I went to turn my garage lights on and found that the power to the
garage had gone.
Checked the fusebox and one MCB and the RCD in the main consumer
unit had tripped. Now the RCD won't reset even with every circuit
turned off.
RCD fault? (In addition to whatever tripped the garage circuit).
Tim
I went to turn my garage lights on and found that the power to the
garage had gone.
Checked the fusebox and one MCB and the RCD in the main consumer
unit had tripped. Now the RCD won't reset even with every circuit
turned off.
RCD fault? (In addition to whatever tripped the garage circuit).
I went to turn my garage lights on and found that the power to the
garage had gone.
Checked the fusebox and one MCB and the RCD in the main consumer
unit had tripped. Now the RCD won't reset even with every circuit
turned off.
RCD fault? (In addition to whatever tripped the garage circuit).
Tim--
tim+ <timdownieuk@yahoo.co.uk> wrote:
I went to turn my garage lights on and found that the power to the
garage had gone.
Checked the fusebox and one MCB and the RCD in the main consumer
unit had tripped. Now the RCD won't reset even with every circuit
turned off.
RCD fault? (In addition to whatever tripped the garage circuit).
Leakage between neutral and earth. Typically your MCB is single pole and >interrupting the live but not the neutral. Try disconnecting the neutrals
of each circuit one at a time until you find which is causing the trip.
(it may not be the garage)
Theo
In article <lei*O3blA@news.chiark.greenend.org.uk>, Theo <theom+news@chi ark.greenend.org.uk> scribeth thus
tim+ <timdownieuk@yahoo.co.uk> wrote:
I went to turn my garage lights on and found that the power to the
garage had gone.
Checked the fusebox and one MCB and the RCD in the main consumer
unit had tripped. Now the RCD won't reset even with every circuit
turned off.
RCD fault? (In addition to whatever tripped the garage circuit).
Leakage between neutral and earth. Typically your MCB is single pole and
interrupting the live but not the neutral. Try disconnecting the neutrals >> of each circuit one at a time until you find which is causing the trip.
(it may not be the garage)
Theo
If it is neutral to earth it needs a bit of current to be flowing anyway
else it won't trip..
tim+ <timdownieuk@yahoo.co.uk> wrote:
I went to turn my garage lights on and found that the power to the
garage had gone.
Checked the fusebox and one MCB and the RCD in the main consumer
unit had tripped. Now the RCD won't reset even with every circuit
turned off.
RCD fault? (In addition to whatever tripped the garage circuit).
Leakage between neutral and earth. Typically your MCB is single pole and interrupting the live but not the neutral. Try disconnecting the neutrals
of each circuit one at a time until you find which is causing the trip.
(it may not be the garage)
Theo
Theo <theom+news@chiark.greenend.org.uk> wrote:
tim+ <timdownieuk@yahoo.co.uk> wrote:
I went to turn my garage lights on and found that the power to the
garage had gone.
Checked the fusebox and one MCB and the RCD in the main consumer
unit had tripped. Now the RCD won't reset even with every circuit
turned off.
RCD fault? (In addition to whatever tripped the garage circuit).
Leakage between neutral and earth. Typically your MCB is single pole and interrupting the live but not the neutral. Try disconnecting the neutrals of each circuit one at a time until you find which is causing the trip.
(it may not be the garage)
Theo
A bit if an update. I had to leave the house to run an errand and when I
got back about 25 minutes later, the RCD reset normally and everything is working again.
In article <lei*O3blA@news.chiark.greenend.org.uk>, Theo <theom+news@chi ark.greenend.org.uk> scribeth thus
tim+ <timdownieuk@yahoo.co.uk> wrote:
I went to turn my garage lights on and found that the power to the
garage had gone.
Checked the fusebox and one MCB and the RCD in the main consumer
unit had tripped. Now the RCD won't reset even with every circuit
turned off.
RCD fault? (In addition to whatever tripped the garage circuit).
Leakage between neutral and earth. Typically your MCB is single pole and
interrupting the live but not the neutral. Try disconnecting the neutrals >> of each circuit one at a time until you find which is causing the trip.
