• MCB tripped, and now RCD won't reset

    From tim+@timdownieuk@yahoo.co.uk to uk.d-i-y on Thu Aug 28 15:49:26 2025
    From Newsgroup: uk.d-i-y

    I went to turn my garage lights on and found that the power to the
    garage had gone.

    Checked the fusebox and one MCB and the RCD in the main consumer
    unit had tripped. Now the RCD won't reset even with every circuit
    turned off.

    RCD fault? (In addition to whatever tripped the garage circuit).

    Tim
    --
    --- Synchronet 3.21a-Linux NewsLink 1.2
  • From No mail@nomail@aolbin.com to uk.d-i-y on Thu Aug 28 16:11:44 2025
    From Newsgroup: uk.d-i-y

    tim+ wrote:
    I went to turn my garage lights on and found that the power to the
    garage had gone.

    Checked the fusebox and one MCB and the RCD in the main consumer
    unit had tripped. Now the RCD won't reset even with every circuit
    turned off.

    RCD fault? (In addition to whatever tripped the garage circuit).

    Tim

    What happens if you disconnect the output of the RCD?
    --- Synchronet 3.21a-Linux NewsLink 1.2
  • From Theo@theom+news@chiark.greenend.org.uk to uk.d-i-y on Thu Aug 28 16:37:07 2025
    From Newsgroup: uk.d-i-y

    tim+ <timdownieuk@yahoo.co.uk> wrote:
    I went to turn my garage lights on and found that the power to the
    garage had gone.

    Checked the fusebox and one MCB and the RCD in the main consumer
    unit had tripped. Now the RCD won't reset even with every circuit
    turned off.

    RCD fault? (In addition to whatever tripped the garage circuit).

    Leakage between neutral and earth. Typically your MCB is single pole and interrupting the live but not the neutral. Try disconnecting the neutrals
    of each circuit one at a time until you find which is causing the trip.
    (it may not be the garage)

    Theo
    --- Synchronet 3.21a-Linux NewsLink 1.2
  • From The Natural Philosopher@tnp@invalid.invalid to uk.d-i-y on Thu Aug 28 17:26:40 2025
    From Newsgroup: uk.d-i-y

    On 28/08/2025 15:49, tim+ wrote:
    I went to turn my garage lights on and found that the power to the
    garage had gone.

    Checked the fusebox and one MCB and the RCD in the main consumer
    unit had tripped. Now the RCD won't reset even with every circuit
    turned off.

    RCD fault? (In addition to whatever tripped the garage circuit).

    Unlikely. More likely you have a genuine earth to neutral short


    Tim
    --
    rCLwhen things get difficult you just have to lierCY

    rCo Jean Claud J|+ncker

    --- Synchronet 3.21a-Linux NewsLink 1.2
  • From tony sayer@tony@bancom.co.uk to uk.d-i-y on Thu Aug 28 21:26:00 2025
    From Newsgroup: uk.d-i-y

    In article <lei*O3blA@news.chiark.greenend.org.uk>, Theo <theom+news@chi ark.greenend.org.uk> scribeth thus
    tim+ <timdownieuk@yahoo.co.uk> wrote:
    I went to turn my garage lights on and found that the power to the
    garage had gone.

    Checked the fusebox and one MCB and the RCD in the main consumer
    unit had tripped. Now the RCD won't reset even with every circuit
    turned off.

    RCD fault? (In addition to whatever tripped the garage circuit).

    Leakage between neutral and earth. Typically your MCB is single pole and >interrupting the live but not the neutral. Try disconnecting the neutrals
    of each circuit one at a time until you find which is causing the trip.
    (it may not be the garage)

    Theo

    If it is neutral to earth it needs a bit of current to be flowing anyway
    else it won't trip..
    --
    Tony Sayer


    Man is least himself when he talks in his own person.

    Give him a keyboard, and he will reveal himself.


