    From Dark Brandon@21:1/5 to All on Thu May 1 11:49:15 2025
    XPost: alt.survival, misc.survivalism

    Story by Capell Aris The Telegraph

    Last Monday, the Iberian grid suffered a disturbance in the south-west
    at 12:33. In 3.5 seconds this worsened and the interconnection to France disconnected. All renewable generation then went off-line, followed by disconnection of all rotating generation plant. The Iberian blackout was complete within a few seconds.

    At the time the grid was producing 28.4 GW of power, of which 79 per
    cent was solar and wind. This was a problematic situation as solar and
    wind plants have another, not widely known, downside – one quite apart
    from their intermittency and expense.

    This is the fact that they do not supply any inertia to the grid.
    Thermal powerplants – coal, gas, nuclear, for example – drive large spinning generators which are directly, synchronously connected to the
    grid. If there are changes which cause a difference between demand and
    supply, the generators will start to spin faster or slower: but their
    inertia resists this process, meaning that the frequency of the
    alternating current in the grid changes only slowly. There is time for
    the grid managers to act, matching supply to demand and keeping the grid frequency within limits.

    This is vital because all grids must supply power at a steady frequency
    so that electrical appliances work properly and safely. Deviations from
    the standard grid frequency can cause damage to equipment and other
    problems: in practice what happens quite rapidly when frequency changes significantly is that grid machinery trips out to prevent these issues
    and grids go down.

    When a grid has very little inertia in it – as with the Iberian one on
    Monday – a problem which a high-inertia grid would easily resist can
    cause a blackout within seconds. Lack of inertia was almost certainly
    the primary cause of the Iberian blackout, as Matt Oliver has opined in
    these pages. A grid with more inertia would not have collapsed as
    quickly, and its operators would have had time to keep it up and running.

    Restoration of supplies was completed by early Tuesday morning, based on reconnection to France, which facilitated progressive area reconnections
    across Spain and Portugal.

    Iberia is part of the Continental Europe Synchronous Area which
    stretches to 32 countries. It is interconnected as a phase-locked, 50 Hz
    grid with a generation capacity of 700 GW. To improve the stability of
    this grid, the EU aim is that all partners will extract 10 per cent of
    their power consumption from synchronous interconnectors – ones which transmit grid inertia – helping to make the whole system more resilient. France is at 10 per cent, but peninsula grids and those at the
    geographical fringe are the least interconnected. Spain has just 2 per
    cent from synchronous interconnectors.

    But there are places where things are worse. The UK and Ireland are
    island grids. They do have undersea power interconnectors to Europe but
    these are non-synchronous DC links and transmit no grid inertia. There’s little prospect that this will change.

    Both the Irish and UK grid system operators had developed an array of
    grid protection services that can control grid frequency, loss of load
    or generation protection, grid phase angle and recovering from grid
    outages. Neither country has, to date, ever experienced a total system
    failure, even during WWII.

    In 1974 construction started on Dinorwig Power Station. It is a pumped
    storage generation plant designed specifically for the provision of all
    the UK’s grid protection services. Dinorwig can make huge changes to its output in a matter of seconds, compensating for sudden events. Operation
    began in 1984. In 1990 all the UK’s generating stations could provide inertia.

    Nowadays, 55 per cent of our generation mix (wind, solar, DC imports)
    cannot supply inertia to the grid. Are we approaching a system that
    compares with Spain and Portugal on Monday?

    It certainly looks that way. In 2012 the National Grid produced a solar briefing note for the government which is still available online. In
    that note they imagine a system that has 22 GW of solar power attached
    to the grid. They demonstrate their concerns based on a sunny summer day
    when demand is low. The sun rises at 5 o’clock when little or no
    synchronous plant other than nuclear generation will be on line and at
    midday, solar is 60 per cent of all generation. The Grid’s engineers
    then considered that situation “difficult to manage” and concluded that wind+solar power must never exceed 60 per cent of generation.

    We now have 17.7 GW of grid-connected solar farms to which we must add
    all rooftop solar installations. At midday on Tuesday according to
    Gridwatch the UK’s asynchronous, no-inertia generation was at 66 per
    cent of total generation.

    In 2014 National Grid produced a System Operability Framework document.
    Their objective was to outline how future scenarios of generation mixes
    would impact upon protection services for the grid. As more and more
    renewable generators are brought on-line, the difficulties of managing
    the grid have become more and more onerous. For example, one service
    titled “primary response” in 1990 called for selected generation plants
    to increase generation within 10 seconds after a fault is detected: by
    1,200 MW in winter and 1,500 MW in summer. In 2024 these increases are
    required in 1.2 seconds!

