their efficiency so wouldn't want to go playing around
    with alternate devices and discover something died
    prematurely, as a result.

    [And, lots of UPSs available for rescue.  I brought home
    four 2200VA units two weeks ago and decided to scrap them
    as they were double-conversion models.  I cut off the
    #12AWG power cords and made four "extension cords" from
    the set!]

    Heh.

    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Don Y on Fri May 9 14:18:53 2025
    On 2025-05-08 23:57, Don Y wrote:
    That is a feature of UPS design that specsmanship to get the longest
    run time for the sales datasheet means that they cook their
    batteries. I have seen them swell to the point of bursting inside a
    UPS. Thick rubber gloves needed to remove the remains. Support
    metalwork was a real corroded rusty mess but electronics above it
    remained OK.

    That level of "not working" has not happened to me. Maybe because some
    power failure makes me find out that the battery is dead.

    I've rescued a fair number of UPSs over the years.  In probably 80% of
    them, the batteries have swollen to the point where removing the battery
    or battery PACK is difficult.  This is especially true of the "better"
    UPSs (sine output, 48V battery, metal fabrication) where there is
    little "give" in the mechanical design.  Often one has to disassemble
    the UPS to see where one can gain leverage on the battery pack
    to force it from the case.

    They really think I'm going to buy their vastly overpriced replacements?

    I don't.

    But last battery I replaced was not even two years old, rather 5
    months short. I replaced it just in time to serve during the Gran Apagón.

    That's the problem; you don't KNOW how long a particular battery will last, even in an environment where it is never called on for backup!

    Instead, you are forced into a "reactive" mode -- waiting for something
    to tell you you're screwed and need a replacement, now!

    My largest UPS uses 50 pound batteries (8 of them).

    Are they 12 volts each, or just one cell?

    On phone exchanges I saw huge batteries, actually individual cells
    connected in series. 48 volts nominally, so 24 cells. I don't think they
    were gel types, they needed adding water now and then.

    It's
    REALLY inconvenient to have to replace them *now* cuz they
    are costly and physically inconvenient to man-handle.  I
    would much appreciate some advance notice that they are likely
    to need replacement in, say, 30 days (given the current usage
    pattern).

    Maybe folks will start putting more smarts into their product
    designs instead of simple "threshold" events.

    Some UPS say they can test the battery. Mine do not, or the software I
    have doesn't.

    When looking at specs for a replacement UPS, possibly an Eaton, I saw
    they mentioned emitting a beep when battery is bad.

    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From john larkin@21:1/5 to All on Fri May 9 07:35:10 2025
    On Thu, 8 May 2025 14:18:47 -0700, Don Y <blockedofcourse@foo.invalid>
    wrote:

    On 5/8/2025 12:51 PM, KevinJ93 wrote:
    When the coal miner's strike power usage reductions were in effect I was
    working at Marconi-Elliott in Borehamwood.á We were not allowed to have the >> lights or heating on but it was permitted to use test equipment so we would >> huddle around our Tektronix 547 scopes to keep warm, they used to put out a lot
    of heat.

    The only "utility" that I can recall being VOLUNTARILY rationed was water, >back east, during a period of drought. We were "strongly discouragd"
    from watering lawns, washing cars (car washes are far more efficient
    at this as they recycle the water), etc.

    Here, of course (desert southwest), peer pressure and threats of fines
    tend to keep folks inline.

    The idea of using a garden hose to "sweep" debris off your
    driveway or sidewalk would be met with a gasp and a glare.


    Here in San Francisco you can do that, or wash a car, but the hose
    must have an automatic shutoff nozzle on the end. Of course nobody
    enforces that.

    We rarely have lawns (real living ones) here, and no pools that I know
    of, which helps.

    I hated mowing lawns. What stupid things.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From john larkin@21:1/5 to robin_listas@es.invalid on Fri May 9 07:55:52 2025
    On Fri, 9 May 2025 13:24:51 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-09 12:38, Don Y wrote:
    On 5/9/2025 1:21 AM, Martin Brown wrote:
    On 08/05/2025 22:18, Don Y wrote:
    On 5/8/2025 12:51 PM, KevinJ93 wrote:
    When the coal miner's strike power usage reductions were in effect I >>>>> was working at Marconi-Elliott in Borehamwood.á We were not allowed
    to have the lights or heating on but it was permitted to use test
    equipment so we would huddle around our Tektronix 547 scopes to keep >>>>> warm, they used to put out a lot of heat.

    The only "utility" that I can recall being VOLUNTARILY rationed was
    water,
    back east, during a period of drought.á We were "strongly discouragd"
    from watering lawns, washing cars (car washes are far more efficient
    at this as they recycle the water), etc.

    We also live on the watershed for that. Just far enough north to be on
    the copious Northumbrian water supply (intended for all the now
    defunct steelworks) but with sewage outflow going downhill to
    Yorkshire Water.

    We always had ample water -- so it was *common* to use a hose as a broom.
    Or, to water a lawn, wash a car in the driveway, etc.

    The "drought restrictions" were a bit of a shock to people as everyone
    always thought water was limitless.á Driving around town there were
    many reservoirs -- some in places where only a single lane road would
    separate you from the reservoir to your left vs. the one on your right.

    It has great advantages - Yorkshire Water has many leaks and not
    enough reservoirs so hose pipe bans are almost inevitable every
    summer. One particularly bad year they were moving drinking water in
    tankers from Northumberland Water to Yorkshire to maintain supply.
    When it gets really serious they have had to resort to stand pipes in
    the street.

    Looks like this year will be a bumper year for drought orders as there
    hasn't been any significant rain here for nearly a month now and we
    have have broken record temperatures for May already. Reservoirs in
    sensitive areas are at abnormally low levels for this time of year.

    We've (here) been in a state of drought for ~25 years.á And, that's
    with an normal annual precipitation of ~11 inches.á The shift in mindset
    is astonishing -- to go from ~50 in/yr to less than a quarter of that.
    And, for it to be confined to just 2.5 months out of the year...

    Here, of course (desert southwest), peer pressure and threats of fines >>>> tend to keep folks inline.

    The idea of using a garden hose to "sweep" debris off your
    driveway or sidewalk would be met with a gasp and a glare.

