We have an interesting power supply problem at the moment, which
Northern Powergrid are trying to fix. Power to our village is present
(for everyone, AFAIK) but the voltage has dropped to 95 V (barely enough
to turn on the LCD display on my power-monitoring plug!). NP say it is
due to a circuit breaker having tripped just one of the three phases in
the supply to our village.
Is it plausible that this could cause low voltage for everyone, as
opposed to full voltage for those houses that are on good phases and
total power loss for people on the phase that has tripped?
We have an interesting power supply problem at the moment, which
Northern Powergrid are trying to fix. Power to our village is present
(for everyone, AFAIK) but the voltage has dropped to 95 V (barely enough
to turn on the LCD display on my power-monitoring plug!). NP say it is
due to a circuit breaker having tripped just one of the three phases in
the supply to our village.
Is it plausible that this could cause low voltage for everyone, as
opposed to full voltage for those houses that are on good phases and
total power loss for people on the phase that has tripped?
We have an interesting power supply problem at the moment, which
Northern Powergrid are trying to fix. Power to our village is present
(for everyone, AFAIK) but the voltage has dropped to 95 V (barely enough
to turn on the LCD display on my power-monitoring plug!). NP say it is
due to a circuit breaker having tripped just one of the three phases in
the supply to our village.
Is it plausible that this could cause low voltage for everyone, as
opposed to full voltage for those houses that are on good phases and
total power loss for people on the phase that has tripped?
On 2025-10-14 10:33, NY wrote:
We have an interesting power supply problem at the moment, which
Northern Powergrid are trying to fix. Power to our village is present
(for everyone, AFAIK) but the voltage has dropped to 95 V (barely
enough to turn on the LCD display on my power-monitoring plug!). NP
say it is due to a circuit breaker having tripped just one of the
three phases in the supply to our village.
Is it plausible that this could cause low voltage for everyone, as
opposed to full voltage for those houses that are on good phases and
total power loss for people on the phase that has tripped?
Assuming that your local neutral and earth are still at roughly earth potential, perhaps before your local transformer the imbalance between phases somewhere in the higher-voltage supply has raised a neutral and
your supply transformer is working between that and one of the active phases?
nib
On 14/10/2025 10:33, NY wrote:
We have an interesting power supply problem at the moment, which Northern >> Powergrid are trying to fix. Power to our village is present (for
everyone, AFAIK) but the voltage has dropped to 95 V (barely enough to
turn on the LCD display on my power-monitoring plug!). NP say it is due
to a circuit breaker having tripped just one of the three phases in the
supply to our village.
Is it plausible that this could cause low voltage for everyone, as
opposed to full voltage for those houses that are on good phases and
total power loss for people on the phase that has tripped?
I think so, though I cant quite visualise exactly how right now (coffee infusion hasn't quite levelled out)
A three phase transformer takes all phases and magnetically couples them
not only to the output phases as you might expect, but also to each other.
"A 3-phase transformer or 3-a transformer can be constructed either by connecting together three single-phase transformers, thereby forming a so-called three phase transformer bank, *or by using one pre-assembled and balanced three phase transformer*which consists of three pairs of single phase windings mounted onto *one single laminated core.*
The advantages of building a single three phase transformer is that for
the same kVA rating it will be smaller, cheaper and lighter than three individual single phase transformers connected together. This is because
the copper and iron core are used more effectively."
https://www.electronics-tutorials.ws/transformer/three-phase-transformer.html
Now the analysis of what happens to such a beast when you lose a single input phase is beyond me at this stage in the morning, but it certainly includes the possibility of weird shit on *all* the output phases.
On 14/10/2025 10:33, NY wrote:
We have an interesting power supply problem at the moment, which
Northern Powergrid are trying to fix. Power to our village is present
(for everyone, AFAIK) but the voltage has dropped to 95 V (barely
enough to turn on the LCD display on my power-monitoring plug!). NP
say it is due to a circuit breaker having tripped just one of the
three phases in the supply to our village.
Is it plausible that this could cause low voltage for everyone, as
opposed to full voltage for those houses that are on good phases and
total power loss for people on the phase that has tripped?
Happens quite regularly here.-a I've heard it blamed on incinerated squirrels and - improbably - on a metallised balloon, tripping an 11kV breaker.-a My phase well below spec - the other two phases high - but
just in spec.