    --- Synchronet 3.21a-Linux NewsLink 1.2
  • From John Rumm@see.my.signature@nowhere.null to uk.d-i-y on Thu Aug 28 21:51:28 2025
    From Newsgroup: uk.d-i-y

    On 28/08/2025 21:26, tony sayer wrote:
    In article <lei*O3blA@news.chiark.greenend.org.uk>, Theo <theom+news@chi ark.greenend.org.uk> scribeth thus
    tim+ <timdownieuk@yahoo.co.uk> wrote:
    I went to turn my garage lights on and found that the power to the
    garage had gone.

    Checked the fusebox and one MCB and the RCD in the main consumer
    unit had tripped. Now the RCD won't reset even with every circuit
    turned off.

    RCD fault? (In addition to whatever tripped the garage circuit).

    Leakage between neutral and earth. Typically your MCB is single pole and
    interrupting the live but not the neutral. Try disconnecting the neutrals >> of each circuit one at a time until you find which is causing the trip.
    (it may not be the garage)

    Theo

    If it is neutral to earth it needs a bit of current to be flowing anyway
    else it won't trip..

    Although with TN-S that current could be in another property... (causing
    a voltage rise on neutral WRT to earth).
    --
    Cheers,

    John.

    /=================================================================\
    | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------|
    | John Rumm - john(at)internode(dot)co(dot)uk | \=================================================================/
    --- Synchronet 3.21a-Linux NewsLink 1.2
  • From Tim+@timdownieuk@yahoo.co.youkay to uk.d-i-y on Thu Aug 28 21:22:26 2025
    From Newsgroup: uk.d-i-y

    Theo <theom+news@chiark.greenend.org.uk> wrote:
    tim+ <timdownieuk@yahoo.co.uk> wrote:
    I went to turn my garage lights on and found that the power to the
    garage had gone.

    Checked the fusebox and one MCB and the RCD in the main consumer
    unit had tripped. Now the RCD won't reset even with every circuit
    turned off.

    RCD fault? (In addition to whatever tripped the garage circuit).

    Leakage between neutral and earth. Typically your MCB is single pole and interrupting the live but not the neutral. Try disconnecting the neutrals
    of each circuit one at a time until you find which is causing the trip.
    (it may not be the garage)

    Theo


    A bit if an update. I had to leave the house to run an errand and when I
    got back about 25 minutes later, the RCD reset normally and everything is working again.

    Not sure what to do now.


    Tim
    --
    Please don't feed the trolls
    --- Synchronet 3.21a-Linux NewsLink 1.2
  • From Chris Green@cl@isbd.net to uk.d-i-y on Fri Aug 29 09:45:35 2025
    From Newsgroup: uk.d-i-y

    Tim+ <timdownieuk@yahoo.co.youkay> wrote:
    Theo <theom+news@chiark.greenend.org.uk> wrote:
    tim+ <timdownieuk@yahoo.co.uk> wrote:
    I went to turn my garage lights on and found that the power to the
    garage had gone.

    Checked the fusebox and one MCB and the RCD in the main consumer
    unit had tripped. Now the RCD won't reset even with every circuit
    turned off.

    RCD fault? (In addition to whatever tripped the garage circuit).

    Leakage between neutral and earth. Typically your MCB is single pole and interrupting the live but not the neutral. Try disconnecting the neutrals of each circuit one at a time until you find which is causing the trip.
    (it may not be the garage)

    Theo


    A bit if an update. I had to leave the house to run an errand and when I
    got back about 25 minutes later, the RCD reset normally and everything is working again.

    RCDs do sometimes get 'nervous' in my experience and, after a rest, will reset.

    I'd do nothing for the present to see if the problem recurs at all.
    --
    Chris Green
    -+
    --- Synchronet 3.21a-Linux NewsLink 1.2
  • From The Natural Philosopher@tnp@invalid.invalid to uk.d-i-y on Fri Aug 29 10:41:36 2025
    From Newsgroup: uk.d-i-y

    On 28/08/2025 21:26, tony sayer wrote:
    In article <lei*O3blA@news.chiark.greenend.org.uk>, Theo <theom+news@chi ark.greenend.org.uk> scribeth thus
    tim+ <timdownieuk@yahoo.co.uk> wrote:
    I went to turn my garage lights on and found that the power to the
    garage had gone.