    After nearly 50 years of operation, Dinorwig Power Station is currently
    shut down for major repairs and there has been no information on when it
    will re-open. Over the next five years all of our nuclear stations, bar Sizewell, will be closed. Over the same period our combined cycle gas
    generator fleet will halve from 30 GW to 15 GW. (It takes 5 years to
    build a new CCGT even using an existing site. The new ones are 66 per
    cent efficient and cost less than £1 billion to build a 1 GW plant – one third the cost of an offshore windmill.)

    We will lose huge amounts of grid inertia. Low-inertia operation will
    become routine. It is hard to imagine that we won’t start to suffer
    complete national blackouts like the Iberian one.

    One last piece of doom: the recovery of Spain’s grid in just one day is impressive. This speed is certainly due to the assistance of a large,
    stable grid reconnecting into the Iberian system thus allowing recovery
    in a series of stable steps as each grid area is recovered. We will not
    have that facility in the UK with our asynchronous interconnectors.

    Dr Capell Aris PhD spent his career in the electricity generation
    sector. He is a Fellow of the Institute of Engineering and Technology

    https://www.msn.com/en-us/money/companies/a-power-engineer-on-the-iberian-grid-collapse-it-makes-me-very-afraid-for-britain/ar-AA1DZjGo

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Jan Panteltje@21:1/5 to All on Fri May 2 05:34:10 2025
    XPost: alt.survival, misc.survivalism

    Story by Capell Aris The Telegraph

    Last Monday, the Iberian grid suffered a disturbance in the south-west
    at 12:33. In 3.5 seconds this worsened and the interconnection to France >disconnected. All renewable generation then went off-line, followed by >disconnection of all rotating generation plant. The Iberian blackout was >complete within a few seconds.

    At the time the grid was producing 28.4 GW of power, of which 79 per
    cent was solar and wind. This was a problematic situation as solar and
    wind plants have another, not widely known, downside – one quite apart
    from their intermittency and expense.

    This is the fact that they do not supply any inertia to the grid.
    Thermal powerplants – coal, gas, nuclear, for example – drive large >spinning generators which are directly, synchronously connected to the
    grid. If there are changes which cause a difference between demand and >supply, the generators will start to spin faster or slower: but their
    inertia resists this process, meaning that the frequency of the
    alternating current in the grid changes only slowly. There is time for
    the grid managers to act, matching supply to demand and keeping the grid >frequency within limits.

    This is vital because all grids must supply power at a steady frequency
    so that electrical appliances work properly and safely. Deviations from
    the standard grid frequency can cause damage to equipment and other
    problems: in practice what happens quite rapidly when frequency changes >significantly is that grid machinery trips out to prevent these issues
    and grids go down.

    When a grid has very little inertia in it – as with the Iberian one on >Monday – a problem which a high-inertia grid would easily resist can
    cause a blackout within seconds. Lack of inertia was almost certainly
    the primary cause of the Iberian blackout, as Matt Oliver has opined in
    these pages. A grid with more inertia would not have collapsed as
    quickly, and its operators would have had time to keep it up and running.

    Restoration of supplies was completed by early Tuesday morning, based on >reconnection to France, which facilitated progressive area reconnections >across Spain and Portugal.

    Iberia is part of the Continental Europe Synchronous Area which
    stretches to 32 countries. It is interconnected as a phase-locked, 50 Hz
    grid with a generation capacity of 700 GW. To improve the stability of
    this grid, the EU aim is that all partners will extract 10 per cent of
    their power consumption from synchronous interconnectors – ones which >transmit grid inertia – helping to make the whole system more resilient. >France is at 10 per cent, but peninsula grids and those at the
    geographical fringe are the least interconnected. Spain has just 2 per
    cent from synchronous interconnectors.

    But there are places where things are worse. The UK and Ireland are
    island grids. They do have undersea power interconnectors to Europe but
    these are non-synchronous DC links and transmit no grid inertia. There’s >little prospect that this will change.

    Both the Irish and UK grid system operators had developed an array of
    grid protection services that can control grid frequency, loss of load
    or generation protection, grid phase angle and recovering from grid
    outages. Neither country has, to date, ever experienced a total system >failure, even during WWII.

    In 1974 construction started on Dinorwig Power Station. It is a pumped >storage generation plant designed specifically for the provision of all
    the UK’s grid protection services. Dinorwig can make huge changes to its >output in a matter of seconds, compensating for sudden events. Operation >began in 1984. In 1990 all the UK’s generating stations could provide >inertia.