(it may not be the garage)
Theo
If it is neutral to earth it needs a bit of current to be flowing anyway
else it won't trip..
Theo <theom+news@chiark.greenend.org.uk> wrote:
tim+ <timdownieuk@yahoo.co.uk> wrote:
I went to turn my garage lights on and found that the power to the
garage had gone.
Checked the fusebox and one MCB and the RCD in the main consumer
unit had tripped. Now the RCD won't reset even with every circuit
turned off.
RCD fault? (In addition to whatever tripped the garage circuit).
Leakage between neutral and earth. Typically your MCB is single pole and
interrupting the live but not the neutral. Try disconnecting the neutrals >> of each circuit one at a time until you find which is causing the trip.
(it may not be the garage)
Theo
A bit if an update. I had to leave the house to run an errand and when I
got back about 25 minutes later, the RCD reset normally and everything is working again.
Not sure what to do now.
Tim--
In article <lei*O3blA@news.chiark.greenend.org.uk>, Theo <theom+news@chi ark.greenend.org.uk> scribeth thus
tim+ <timdownieuk@yahoo.co.uk> wrote:
I went to turn my garage lights on and found that the power to the
garage had gone.
Checked the fusebox and one MCB and the RCD in the main consumer
unit had tripped. Now the RCD won't reset even with every circuit
turned off.
RCD fault? (In addition to whatever tripped the garage circuit).
Leakage between neutral and earth. Typically your MCB is single pole and >interrupting the live but not the neutral. Try disconnecting the neutrals >of each circuit one at a time until you find which is causing the trip.
(it may not be the garage)
Theo
If it is neutral to earth it needs a bit of current to be flowing anyway
else it won't trip..
Tim+ <timdownieuk@yahoo.co.youkay> wrote:
Theo <theom+news@chiark.greenend.org.uk> wrote:RCDs do sometimes get 'nervous' in my experience and, after a rest, will reset.
tim+ <timdownieuk@yahoo.co.uk> wrote:
I went to turn my garage lights on and found that the power to the
garage had gone.
Checked the fusebox and one MCB and the RCD in the main consumer
unit had tripped. Now the RCD won't reset even with every circuit
turned off.
RCD fault? (In addition to whatever tripped the garage circuit).
Leakage between neutral and earth. Typically your MCB is single pole and >>> interrupting the live but not the neutral. Try disconnecting the neutrals >>> of each circuit one at a time until you find which is causing the trip.
(it may not be the garage)
Theo
A bit if an update. I had to leave the house to run an errand and when I
got back about 25 minutes later, the RCD reset normally and everything is
working again.
I'd do nothing for the present to see if the problem recurs at all.
Theo <theom+news@chiark.greenend.org.uk> wrote:
tim+ <timdownieuk@yahoo.co.uk> wrote:A bit if an update. I had to leave the house to run an errand and when
I went to turn my garage lights on and found that the power to the
garage had gone.
Checked the fusebox and one MCB and the RCD in the main consumer unit
had tripped. Now the RCD won't reset even with every circuit turned
off.
RCD fault? (In addition to whatever tripped the garage circuit).
Leakage between neutral and earth. Typically your MCB is single pole
and interrupting the live but not the neutral. Try disconnecting the
neutrals of each circuit one at a time until you find which is causing
the trip. (it may not be the garage)
Theo
I got back about 25 minutes later, the RCD reset normally and everything
is working again.
Not sure what to do now.
On Thu, 28 Aug 2025 21:22:26 +0000, Tim+ wrote:
A bit if an update. I had to leave the house to run an errand and when
I got back about 25 minutes later, the RCD reset normally and everything
is working again.
Not sure what to do now.
Some sort of capacitance at work ?
tony sayer <tony@bancom.co.uk> wrote:
In article <lei*O3blA@news.chiark.greenend.org.uk>, Theo <theom+news@chi
ark.greenend.org.uk> scribeth thus
tim+ <timdownieuk@yahoo.co.uk> wrote:
I went to turn my garage lights on and found that the power to the
garage had gone.