    Checked the fusebox and one MCB and the RCD in the main consumer
    unit had tripped. Now the RCD won't reset even with every circuit
    turned off.

    RCD fault? (In addition to whatever tripped the garage circuit).

    Leakage between neutral and earth. Typically your MCB is single pole and
    interrupting the live but not the neutral. Try disconnecting the neutrals >> of each circuit one at a time until you find which is causing the trip.
    (it may not be the garage)

    Theo

    If it is neutral to earth it needs a bit of current to be flowing anyway
    else it won't trip..

    True, but that must be happening or the RCD wouldn't keep tripping
    would it?
    --
    I would rather have questions that cannot be answered...
    ...than to have answers that cannot be questioned

    Richard Feynman



    --- Synchronet 3.21a-Linux NewsLink 1.2
  • From The Natural Philosopher@tnp@invalid.invalid to uk.d-i-y on Fri Aug 29 10:43:52 2025
    From Newsgroup: uk.d-i-y

    On 28/08/2025 22:22, Tim+ wrote:
    Theo <theom+news@chiark.greenend.org.uk> wrote:
    tim+ <timdownieuk@yahoo.co.uk> wrote:
    I went to turn my garage lights on and found that the power to the
    garage had gone.

    Checked the fusebox and one MCB and the RCD in the main consumer
    unit had tripped. Now the RCD won't reset even with every circuit
    turned off.

    RCD fault? (In addition to whatever tripped the garage circuit).

    Leakage between neutral and earth. Typically your MCB is single pole and
    interrupting the live but not the neutral. Try disconnecting the neutrals >> of each circuit one at a time until you find which is causing the trip.
    (it may not be the garage)

    Theo


    A bit if an update. I had to leave the house to run an errand and when I
    got back about 25 minutes later, the RCD reset normally and everything is working again.

    Not sure what to do now.


    Ive seen that occasionally.

    Try turning each appliance on until it pops again.

    If its earth neutral short each circuit will need a load on to pop it Sonething like an electric drill works well - nice high startup current


    Tim
    --
    I would rather have questions that cannot be answered...
    ...than to have answers that cannot be questioned

    Richard Feynman



    --- Synchronet 3.21a-Linux NewsLink 1.2
  • From Theo@theom+news@chiark.greenend.org.uk to uk.d-i-y on Fri Aug 29 13:58:47 2025
    From Newsgroup: uk.d-i-y

    tony sayer <tony@bancom.co.uk> wrote:
    In article <lei*O3blA@news.chiark.greenend.org.uk>, Theo <theom+news@chi ark.greenend.org.uk> scribeth thus
    tim+ <timdownieuk@yahoo.co.uk> wrote:
    I went to turn my garage lights on and found that the power to the
    garage had gone.

    Checked the fusebox and one MCB and the RCD in the main consumer
    unit had tripped. Now the RCD won't reset even with every circuit
    turned off.

    RCD fault? (In addition to whatever tripped the garage circuit).

    Leakage between neutral and earth. Typically your MCB is single pole and >interrupting the live but not the neutral. Try disconnecting the neutrals >of each circuit one at a time until you find which is causing the trip.
    (it may not be the garage)

    Theo

    If it is neutral to earth it needs a bit of current to be flowing anyway
    else it won't trip..

    Yebbut you can still get that if the MCB to the circuit is turned off.

    ie:

    live - RCD - MCB for circuit 1 - light bulb - neutral for circuit 1 -
    neutral busbar in CU - neutral for circuit 2 - neutral/earth leak - earth.

    ie the leak is on circuit 2, but it doesn't need any power to be on the live side of circuit 2 to cause an RCD trip. Turning off MCB 1 doesn't tell you anything about the location of the fault.

    If instead there was one RCBO per circuit then the RCBO for circuit 2 would have tripped, telling you where the fault was.