    Nowadays, 55 per cent of our generation mix (wind, solar, DC imports)
    cannot supply inertia to the grid. Are we approaching a system that
    compares with Spain and Portugal on Monday?

    It certainly looks that way. In 2012 the National Grid produced a solar >briefing note for the government which is still available online. In
    that note they imagine a system that has 22 GW of solar power attached
    to the grid. They demonstrate their concerns based on a sunny summer day
    when demand is low. The sun rises at 5 o’clock when little or no >synchronous plant other than nuclear generation will be on line and at >midday, solar is 60 per cent of all generation. The Grid’s engineers
    then considered that situation “difficult to manage” and concluded that >wind+solar power must never exceed 60 per cent of generation.

    We now have 17.7 GW of grid-connected solar farms to which we must add
    all rooftop solar installations. At midday on Tuesday according to
    Gridwatch the UK’s asynchronous, no-inertia generation was at 66 per
    cent of total generation.

    In 2014 National Grid produced a System Operability Framework document.
    Their objective was to outline how future scenarios of generation mixes
    would impact upon protection services for the grid. As more and more >renewable generators are brought on-line, the difficulties of managing
    the grid have become more and more onerous. For example, one service
    titled “primary response” in 1990 called for selected generation plants >to increase generation within 10 seconds after a fault is detected: by
    1,200 MW in winter and 1,500 MW in summer. In 2024 these increases are >required in 1.2 seconds!

    After nearly 50 years of operation, Dinorwig Power Station is currently
    shut down for major repairs and there has been no information on when it
    will re-open. Over the next five years all of our nuclear stations, bar >Sizewell, will be closed. Over the same period our combined cycle gas >generator fleet will halve from 30 GW to 15 GW. (It takes 5 years to
    build a new CCGT even using an existing site. The new ones are 66 per
    cent efficient and cost less than £1 billion to build a 1 GW plant – one >third the cost of an offshore windmill.)

    We will lose huge amounts of grid inertia. Low-inertia operation will
    become routine. It is hard to imagine that we won’t start to suffer >complete national blackouts like the Iberian one.

    One last piece of doom: the recovery of Spain’s grid in just one day is >impressive. This speed is certainly due to the assistance of a large,
    stable grid reconnecting into the Iberian system thus allowing recovery
    in a series of stable steps as each grid area is recovered. We will not
    have that facility in the UK with our asynchronous interconnectors.

    Dr Capell Aris PhD spent his career in the electricity generation
    sector. He is a Fellow of the Institute of Engineering and Technology

    https://www.msn.com/en-us/money/companies/a-power-engineer-on-the-iberian-grid-collapse-it-makes-me-very-afraid-for-britain/ar-AA
    1DZjGo

    DC is already used for long distances power transfer.
    These days with electronics it is easy to convert that to AC locally, synchronized if need be.
    But you could drop the 50 Hz or 60 Hz net altogether and do local conversion to AC, and / or to a lower DC voltage
    even for for each household.
    Using high frequency switching converters reduces the amount of huge transformers.
    Local batteries and solar cells... I have a 250 Ah battery pack and solar cells and a 2 kW DC to AC pure sinewave inverter here.
    Will at least run the fridge and microwave if the net goes down.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Dark Brandon@21:1/5 to Jan Panteltje on Fri May 2 09:42:20 2025
    XPost: alt.survival, misc.survivalism

    On 5/1/2025 11:34 PM, Jan Panteltje wrote:
    Story by Capell Aris The Telegraph

    Last Monday, the Iberian grid suffered a disturbance in the south-west
    at 12:33. In 3.5 seconds this worsened and the interconnection to France
    disconnected. All renewable generation then went off-line, followed by
    disconnection of all rotating generation plant. The Iberian blackout was
    complete within a few seconds.

    At the time the grid was producing 28.4 GW of power, of which 79 per
    cent was solar and wind. This was a problematic situation as solar and
    wind plants have another, not widely known, downside – one quite apart >>from their intermittency and expense.

    This is the fact that they do not supply any inertia to the grid.
    Thermal powerplants – coal, gas, nuclear, for example – drive large
    spinning generators which are directly, synchronously connected to the
    grid. If there are changes which cause a difference between demand and
    supply, the generators will start to spin faster or slower: but their
    inertia resists this process, meaning that the frequency of the
    alternating current in the grid changes only slowly. There is time for
    the grid managers to act, matching supply to demand and keeping the grid
    frequency within limits.

    This is vital because all grids must supply power at a steady frequency
    so that electrical appliances work properly and safely. Deviations from
    the standard grid frequency can cause damage to equipment and other
    problems: in practice what happens quite rapidly when frequency changes
    significantly is that grid machinery trips out to prevent these issues
    and grids go down.