    Fair enough. Where I live the water supply is the huge Kielder
    reservoir built to service a once thriving major steel industry on
    Teesside. Even if it didn't rain at all for a year we would still be
    on supply.

    Next village is on Yorkshire and often get hosepipe bans in summer.

    We "store" water in the ground.á The hope being that we can extract
    it when the time comes.

    There have been some foreign companies exploiting our water supplies
    (deep wells to farm and then export the farmed products).á I htink
    there is some action being taken to confound this practice.


    Yesterday I heard on the news that most cities in the USA are sinking
    down, due to water extraction from wells.

    Not most cities, but many. Some places that have lots of water are
    sinking because pumps kick in when there's lots of rain. And because
    most of the surfaces have been paved over. New Orleans is on the
    Mississippi river but is sinking, because levees now keep the river
    out of town and pumps export the rainwater. Usually.

    (Many of the older pumping stations ran on 25 Hz power, and shut down
    in a hurricane.)

    The California Central Valley is sinking from groundwater extraction,
    most by farms. It's crazy to grow nuts and rice and wheat, export
    crops, in what is legally a desert.

    It's getting harder and harder to sink a well deep enough to hit
    actual water.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Joe Gwinn@21:1/5 to robin_listas@es.invalid on Fri May 9 12:22:02 2025
    On Fri, 9 May 2025 14:18:53 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-08 23:57, Don Y wrote:
    That is a feature of UPS design that specsmanship to get the longest
    run time for the sales datasheet means that they cook their
    batteries. I have seen them swell to the point of bursting inside a
    UPS. Thick rubber gloves needed to remove the remains. Support
    metalwork was a real corroded rusty mess but electronics above it
    remained OK.

    That level of "not working" has not happened to me. Maybe because some
    power failure makes me find out that the battery is dead.

    I've rescued a fair number of UPSs over the years.á In probably 80% of
    them, the batteries have swollen to the point where removing the battery
    or battery PACK is difficult.á This is especially true of the "better"
    UPSs (sine output, 48V battery, metal fabrication) where there is
    little "give" in the mechanical design.á Often one has to disassemble
    the UPS to see where one can gain leverage on the battery pack
    to force it from the case.

    They really think I'm going to buy their vastly overpriced replacements? >>>
    I don't.

    But last battery I replaced was not even two years old, rather 5
    months short. I replaced it just in time to serve during the Gran Apag≤n. >>
    That's the problem; you don't KNOW how long a particular battery will last, >> even in an environment where it is never called on for backup!

    Instead, you are forced into a "reactive" mode -- waiting for something
    to tell you you're screwed and need a replacement, now!

    My largest UPS uses 50 pound batteries (8 of them).

    Are they 12 volts each, or just one cell?

    On phone exchanges I saw huge batteries, actually individual cells
    connected in series. 48 volts nominally, so 24 cells. I don't think they
    were gel types, they needed adding water now and then.

    The were most likely KS-20472 BELLCELL lead-acid battery cells,
    originally made by Western Electric, or European equivalent. These
    are 2.2 volts per cell.

    .<https://library.industrialsolutions.abb.com/publibrary/checkout/107852477?TNR=Installation%20and%20Instruction%7C107852477%7CPDF>

    Joe

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to Carlos E.R. on Fri May 9 14:32:11 2025
    On 5/9/2025 5:07 AM, Carlos E.R. wrote:
    There are places where copper products (wire, plumbing) are stolen
    for their "recycle value".  The solution, so far, has been to
    require recyclers to get and record identification of people
    bringing in such items.

    Not enough, apparently.

    The hut they vandalized has a notice board that says all the cables are aluminum.

    I wonder if the would-be thieves even bother to READ...

    I think there have been cases of people trying to steal the wiring in
    outside lighting systems -- and not taking adequate provisions to
    protect against electrocution!

    Yeah, here too. They even tried to rip the railway catenary at some place. Some
    of those died on the spot.

    How much "protection" do you think a SIGN would provide? "Hey, Bob,
    don't these got electricity in them?"

    I would like to make some backlit copper lighted displays for the house
    (AZ is The Copper State) but am afraid its oxidized color would attract
    some thief eager to make a few dollars off it.

    Sigh.

    Some places have copper roofs.

    Yes. We had looked into it (because it is far more durable than
    virtually any other roofing material in common use, here (including
    tile). But, you need a minimum pitch to ensure the water doesn't
    pool on the roof.

    25€. A 9Ah item, high discharge rate.

    Different grades exist, here.  If you buy from an electronics supplier
    (e.g., Digikey), you will likely get a "fairer" price (value for money)
    than a local battery store (which may be 50% higher).  UPS manufacturers
    typically charge about double what a reasonable price might be (though
    the usually assemble the batteries into the requisite "packs"...
    a trivial exercise for even 48V units).

    Let me check. The computer place here offers:

    Phasak PHB 1209 Batería SAI/UPS 9Ah 12V        29,17€

    Salicru UBT 12/9 Batería para SAI/UPS 9aH 12v    18,98€ (was 20,63€)

    So the brand name battery replacement for my UPS is actually cheaper than what
    I paid. Surprise!

    The nominal 12V 7.2AHr batteries (also available at 9AHr in the same
    case size) that many of my UPSs use are ~20-30, here, neglecting
    shipping and tax. Putting two (for smaller UPSs) or 4 in each UPS
    gets pricey -- if you have to do it every 3 years (and have a dozen
    UPSs)!

    I've tried a new configuration where I am hanging many of the
    UPSs off a couple of larger units. The thinking being that I
    only have to maintain the larger units' batteries (and still
    get the benefits of a UPS per workstation).

    Digikey used to have a policy of free shipping for prepaid (cash)
    orders.  I would buy batteries in lots of 10 and send prepayment.
    Shipping charges can be a significant fraction of a battery's
    cost.  They now exclude batteries from this policy (when I last
    checked).

    Right, they are very heavy. Yep, the place above charges 5.25€ for shipping.

    As I said, I try to rescue them (often I come across NiB UPSs
    that some moron in IT ordered but opted not to install.
    As the recycle value of batteries is just weight (regardless of
    ability to hold a charge), I swap my dead batteries for such
    new batteries and everyone is happy!