    Theo
    --- Synchronet 3.21a-Linux NewsLink 1.2
  • From Tim+@timdownieuk@yahoo.co.youkay to uk.d-i-y on Fri Aug 29 13:24:44 2025
    From Newsgroup: uk.d-i-y

    Chris Green <cl@isbd.net> wrote:
    Tim+ <timdownieuk@yahoo.co.youkay> wrote:
    Theo <theom+news@chiark.greenend.org.uk> wrote:
    tim+ <timdownieuk@yahoo.co.uk> wrote:
    I went to turn my garage lights on and found that the power to the
    garage had gone.

    Checked the fusebox and one MCB and the RCD in the main consumer
    unit had tripped. Now the RCD won't reset even with every circuit
    turned off.

    RCD fault? (In addition to whatever tripped the garage circuit).

    Leakage between neutral and earth. Typically your MCB is single pole and >>> interrupting the live but not the neutral. Try disconnecting the neutrals >>> of each circuit one at a time until you find which is causing the trip.
    (it may not be the garage)

    Theo


    A bit if an update. I had to leave the house to run an errand and when I
    got back about 25 minutes later, the RCD reset normally and everything is
    working again.

    RCDs do sometimes get 'nervous' in my experience and, after a rest, will reset.

    I'd do nothing for the present to see if the problem recurs at all.


    Sounds like the simplest approach for the meantime. ;-)

    Tim
    --
    Please don't feed the trolls
    --- Synchronet 3.21a-Linux NewsLink 1.2
  • From Jethro_uk@jethro_uk@hotmailbin.com to uk.d-i-y on Fri Aug 29 16:39:43 2025
    From Newsgroup: uk.d-i-y

    On Thu, 28 Aug 2025 21:22:26 +0000, Tim+ wrote:

    Theo <theom+news@chiark.greenend.org.uk> wrote:
    tim+ <timdownieuk@yahoo.co.uk> wrote:
    I went to turn my garage lights on and found that the power to the
    garage had gone.

    Checked the fusebox and one MCB and the RCD in the main consumer unit
    had tripped. Now the RCD won't reset even with every circuit turned
    off.

    RCD fault? (In addition to whatever tripped the garage circuit).

    Leakage between neutral and earth. Typically your MCB is single pole
    and interrupting the live but not the neutral. Try disconnecting the
    neutrals of each circuit one at a time until you find which is causing
    the trip. (it may not be the garage)

    Theo


    A bit if an update. I had to leave the house to run an errand and when
    I got back about 25 minutes later, the RCD reset normally and everything
    is working again.

    Not sure what to do now.

    Some sort of capacitance at work ?
    --- Synchronet 3.21a-Linux NewsLink 1.2
  • From Theo@theom+news@chiark.greenend.org.uk to uk.d-i-y on Fri Aug 29 17:49:33 2025
    From Newsgroup: uk.d-i-y

    Jethro_uk <jethro_uk@hotmailbin.com> wrote:
    On Thu, 28 Aug 2025 21:22:26 +0000, Tim+ wrote:
    A bit if an update. I had to leave the house to run an errand and when
    I got back about 25 minutes later, the RCD reset normally and everything
    is working again.

    Not sure what to do now.

    Some sort of capacitance at work ?

    Could be something on a timer or switch? eg immersion heater is on a timer, but it's only powered when the tank stat says the water is too cold. So
    it'll only cause a trip during timed periods but also only when hot water
    has been drained.

    The next day it's cold so the boiler runs the central heating and heats the water, and the immersion doesn't fire so no trip. It'll only trip on warm
    days when somebody also had a bath.

    (you can construct similar scenarios for various other appliances)

    Theo
    --- Synchronet 3.21a-Linux NewsLink 1.2
  • From The Natural Philosopher@tnp@invalid.invalid to uk.d-i-y on Fri Aug 29 19:31:19 2025
    From Newsgroup: uk.d-i-y

    On 29/08/2025 13:58, Theo wrote:
    tony sayer <tony@bancom.co.uk> wrote:
    In article <lei*O3blA@news.chiark.greenend.org.uk>, Theo <theom+news@chi
    ark.greenend.org.uk> scribeth thus
    tim+ <timdownieuk@yahoo.co.uk> wrote:
    I went to turn my garage lights on and found that the power to the
    garage had gone.