    When a grid has very little inertia in it – as with the Iberian one on
    Monday – a problem which a high-inertia grid would easily resist can
    cause a blackout within seconds. Lack of inertia was almost certainly
    the primary cause of the Iberian blackout, as Matt Oliver has opined in
    these pages. A grid with more inertia would not have collapsed as
    quickly, and its operators would have had time to keep it up and running.

    Restoration of supplies was completed by early Tuesday morning, based on
    reconnection to France, which facilitated progressive area reconnections
    across Spain and Portugal.

    Iberia is part of the Continental Europe Synchronous Area which
    stretches to 32 countries. It is interconnected as a phase-locked, 50 Hz
    grid with a generation capacity of 700 GW. To improve the stability of
    this grid, the EU aim is that all partners will extract 10 per cent of
    their power consumption from synchronous interconnectors – ones which
    transmit grid inertia – helping to make the whole system more resilient. >> France is at 10 per cent, but peninsula grids and those at the
    geographical fringe are the least interconnected. Spain has just 2 per
    cent from synchronous interconnectors.

    But there are places where things are worse. The UK and Ireland are
    island grids. They do have undersea power interconnectors to Europe but
    these are non-synchronous DC links and transmit no grid inertia. There’s >> little prospect that this will change.

    Both the Irish and UK grid system operators had developed an array of
    grid protection services that can control grid frequency, loss of load
    or generation protection, grid phase angle and recovering from grid
    outages. Neither country has, to date, ever experienced a total system
    failure, even during WWII.

    In 1974 construction started on Dinorwig Power Station. It is a pumped
    storage generation plant designed specifically for the provision of all
    the UK’s grid protection services. Dinorwig can make huge changes to its >> output in a matter of seconds, compensating for sudden events. Operation
    began in 1984. In 1990 all the UK’s generating stations could provide
    inertia.

    Nowadays, 55 per cent of our generation mix (wind, solar, DC imports)
    cannot supply inertia to the grid. Are we approaching a system that
    compares with Spain and Portugal on Monday?

    It certainly looks that way. In 2012 the National Grid produced a solar
    briefing note for the government which is still available online. In
    that note they imagine a system that has 22 GW of solar power attached
    to the grid. They demonstrate their concerns based on a sunny summer day
    when demand is low. The sun rises at 5 o’clock when little or no
    synchronous plant other than nuclear generation will be on line and at
    midday, solar is 60 per cent of all generation. The Grid’s engineers
    then considered that situation “difficult to manage” and concluded that >> wind+solar power must never exceed 60 per cent of generation.

    We now have 17.7 GW of grid-connected solar farms to which we must add
    all rooftop solar installations. At midday on Tuesday according to
    Gridwatch the UK’s asynchronous, no-inertia generation was at 66 per
    cent of total generation.

    In 2014 National Grid produced a System Operability Framework document.
    Their objective was to outline how future scenarios of generation mixes
    would impact upon protection services for the grid. As more and more
    renewable generators are brought on-line, the difficulties of managing
    the grid have become more and more onerous. For example, one service
    titled “primary response” in 1990 called for selected generation plants >> to increase generation within 10 seconds after a fault is detected: by
    1,200 MW in winter and 1,500 MW in summer. In 2024 these increases are
    required in 1.2 seconds!

    After nearly 50 years of operation, Dinorwig Power Station is currently
    shut down for major repairs and there has been no information on when it
    will re-open. Over the next five years all of our nuclear stations, bar
    Sizewell, will be closed. Over the same period our combined cycle gas
    generator fleet will halve from 30 GW to 15 GW. (It takes 5 years to
    build a new CCGT even using an existing site. The new ones are 66 per
    cent efficient and cost less than £1 billion to build a 1 GW plant – one >> third the cost of an offshore windmill.)

    We will lose huge amounts of grid inertia. Low-inertia operation will
    become routine. It is hard to imagine that we won’t start to suffer
    complete national blackouts like the Iberian one.

    One last piece of doom: the recovery of Spain’s grid in just one day is
    impressive. This speed is certainly due to the assistance of a large,
    stable grid reconnecting into the Iberian system thus allowing recovery
    in a series of stable steps as each grid area is recovered. We will not
    have that facility in the UK with our asynchronous interconnectors.

    Dr Capell Aris PhD spent his career in the electricity generation
    sector. He is a Fellow of the Institute of Engineering and Technology

    https://www.msn.com/en-us/money/companies/a-power-engineer-on-the-iberian-grid-collapse-it-makes-me-very-afraid-for-britain/ar-AA
    1DZjGo

    DC is already used for long distances power transfer.