On the last brown-out I got the engineers to switch my house to one of
the other phases.-a No brown-out in the two years since.
Still plenty of brief cuts.-a A pretty pathetic service.
We definitely got "weird shit". My desktop PC switched off as if there
had been a power cut but my LED desk lamp was still on, as were the
router and the various mesh network nodes around the house.
We have an interesting power supply problem at the moment, which
Northern Powergrid are trying to fix. Power to our village is present
(for everyone, AFAIK) but the voltage has dropped to 95 V (barely enough
to turn on the LCD display on my power-monitoring plug!). NP say it is
due to a circuit breaker having tripped just one of the three phases in
the supply to our village.
Is it plausible that this could cause low voltage for everyone, as
opposed to full voltage for those houses that are on good phases and
total power loss for people on the phase that has tripped?
NY wrote:
We definitely got "weird shit". My desktop PC switched off as if there
had been a power cut but my LED desk lamp was still on, as were the
router and the various mesh network nodes around the house.
Have had similar here (though I don't know whether it was a lost phase,
or lost neutral) anything "electronic" just carried on, the fridge was distinctly unhappy.
"The Natural Philosopher" <tnp@invalid.invalid> wrote in message news:10cl6j1$2q6c4$13@dont-email.me...
On 14/10/2025 10:33, NY wrote:
We have an interesting power supply problem at the moment, which
Northern Powergrid are trying to fix. Power to our village is present
(for everyone, AFAIK) but the voltage has dropped to 95 V (barely
enough to turn on the LCD display on my power-monitoring plug!). NP
say it is due to a circuit breaker having tripped just one of the
three phases in the supply to our village.
Is it plausible that this could cause low voltage for everyone, as
opposed to full voltage for those houses that are on good phases and
total power loss for people on the phase that has tripped?
I think so, though I cant quite visualise exactly how right now
(coffee infusion hasn't quite levelled out)
A three phase transformer takes all phases and magnetically couples
them not only to the output phases as you might expect, but also to
each other.
"Also to each other" - that's the crucial thing!
"A 3-phase transformer or 3-a transformer can be constructed either by
connecting together three single-phase transformers, thereby forming a
so-called three phase transformer bank, *or by using one pre-assembled
and balanced three phase transformer*which consists of three pairs of
single phase windings mounted onto *one single laminated core.*
The advantages of building a single three phase transformer is that
for the same kVA rating it will be smaller, cheaper and lighter than
three individual single phase transformers connected together. This is
because the copper and iron core are used more effectively."
https://www.electronics-tutorials.ws/transformer/three-phase-transformer.html
Now the analysis of what happens to such a beast when you lose a
single input phase is beyond me at this stage in the morning, but it
certainly includes the possibility of weird shit on *all* the output
phases.
We definitely got "weird shit". My desktop PC switched off as if there
had been a power cut but my LED desk lamp was still on, as were the
router and the various mesh network nodes around the house.
her home office in the bedroom, was not aware of any problem. I checked
the "fuse box" for a tripped ring main - fine! The fridge and freezer
were "on" (display of temperature but no motors... but then the
thermostat may not have switched them on. Then I noticed that a mains power-monitoring plug was displaying a very faint "95.6 V". The miracle
is that so many electronic devices were getting their full power - switched-mode power supplies are wonderful beasts! I know a lot are
rated for input voltages from about 80V up to 260 V, and either 50 or 60
Hz, so they can be used anywhere in the world - just with a greater duty cycle if the mains voltage is lower.
Reminds me of the switched-mode PSU project that we all did at
university 40-odd years ago. Our PSU had to deliver 12 V at 5 A, with
input voltage ranging from 50 V AC to 300 V AC, and drawing up to the
full 5 A even with 50 V going in - almost 100% duty cycle! Our team won
the prize for regulation range and efficiency - because a genius on our
team worked out that rather than using resistors to perform potential divider somewhere, we could use capacitors which would be lossless - as
long as the frequency remained around 50 Hz. I still have the book
somewhere which everyone in our team won.
I would probably have known how to calculate the effect of losing one
phase of a 3-phase transformer - but it was 45 years ago and the "use it
or lose it" principle means I've forgotten.
power came back a little while ago so all computers, router, mesh nodes
etc - and washing machine! - are now working.