    Checked the fusebox and one MCB and the RCD in the main consumer
    unit had tripped. Now the RCD won't reset even with every circuit
    turned off.

    RCD fault? (In addition to whatever tripped the garage circuit).

    Leakage between neutral and earth. Typically your MCB is single pole and >>> interrupting the live but not the neutral. Try disconnecting the neutrals >>> of each circuit one at a time until you find which is causing the trip.
    (it may not be the garage)

    Theo

    If it is neutral to earth it needs a bit of current to be flowing anyway
    else it won't trip..

    Yebbut you can still get that if the MCB to the circuit is turned off.

    How?

    ie:

    live - RCD - MCB for circuit 1 - light bulb - neutral for circuit 1 -
    neutral busbar in CU - neutral for circuit 2 - neutral/earth leak - earth.

    ie the leak is on circuit 2, but it doesn't need any power to be on the live side of circuit 2 to cause an RCD trip. Turning off MCB 1 doesn't tell you anything about the location of the fault.

    If instead there was one RCBO per circuit then the RCBO for circuit 2 would have tripped, telling you where the fault was.

    He said he turned off EVERTYHING and it still tripped

    Theo
    --
    "When one man dies it's a tragedy. When thousands die it's statistics."

    Josef Stalin


    --- Synchronet 3.21a-Linux NewsLink 1.2
  • From The Natural Philosopher@tnp@invalid.invalid to uk.d-i-y on Fri Aug 29 19:33:11 2025
    From Newsgroup: uk.d-i-y

    On 29/08/2025 17:49, Theo wrote:
    Jethro_uk <jethro_uk@hotmailbin.com> wrote:
    On Thu, 28 Aug 2025 21:22:26 +0000, Tim+ wrote:
    A bit if an update. I had to leave the house to run an errand and when
    I got back about 25 minutes later, the RCD reset normally and everything >>> is working again.

    Not sure what to do now.

    Some sort of capacitance at work ?

    Could be something on a timer or switch? eg immersion heater is on a timer, but it's only powered when the tank stat says the water is too cold. So it'll only cause a trip during timed periods but also only when hot water
    has been drained.

    The next day it's cold so the boiler runs the central heating and heats the water, and the immersion doesn't fire so no trip. It'll only trip on warm days when somebody also had a bath.

    (you can construct similar scenarios for various other appliances)

    Theo

    You can also construct scenarios where several items together will cause enough earth leakage, but one alone will not. That is particularly true
    of an earth neutral short
    --
    How fortunate for governments that the people they administer don't think.

    Adolf Hitler


    --- Synchronet 3.21a-Linux NewsLink 1.2
  • From Theo@theom+news@chiark.greenend.org.uk to uk.d-i-y on Sat Aug 30 10:50:35 2025
    From Newsgroup: uk.d-i-y

    The Natural Philosopher <tnp@invalid.invalid> wrote:
    On 29/08/2025 13:58, Theo wrote:
    live - RCD - MCB for circuit 1 - light bulb - neutral for circuit 1 - neutral busbar in CU - neutral for circuit 2 - neutral/earth leak - earth.

    ie the leak is on circuit 2, but it doesn't need any power to be on the live
    side of circuit 2 to cause an RCD trip. Turning off MCB 1 doesn't tell you anything about the location of the fault.

    If instead there was one RCBO per circuit then the RCBO for circuit 2 would have tripped, telling you where the fault was.

    He said he turned off EVERTYHING and it still tripped

    Ah, I missed that. If every single MCB in the installation is off there
    could still be a leakage path from neutral to earth but the current would
    have to come from somewhere external, eg from a neighbour. I would be
    checking the supply N-E impedance as it might suggest there isn't a good
    bond between them.

    If it is a TT supply, the neutral is only bonded to earth at the transformer
    so there could be a decent voltage between N and the customer's earth rod.
    If there was N-E leak downstream of the RCD that could cause a N-E current
    to flow through the RCD and trip it.