    I was taught (in electronics classes) that the problem with DC is that
    it suffers significant power loss over distances due to the resistance
    in copper, aluminum or steel wire. OHM's law applies to wire as anyone
    who studies electronics knows. Alternating current overcame the
    resistance in wire due to the "skin effect" where the collapsing
    magnetic field around the wire during the negative phase of alternating
    current cycle replenishes the flow of electrons in the wire.

    There were electric street cars (trolley cars) that went from City Park
    to College Avenue in Fort Collins, CO in the 20th century (and may still
    be running) that had DC motors. The voltage at the source of the power
    for the street cars was 800 volts DC at City Park. The voltage two
    miles away at the end of the line on College Avenue was reduced by 200
    volts due to the resistance in the copper wire to 500 volts. Unless a
    way has been devised to overcome OHM's law, I don't see how high voltage
    can be transmitted across Europe using direct current. Perhaps you can
    explain.


    These days with electronics it is easy to convert that to AC locally, synchronized if need be.
    But you could drop the 50 Hz or 60 Hz net altogether and do local conversion to AC, and / or to a lower DC voltage
    even for for each household.
    Using high frequency switching converters reduces the amount of huge transformers.
    Local batteries and solar cells... I have a 250 Ah battery pack and solar cells and a 2 kW DC to AC pure sinewave inverter here.
    Will at least run the fridge and microwave if the net goes down.




    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Jan Panteltje@21:1/5 to All on Sat May 3 04:57:07 2025
    XPost: alt.survival, misc.survivalism

    On 5/1/2025 11:34 PM, Jan Panteltje wrote:
    Story by Capell Aris The Telegraph

    Last Monday, the Iberian grid suffered a disturbance in the south-west
    at 12:33. In 3.5 seconds this worsened and the interconnection to France >>> disconnected. All renewable generation then went off-line, followed by
    disconnection of all rotating generation plant. The Iberian blackout was >>> complete within a few seconds.

    At the time the grid was producing 28.4 GW of power, of which 79 per
    cent was solar and wind. This was a problematic situation as solar and
    wind plants have another, not widely known, downside – one quite apart >>>from their intermittency and expense.

    This is the fact that they do not supply any inertia to the grid.
    Thermal powerplants – coal, gas, nuclear, for example – drive large
    spinning generators which are directly, synchronously connected to the
    grid. If there are changes which cause a difference between demand and
    supply, the generators will start to spin faster or slower: but their
    inertia resists this process, meaning that the frequency of the
    alternating current in the grid changes only slowly. There is time for
    the grid managers to act, matching supply to demand and keeping the grid >>> frequency within limits.

    This is vital because all grids must supply power at a steady frequency
    so that electrical appliances work properly and safely. Deviations from
    the standard grid frequency can cause damage to equipment and other
    problems: in practice what happens quite rapidly when frequency changes
    significantly is that grid machinery trips out to prevent these issues
    and grids go down.

    When a grid has very little inertia in it – as with the Iberian one on >>> Monday – a problem which a high-inertia grid would easily resist can
    cause a blackout within seconds. Lack of inertia was almost certainly
    the primary cause of the Iberian blackout, as Matt Oliver has opined in
    these pages. A grid with more inertia would not have collapsed as
    quickly, and its operators would have had time to keep it up and running. >>>
    Restoration of supplies was completed by early Tuesday morning, based on >>> reconnection to France, which facilitated progressive area reconnections >>> across Spain and Portugal.

    Iberia is part of the Continental Europe Synchronous Area which
    stretches to 32 countries. It is interconnected as a phase-locked, 50 Hz >>> grid with a generation capacity of 700 GW. To improve the stability of
    this grid, the EU aim is that all partners will extract 10 per cent of
    their power consumption from synchronous interconnectors – ones which
    transmit grid inertia – helping to make the whole system more resilient. >>> France is at 10 per cent, but peninsula grids and those at the
    geographical fringe are the least interconnected. Spain has just 2 per
    cent from synchronous interconnectors.

    But there are places where things are worse. The UK and Ireland are
    island grids. They do have undersea power interconnectors to Europe but
    these are non-synchronous DC links and transmit no grid inertia. There’s >>> little prospect that this will change.

    Both the Irish and UK grid system operators had developed an array of
    grid protection services that can control grid frequency, loss of load
    or generation protection, grid phase angle and recovering from grid
    outages. Neither country has, to date, ever experienced a total system
    failure, even during WWII.