On Tue, 14 Oct 2025 10:33:52 +0100, NY wrote:
We have an interesting power supply problem at the moment, which
Northern Powergrid are trying to fix. Power to our village is present
(for everyone, AFAIK) but the voltage has dropped to 95 V (barely enough
to turn on the LCD display on my power-monitoring plug!). NP say it is
due to a circuit breaker having tripped just one of the three phases in
the supply to our village.
Is it plausible that this could cause low voltage for everyone, as
opposed to full voltage for those houses that are on good phases and
total power loss for people on the phase that has tripped?
Indeed. Your 230v supply is the difference between 2 phases of a 380v
3 phase feed. So only the users on the two good phases will get
full voltage.
On 2025-10-14 12:20, crn wrote:
On Tue, 14 Oct 2025 10:33:52 +0100, NY wrote:
We have an interesting power supply problem at the moment, which
Northern Powergrid are trying to fix. Power to our village is present
(for everyone, AFAIK) but the voltage has dropped to 95 V (barely enough >>> to turn on the LCD display on my power-monitoring plug!). NP say it is
due to a circuit breaker having tripped just one of the three phases in
the supply to our village.
Is it plausible that this could cause low voltage for everyone, as
opposed to full voltage for those houses that are on good phases and
total power loss for people on the phase that has tripped?
Indeed. Your 230v supply is the difference between 2 phases of a 380v
3 phase feed. So only the users on the two good phases will get
full voltage.
If you imagine a 3-phase transformer with the three output sides forming
the star-connected final distribution to premises, with each domestic property working from one phase to neutral...
and the input sides connected to a delta-connected incoming mains, and
just one of the incoming mains goes open circuit (say L3)...
then one of the output phases works as normal, giving 230V (the one with
the transformer input connected betweeen L1 and L2). The other two
output phases both see the outputs from transformers with inputs
connected in series between L1 and L2 (via the open-circuit L3), so you would expect them to see half volts.
So I would expect one phase to keep working at 230/240V and the other
two to see 115/120V.
nib
Too many words! Like this:
<https://drive.google.com/file/d/1VJCZ1jas8N7AbGCN2QwkqINinTX5quVq/view?usp=sharing>
nib
NY wrote:
We definitely got "weird shit". My desktop PC switched off as if there had been a power cut but my LED desk lamp was still on, as were the router and the various mesh network nodes around the house.
Have had similar here (though I don't know whether it was a lost phase, or lost neutral) anything "electronic" just carried on, the fridge was distinctly unhappy.
On 14/10/2025 09:56, Peter Able wrote:
On 14/10/2025 10:33, NY wrote:Round here it tends to be falling branches. The 11kV is too widely
We have an interesting power supply problem at the moment, which
Northern Powergrid are trying to fix. Power to our village is present
(for everyone, AFAIK) but the voltage has dropped to 95 V (barely
enough to turn on the LCD display on my power-monitoring plug!). NP
say it is due to a circuit breaker having tripped just one of the
three phases in the supply to our village.
Is it plausible that this could cause low voltage for everyone, as
opposed to full voltage for those houses that are on good phases and
total power loss for people on the phase that has tripped?
Happens quite regularly here.-a I've heard it blamed on incinerated
squirrels and - improbably - on a metallised balloon, tripping an 11kV
breaker.-a My phase well below spec - the other two phases high - but
just in spec.
spaced for a squirrel to stretch...
That's no comfort to a user in an all-overhead area !On the last brown-out I got the engineers to switch my house to one ofWell back in the day it was a reasonable way cost-benefit to string up overhead 11kV lines. With pole mounted transformers, when electricity
the other phases.-a No brown-out in the two years since.
Still plenty of brief cuts.-a A pretty pathetic service.
was a luxury. not a necessity.
Then the trees grew. And the demands grew. And the dependency grew.
No one lays out overhead 11KV any more if they can help it.
It's all undergrounded at quite considerable cost.
But you save an enormous amount in maintenance. Tree pollarding hereis > now an annual preventative measure.
As are outages due to trees that are not on the annual schedule.
On 14/10/2025 10:33, NY wrote:
We have an interesting power supply problem at the moment, which
Northern Powergrid are trying to fix. Power to our village is present
(for everyone, AFAIK) but the voltage has dropped to 95 V (barely
enough to turn on the LCD display on my power-monitoring plug!). NP
say it is due to a circuit breaker having tripped just one of the
three phases in the supply to our village.