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to Carlos E.R. on Fri May 9 14:44:23 2025
    On 5/9/2025 5:20 AM, Carlos E.R. wrote:
    I figure whoever specified the fans must have considered
    their efficiency so wouldn't want to go playing around
    with alternate devices and discover something died
    prematurely, as a result.

    [And, lots of UPSs available for rescue.  I brought home
    four 2200VA units two weeks ago and decided to scrap them
    as they were double-conversion models.  I cut off the
    #12AWG power cords and made four "extension cords" from
    the set!]

    Heh.

    They are short (~10 ft) but will come in handy in the back yard,
    garage, and kitchen as generic extension cords (despite having
    NEMA 5-20Ps on the supply -- and load -- ends)

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Joe Gwinn on Fri May 9 23:28:29 2025
    On 2025-05-09 18:22, Joe Gwinn wrote:
    On Fri, 9 May 2025 14:18:53 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-08 23:57, Don Y wrote:
    That is a feature of UPS design that specsmanship to get the longest >>>>> run time for the sales datasheet means that they cook their
    batteries. I have seen them swell to the point of bursting inside a
    UPS. Thick rubber gloves needed to remove the remains. Support
    metalwork was a real corroded rusty mess but electronics above it
    remained OK.

    That level of "not working" has not happened to me. Maybe because some >>>> power failure makes me find out that the battery is dead.

    I've rescued a fair number of UPSs over the years.  In probably 80% of
    them, the batteries have swollen to the point where removing the battery >>> or battery PACK is difficult.  This is especially true of the "better"
    UPSs (sine output, 48V battery, metal fabrication) where there is
    little "give" in the mechanical design.  Often one has to disassemble
    the UPS to see where one can gain leverage on the battery pack
    to force it from the case.

    They really think I'm going to buy their vastly overpriced replacements? >>>>
    I don't.

    But last battery I replaced was not even two years old, rather 5
    months short. I replaced it just in time to serve during the Gran Apagón. >>>
    That's the problem; you don't KNOW how long a particular battery will last, >>> even in an environment where it is never called on for backup!

    Instead, you are forced into a "reactive" mode -- waiting for something
    to tell you you're screwed and need a replacement, now!

    My largest UPS uses 50 pound batteries (8 of them).

    Are they 12 volts each, or just one cell?

    On phone exchanges I saw huge batteries, actually individual cells
    connected in series. 48 volts nominally, so 24 cells. I don't think they
    were gel types, they needed adding water now and then.

    The were most likely KS-20472 BELLCELL lead-acid battery cells,
    originally made by Western Electric, or European equivalent. These
    are 2.2 volts per cell.

    .<https://library.industrialsolutions.abb.com/publibrary/checkout/107852477?TNR=Installation%20and%20Instruction%7C107852477%7CPDF>

    Those I saw were prismatic, not cylindrical.

    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to Carlos E.R. on Fri May 9 14:41:28 2025
    On 5/9/2025 5:18 AM, Carlos E.R. wrote:
    Instead, you are forced into a "reactive" mode -- waiting for something
    to tell you you're screwed and need a replacement, now!

    My largest UPS uses 50 pound batteries (8 of them).

    Are they 12 volts each, or just one cell?

    No, real batteries. They are just considerably larger than
    the sorts of SLAs you find in most UPSs (the battery
    compartments are about the size of a dishwasher in total
    volume; the UPS electronics are in a separate box)

    On phone exchanges I saw huge batteries, actually individual cells connected in
    series. 48 volts nominally, so 24 cells. I don't think they were gel types, they needed adding water now and then.

    Yes. You can adjust the specific gravity of the electrolyte to
    increase battery service life.

    The "exchange" is actually POWERED by the batteries and the
    mains acts to charge them. The CO that my uncle managed
    had a small jet engine in an out-building that powered the
    backup generator. It is INCREDIBLY loud (housed in its
    own building, likely to confine the sound) when operating.
    The "billing computer" was left without a backup power
    supply (no doubt because it would represent a larger load
    and its requirements could be expected to change, over time,
    more than the phone network itself (in the 60's, it was hard
    to imagine how computers would evolve)

    It's
    REALLY inconvenient to have to replace them *now* cuz they
    are costly and physically inconvenient to man-handle.  I
    would much appreciate some advance notice that they are likely
    to need replacement in, say, 30 days (given the current usage
    pattern).

    Maybe folks will start putting more smarts into their product
    designs instead of simple "threshold" events.

    Some UPS say they can test the battery. Mine do not, or the software I have doesn't.

    Yes, but the problem with this is that they use YOUR load to test
    the battery! So, if the battery is shit, then the daily/weekly
    test is guaranteed to drop power to your load!

    The first thing that I do is disable this test. It's just one more
    opportunity for the system to crash (if the battery IS bad, I
    will find out when the next RARE outage strikes; why sooner?)

    When looking at specs for a replacement UPS, possibly an Eaton, I saw they mentioned emitting a beep when battery is bad.

    They likely don't load test, then. Perhaps just watch the open
    circuit voltage on the "charged" battery.

    It is distressing how little the technology associated with
    battery monitoring and charging has advanced in these sorts
    of applications. Again, likely because there is little
    incentive to maximize battery life!

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Glen Walpert@21:1/5 to Joe Gwinn on Fri May 9 22:50:48 2025
    On Fri, 09 May 2025 12:22:02 -0400, Joe Gwinn wrote:

    On Fri, 9 May 2025 14:18:53 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-08 23:57, Don Y wrote:
    That is a feature of UPS design that specsmanship to get the longest >>>>> run time for the sales datasheet means that they cook their
    batteries. I have seen them swell to the point of bursting inside a
    UPS. Thick rubber gloves needed to remove the remains. Support
    metalwork was a real corroded rusty mess but electronics above it
    remained OK.

    That level of "not working" has not happened to me. Maybe because
    some power failure makes me find out that the battery is dead.

    I've rescued a fair number of UPSs over the years.  In probably 80% of
    them, the batteries have swollen to the point where removing the
    battery or battery PACK is difficult.  This is especially true of the
    "better" UPSs (sine output, 48V battery, metal fabrication) where
    there is little "give" in the mechanical design.  Often one has to
    disassemble the UPS to see where one can gain leverage on the battery
    pack to force it from the case.

    They really think I'm going to buy their vastly overpriced
    replacements?

    I don't.