    In 1974 construction started on Dinorwig Power Station. It is a pumped
    storage generation plant designed specifically for the provision of all
    the UK’s grid protection services. Dinorwig can make huge changes to its >>> output in a matter of seconds, compensating for sudden events. Operation >>> began in 1984. In 1990 all the UK’s generating stations could provide
    inertia.

    Nowadays, 55 per cent of our generation mix (wind, solar, DC imports)
    cannot supply inertia to the grid. Are we approaching a system that
    compares with Spain and Portugal on Monday?

    It certainly looks that way. In 2012 the National Grid produced a solar
    briefing note for the government which is still available online. In
    that note they imagine a system that has 22 GW of solar power attached
    to the grid. They demonstrate their concerns based on a sunny summer day >>> when demand is low. The sun rises at 5 o’clock when little or no
    synchronous plant other than nuclear generation will be on line and at
    midday, solar is 60 per cent of all generation. The Grid’s engineers
    then considered that situation “difficult to manage” and concluded that >>> wind+solar power must never exceed 60 per cent of generation.

    We now have 17.7 GW of grid-connected solar farms to which we must add
    all rooftop solar installations. At midday on Tuesday according to
    Gridwatch the UK’s asynchronous, no-inertia generation was at 66 per
    cent of total generation.

    In 2014 National Grid produced a System Operability Framework document.
    Their objective was to outline how future scenarios of generation mixes
    would impact upon protection services for the grid. As more and more
    renewable generators are brought on-line, the difficulties of managing
    the grid have become more and more onerous. For example, one service
    titled “primary response” in 1990 called for selected generation plants >>> to increase generation within 10 seconds after a fault is detected: by
    1,200 MW in winter and 1,500 MW in summer. In 2024 these increases are
    required in 1.2 seconds!

    After nearly 50 years of operation, Dinorwig Power Station is currently
    shut down for major repairs and there has been no information on when it >>> will re-open. Over the next five years all of our nuclear stations, bar
    Sizewell, will be closed. Over the same period our combined cycle gas
    generator fleet will halve from 30 GW to 15 GW. (It takes 5 years to
    build a new CCGT even using an existing site. The new ones are 66 per
    cent efficient and cost less than £1 billion to build a 1 GW plant – one >>> third the cost of an offshore windmill.)

    We will lose huge amounts of grid inertia. Low-inertia operation will
    become routine. It is hard to imagine that we won’t start to suffer
    complete national blackouts like the Iberian one.

    One last piece of doom: the recovery of Spain’s grid in just one day is >>> impressive. This speed is certainly due to the assistance of a large,
    stable grid reconnecting into the Iberian system thus allowing recovery
    in a series of stable steps as each grid area is recovered. We will not
    have that facility in the UK with our asynchronous interconnectors.

    Dr Capell Aris PhD spent his career in the electricity generation
    sector. He is a Fellow of the Institute of Engineering and Technology


    https://www.msn.com/en-us/money/companies/a-power-engineer-on-the-iberian-grid-collapse-it-makes-me-very-afraid-for-britain/ar-AA
    1DZjGo

    DC is already used for long distances power transfer.

    I was taught (in electronics classes) that the problem with DC is that
    it suffers significant power loss over distances due to the resistance
    in copper, aluminum or steel wire.

    That is why long distance DC uses very high voltages, so higher voltage lower current, less Ohmic losses.


    OHM's law applies to wire as anyone
    who studies electronics knows. Alternating current overcame the
    resistance in wire due to the "skin effect" where the collapsing
    magnetic field around the wire during the negative phase of alternating >current cycle replenishes the flow of electrons in the wire.

    That is not corrent
    One problem with AC is _inductance_ of the wire.
    Skin effect only works for AC and causes the current to flow mainly on the outside of the inductor / cable,
    requiring thicker (or maybe hollow?) cables.
    https://en.wikipedia.org/wiki/Skin_effect




    to College Avenue in Fort Collins, CO in the 20th century (and may still
    be running) that had DC motors. The voltage at the source of the power
    for the street cars was 800 volts DC at City Park. The voltage two
    miles away at the end of the line on College Avenue was reduced by 200
    volts due to the resistance in the copper wire to 500 volts. Unless a
    way has been devised to overcome OHM's law, I don't see how high voltage
    can be transmitted across Europe using direct current. Perhaps you can >explain.

    You are confused, or your teacher were:
    https://en.wikipedia.org/wiki/High-voltage_direct_current

    There are high voltage long distance links in the US too.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Dark Brandon@21:1/5 to Jan Panteltje on Sat May 3 09:15:42 2025
    XPost: alt.survival, misc.survivalism

    On 5/2/2025 10:57 PM, Jan Panteltje wrote:
    On 5/1/2025 11:34 PM, Jan Panteltje wrote:
    Story by Capell Aris The Telegraph

    Last Monday, the Iberian grid suffered a disturbance in the south-west >>>> at 12:33. In 3.5 seconds this worsened and the interconnection to France >>>> disconnected. All renewable generation then went off-line, followed by >>>> disconnection of all rotating generation plant. The Iberian blackout was >>>> complete within a few seconds.