Is it plausible that this could cause low voltage for everyone, as
opposed to full voltage for those houses that are on good phases and
total power loss for people on the phase that has tripped?
Happens quite regularly here.-a I've heard it blamed on incinerated squirrels and - improbably - on a metallised balloon, tripping an 11kV breaker.-a My phase well below spec - the other two phases high - but
just in spec.
It's not *quite* like that.-a Upstream of the final three phase
transformer there IS no neutral. As such.
That final transformer - probably a grey or green box somewhere local,
will be a *single* iron core with six windings fed from three 11kV (sometimes 33kV)-a lines.
NY wrote:
We definitely got "weird shit". My desktop PC switched off as if there
had been a power cut but my LED desk lamp was still on, as were the
router and the various mesh network nodes around the house.
Have had similar here (though I don't know whether it was a lost phase,
or lost neutral) anything "electronic" just carried on, the fridge was distinctly unhappy.
Andy Burns <usenet@andyburns.uk> wrote in news:ml6o4nFkfevU1 @mid.individual.net:
NY wrote:
We definitely got "weird shit". My desktop PC switched off as if there
had been a power cut but my LED desk lamp was still on, as were the
router and the various mesh network nodes around the house.
Have had similar here (though I don't know whether it was a lost phase,
or lost neutral) anything "electronic" just carried on, the fridge was
distinctly unhappy.
Watch out for fridges & freezers on brown-outs, it can lead to a compressor stall & burnout. Common in India where power supply irregularities are more common is a little monitor box plugged in before fridges to cut the power
to them if it is badly out of spec. Possible that our modern appliances
will monitor the supply and do similar, I don't know.
On Tue, 10/14/2025 6:48 AM, Andy Burns wrote:
NY wrote:
We definitely got "weird shit". My desktop PC switched off as if there had been a power cut but my LED desk lamp was still on, as were the router and the various mesh network nodes around the house.
Have had similar here (though I don't know whether it was a lost phase, or lost neutral) anything "electronic" just carried on, the fridge was distinctly unhappy.
On a phase failure here, I switched off at the incomer until it was repaired.
I didn't even need to do repeated measurements with a meter, to determine the all clear.
Just watched a local traffic light, until the lighting on it was "normal again".
On the electrical system, the dining table serves up:
1) 0 volts. The one we all love and quite common.
2) A rise in voltage. Incandescent bulbs pop. Bad for motors (heat from excess voltage).
Bad for the audio power amp in your multimedia rack. Switch off at incomer and wait for service.
3) A fall in voltage. Electric motors lug and in some cases, don't start properly
and the motor can burn out. Switch off at incomer and wait for service.
On 14/10/2025 11:16, NY wrote:
"The Natural Philosopher" <tnp@invalid.invalid> wrote in message
news:10cl6j1$2q6c4$13@dont-email.me...
On 14/10/2025 10:33, NY wrote:
We have an interesting power supply problem at the moment, which
Northern Powergrid are trying to fix. Power to our village is
present (for everyone, AFAIK) but the voltage has dropped to 95 V
(barely enough to turn on the LCD display on my power-monitoring
plug!). NP say it is due to a circuit breaker having tripped just
one of the three phases in the supply to our village.
Is it plausible that this could cause low voltage for everyone, as
opposed to full voltage for those houses that are on good phases and
total power loss for people on the phase that has tripped?
I think so, though I cant quite visualise exactly how right now
(coffee infusion hasn't quite levelled out)
A three phase transformer takes all phases and magnetically couples
them not only to the output phases as you might expect, but also to
each other.
"Also to each other" - that's the crucial thing!
"A 3-phase transformer or 3-a transformer can be constructed either by
connecting together three single-phase transformers, thereby forming
a so-called three phase transformer bank, *or by using one pre-
assembled and balanced three phase transformer*which consists of
three pairs of single phase windings mounted onto *one single
laminated core.*
The advantages of building a single three phase transformer is that
for the same kVA rating it will be smaller, cheaper and lighter than
three individual single phase transformers connected together. This
is because the copper and iron core are used more effectively."
https://www.electronics-tutorials.ws/transformer/three-phase-
transformer.html
Now the analysis of what happens to such a beast when you lose a
single input phase is beyond me at this stage in the morning, but it
certainly includes the possibility of weird shit on *all* the output
phases.