    But last battery I replaced was not even two years old, rather 5
    months short. I replaced it just in time to serve during the Gran
    Apagón.

    That's the problem; you don't KNOW how long a particular battery will
    last,
    even in an environment where it is never called on for backup!

    Instead, you are forced into a "reactive" mode -- waiting for
    something to tell you you're screwed and need a replacement, now!

    My largest UPS uses 50 pound batteries (8 of them).

    Are they 12 volts each, or just one cell?

    On phone exchanges I saw huge batteries, actually individual cells >>connected in series. 48 volts nominally, so 24 cells. I don't think they >>were gel types, they needed adding water now and then.

    The were most likely KS-20472 BELLCELL lead-acid battery cells,
    originally made by Western Electric, or European equivalent. These are
    2.2 volts per cell.

    .<https://library.industrialsolutions.abb.com/publibrary/checkout/
    107852477?TNR=Installation%20and%20Instruction%7C107852477%7CPDF>

    Joe

    Back in the mid 80's I read a review of lead acid battery manufacturing technology which listed the Western Electric round cell design as the most reliable by far, with some batteries testing at higher capacity after 20
    years in backup service than when new - benign environment and low cycles
    noted - and average service life well over 10 years. The high reliability
    is mostly due to the horizontal stack of symmetrical round plates which
    can expand and contract due to charge/discharge with very low stress. The other key is pure lead bus and plate grids made possible by the low stress design - the lead-antimony alloy used in vertical plate batteries for
    strength and low cost (recycled lead) corrodes much more rapidly.

    Reminds me of one of the 2 major east coast blackouts, where the
    transmission line lost due to an incorrect relay setting would have been a minor incident except for the failure of an automatic switch to transfer
    to the available and adequate alternate source due to long dead backup batteries.

    Glen

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Don Y on Sat May 10 03:26:38 2025
    On 2025-05-09 23:41, Don Y wrote:
    On 5/9/2025 5:18 AM, Carlos E.R. wrote:

    ...

    When looking at specs for a replacement UPS, possibly an Eaton, I saw
    they mentioned emitting a beep when battery is bad.

    They likely don't load test, then.  Perhaps just watch the open
    circuit voltage on the "charged" battery.

    It is distressing how little the technology associated with
    battery monitoring and charging has advanced in these sorts
    of applications.  Again, likely because there is little
    incentive to maximize battery life!

    At my garage they have some gadgetry that I have not seen to test
    batteries. I saw the one at the battery shop. I assume they put some
    calibrated load on the battery and measure both voltage and current, and
    make some estimate on battery life. The one at my garage has a printer,
    I got the paper slip somewhere.


    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Don Y on Sat May 10 03:19:41 2025
    On 2025-05-09 23:32, Don Y wrote:
    On 5/9/2025 5:07 AM, Carlos E.R. wrote:
    There are places where copper products (wire, plumbing) are stolen
    for their "recycle value".  The solution, so far, has been to
    require recyclers to get and record identification of people
    bringing in such items.

    Not enough, apparently.

    The hut they vandalized has a notice board that says all the cables
    are aluminum.

    I wonder if the would-be thieves even bother to READ...

    I think there have been cases of people trying to steal the wiring in
    outside lighting systems -- and not taking adequate provisions to
    protect against electrocution!

    Yeah, here too. They even tried to rip the railway catenary at some
    place. Some of those died on the spot.

    How much "protection" do you think a SIGN would provide?  "Hey, Bob,
    don't these got electricity in them?"

    That was a different theft, eh? Different thieves, city, all. :-)


    I would like to make some backlit copper lighted displays for the house
    (AZ is The Copper State) but am afraid its oxidized color would attract
    some thief eager to make a few dollars off it.

    Sigh.

    Some places have copper roofs.

    Yes.  We had looked into it (because it is far more durable than
    virtually any other roofing material in common use, here (including
    tile).  But, you need a minimum pitch to ensure the water doesn't
    pool on the roof.

    Yes, of course. Around here we have many flat roofed houses. Many of
    those use aluminum foil with asphalt. If well done, it could hold a pool.


    25€. A 9Ah item, high discharge rate.

    Different grades exist, here.  If you buy from an electronics supplier
    (e.g., Digikey), you will likely get a "fairer" price (value for money)
    than a local battery store (which may be 50% higher).  UPS manufacturers >>> typically charge about double what a reasonable price might be (though
    the usually assemble the batteries into the requisite "packs"...
    a trivial exercise for even 48V units).

    Let me check. The computer place here offers:

    Phasak PHB 1209 Batería SAI/UPS 9Ah 12V        29,17€

    Salicru UBT 12/9 Batería para SAI/UPS 9aH 12v    18,98€ (was 20,63€) >>
    So the brand name battery replacement for my UPS is actually cheaper
    than what I paid. Surprise!

    The nominal 12V 7.2AHr batteries (also available at 9AHr in the same
    case size) that many of my UPSs use are ~20-30, here, neglecting
    shipping and tax.  Putting two (for smaller UPSs) or 4 in each UPS
    gets pricey -- if you have to do it every 3 years (and have a dozen
    UPSs)!

    Indeed!


    I've tried a new configuration where I am hanging many of the
    UPSs off a couple of larger units.  The thinking being that I
    only have to maintain the larger units' batteries (and still
    get the benefits of a UPS per workstation).

    Maybe just a big unit, and wiring around the place. Red coloured
    sockets. Lilke in computer centres.



    Digikey used to have a policy of free shipping for prepaid (cash)
    orders.  I would buy batteries in lots of 10 and send prepayment.
    Shipping charges can be a significant fraction of a battery's
    cost.  They now exclude batteries from this policy (when I last
    checked).

    Right, they are very heavy. Yep, the place above charges 5.25€ for
    shipping.

    As I said, I try to rescue them (often I come across NiB UPSs
    that some moron in IT ordered but opted not to install.
    As the recycle value of batteries is just weight (regardless of
    ability to hold a charge), I swap my dead batteries for such
    new batteries and everyone is happy!

    :-D

    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to All on Fri May 9 19:37:15 2025
    Yes, of course. Around here we have many flat roofed houses. Many of those use
    aluminum foil with asphalt. If well done, it could hold a pool.

    Sadly, organic debris accumulates on them. Then, water gets trapped
    in the debris -- and slowly rots the roof in that location. Drainage
    being important and hard to accomplish with low pitch.