    At the time the grid was producing 28.4 GW of power, of which 79 per
    cent was solar and wind. This was a problematic situation as solar and >>>> wind plants have another, not widely known, downside – one quite apart >>> >from their intermittency and expense.

    This is the fact that they do not supply any inertia to the grid.
    Thermal powerplants – coal, gas, nuclear, for example – drive large >>>> spinning generators which are directly, synchronously connected to the >>>> grid. If there are changes which cause a difference between demand and >>>> supply, the generators will start to spin faster or slower: but their
    inertia resists this process, meaning that the frequency of the
    alternating current in the grid changes only slowly. There is time for >>>> the grid managers to act, matching supply to demand and keeping the grid >>>> frequency within limits.

    This is vital because all grids must supply power at a steady frequency >>>> so that electrical appliances work properly and safely. Deviations from >>>> the standard grid frequency can cause damage to equipment and other
    problems: in practice what happens quite rapidly when frequency changes >>>> significantly is that grid machinery trips out to prevent these issues >>>> and grids go down.

    When a grid has very little inertia in it – as with the Iberian one on >>>> Monday – a problem which a high-inertia grid would easily resist can >>>> cause a blackout within seconds. Lack of inertia was almost certainly
    the primary cause of the Iberian blackout, as Matt Oliver has opined in >>>> these pages. A grid with more inertia would not have collapsed as
    quickly, and its operators would have had time to keep it up and running. >>>>
    Restoration of supplies was completed by early Tuesday morning, based on >>>> reconnection to France, which facilitated progressive area reconnections >>>> across Spain and Portugal.

    Iberia is part of the Continental Europe Synchronous Area which
    stretches to 32 countries. It is interconnected as a phase-locked, 50 Hz >>>> grid with a generation capacity of 700 GW. To improve the stability of >>>> this grid, the EU aim is that all partners will extract 10 per cent of >>>> their power consumption from synchronous interconnectors – ones which >>>> transmit grid inertia – helping to make the whole system more resilient. >>>> France is at 10 per cent, but peninsula grids and those at the
    geographical fringe are the least interconnected. Spain has just 2 per >>>> cent from synchronous interconnectors.

    But there are places where things are worse. The UK and Ireland are
    island grids. They do have undersea power interconnectors to Europe but >>>> these are non-synchronous DC links and transmit no grid inertia. There’s >>>> little prospect that this will change.

    Both the Irish and UK grid system operators had developed an array of
    grid protection services that can control grid frequency, loss of load >>>> or generation protection, grid phase angle and recovering from grid
    outages. Neither country has, to date, ever experienced a total system >>>> failure, even during WWII.

    In 1974 construction started on Dinorwig Power Station. It is a pumped >>>> storage generation plant designed specifically for the provision of all >>>> the UK’s grid protection services. Dinorwig can make huge changes to its >>>> output in a matter of seconds, compensating for sudden events. Operation >>>> began in 1984. In 1990 all the UK’s generating stations could provide >>>> inertia.

    Nowadays, 55 per cent of our generation mix (wind, solar, DC imports)
    cannot supply inertia to the grid. Are we approaching a system that
    compares with Spain and Portugal on Monday?

    It certainly looks that way. In 2012 the National Grid produced a solar >>>> briefing note for the government which is still available online. In
    that note they imagine a system that has 22 GW of solar power attached >>>> to the grid. They demonstrate their concerns based on a sunny summer day >>>> when demand is low. The sun rises at 5 o’clock when little or no
    synchronous plant other than nuclear generation will be on line and at >>>> midday, solar is 60 per cent of all generation. The Grid’s engineers >>>> then considered that situation “difficult to manage” and concluded that
    wind+solar power must never exceed 60 per cent of generation.

    We now have 17.7 GW of grid-connected solar farms to which we must add >>>> all rooftop solar installations. At midday on Tuesday according to
    Gridwatch the UK’s asynchronous, no-inertia generation was at 66 per >>>> cent of total generation.

    In 2014 National Grid produced a System Operability Framework document. >>>> Their objective was to outline how future scenarios of generation mixes >>>> would impact upon protection services for the grid. As more and more
    renewable generators are brought on-line, the difficulties of managing >>>> the grid have become more and more onerous. For example, one service
    titled “primary response” in 1990 called for selected generation plants
    to increase generation within 10 seconds after a fault is detected: by >>>> 1,200 MW in winter and 1,500 MW in summer. In 2024 these increases are >>>> required in 1.2 seconds!