We definitely got "weird shit". My desktop PC switched off as if there
had been a power cut but my LED desk lamp was still on, as were the
router and the various mesh network nodes around the house.
Many of today's switched mode power supplies are happy from 48vDC to
250vAC.
Yup.
Reminds me of the switched-mode PSU project that we all did atNice project!
university 40-odd years ago. Our PSU had to deliver 12 V at 5 A, with
input voltage ranging from 50 V AC to 300 V AC, and drawing up to the
full 5 A even with 50 V going in - almost 100% duty cycle! Our team
won the prize for regulation range and efficiency - because a genius
on our team worked out that rather than using resistors to perform
potential divider somewhere, we could use capacitors which would be
lossless - as long as the frequency remained around 50 Hz. I still
have the book somewhere which everyone in our team won.
On Tue, 14 Oct 2025 10:33:52 +0100, NY wrote:
We have an interesting power supply problem at the moment, which
Northern Powergrid are trying to fix. Power to our village is present
(for everyone, AFAIK) but the voltage has dropped to 95 V (barely enough
to turn on the LCD display on my power-monitoring plug!). NP say it is
due to a circuit breaker having tripped just one of the three phases in
the supply to our village.
Is it plausible that this could cause low voltage for everyone, as
opposed to full voltage for those houses that are on good phases and
total power loss for people on the phase that has tripped?
Indeed. Your 230v supply is the difference between 2 phases of a 380v
3 phase feed. So only the users on the two good phases will get
full voltage.
The Natural Philosopher wrote:I knew someone who made a portable battery pack to run their BBC micro.
Many of today's switched mode power supplies are happy from 48vDC to
250vAC.
DC?
On 14/10/2025 12:50, The Natural Philosopher wrote:
Many of today's switched mode power supplies are happy from 48vDC to
250vAC.
DC? I suppose a simple 4-diode bridge rectifier (the input between the
mains and the step-down transformer) will pass DC no matter what the polarity is, and if the step-down transformer is *after* the switching circuit (making the transformer much smaller) then DC will reach the oscillator, control circuit and power transistor.
Hmmm. I can believe that. What is odd is that everyone in the village,
no matter which phase their house was on, got low voltage. You'd think
that one house in three (between the two good phases) would have been
OK. Certainly no-one in the village said on our Facebook group "it's
fine for us". Weird.
NY <me@privacy.net> wrote in news:10cp8g3$pvr$1@dont-email.me:
Hmmm. I can believe that. What is odd is that everyone in the village,
no matter which phase their house was on, got low voltage. You'd think
that one house in three (between the two good phases) would have been
OK. Certainly no-one in the village said on our Facebook group "it's
fine for us". Weird.
That's not how it works, people are not fed with power between phases but between 'low' voltage[1] phase and neutral. On a low voltage supply that is
4 wires (each home normally getting only 2, 1 phase, 1 neutral). High
voltage supply (11kV+) is on 3 phase wires only (to save on copper) with
the final conversion from 'delta' to 'star' via the low voltage
transformer. Lose one of the input phases and the whole lot turns to shit (heavy mathematical vector proof omitted).
[1] In power distribution 230V counts as low voltage.
I have seen some examples where individual houses (in rural areas)
are fed from the difference between phases.-a The main feed is 3 phase
11kV with no neutral.-a A branch takes two conductors at 11kV from the available three and drives a transformer on a pole which then feeds
the house.
On 16/10/2025 15:38, fred wrote:
That's not how it works, people are not fed with power between phases
but between 'low' voltage[1] phase and neutral. On a low voltage
supply that is 4 wires (each home normally getting only 2, 1 phase, 1
neutral). High voltage supply (11kV+) is on 3 phase wires only (to
save on copper) with the final conversion from 'delta' to 'star' via
the low voltage transformer. Lose one of the input phases and the
whole lot turns to shit (heavy mathematical vector proof omitted).
[1] In power distribution 230V counts as low voltage.
I have seen some examples where individual houses (in rural areas)
are fed from the difference between phases. The main feed is 3 phase
11kV with no neutral. A branch takes two conductors at 11kV from the available three and drives a transformer on a pole which then feeds
the house.
John