    I've tried a new configuration where I am hanging many of the
    UPSs off a couple of larger units.  The thinking being that I
    only have to maintain the larger units' batteries (and still
    get the benefits of a UPS per workstation).

    Maybe just a big unit, and wiring around the place. Red coloured sockets. Lilke
    in computer centres.

    Wiring *in* the structure would necessitate an inspection.
    But, plugging three UPSs (with long power cords) into a
    single UPS is acceptable. Then, the single UPS can
    serve those three loads or any combination.

    ONE set of batteries to replace (let the other three "slaves"
    complain that they are missing batteries... who cares?!)

    Digikey used to have a policy of free shipping for prepaid (cash)
    orders.  I would buy batteries in lots of 10 and send prepayment.
    Shipping charges can be a significant fraction of a battery's
    cost.  They now exclude batteries from this policy (when I last
    checked).

    Right, they are very heavy. Yep, the place above charges 5.25€ for shipping.

    As I said, I try to rescue them (often I come across NiB UPSs
    that some moron in IT ordered but opted not to install.
    As the recycle value of batteries is just weight (regardless of
    ability to hold a charge), I swap my dead batteries for such
    new batteries and everyone is happy!

    :-D

    An SLA battery is worth about 22c/pound for its lead content.
    So, *taking* viable batteries is effectively theft (though on
    a very small scale). Replacing them with an equivalent
    weight of recyclable lead leave no grounds for objection:
    "How better to RECYCLE this *good* battery than to return it
    to service?!"

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to Carlos E.R. on Fri May 9 20:52:13 2025
    On 5/9/2025 6:26 PM, Carlos E.R. wrote:
    On 2025-05-09 23:41, Don Y wrote:
    On 5/9/2025 5:18 AM, Carlos E.R. wrote:

    ...

    When looking at specs for a replacement UPS, possibly an Eaton, I saw they >>> mentioned emitting a beep when battery is bad.

    They likely don't load test, then.  Perhaps just watch the open
    circuit voltage on the "charged" battery.

    It is distressing how little the technology associated with
    battery monitoring and charging has advanced in these sorts
    of applications.  Again, likely because there is little
    incentive to maximize battery life!

    At my garage they have some gadgetry that I have not seen to test batteries. I
    saw the one at the battery shop. I assume they put some calibrated load on the
    battery and measure both voltage and current, and make some estimate on battery
    life. The one at my garage has a printer, I got the paper slip somewhere.

    Yes. "Load testing". The goal being to determine the maximum
    "cold cranking amps" that it can deliver to the starter at
    a specific load voltage. There's some magic involved as the
    CCA specification pertains to operation at 0C (or 0F? I don't
    recall) and chances are, you're not going to be testing at that
    temperature.

    Cold temperatures impede the efficiency of the battery and, at the
    same time, make the mechanical load appear larger. I think they
    combine to represent about a 4X performance hit.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Joe Gwinn@21:1/5 to robin_listas@es.invalid on Sat May 10 08:03:57 2025
    On Fri, 9 May 2025 23:28:29 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-09 18:22, Joe Gwinn wrote:
    On Fri, 9 May 2025 14:18:53 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-08 23:57, Don Y wrote:
    That is a feature of UPS design that specsmanship to get the longest >>>>>> run time for the sales datasheet means that they cook their
    batteries. I have seen them swell to the point of bursting inside a >>>>>> UPS. Thick rubber gloves needed to remove the remains. Support
    metalwork was a real corroded rusty mess but electronics above it
    remained OK.

    That level of "not working" has not happened to me. Maybe because some >>>>> power failure makes me find out that the battery is dead.

    I've rescued a fair number of UPSs over the years.á In probably 80% of >>>> them, the batteries have swollen to the point where removing the battery >>>> or battery PACK is difficult.á This is especially true of the "better" >>>> UPSs (sine output, 48V battery, metal fabrication) where there is
    little "give" in the mechanical design.á Often one has to disassemble
    the UPS to see where one can gain leverage on the battery pack
    to force it from the case.

    They really think I'm going to buy their vastly overpriced replacements? >>>>>
    I don't.

    But last battery I replaced was not even two years old, rather 5
    months short. I replaced it just in time to serve during the Gran Apag≤n. >>>>
    That's the problem; you don't KNOW how long a particular battery will last,
    even in an environment where it is never called on for backup!

    Instead, you are forced into a "reactive" mode -- waiting for something >>>> to tell you you're screwed and need a replacement, now!

    My largest UPS uses 50 pound batteries (8 of them).

    Are they 12 volts each, or just one cell?

    On phone exchanges I saw huge batteries, actually individual cells
    connected in series. 48 volts nominally, so 24 cells. I don't think they >>> were gel types, they needed adding water now and then.

    The were most likely KS-20472 BELLCELL lead-acid battery cells,
    originally made by Western Electric, or European equivalent. These
    are 2.2 volts per cell.

    .<https://library.industrialsolutions.abb.com/publibrary/checkout/107852477?TNR=Installation%20and%20Instruction%7C107852477%7CPDF>

    Those I saw were prismatic, not cylindrical.

    OK. Later production is rectangular, largely to improve packing
    density in the battery room.

    The key was the nested alternating conical battery plates that allowed
    the plates to grow and shrink without shorting.

    Joe

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Don Y on Sat May 10 16:04:28 2025
    On 2025-05-10 04:37, Don Y wrote:
    Yes, of course. Around here we have many flat roofed houses. Many of
    those use aluminum foil with asphalt. If well done, it could hold a pool.

    Sadly, organic debris accumulates on them.  Then, water gets trapped
    in the debris -- and slowly rots the roof in that location.  Drainage
    being important and hard to accomplish with low pitch.

    The intense sun dries it up soon :-)


    I've tried a new configuration where I am hanging many of the
    UPSs off a couple of larger units.  The thinking being that I
    only have to maintain the larger units' batteries (and still
    get the benefits of a UPS per workstation).

    Maybe just a big unit, and wiring around the place. Red coloured
    sockets. Lilke in computer centres.

    Wiring *in* the structure would necessitate an inspection.
    But, plugging three UPSs (with long power cords) into a
    single UPS is acceptable.  Then, the single UPS can
    serve those three loads or any combination.