    After nearly 50 years of operation, Dinorwig Power Station is currently >>>> shut down for major repairs and there has been no information on when it >>>> will re-open. Over the next five years all of our nuclear stations, bar >>>> Sizewell, will be closed. Over the same period our combined cycle gas
    generator fleet will halve from 30 GW to 15 GW. (It takes 5 years to
    build a new CCGT even using an existing site. The new ones are 66 per
    cent efficient and cost less than £1 billion to build a 1 GW plant – one
    third the cost of an offshore windmill.)

    We will lose huge amounts of grid inertia. Low-inertia operation will
    become routine. It is hard to imagine that we won’t start to suffer
    complete national blackouts like the Iberian one.

    One last piece of doom: the recovery of Spain’s grid in just one day is >>>> impressive. This speed is certainly due to the assistance of a large,
    stable grid reconnecting into the Iberian system thus allowing recovery >>>> in a series of stable steps as each grid area is recovered. We will not >>>> have that facility in the UK with our asynchronous interconnectors.

    Dr Capell Aris PhD spent his career in the electricity generation
    sector. He is a Fellow of the Institute of Engineering and Technology


    https://www.msn.com/en-us/money/companies/a-power-engineer-on-the-iberian-grid-collapse-it-makes-me-very-afraid-for-britain/ar-AA
    1DZjGo

    DC is already used for long distances power transfer.

    I was taught (in electronics classes) that the problem with DC is that
    it suffers significant power loss over distances due to the resistance
    in copper, aluminum or steel wire.

    That is why long distance DC uses very high voltages, so higher voltage lower current, less Ohmic losses.


    OHM's law applies to wire as anyone
    who studies electronics knows. Alternating current overcame the
    resistance in wire due to the "skin effect" where the collapsing
    magnetic field around the wire during the negative phase of alternating
    current cycle replenishes the flow of electrons in the wire.

    That is not corrent
    One problem with AC is _inductance_ of the wire.
    Skin effect only works for AC and causes the current to flow mainly on the outside of the inductor / cable,
    requiring thicker (or maybe hollow?) cables.
    https://en.wikipedia.org/wiki/Skin_effect




    to College Avenue in Fort Collins, CO in the 20th century (and may still
    be running) that had DC motors. The voltage at the source of the power
    for the street cars was 800 volts DC at City Park. The voltage two
    miles away at the end of the line on College Avenue was reduced by 200
    volts due to the resistance in the copper wire to 500 volts. Unless a
    way has been devised to overcome OHM's law, I don't see how high voltage
    can be transmitted across Europe using direct current. Perhaps you can
    explain.

    You are confused, or your teacher were:
    https://en.wikipedia.org/wiki/High-voltage_direct_current

    There are high voltage long distance links in the US too.


    I stand corrected. I'm not sure, in retrospect, if I was given
    misinformation at the community college I attended back in the '80s or
    if I misremember what they were teaching per the topic under discussion.
    Either way, thank you for correcting my lack of knowledge and setting
    the record straight.
    --
    AOC, when asked how her multi-trillion dollar Green New Deal could be
    funded, replied, "Taxes can pay some, and government can pay the rest".

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Jan Panteltje@21:1/5 to All on Sun May 4 14:02:38 2025
    XPost: alt.survival, misc.survivalism

    I stand corrected. I'm not sure, in retrospect, if I was given >misinformation at the community college I attended back in the '80s or
    if I misremember what they were teaching per the topic under discussion.
    Either way, thank you for correcting my lack of knowledge and setting
    the record straight.


    No problem.
    It is an interesting subject.
    Some years ago here in the Netherlands the mains (50 Hz) frequency got out of sync with other parts of Europe
    and my microwave clock ran a minute or so out of time.
    They fixed it.

    Time these days.. I have a Casio radio watch that gets the time from the DCF77 radio station reference..
    Desktop alarm clock also runs on DCF77.
    https://en.wikipedia.org/wiki/DCF77
    And I have several GPS modules, the computer on my desk uses GPS time.
    So time keeping by means of mains frequency is still used, but less reliable and needs a manual clock reset after a mains interruption.
    Smartphones get their time from the local stations, those will be out after a while if no power.
    I think GPS time is most reliable, those modules only cost a few dollars
    and require a few lines of code to implement on a computer, been there done that:
    https://panteltje.nl/panteltje/xgpspc/index.html
    electronics is fun.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)