    Theo
    --- Synchronet 3.21a-Linux NewsLink 1.2
  • From Theo@theom+news@chiark.greenend.org.uk to uk.d-i-y on Sat Aug 30 11:12:25 2025
    From Newsgroup: uk.d-i-y

    Theo <theom+news@chiark.greenend.org.uk> wrote:
    Ah, I missed that. If every single MCB in the installation is off there could still be a leakage path from neutral to earth but the current would have to come from somewhere external, eg from a neighbour. I would be checking the supply N-E impedance as it might suggest there isn't a good
    bond between them.

    If it is a TT supply, the neutral is only bonded to earth at the transformer so there could be a decent voltage between N and the customer's earth rod. If there was N-E leak downstream of the RCD that could cause a N-E current
    to flow through the RCD and trip it.

    Actually, TT could be the source of randomness too. If it's dry, the ground dries up and the earth impedance to the substation increases, meaning the N from the transformer floats higher above local earth. A higher voltage
    means more current can flow into a N-E fault, perhaps enough to trip the
    RCD.

    Then it rains, and the ground gets wet. E impedance to the transformer decreases (ie the quality of the earth bond improves) and there's less potential difference between N and local E. That could reduce the current flowing into a local fault and could fail to trip the RCD.

    Would need some measurements to tell if this is at all plausible...

    Theo
    --- Synchronet 3.21a-Linux NewsLink 1.2
  • From tony sayer@tony@bancom.co.uk to uk.d-i-y on Sun Aug 31 13:39:47 2025
    From Newsgroup: uk.d-i-y

    In article <fu58ol-k35m.ln1@q957.zbmc.eu>, Chris Green <cl@isbd.net>
    scribeth thus
    Tim+ <timdownieuk@yahoo.co.youkay> wrote:
    Theo <theom+news@chiark.greenend.org.uk> wrote:
    tim+ <timdownieuk@yahoo.co.uk> wrote:
    I went to turn my garage lights on and found that the power to the
    garage had gone.

    Checked the fusebox and one MCB and the RCD in the main consumer
    unit had tripped. Now the RCD won't reset even with every circuit
    turned off.

    RCD fault? (In addition to whatever tripped the garage circuit).

    Leakage between neutral and earth. Typically your MCB is single pole and >> > interrupting the live but not the neutral. Try disconnecting the neutrals >> > of each circuit one at a time until you find which is causing the trip.
    (it may not be the garage)

    Theo


    A bit if an update. I had to leave the house to run an errand and when I
    got back about 25 minutes later, the RCD reset normally and everything is
    working again.

    RCDs do sometimes get 'nervous' in my experience and, after a rest, will reset.

    I'd do nothing for the present to see if the problem recurs at all.


    Amusing nervous the RCD! Perhaps what is happening is that there is
    possibly a degree of leakage thats residual, like the leakage of a PC
    power unit caps in it on the incoming supply line. Had this at a local
    radio station years ago would take a large rewire to make it better as
    more staff stated up their PC's the leakage rose, and sometimes the
    next PC online too much for the RCD who said "stuff that I'm off"!.

    RCBO's wouldn't have helped that as there was only the one ring main in
    use in the building, the owners flogged the licence and the building is
    now a Pizza hut!..
    --
    Tony Sayer


    Man is least himself when he talks in his own person.

    Give him a keyboard, and he will reveal himself.


    --- Synchronet 3.21a-Linux NewsLink 1.2
  • From The Natural Philosopher@tnp@invalid.invalid to uk.d-i-y on Sun Aug 31 14:18:16 2025
    From Newsgroup: uk.d-i-y

    On 31/08/2025 13:39, tony sayer wrote:
    Had this at a local
    radio station years ago would take a large rewire to make it better as
    more staff stated up their PC's the leakage rose, and sometimes the
    next PC online too much for the RCD who said "stuff that I'm off"!.

    RCBO's wouldn't have helped that as there was only the one ring main in
    use in the building, the owners flogged the licence and the building is
    now a Pizza hut!..

    Had this at our office building years ago. 35PCs simply tripped a 60A
    mains incoming if they all powered on at once, We had to turn them on
    one at a time., We fiitted 100A eventually
    --
    You can get much farther with a kind word and a gun than you can with a
    kind word alone.

    Al Capone