    Ah.


    ONE set of batteries to replace (let the other three "slaves"
    complain that they are missing batteries... who cares?!)

    Why not remove those three UPS, and connect the loads direct to the main
    UPS? :-?


    Digikey used to have a policy of free shipping for prepaid (cash)
    orders.  I would buy batteries in lots of 10 and send prepayment.
    Shipping charges can be a significant fraction of a battery's
    cost.  They now exclude batteries from this policy (when I last
    checked).

    Right, they are very heavy. Yep, the place above charges 5.25€ for
    shipping.

    As I said, I try to rescue them (often I come across NiB UPSs
    that some moron in IT ordered but opted not to install.
    As the recycle value of batteries is just weight (regardless of
    ability to hold a charge), I swap my dead batteries for such
    new batteries and everyone is happy!

    :-D

    An SLA battery is worth about 22c/pound for its lead content.
    So, *taking* viable batteries is effectively theft (though on
    a very small scale).  Replacing them with an equivalent
    weight of recyclable lead leave no grounds for objection:
    "How better to RECYCLE this *good* battery than to return it
    to service?!"

    Indeed :-)

    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Joe Gwinn on Sat May 10 16:05:35 2025
    On 2025-05-10 14:03, Joe Gwinn wrote:
    On Fri, 9 May 2025 23:28:29 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-09 18:22, Joe Gwinn wrote:
    On Fri, 9 May 2025 14:18:53 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-08 23:57, Don Y wrote:
    That is a feature of UPS design that specsmanship to get the longest >>>>>>> run time for the sales datasheet means that they cook their
    batteries. I have seen them swell to the point of bursting inside a >>>>>>> UPS. Thick rubber gloves needed to remove the remains. Support
    metalwork was a real corroded rusty mess but electronics above it >>>>>>> remained OK.

    That level of "not working" has not happened to me. Maybe because some >>>>>> power failure makes me find out that the battery is dead.

    I've rescued a fair number of UPSs over the years.  In probably 80% of >>>>> them, the batteries have swollen to the point where removing the battery >>>>> or battery PACK is difficult.  This is especially true of the "better" >>>>> UPSs (sine output, 48V battery, metal fabrication) where there is
    little "give" in the mechanical design.  Often one has to disassemble >>>>> the UPS to see where one can gain leverage on the battery pack
    to force it from the case.

    They really think I'm going to buy their vastly overpriced replacements?

    I don't.

    But last battery I replaced was not even two years old, rather 5
    months short. I replaced it just in time to serve during the Gran Apagón.

    That's the problem; you don't KNOW how long a particular battery will last,
    even in an environment where it is never called on for backup!

    Instead, you are forced into a "reactive" mode -- waiting for something >>>>> to tell you you're screwed and need a replacement, now!

    My largest UPS uses 50 pound batteries (8 of them).

    Are they 12 volts each, or just one cell?

    On phone exchanges I saw huge batteries, actually individual cells
    connected in series. 48 volts nominally, so 24 cells. I don't think they >>>> were gel types, they needed adding water now and then.

    The were most likely KS-20472 BELLCELL lead-acid battery cells,
    originally made by Western Electric, or European equivalent. These
    are 2.2 volts per cell.

    .<https://library.industrialsolutions.abb.com/publibrary/checkout/107852477?TNR=Installation%20and%20Instruction%7C107852477%7CPDF>

    Those I saw were prismatic, not cylindrical.

    OK. Later production is rectangular, largely to improve packing
    density in the battery room.

    The key was the nested alternating conical battery plates that allowed
    the plates to grow and shrink without shorting.

    I see. That, I do not remember.



    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to Carlos E.R. on Sat May 10 09:13:57 2025
    On 5/10/2025 7:04 AM, Carlos E.R. wrote:
    On 2025-05-10 04:37, Don Y wrote:
    Yes, of course. Around here we have many flat roofed houses. Many of those >>> use aluminum foil with asphalt. If well done, it could hold a pool.

    Sadly, organic debris accumulates on them.  Then, water gets trapped
    in the debris -- and slowly rots the roof in that location.  Drainage
    being important and hard to accomplish with low pitch.

    The intense sun dries it up soon :-)

    Not with pine needles in a corner of the roof shaded by said tree!

    ONE set of batteries to replace (let the other three "slaves"
    complain that they are missing batteries... who cares?!)

    Why not remove those three UPS, and connect the loads direct to the main UPS?  :-?

    Because the power cords of the UPSs are longer than the power cords of
    each of the workstations AND THEIR ASSOCIATED PERIPHERALS.

    Additionally, the UPS lets me monitor the power consumed by the
    attached loads so I can figure out how much I can tax the
    upstream UPS (when using multiple workstations)

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Joe Gwinn@21:1/5 to robin_listas@es.invalid on Sat May 10 14:47:52 2025
    On Sat, 10 May 2025 16:05:35 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-10 14:03, Joe Gwinn wrote:
    On Fri, 9 May 2025 23:28:29 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-09 18:22, Joe Gwinn wrote:
    On Fri, 9 May 2025 14:18:53 +0200, "Carlos E.R."
    <robin_listas@es.invalid> wrote:

    On 2025-05-08 23:57, Don Y wrote:
    That is a feature of UPS design that specsmanship to get the longest >>>>>>>> run time for the sales datasheet means that they cook their
    batteries. I have seen them swell to the point of bursting inside a >>>>>>>> UPS. Thick rubber gloves needed to remove the remains. Support >>>>>>>> metalwork was a real corroded rusty mess but electronics above it >>>>>>>> remained OK.

    That level of "not working" has not happened to me. Maybe because some >>>>>>> power failure makes me find out that the battery is dead.

    I've rescued a fair number of UPSs over the years.á In probably 80% of >>>>>> them, the batteries have swollen to the point where removing the battery >>>>>> or battery PACK is difficult.á This is especially true of the "better" >>>>>> UPSs (sine output, 48V battery, metal fabrication) where there is
    little "give" in the mechanical design.á Often one has to disassemble >>>>>> the UPS to see where one can gain leverage on the battery pack
    to force it from the case.

    They really think I'm going to buy their vastly overpriced replacements?

    I don't.

    But last battery I replaced was not even two years old, rather 5 >>>>>>> months short. I replaced it just in time to serve during the Gran Apag≤n.