Checked the fusebox and one MCB and the RCD in the main consumer
unit had tripped. Now the RCD won't reset even with every circuit
turned off.
RCD fault? (In addition to whatever tripped the garage circuit).
Leakage between neutral and earth. Typically your MCB is single pole and >>> interrupting the live but not the neutral. Try disconnecting the neutrals >>> of each circuit one at a time until you find which is causing the trip.
(it may not be the garage)
Theo
If it is neutral to earth it needs a bit of current to be flowing anyway
else it won't trip..
Yebbut you can still get that if the MCB to the circuit is turned off.
ie:
live - RCD - MCB for circuit 1 - light bulb - neutral for circuit 1 -
neutral busbar in CU - neutral for circuit 2 - neutral/earth leak - earth.
ie the leak is on circuit 2, but it doesn't need any power to be on the live side of circuit 2 to cause an RCD trip. Turning off MCB 1 doesn't tell you anything about the location of the fault.
If instead there was one RCBO per circuit then the RCBO for circuit 2 would have tripped, telling you where the fault was.
Theo--
Jethro_uk <jethro_uk@hotmailbin.com> wrote:
On Thu, 28 Aug 2025 21:22:26 +0000, Tim+ wrote:
A bit if an update. I had to leave the house to run an errand and when
I got back about 25 minutes later, the RCD reset normally and everything >>> is working again.
Not sure what to do now.
Some sort of capacitance at work ?
Could be something on a timer or switch? eg immersion heater is on a timer, but it's only powered when the tank stat says the water is too cold. So it'll only cause a trip during timed periods but also only when hot water
has been drained.
The next day it's cold so the boiler runs the central heating and heats the water, and the immersion doesn't fire so no trip. It'll only trip on warm days when somebody also had a bath.
(you can construct similar scenarios for various other appliances)
Theo
On 29/08/2025 13:58, Theo wrote:
live - RCD - MCB for circuit 1 - light bulb - neutral for circuit 1 - neutral busbar in CU - neutral for circuit 2 - neutral/earth leak - earth.
ie the leak is on circuit 2, but it doesn't need any power to be on the live
side of circuit 2 to cause an RCD trip. Turning off MCB 1 doesn't tell you anything about the location of the fault.
If instead there was one RCBO per circuit then the RCBO for circuit 2 would have tripped, telling you where the fault was.
He said he turned off EVERTYHING and it still tripped
Ah, I missed that. If every single MCB in the installation is off there could still be a leakage path from neutral to earth but the current would have to come from somewhere external, eg from a neighbour. I would be checking the supply N-E impedance as it might suggest there isn't a good
bond between them.
If it is a TT supply, the neutral is only bonded to earth at the transformer so there could be a decent voltage between N and the customer's earth rod. If there was N-E leak downstream of the RCD that could cause a N-E current
to flow through the RCD and trip it.
Tim+ <timdownieuk@yahoo.co.youkay> wrote:
Theo <theom+news@chiark.greenend.org.uk> wrote:RCDs do sometimes get 'nervous' in my experience and, after a rest, will reset.
tim+ <timdownieuk@yahoo.co.uk> wrote:
I went to turn my garage lights on and found that the power to the
garage had gone.
Checked the fusebox and one MCB and the RCD in the main consumer
unit had tripped. Now the RCD won't reset even with every circuit
turned off.
RCD fault? (In addition to whatever tripped the garage circuit).
Leakage between neutral and earth. Typically your MCB is single pole and >> > interrupting the live but not the neutral. Try disconnecting the neutrals >> > of each circuit one at a time until you find which is causing the trip.
(it may not be the garage)
Theo
A bit if an update. I had to leave the house to run an errand and when I
got back about 25 minutes later, the RCD reset normally and everything is
working again.
I'd do nothing for the present to see if the problem recurs at all.
Had this at a local
radio station years ago would take a large rewire to make it better as
more staff stated up their PC's the leakage rose, and sometimes the
next PC online too much for the RCD who said "stuff that I'm off"!.
RCBO's wouldn't have helped that as there was only the one ring main in
use in the building, the owners flogged the licence and the building is
now a Pizza hut!..