    That's the problem; you don't KNOW how long a particular battery will last,
    even in an environment where it is never called on for backup!

    Instead, you are forced into a "reactive" mode -- waiting for something >>>>>> to tell you you're screwed and need a replacement, now!

    My largest UPS uses 50 pound batteries (8 of them).

    Are they 12 volts each, or just one cell?

    On phone exchanges I saw huge batteries, actually individual cells
    connected in series. 48 volts nominally, so 24 cells. I don't think they >>>>> were gel types, they needed adding water now and then.

    The were most likely KS-20472 BELLCELL lead-acid battery cells,
    originally made by Western Electric, or European equivalent. These
    are 2.2 volts per cell.

    .<https://library.industrialsolutions.abb.com/publibrary/checkout/107852477?TNR=Installation%20and%20Instruction%7C107852477%7CPDF>

    Those I saw were prismatic, not cylindrical.

    OK. Later production is rectangular, largely to improve packing
    density in the battery room.

    The key was the nested alternating conical battery plates that allowed
    the plates to grow and shrink without shorting.

    I see. That, I do not remember.

    There was a set of articles in the Bell System Technical Journal on
    the evolution and design of those batteries, which were a considerable
    advance in their day. If we can find the issue number, these articles
    are free.

    Joe

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Don Y on Sun May 11 15:04:45 2025
    On 2025-05-10 18:13, Don Y wrote:
    On 5/10/2025 7:04 AM, Carlos E.R. wrote:
    On 2025-05-10 04:37, Don Y wrote:
    Yes, of course. Around here we have many flat roofed houses. Many of
    those use aluminum foil with asphalt. If well done, it could hold a
    pool.

    Sadly, organic debris accumulates on them.  Then, water gets trapped
    in the debris -- and slowly rots the roof in that location.  Drainage
    being important and hard to accomplish with low pitch.

    The intense sun dries it up soon :-)

    Not with pine needles in a corner of the roof shaded by said tree!

    Ok...


    ONE set of batteries to replace (let the other three "slaves"
    complain that they are missing batteries... who cares?!)

    Why not remove those three UPS, and connect the loads direct to the
    main UPS?  :-?

    Because the power cords of the UPSs are longer than the power cords of
    each of the workstations AND THEIR ASSOCIATED PERIPHERALS.

    I'd just use a cable extender.


    Additionally, the UPS lets me monitor the power consumed by the
    attached loads so I can figure out how much I can tax the
    upstream UPS (when using multiple workstations)

    Ok, that's a powerful reason :-)


    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Don Y on Sun May 11 15:21:13 2025
    On 2025-05-10 05:52, Don Y wrote:
    On 5/9/2025 6:26 PM, Carlos E.R. wrote:
    On 2025-05-09 23:41, Don Y wrote:
    On 5/9/2025 5:18 AM, Carlos E.R. wrote:

    ...

    When looking at specs for a replacement UPS, possibly an Eaton, I
    saw they mentioned emitting a beep when battery is bad.

    They likely don't load test, then.  Perhaps just watch the open
    circuit voltage on the "charged" battery.

    It is distressing how little the technology associated with
    battery monitoring and charging has advanced in these sorts
    of applications.  Again, likely because there is little
    incentive to maximize battery life!

    At my garage they have some gadgetry that I have not seen to test
    batteries. I saw the one at the battery shop. I assume they put some
    calibrated load on the battery and measure both voltage and current,
    and make some estimate on battery life. The one at my garage has a
    printer, I got the paper slip somewhere.

    Yes.  "Load testing".  The goal being to determine the maximum
    "cold cranking amps" that it can deliver to the starter at
    a specific load voltage.  There's some magic involved as the
    CCA specification pertains to operation at 0C (or 0F?  I don't
    recall) and chances are, you're not going to be testing at that
    temperature.

    Cold temperatures impede the efficiency of the battery and, at the
    same time, make the mechanical load appear larger.  I think they
    combine to represent about a 4X performance hit.


    The paper slip says they tested 12.4 volts and 279A.


    I copy the text of the slip,

    ???813 (part of the paper ripped out by the stapler)
    FGA
    V1.00 EU

    ....

    PRUEBA BATERíA
    CORRECTA-CARGUE

    VOLTAJE 12.40V
    MEDIDO 279 A(EN)

    CODIGO PRUEBA (test code)
    XXXXXXXXX

    CLASF 360 A(EN)
    TEMPERATURA 20°C (temp)

    UBICACIÓN BAT. EN EL VEHICULO (battery is on the vehicle) UBIC PRUEBA BORNE ARRIBA (terminal up ?)
    TIPO DE BAT. NORMAL/AUTO

    Then there are two graphs. One is health, which shows about 75%, and another is "EDC", which marks 75%.


    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to Carlos E.R. on Sun May 11 06:46:52 2025
    On 5/11/2025 6:04 AM, Carlos E.R. wrote:
    On 2025-05-10 18:13, Don Y wrote:
    On 5/10/2025 7:04 AM, Carlos E.R. wrote:
    On 2025-05-10 04:37, Don Y wrote:
    Yes, of course. Around here we have many flat roofed houses. Many of those
    use aluminum foil with asphalt. If well done, it could hold a pool.

    Sadly, organic debris accumulates on them.  Then, water gets trapped
    in the debris -- and slowly rots the roof in that location.  Drainage >>>> being important and hard to accomplish with low pitch.

    The intense sun dries it up soon :-)

    Not with pine needles in a corner of the roof shaded by said tree!

    Ok...

    Most frontier style roofs, here, have a wall that surrounds the
    roof (three sides) above the roof level. So, there is always a
    dead spot where debris accumulates (you can see it swirl in these
    little pockets as the wind blows).

    And, depending on the season, the sun may be lower in the sky
    thus creating a permanent shadow near that wall.

    We have one "bad spot" where I regularly "harvest" 20-30 cubic
    feet of pine needles, several times each year. I use a "snow
    shovel" to lift them up over that wall and down onto the ground,
    below, where I can later rake them up and discard them.

    Pine needles acidify the "solution" formed when wet.

    ONE set of batteries to replace (let the other three "slaves"
    complain that they are missing batteries... who cares?!)

    Why not remove those three UPS, and connect the loads direct to the main >>> UPS?  :-?

    Because the power cords of the UPSs are longer than the power cords of
    each of the workstations AND THEIR ASSOCIATED PERIPHERALS.

    I'd just use a cable extender.

    You need to have multiple receptacles on the load end as there
    are multiple loads to be plugged to each UPS. I.e., use an
    outlet strip. Hey! A UPS can act as an outlet strip! :>

    The UPS per workstation was a handy approach as it let me power down
    (or up) everything that the workstation would typically need,
    beyond just the "CPU". E.g., scanners, digitizing tablets,
    external drives, etc.

    Additionally, the UPS lets me monitor the power consumed by the
    attached loads so I can figure out how much I can tax the
    upstream UPS (when using multiple workstations)

    Ok, that's a powerful reason :-)

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Carlos E.R.@21:1/5 to Don Y on Sun May 11 21:25:30 2025
    On 2025-05-11 15:46, Don Y wrote:
    On 5/11/2025 6:04 AM, Carlos E.R. wrote:
    On 2025-05-10 18:13, Don Y wrote:
    On 5/10/2025 7:04 AM, Carlos E.R. wrote:
    On 2025-05-10 04:37, Don Y wrote:
    Yes, of course. Around here we have many flat roofed houses. Many
    of those use aluminum foil with asphalt. If well done, it could
    hold a pool.

    Sadly, organic debris accumulates on them.  Then, water gets trapped >>>>> in the debris -- and slowly rots the roof in that location.  Drainage >>>>> being important and hard to accomplish with low pitch.

    The intense sun dries it up soon :-)

    Not with pine needles in a corner of the roof shaded by said tree!

    Ok...

    Most frontier style roofs, here, have a wall that surrounds the
    roof (three sides) above the roof level.  So, there is always a
    dead spot where debris accumulates (you can see it swirl in these
    little pockets as the wind blows).

    And, depending on the season, the sun may be lower in the sky
    thus creating a permanent shadow near that wall.

    We have one "bad spot" where I regularly "harvest" 20-30 cubic
    feet of pine needles, several times each year.  I use a "snow
    shovel" to lift them up over that wall and down onto the ground,
    below, where I can later rake them up and discard them.

    Pine needles acidify the "solution" formed when wet.

    I had a place near the beach with such a flat roof. No pines over there.


    ONE set of batteries to replace (let the other three "slaves"
    complain that they are missing batteries... who cares?!)

    Why not remove those three UPS, and connect the loads direct to the
    main UPS?  :-?

    Because the power cords of the UPSs are longer than the power cords of
    each of the workstations AND THEIR ASSOCIATED PERIPHERALS.

    I'd just use a cable extender.

    You need to have multiple receptacles on the load end as there
    are multiple loads to be plugged to each UPS.  I.e., use an
    outlet strip.  Hey! A UPS can act as an outlet strip!  :>

    The UPS per workstation was a handy approach as it let me power down
    (or up) everything that the workstation would typically need,
    beyond just the "CPU".  E.g., scanners, digitizing tablets,
    external drives, etc.

    Sure, yes. My extenders have multiple receptacles, typically 3, and 5
    metres. There are many choices in the supermarket or in Amazon. Many
    have a switch. Some of them have surge protection and filtering.


    Additionally, the UPS lets me monitor the power consumed by the
    attached loads so I can figure out how much I can tax the
    upstream UPS (when using multiple workstations)

    Ok, that's a powerful reason :-)



    --
    Cheers, Carlos.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Don Y@21:1/5 to Carlos E.R. on Mon May 12 11:07:17 2025
    On 5/11/2025 12:25 PM, Carlos E.R. wrote:
    Not with pine needles in a corner of the roof shaded by said tree!

    Ok...

    Most frontier style roofs, here, have a wall that surrounds the
    roof (three sides) above the roof level.  So, there is always a
    dead spot where debris accumulates (you can see it swirl in these
    little pockets as the wind blows).

    And, depending on the season, the sun may be lower in the sky
    thus creating a permanent shadow near that wall.

    We have one "bad spot" where I regularly "harvest" 20-30 cubic
    feet of pine needles, several times each year.  I use a "snow
    shovel" to lift them up over that wall and down onto the ground,
    below, where I can later rake them up and discard them.

    Pine needles acidify the "solution" formed when wet.

    I had a place near the beach with such a flat roof. No pines over there.

    Pines are some of the few "tall trees" that we have, here -- easily
    growing to 50 ft. Their needles shed continuously (not at a single
    season like deciduous trees).

    A neighbor with three such trees recently felled theirs. This appears
    to have dramatically reduced the accumulation on the roof (despite
    a 25 ft pine being located nearby).

    I suspect the number of such tall pines falling in local microbursts
    may have played a part in their decision to remove the trees. Previously,
    they had claimed any of the trees falling on our property would be treated
    as "act of god" in terms of insurance coverage. I suspect they eventually realized said trees falling onto THEIR property would similarly be treated!

    oops!

    Because the power cords of the UPSs are longer than the power cords of >>>> each of the workstations AND THEIR ASSOCIATED PERIPHERALS.

    I'd just use a cable extender.

    You need to have multiple receptacles on the load end as there
    are multiple loads to be plugged to each UPS.  I.e., use an
    outlet strip.  Hey! A UPS can act as an outlet strip!  :>

    The UPS per workstation was a handy approach as it let me power down
    (or up) everything that the workstation would typically need,
    beyond just the "CPU".  E.g., scanners, digitizing tablets,
    external drives, etc.

    Sure, yes. My extenders have multiple receptacles, typically 3, and 5 metres. There are many choices in the supermarket or in Amazon. Many have a switch. Some of them have surge protection and filtering.

    My "outlet strips" support 6 receptacles, fused and with switch/indicator.
    But, these need to be secured to <something> to avoid flailing around
    as connected loads are moved, rearranged, etc.

    The UPSs fit nicely atop each associated tower. Even without the mass of
    their internal batteries (removed in favor of the upstream UPS), the
    UPS sits in place -- presenting its display (and controls) to the
    front where they are easily accessed. The USB port lets the workstation
    talk to the UPS while the NIC lets the network talk to it.

    And, they are essentially free (my outlet strips were $30/each). Their value lies in the lead content of their batteries which, if depleted, have no value to *me* (so can be left behind).